Good Day! Please help. As I run the analysis , the SEISMIC MASS result do not match the total deadload in the reaction. What to do? Please help :(((
1. STAAD SPACE 2. START JOB INFORMATION 3. ENGINEER DATE 4. END JOB INFORMATION 5. INPUT WIDTH 79 6. UNIT METER KN 7. JOINT COORDINATES 8. 1 0 1 0; 2 1.25 1 0; 3 2.6 1 0; 4 3.85 1 0; 5 0 1 3; 6 1.25 1 3; 7 2.6 1 3 9. 8 3.85 1 3; 9 0 0 0; 10 3.85 0 0; 11 0 0 3; 12 3.85 0 3; 13 0 3 0; 14 3.85 3 0 10. 15 0 3 3; 16 3.85 3 3 11. MEMBER INCIDENCES 12. 1 1 2; 2 2 3; 3 3 4; 4 1 5; 5 2 6; 6 3 7; 7 4 8; 8 5 6; 9 6 7; 10 7 8; 11 9 1 13. 12 10 4; 13 11 5; 14 12 8; 15 1 13; 16 4 14; 17 5 15; 18 8 16; 19 13 14 14. 20 13 15; 21 14 16; 22 15 16 15. DEFINE MATERIAL START 16. ISOTROPIC CONCRETE 17. E 2.17185E+007 18. POISSON 0.17 19. DENSITY 23.5616 20. ALPHA 1E-005 21. DAMP 0.05 22. TYPE CONCRETE 23. STRENGTH FCU 27579 24. END DEFINE MATERIAL 25. MEMBER PROPERTY AMERICAN 26. 11 TO 18 PRIS YD 0.2 ZD 0.2 27. 1 TO 10 19 TO 22 PRIS YD 0.2 ZD 0.15 28. CONSTANTS 29. MATERIAL CONCRETE ALL 30. SUPPORTS 31. 9 TO 12 FIXED 32. MEMBER RELEASE 33. 5 6 START MZ 34. 5 6 END MZ 35. DEFINE REFERENCE LOADS 36. LOAD R1 LOADTYPE DEAD TITLE REF LOAD - DL 37. SELFWEIGHT Y -1 38. MEMBER LOAD STAAD SPACE -- PAGE NO. 2
39. 1 TO 4 7 UNI GY 5.6 40. 5 6 UNI GY 5.4 41. 19 22 UNI GY 1.224 42. END DEFINE REFERENCE LOADS 43. FLOOR DIAPHRAGM 44. DIA 1 TYPE RIG HEI 1 JOINT 1 TO 8 45. DIA 2 TYPE RIG HEI 3 JOINT 13 TO 16 *** NOTE: NEITHER "MASS" NOR "GRAVITY" REFERENCE LOADTYPE IS PRESENT. MASS MODEL IS FORMED BY COMBINING ALL "DEAD" AND "LIVE" (IF ANY) REFERENCE LOADTYPES.
*** NOTE: MASS MODEL FORMED WILL BE USED IN SEISMIC/RESPONSE/TIME HISTORY LOADING, IF ANY. IF MASS MODEL IS SEPARATELY PROVIDED IN INDIVIDUAL LOADING, THE GENERATED MASS WILL BE REPLACED BY THE MASS PROVIDED IN INDIVIDUAL LOADING.
************************************************************************************ FLOOR DIAPHRAGM UNIT - KN METE --------------- ---------------- NO. TYPE FL. LEVEL FL. WT CENTRE OF MASS MASTER JOINT NO. X Z
1 RIGID 1.000 67.98 1.925 1.024 17 2 RIGID 3.000 4.03 1.925 1.500 18
47. DEFINE UBC LOAD 48. ZONE 0.4 I 1 RWX 8.5 RWZ 8.5 STYP 4 CT 0.0731 NA 1 NV 1 49. REFERENCE LOAD Y
*** NOTE: SEISMIC WEIGHT TABLE IS PRESENT.THIS WEIGHT TABLE WILL BE CONSIDERED IN STATIC SEISMIC ANALYSIS.
50. R1 1.0 51. DEFINE WIND LOAD 52. TYPE 1 WWX 53. <! STAAD PRO GENERATED DATA DO NOT MODIFY !!! 54. ASCE-7-2010:PARAMS 240.000 KMPH 0 1 3 0 0.000 FT 0.000 FT 0.000 FT 1 - 55. 1 3.000 M 3.000 M 3.850 M 2.000 0.010 0 - 56. 0 0 0 0 0.575 1.000 1.000 0.850 0 - 57. 0 0 0 0.892 0.800 -0.550 58. !> END GENERATED DATA BLOCK 59. INT 1.68306 1.68306 HEIG 0 4.572 60. TYPE 2 LWX 61. <! STAAD PRO GENERATED DATA DO NOT MODIFY !!! 62. ASCE-7-2010:PARAMS 240.000 KMPH 0 1 3 0 0.000 FT 0.000 FT 0.000 FT 1 - STAAD SPACE -- PAGE NO. 3
63. 1 3.000 M 3.000 M 3.850 M 2.000 0.010 1 - 64. 0 0 0 0 0.575 1.000 1.000 0.850 0 - 65. 0 0 0 0.892 -0.500 0.550 66. !> END GENERATED DATA BLOCK 67. INT -1.32657 -1.32657 HEIG 0 3 68. TYPE 3 WWZ 69. <! STAAD PRO GENERATED DATA DO NOT MODIFY !!! 70. ASCE-7-2010:PARAMS 240.000 KMPH 0 1 3 0 0.000 FT 0.000 FT 0.000 FT 1 - 71. 1 3.000 M 3.850 M 3.000 M 2.000 0.010 0 - 72. 0 0 0 0 0.575 1.000 1.000 0.850 0 - 73. 0 0 0 0.895 0.800 -0.550 74. !> END GENERATED DATA BLOCK 75. INT 1.68564 1.68564 HEIG 0 4.572 76. TYPE 4 LWZ 77. <! STAAD PRO GENERATED DATA DO NOT MODIFY !!! 78. ASCE-7-2010:PARAMS 240.000 KMPH 0 1 3 0 0.000 FT 0.000 FT 0.000 FT 1 - 79. 1 3.000 M 3.850 M 3.000 M 2.000 0.010 1 - 80. 0 0 0 0 0.575 1.000 1.000 0.850 0 - 81. 0 0 0 0.895 -0.443 0.550 82. !> END GENERATED DATA BLOCK 83. INT -1.26066 -1.26066 HEIG 0 3 84. CHECK SOFT STORY ASCE7 85. LOAD 1 LOADTYPE SEISMIC TITLE EX 86. UBC LOAD X 1 DEC 1 ACC 0.05 87. PERFORM ANALYSIS
P R O B L E M S T A T I S T I C S ----------------------------------- NUMBER OF JOINTS 18 NUMBER OF MEMBERS 22 NUMBER OF PLATES 0 NUMBER OF SOLIDS 0 NUMBER OF SURFACES 0 NUMBER OF SUPPORTS 4
SOLVER USED IS THE OUT-OF-CORE BASIC SOLVER
ORIGINAL/FINAL BAND-WIDTH= 12/ 5/ 48 DOF TOTAL PRIMARY LOAD CASES = 1, TOTAL DEGREES OF FREEDOM = 48 TOTAL LOAD COMBINATION CASES = 0 SO FAR. SIZE OF STIFFNESS MATRIX = 3 DOUBLE KILO-WORDS REQRD/AVAIL. DISK SPACE = 12.1/ 862715.7 MB
STAAD SPACE -- PAGE NO. 4
VERTICAL STRUCTURAL IRREGULARITIES : SOFT STORY CHECK - ASCE/SEI 7-05 -------- ---------- -------------- STORY FL. LEVEL IN METE S T A T U S ----- ----------------- -------------------- X Z
1 1.00 OK OK 2 3.00 OK OK
NOTE : NO SOFT STOREY IS DETECTED.
*********************************************************** * * * X DIRECTION : Ta = 0.167 Tb = 0.081 Tuser = 0.000 * * T = 0.081, LOAD FACTOR = 1.000 * * UBC TYPE = 97 * * UBC FACTOR V = 0.1294 x 73.89 = 9.56 KN * * * *********************************************************** ************************************************************************
***NOTE: SEISMIC LOAD IS ACTING AT CENTER OF MASS FOR RIGID DIAPHRAGM. TORSION FROM STATIC ECCENTRICITY (esi) IS INCLUDED IN ANALYSIS. DYNAMIC ECCENTRICITY APPLIED = DEC - 1
LOAD NO.: 1 DIRECTION : X UNIT - METE STORY LEVEL DYN. ECC. (dec) ACC. ECC. (aec) DESIGN ECC. ----- ----- --------------- --------------- --------------- X Z X Z X Z dec + aec dec + aec STAAD SPACE -- PAGE NO. 5
1 1.00 0.00 0.00 0.19 0.15 0.00 0.15 2 3.00 0.00 0.00 0.19 0.15 0.00 0.15 ************************************************************************ 88. CHANGE 89. LOAD 2 LOADTYPE SEISMIC TITLE EZ 90. UBC LOAD Z 1 DEC 1 ACC 0.05 91. PERFORM ANALYSIS
*********************************************************** * * * Z DIRECTION : Ta = 0.167 Tb = 0.077 Tuser = 0.000 * * T = 0.077, LOAD FACTOR = 1.000 * * UBC TYPE = 97 * * UBC FACTOR V = 0.1294 x 73.89 = 9.56 KN * * * *********************************************************** STAAD SPACE -- PAGE NO. 6
LOAD NO.: 2 DIRECTION : Z UNIT - METE STORY LEVEL DYN. ECC. (dec) ACC. ECC. (aec) DESIGN ECC. ----- ----- --------------- --------------- --------------- X Z X Z X Z dec + aec dec + aec
1 1.00 0.00 0.00 0.19 0.15 0.19 0.00 2 3.00 0.00 0.00 0.19 0.15 0.19 0.00 ************************************************************************ 92. CHANGE 93. LOAD 3 LOADTYPE WIND TITLE WL1 94. WIND LOAD X 1 TYPE 1 YR 1 3 95. WIND LOAD -X 1 TYPE 2 YR 1 3 96. LOAD 4 LOADTYPE WIND TITLE WL2 97. WIND LOAD X -1 TYPE 1 YR 1 3 98. WIND LOAD -X -1 TYPE 2 YR 1 3 99. LOAD 5 LOADTYPE WIND TITLE WL3 100. WIND LOAD Z 1 TYPE 3 YR 1 3 101. WIND LOAD -Z 1 TYPE 4 YR 1 3 STAAD SPACE -- PAGE NO. 7
102. LOAD 6 LOADTYPE WIND TITLE WL4 103. WIND LOAD Z -1 TYPE 3 YR 1 3 ZR 3 3 104. WIND LOAD -Z -1 TYPE 4 YR 1 3 105. LOAD 7 LOADTYPE DEAD TITLE DL 106. REFERENCE LOAD 107. R1 -1.0 108. LOAD 8 LOADTYPE LIVE TITLE LL 109. MEMBER LOAD 110. 19 22 UNI GY -1.35 111. LOAD COMB 9 GENERATED NSCP 2015 DRIFT CHECK COMBINATION 1 112. 7 1.2 8 0.5 1 1.0 113. LOAD COMB 10 GENERATED NSCP 2015 DRIFT CHECK COMBINATION 2 114. 7 1.2 8 0.5 2 1.0 115. LOAD COMB 11 GENERATED NSCP 2015 DRIFT CHECK COMBINATION 3 116. 7 1.2 8 0.5 1 -1.0 117. LOAD COMB 12 GENERATED NSCP 2015 DRIFT CHECK COMBINATION 4 118. 7 1.2 8 0.5 2 -1.0 119. LOAD COMB 13 GENERATED NSCP 2015 DRIFT CHECK COMBINATION 5 120. 7 0.9 1 1.0 121. LOAD COMB 14 GENERATED NSCP 2015 DRIFT CHECK COMBINATION 6 122. 7 0.9 2 1.0 123. LOAD COMB 15 GENERATED NSCP 2015 DRIFT CHECK COMBINATION 7 124. 7 0.9 1 -1.0 125. LOAD COMB 16 GENERATED NSCP 2015 DRIFT CHECK COMBINATION 8 126. 7 0.9 2 -1.0 127. LOAD COMB 17 GENERATED NSCP 2015 USD COMBINATION 1 128. 7 1.4 129. LOAD COMB 18 GENERATED NSCP 2015 USD COMBINATION 2 130. 7 1.2 8 1.6 131. LOAD COMB 19 GENERATED NSCP 2015 USD COMBINATION 3 132. 7 1.2 8 0.5 133. LOAD COMB 20 GENERATED NSCP 2015 USD COMBINATION 4 134. 7 1.2 3 0.5 135. LOAD COMB 21 GENERATED NSCP 2015 USD COMBINATION 5 136. 7 1.2 4 0.5 137. LOAD COMB 22 GENERATED NSCP 2015 USD COMBINATION 6 138. 7 1.2 5 0.5 139. LOAD COMB 23 GENERATED NSCP 2015 USD COMBINATION 7 140. 7 1.2 6 0.5 141. LOAD COMB 24 GENERATED NSCP 2015 USD COMBINATION 8 142. 7 1.2 8 0.5 3 1.0 143. LOAD COMB 25 GENERATED NSCP 2015 USD COMBINATION 9 144. 7 1.2 8 0.5 4 1.0 145. LOAD COMB 26 GENERATED NSCP 2015 USD COMBINATION 10 146. 7 1.2 8 0.5 5 1.0 147. LOAD COMB 27 GENERATED NSCP 2015 USD COMBINATION 11 148. 7 1.2 8 0.5 6 1.0 STAAD SPACE -- PAGE NO. 8
149. LOAD COMB 28 GENERATED NSCP 2015 USD COMBINATION 12 150. 7 1.2 8 0.5 1 1.0 151. LOAD COMB 29 GENERATED NSCP 2015 USD COMBINATION 13 152. 7 1.2 8 0.5 2 1.0 153. LOAD COMB 30 GENERATED NSCP 2015 USD COMBINATION 14 154. 7 0.9 3 1.0 155. LOAD COMB 31 GENERATED NSCP 2015 USD COMBINATION 15 156. 7 0.9 4 1.0 157. LOAD COMB 32 GENERATED NSCP 2015 USD COMBINATION 16 158. 7 0.9 5 1.0 159. LOAD COMB 33 GENERATED NSCP 2015 USD COMBINATION 17 160. 7 0.9 6 1.0 161. LOAD COMB 34 GENERATED NSCP 2015 USD COMBINATION 18 162. 7 0.9 1 1.0 163. LOAD COMB 35 GENERATED NSCP 2015 USD COMBINATION 19 164. 7 0.9 2 1.0 165. LOAD COMB 36 NSCP 2015 ASD 1 166. 7 1.0 167. LOAD COMB 37 NSCP 2015 ASD 2 168. 7 1.0 8 1.0 169. LOAD COMB 38 NSCP 2015 ASD 3 170. 7 1.0 8 0.75 171. LOAD COMB 39 NSCP 2015 ASD 4 172. 7 1.0 3 0.6 173. LOAD COMB 40 NSCP 2015 ASD 5 174. 7 1.0 4 0.6 175. LOAD COMB 41 NSCP 2015 ASD 6 176. 7 1.0 5 0.6 177. LOAD COMB 42 NSCP 2015 ASD 7 178. 7 1.0 6 0.6 179. LOAD COMB 43 NSCP 2015 ASD 8 180. 7 1.0 1 0.714286 181. LOAD COMB 44 NSCP 2015 ASD 9 182. 7 1.0 2 0.714286 183. PERFORM ANALYSIS
NOTE : NO SOFT STOREY IS DETECTED. STAAD SPACE -- PAGE NO. 9
184. LOAD LIST 9 TO 44 185. PRINT STORY DRIFT 0.004200 STAAD SPACE -- PAGE NO. 10
STORY HEIGHT LOAD AVG. DISP(CM ) DRIFT(CM ) RATIO STATUS ------------------------------------------------------------------------------------------ (METE) X Z X Z BASE= 0.00 ALLOW. DRIFT = L / 238
1 0.00 9 0.0000 0.0000 0.0000 0.0000 L /999999 PASS 10 0.0000 0.0000 0.0000 0.0000 L /999999 PASS 11 0.0000 0.0000 0.0000 0.0000 L /999999 PASS 12 0.0000 0.0000 0.0000 0.0000 L /999999 PASS 13 0.0000 0.0000 0.0000 0.0000 L /999999 PASS 14 0.0000 0.0000 0.0000 0.0000 L /999999 PASS 15 0.0000 0.0000 0.0000 0.0000 L /999999 PASS 16 0.0000 0.0000 0.0000 0.0000 L /999999 PASS 17 0.0000 0.0000 0.0000 0.0000 L /999999 PASS 18 0.0000 0.0000 0.0000 0.0000 L /999999 PASS 19 0.0000 0.0000 0.0000 0.0000 L /999999 PASS 20 0.0000 0.0000 0.0000 0.0000 L /999999 PASS 21 0.0000 0.0000 0.0000 0.0000 L /999999 PASS 22 0.0000 0.0000 0.0000 0.0000 L /999999 PASS 23 0.0000 0.0000 0.0000 0.0000 L /999999 PASS 24 0.0000 0.0000 0.0000 0.0000 L /999999 PASS 25 0.0000 0.0000 0.0000 0.0000 L /999999 PASS STAAD SPACE -- PAGE NO. 11
26 0.0000 0.0000 0.0000 0.0000 L /999999 PASS 27 0.0000 0.0000 0.0000 0.0000 L /999999 PASS 28 0.0000 0.0000 0.0000 0.0000 L /999999 PASS 29 0.0000 0.0000 0.0000 0.0000 L /999999 PASS 30 0.0000 0.0000 0.0000 0.0000 L /999999 PASS 31 0.0000 0.0000 0.0000 0.0000 L /999999 PASS 32 0.0000 0.0000 0.0000 0.0000 L /999999 PASS 33 0.0000 0.0000 0.0000 0.0000 L /999999 PASS 34 0.0000 0.0000 0.0000 0.0000 L /999999 PASS 35 0.0000 0.0000 0.0000 0.0000 L /999999 PASS 36 0.0000 0.0000 0.0000 0.0000 L /999999 PASS 37 0.0000 0.0000 0.0000 0.0000 L /999999 PASS 38 0.0000 0.0000 0.0000 0.0000 L /999999 PASS 39 0.0000 0.0000 0.0000 0.0000 L /999999 PASS 40 0.0000 0.0000 0.0000 0.0000 L /999999 PASS 41 0.0000 0.0000 0.0000 0.0000 L /999999 PASS 42 0.0000 0.0000 0.0000 0.0000 L /999999 PASS 43 0.0000 0.0000 0.0000 0.0000 L /999999 PASS 44 0.0000 0.0000 0.0000 0.0000 L /999999 PASS 2 1.00 9 0.0194 -0.0002 0.0194 0.0002 L / 5164 PASS 10 -0.0003 0.0175 0.0003 0.0175 L / 5727 PASS 11 -0.0194 -0.0002 0.0194 0.0002 L / 5164 PASS 12 0.0003 -0.0178 0.0003 0.0178 L / 5623 PASS 13 0.0194 -0.0001 0.0194 0.0001 L / 5164 PASS 14 -0.0003 0.0175 0.0003 0.0175 L / 5713 PASS 15 -0.0194 -0.0001 0.0194 0.0001 L / 5164 PASS 16 0.0003 -0.0177 0.0003 0.0177 L / 5636 PASS 17 -0.0000 -0.0002 0.0000 0.0002 L /999999 PASS STAAD SPACE -- PAGE NO. 12
18 -0.0000 -0.0002 0.0000 0.0002 L /999999 PASS 19 -0.0000 -0.0002 0.0000 0.0002 L /999999 PASS 20 0.0251 -0.0002 0.0251 0.0002 L / 3983 PASS 21 -0.0251 -0.0002 0.0251 0.0002 L / 3983 PASS 22 -0.0000 0.0283 0.0000 0.0283 L / 3537 PASS 23 -0.0000 -0.0286 0.0000 0.0286 L / 3497 PASS 24 0.0502 -0.0002 0.0502 0.0002 L / 1991 PASS 25 -0.0502 -0.0002 0.0502 0.0002 L / 1991 PASS 26 -0.0000 0.0567 0.0000 0.0567 L / 1763 PASS 27 -0.0000 -0.0570 0.0000 0.0570 L / 1754 PASS 28 0.0194 -0.0002 0.0194 0.0002 L / 5164 PASS 29 -0.0003 0.0175 0.0003 0.0175 L / 5727 PASS 30 0.0502 -0.0001 0.0502 0.0001 L / 1991 PASS 31 -0.0502 -0.0001 0.0502 0.0001 L / 1991 PASS 32 -0.0000 0.0567 0.0000 0.0567 L / 1762 PASS 33 -0.0000 -0.0570 0.0000 0.0570 L / 1755 PASS 34 0.0194 -0.0001 0.0194 0.0001 L / 5164 PASS 35 -0.0003 0.0175 0.0003 0.0175 L / 5713 PASS STAAD SPACE -- PAGE NO. 13
36 -0.0000 -0.0001 0.0000 0.0001 L /999999 PASS 37 -0.0000 -0.0001 0.0000 0.0001 L /999999 PASS 38 -0.0000 -0.0001 0.0000 0.0001 L /999999 PASS 39 0.0301 -0.0001 0.0301 0.0001 L / 3319 PASS 40 -0.0301 -0.0001 0.0301 0.0001 L / 3319 PASS 41 -0.0000 0.0340 0.0000 0.0340 L / 2943 PASS 42 -0.0000 -0.0343 0.0000 0.0343 L / 2919 PASS 43 0.0138 -0.0001 0.0138 0.0001 L / 7230 PASS 44 -0.0002 0.0125 0.0002 0.0125 L / 8030 PASS 3 3.00 9 0.0650 -0.0009 0.0457 0.0008 L / 4378 PASS 10 -0.0000 0.0566 0.0003 0.0391 L / 5109 PASS 11 -0.0650 -0.0009 0.0457 0.0008 L / 4378 PASS 12 -0.0000 -0.0585 0.0003 0.0407 L / 4914 PASS 13 0.0650 -0.0007 0.0457 0.0006 L / 4378 PASS 14 -0.0000 0.0568 0.0003 0.0393 L / 5083 PASS 15 -0.0650 -0.0007 0.0457 0.0006 L / 4378 PASS 16 -0.0000 -0.0582 0.0003 0.0405 L / 4938 PASS 17 -0.0000 -0.0011 0.0000 0.0009 L /999999 PASS 18 -0.0000 -0.0009 0.0000 0.0008 L /999999 PASS 19 -0.0000 -0.0009 0.0000 0.0008 L /999999 PASS 20 0.1219 -0.0009 0.0968 0.0008 L / 2065 PASS 21 -0.1219 -0.0009 0.0968 0.0008 L / 2065 PASS 22 -0.0000 0.1345 0.0000 0.1062 L / 1883 PASS 23 -0.0000 -0.1364 0.0000 0.1078 L / 1856 PASS 24 0.2439 -0.0009 0.1937 0.0008 L / 1032 PASS 25 -0.2439 -0.0009 0.1937 0.0008 L / 1032 PASS 26 -0.0000 0.2699 0.0000 0.2132 L / 938 PASS 27 -0.0000 -0.2718 0.0000 0.2148 L / 931 PASS STAAD SPACE -- PAGE NO. 14
28 0.0650 -0.0009 0.0457 0.0008 L / 4378 PASS 29 -0.0000 0.0566 0.0003 0.0391 L / 5109 PASS 30 0.2439 -0.0007 0.1937 0.0006 L / 1032 PASS 31 -0.2439 -0.0007 0.1937 0.0006 L / 1032 PASS 32 -0.0000 0.2702 0.0000 0.2134 L / 937 PASS 33 -0.0000 -0.2716 0.0000 0.2146 L / 932 PASS 34 0.0650 -0.0007 0.0457 0.0006 L / 4378 PASS 35 -0.0000 0.0568 0.0003 0.0393 L / 5083 PASS 36 -0.0000 -0.0008 0.0000 0.0006 L /999999 PASS 37 -0.0000 -0.0008 0.0000 0.0006 L /999999 PASS 38 -0.0000 -0.0008 0.0000 0.0006 L /999999 PASS 39 0.1463 -0.0008 0.1162 0.0006 L / 1721 PASS 40 -0.1463 -0.0008 0.1162 0.0006 L / 1721 PASS 41 -0.0000 0.1617 0.0000 0.1277 L / 1565 PASS 42 -0.0000 -0.1633 0.0000 0.1290 L / 1550 PASS 43 0.0465 -0.0008 0.0326 0.0006 L / 6130 PASS 44 -0.0000 0.0403 0.0002 0.0279 L / 7176 PASS 186. PRINT DIA CR STAAD SPACE -- PAGE NO. 15
************************************************************ CENTRE OF RIGIDITY UNIT - METE ------------------ ----------- DIAPHRAM FL. LEVEL X-COORDINATE Z-COORDINATE
1 1.000 1.925 1.500 2 3.000 1.925 1.500
187. FINISH
please help
This is most likely because in your reference load case, which you have used for seismic weight definition for your seismic case, you have applied selfweight in -Y and other member loads in +Y. So part of the weight is cancelling out.
Also when you post a question in future, please do not upload an analysis output file ( anl file) or the input commands. Instead please upload the .std file.