STAAD FOUNDATION ADVANCED (DESIGN OF COMBINED FOOTING)

Good day Engineers!!! Can anyone help me solve this problem that I encountered in my program? Thanks!!! Footing Design.sfa

16:24:17
[ERROR] UNABLE TO DETERMINE A SUITABLE WIDTH FOR THE GIVEN LOADING. LAST WIDTH TRIED = 3.609 FT

16:39:30
[ERROR] UNABLE TO DETERMINE A SUITABLE LENGTH FOR THE GIVEN LOADING. LAST LENGTH TRIED = 23.130 FT
16:44:15
[ERROR] THE BAR SIZE CAN NOT BE SELECTED. PLEASE CHECK THE MAXIMUM AND MINIMUM BAR SIZES INDICATED, LOAD CASE = 109

17:20:25
[ERROR] UNABLE TO DETERMINE A SUITABLE WIDTH FOR THE GIVEN LOADING. LAST WIDTH TRIED = 4.101 FT

Parents Reply Children
  • By primary, I presume you are referring to pure component load cases. It doesn't make sense to design for such load cases. Designing for a load case that represents just wind, or pure seismic means you will have a lot of de-stabilizing effect due to lateral loads, and no stabilizing effect from the vertical loads to accompany that. If you do this, you may end up with much larger foundation sizes than warranted, or a failure when there shouldn't be one.

    It makes sense to solve just for the load combinations since they represent the simultaneous action of gravity with live, gravity with wind, gravity with seismic, etc.

    This principle applies to all types of foundations - isolated footings, pilecaps, mats, etc.