T-Beam section geometry in ACI 318 14 and ACI 318 11

Dear Seth,

In the ACI 318-11, the effective flange width was taken the smallest of three limitations (Section 8.12) . The first one is limited to 1/4 of the span length, which means that  if we have a span of 4 m and  wide beam of 1.2 m width the effective flange width will be 1 m  less than the web width. This is also done exactly by Ram Concept for this situation. 

In the ACI 318-14, the effective flange width was taken the smallest of three limitations (Section 6.3.2) . The same condition was changed to web width plus 1/8 of the span length from each side of the web (bw+L/4 - in total),  which means that  if we have a span of 4 m and  wide beam of 1.2 m width the effective flange width will be (1.2+1=2.2 m) . This is NOT done by Ram Concept  according to ACI 318-14 for this situation. Ram Concept still determining the same flange width as ACI 318-11.

Is it right ? or I have to edit the design strip manually to satisfy the ACI 318-14?

Thank You again for Your help.

BR

Nasr