WELDING DESIGN CALCULATION FOR PRE ENGINEERING I BEAM
Dear All,
I am using a pre-engineering steel beam in my calculation. Can anybody tell me how we can calculate the welding thickness for PEB?
Thank you,
  • well as far as i know you cannot calculate it in staad .
    if you talking of fillet weld between  flange and web , you need to claculate the stress in shear ( consider resultant of Fy and F z shear force) at critical section taken in to consideration , and compare it wiht allowable stress of weld ( 0.3 x Fu of weld )
    Best Regards,
    Alex Immanuel Thainese
  • beam flange is 80*500mm and the web is 20*940mm .combined stresses at mid of the beam is 88N/mm2 .so what will be the leg size of the weld?
  • as mentioned earlier , you need to only consider stress due to shear . combined stress  should  not be used  for weld check .
    choose a weld leg size  and calculate tau
    stress due to shear  - tau = F Ay / (Izz  x b)
    F = shear force on the section   =   sqrt ( Fy2 + Fz 2)
    Fy & Fz = shear stress on the crossection along axis parallel to web and perpendicular to web )
    A y = (topFlangeWidth*topFlangeThickness*(webDepth/2+topFlangeThickness/2))
    b = 0.707 x weld leg size
    this tau < =  0.3 Fu        (  as per AISC)
    Fu =  ultimate stregnth of weld electrode .
    hope it is clear .
    Best Regards,