concrete wall at the ram modeler

I have modeling issues for the concrete shear wall.

1) I deleted the shear wall on the plan.  But still, there is a wall on the 3-d model. 

2) I drew the wall along the grid line. But the wall showed up at another grid line. 

3) There is no shear wall overlapped on the plan. But the warning message has the wall overlapped and the 3-d Model has wall overlapped. 

Please let me know how to solve these issues.

Thanks,

Parents Reply
  • This is a strange case. Something seems to have become corrupted in the model unique ID structure. If I try to use the Options - Renumber members command, for example, then several of the walls disappear. 

    The best solution is to:

    1. make a new layout type,
    2. copy the geometry and loads from the 2nd floor to the new level and
    3. use the new level in the story data,
    4. then delete the original layout.
    5. This will require the remodeling of wall openings and braces in the lowest story, however. 