RAM Concept Design Status Failure: 8.6.1.1

I have a 10" slab with Gr. 60 #6 at 18" OC each way T&B (steel density provided= .0024 each face) and I'm getting a design status error for ACI 318-14 section 8.6.1.1 (minimum steel). When I use the section audit, it appears as though the steel is accounted for and developed and has sufficient density (.0022). I'm confused at what is prompting this error - any help? Thank you,.

Parents Reply
  • In the Audit I see: 

    Two-way slab in critical span region - checking 2 * h spacing limit (per 8.7.2.2).
    Checking 8.6.1.1
    Ac 797.5 in²
    Reinforcing Ratio (using all reinforcement) 0.002207
    Modified Reinforcing Ratio (fy > 60 ksi) 0.002207
    Maximum allowed bar spacing 18 inches
    Maximum actual bar spacing 19.94 inches

    What's happening is illustrated below:

    You can ignore it since your spacing is literally 18" OC (or turn off code min design rule).



    Answer Verified By: Stephen Figueira 