Googevening,
performing concrete slab verification with staad pro (ACI Code), I noticed some discrepancies between input data definition, as reported below:
and output results obtanained from calculations are listed below:
in particular the following results report in STAAD_Pro output are not in compliance:
- concrete cover definition that must be equal to 75mm but staad defines cover at top and bottom equal to 19.05 mm
- concrete strength that must be 14.16 N/mm2 but staad defines 27.58 MPa
- steel reinforcement strength 450 N/mm2 but staad defines 413.68 MPa.
How these parameters are evaluated by STAAD?
How can I set in a correct way these input data?
It means that in my STAAD_pro version, crack checks is not available. Correct?
Correct. The ELEMENT DESIGN in STAAD.Pro as per the ACI 318 code just gives you the required reinforcement area. The onus is on the user to choose an appropriate bar size and spacing so that the required reinforcement area is satisfied. As you know, it is the spacing between bars in the tension face, the stress in the steel closest to the extreme tension face and the clear cover to the reinforcement from the tension face, that control the cracking. Since the ELEMENT DESIGN does not venture into these areas, the user needs to make sure that the spacing requirements are met to keep cracking within acceptable limits. If you need more detailed design, you may use the Advanced Concrete Design option.
Answer Verified By: SILVIA CONTI