RAM Structural - Mezzanine Lateral

We have a project with two internal mezzanines (therefore no wind load), and we are in SDC A, so we would like to handle their seismic lateral through full-height column bending of the columns that run through the mezzanine. We tried turning all of the columns that go through the mezzanine to lateral columns, but got P-Delta errors even using the maximum size W14 column. This was with a rigid diaphragm.

We tried changing the diaphragm to semi-rigid, but when we looked at the deflected shape it showed the diaphragm bending as if it were a moment frame with the lateral columns.

Is there a correct way to model this situation in RAM? I saw a response from Seth Guthrie on eng-tips from several years ago (https://www.eng-tips.com/viewthread.cfm?qid=306557) where he addresses this and says "Note, these types of structures tend to be very sensitive to P-Delta amplification and I usually recommend no P-Delta analysis, at least in the preliminary design."

Can we be confident that everything is being designed correctly if we turn P-Delta off? And this is not for a preliminary design, this is for Construction Documents, so any advice you can give would be very helpful.

Thank you.