Why I am getting an Errror in Concrete design using IS 13920_2016_while IS 13920-1993 worked

I am getting a error.

While trying to design check column using IS 13920-2016 in Concrete design workflow error is coming as under: 

*** ERROR: MINIMUM DIMENSION OF COLUMN # 1 SHOULD NOT BE LESS THAN
20 TIMES THE DIAMETER OF THE LARGEST LONGITUDINAL REINFORCEMENT
BAR OF THE BEAM AT THE COLUMN JOINT AS PER CL 7.1.1 a) OF IS-13920:2016.

, {NOT IN RCDC/Advanced concrete designbut in StaadPro Design module only.

I have used StaadPro connect edition 22.04.00.40, updated till date.

A clip and Staad file being attached, for checking and confirm finding the same error while using IS13920: 2016, or I am doing some workflow error in commands?

Thanking you.

  TestIS13920_2019-error.STD

Parents
  • IS 13920 2016 code has asked for few new checks that was not available in old code. For those check information regarding beam design is required for column design. As your file is not having any beam design command so beams have not been designed and the program is unable to do the check. Please put a beam design command before Column design command in your file and the issue will be solved.

    Thanks & Regards,
    Abhisek Mandal
    Global Technical Support

    Answer Verified By: Arun Chugh 

Reply
  • IS 13920 2016 code has asked for few new checks that was not available in old code. For those check information regarding beam design is required for column design. As your file is not having any beam design command so beams have not been designed and the program is unable to do the check. Please put a beam design command before Column design command in your file and the issue will be solved.

    Thanks & Regards,
    Abhisek Mandal
    Global Technical Support

    Answer Verified By: Arun Chugh 

Children