ERROR: NO REFERENCE LOAD CASE OF TYPE MASS/GRIVITY/DEAD/LIVE IS DEFINED FOR MASS MODELING. CENTRE OF MASS CALCULATION IS NOT POSSIBLE.

I get this message:

ERROR: NO REFERENCE LOAD CASE OF TYPE MASS/GRIVITY/DEAD/LIVE IS DEFINED FOR MASS MODELING.

     CENTRE OF MASS CALCULATION IS NOT POSSIBLE.

Can you please help me?

RB-XX 3er Milenium Torre 1 Analisis Completo 1 Nov 15.std

Parents
  • You need to provide "Type" for reference load used in the file. You have provided "None" as type and hence program is unable to calculate centre of mass. Please change it to mass or gravity to overcome this issue.

    /resized-image/__size/1040x731/__key/communityserver-discussions-components-files/5932/pastedimage1542947260770v1.png

    Also you have used "load case#2" two times. please change the first one to #1.

    Thanks & Regards,
    Abhisek Mandal
    Global Technical Support

  • Could you help me this? Thank you.

    STAAD SPACE
    START JOB INFORMATION
    ENGINEER DATE 16-Jan-23
    END JOB INFORMATION
    INPUT WIDTH 79
    UNIT METER KN
    JOINT COORDINATES
    1 0 0 0; 2 3.1 0 0; 3 6.2 0 0; 4 0 0 3.05; 5 6.2 0 3.05; 6 0 0 3.05;
    7 0 0 6.75; 8 6.2 0 6.75; 9 0 0 10.45; 10 3.1 0 11.45; 11 6.2 0 11.45;
    12 0 0 15; 13 3.1 0 15; 14 6.2 0 15; 15 0 3.1 0; 16 3.1 3.1 0; 17 6.2 3.1 0;
    18 0 3.1 3.05; 19 6.2 3.1 3.05; 20 0 3.1 3.05; 21 0 3.1 6.75; 22 6.2 3.1 6.75;
    23 0 3.1 10.45; 24 3.1 3.1 11.45; 25 6.2 3.1 11.45; 26 0 3.1 15; 27 3.1 3.1 15;
    28 6.2 3.1 15; 29 3.1 3.1 3.05; 30 3.1 3.1 6.75; 31 3.1 3.1 10.45;
    32 0 3.1 11.45; 33 0 6.1 0; 34 3.1 6.1 0; 35 6.2 6.1 0; 36 0 6.1 3.05;
    37 6.2 6.1 3.05; 38 0 6.1 3.05; 39 0 6.1 6.75; 40 6.2 6.1 6.75; 41 0 6.1 10.45;
    42 3.1 6.1 11.45; 43 6.2 6.1 11.45; 44 0 6.1 15; 45 3.1 6.1 15; 46 6.2 6.1 15;
    47 3.1 6.1 3.05; 48 3.1 6.1 6.75; 49 0 6.1 11.45; 50 -0.6 3.1 0;
    51 -0.6 3.1 3.05; 52 -0.6 3.1 6.75; 53 -0.6 3.1 10.45; 54 -0.6 3.1 13.1;
    55 0 3.1 13.1; 56 0.8 3.1 15; 57 3.1 3.1 15.6; 58 6.2 3.1 15.6;
    59 0.8 3.1 15.6; 60 -0.6 6.1 0; 61 -0.6 6.1 3.05; 62 -0.6 6.1 6.75;
    63 -0.6 6.1 10.45; 64 3.1 6.1 15.6; 65 6.2 6.1 15.6; 66 -0.6 6.1 15.6;
    MEMBER INCIDENCES
    1 1 15; 2 2 16; 3 3 17; 4 4 18; 5 5 19; 6 7 21; 7 8 22; 8 9 23; 9 10 24;
    10 11 25; 11 12 26; 12 13 27; 13 14 28; 14 15 18; 15 18 21; 16 21 23; 17 23 32;
    18 16 29; 19 24 27; 20 17 19; 21 19 22; 22 22 25; 23 25 28; 24 15 16; 25 16 17;
    26 29 30; 27 30 31; 28 18 29; 29 29 19; 30 21 30; 31 30 22; 32 31 24; 33 23 31;
    34 32 55; 35 32 24; 36 24 25; 37 26 56; 38 27 28; 39 15 33; 40 16 34; 41 17 35;
    42 18 36; 43 19 37; 44 21 39; 45 22 40; 46 23 41; 47 24 42; 48 25 43; 49 26 44;
    50 27 45; 51 28 46; 52 33 36; 53 36 39; 54 39 41; 55 41 49; 56 34 47; 57 42 45;
    58 35 37; 59 37 40; 60 40 43; 61 43 46; 62 33 34; 63 34 35; 64 47 48; 65 36 47;
    66 47 37; 67 39 48; 68 48 40; 69 49 44; 70 49 42; 71 42 43; 72 44 45; 73 45 46;
    74 48 42; 75 50 51; 76 51 52; 77 52 53; 78 53 54; 79 55 26; 80 50 15; 81 51 18;
    82 52 21; 83 53 23; 84 54 55; 85 56 27; 86 59 57; 87 57 58; 88 56 59; 89 27 57;
    90 28 58; 91 60 61; 92 61 62; 93 62 63; 94 64 65; 95 63 66; 96 66 64; 97 60 33;
    98 61 36; 99 62 39; 100 63 41; 101 45 64; 102 46 65;
    START GROUP DEFINITION
    FLOOR
    _FLR 14 TO 16 18 TO 38 79 85
    _SDL 14 TO 16 18 TO 38 79 85
    _RD 52 TO 74
    _RDSDL 52 TO 74
    _ONEFLR 17 32 33 35
    _ONESDL 17 32 33 35
    _ROOM 14 15 18 TO 21 23 TO 26 28 TO 31 34 TO 38 79 85
    _BALCON 16 27 30 33
    _AS_ST 22 27 31 32 36
    _ONEROOM 17 32 33 35
    _STRD 54 55 60 67 68 70 71 74
    _BALCONRD 52 53 56 58 59 61 TO 73
    MEMBER
    _CHB 14 TO 17 20 TO 25 34 37 38 54 55 60 67 68 70 71 79 85
    _CHBINT 28 TO 31 33 35 36
    END GROUP DEFINITION
    DEFINE MATERIAL START
    ISOTROPIC CONCRETE
    E 2.17185e+007
    POISSON 0.17
    DENSITY 23.5616
    ALPHA 1e-005
    DAMP 0.05
    TYPE CONCRETE
    STRENGTH FCU 27579
    ISOTROPIC 20.7MPA
    E 2.1384e+007
    POISSON 0.17
    DENSITY 24
    ALPHA 1e-005
    DAMP 0.05
    G 9.28139e+006
    TYPE CONCRETE
    STRENGTH FCU 20700
    END DEFINE MATERIAL
    MEMBER PROPERTY AMERICAN
    1 TO 13 39 TO 51 PRIS YD 0.3 ZD 0.3
    14 TO 38 52 TO 74 79 85 PRIS YD 0.35 ZD 0.2
    MEMBER PROPERTY AMERICAN
    75 TO 78 80 TO 84 86 TO 102 PRIS YD 0.3 ZD 0.2
    CONSTANTS
    MATERIAL 20.7MPA ALL
    MEMBER RELEASE
    35 70 75 81 TO 83 86 88 96 TO 100 START MZ
    33 78 84 87 89 94 101 END MZ
    MEMBER CRACKED
    1 TO 13 39 TO 51 REDUCTION RIY 0.700000 RIZ 0.700000
    14 TO 38 52 TO 102 REDUCTION RIY 0.350000 RIZ 0.350000
    FLOOR DIAPHRAGM
    DIA 1 TYPE RIG HEI 3.1 JOINT 15 TO 32 50 TO 59
    DIA 2 TYPE RIG HEI 6.1 JOINT 33 TO 49 60 TO 66
    SUPPORTS
    1 TO 14 FIXED
    DEFINE REFERENCE LOADS
    LOAD R1 LOADTYPE Mass TITLE DL
    SELFWEIGHT Y 1 LIST ALL
    FLOOR LOAD
    _FLR FLOAD 2.4 GY
    _SDL FLOAD 5 GY
    _RD FLOAD 2.4 GY
    _RDSDL FLOAD 5 GY
    ONEWAY LOAD
    _ONEFLR ONE 2.4 GY
    _ONESDL ONE 5 GY
    MEMBER LOAD
    14 TO 17 20 TO 25 34 37 38 54 55 60 67 68 70 71 79 85 UNI GY 10
    28 TO 31 33 35 36 UNI GY 9.6
    END DEFINE REFERENCE LOADS
    DEFINE UBC LOAD
    ZONE 0.4 I 1.5 RWX 8.5 RWZ 8.5 STYP 4 CT 0.0731 PX 0.284 PZ 0.284 NA 1 NV 1
    LOAD 1 LOADTYPE Seismic TITLE EQ +X +E
    UBC LOAD X 1 DEC 1 ACC 0.05
    LOAD 2 LOADTYPE Seismic TITLE EQ +X -E
    UBC LOAD X 1 DEC 1 ACC -0.05
    LOAD 3 LOADTYPE Seismic TITLE EQ -X +E
    UBC LOAD X -1 DEC 1 ACC 0.05
    LOAD 4 LOADTYPE Seismic TITLE EQ -X -E
    UBC LOAD X -1 DEC 1 ACC -0.05
    LOAD 5 LOADTYPE Seismic TITLE EQ +Z +E
    UBC LOAD Z 1 DEC 1 ACC 0.05
    LOAD 6 LOADTYPE Seismic TITLE EQ +Z -E
    UBC LOAD Z 1 DEC 1 ACC -0.05
    LOAD 7 LOADTYPE Seismic TITLE EQ -Z +E
    UBC LOAD Z -1 DEC 1 ACC 0.05
    LOAD 8 LOADTYPE Seismic TITLE EQ -Z -E
    UBC LOAD Z -1 DEC 1 ACC -0.05
    LOAD 9 LOADTYPE Dead TITLE DL
    REFERENCE LOAD
    R1 -1.0
    LOAD 10 LOADTYPE Live TITLE LL
    FLOOR LOAD
    _ROOM FLOAD -2.4 GY
    ONEWAY LOAD
    _ONEROOM ONE -2.4 GY
    FLOOR LOAD
    _BALCON FLOAD -2.9 GY
    _AS_ST FLOAD -4.8 GY
    LOAD 11 LOADTYPE Roof Live TITLE LLR
    FLOOR LOAD
    _STRD FLOAD -4.8 GY
    _BALCONRD FLOAD -2.9 GY
    PERFORM ANALYSIS
    FINISH

Reply
  • Could you help me this? Thank you.

    STAAD SPACE
    START JOB INFORMATION
    ENGINEER DATE 16-Jan-23
    END JOB INFORMATION
    INPUT WIDTH 79
    UNIT METER KN
    JOINT COORDINATES
    1 0 0 0; 2 3.1 0 0; 3 6.2 0 0; 4 0 0 3.05; 5 6.2 0 3.05; 6 0 0 3.05;
    7 0 0 6.75; 8 6.2 0 6.75; 9 0 0 10.45; 10 3.1 0 11.45; 11 6.2 0 11.45;
    12 0 0 15; 13 3.1 0 15; 14 6.2 0 15; 15 0 3.1 0; 16 3.1 3.1 0; 17 6.2 3.1 0;
    18 0 3.1 3.05; 19 6.2 3.1 3.05; 20 0 3.1 3.05; 21 0 3.1 6.75; 22 6.2 3.1 6.75;
    23 0 3.1 10.45; 24 3.1 3.1 11.45; 25 6.2 3.1 11.45; 26 0 3.1 15; 27 3.1 3.1 15;
    28 6.2 3.1 15; 29 3.1 3.1 3.05; 30 3.1 3.1 6.75; 31 3.1 3.1 10.45;
    32 0 3.1 11.45; 33 0 6.1 0; 34 3.1 6.1 0; 35 6.2 6.1 0; 36 0 6.1 3.05;
    37 6.2 6.1 3.05; 38 0 6.1 3.05; 39 0 6.1 6.75; 40 6.2 6.1 6.75; 41 0 6.1 10.45;
    42 3.1 6.1 11.45; 43 6.2 6.1 11.45; 44 0 6.1 15; 45 3.1 6.1 15; 46 6.2 6.1 15;
    47 3.1 6.1 3.05; 48 3.1 6.1 6.75; 49 0 6.1 11.45; 50 -0.6 3.1 0;
    51 -0.6 3.1 3.05; 52 -0.6 3.1 6.75; 53 -0.6 3.1 10.45; 54 -0.6 3.1 13.1;
    55 0 3.1 13.1; 56 0.8 3.1 15; 57 3.1 3.1 15.6; 58 6.2 3.1 15.6;
    59 0.8 3.1 15.6; 60 -0.6 6.1 0; 61 -0.6 6.1 3.05; 62 -0.6 6.1 6.75;
    63 -0.6 6.1 10.45; 64 3.1 6.1 15.6; 65 6.2 6.1 15.6; 66 -0.6 6.1 15.6;
    MEMBER INCIDENCES
    1 1 15; 2 2 16; 3 3 17; 4 4 18; 5 5 19; 6 7 21; 7 8 22; 8 9 23; 9 10 24;
    10 11 25; 11 12 26; 12 13 27; 13 14 28; 14 15 18; 15 18 21; 16 21 23; 17 23 32;
    18 16 29; 19 24 27; 20 17 19; 21 19 22; 22 22 25; 23 25 28; 24 15 16; 25 16 17;
    26 29 30; 27 30 31; 28 18 29; 29 29 19; 30 21 30; 31 30 22; 32 31 24; 33 23 31;
    34 32 55; 35 32 24; 36 24 25; 37 26 56; 38 27 28; 39 15 33; 40 16 34; 41 17 35;
    42 18 36; 43 19 37; 44 21 39; 45 22 40; 46 23 41; 47 24 42; 48 25 43; 49 26 44;
    50 27 45; 51 28 46; 52 33 36; 53 36 39; 54 39 41; 55 41 49; 56 34 47; 57 42 45;
    58 35 37; 59 37 40; 60 40 43; 61 43 46; 62 33 34; 63 34 35; 64 47 48; 65 36 47;
    66 47 37; 67 39 48; 68 48 40; 69 49 44; 70 49 42; 71 42 43; 72 44 45; 73 45 46;
    74 48 42; 75 50 51; 76 51 52; 77 52 53; 78 53 54; 79 55 26; 80 50 15; 81 51 18;
    82 52 21; 83 53 23; 84 54 55; 85 56 27; 86 59 57; 87 57 58; 88 56 59; 89 27 57;
    90 28 58; 91 60 61; 92 61 62; 93 62 63; 94 64 65; 95 63 66; 96 66 64; 97 60 33;
    98 61 36; 99 62 39; 100 63 41; 101 45 64; 102 46 65;
    START GROUP DEFINITION
    FLOOR
    _FLR 14 TO 16 18 TO 38 79 85
    _SDL 14 TO 16 18 TO 38 79 85
    _RD 52 TO 74
    _RDSDL 52 TO 74
    _ONEFLR 17 32 33 35
    _ONESDL 17 32 33 35
    _ROOM 14 15 18 TO 21 23 TO 26 28 TO 31 34 TO 38 79 85
    _BALCON 16 27 30 33
    _AS_ST 22 27 31 32 36
    _ONEROOM 17 32 33 35
    _STRD 54 55 60 67 68 70 71 74
    _BALCONRD 52 53 56 58 59 61 TO 73
    MEMBER
    _CHB 14 TO 17 20 TO 25 34 37 38 54 55 60 67 68 70 71 79 85
    _CHBINT 28 TO 31 33 35 36
    END GROUP DEFINITION
    DEFINE MATERIAL START
    ISOTROPIC CONCRETE
    E 2.17185e+007
    POISSON 0.17
    DENSITY 23.5616
    ALPHA 1e-005
    DAMP 0.05
    TYPE CONCRETE
    STRENGTH FCU 27579
    ISOTROPIC 20.7MPA
    E 2.1384e+007
    POISSON 0.17
    DENSITY 24
    ALPHA 1e-005
    DAMP 0.05
    G 9.28139e+006
    TYPE CONCRETE
    STRENGTH FCU 20700
    END DEFINE MATERIAL
    MEMBER PROPERTY AMERICAN
    1 TO 13 39 TO 51 PRIS YD 0.3 ZD 0.3
    14 TO 38 52 TO 74 79 85 PRIS YD 0.35 ZD 0.2
    MEMBER PROPERTY AMERICAN
    75 TO 78 80 TO 84 86 TO 102 PRIS YD 0.3 ZD 0.2
    CONSTANTS
    MATERIAL 20.7MPA ALL
    MEMBER RELEASE
    35 70 75 81 TO 83 86 88 96 TO 100 START MZ
    33 78 84 87 89 94 101 END MZ
    MEMBER CRACKED
    1 TO 13 39 TO 51 REDUCTION RIY 0.700000 RIZ 0.700000
    14 TO 38 52 TO 102 REDUCTION RIY 0.350000 RIZ 0.350000
    FLOOR DIAPHRAGM
    DIA 1 TYPE RIG HEI 3.1 JOINT 15 TO 32 50 TO 59
    DIA 2 TYPE RIG HEI 6.1 JOINT 33 TO 49 60 TO 66
    SUPPORTS
    1 TO 14 FIXED
    DEFINE REFERENCE LOADS
    LOAD R1 LOADTYPE Mass TITLE DL
    SELFWEIGHT Y 1 LIST ALL
    FLOOR LOAD
    _FLR FLOAD 2.4 GY
    _SDL FLOAD 5 GY
    _RD FLOAD 2.4 GY
    _RDSDL FLOAD 5 GY
    ONEWAY LOAD
    _ONEFLR ONE 2.4 GY
    _ONESDL ONE 5 GY
    MEMBER LOAD
    14 TO 17 20 TO 25 34 37 38 54 55 60 67 68 70 71 79 85 UNI GY 10
    28 TO 31 33 35 36 UNI GY 9.6
    END DEFINE REFERENCE LOADS
    DEFINE UBC LOAD
    ZONE 0.4 I 1.5 RWX 8.5 RWZ 8.5 STYP 4 CT 0.0731 PX 0.284 PZ 0.284 NA 1 NV 1
    LOAD 1 LOADTYPE Seismic TITLE EQ +X +E
    UBC LOAD X 1 DEC 1 ACC 0.05
    LOAD 2 LOADTYPE Seismic TITLE EQ +X -E
    UBC LOAD X 1 DEC 1 ACC -0.05
    LOAD 3 LOADTYPE Seismic TITLE EQ -X +E
    UBC LOAD X -1 DEC 1 ACC 0.05
    LOAD 4 LOADTYPE Seismic TITLE EQ -X -E
    UBC LOAD X -1 DEC 1 ACC -0.05
    LOAD 5 LOADTYPE Seismic TITLE EQ +Z +E
    UBC LOAD Z 1 DEC 1 ACC 0.05
    LOAD 6 LOADTYPE Seismic TITLE EQ +Z -E
    UBC LOAD Z 1 DEC 1 ACC -0.05
    LOAD 7 LOADTYPE Seismic TITLE EQ -Z +E
    UBC LOAD Z -1 DEC 1 ACC 0.05
    LOAD 8 LOADTYPE Seismic TITLE EQ -Z -E
    UBC LOAD Z -1 DEC 1 ACC -0.05
    LOAD 9 LOADTYPE Dead TITLE DL
    REFERENCE LOAD
    R1 -1.0
    LOAD 10 LOADTYPE Live TITLE LL
    FLOOR LOAD
    _ROOM FLOAD -2.4 GY
    ONEWAY LOAD
    _ONEROOM ONE -2.4 GY
    FLOOR LOAD
    _BALCON FLOAD -2.9 GY
    _AS_ST FLOAD -4.8 GY
    LOAD 11 LOADTYPE Roof Live TITLE LLR
    FLOOR LOAD
    _STRD FLOAD -4.8 GY
    _BALCONRD FLOAD -2.9 GY
    PERFORM ANALYSIS
    FINISH

Children
No Data