Hi Friends,
I have modelled and take a report for loading.
In that only self-weight is mentioned not floor load why?
can anyone check this out I have attached model and report for your reference.../PDF5153.model.std
This is a known issue and is already reported for the developers as a defect #376380. Unfortunately, the issue is not fixed yet, but it should be addressed in the upcoming versions of STAAD.Pro.
As this defect states, this issue happens to the floor loads, which are applied on the created floor groups. If the floor load is applied using the YRANGE option instead of the Group option, the report would be setup correctly. So till this issue is not fixed yet, I would recommend you to use this workaround - use the YRANGE option instead of the Group option in the Floor Load to see this load in the report.
Thank you,
But unable to give floor load in YRANGE option because the roof is inclined so what shall I do for this?
You can apply load after creating floor group or you can provide Y range from 2.33 to 2.475 for floor load.
Ya right.
If I give floor load by the group option then I cannot be viewed it in the report.../
If I give floor load by Y range from 2.33 to 2.475 it unable to assign because the roof is inclined.../
The Group option should work fine. can you please send the updated file and screenshot of your issues?