Hi everyone,
I'm a novice designer. I'm designing a building as per is 13920 2016 in staad pro but getting many errors/warnings mentioned below, hope I will get solutions to them
1. ERROR: THE AXIAL STRESS ON MEMBER # 246 DESIGNED AS BEAM EXCEEDS 0.08FCK (what should I do to remove these errors)
2. WARNING: DEPTH OF BEAM # 134 SHALL PREFERABLY BE LESS THAN THE 1/4TH OF CLEAR SPAN ASSUMING IT TO BE SPANNING BETWEEN SUPPORTS.if NOT, USE COMBINE PARAMETER.
(I read about COMBINE parameter but to apply it on all subdivided beams is a tedious task, is there any alternative to this)
3. ERROR: MINIMUM DIMENSION OF COLUMN # 1014 SHOULD NOT BE LESS THAN 20 TIMES THE DIAMETER.........
(I this case i used maxmain parameter set to 20 mm dia. for all beams(earlier I put design column command before design beam command and it shows this error for all columns but even after putting design beam command above design column it still shows few columns with this error)
4. NOTE: SOME OF THE BEAMS CONNECTED TO THE COLUMN NO. 2026 ARE NOT DESIGNED. ONLY SHEAR FORCE FROM ANALYSIS WILL BE CONSIDERED FOR SHEAR DESIGN.
(in this case i checked for few columns with this note and found that all beams connected to columns are designed as oppposite to statement in above note.)
5. WARNING: CHECK FOR MINIMUM DIMENSION OF COLUMN # 2030 IS IGNORED AS PERCL 7.1.1 a) OF IS-13920:2016. SOME OF THE BEAMS CONNECTED TO THE COLUMN ARE NOT DESIGNED.
(here the check for minimun dimension of column is ignored why???)
6. does staad design for under reinforced section or balanced section?
7. i attached the code, please review it and suggest me any modification or changes or mistakes done by me.
UNIT METER KN JOINT COORDINATES 11 0 0 0; 12 3.55 0 0; 13 7.2 0 0; 14 10.75 0 0; 15 0 0 -4.31; 16 3.55 0 -4.31; 17 7.2 0 -4.31; 18 10.75 0 -4.31; 19 10.75 0 -6.14; 20 0 0 -7.9; 21 3.55 0 -7.9; 22 7.2 0 -7.9; 23 10.75 0 -9.68; 24 0 0 -10.47; 25 3.55 0 -10.47; 26 7.2 3.4 -11.42; 27 0 3.4 -14.4; 28 3.55 3.4 -14.4; 29 7.2 3.4 -14.4; 30 10.75 3.4 -14.4; 111 0 1.8 0; 112 3.55 1.8 0; 113 7.2 1.8 0; 114 10.75 1.8 0; 115 0 1.8 -4.31; 116 3.55 1.8 -4.31; 117 7.2 1.8 -4.31; 118 10.75 1.8 -4.31; 119 10.75 1.8 -6.14; 120 7.2 1.8 -6.14; 121 0 1.8 -7.9; 122 3.55 1.8 -7.9; 123 7.2 1.8 -7.9; 124 10.75 1.8 -9.68; 125 7.2 1.8 -9.68; 126 0 1.8 -10.47; 127 3.55 1.8 -10.47; 128 7.2 1.8 -10.47; 211 0 4.9 0; 212 3.55 4.9 0; 213 7.2 4.9 0; 214 10.75 4.9 0; 215 5.09 4.9 0; 216 3.55 4.9 -3.15; 217 7.2 4.9 -3.15; 218 5.09 4.9 -3.15; 219 0 4.9 -4.31; 220 3.55 4.9 -4.31; 221 7.2 4.9 -4.31; 222 10.75 4.9 -4.31; 223 8.35 4.9 -4.31; 224 10.75 4.9 -6.14; 225 7.2 4.9 -6.14; 226 8.35 4.9 -6.14; 227 0 4.9 -7.9; 228 3.55 4.9 -7.9; 229 7.2 4.9 -7.9; 230 10.75 4.9 -9.68; 231 7.2 4.9 -9.68; 232 0 4.9 -10.47; 233 3.55 4.9 -10.47; 234 7.2 4.9 -10.47; 235 7.2 4.9 -11.42; 236 10.75 4.9 -11.42; 237 0 4.9 -14.4; 238 3.55 4.9 -14.4; 239 7.2 4.9 -14.4; 240 10.75 4.9 -14.4; 241 10.75 5.783 -9.68; 242 10.75 5.783 -8.68; 243 10.75 6.816 -7.14; 244 10.75 6.816 -6.14; 256 10.75 2.683 -9.68; 257 10.75 3.716 -6.14; 258 10.75 2.683 -8.68; 259 10.75 3.716 -7.14; 311 0 8 0; 312 3.55 8 0; 313 7.2 8 0; 314 10.75 8 0; 315 5.09 8 0; 316 3.55 8 -3.15; 317 7.2 8 -3.15; 318 5.09 8 -3.15; 319 0 8 -4.31; 320 3.55 8 -4.31; 321 7.2 8 -4.31; 322 10.75 8 -4.31; 323 8.35 8 -4.31; 324 10.75 8 -6.14; 325 7.2 8 -6.14; 326 8.35 8 -6.14; 327 0 8 -7.9; 328 3.55 8 -7.9; 329 7.2 8 -7.9; 330 10.75 8 -9.68; 331 7.2 8 -9.68; 332 8.35 8 -9.68; 333 0 8 -10.47; 334 3.55 8 -10.47; 335 7.2 8 -10.47; 336 7.2 8 -11.42; 337 10.75 8 -11.42; 338 8.35 8 -11.42; 339 3.55 8 -13.56; 340 7.2 8 -13.56; 341 0 8 -14.4; 342 3.55 8 -14.4; 343 7.2 8 -14.4; 344 10.75 8 -14.4; 345 10.75 8.883 -9.68; 346 10.75 8.883 -8.68; 347 10.75 9.916 -7.14; 348 10.75 9.916 -6.14; 411 0 11.1 0; 412 3.55 11.1 0; 413 7.2 11.1 0; 414 10.75 11.1 0; 415 5.09 11.1 0; 416 3.55 11.1 -3.15; 417 7.2 11.1 -3.15; 418 5.09 11.1 -3.15; 419 0 11.1 -4.31; 420 3.55 11.1 -4.31; 421 7.2 11.1 -4.31; 422 10.75 11.1 -4.31; 423 8.35 11.1 -4.31; 424 10.75 11.1 -6.14; 425 7.2 11.1 -6.14; 426 8.35 11.1 -6.14; 427 0 11.1 -7.9; 428 3.55 11.1 -7.9; 429 7.2 11.1 -7.9; 430 10.75 11.1 -9.68; 431 7.2 11.1 -9.68; 432 8.35 11.1 -9.68; 433 0 11.1 -10.47; 434 3.55 11.1 -10.47; 435 7.2 11.1 -10.47; 436 7.2 11.1 -11.42; 437 10.75 11.1 -11.42; 438 8.35 11.1 -11.42; 439 3.55 11.1 -13.56; 440 7.2 11.1 -13.56; 441 0 11.1 -14.4; 442 3.55 11.1 -14.4; 443 7.2 11.1 -14.4; 444 10.75 11.1 -14.4; 445 10.75 11.983 -9.68; 446 10.75 11.983 -8.68; 447 10.75 13.016 -7.14; 448 10.75 13.016 -6.14; 511 0 14.2 0; 512 3.55 14.2 0; 513 7.2 14.2 0; 514 10.75 14.2 0; 515 0 14.2 -4.31; 516 3.55 14.2 -4.31; 517 7.2 14.2 -4.31; 518 10.75 14.2 -4.31; 519 10.75 14.2 -6.14; 520 7.2 14.2 -6.14; 521 0 14.2 -7.9; 522 3.55 14.2 -7.9; 523 7.2 14.2 -7.9; 524 10.75 14.2 -9.68; 525 7.2 14.2 -9.68; 526 0 14.2 -10.47; 527 3.55 14.2 -10.47; 528 7.2 14.2 -10.47; 529 7.2 14.2 -11.42; 530 10.75 14.2 -11.42; 531 0 14.2 -14.4; 532 3.55 14.2 -14.4; 533 7.2 14.2 -14.4; 534 10.75 14.2 -14.4; 535 0 4.9 0.63; 536 3.55 4.9 0.63; 537 7.2 4.9 0.63; 538 10.75 4.9 0.63; 539 0 8 0.63; 540 3.55 8 0.63; 541 7.2 8 0.63; 542 10.75 8 0.63; 543 0 11.1 0.63; 544 3.55 11.1 0.63; 545 7.2 11.1 0.63; 546 10.75 11.1 0.63; 547 3.55 8 -15.03; 548 7.2 8 -15.03; 549 3.55 11.1 -15.03; 550 7.2 11.1 -15.03; 551 2.42 8 -7.9; 552 2.42 8 -10.47; 553 2.42 11.1 -7.9; 554 2.42 11.1 -10.47; MEMBER INCIDENCES 111 111 112; 112 112 113; 113 113 114; 114 111 115; 115 112 116; 116 113 117; 117 114 118; 118 115 116; 119 116 117; 120 117 118; 121 117 120; 122 118 119; 123 115 121; 124 116 122; 125 119 120; 126 120 123; 127 121 122; 128 122 123; 129 119 124; 130 123 125; 131 121 126; 132 122 127; 133 124 125; 134 125 128; 135 126 127; 136 127 128; 211 211 212; 212 212 215; 213 213 214; 214 215 213; 215 212 216; 216 213 217; 217 215 218; 218 211 219; 219 214 222; 220 216 218; 221 218 217; 222 216 220; 223 217 221; 224 219 220; 225 220 221; 226 221 223; 227 223 222; 228 221 225; 229 222 224; 230 223 226; 231 219 227; 232 220 228; 233 224 226; 234 226 225; 235 225 229; 236 227 228; 237 228 229; 238 224 230; 239 229 231; 240 227 232; 241 228 233; 242 230 231; 243 231 234; 244 232 233; 245 233 234; 246 230 236; 247 234 235; 248 235 236; 249 232 237; 250 233 238; 251 235 239; 252 236 240; 253 238 239; 254 239 240; 255 237 238; 311 311 312; 312 312 315; 313 313 314; 314 315 313; 315 312 316; 316 313 317; 317 315 318; 318 311 319; 319 314 322; 320 316 318; 321 318 317; 322 316 320; 323 317 321; 324 319 320; 325 320 321; 326 321 323; 327 323 322; 328 321 325; 329 322 324; 330 323 326; 331 319 327; 332 320 328; 333 324 326; 334 326 325; 335 325 329; 336 327 551; 337 328 329; 338 324 330; 339 329 331; 340 327 333; 341 328 334; 342 330 332; 343 332 331; 344 331 335; 345 333 552; 346 334 335; 347 330 337; 348 332 338; 349 335 336; 350 336 338; 351 338 337; 352 334 339; 353 333 341; 354 336 340; 355 337 344; 356 339 340; 357 339 342; 358 340 343; 359 342 343; 360 343 344; 361 341 342; 411 411 412; 412 412 415; 413 413 414; 414 415 413; 415 412 416; 416 413 417; 417 415 418; 418 411 419; 419 414 422; 420 416 418; 421 418 417; 422 416 420; 423 417 421; 424 419 420; 425 420 421; 426 421 423; 427 423 422; 428 421 425; 429 422 424; 430 423 426; 431 419 427; 432 420 428; 433 424 426; 434 426 425; 435 425 429; 436 427 553; 437 428 429; 438 424 430; 439 429 431; 440 427 433; 441 428 434; 442 430 432; 443 432 431; 444 431 435; 445 433 554; 446 434 435; 447 430 437; 448 432 438; 449 435 436; 450 436 438; 451 438 437; 452 434 439; 453 433 441; 454 436 440; 455 437 444; 456 439 440; 457 439 442; 458 440 443; 459 442 443; 460 443 444; 461 441 442; 511 511 512; 512 512 513; 513 513 514; 514 511 515; 515 512 516; 516 513 517; 517 514 518; 518 515 516; 519 516 517; 520 517 518; 521 517 520; 522 518 519; 523 515 521; 524 516 522; 525 519 520; 526 520 523; 527 521 522; 528 522 523; 529 519 524; 530 523 525; 531 521 526; 532 522 527; 533 524 525; 534 525 528; 535 526 527; 536 527 528; 537 524 530; 538 528 529; 539 529 530; 540 526 531; 541 527 532; 542 529 533; 543 530 534; 544 532 533; 545 533 534; 546 531 532; 1011 11 111; 1012 12 112; 1013 13 113; 1014 14 114; 1015 15 115; 1016 16 116; 1017 17 117; 1018 18 118; 1019 19 119; 1020 20 121; 1021 21 122; 1022 22 123; 1023 23 124; 1024 24 126; 1025 25 127; 2011 111 211; 2012 112 212; 2013 113 213; 2014 114 214; 2015 115 219; 2016 116 220; 2017 117 221; 2018 118 222; 2019 119 257; 2020 257 224; 2021 121 227; 2022 122 228; 2023 123 229; 2024 124 256; 2025 256 230; 2026 126 232; 2027 127 233; 2028 235 26; 2029 237 27; 2030 238 28; 2031 239 29; 2032 240 30; 3011 211 311; 3012 212 312; 3013 213 313; 3014 214 314; 3015 219 319; 3016 220 320; 3017 221 321; 3018 222 322; 3019 224 244; 3020 244 324; 3021 227 327; 3022 228 328; 3023 229 329; 3024 230 241; 3025 241 330; 3026 232 333; 3027 233 334; 3028 235 336; 3029 237 341; 3030 238 342; 3031 239 343; 3032 240 344; 4011 311 411; 4012 312 412; 4013 313 413; 4014 314 414; 4015 319 419; 4016 320 420; 4017 321 421; 4018 322 422; 4019 324 348; 4020 348 424; 4021 327 427; 4022 328 428; 4023 329 429; 4024 330 345; 4025 345 430; 4026 333 433; 4027 334 434; 4028 336 436; 4029 341 441; 4030 342 442; 4031 343 443; 4032 344 444; 5011 411 511; 5012 412 512; 5013 413 513; 5014 414 514; 5015 419 515; 5016 420 516; 5017 421 517; 5018 422 518; 5019 424 448; 5020 448 519; 5021 427 521; 5022 428 522; 5023 429 523; 5024 430 445; 5025 445 524; 5026 433 526; 5027 434 527; 5028 436 529; 5029 441 531; 5030 442 532; 5031 443 533; 5032 444 534; 6011 256 258; 6012 241 242; 6013 345 346; 6014 445 446; 6015 258 259; 6016 242 243; 6017 346 347; 6018 446 447; 6019 257 259; 6020 244 243; 6021 348 347; 6022 448 447; 6023 211 535; 6024 212 536; 6025 213 537; 6026 214 538; 6027 311 539; 6028 312 540; 6029 313 541; 6030 314 542; 6031 411 543; 6032 412 544; 6033 413 545; 6034 414 546; 6035 535 536; 6036 537 538; 6037 539 540; 6038 541 542; 6039 543 544; 6040 545 546; 6041 342 547; 6042 343 548; 6043 442 549; 6044 443 550; 6045 547 548; 6046 549 550; 6047 551 328; 6048 552 334; 6049 553 428; 6050 554 434; 6051 551 552; 6052 553 554; DEFINE MATERIAL START ISOTROPIC CONCRETE E 2.17185e+07 POISSON 0.17 DENSITY 23.5616 ALPHA 1e-05 DAMP 0.05 TYPE CONCRETE STRENGTH FCU 27579 END DEFINE MATERIAL MEMBER PROPERTY AMERICAN 2016 2019 TO 2026 3016 3019 TO 3026 4016 4019 TO 4026 5016 5019 TO 5025 - 5026 PRIS YD 0.45 ZD 0.45 2011 TO 2015 2017 2018 2027 3011 TO 3015 3017 3018 3027 TO 3032 4011 TO 4015 - 4017 4018 4027 TO 4032 5011 TO 5015 5017 5018 5027 TO 5031 - 5032 PRIS YD 0.45 ZD 0.45 111 TO 136 6011 TO 6022 PRIS YD 0.3 ZD 0.45 211 TO 216 218 219 222 TO 229 231 TO 255 311 TO 316 318 319 322 TO 329 331 - 332 TO 347 349 TO 355 357 TO 361 411 TO 416 418 419 422 TO 429 431 TO 447 - 449 TO 455 457 TO 461 511 TO 546 6023 TO 6034 6041 TO 6044 6047 TO 6051 - 6052 PRIS YD 0.3 ZD 0.45 217 220 221 230 317 320 321 330 348 356 417 420 421 430 448 - 456 PRIS YD 0.3 ZD 0.3 MEMBER PROPERTY AMERICAN 6035 TO 6040 6045 6046 PRIS YD 0.5 ZD 0.2 UNIT MMS NEWTON MEMBER PROPERTY 1011 TO 1025 2028 TO 2032 PRIS YD 600 ZD 600 UNIT METER KN CONSTANTS MATERIAL CONCRETE ALL SUPPORTS 11 TO 30 FIXED MEMBER RELEASE 217 230 317 330 348 417 430 448 6051 6052 START MPX 0.99 220 320 356 420 456 6035 TO 6040 6045 6046 START MPZ 0.99 230 330 348 430 448 6051 6052 END MPX 0.99 136 221 245 321 346 356 421 446 456 536 6035 TO 6040 6045 6046 END MPZ 0.99 DEFINE IS1893 2016 LOAD ZONE 0.36 RF 5 I 1.2 SS 2 ST 1 DM 0.05 DT 1.8 SELFWEIGHT 1 MEMBER WEIGHT 125 126 129 130 133 TO 136 211 TO 214 218 219 229 231 235 TO 239 242 - 311 TO 314 318 319 329 331 335 TO 340 347 353 355 356 359 TO 361 411 TO 414 - 418 419 429 431 435 TO 440 447 453 455 456 459 TO 461 6047 6049 UNI 12 215 TO 217 220 TO 224 226 227 230 233 234 315 TO 317 320 TO 324 326 327 330 - 333 334 342 343 345 348 350 TO 352 354 357 358 415 TO 417 420 TO 424 426 - 427 430 433 434 442 443 445 448 450 TO 452 454 457 458 6048 6050 TO 6051 - 6052 UNI 7 531 537 540 543 TO 546 UNI 4 6011 TO 6014 6019 TO 6022 UNI 10 FLOOR WEIGHT YRANGE 4.9 11.1 FLOAD 4.5 XRANGE 0 10.75 ZRANGE -7.9 0.63 YRANGE 4.9 11.1 FLOAD 6.5 XRANGE 3.5 7.2 ZRANGE -3.15 0 YRANGE 4.9 11.1 FLOAD 6.5 XRANGE 8.35 10.75 ZRANGE -6.14 -4.31 YRANGE 8 11.1 FLOAD 4.5 XRANGE 0 10.75 ZRANGE -15.03 -7.9 YRANGE 8 11.1 FLOAD 6.5 XRANGE 0 2.42 ZRANGE -10.47 -7.9 YRANGE 8 11.1 FLOAD 6.5 XRANGE 8.35 10.75 ZRANGE -11.42 -9.68 YRANGE 14.2 14.2 FLOAD 4.5 XRANGE 0 10.75 ZRANGE -14.4 0 YRANGE 14.2 14.2 FLOAD 1.5 XRANGE 0 10.75 ZRANGE -14.4 0 *LLreducible YRANGE 4.9 11.1 FLOAD 1.5 XRANGE 0 10.75 ZRANGE -7.9 0.63 YRANGE 4.9 11.1 FLOAD 0.5 XRANGE 3.5 7.2 ZRANGE -3.15 0 YRANGE 4.9 11.1 FLOAD 0.5 XRANGE 8.35 10.75 ZRANGE -6.14 -4.31 YRANGE 8 11.1 FLOAD 1.5 XRANGE 0 10.75 ZRANGE -15.03 -7.9 YRANGE 8 11.1 FLOAD 0.5 XRANGE 0 2.42 ZRANGE -10.47 -7.9 YRANGE 8 11.1 FLOAD 0.5 XRANGE 8.35 10.75 ZRANGE -11.42 -9.68 YRANGE 14.2 14.2 FLOAD 1.5 XRANGE 0 10.75 ZRANGE -15.03 -7.9 LOAD 1 LOADTYPE Seismic TITLE EQX 1893 LOAD X 1 LOAD 2 LOADTYPE Seismic TITLE EQZ 1893 LOAD Z 1 LOAD 3 LOADTYPE Dead TITLE DL SELFWEIGHT Y -1 MEMBER LOAD 125 126 129 130 133 TO 136 211 TO 214 218 219 229 231 235 TO 239 242 - 311 TO 314 318 319 329 331 335 TO 340 347 353 355 356 359 TO 361 411 TO 414 - 418 419 429 431 435 TO 440 447 453 455 456 459 TO 461 6047 6049 UNI GY -12 215 TO 217 220 TO 224 226 227 230 233 234 315 TO 317 320 TO 324 326 327 330 - 333 334 342 343 345 348 350 TO 352 354 357 358 415 TO 417 420 TO 424 426 - 427 430 433 434 442 443 445 448 450 TO 452 454 457 458 6048 6050 TO 6051 - 6052 UNI GY -7 531 537 540 543 TO 546 UNI GY -4 6011 TO 6014 6019 TO 6022 UNI GY -10 FLOOR LOAD YRANGE 4.9 11.1 FLOAD -4.5 XRANGE 0 10.75 ZRANGE -7.9 0.63 GY YRANGE 4.9 11.1 FLOAD -6.5 XRANGE 3.5 7.2 ZRANGE -3.15 0 GY YRANGE 4.9 11.1 FLOAD -6.5 XRANGE 8.35 10.75 ZRANGE -6.14 -4.31 GY YRANGE 8 11.1 FLOAD -4.5 XRANGE 0 10.75 ZRANGE -15.03 -7.9 GY YRANGE 8 11.1 FLOAD -6.5 XRANGE 0 2.42 ZRANGE -10.47 -7.9 GY YRANGE 8 11.1 FLOAD -6.5 XRANGE 8.35 10.75 ZRANGE -11.42 -9.68 GY YRANGE 14.2 14.2 FLOAD -4.5 XRANGE 0 10.75 ZRANGE -14.4 0 GY YRANGE 14.2 14.2 FLOAD -1.5 XRANGE 0 10.75 ZRANGE -14.4 0 GY LOAD 4 LOADTYPE Live TITLE LL FLOOR LOAD YRANGE 4.9 11.1 FLOAD -3 XRANGE 0 10.75 ZRANGE -7.9 0.63 GY YRANGE 4.9 11.1 FLOAD -2 XRANGE 3.5 7.2 ZRANGE -3.15 0 GY YRANGE 4.9 11.1 FLOAD -2 XRANGE 8.35 10.75 ZRANGE -6.14 -4.31 GY YRANGE 8 11.1 FLOAD -3 XRANGE 0 10.75 ZRANGE -15.03 -7.9 GY YRANGE 8 11.1 FLOAD -2 XRANGE 0 2.42 ZRANGE -10.47 -7.9 GY YRANGE 8 11.1 FLOAD -2 XRANGE 8.35 10.75 ZRANGE -11.42 -9.68 GY YRANGE 14.2 14.2 FLOAD -3 XRANGE 0 10.75 ZRANGE -15.03 -7.9 GY LOAD 5 LOADTYPE Live TITLE LL50% FLOOR LOAD YRANGE 4.9 11.1 FLOAD -1.5 XRANGE 0 10.75 ZRANGE -7.9 0.63 GY YRANGE 4.9 11.1 FLOAD -0.5 XRANGE 3.5 7.2 ZRANGE -3.15 0 GY YRANGE 4.9 11.1 FLOAD -0.5 XRANGE 8.35 10.75 ZRANGE -6.14 -4.31 GY YRANGE 8 11.1 FLOAD -1.5 XRANGE 0 10.75 ZRANGE -15.03 -7.9 GY YRANGE 8 11.1 FLOAD -0.5 XRANGE 0 2.42 ZRANGE -10.47 -7.9 GY YRANGE 8 11.1 FLOAD -0.5 XRANGE 8.35 10.75 ZRANGE -11.42 -9.68 GY YRANGE 14.2 14.2 FLOAD -1.5 XRANGE 0 10.75 ZRANGE -15.03 -7.9 GY LOAD COMBINATION 7 3 1.0 4 1.0 LOAD COMBINATION 8 1 1.2 3 1.2 5 1.2 LOAD COMBINATION 9 1 -1.2 3 1.2 5 1.2 LOAD COMBINATION 10 2 1.2 3 1.2 5 1.2 LOAD COMBINATION 11 2 -1.2 3 1.2 5 1.2 LOAD COMBINATION 12 1 1.5 3 1.5 LOAD COMBINATION 13 1 -1.5 3 1.5 LOAD COMBINATION 14 2 1.5 3 1.5 LOAD COMBINATION 15 2 -1.5 3 1.5 LOAD COMBINATION 16 1 1.5 3 0.9 LOAD COMBINATION 17 1 -1.5 3 0.9 LOAD COMBINATION 18 2 1.5 3 0.9 LOAD COMBINATION 19 2 -1.5 3 0.9 LOAD COMBINATION 20 3 1.5 4 1.5 PERFORM ANALYSIS LOAD LIST 7 PRINT SUPPORT REACTION LOAD LIST 8 TO 20 START CONCRETE DESIGN CODE IS13920 2016 UNIT MMS NEWTON FC 25 ALL FYMAIN 415 ALL MINMAIN 12 ALL MAXMAIN 20 MEMB 111 TO 136 211 TO 255 311 TO 361 411 TO 461 511 TO 546 6011 - 6012 TO 6052 GLD 7 MEMB 111 TO 136 211 TO 255 311 TO 361 411 TO 461 511 TO 546 6011 TO 6052 DESIGN BEAM 111 TO 136 211 TO 255 311 TO 361 411 TO 461 511 TO 546 6011 TO 6052 DESIGN COLUMN 1011 TO 1025 2011 TO 2032 3011 TO 3032 4011 TO 4032 5011 TO 5032 END CONCRETE DESIGN FINISH
Dear User,
Please find the replies below.
1. You need to design those members as column.
2. Unfortunately no.
3. This looks a bug to me. I will let you know once I get confirmed about this.
4. For column 2026 if you notice closely, the beam #249 has not been designed as per IS 13920,2016. the design you see is for IS 456 only. Hence this warning is there.
5. For this Beam # 250 has not been designed as per IS 13920,2016. Hence this warning.
6. Staad designs for under reinforced section.
Answer Verified By: sharm ank
Thank you very much for the reply sir
but I have some more doubts if you could please clear them.
1. those members whose axial stress exceed 0.08fck are "BEAMS"( spanning in xz plane or horizontally) cant they be designed as beams?
4. and 5 . why those beams are not designed as per is13920, whats wrong with them?
Please see the below screenshot from IS 13920.
As per this clause the beams have not been designed as they should be designed as columns *** per requirements of section 7.
thanks for the reply sir, i read this clause yesterday but only now i understand it fully. thanks for your time.
hello sir,
can you verify the error in point 3.(regarding showing error about minimum dimension of column even after specifying maxmain reinforment dia. to beams? I'm not able to figure this out.