I was trying to fix 3 things in the last couple of days. unfortunately, I could not fix all the problems, so I hope to get help ASAP.
the First problem that I had and I could fix is the warning that says "Review shear min density/max spacing Cl 9.7.6.2.2" I just increased the cross section area, then the warning did not appear. However, I would like to get comments about the solution that I made or other solutions.
the second problem is that after I removed all warning, I am still not getting design tab (after running the analysis) by double click on the member (the tab I am talking about is to the right of the deflection tab. THIS TAB IS NOT IN THE OUTPUT)
the third problem is that the take off command for the RCC building is not working even without any warning I am still getting 0 CU.meter.
Finally, I appreciate any help, and I can provide the input text if needed.
What product are you using?
What version?
Do you have a file that illustrates the problem? If so send it.
Hi
Dear Seth,
I am Using STAAD.Pro CONNECT Edition V22.
I also just uploaded the file.
Thanks.
Yes the second and third points are related to the ACI 318-14 code implementation in STAAD.Pro. One thing you can do for now is use the ACI 318-11 code and all of the issues you mentioned should be handled. To use the ACI 318-2011, you need to change the command as show below
START CONCRETE DESIGN
CODE ACI 2011
Also you may want to add a LOAD LIST 7 TO 11 command just before the START CONCRETE DESIGN to limit the design to the combinations only
Dear Sye,
First of all, I appreciate your effort. you are right as soon as i used ACI 2011 The last 2 issues as well as the 1st issue were fixed.
As a result, applying the code ACI 2014 is not appropriate since the 1st problem was fixed with ACI-2011. Clearly for the viewers, DO NOT USE ACI 2014 for now because you may get warnings that are not right, and I will try to confirm that by manual calculation to check if the 1st warning exist or not.
Best Regards.
I am still looking for an answer to the "Review shear min density/max spacing Cl 9.7.6.2.2" warning message when using the ACI 318-2014 code. I am using STAAD.Pro 22.04.00.40. any updates ?