I am receiving an unstable structure error. i have researched this error on the forum. I was able to run the analysis if I used the "Direct Solver" instead of the "Direct Sparse Solver", but the analysis takes up to 20min for a relatively simple structure.
Any help would be appreciated. I have also send in my model to the Secure File Upload. Thank you!
The program's wind load generation for big buildings with small low-roof areas is limited. The program will load the low roof with windward and leeward pressure which can be too much. See: https://communities.bentley.com/products/ram-staad/w/structural_analysis_and_design__wiki/2052/ram-frame---wind-loads-faq
The frames perpendicular to the load will take some small amount of the lateral force in this case since the columns are continuous through 2 stories. You could pin the columns vs. weak axis bending at the bottom of the top story to alleviate that.
Seth, thank you for the information. I have gone through my model and made some adjustments, but am still not getting the results I would think are correct. It appears the loads are not being distributed properly (even when I use a rigid diaphragm). An exterior frame line is not receiving any of the wind loads. It looks like the frames that are perpendicular to the wind load are taking the loads. I uploaded my file to the secure file upload. Thanks!
/resized-image/__size/320x240/__key/communityserver-discussions-components-files/5932/pastedimage1600268821210v1.png
Sounds like you have a semi-rigid diaphragm. I sometimes coach people to increase the deck thickness and turn on the out-of-plane stiffness when that's needed for stability.
See: