*WARNING- NO MEMBERS LOADED FOR A WIND LOAD GENERATION.

*WARNING- NO MEMBERS LOADED FOR A WIND LOAD GENERATION

I tried finding anything regarding this warning in the output viewer but found nothing. What could cause this warning to show up? I reviewed the applied wind load and everything looks normal. I have this warning repeated 4 times at different lines of the input.

File attached.

Thanks.

RESIDENTIAL BUILDING 23.std

Parents
  • Dear user,

    there are 2 observations for your structure.

    1. Your structure contains duplicate beams. You can check the same under Utilities>Beam Tools> Duplicate Beams, as shown below. Please merge those beams .

    2. The Y range provided for wind load along X direction for the top portion of the structure is not correct. Please check line # 7146,7151,7161,7169. Please check the co-ordinates for Y range and change  

    YR 52.8 55.8

    to

    YR 51.73 54.73.

    You may also change the Y range for others as the max height is 54.73m instead of 55.8m. This will solve your issue.

    Cheers!!

    Thanks & Regards,
    Abhisek Mandal
    Global Technical Support

Reply
  • Dear user,

    there are 2 observations for your structure.

    1. Your structure contains duplicate beams. You can check the same under Utilities>Beam Tools> Duplicate Beams, as shown below. Please merge those beams .

    2. The Y range provided for wind load along X direction for the top portion of the structure is not correct. Please check line # 7146,7151,7161,7169. Please check the co-ordinates for Y range and change  

    YR 52.8 55.8

    to

    YR 51.73 54.73.

    You may also change the Y range for others as the max height is 54.73m instead of 55.8m. This will solve your issue.

    Cheers!!

    Thanks & Regards,
    Abhisek Mandal
    Global Technical Support