Ram Elements Wood Design Repetitive Member Factor Cr
I am using spaced wood sections defined by your Leo SPCa.leo.  There is one section in the standard United States group and we added several sections to a custom group for our office.
Our sections typically use 4 combined members.  The members are typically 2x12's.  So, we would have (2)2x12's nailed together with a space of 5.5" and another set of (2)2x12's on the other side.  The total width of the beam-column is 11.5".  These sections have bending in the major axis and axial stress.  I have attached an Output Report for a beam-column  that has a total of (2)4x12's and (2)2/12's as one example.
The program has a check box to apply the Repetitive Member Factor Cr in the Wood Design Parameters.  The output shows that the member is a repetitive member under the heading "DESIGN CRITERIA", but the section "DESIGN FOR FLEXURE" for M33 shows Cr = 1.00 instead of 1.15.  I checked the box to use 1.15.  Why is Ram Elements ignoring this factor?
On another note for the same type spaced sections using SPCa.leo, the program will let me set Lu, but the spreadsheet tools will not assign Le.  The error message says it only works for rectangular or circular sections.  Why?
PDF
  • The help topic for Cr indicates it only applies to dimension lumber (e.g. S4S) which is probably why it's not being considered here.
    Repetitive Member
    This flag can be applied to joists, truss chords, etc. which are in contact or spaced not more than 24" on centers and fulfill the conditions specified in Section 4.3.9. of the Specifications.
    This parameter defines the value to be used for the repetitive member factor (Cr) for dimension lumber.
    You could possibly modify the .leo to force the program to consider your section as dimension lumber. I think it's the line that says FORMULATION='LUMBER' that matters here (vs. 'GLULAM')
  • Seth,
    I checked the Bentley Leo SPCa.  If this helps, here is the header information:
    //common parameters
    UNIT='In'
    TYPE='SOLID'
    SHAPE='Spaced'
    CODE='WOOD'
    CONNECTION='CONTINUOUS'
    COMMENTARY='(Rectangular section for columns spaced by blocks "Condition a")'
    Page 235 of the Ram Elements manual "For wood members, the following formulations are available: LUMBER: This formulation should be used with rectangular and rounded sections. Spaced columns are also considered. This formulation is explained in Chapter 4 of the NDS-Specifications."
    NDS 4.3.9 Repetitive Factor Cr applies to 3 or more members of dimension lumber that is "in contact or spaced no more than 24" on center.". Based on NDS, multi-ply beams and joists can use Cr as long as the members used are not timbers (Table 4D) or Glulam.  The commentary C4.3.9 specifically addresses multi-ply beams as long as there are 3 or more members.
    The S4S lumber used here are standard sizes and have design values from Table 4A.  It looks like Ram recognizes that I checked the Cr box but then does not use it when you look at the Wood Design output.
  • We have a different interpretation of that code section. We are looking at the total width of the section. It means that if you have, for example, 3 (or more) rafters spaced 24" on center (or less) and that the rafters are each 4" wide (or less) you can apply Cr. You could use a section made up of 2 x 1.5" wide shapes and those would still get the advantage of the Cr factor, because each is 3" wide, but if you make a section with 3 x 1.5" layers (4.5" wide) that would no longer qualify.  LIkewise a section using 2 x 1.5" sections with a 1.5" gap in the middle would also be too wide.
  • I felt much the same way as you do until I read the NDS Commentary C4.3.9.  It is clear. The last paragraph reads:
    "The repetitive member increase also applies to an assembly
    of three or more essentially parallel members of
    equal size and of the same orientation which are in direct
    contact with each other (28). In this case the transverse
    elements may be mechanical fasteners such as nails, nail
    gluing, tongue and groove joints, or bearing plates. The
    required condition is that the three or more members act
    together to resist the applied moment. "
  • That helps, my copy of the NDS doesn't have the commentary.
  • We asked for a clarification to the NDS and they replied. The dimension limit should not be applied to assemblies. Therefore, we will implement and remove the size validation. In this way, the user will have the freedom to check it where it is required, but also will have the responsibility to check the size limitation when needed.
    Answer Verified By: SVGregory
Reply Children