This is the first time this has happened to me, but point loads that I placed on a beam in the RAM modeler are not acting on that beam when checked in the beam/joist module. However, they are acting on a different beam along the same construction grid line. The image below shows the beam in question as well as the two problematic point loads (all circled in red).
When I go to the beam design module and view the beam's load diagrams, this is what I see:
P1 & P2 are correct. However, P3 should not be there. When I delete the two circled point loads and recheck this beam, P3 disappears. When I add the point loads back in, it shows back up on this beam. Additionally, the point loads are not showing up or impacting the beams they are actually located on.
This has led to the beam in question "failing" even though without that point load P3, it might be fine. It has also led to the beams with the actual load not being analyzed for the applied loads.
Any help or recommendations would be appreciated. I have tried deleting and re-adding the beams and point loads several times with no luck.
Try regenerating the slab edge - whole perimeter. Make sure the deck angle is correct and if the deck changes, the edges fall on beam center-lines. See also: https://communities.bentley.com/products/ram-staad/w/structural_analysis_and_design__wiki/18040/missing-or-incorrect-loads-near-perimeter-beams and https://communities.bentley.com/products/ram-staad/w/structural_analysis_and_design__wiki/21833/effects-of-changing-deck-type
Answer Verified By: Jacob Witt
That fixed it. Thank you!