Basak Framing V4.rar
Hi,
Attached herein is my analysis of a 2-Storey House in Staad Pro; the problem is that when i used this file in RCDC 6.3 to design Column, the result is all failed. It seems like the program wants me to increase the dimension of column with many rebars. Please refer below for the info:
1. Concrete = C21
2. Rebar =fy275
3. Ductile Special is selected
4. Joint Check option is selected
5. 25mm clear cover
6. preferably 16mm diam bar for main reinf & 10mm on ties
7. Location = Philippines
8. Design Code = ACI 318M-2011
9. Column dimension is (Footing to 2F Level = 200x450mm / 2F Level to Roof Beam = 200x350mm)
Hope anyone could assist me on this. Thanks in advance.
hi i encounter this error also, i tried to change larger section but still doesnt pass the design, am using 8.0 rcdc
Hi Marlon ,
I would recommend you to upgrade your RCDC to the latest version of V9.04.00.128 and check if this helps you resolve the issue. There are lot of enhancements being done after the V8.
This is also my problem. Almost all of my beams fail in ductile design (special frame) but pass in intermediate frame design. Im using rcdc v10
Hi Jan,
Request you to kindly share RCDC file with us for further investigation at our end.
HI! Did they solved your problem?
This issue is resolved in version 11.00.00.143.
However, the latest version now is 11.01.00.180.
You can use any one to check the issue.
Thanks.