Hello,I have a large steel industrial building that I am only trying to do a deflection check on in this model. The strength design is done in a different model under AISC 2016. This deflection model is under AISC 2010 as I have been directed by coworkers that there is a bug or something with the 2016 version showing deflection incorrectly. My problem is that I am getting a failure in one small portion of a beam only, and it is 94 times the allowable deflection, and for a combination that is not the worst case combination. The member is not failing in any other way that I can see. Any input would be greatly appreciated! Also, sorry for a messy command file, this is my first structure in STAAD and it just so happens it's very very irregular as well.
STAAD SPACESTART JOB INFORMATIONENGINEER DATE 12-May-21END JOB INFORMATIONINPUT WIDTH 79UNIT INCHES KIPJOINT COORDINATES1 -631.226 0 -594.746; 2 -631.22 201 -594.746; 3 -631.22 471 -594.746;4 -631.22 713 -594.746; 5 -631.22 900 -594.746; 6 -630.972 900 -984.889;7 -630.972 1168 -779.746; 8 -630.972 1168 -594.746; 9 -630.97 0 -1138.75;10 -630.97 201 -1138.75; 11 -630.97 471 -1138.75; 12 -630.97 713 -1138.75;13 -630.97 900 -1138.75; 14 -630.97 1168 -1138.75; 15 -630.97 713 -1074.46;16 -630.97 900 -1074.46; 17 -630.97 471 -1074.08; 18 -630.97 201 -1073.19;19 -630.97 713 -1039.08; 20 -630.97 900 -1036.17; 21 -630.97 201 -1023.98;22 -630.97 471 -1011.62; 23 -630.97 713 -987.078; 24 -630.97 201 -975.211;25 -630.97 471 -954.624; 26 -630.97 713 -935.078; 27 -630.97 900 -933.603;28 -630.97 201 -926.298; 29 -630.97 713 -893.078; 30 -630.97 471 -892.992;31 -630.97 900 -882.318; 32 -630.97 201 -877.384; 33 -630.97 713 -855.972;34 -630.97 471 -840.084; 35 -630.97 900 -831.032; 36 -630.97 201 -828.47;37 -630.97 713 -817.975; 38 -630.97 0 -779.746; 39 -630.97 201 -779.746;40 -630.97 471 -779.746; 41 -630.97 713 -779.746; 42 -630.97 900 -779.746;43 -603.108 471 -1138.75; 44 -603.106 713 -1138.75; 45 -603.106 900 -1138.75;46 -603.106 713 -1074.46; 47 -603.106 900 -1074.46; 48 -603.106 471 -1074.08;49 -598.462 201 -1073.19; 50 -598.462 201 -1023.98; 51 -567.148 201 -1073.19;52 -567.148 201 -1023.98; 53 -566.448 471 -1138.75; 54 -566.446 713 -1138.75;55 -566.446 900 -1138.75; 56 -566.446 713 -1074.46; 57 -566.446 900 -1074.46;58 -566.446 471 -1074.08; 59 -558.35 713 -1039.08; 60 -558.35 713 -987.078;61 -558.35 713 -935.078; 62 -558.35 713 -893.078; 63 -554.537 471 -1074.08;64 -554.537 471 -954.624; 65 -554.537 471 -892.992; 66 -554.532 471 -1011.62;67 -525.248 201 -1073.19; 68 -525.248 201 -1023.98; 69 -523.22 201 -779.746;70 -523.22 471 -779.746; 71 -523.22 713 -779.746; 72 -523.22 900 -779.746;73 -523.22 713 -743.746; 74 -523.22 900 -733.496; 75 -523.22 201 -733.306;76 -523.22 471 -733.306; 77 -523.22 713 -705.246; 78 -523.22 900 -687.246;79 -523.22 201 -687.056; 80 -523.22 471 -687.056; 81 -523.22 713 -649.996;82 -523.22 900 -640.996; 83 -523.22 201 -640.806; 84 -523.22 471 -640.806;85 -523.22 201 -594.746; 86 -523.22 471 -594.746; 87 -523.22 713 -594.746;88 -523.22 900 -594.746; 89 -519.359 471 -1074.08; 90 -519.359 471 -1011.62;91 -519.359 471 -954.624; 92 -519.359 471 -892.992; 93 -516.636 471 -1138.75;94 -516.63 713 -1138.75; 95 -516.63 900 -1138.75; 96 -516.63 713 -1074.46;97 -516.63 900 -1074.46; 98 -516.63 471 -1074.08; 99 -494.967 201 -1073.19;100 -494.967 201 -1023.98; 101 -485.865 713 -1039.08;102 -485.865 713 -987.078; 103 -485.865 713 -935.078;104 -485.865 713 -893.078; 105 -479.976 471 -1138.75; 106 -479.97 713 -1138.75;107 -479.97 900 -1138.75; 108 -479.97 713 -1074.46; 109 -479.97 900 -1074.46;110 -479.97 471 -1074.08; 111 -452.976 471 -1074.09; 112 -452.976 713 -1029.97;113 -452.976 471 -1021.18; 114 -452.976 713 -851.475; 115 -452.97 0 -1138.75;116 -452.97 201 -1138.75; 117 -452.97 471 -1138.75; 118 -452.97 713 -1138.75;119 -452.97 900 -1138.75; 120 -452.97 1168 -1138.75; 121 -452.97 713 -1074.46;122 -452.97 900 -1074.46; 123 -452.97 201 -1073.19; 124 -452.97 713 -1039.08;125 -452.97 900 -1036.17; 126 -452.97 201 -1023.98; 127 -452.97 201 -1019.19;128 -452.97 471 -1011.62; 129 -452.97 713 -987.078; 130 -452.97 900 -984.889;131 -452.97 471 -983.552; 132 -452.97 713 -975.975; 133 -452.97 201 -975.211;134 -452.97 201 -965.191; 135 -452.97 471 -954.624; 136 -452.97 713 -935.078;137 -452.97 900 -933.603; 138 -452.97 471 -930.637; 139 -452.97 201 -926.298;140 -452.97 713 -921.975; 141 -452.97 201 -905.191; 142 -452.97 713 -893.078;143 -452.97 471 -892.992; 144 -452.97 900 -882.318; 145 -452.97 201 -877.384;146 -452.97 713 -855.975; 147 -452.97 201 -845.191; 148 -452.97 471 -840.081;149 -452.97 471 -838.624; 150 -452.97 900 -831.032; 151 -452.97 201 -828.47;152 -452.97 713 -817.975; 153 -452.97 0 -779.746; 154 -452.97 201 -779.746;155 -452.97 471 -779.746; 156 -452.97 713 -779.746; 157 -452.97 900 -779.746;158 -452.97 1168 -779.746; 159 -452.97 713 -743.746; 160 -452.97 900 -733.496;161 -452.97 201 -733.306; 162 -452.97 471 -733.306; 163 -452.97 471 -711.904;164 -452.97 713 -705.246; 165 -452.97 900 -687.246; 166 -452.97 201 -687.056;167 -452.97 471 -687.056; 168 -452.97 471 -658.989; 169 -452.97 713 -649.996;170 -452.97 900 -640.996; 171 -452.97 201 -640.806; 172 -452.97 471 -640.806;173 -452.97 0 -594.746; 174 -452.97 201 -594.746; 175 -452.97 471 -594.746;176 -452.97 713 -594.746; 177 -452.97 900 -594.746; 178 -452.97 1168 -594.746;179 -412.441 471 -1074.09; 180 -412.441 471 -1021.18;181 -412.441 471 -983.552; 182 -412.441 471 -930.637;183 -412.441 471 -892.995; 184 -412.441 471 -840.081;185 -412.441 471 -779.746; 186 -412.441 471 -711.904;187 -412.441 471 -658.989; 188 -404.26 713 -1029.97; 189 -404.26 713 -975.975;190 -394.97 201 -1138.75; 191 -394.97 471 -1138.75; 192 -394.97 713 -1138.75;193 -394.97 900 -1138.75; 194 -394.97 713 -1074.46; 195 -394.97 900 -1074.46;196 -394.97 471 -1074.09; 197 -394.97 201 -1073.19; 198 -375.396 713 -1029.97;199 -375.396 713 -975.975; 200 -355.239 471 -1074.09;201 -355.239 471 -1021.18; 202 -355.239 471 -983.552;203 -355.239 471 -930.637; 204 -355.239 471 -892.995;205 -355.239 471 -840.081; 206 -355.239 471 -779.746;207 -355.239 471 -711.904; 208 -355.239 471 -658.989; 209 -334.97 201 -1138.75;210 -334.97 471 -1138.75; 211 -334.97 713 -1138.75; 212 -334.97 900 -1138.75;213 -334.97 900 -1074.46; 214 -334.97 471 -1074.09; 215 -334.97 201 -1073.19;216 -334.968 713 -1074.46; 217 -311.699 713 -1029.97;218 -311.699 713 -975.975; 219 -311.699 713 -921.975;220 -311.699 713 -855.975; 221 -300.975 201 -1138.75;222 -300.975 471 -1138.75; 223 -300.975 713 -1138.75;224 -300.975 900 -1138.75; 225 -300.975 713 -1074.46;226 -300.975 900 -1074.46; 227 -300.975 471 -1074.09;228 -300.975 201 -1073.19; 229 -296.97 713 -705.246; 230 -296.97 713 -671.246;231 -296.97 713 -649.996; 232 -296.97 713 -640.246; 233 -296.97 713 -594.746;234 -269.112 201 -1073.19; 235 -269.112 201 -1019.19;236 -269.112 201 -965.191; 237 -269.112 201 -905.191;238 -269.112 201 -845.191; 239 -264.894 900 -687.246;240 -264.894 900 -677.871; 241 -264.894 900 -640.996;242 -264.894 900 -622.622; 243 -264.894 900 -594.746; 244 -262.97 713 -705.246;245 -259.97 201 -1138.75; 246 -259.97 471 -1138.75; 247 -259.97 713 -1138.75;248 -259.97 900 -1138.75; 249 -259.97 713 -1074.46; 250 -259.97 900 -1074.46;251 -259.97 471 -1074.09; 252 -259.97 201 -1073.19; 253 -251.47 713 -594.746;254 -240.473 713 -594.746; 255 -236.244 713 -921.975;256 -236.244 713 -855.975; 257 -236.225 713 -1029.97;258 -236.225 713 -975.975; 259 -233.522 201 -1073.19;260 -233.522 201 -965.191; 261 -233.522 201 -845.191;262 -228.973 713 -705.246; 263 -227.049 900 -687.246;264 -227.049 900 -677.871; 265 -227.049 900 -640.996;266 -227.049 900 -622.622; 267 -227.049 900 -594.746; 268 -223.97 201 -1138.75;269 -223.97 471 -1138.75; 270 -223.97 713 -1138.75; 271 -223.97 900 -1138.75;272 -223.97 713 -1074.46; 273 -223.97 900 -1074.46; 274 -223.97 471 -1074.09;275 -223.97 201 -1073.19; 276 -188.976 471 -1074.09; 277 -188.976 201 -989.998;278 -188.97 0 -1138.75; 279 -188.97 201 -1138.75; 280 -188.97 471 -1138.75;281 -188.97 713 -1138.75; 282 -188.97 900 -1138.75; 283 -188.97 1168 -1138.75;284 -188.97 713 -1109.75; 285 -188.97 201 -1104; 286 -188.97 900 -1087.46;287 -188.97 713 -1074.46; 288 -188.97 900 -1074.46; 289 -188.97 201 -1073.19;290 -188.97 201 -1047; 291 -188.97 900 -1036.17; 292 -188.97 713 -1029.97;293 -188.97 471 -1021.18; 294 -188.97 900 -984.889; 295 -188.97 471 -983.552;296 -188.97 713 -975.975; 297 -188.97 201 -965.191; 298 -188.97 201 -937.273;299 -188.97 900 -933.603; 300 -188.97 471 -930.637; 301 -188.97 471 -925.536;302 -188.97 713 -921.975; 303 -188.97 471 -892.995; 304 -188.97 201 -884.701;305 -188.97 900 -882.318; 306 -188.97 471 -877.509; 307 -188.97 713 -871.746;308 -188.97 713 -855.975; 309 -188.97 201 -845.191; 310 -188.97 471 -840.081;311 -188.97 201 -832.129; 312 -188.97 900 -831.032; 313 -188.97 471 -828.533;314 -188.97 713 -817.975; 315 -188.97 0 -779.746; 316 -188.97 201 -779.746;317 -188.97 471 -779.746; 318 -188.97 713 -779.746; 319 -188.97 900 -779.746;320 -188.97 1168 -779.746; 321 -188.97 713 -743.746; 322 -188.97 900 -733.496;323 -188.97 201 -733.306; 324 -188.97 471 -733.306; 325 -188.97 471 -711.904;326 -188.97 713 -705.246; 327 -188.97 713 -693.246; 328 -188.97 900 -687.246;329 -188.97 201 -687.056; 330 -188.97 471 -687.056; 331 -188.97 713 -665.243;332 -188.97 471 -658.989; 333 -188.97 713 -646.249; 334 -188.97 713 -643.996;335 -188.97 900 -640.996; 336 -188.97 201 -640.806; 337 -188.97 471 -640.806;338 -188.97 0 -594.746; 339 -188.97 201 -594.746; 340 -188.97 471 -594.746;341 -188.97 713 -594.746; 342 -188.97 900 -594.746; 343 -188.97 1168 -594.746;344 -128.97 713 -693.246; 345 -128.97 713 -657.392; 346 -128.97 713 -643.996;347 -128.97 713 -634.1; 348 -128.97 713 -594.746; 349 -112.957 900 -687.246;350 -112.957 900 -640.996; 351 -112.957 900 -594.746;352 -107.676 201 -1138.75; 353 -107.676 201 -1104; 354 -103.97 900 -984.889;355 -103.968 900 -933.603; 356 -103.449 201 -1047; 357 -103.449 201 -989.998;358 -94.3461 713 -693.246; 359 -90.9662 713 -594.746;360 -86.9739 713 -594.746; 361 -83.5939 713 -693.246;362 -74.9732 900 -984.889; 363 -74.9732 900 -933.603; 364 -71.5593 201 -1047;365 -71.5593 201 -989.998; 366 -65.9569 900 -687.246;367 -65.9569 900 -640.996; 368 -65.9569 900 -594.746;369 -54.2172 201 -1138.75; 370 -54.2172 201 -1104; 371 -49.97 713 -693.246;372 -49.97 713 -658.428; 373 -49.97 713 -643.996; 374 -49.97 713 -633.065;375 -49.97 713 -594.746; 376 10.03 0 -1138.75; 377 10.03 201 -1138.75;378 10.03 471 -1138.75; 379 10.03 713 -1138.75; 380 10.03 900 -1138.75;381 10.03 1168 -1138.75; 382 10.03 713 -1109.75; 383 10.03 201 -1104;384 10.03 900 -1087.46; 385 10.03 201 -1078.75; 386 10.03 713 -1074.46;387 10.03 900 -1074.46; 388 10.03 471 -1068.36; 389 10.03 201 -1047;390 10.03 713 -1038.75; 391 10.03 900 -1036.17; 392 10.03 471 -1012.18;393 10.03 713 -994.746; 394 10.03 201 -989.998; 395 10.03 900 -984.889;396 10.03 201 -970.746; 397 10.03 713 -950.746; 398 10.03 471 -948.483;399 10.03 201 -937.273; 400 10.03 900 -933.603; 401 10.03 471 -925.532;402 10.03 713 -921.972; 403 10.03 201 -918.51; 404 10.03 713 -896.084;405 10.03 201 -884.701; 406 10.03 900 -882.318; 407 10.03 471 -877.509;408 10.03 471 -875.746; 409 10.03 713 -871.746; 410 10.03 713 -837.915;411 10.03 201 -832.129; 412 10.03 900 -831.032; 413 10.03 471 -828.533;414 10.03 201 -821.297; 415 10.03 713 -817.746; 416 10.03 0 -779.746;417 10.03 201 -779.746; 418 10.03 471 -779.746; 419 10.03 713 -779.746;420 10.03 900 -779.746; 421 10.03 1168 -779.746; 422 10.03 713 -743.746;423 10.03 900 -733.496; 424 10.03 201 -733.306; 425 10.03 471 -733.306;426 10.03 713 -705.246; 427 10.03 713 -693.246; 428 10.03 900 -687.246;429 10.03 201 -687.056; 430 10.03 471 -687.056; 431 10.03 713 -665.246;432 10.03 713 -646.246; 433 10.03 713 -643.996; 434 10.03 900 -642.996;435 10.03 900 -640.992; 436 10.03 201 -640.806; 437 10.03 471 -640.806;438 10.03 0 -594.746; 439 10.03 201 -594.746; 440 10.03 471 -594.746;441 10.03 713 -594.746; 442 10.03 900 -594.746; 443 10.03 1168 -594.746;444 38.1339 201 -918.51; 445 38.1339 201 -889.297; 446 38.1339 201 -845.128;447 38.1339 201 -821.297; 448 39.4058 201 -1078.75; 449 39.4058 201 -1062;450 39.4058 201 -1032; 451 39.4058 201 -987.79; 452 39.4058 201 -970.746;453 42.5083 471 -1068.36; 454 42.5083 471 -1012.18; 455 42.5083 471 -992.119;456 42.5083 471 -948.483; 457 42.5083 471 -925.532; 458 42.5083 471 -875.746;459 42.5083 471 -849.458; 460 42.5083 471 -828.528; 461 42.5083 471 -779.746;462 50.03 201 -1138.75; 463 50.03 471 -1138.75; 464 50.03 713 -1138.75;465 50.03 900 -1138.75; 466 50.03 201 -1078.75; 467 50.03 713 -1074.46;468 50.03 900 -1074.46; 469 50.03 471 -1068.36; 470 50.03 713 -705.246;471 54.1676 900 -687.246; 472 54.1676 900 -671.664; 473 54.1676 900 -640.992;474 54.1676 900 -629.996; 475 54.168 900 -594.746; 476 61.53 713 -594.746;477 72.5253 713 -594.746; 478 78.528 471 -1068.36; 479 78.528 471 -1012.18;480 78.528 471 -992.119; 481 78.528 471 -948.483; 482 78.528 471 -925.532;483 78.528 471 -875.746; 484 78.528 471 -849.619; 485 78.528 471 -827.746;486 78.528 471 -779.746; 487 80.136 900 -594.746; 488 80.1376 900 -687.246;489 80.1376 900 -671.664; 490 80.1376 900 -640.992; 491 80.1376 900 -629.996;492 81.6305 201 -1078.75; 493 81.6305 201 -1062; 494 81.6305 201 -1032;495 81.6305 201 -1029.76; 496 81.6305 201 -987.79; 497 81.6305 201 -970.746;498 81.6305 201 -918.51; 499 81.6305 201 -889.297; 500 81.6305 201 -869.27;501 81.6305 201 -845.128; 502 81.6305 201 -821.297; 503 84.0253 713 -705.246;504 90.03 201 -1138.75; 505 90.03 471 -1138.75; 506 90.03 713 -1138.75;507 90.03 900 -1138.75; 508 90.03 201 -1078.75; 509 90.03 713 -1074.46;510 90.03 900 -1074.46; 511 90.03 471 -1068.36; 512 123.66 201 -1138.75;513 123.66 471 -1138.75; 514 123.66 713 -1138.75; 515 123.66 900 -1138.75;516 123.66 201 -1078.75; 517 123.66 713 -1074.46; 518 123.66 900 -1074.46;519 123.66 471 -1068.36; 520 126.03 713 -705.246; 521 126.03 713 -664.314;522 126.03 713 -663.242; 523 126.03 713 -648.251; 524 126.03 713 -647.179;525 126.03 713 -594.746; 526 147.03 713 -1038.75; 527 147.03 713 -994.746;528 147.03 713 -950.746; 529 147.03 713 -896.084; 530 147.03 713 -837.915;531 147.03 713 -779.746; 532 147.161 471 -1068.36; 533 147.161 471 -1012.18;534 147.161 471 -948.483; 535 147.161 471 -925.532; 536 147.161 471 -875.746;537 147.161 471 -827.746; 538 147.161 471 -779.746; 539 152.292 201 -1029.76;540 152.292 201 -970.746; 541 152.293 201 -995.746; 542 156.66 201 -1138.75;543 156.66 471 -1138.75; 544 156.66 201 -1078.75; 545 156.66 471 -1068.36;546 157.03 713 -1138.75; 547 157.03 900 -1138.75; 548 157.03 713 -1074.46;549 157.03 900 -1074.46; 550 163.035 900 -687.246; 551 163.035 900 -673.496;552 163.045 900 -640.992; 553 163.045 900 -627.496; 554 163.045 900 -594.746;555 164.2 713 -705.246; 556 174.924 713 -594.746; 557 175.339 713 -896.084;558 175.339 713 -855.344; 559 175.339 713 -828.225; 560 175.339 713 -779.746;561 175.415 713 -1038.75; 562 175.415 713 -997.996; 563 175.415 713 -970.887;564 175.415 713 -950.746; 565 175.465 471 -1068.36; 566 175.465 471 -998.006;567 175.465 471 -970.887; 568 175.465 471 -948.483; 569 175.465 471 -925.532;570 175.465 471 -888.532; 571 175.465 471 -855.506; 572 175.465 471 -828.387;573 175.465 471 -779.746; 574 189.136 713 -594.746; 575 189.255 201 -1029.76;576 189.255 201 -995.746; 577 189.255 201 -970.746; 578 190.524 471 -1068.36;579 190.53 201 -1138.75; 580 190.53 471 -1138.75; 581 190.53 201 -1078.75;582 191.03 713 -1138.75; 583 191.03 900 -1138.75; 584 191.03 713 -1074.46;585 191.03 900 -1074.46; 586 199.86 713 -705.246; 587 201.015 900 -687.246;588 201.015 900 -673.496; 589 201.015 900 -640.992; 590 201.015 900 -627.496;591 201.015 900 -594.746; 592 223.88 713 -1138.75; 593 223.88 900 -1138.75;594 223.88 713 -1074.46; 595 223.88 900 -1074.46; 596 224.38 201 -1138.75;597 224.38 471 -1138.75; 598 224.38 201 -1078.75; 599 224.38 471 -1068.36;600 239.028 201 -1029.76; 601 239.028 900 -733.496; 602 239.03 0 -1138.75;603 239.03 201 -1138.75; 604 239.03 471 -1138.75; 605 239.03 713 -1138.75;606 239.03 900 -1138.75; 607 239.03 1168 -1138.75; 608 239.03 713 -1094.75;609 239.03 201 -1078.75; 610 239.03 471 -1078.75; 611 239.03 713 -1074.46;612 239.03 900 -1074.46; 613 239.03 471 -1068.36; 614 239.03 900 -1052.46;615 239.03 713 -1050.75; 616 239.03 713 -1038.76; 617 239.03 900 -1036.18;618 239.03 471 -1035.99; 619 239.03 201 -1003.78; 620 239.03 471 -998.006;621 239.03 713 -997.996; 622 239.03 900 -984.889; 623 239.03 471 -970.887;624 239.03 713 -970.887; 625 239.03 201 -970.746; 626 239.03 713 -950.746;627 239.03 471 -948.483; 628 239.03 713 -942.746; 629 239.03 900 -933.603;630 239.03 471 -925.532; 631 239.03 201 -918.51; 632 239.03 201 -908.746;633 239.03 713 -896.084; 634 239.03 471 -888.532; 635 239.03 900 -882.318;636 239.03 471 -870.636; 637 239.03 201 -869.27; 638 239.03 471 -855.506;639 239.03 713 -855.344; 640 239.03 201 -844.246; 641 239.03 713 -837.915;642 239.03 471 -836.581; 643 239.03 900 -831.032; 644 239.03 471 -828.387;645 239.03 713 -828.225; 646 239.03 201 -821.297; 647 239.03 0 -779.746;648 239.03 201 -779.746; 649 239.03 471 -779.746; 650 239.03 713 -779.746;651 239.03 900 -779.746; 652 239.03 1168 -779.746; 653 239.03 713 -743.746;654 239.03 201 -733.306; 655 239.03 471 -733.306; 656 239.03 713 -705.246;657 239.03 900 -687.246; 658 239.03 201 -687.056; 659 239.03 471 -687.056;660 239.03 713 -663.242; 661 239.03 713 -649.996; 662 239.03 900 -640.996;663 239.03 201 -640.806; 664 239.03 471 -640.806; 665 239.03 0 -594.746;666 239.03 201 -594.746; 667 239.03 471 -594.746; 668 239.03 713 -594.746;669 239.03 900 -594.746; 670 239.03 1168 -594.746; 671 267.302 900 -1052.46;672 267.302 900 -933.603; 673 284.03 900 -1138.75; 674 284.03 900 -1074.46;675 284.185 201 -1138.75; 676 284.185 471 -1138.75; 677 284.185 201 -1078.75;678 284.185 471 -1078.75; 679 299.03 713 -705.246; 680 299.03 713 -670.043;681 299.03 713 -649.996; 682 299.03 713 -641.449; 683 299.03 713 -594.746;684 307.788 201 -1029.75; 685 307.792 201 -1003.78; 686 307.792 201 -970.74;687 307.792 201 -908.746; 688 315.208 201 -1138.75; 689 315.208 471 -1138.75;690 315.208 201 -1078.75; 691 315.208 471 -1078.75; 692 327.68 900 -687.246;693 327.68 900 -640.992; 694 327.68 900 -594.746; 695 329.03 900 -1138.75;696 329.03 900 -1074.46; 697 334.233 713 -705.246; 698 345.247 900 -1052.46;699 345.247 900 -993.032; 700 345.247 900 -933.603; 701 345.733 713 -594.746;702 346.239 201 -1138.75; 703 346.239 471 -1138.75; 704 346.239 201 -1078.75;705 346.239 471 -1078.75; 706 356.327 713 -594.746; 707 367.827 713 -705.246;708 374.03 900 -1138.75; 709 374.03 900 -1074.46; 710 374.381 201 -1138.75;711 374.381 471 -1138.75; 712 374.381 201 -1078.75; 713 374.381 471 -1078.75;714 374.631 713 -1138.75; 715 374.631 713 -1094.75; 716 374.631 713 -1050.75;717 374.68 900 -687.246; 718 374.68 900 -640.996; 719 374.68 900 -594.746;720 403.03 713 -705.246; 721 403.03 713 -670.043; 722 403.03 713 -641.449;723 403.03 713 -594.746; 724 408.014 900 -1138.75; 725 408.014 900 -1074.46;726 408.03 201 -1138.75; 727 408.03 471 -1138.75; 728 408.03 713 -1138.75;729 408.03 201 -1078.75; 730 408.03 471 -1078.75; 731 408.03 713 -1050.75;732 413.264 201 -1029.75; 733 413.264 201 -970.74; 734 413.268 201 -908.746;735 421.03 201 -779.746; 736 421.03 471 -779.746; 737 421.03 713 -779.746;738 421.03 900 -779.746; 739 421.03 713 -743.746; 740 421.03 900 -733.496;741 421.03 201 -733.306; 742 421.03 471 -733.306; 743 421.03 713 -705.246;744 421.03 900 -687.246; 745 421.03 201 -687.056; 746 421.03 471 -687.056;747 421.03 900 -640.996; 748 421.03 201 -640.806; 749 421.03 471 -640.806;750 421.03 201 -594.746; 751 421.03 471 -594.746; 752 421.03 713 -594.746;753 421.03 900 -594.746; 754 439.31 713 -1138.75; 755 439.31 713 -1082.75;756 439.31 713 -1050.75; 757 440.014 900 -1138.75; 758 440.014 900 -1074.46;759 440.06 201 -1138.75; 760 440.06 471 -1138.75; 761 440.06 201 -1078.75;762 440.06 471 -1078.75; 763 461.53 713 -942.746; 764 461.53 713 -896.084;765 461.53 713 -837.915; 766 481.03 201 -1138.75; 767 481.03 201 -1119.5;768 481.03 201 -1099.5; 769 481.03 201 -1078.75; 770 484.014 900 -1138.75;771 484.014 900 -1074.46; 772 484.53 471 -1138.75; 773 484.53 471 -1078.75;774 491.405 713 -942.746; 775 491.405 713 -896.084; 776 491.405 713 -837.915;777 529.03 0 -1138.75; 778 529.03 201 -1138.75; 779 529.03 471 -1138.75;780 529.03 713 -1138.75; 781 529.03 900 -1138.75; 782 529.03 1168 -1138.75;783 529.03 201 -1119.5; 784 529.03 201 -1099.5; 785 529.03 713 -1082.75;786 529.03 201 -1078.75; 787 529.03 471 -1078.75; 788 529.03 900 -1074.46;789 529.03 900 -1052.46; 790 529.03 713 -1050.75; 791 529.03 471 -1035.99;792 529.03 201 -1029.75; 793 529.03 471 -998.004; 794 529.03 713 -996.746;795 529.03 900 -993.032; 796 529.03 201 -970.74; 797 529.03 471 -948.48;798 529.03 713 -942.746; 799 529.03 900 -933.603; 800 529.03 471 -925.536;801 529.03 713 -896.084; 802 529.03 900 -882.318; 803 529.03 471 -870.636;804 529.03 201 -844.246; 805 529.03 713 -837.915; 806 529.03 471 -836.581;807 529.03 900 -831.032; 808 529.03 0 -779.746; 809 529.03 201 -779.746;810 529.03 471 -779.746; 811 529.03 713 -779.746; 812 529.03 900 -779.746;813 529.03 1168 -779.746; 814 529.03 0 -594.746; 815 529.03 201 -594.746;816 529.03 471 -594.746; 817 529.03 713 -594.746; 818 529.03 900 -594.746;819 529.03 1168 -594.746; 820 529.032 201 -908.746;MEMBER INCIDENCES1 1 2; 2 2 3; 3 3 4; 4 4 5; 5 5 8; 6 39 2; 7 40 3; 8 41 4; 9 42 5; 10 8 7;11 20 6; 12 7 13; 13 7 14; 14 6 27; 15 42 7; 16 9 10; 17 10 11; 18 11 12;19 12 13; 20 13 14; 21 12 15; 22 13 16; 23 11 17; 24 10 18; 25 15 19; 26 16 20;27 18 21; 28 17 22; 29 19 23; 30 21 24; 31 22 25; 32 23 26; 33 10 38; 34 9 39;35 11 39; 36 40 10; 37 12 40; 38 41 11; 39 13 41; 40 12 42; 41 14 42; 42 24 28;43 25 30; 44 26 29; 45 27 31; 46 28 32; 47 29 33; 48 30 34; 49 31 35; 50 32 36;51 33 37; 52 34 40; 53 35 42; 54 36 39; 55 37 41; 56 38 39; 57 39 40; 58 40 41;59 41 42; 60 11 43; 61 12 44; 62 13 45; 63 15 46; 64 16 47; 65 17 48; 66 18 49;67 21 50; 68 48 43; 69 46 44; 70 47 45; 71 49 50; 72 59 19; 73 60 23; 74 61 26;75 62 29; 76 25 64; 77 30 65; 78 22 66; 79 43 53; 80 44 54; 81 45 55; 82 46 56;83 47 57; 84 48 58; 85 49 51; 86 50 52; 87 85 2; 88 86 3; 89 87 4; 90 88 5;91 39 69; 92 40 70; 93 41 71; 94 42 72; 95 51 52; 96 58 53; 97 56 54; 98 57 55;99 58 63; 100 60 59; 101 62 61; 102 64 65; 103 63 66; 104 66 64; 105 51 67;106 52 68; 107 6 130; 108 7 158; 109 178 8; 110 10 116; 111 14 120; 112 20 125;113 24 133; 114 27 137; 115 28 139; 116 31 144; 117 32 145; 118 33 146;119 34 148; 120 35 150; 121 36 151; 122 37 152; 123 53 93; 124 54 94;125 55 95; 126 56 96; 127 57 97; 128 63 89; 129 64 91; 130 65 92; 131 66 90;132 67 68; 133 71 73; 134 72 74; 135 75 69; 136 70 76; 137 73 77; 138 74 78;139 79 75; 140 76 80; 141 77 81; 142 78 82; 143 83 79; 144 80 84; 145 81 87;146 82 88; 147 85 83; 148 84 86; 149 101 59; 150 102 60; 151 103 61;152 104 62; 153 89 90; 154 90 91; 155 91 92; 156 89 98; 157 98 93; 158 96 94;159 97 95; 160 67 99; 161 68 100; 162 93 105; 163 94 106; 164 95 107;165 96 108; 166 97 109; 167 98 110; 168 99 100; 169 69 154; 170 70 155;171 71 156; 172 72 157; 173 159 73; 174 74 160; 175 75 161; 176 76 162;177 77 164; 178 78 165; 179 79 166; 180 80 167; 181 81 169; 182 82 170;183 83 171; 184 84 172; 185 85 174; 186 86 175; 187 87 176; 188 88 177;189 90 128; 190 91 135; 191 92 143; 192 102 101; 193 104 103; 194 110 105;195 108 106; 196 109 107; 197 99 123; 198 100 126; 199 124 101; 200 129 102;201 136 103; 202 142 104; 203 105 117; 204 111 110; 205 106 118; 206 107 119;207 108 121; 208 109 122; 209 111 113; 210 117 111; 211 124 112; 212 113 128;213 112 129; 214 146 114; 215 114 152; 216 115 116; 217 116 117; 218 117 118;219 118 119; 220 119 120; 221 118 121; 222 119 122; 223 116 123; 224 121 124;225 122 125; 226 123 126; 227 126 127; 228 125 130; 229 128 131; 230 127 133;231 129 132; 232 133 134; 233 131 135; 234 155 118; 235 117 156; 236 118 157;237 156 119; 238 157 120; 239 119 158; 240 120 158; 241 130 137; 242 132 136;243 134 139; 244 135 138; 245 136 140; 246 139 141; 247 138 143; 248 137 144;249 140 142; 250 141 145; 251 142 146; 252 143 148; 253 145 147; 254 144 150;255 148 149; 256 147 151; 257 149 155; 258 150 157; 259 151 154; 260 152 156;261 153 154; 262 154 155; 263 155 156; 264 156 157; 265 157 158; 266 156 159;267 157 160; 268 154 161; 269 155 162; 270 159 164; 271 162 163; 272 160 165;273 161 166; 274 163 167; 275 174 153; 276 154 173; 277 155 174; 278 175 154;279 158 178; 280 164 169; 281 167 168; 282 165 170; 283 166 171; 284 168 172;285 169 176; 286 170 177; 287 171 174; 288 172 175; 289 173 174; 290 174 175;291 175 176; 292 176 177; 293 177 178; 294 179 111; 295 113 180; 296 131 181;297 138 182; 298 143 183; 299 148 184; 300 155 185; 301 163 186; 302 168 187;303 112 188; 304 132 189; 305 116 190; 306 117 191; 307 118 192; 308 119 193;309 121 194; 310 122 195; 311 123 197; 312 179 180; 313 181 182; 314 183 184;315 185 184; 316 185 186; 317 186 187; 318 188 189; 319 179 196; 320 192 194;321 193 195; 322 191 196; 323 190 197; 324 188 198; 325 189 199; 326 180 201;327 181 202; 328 182 203; 329 183 204; 330 184 205; 331 185 206; 332 186 207;333 187 208; 334 140 219; 335 146 220; 336 198 199; 337 196 200; 338 164 229;339 169 231; 340 176 233; 341 190 209; 342 191 210; 343 192 211; 344 193 212;345 195 213; 346 197 215; 347 194 216; 348 127 235; 349 134 236; 350 237 141;351 147 238; 352 165 239; 353 170 241; 354 177 243; 355 200 201; 356 202 203;357 204 205; 358 206 205; 359 206 207; 360 207 208; 361 200 214; 362 198 217;363 199 218; 364 212 213; 365 210 214; 366 209 215; 367 211 216; 368 115 279;369 278 116; 370 279 117; 371 116 280; 372 280 118; 373 117 281; 374 281 119;375 118 282; 376 283 119; 377 282 120; 378 120 283; 379 125 291; 380 130 294;381 137 299; 382 144 305; 383 150 312; 384 152 314; 385 154 316; 386 156 318;387 157 319; 388 158 320; 389 159 321; 390 160 322; 391 161 323; 392 166 329;393 171 336; 394 173 339; 395 338 174; 396 174 339; 397 339 175; 398 174 340;399 175 340; 400 340 176; 401 175 341; 402 341 177; 403 176 342; 404 343 177;405 342 178; 406 343 178; 407 209 221; 408 210 222; 409 211 223; 410 212 224;411 213 226; 412 214 227; 413 215 228; 414 216 225; 415 217 218; 416 219 220;417 223 225; 418 224 226; 419 222 227; 420 221 228; 421 229 230; 422 230 231;423 231 232; 424 232 233; 425 228 234; 426 221 245; 427 222 246; 428 223 247;429 224 248; 430 225 249; 431 226 250; 432 227 251; 433 229 244; 434 230 244;435 232 253; 436 233 253; 437 219 255; 438 220 256; 439 217 257; 440 218 258;441 201 293; 442 202 295; 443 203 300; 444 204 303; 445 205 310; 446 206 317;447 207 325; 448 208 332; 449 234 235; 450 235 236; 451 236 237; 452 237 238;453 239 240; 454 240 241; 455 241 242; 456 242 243; 457 234 252; 458 247 249;459 248 250; 460 246 251; 461 245 252; 462 236 260; 463 238 261; 464 252 259;465 244 262; 466 239 263; 467 264 240; 468 241 265; 469 266 242; 470 253 254;471 243 267; 472 245 268; 473 246 269; 474 247 270; 475 248 271; 476 249 272;477 250 273; 478 251 274; 479 255 256; 480 257 258; 481 259 260; 482 260 261;483 259 275; 484 263 264; 485 264 265; 486 265 266; 487 266 267; 488 270 272;489 271 273; 490 269 274; 491 268 275; 492 334 254; 493 254 341; 494 255 302;495 256 308; 496 257 292; 497 258 296; 498 260 297; 499 261 309; 500 262 326;501 331 262; 502 263 328; 503 265 335; 504 267 342; 505 274 276; 506 268 279;507 269 280; 508 270 281; 509 271 282; 510 272 287; 511 273 288; 512 275 289;513 280 276; 514 276 293; 515 290 277; 516 277 297; 517 278 279; 518 279 280;519 280 281; 520 281 282; 521 282 283; 522 281 284; 523 279 285; 524 282 286;525 284 287; 526 285 289; 527 286 288; 528 289 290; 529 288 291; 530 287 292;531 291 294; 532 292 296; 533 293 295; 534 317 281; 535 280 318; 536 281 319;537 318 282; 538 319 283; 539 282 320; 540 283 320; 541 294 299; 542 295 300;543 297 298; 544 296 302; 545 300 301; 546 298 304; 547 301 303; 548 299 305;549 302 307; 550 303 306; 551 304 309; 552 307 308; 553 306 310; 554 305 312;555 309 311; 556 308 314; 557 310 313; 558 311 316; 559 312 319; 560 313 317;561 314 318; 562 315 316; 563 316 317; 564 317 318; 565 318 319; 566 319 320;567 318 321; 568 319 322; 569 316 323; 570 317 324; 571 321 326; 572 324 325;573 322 328; 574 323 329; 575 325 330; 576 326 327; 577 339 315; 578 316 338;579 317 339; 580 340 316; 581 320 343; 582 327 331; 583 330 332; 584 328 335;585 329 336; 586 331 333; 587 332 337; 588 333 334; 589 334 341; 590 335 342;591 336 339; 592 337 340; 593 338 339; 594 339 340; 595 340 341; 596 341 342;597 342 343; 598 327 344; 599 346 334; 600 341 348; 601 328 349; 602 335 350;603 342 351; 604 279 352; 605 285 353; 606 294 354; 607 299 355; 608 277 357;609 290 356; 610 344 345; 611 345 346; 612 346 347; 613 347 348; 614 349 350;615 350 351; 616 344 358; 617 345 358; 618 347 359; 619 348 359; 620 352 353;621 355 354; 622 356 357; 623 354 362; 624 355 363; 625 376 279; 626 278 377;627 280 377; 628 279 378; 629 280 378; 630 280 379; 631 378 281; 632 281 379;633 281 380; 634 379 282; 635 282 380; 636 380 283; 637 282 381; 638 283 381;639 284 382; 640 286 384; 641 291 391; 642 298 399; 643 301 401; 644 302 402;645 304 405; 646 305 406; 647 306 407; 648 307 409; 649 311 411; 650 312 412;651 313 413; 652 314 415; 653 316 417; 654 317 418; 655 318 419; 656 319 420;657 320 421; 658 321 422; 659 322 423; 660 323 424; 661 324 425; 662 329 429;663 330 430; 664 336 436; 665 337 437; 666 438 339; 667 338 439; 668 339 439;669 340 439; 670 339 440; 671 340 440; 672 340 441; 673 440 341; 674 341 442;675 441 342; 676 442 343; 677 342 443; 678 343 443; 679 349 366; 680 350 367;681 351 368; 682 359 360; 683 358 361; 684 356 364; 685 357 365; 686 352 369;687 353 370; 688 363 362; 689 364 365; 690 374 360; 691 360 375; 692 361 371;693 372 361; 694 366 367; 695 367 368; 696 369 370; 697 371 372; 698 372 373;699 373 374; 700 374 375; 701 362 395; 702 363 400; 703 364 389; 704 365 394;705 366 428; 706 367 435; 707 368 442; 708 369 377; 709 370 383; 710 371 427;711 373 433; 712 375 441; 713 376 377; 714 377 378; 715 378 379; 716 379 380;717 380 381; 718 379 382; 719 377 383; 720 380 384; 721 378 388; 722 382 386;723 383 385; 724 384 387; 725 385 389; 726 386 390; 727 387 391; 728 388 392;729 389 394; 730 390 393; 731 391 395; 732 394 396; 733 392 398; 734 393 397;735 418 379; 736 378 419; 737 379 420; 738 419 380; 739 420 381; 740 380 421;741 381 421; 742 395 400; 743 396 399; 744 398 401; 745 397 402; 746 399 403;747 402 404; 748 400 406; 749 403 405; 750 401 407; 751 404 409; 752 407 408;753 405 411; 754 406 412; 755 409 410; 756 408 413; 757 410 415; 758 411 414;759 412 420; 760 414 417; 761 415 419; 762 416 417; 763 417 418; 764 418 419;765 419 420; 766 420 421; 767 419 422; 768 420 423; 769 417 424; 770 418 425;771 422 426; 772 423 428; 773 424 429; 774 425 430; 775 426 427; 776 439 416;777 417 438; 778 418 439; 779 440 417; 780 421 443; 781 427 431; 782 428 434;783 429 436; 784 430 437; 785 431 432; 786 432 433; 787 434 435; 788 433 441;789 435 442; 790 436 439; 791 437 440; 792 438 439; 793 439 440; 794 440 441;795 441 442; 796 442 443; 797 444 403; 798 447 414; 799 448 385; 800 452 396;801 388 453; 802 454 392; 803 398 456; 804 401 457; 805 458 408; 806 460 413;807 418 461; 808 377 462; 809 378 463; 810 379 464; 811 380 465; 812 386 467;813 387 468; 814 426 470; 815 431 470; 816 428 471; 817 435 473; 818 442 475;819 433 476; 820 441 476; 821 444 445; 822 445 446; 823 446 447; 824 448 449;825 449 450; 826 450 451; 827 451 452; 828 453 454; 829 454 455; 830 455 456;831 457 458; 832 458 459; 833 459 460; 834 460 461; 835 466 448; 836 453 469;837 462 466; 838 464 467; 839 465 468; 840 463 469; 841 471 472; 842 472 473;843 473 474; 844 474 475; 845 498 444; 846 445 499; 847 446 501; 848 502 447;849 449 493; 850 450 494; 851 455 480; 852 451 496; 853 497 452; 854 456 481;855 457 482; 856 459 484; 857 461 486; 858 469 478; 859 492 466; 860 470 503;861 476 477; 862 475 487; 863 471 488; 864 489 472; 865 473 490; 866 491 474;867 462 504; 868 463 505; 869 464 506; 870 465 507; 871 467 509; 872 468 510;873 478 479; 874 479 480; 875 480 481; 876 482 483; 877 483 484; 878 484 485;879 485 486; 880 390 526; 881 393 527; 882 397 528; 883 404 529; 884 410 530;885 419 531; 886 491 487; 887 488 489; 888 489 490; 889 490 491; 890 492 493;891 493 494; 892 494 495; 893 495 496; 894 496 497; 895 498 499; 896 499 500;897 500 501; 898 501 502; 899 478 511; 900 508 492; 901 504 508; 902 506 509;903 507 510; 904 505 511; 905 523 477; 906 477 525; 907 503 520; 908 522 503;909 504 512; 910 505 513; 911 506 514; 912 507 515; 913 516 508; 914 509 517;915 510 518; 916 511 519; 917 479 533; 918 481 534; 919 482 535; 920 483 536;921 485 537; 922 486 538; 923 495 539; 924 540 497; 925 488 550; 926 487 554;927 490 552; 928 512 516; 929 514 517; 930 515 518; 931 513 519; 932 423 601;933 381 607; 934 391 617; 935 395 622; 936 400 629; 937 406 635; 938 412 643;939 417 648; 940 420 651; 941 421 652; 942 422 653; 943 424 654; 944 425 655;945 429 658; 946 430 659; 947 436 663; 948 437 664; 949 439 666; 950 440 667;951 443 670; 952 521 520; 953 522 521; 954 523 522; 955 524 523; 956 525 524;957 519 532; 958 512 542; 959 513 543; 960 544 516; 961 514 546; 962 515 547;963 517 548; 964 518 549; 965 520 555; 966 521 555; 967 526 527; 968 527 528;969 529 530; 970 530 531; 971 532 533; 972 533 534; 973 535 536; 974 536 537;975 537 538; 976 524 556; 977 525 556; 978 532 545; 979 539 541; 980 541 540;981 542 544; 982 543 545; 983 546 548; 984 547 549; 985 631 498; 986 500 637;987 646 502; 988 529 557; 989 531 560; 990 526 561; 991 528 564; 992 534 568;993 535 569; 994 538 573; 995 550 551; 996 551 552; 997 552 553; 998 553 554;999 545 565; 1000 539 575; 1001 577 540; 1002 541 576; 1003 542 579;1004 543 580; 1005 581 544; 1006 546 582; 1007 547 583; 1008 548 584;1009 549 585; 1010 557 558; 1011 558 559; 1012 559 560; 1013 561 562;1014 562 563; 1015 563 564; 1016 565 566; 1017 566 567; 1018 567 568;1019 569 570; 1020 570 571; 1021 571 572; 1022 572 573; 1023 550 587;1024 588 551; 1025 555 586; 1026 552 589; 1027 590 553; 1028 556 574;1029 554 591; 1030 565 578; 1031 575 576; 1032 576 577; 1033 580 578;1034 579 581; 1035 582 584; 1036 583 585; 1037 587 588; 1038 588 589;1039 589 590; 1040 590 591; 1041 557 633; 1042 639 558; 1043 645 559;1044 560 650; 1045 561 616; 1046 621 562; 1047 624 563; 1048 564 626;1049 566 620; 1050 567 623; 1051 568 627; 1052 569 630; 1053 570 634;1054 571 638; 1055 572 644; 1056 573 649; 1057 578 599; 1058 579 596;1059 580 597; 1060 582 592; 1061 583 593; 1062 598 581; 1063 584 594;1064 585 595; 1065 661 574; 1066 574 668; 1067 575 600; 1068 625 577;1069 586 656; 1070 660 586; 1071 587 657; 1072 589 662; 1073 591 669;1074 592 594; 1075 593 595; 1076 596 598; 1077 597 599; 1078 592 605;1079 593 606; 1080 594 611; 1081 595 612; 1082 596 603; 1083 597 604;1084 609 598; 1085 599 613; 1086 609 600; 1087 600 619; 1088 651 601;1089 601 657; 1090 602 603; 1091 603 604; 1092 604 605; 1093 605 606;1094 606 607; 1095 605 608; 1096 603 609; 1097 604 610; 1098 606 612;1099 608 611; 1100 610 613; 1101 612 614; 1102 611 615; 1103 613 618;1104 615 616; 1105 614 617; 1106 616 621; 1107 618 620; 1108 617 622;1109 619 625; 1110 620 623; 1111 621 624; 1112 624 626; 1113 623 627;1114 649 605; 1115 604 650; 1116 605 651; 1117 650 606; 1118 651 607;1119 606 652; 1120 607 652; 1121 622 629; 1122 626 628; 1123 625 631;1124 627 630; 1125 628 633; 1126 631 632; 1127 629 635; 1128 630 634;1129 632 637; 1130 634 636; 1131 633 639; 1132 636 638; 1133 637 640;1134 635 643; 1135 639 641; 1136 638 642; 1137 641 645; 1138 640 646;1139 642 644; 1140 643 651; 1141 644 649; 1142 645 650; 1143 646 648;1144 647 648; 1145 648 649; 1146 649 650; 1147 650 651; 1148 651 652;1149 650 653; 1150 648 654; 1151 649 655; 1152 653 656; 1153 654 658;1154 655 659; 1155 666 647; 1156 648 665; 1157 649 666; 1158 667 648;1159 652 670; 1160 656 660; 1161 657 662; 1162 658 663; 1163 659 664;1164 660 661; 1165 661 668; 1166 662 669; 1167 663 666; 1168 664 667;1169 665 666; 1170 666 667; 1171 667 668; 1172 668 669; 1173 669 670;1174 614 671; 1175 629 672; 1176 606 673; 1177 612 674; 1178 603 675;1179 604 676; 1180 609 677; 1181 610 678; 1182 671 672; 1183 656 679;1184 681 661; 1185 668 683; 1186 600 684; 1187 619 685; 1188 625 686;1189 632 687; 1190 657 692; 1191 662 693; 1192 669 694; 1193 673 674;1194 677 675; 1195 678 676; 1196 679 680; 1197 680 681; 1198 681 682;1199 682 683; 1200 675 688; 1201 676 689; 1202 677 690; 1203 678 691;1204 671 698; 1205 672 700; 1206 673 695; 1207 674 696; 1208 605 714;1209 715 608; 1210 615 716; 1211 684 685; 1212 685 686; 1213 686 687;1214 690 688; 1215 691 689; 1216 679 697; 1217 697 680; 1218 701 682;1219 683 701; 1220 692 693; 1221 693 694; 1222 695 696; 1223 601 740;1224 648 735; 1225 649 736; 1226 650 737; 1227 651 738; 1228 653 739;1229 654 741; 1230 655 742; 1231 658 745; 1232 659 746; 1233 663 748;1234 664 749; 1235 666 750; 1236 667 751; 1237 688 702; 1238 689 703;1239 690 704; 1240 691 705; 1241 698 699; 1242 699 700; 1243 704 702;1244 705 703; 1245 628 763; 1246 633 764; 1247 641 765; 1248 697 707;1249 701 706; 1250 692 717; 1251 693 718; 1252 694 719; 1253 695 708;1254 696 709; 1255 702 710; 1256 703 711; 1257 704 712; 1258 705 713;1259 684 732; 1260 686 733; 1261 687 734; 1262 708 709; 1263 712 710;1264 713 711; 1265 715 714; 1266 716 715; 1267 717 718; 1268 718 719;1269 706 722; 1270 706 723; 1271 607 782; 1272 618 791; 1273 620 793;1274 621 794; 1275 627 797; 1276 630 800; 1277 635 802; 1278 636 803;1279 640 804; 1280 642 806; 1281 643 807; 1282 652 813; 1283 670 819;1284 707 720; 1285 707 721; 1286 708 724; 1287 709 725; 1288 710 726;1289 711 727; 1290 712 729; 1291 713 730; 1292 714 728; 1293 716 731;1294 717 744; 1295 718 747; 1296 719 753; 1297 720 721; 1298 721 722;1299 722 723; 1300 725 724; 1301 729 726; 1302 730 727; 1303 731 728;1304 720 743; 1305 723 752; 1306 732 733; 1307 733 734; 1308 739 737;1309 738 740; 1310 741 735; 1311 736 742; 1312 739 743; 1313 740 744;1314 745 741; 1315 742 746; 1316 744 747; 1317 748 745; 1318 746 749;1319 743 752; 1320 747 753; 1321 750 748; 1322 749 751; 1323 728 754;1324 731 756; 1325 724 757; 1326 725 758; 1327 726 759; 1328 727 760;1329 729 761; 1330 730 762; 1331 698 789; 1332 699 795; 1333 700 799;1334 755 754; 1335 756 755; 1336 757 758; 1337 761 759; 1338 762 760;1339 759 766; 1340 761 769; 1341 763 764; 1342 765 764; 1343 757 770;1344 758 771; 1345 760 772; 1346 762 773; 1347 732 792; 1348 733 796;1349 734 820; 1350 735 809; 1351 736 810; 1352 737 811; 1353 738 812;1354 750 815; 1355 816 751; 1356 817 752; 1357 818 753; 1358 763 774;1359 764 775; 1360 765 776; 1361 766 767; 1362 767 768; 1363 768 769;1364 770 771; 1365 754 780; 1366 755 785; 1367 756 790; 1368 772 773;1369 774 775; 1370 776 775; 1371 766 778; 1372 767 783; 1373 768 784;1374 769 786; 1375 770 781; 1376 771 788; 1377 772 779; 1378 773 787;1379 774 798; 1380 775 801; 1381 776 805; 1382 777 778; 1383 778 779;1384 779 780; 1385 780 781; 1386 781 782; 1387 778 783; 1388 780 785;1389 783 784; 1390 779 787; 1391 781 788; 1392 784 786; 1393 785 790;1394 788 789; 1395 787 791; 1396 786 792; 1397 790 794; 1398 789 795;1399 791 793; 1400 792 796; 1401 793 797; 1402 794 798; 1403 795 799;1404 778 808; 1405 777 809; 1406 779 809; 1407 810 778; 1408 780 810;1409 811 779; 1410 781 811; 1411 780 812; 1412 782 812; 1413 813 781;1414 782 813; 1415 797 800; 1416 798 801; 1417 799 802; 1418 800 803;1419 801 805; 1420 802 807; 1421 803 806; 1422 804 809; 1423 805 811;1424 806 810; 1425 807 812; 1426 808 809; 1427 809 810; 1428 810 811;1429 811 812; 1430 812 813; 1431 809 815; 1432 810 816; 1433 811 817;1434 812 818; 1435 819 813; 1436 814 815; 1437 815 816; 1438 816 817;1439 817 818; 1440 818 819; 1441 796 820; 1442 820 804; 1443 413 418; 1444 7 5;1445 8 42; 1446 42 4; 1447 41 5; 1448 3 41; 1449 40 4; 1450 2 40; 1451 3 39;1452 38 2; 1453 39 1; 1454 819 812; 1455 813 818; 1456 818 811; 1457 817 812;1458 817 810; 1459 816 811; 1460 816 809; 1461 815 810; 1462 815 808;1463 814 809;ELEMENT INCIDENCES SHELL1464 14 7 158 120; 1465 120 283 320 158; 1466 7 8 178 158;1467 158 320 343 178; 1468 283 381 421 320; 1469 320 421 443 343;1470 381 607 652 421; 1471 421 652 670 443; 1472 607 782 813 652;1473 652 813 819 670;ELEMENT PROPERTY1466 THICKNESS 0.031251464 THICKNESS 0.031251465 THICKNESS 0.031251467 THICKNESS 0.031251468 THICKNESS 0.031251469 THICKNESS 0.031251470 THICKNESS 0.031251471 THICKNESS 0.031251472 THICKNESS 0.031251473 THICKNESS 0.03125DEFINE MATERIAL STARTISOTROPIC STEELE 29000POISSON 0.3DENSITY 0.000283ALPHA 6.5e-06DAMP 0.03TYPE STEELSTRENGTH FY 50 FU 65 RY 1 RT 1ISOTROPIC STEEL_ASTM_A992E 29000POISSON 0.3DENSITY 0.000283TYPE STEELSTRENGTH FY 50 FU 65 RY 1 RT 1ISOTROPIC STEEL_ASTM_A500_GRADE_B_RECTANGULAR_AND_SQUAREE 29000POISSON 0.3DENSITY 0.000283ISOTROPIC STEEL_50_KSIE 29000POISSON 0.3DENSITY 0.000283ALPHA 6.5e-06DAMP 0.03TYPE STEELSTRENGTH FY 50 FU 62 RY 1 RT 1G 11200ISOTROPIC STEEL_DECKE 29000POISSON 0.3DENSITY 0.000283ALPHA 6.5e-06DAMP 0.03G 11200TYPE STEELSTRENGTH FY 33 FU 45 RY 1 RT 1END DEFINE MATERIALMEMBER PROPERTY AMERICAN11 13 14 21 TO 32 42 TO 55 209 210 212 222 223 225 TO 230 232 233 240 241 -243 244 246 TO 248 250 252 TO 259 515 516 523 524 526 TO 529 531 540 541 -543 546 548 551 554 555 558 559 719 720 723 TO 725 727 729 731 732 -741 TO 743 746 748 749 753 754 758 TO 760 1086 1087 1096 1098 1101 1105 1108 -1109 1120 1121 1123 1126 1127 1129 1133 1134 1138 1140 1143 1387 TO 1403 -1414 TO 1425 1441 1442 TABLE ST W24X846 TO 9 266 TO 274 279 TO 288 567 TO 576 581 TO 592 767 TO 775 780 TO 791 1088 -1089 1149 TO 1154 1159 TO 1168 1431 TO 1434 TABLE ST W24X5568 TO 71 95 TO 98 132 153 TO 155 157 TO 159 168 194 TO 196 312 TO 318 320 -321 TO 323 336 355 TO 360 364 TO 367 417 TO 420 434 435 453 TO 456 -458 TO 461 467 469 484 TO 492 501 614 615 617 618 620 TO 622 688 TO 690 693 -694 TO 696 802 805 806 815 819 828 TO 834 837 TO 844 846 847 849 TO 852 856 -864 866 873 TO 879 886 TO 889 901 TO 905 908 917 920 921 928 TO 931 966 976 -979 TO 984 995 TO 998 1002 1024 1027 1031 TO 1040 1042 1043 1046 1047 1049 -1050 1053 TO 1055 1065 1070 1074 TO 1077 1184 1193 TO 1195 1211 TO 1215 1217 -1218 1220 TO 1222 1243 1244 1262 TO 1269 1285 1300 TO 1303 1306 1307 1334 -1335 TO 1338 1341 1342 1361 TO 1364 1366 1368 TO 1370 1372 -1373 TABLE ST W12X26102 TO 104 415 416 449 TO 452 479 TO 482 821 TO 827 881 884 890 TO 898 967 -968 TO 975 1010 TO 1022 1182 1187 1209 1241 1242 1332 TABLE ST W12X40100 101 192 193 TABLE ST W12X5310 60 TO 62 79 TO 81 87 TO 94 108 TO 111 123 TO 125 162 TO 164 169 TO 172 -185 TO 188 203 205 206 300 305 TO 308 331 340 TO 344 354 378 386 TO 388 396 -399 406 TO 410 426 TO 429 436 446 470 TO 475 493 504 506 TO 509 600 603 604 -619 629 632 635 638 653 TO 657 668 671 678 681 682 686 691 707 708 712 807 -808 TO 811 818 820 857 861 862 867 TO 870 885 906 909 TO 912 922 926 933 939 -940 TO 941 949 TO 951 958 959 961 962 977 989 994 1003 1004 1006 1007 1028 -1029 1044 1056 1058 TO 1061 1066 1073 1078 1079 1082 1083 1176 1178 1179 -1185 1192 1200 1201 1206 1208 1219 1224 TO 1227 1235 TO 1238 1249 1252 1253 -1255 1256 1270 1271 1282 1283 1286 1288 1289 1292 1296 1305 1323 1325 1327 -1328 1339 1343 1345 1350 TO 1357 1365 1371 1375 1377 1435 TABLE ST W21X5012 33 TO 41 234 TO 239 275 TO 278 368 TO 377 394 395 397 398 400 TO 405 534 -535 TO 539 577 TO 580 625 TO 628 630 631 633 634 636 637 666 667 669 670 672 -673 TO 677 735 TO 740 776 TO 779 1114 TO 1119 1155 TO 1158 1404 TO 1413 1444 -1445 TO 1463 TABLE ST HSST6X6X0.375UNIT FEET KIPMEMBER PROPERTY AMERICAN133 TO 148 1175 1181 1203 1205 1240 1258 1272 1273 1275 1276 1278 TO 1280 -1291 1308 TO 1322 1330 1333 1346 1378 TABLE ST W18X5063 TO 67 72 TO 78 82 TO 86 99 105 TO 107 112 TO 122 126 TO 131 149 TO 152 -156 160 161 165 TO 167 173 TO 184 189 TO 191 197 TO 202 204 207 208 -294 TO 299 301 TO 304 309 TO 311 319 324 TO 330 332 TO 335 337 TO 339 345 -346 TO 353 361 TO 363 379 TO 384 389 TO 393 411 TO 414 421 TO 425 430 TO 433 -437 TO 445 447 448 457 462 TO 466 468 476 TO 478 483 494 TO 500 502 503 505 -510 TO 512 598 599 601 602 605 TO 613 616 623 624 639 TO 652 658 TO 665 679 -680 683 TO 685 687 692 697 TO 706 709 TO 711 797 TO 801 803 804 812 TO 814 -816 817 835 836 845 848 853 TO 855 858 TO 860 863 865 871 872 880 882 883 -899 900 907 913 TO 916 918 919 923 TO 925 927 932 934 TO 938 942 TO 948 952 -953 TO 957 960 963 TO 965 978 985 TO 988 990 TO 993 999 TO 1001 1005 1008 -1009 1023 1025 1026 1030 1041 1045 1048 1051 1052 1057 1062 TO 1064 1067 -1068 TO 1069 1071 1072 1080 1081 1084 1085 1174 1177 1180 1183 1186 -1188 TO 1191 1196 TO 1199 1202 1204 1207 1210 1216 1223 1228 TO 1234 1239 -1245 TO 1248 1250 1251 1254 1257 1259 TO 1261 1274 1277 1281 1284 1287 1290 -1293 TO 1295 1297 TO 1299 1304 1324 1326 1329 1331 1340 1344 1347 TO 1348 -1349 TABLE ST W16X401358 TO 1360 1367 1374 1376 1379 TO 1381 TABLE ST W16X40211 213 TO 215 221 224 231 242 245 249 251 260 513 514 533 542 545 547 550 -553 557 560 721 728 733 744 750 752 756 1443 TABLE ST W30X148522 525 530 532 544 549 552 556 561 718 722 726 730 734 745 747 751 755 757 -761 1095 1097 1099 1100 1102 TO 1104 1106 1107 1110 TO 1113 1122 1124 1125 -1128 1130 TO 1132 1135 TO 1137 1139 1141 1142 TABLE ST W27X102385 TABLE ST W21X681 TO 5 15 TO 20 56 TO 59 216 TO 220 261 TO 265 289 TO 293 517 TO 521 -562 TO 566 593 TO 597 713 TO 717 762 TO 766 792 TO 796 1090 TO 1094 1144 -1145 TO 1148 1169 TO 1173 1382 TO 1386 1426 TO 1430 1436 TO 1439 -1440 TABLE ST W18X97UNIT INCHES KIPCONSTANTSBETA 270 MEMB 1 TO 5 16 TO 20 216 TO 220 289 TO 293 517 TO 521 593 TO 597 -713 TO 717 792 TO 796 1090 TO 1094 1169 TO 1173 1382 TO 1386 1436 TO 1440MATERIAL STEEL_50_KSI MEMB 12 33 TO 41 234 TO 239 275 TO 278 368 TO 377 394 -395 397 398 400 TO 405 534 TO 539 577 TO 580 625 TO 628 630 631 633 634 636 -637 666 667 669 670 672 TO 677 735 TO 740 776 TO 779 1114 TO 1119 -1155 TO 1158 1404 TO 1413 1444 TO 1463MATERIAL STEEL_ASTM_A992 MEMB 6 TO 11 13 14 21 TO 32 42 TO 55 60 TO 210 212 -222 223 225 TO 230 232 233 240 241 243 244 246 TO 248 250 252 TO 259 266 -267 TO 274 279 TO 288 294 TO 367 378 TO 384 386 TO 393 396 399 406 TO 512 -515 516 522 TO 532 540 541 543 544 546 548 549 551 552 554 TO 556 558 559 -561 567 TO 576 581 TO 592 598 TO 624 629 632 635 638 TO 665 668 671 -678 TO 712 718 TO 720 722 TO 727 729 TO 732 734 741 TO 743 745 TO 749 751 -753 TO 755 757 TO 761 767 TO 775 780 TO 791 797 TO 1089 1095 TO 1113 1120 -1121 TO 1143 1149 TO 1154 1159 TO 1168 1174 TO 1381 1387 TO 1403 1414 TO 1425 -1431 TO 1435 1441 1442MATERIAL STEEL_DECK MEMB 1464 TO 1473MATERIAL STEEL MEMB 1 TO 5 15 TO 20 56 TO 59 211 213 TO 221 224 231 242 245 -249 251 260 TO 265 289 TO 293 385 513 514 517 TO 521 533 542 545 547 550 -553 557 560 562 TO 566 593 TO 597 713 TO 717 721 728 733 744 750 752 756 -762 TO 766 792 TO 796 1090 TO 1094 1144 TO 1148 1169 TO 1173 1382 TO 1386 -1426 TO 1430 1436 TO 1440 1443MEMBER OFFSET817 START 0 0 0817 END 0 0 0865 START 0 0 0865 END 0 0 0927 START 0 0 0927 END 0 0 01026 START 0 0 01026 END 0 0 01072 START 0 0 0618 END 0 0 0819 START 0 0 0966 START 0 0 0976 START 0 0 0153 START 0 0 0329 END 0 0 0444 START 0 0 0643 START 0 0 0647 END 0 0 067 END 0 0 086 START 0 0 086 END 0 0 0106 START 0 0 0106 END 0 0 0161 START 0 0 0161 END 0 0 0198 START 0 0 0198 END 0 0 0850 END 0 0 01186 END 0 0 01259 START 0 0 01259 END 0 0 01347 START 0 0 01188 END 0 0 01260 START 0 0 01260 END 0 0 01348 START 0 0 0995 END 0 0 0996 START 0 0 0MEMBER RELEASE6 10 13 21 23 24 61 63 TO 70 76 TO 78 93 96 TO 98 100 TO 104 107 108 -112 TO 122 132 147 153 TO 155 157 TO 159 168 173 TO 184 192 TO 196 -199 TO 202 204 210 221 223 240 266 268 269 279 295 TO 299 301 TO 304 309 -310 TO 318 320 TO 322 334 TO 336 338 339 348 349 352 353 355 TO 360 364 365 -367 379 TO 384 389 TO 393 415 TO 419 421 434 435 449 453 455 458 TO 460 467 -469 479 TO 481 484 486 488 TO 490 492 501 513 522 TO 524 540 567 TO 570 581 -598 600 TO 602 606 607 614 615 617 618 621 639 TO 641 643 644 646 TO 648 -650 TO 652 658 TO 665 688 690 693 TO 695 711 718 TO 721 741 767 TO 770 780 -801 TO 806 812 TO 817 819 820 828 831 838 TO 841 843 850 851 856 864 866 -873 876 880 TO 885 887 889 901 TO 905 908 917 920 921 929 TO 932 934 TO 938 -942 TO 948 956 966 967 969 971 973 976 982 TO 984 997 1010 1013 1016 1019 -1024 1027 1033 1035 TO 1037 1039 1042 1043 1046 1047 1049 1050 1053 TO 1055 -1065 1070 1074 1075 1077 1084 1088 1095 TO 1098 1120 1149 1151 1159 1174 -1175 1177 1180 TO 1185 1190 1191 1193 TO 1196 1209 1210 1214 1215 1217 1218 -1222 1223 1226 TO 1234 1241 1243 TO 1247 1262 TO 1264 1266 1267 1269 1272 -1273 TO 1278 1280 START MY MZ1281 TO 1283 1285 1297 1300 TO 1303 1309 1321 1332 1335 TO 1338 1341 1342 -1357 1361 1364 1366 1368 TO 1370 1387 1388 1391 1414 1431 1433 -1435 START MY MZ7 TO 9 133 136 1311 1355 1356 1432 1434 START MY MZ351 605 620 696 837 928 981 1034 1076 START MY MZ22 60 62 71 91 92 94 95 109 TO 111 134 222 267 305 TO 308 323 340 350 354 -366 378 396 399 406 420 451 461 482 491 603 604 608 609 622 629 632 635 638 -642 645 649 668 671 678 689 807 TO 811 818 821 824 846 847 849 852 890 895 -923 933 939 TO 941 949 TO 951 979 985 TO 987 995 1002 1031 1068 1176 1178 -1179 1186 TO 1189 1192 1208 1211 1213 1220 1224 1225 1235 1236 1271 1279 -1306 1307 1372 1373 START MY MZ6 TO 9 52 TO 55 68 TO 70 72 TO 75 87 TO 89 96 TO 98 100 TO 104 107 109 112 -113 TO 122 132 135 145 146 148 153 TO 155 157 TO 159 168 173 TO 185 -189 TO 198 207 208 257 TO 260 285 TO 288 294 312 TO 318 320 TO 322 336 339 -348 355 TO 360 364 365 367 379 TO 384 389 TO 393 406 415 TO 419 424 434 435 -441 TO 445 447 448 450 454 456 458 TO 460 467 469 479 TO 481 485 487 TO 490 -492 494 TO 498 500 TO 503 505 510 TO 512 558 TO 561 589 TO 592 599 -613 TO 615 617 618 621 639 TO 641 643 644 646 TO 648 650 TO 652 658 TO 665 -688 690 693 TO 695 700 TO 702 705 706 710 TO 712 759 TO 761 788 TO 791 802 -805 806 815 819 830 834 838 TO 840 842 844 850 851 856 864 866 875 879 881 -884 886 888 902 TO 905 908 917 920 921 929 TO 932 934 TO 938 942 TO 948 952 -966 968 970 972 975 976 982 TO 984 998 1012 1015 1018 1022 1024 1027 1033 -1035 1036 1038 1040 TO 1043 1045 TO 1055 1065 1066 1069 TO 1072 1074 1075 -1077 1080 1081 1085 1140 TO 1143 1165 TO 1168 1182 1184 1193 1195 1199 1209 -1215 1217 1218 1221 TO 1223 1228 TO 1234 1242 1244 1262 TO 1265 1268 1269 -1272 TO 1278 1280 1281 1283 1285 1294 1295 1299 TO 1304 1308 1310 1319 -1320 END MY MZ1443 END MY MZ1322 1331 TO 1334 1336 TO 1338 1352 TO 1354 1364 1366 TO 1368 1374 1376 1378 -1379 TO 1381 1422 TO 1425 1431 TO 1433 END MY MZ10 13 90 108 240 279 540 581 741 780 1120 1159 1282 1414 1435 END MY MZ71 95 110 111 169 TO 172 186 TO 188 203 205 206 323 350 366 378 396 399 420 -452 461 482 491 493 499 504 506 TO 509 620 622 629 632 635 638 642 645 649 -668 671 678 689 696 703 704 707 TO 709 797 TO 800 823 827 837 846 847 849 -852 894 898 901 928 933 939 TO 941 949 TO 951 980 981 986 996 1002 1032 1034 -1044 1056 1067 1073 1076 1078 1079 1082 1083 1187 1194 1212 TO 1214 1243 -1271 1279 1306 1307 1347 TO 1351 1363 1365 1371 TO 1373 1375 -1377 END MY MZ1434 END MY MZSUPPORTS1 9 38 115 153 173 278 315 338 376 416 438 602 647 665 777 808 814 PINNEDUNIT FEET KIPMEMBER TENSION 12 33 TO 41 234 TO 239 275 TO 278 368 TO 377 394 395 397 398 400 TO 405 534 -535 TO 539 577 TO 580 625 TO 628 630 631 633 634 636 637 666 667 669 670 672 -673 TO 677 735 TO 740 776 TO 779 1114 TO 1119 1155 TO 1158 1404 TO 1413 1444 -1445 TO 1463UNIT INCHES KIPELEMENT PLANE STRESS1464 TO 1473LOAD 1 LOADTYPE Dead TITLE DEAD LOADSELFWEIGHT Y -1 UNIT FEET KIPMEMBER LOAD934 TO 937 CON GY -0.36JOINT LOAD518 FY -0.36240 242 264 266 472 474 489 491 551 553 588 590 FY -0.53MEMBER LOAD614 615 694 695 1220 1221 1267 1268 CON GY -0.53 1.251182 1241 1242 CON GY -2.2 2.51182 CON GY -2.2 7.5434 501 815 908 966 1070 1217 1285 CON GY -2.9 2.5435 492 819 905 976 1065 1218 1269 CON GY -2.9 3617 618 690 693 CON GY -1.5 1.51210 1245 TO 1247 1274 CON GY -0.45 61366 1367 CON GY -0.4 1.6671341 1342 1369 1370 CON GY -0.41366 1367 CON GY -0.41042 1043 1046 1047 UNI GY -0.6967 969 975 1010 1012 1013 1015 1018 1022 CON GY -1.8 0.5968 CON GY -1.8 2.5970 CON GY -1.8 1.25880 TO 883 CON GY -0.4 4.25869 871 CON GY -0.4 1JOINT LOAD217 257 FY -0.8MEMBER LOAD415 416 479 480 CON GY -0.8416 479 CON GY -0.8 0.75JOINT LOAD189 199 FY -0.17MEMBER LOAD318 336 CON GY -0.17 1343 CON GY -0.4 0.667347 CON GY -0.644 0.667324 325 CON GY -0.65 1.41667334 335 339 CON GY -0.72 5.5338 340 384 386 389 CON GY -0.465 5.5100 101 192 193 CON GY -3.65 1.251272 1273 1275 1276 1278 1280 CON GY -2.1 201272 1273 1275 1276 1278 1280 CON GY -2.1 5.5JOINT LOAD705 713 FY -0.21MEMBER LOAD1291 CON GY -0.21 1.251272 1273 1275 1276 1278 1280 CON GY -0.41272 1273 1275 1276 CON GY -0.4 11.251272 1273 1275 1276 1278 1280 CON GY -0.4 8.6671050 1054 1055 UNI GY -0.6971 973 1016 1019 CON GY -1.8 3972 CON GY -1.8 4828 831 873 876 CON GY -1 0.667828 831 873 876 CON GY -1 3.5JOINT LOAD455 459 480 484 FY -1MEMBER LOAD971 TO 975 1016 TO 1022 UNI GY -0.053513 721 733 CON GY -67.5 4.75542 CON GY -67.5 2.25643 647 651 654 661 663 665 CON GY -0.28 1.5361 441 TO 448 CON GY -0.68 0.667337 CON GY -1.05 0.75326 TO 333 CON GY -1.086 2.25399 CON GY -0.6 5.667JOINT LOAD179 TO 184 186 187 200 TO 205 207 208 FY -1.05MEMBER LOAD316 359 CON GY -1.05 2.5315 358 CON GY -1.05 1.75103 153 CON GY -0.4 0.5103 153 CON GY -0.4 4.5103 CON GY -0.4 2.25102 104 CON GY -0.4 1.667104 CON GY -0.4 4154 CON GY -0.4 2.334155 CON GY -0.4 1.1667JOINT LOAD684 687 732 734 FY -0.75MEMBER LOAD1306 CON GY -0.75 3.16671213 1307 CON GY -0.75 1.83341212 CON GY -0.75 11259 TO 1261 CON GY -0.57 0.3341259 TO 1261 CON GY -0.57 1.751259 TO 1261 CON GY -0.57 71347 TO 1349 CON GY -0.57 11202 CON GY -0.234 2.251239 CON GY -0.234 1.16671290 CON GY -0.234 1.3341329 CON GY -0.234 1.5945 947 CON GY -0.23 16.0833JOINT LOAD539 541 575 576 FY -0.45444 TO 446 449 TO 451 493 494 496 498 499 501 FY -1MEMBER LOAD845 TO 850 852 853 CON GY -0.354 1.8334859 CON GY -0.354 1622 689 CON GY -0.275 1622 689 CON GY -0.275 3.75608 609 CON GY -0.65 2.8334449 481 CON GY -0.575 2.25481 CON GY -0.575 7.5451 482 CON GY -0.575 3.25482 CON GY -0.575 8.334481 482 UNI GY -0.125JOINT LOAD68 100 FY -0.4549 51 FY -0.28MEMBER LOAD132 168 CON GY -0.45 1.2571 95 CON GY -0.28 2.667ONEWAY LOADYRANGE 16 17.5 ONE -0.015 GYYRANGE 38 40 ONE -0.015 GYYRANGE 58 60 ONE -0.015 GYYRANGE 73 76 ONE -0.015 GYYRANGE 95 99 ONE -0.015 GY TOWARDS 13JOINT LOAD188 189 198 199 FY -3.25UNIT INCHES KIPMEMBER LOAD450 452 CON GY -0.575 36UNIT FEET KIP1049 UNI GY -0.6UNIT INCHES KIPLOAD 2 LOADTYPE Live TITLE FLOOR LIVEUNIT FEET KIPONEWAY LOADYRANGE 16 17.5 ONE -0.125 GYYRANGE 38 40 ONE -0.125 GYYRANGE 59 60 ONE -0.125 GYYRANGE 74 76 ONE -0.125 GYMEMBER LOAD103 CON GY -0.74 2.25153 CON GY -0.95 0.5153 CON GY -0.95 4.5104 CON GY -0.74 4154 CON GY -0.95 2.334155 CON GY -0.95 1.1667415 416 479 480 CON GY -2.1 3416 479 CON GY -2.1 0.75JOINT LOAD217 257 FY -2.1217 257 FX 2.2MEMBER LOAD416 479 CON GX 2.2 0.75415 416 479 480 CON GX 2.2 3100 101 192 193 CON GY -11.13 1.25100 101 192 193 CON GX 0.15 1.251182 1241 1242 CON GY -3.15 2.51182 CON GY -3.15 7.5LOAD 3 LOADTYPE Roof Live TITLE ROOF LIVE LOADONEWAY LOADYRANGE 95 99 ONE -0.02 GY TOWARDS 13LOAD 8 LOADTYPE Wind TITLE WIND UPLIFTMEMBER LOAD540 581 1120 1159 UNI GY 1.125240 279 741 780 UNI GY 0.96210 13 UNI GY 0.3951414 1435 UNI GY 0.629109 111 378 406 638 678 933 951 1271 1283 UNI GY 0.105108 388 657 941 1282 UNI GY 0.21LOAD COMB 9 DEAD1 1.0 LOAD COMB 10 DEAD + LIVE1 1.0 2 1.0 LOAD COMB 11 DEAD + LIVE ROOF1 1.0 3 1.0 LOAD COMB 12 DEAD + LIVE + LIVE ROOF1 1.0 2 0.75 3 0.75 PERFORM ANALYSIS PRINT STATICS CHECKDEFINE ENVELOPE9 TO 12 ENVELOPE 1 TYPE SERVICEABILITYEND DEFINE ENVELOPELOAD LIST ENV 1PARAMETER 1CODE AISC UNIFIED 2010METHOD ASDFYLD 7200 ALLMAIN 1 MEMB 8 21 25 29 32 44 47 51 55 61 63 69 72 TO 75 80 82 89 93 97 100 -101 118 122 124 126 133 137 141 145 149 TO 152 158 163 165 171 173 177 181 -187 192 193 195 199 TO 202 205 207 211 213 TO 215 221 224 231 242 245 249 -251 260 266 270 280 285 303 304 307 309 318 320 324 325 334 TO 336 -338 TO 340 343 347 362 363 367 384 386 389 409 414 TO 417 421 TO 424 428 -430 433 TO 440 458 465 470 474 476 479 480 488 492 TO 497 500 501 508 510 -522 525 530 532 544 549 552 556 561 567 571 576 582 586 588 589 598 TO 600 -610 TO 613 616 TO 619 632 639 644 648 652 655 658 682 683 690 TO 693 697 -698 TO 700 710 TO 712 718 722 726 730 734 745 747 751 755 757 761 767 771 -775 781 785 786 788 810 812 814 815 819 820 838 860 861 869 871 880 TO 885 -902 905 TO 908 911 914 929 942 952 TO 956 961 963 965 TO 970 976 977 983 -988 TO 991 1006 1008 1010 TO 1015 1025 1028 1035 1041 TO 1048 1060 1063 1065 -1066 1069 1070 1074 1078 1080 1095 1099 1102 1104 1106 1111 1112 1122 1125 -1131 1135 1137 1142 1149 1152 1160 1164 1165 1183 TO 1185 1196 TO 1199 1208 -1209 TO 1210 1216 TO 1219 1226 1228 1245 TO 1249 1265 1266 1269 1270 1274 -1284 1285 1292 1293 1297 TO 1299 1303MAIN 1 MEMB 1304 TO 1305 1308 1312 1319 1323 1324 1334 1335 1341 1342 1352 -1356 1358 TO 1360 1365 TO 1367 1369 1370 1379 TO 1381 1388 1393 1397 1402 -1416 1419 1423 1433TMAIN 1 MEMB 8 21 25 29 32 44 47 51 55 61 63 69 72 TO 75 80 82 89 93 97 100 -101 118 122 124 126 133 137 141 145 149 TO 152 158 163 165 171 173 177 181 -187 192 193 195 199 TO 202 205 207 211 213 TO 215 221 224 231 242 245 249 -251 260 266 270 280 285 303 304 307 309 318 320 324 325 334 TO 336 -338 TO 340 343 347 362 363 367 384 386 389 409 414 TO 417 421 TO 424 428 -430 433 TO 440 458 465 470 474 476 479 480 488 492 TO 497 500 501 508 510 -522 525 530 532 544 549 552 556 561 567 571 576 582 586 588 589 598 TO 600 -610 TO 613 616 TO 619 632 639 644 648 652 655 658 682 683 690 TO 693 697 -698 TO 700 710 TO 712 718 722 726 730 734 745 747 751 755 757 761 767 771 -775 781 785 786 788 810 812 814 815 819 820 838 860 861 869 871 880 TO 885 -902 905 TO 908 911 914 929 942 952 TO 956 961 963 965 TO 970 976 977 983 -988 TO 991 1006 1008 1010 TO 1015 1025 1028 1035 1041 TO 1048 1060 1063 1065 -1066 1069 1070 1074 1078 1080 1095 1099 1102 1104 1106 1111 1112 1122 1125 -1131 1135 1137 1142 1149 1152 1160 1164 1165 1183 TO 1185 1196 TO 1199 1208 -1209 TO 1210 1216 TO 1219 1226 1228 1245 TO 1249 1265 1266 1269 1270 1274 -1284 1285 1292 1293 1297 TO 1299 1303TMAIN 1 MEMB 1304 TO 1305 1308 1312 1319 1323 1324 1334 1335 1341 1342 1352 -1356 1358 TO 1360 1365 TO 1367 1369 1370 1379 TO 1381 1388 1393 1397 1402 -1416 1419 1423 1433DFF 240 ALLDJ1 13 MEMB 11 14 22 26 45 49 53 62 81 125 164 206DJ1 16 MEMB 64 83 127 166 208DJ1 42 MEMB 94 172DJ1 5 MEMB 90 188DJ2 119 MEMB 62 81 125 164 206DJ2 122 MEMB 64 83 127 166 208DJ2 157 MEMB 94 172 222 225 228 241 248 254 258DJ2 177 MEMB 90 188 267 272 282 286DJ2 42 MEMB 11 14 22 26 45 49 53DJ1 157 MEMB 267 272 282 286DJ1 119 MEMB 222 225 228 241 248 254 258 308 344 410 429 475 509DJ1 122 MEMB 310 345 411 431 477 511DJ1 165 MEMB 352 466 502DJ1 170 MEMB 353 468 503DJ1 177 MEMB 354 471 504DJ1 282 MEMB 524 527 529 531 541 548 554 559DJ1 319 MEMB 568 573 584 590DJ1 294 MEMB 606 623 701DJ1 299 MEMB 607 624 702DJ1 328 MEMB 601 679 705DJ1 335 MEMB 602 680 706DJ1 342 MEMB 603 681 707DJ1 380 MEMB 720 724 727 731 742 748 754 759 811 870 912 962 1007 1061 1079DJ1 420 MEMB 768 772 782 787 789DJ2 282 MEMB 308 344 410 429 475 509DJ2 288 MEMB 310 345 411 431 477 511DJ2 328 MEMB 352 466 502DJ2 335 MEMB 353 468 503DJ2 342 MEMB 354 471 504DJ2 319 MEMB 524 527 529 531 541 548 554 559DJ2 342 MEMB 568 573 584 590DJ2 395 MEMB 606 623 701DJ2 400 MEMB 607 624 702DJ2 420 MEMB 720 724 727 731 742 748 754 759DJ2 428 MEMB 601 679 705DJ2 442 MEMB 603 681 707DJ2 435 MEMB 602 680 706DJ1 387 MEMB 813 872 915 964 1009 1064 1081DJ1 428 MEMB 816 863 925 1023 1071DJ1 435 MEMB 817 865 927 1026 1072DJ1 442 MEMB 818 862 926 1029 1073DJ1 606 MEMB 1098 1101 1105 1108 1121 1127 1134 1140 1176 1206 1253 1286 1325 -1343 1375DJ1 612 MEMB 1177 1207 1254 1287 1326 1344 1376DJ1 614 MEMB 1174 1204 1331DJ1 629 MEMB 1175 1205 1333DJ1 698 MEMB 1241 1242DJ1 651 MEMB 1227 1353DJ1 657 MEMB 1190 1250 1294DJ1 662 MEMB 1191 1251 1295DJ1 669 MEMB 1192 1252 1296 1357DJ1 738 MEMB 1309 1313 1316 1320DJ1 781 MEMB 1391 1394 1398 1403 1417 1420 1425DJ2 606 MEMB 811 870 912 962 1007 1061 1079DJ2 612 MEMB 813 872 915 964 1009 1064 1081DJ2 651 MEMB 1098 1101 1105 1108 1121 1127 1134 1140DJ2 669 MEMB 818 862 926 1029 1073 1088 1089 1161 1166DJ2 662 MEMB 817 865 927 1026 1072DJ2 657 MEMB 816 863 925 1023 1071DJ2 781 MEMB 1176 1206 1253 1286 1325 1343 1375DJ2 788 MEMB 1177 1207 1254 1287 1326 1344 1376DJ2 789 MEMB 1174 1204 1331DJ2 799 MEMB 1175 1205 1333DJ2 700 MEMB 1241 1242DJ2 812 MEMB 1391 1394 1398 1403 1417 1420 1425DJ2 753 MEMB 1309 1313 1316 1320DJ2 747 MEMB 1191 1251 1295DJ2 744 MEMB 1190 1250 1294DJ2 818 MEMB 1192 1252 1296 1357DJ1 12 MEMB 21 25 29 32 44 47 51 55 61 80 124 163 205DJ1 15 MEMB 63 82 126 165 207DJ1 19 MEMB 72 149 199DJ1 23 MEMB 73 150 200DJ1 26 MEMB 74 151 201DJ1 29 MEMB 75 152 202DJ1 41 MEMB 93 171DJ1 4 MEMB 89 187DJ1 71 MEMB 133 137 141 145DJ2 118 MEMB 61 80 124 163 205DJ2 121 MEMB 63 82 126 165 207DJ2 124 MEMB 72 149 199DJ2 129 MEMB 73 150 200DJ2 136 MEMB 74 151 201DJ2 142 MEMB 75 152 202DJ2 156 MEMB 93 171 211 213 TO 215 221 224 231 242 245 249 251 260DJ2 176 MEMB 89 187 266 270 280 285DJ1 118 MEMB 211 213 TO 215 221 224 231 242 245 249 251 260 307 343 409 428 -474 508DJ1 156 MEMB 266 270 280 285DJ2 87 MEMB 133 137 141 145DJ1 121 MEMB 309 347 414 430 476 510DJ1 112 MEMB 303 324 362 439 496DJ1 132 MEMB 304 325 363 440 497DJ1 140 MEMB 334 437 494DJ1 146 MEMB 335 438 495DJ1 164 MEMB 338 433 465 500DJ1 176 MEMB 340 436 470 493DJ1 229 MEMB 421 TO 424DJ1 281 MEMB 522 525 530 532 544 549 552 556 561DJ1 318 MEMB 567 571 576 582 586 588 589DJ2 281 MEMB 307 343 409 428 474 508DJ2 287 MEMB 309 347 414 430 476 510DJ2 292 MEMB 303 324 362 439 496DJ2 296 MEMB 304 325 363 440 497DJ2 302 MEMB 334 437 494DJ2 308 MEMB 335 438 495DJ2 326 MEMB 338 433 465 500DJ2 318 MEMB 522 525 530 532 544 549 552 556 561 567DJ2 341 MEMB 340 436 470 493 567 571 576 582 586 588 589DJ2 233 MEMB 421 TO 424DJ1 327 MEMB 598 616 683 692 710DJ1 341 MEMB 600 619 682 691 712DJ1 344 MEMB 610 TO 613DJ1 371 MEMB 697 TO 700DJ1 379 MEMB 718 722 726 730 734 745 747 751 755 757 761 810 869 911 961 1006 -1060 1078DJ1 419 MEMB 767 771 775 781 785 786 788DJ2 419 MEMB 718 722 726 730 734 745 747 751 755 757 761DJ2 348 MEMB 610 TO 613DJ2 375 MEMB 697 TO 700DJ2 427 MEMB 598 616 683 692 710DJ2 441 MEMB 600 619 682 691 712 767 771 775 781 785 786 788DJ1 386 MEMB 812 871 914 963 1008 1063 1080DJ1 390 MEMB 880 990 1045DJ1 397 MEMB 882 991 1048DJ1 404 MEMB 883 988 1041DJ1 419 MEMB 885 989 1044DJ1 426 MEMB 814 860 907 965 1025 1069DJ1 441 MEMB 820 861 906 977 1028 1066DJ1 520 MEMB 952 TO 956DJ1 526 MEMB 967 968DJ1 529 MEMB 969 970DJ1 561 MEMB 1013 TO 1015DJ1 557 MEMB 1010 TO 1012DJ1 605 MEMB 1208 1292 1323 1365DJ1 605 MEMB 1095 1099 1102 1104 1106 1111 1112 1122 1125 1131 1135 1137 1142DJ2 650 MEMB 1095 1099 1102 1104 1106 1111 1112 1122 1125 1131 1135 1137 1142DJ1 650 MEMB 1149 1152 1160 1164 1165DJ2 605 MEMB 810 869 911 961 1006 1060 1078DJ2 611 MEMB 812 871 914 963 1008 1063 1080DJ2 616 MEMB 880 990 1045DJ2 626 MEMB 882 991 1048DJ2 633 MEMB 883 988 1041DJ2 650 MEMB 885 989 1044DJ2 656 MEMB 814 860 907 965 1025 1069DJ2 668 MEMB 820 861 906 977 1028 1066 1149 1152 1160 1164 1165DJ2 525 MEMB 952 TO 956DJ2 531 MEMB 969 970DJ2 560 MEMB 1010 TO 1012DJ2 528 MEMB 967 968DJ2 564 MEMB 1013 TO 1015DJ1 615 MEMB 1210 1293 1324 1367DJ1 628 MEMB 1245 1358 1379DJ1 633 MEMB 1246 1359 1380DJ1 641 MEMB 1247 1360 1381DJ1 650 MEMB 1149 1152 1160 1164 1165 1226 1352DJ1 656 MEMB 1183 1216 1248 1284 1304DJ1 668 MEMB 1185 1219 1249 1270 1305 1356DJ1 714 MEMB 1265 1266DJ1 754 MEMB 1334 1335DJ1 763 MEMB 1341 1342DJ1 774 MEMB 1369 1370DJ1 737 MEMB 1308 1312 1319DJ1 720 MEMB 1297 TO 1299DJ1 679 MEMB 1196 TO 1199DJ1 780 MEMB 1388 1393 1397 1402 1416 1419 1423DJ1 811 MEMB 1433DJ2 780 MEMB 1208 1292 1323 1365DJ2 790 MEMB 1104 1210 1293 1324 1367DJ2 798 MEMB 1245 1358 1379DJ2 801 MEMB 1246 1359 1380DJ2 805 MEMB 1247 1360 1381DJ2 811 MEMB 1226 1352 1388 1393 1397 1402 1416 1419 1423DJ2 817 MEMB 1185 1219 1249 1270 1305 1356 1433DJ2 716 MEMB 1265 1266DJ2 756 MEMB 1334 1335DJ2 765 MEMB 1341 1342DJ2 776 MEMB 1369 1370DJ2 752 MEMB 1308 1312 1319DJ2 723 MEMB 1297 TO 1299DJ2 683 MEMB 1196 TO 1199DJ1 11 MEMB 23 28 31 43 48 52 60 79 123 162 203DJ1 17 MEMB 65 84 99 128 156 167 204DJ1 22 MEMB 78 131 189DJ1 25 MEMB 76 129 190DJ1 30 MEMB 77 130 191DJ1 40 MEMB 92 170DJ1 3 MEMB 88 186DJ1 117 MEMB 209 210 212 229 233 244 247 252 255 257 306 342 408 427 473 507DJ1 155 MEMB 269 271 274 281 284 288 300 331 446DJ1 70 MEMB 136 140 144 148DJ2 117 MEMB 60 79 123 162 203DJ2 111 MEMB 65 84 99 128 156 167 204DJ2 128 MEMB 78 131 189DJ2 135 MEMB 76 129 190DJ2 143 MEMB 77 130 191DJ2 155 MEMB 92 170DJ2 175 MEMB 88 186 269 271 274 281 284 288DJ2 86 MEMB 136 140 144 148DJ1 111 MEMB 294 319 337 361 412 432 478 505DJ1 113 MEMB 295 326 441DJ1 131 MEMB 296 327 442DJ1 138 MEMB 297 328 443DJ1 143 MEMB 298 329 444DJ1 148 MEMB 299 330 445DJ1 163 MEMB 301 332 447DJ1 168 MEMB 302 333 448DJ1 280 MEMB 513 514 533 542 545 547 550 553 557 560DJ1 317 MEMB 570 572 575 583 587 592DJ2 280 MEMB 306 342 408 427 473 507DJ2 276 MEMB 294 319 337 361 412 432 478 505DJ2 293 MEMB 295 326 441DJ2 295 MEMB 296 327 442DJ2 300 MEMB 297 328 443DJ2 303 MEMB 298 329 444DJ2 310 MEMB 299 330 445DJ2 317 MEMB 300 331 446 513 514 533 542 545 547 550 553 557 560DJ2 325 MEMB 301 332 447DJ2 332 MEMB 302 333 448DJ2 340 MEMB 570 572 575 583 587 592DJ1 378 MEMB 721 728 733 744 750 752 756 809 868 910 959 1004 1059 1083 1443DJ1 388 MEMB 801 836 858 899 916 957 978 999 1030 1057 1085DJ1 398 MEMB 803 854 918 992 1051DJ1 401 MEMB 804 855 919 993 1052DJ1 418 MEMB 770 774 784 791 807 857 922 994 1056DJ1 604 MEMB 1097 1100 1103 1107 1110 1113 1124 1128 1130 1132 1136 1139 1141DJ1 649 MEMB 1151 1154 1163 1168 1225 1351DJ1 453 MEMB 828 TO 830DJ1 478 MEMB 873 TO 875DJ1 532 MEMB 971 972DJ1 565 MEMB 1016 TO 1018DJ1 457 MEMB 831 TO 834DJ1 482 MEMB 876 TO 879DJ1 535 MEMB 973 TO 975DJ1 569 MEMB 1019 TO 1022DJ2 604 MEMB 809 868 910 959 1004 1059 1083DJ2 613 MEMB 801 836 858 899 916 957 978 999 1030 1057 1085DJ2 627 MEMB 803 854 918 992 1051DJ2 630 MEMB 804 855 919 993 1052DJ2 649 MEMB 807 857 922 994 1056 1097 1100 1103 1107 1110 1113 1124 1128 -1130 1132 1136 1139 1141DJ2 456 MEMB 828 TO 830DJ2 481 MEMB 873 TO 875DJ2 534 MEMB 971 972DJ2 568 MEMB 1016 TO 1018DJ2 461 MEMB 831 TO 834DJ2 486 MEMB 876 TO 879DJ2 538 MEMB 973 TO 975DJ2 573 MEMB 1019 TO 1022DJ2 440 MEMB 770 774 784 791DJ2 667 MEMB 1151 1154 1163 1168DJ1 610 MEMB 1181 1203 1240 1258 1291 1330 1346 1378DJ1 779 MEMB 1390 1395 1399 1401 1415 1418 1421 1424DJ1 736 MEMB 1311 1315 1318 1322DJ2 779 MEMB 1179 1201 1238 1256 1289 1328 1345 1377DJ2 787 MEMB 1181 1203 1240 1258 1291 1330 1346 1378DJ2 810 MEMB 1390 1395 1399 1401 1415 1418 1421 1424DJ2 751 MEMB 1311 1315 1318 1322DJ1 10 MEMB 24 27 30 42 46 50 54DJ1 18 MEMB 66 85 105 160 197DJ1 21 MEMB 67 86 106 161 198DJ1 39 MEMB 91 169DJ1 69 MEMB 135 139 143 147DJ1 116 MEMB 223 226 227 230 232 243 246 250 253 256 259 305 341 407 426 472 -506DJ1 154 MEMB 268 273 283 287DJ2 123 MEMB 66 85 105 160 197DJ2 126 MEMB 67 86 106 161 198DJ2 154 MEMB 91 169DJ2 85 MEMB 135 139 143 147DJ2 174 MEMB 87 185 268 273 283 287DJ1 2 MEMB 87 185DJ1 123 MEMB 311 346 413 425 457 464 483 512DJ1 134 MEMB 349 462 498DJ1 147 MEMB 351 463 499DJ1 279 MEMB 515 516 523 526 528 543 546 551 555 558 604 686 708DJ1 234 MEMB 449 450DJ1 236 MEMB 451 452DJ1 316 MEMB 569 574 585 591DJ2 279 MEMB 305 341 407 426 472 506DJ2 289 MEMB 311 346 413 425 457 464 483 512DJ2 236 MEMB 449 450DJ2 238 MEMB 451 452DJ2 316 MEMB 515 516 523 526 528 543 546 551 555 558DJ2 339 MEMB 569 574 585 591DJ1 285 MEMB 605 687 709DJ1 290 MEMB 609 684 703DJ1 277 MEMB 608 685 704DJ1 377 MEMB 719 723 725 729 732 743 746 749 753 758 760 808 867 909 958 1003 -1058 1082DJ1 417 MEMB 769 773 783 790DJ2 377 MEMB 604 686 708DJ2 383 MEMB 605 687 709DJ2 389 MEMB 609 684 703DJ2 394 MEMB 608 685 704DJ2 417 MEMB 719 723 725 729 732 743 746 749 753 758 760DJ2 439 MEMB 769 773 783 790DJ1 385 MEMB 799 835 859 900 913 960 1005 1062 1084DJ1 396 MEMB 800 853 924 1001 1068DJ1 495 MEMB 923 1000 1067DJ1 403 MEMB 797 845 985DJ1 414 MEMB 798 848 987DJ1 603 MEMB 1086 1087 1096 1109 1123 1126 1129 1133 1138 1143 1178 1200 1237 -1255 1288 1327 1339 1371DJ1 648 MEMB 1150 1153 1162 1167 1224 1350DJ1 448 MEMB 824 TO 827DJ1 492 MEMB 890 TO 894DJ1 539 MEMB 979 980DJ1 575 MEMB 1031 1032DJ1 444 MEMB 821 TO 823DJ1 498 MEMB 895 TO 898DJ2 603 MEMB 808 867 909 958 1003 1058 1082DJ2 609 MEMB 799 835 859 900 913 960 1005 1062 1084DJ2 600 MEMB 923 1000 1067DJ2 625 MEMB 800 853 924 1001 1068DJ2 631 MEMB 797 845 985DJ2 646 MEMB 798 848 987DJ2 666 MEMB 1150 1153 1162 1167DJ2 452 MEMB 824 TO 827DJ2 497 MEMB 890 TO 894DJ2 447 MEMB 821 TO 823DJ2 502 MEMB 895 TO 898DJ2 648 MEMB 1086 1087 1096 1109 1123 1126 1129 1133 1138 1143DJ2 540 MEMB 979 980DJ2 577 MEMB 1031 1032DJ1 609 MEMB 1180 1202 1239 1257 1290 1329 1340 1374DJ1 600 MEMB 1186 1259 1347DJ1 625 MEMB 1188 1260 1348DJ1 632 MEMB 1189 1261 1349DJ1 778 MEMB 1387 1389 1392 1396 1400 1422 1441 1442DJ1 766 MEMB 1361 TO 1363DJ1 684 MEMB 1211 1212DJ1 666 MEMB 1235 1354DJ1 735 MEMB 1310 1314 1317 1321DJ2 778 MEMB 1178 1200 1237 1255 1288 1327 1339 1371DJ2 786 MEMB 1084 1180 1202 1239 1257 1290 1329 1340 1374DJ2 769 MEMB 1361 TO 1363DJ2 792 MEMB 1186 1259 1347DJ2 796 MEMB 1188 1260 1348DJ2 820 MEMB 1189 1261 1349DJ2 686 MEMB 1211 1212DJ2 809 MEMB 1224 1350 1387 1389 1392 1396 1400 1422 1441 1442DJ2 750 MEMB 1310 1314 1317 1321DJ2 815 MEMB 1235 1354TRACK 2 ALLPRINT SECTION MAX DISPL ALLCHECK CODE ALLFINISH
The deflection check was failing because the member 1104 was incorrectly included in the following member list
*DJ2 790 MEMB 1104 1210 1293 1324 1367
If you change the assignment as shown next, it should work
DJ2 790 MEMB 1210 1293 1324 1367
Also I am not sure which bug you are referring to but there has been fixes made to the deflection check as per AISC 360-16 specification. So you may use the AISC 360-16 code for deflection check. If you have any specific concerns or issues, we can look into those.
Thank you Sye! I looked over that many times, and must have missed it. I will try the deflection design in 2016 as well.
So, your answer did fix my problem with that one member. However I now am trying to run the strength and serviceability design in one model, using the 2016 code. I think I have everything set up properly, but it looks like the program may still be seeing the segments of beams as individual members. Am I missing something? I renumbered the beams and nodes to make it easier to read. Thanks in advance!STAAD SPACESTART JOB INFORMATIONENGINEER DATE 12-May-21END JOB INFORMATIONINPUT WIDTH 79UNIT INCHES KIPJOINT COORDINATES1 -631.226 0 -594.746; 2 -630.97 0 -1138.75; 3 -630.97 0 -779.746;4 -452.97 0 -1138.75; 5 -452.97 0 -779.746; 6 -452.97 0 -594.746;7 -188.97 0 -1138.75; 8 -188.97 0 -779.746; 9 -188.97 0 -594.746;10 10.03 0 -1138.75; 11 10.03 0 -779.746; 12 10.03 0 -594.746;13 239.03 0 -1138.75; 14 239.03 0 -779.746; 15 239.03 0 -594.746;16 529.03 0 -1138.75; 17 529.03 0 -779.746; 18 529.03 0 -594.746;19 -631.22 201 -594.746; 20 -630.97 201 -1138.75; 21 -630.97 201 -1073.19;22 -630.97 201 -1023.98; 23 -630.97 201 -975.211; 24 -630.97 201 -926.298;25 -630.97 201 -877.384; 26 -630.97 201 -828.47; 27 -630.97 201 -779.746;28 -598.462 201 -1073.19; 29 -598.462 201 -1023.98; 30 -567.148 201 -1073.19;31 -567.148 201 -1023.98; 32 -525.248 201 -1073.19; 33 -525.248 201 -1023.98;34 -523.22 201 -779.746; 35 -523.22 201 -733.306; 36 -523.22 201 -687.056;37 -523.22 201 -640.806; 38 -523.22 201 -594.746; 39 -494.967 201 -1073.19;40 -494.967 201 -1023.98; 41 -452.97 201 -1138.75; 42 -452.97 201 -1073.19;43 -452.97 201 -1023.98; 44 -452.97 201 -1019.19; 45 -452.97 201 -975.211;46 -452.97 201 -965.191; 47 -452.97 201 -926.298; 48 -452.97 201 -905.191;49 -452.97 201 -877.384; 50 -452.97 201 -845.191; 51 -452.97 201 -828.47;52 -452.97 201 -779.746; 53 -452.97 201 -733.306; 54 -452.97 201 -687.056;55 -452.97 201 -640.806; 56 -452.97 201 -594.746; 57 -394.97 201 -1138.75;58 -394.97 201 -1073.19; 59 -334.97 201 -1138.75; 60 -334.97 201 -1073.19;61 -300.975 201 -1138.75; 62 -300.975 201 -1073.19; 63 -269.112 201 -1073.19;64 -269.112 201 -1019.19; 65 -269.112 201 -965.191; 66 -269.112 201 -905.191;67 -269.112 201 -845.191; 68 -259.97 201 -1138.75; 69 -259.97 201 -1073.19;70 -233.522 201 -1073.19; 71 -233.522 201 -965.191; 72 -233.522 201 -845.191;73 -223.97 201 -1138.75; 74 -223.97 201 -1073.19; 75 -188.976 201 -989.998;76 -188.97 201 -1138.75; 77 -188.97 201 -1104; 78 -188.97 201 -1073.19;79 -188.97 201 -1047; 80 -188.97 201 -965.191; 81 -188.97 201 -937.273;82 -188.97 201 -884.701; 83 -188.97 201 -845.191; 84 -188.97 201 -832.129;85 -188.97 201 -779.746; 86 -188.97 201 -733.306; 87 -188.97 201 -687.056;88 -188.97 201 -640.806; 89 -188.97 201 -594.746; 90 -107.676 201 -1138.75;91 -107.676 201 -1104; 92 -103.449 201 -1047; 93 -103.449 201 -989.998;94 -71.5593 201 -1047; 95 -71.5593 201 -989.998; 96 -54.2172 201 -1138.75;97 -54.2172 201 -1104; 98 10.03 201 -1138.75; 99 10.03 201 -1104;100 10.03 201 -1078.75; 101 10.03 201 -1047; 102 10.03 201 -989.998;103 10.03 201 -970.746; 104 10.03 201 -937.273; 105 10.03 201 -918.51;106 10.03 201 -884.701; 107 10.03 201 -832.129; 108 10.03 201 -821.297;109 10.03 201 -779.746; 110 10.03 201 -733.306; 111 10.03 201 -687.056;112 10.03 201 -640.806; 113 10.03 201 -594.746; 114 38.1339 201 -918.51;115 38.1339 201 -889.297; 116 38.1339 201 -845.128; 117 38.1339 201 -821.297;118 39.4058 201 -1078.75; 119 39.4058 201 -1062; 120 39.4058 201 -1032;121 39.4058 201 -987.79; 122 39.4058 201 -970.746; 123 50.03 201 -1138.75;124 50.03 201 -1078.75; 125 81.6305 201 -1078.75; 126 81.6305 201 -1062;127 81.6305 201 -1032; 128 81.6305 201 -1029.76; 129 81.6305 201 -987.79;130 81.6305 201 -970.746; 131 81.6305 201 -918.51; 132 81.6305 201 -889.297;133 81.6305 201 -869.27; 134 81.6305 201 -845.128; 135 81.6305 201 -821.297;136 90.03 201 -1138.75; 137 90.03 201 -1078.75; 138 123.66 201 -1138.75;139 123.66 201 -1078.75; 140 152.292 201 -1029.76; 141 152.292 201 -970.746;142 152.293 201 -995.746; 143 156.66 201 -1138.75; 144 156.66 201 -1078.75;145 189.255 201 -1029.76; 146 189.255 201 -995.746; 147 189.255 201 -970.746;148 190.53 201 -1138.75; 149 190.53 201 -1078.75; 150 224.38 201 -1138.75;151 224.38 201 -1078.75; 152 239.028 201 -1029.76; 153 239.03 201 -1138.75;154 239.03 201 -1078.75; 155 239.03 201 -1003.78; 156 239.03 201 -970.746;157 239.03 201 -918.51; 158 239.03 201 -908.746; 159 239.03 201 -869.27;160 239.03 201 -844.246; 161 239.03 201 -821.297; 162 239.03 201 -779.746;163 239.03 201 -733.306; 164 239.03 201 -687.056; 165 239.03 201 -640.806;166 239.03 201 -594.746; 167 284.185 201 -1138.75; 168 284.185 201 -1078.75;169 307.788 201 -1029.75; 170 307.792 201 -1003.78; 171 307.792 201 -970.74;172 307.792 201 -908.746; 173 315.208 201 -1138.75; 174 315.208 201 -1078.75;175 346.239 201 -1138.75; 176 346.239 201 -1078.75; 177 374.381 201 -1138.75;178 374.381 201 -1078.75; 179 408.03 201 -1138.75; 180 408.03 201 -1078.75;181 413.264 201 -1029.75; 182 413.264 201 -970.74; 183 413.268 201 -908.746;184 421.03 201 -779.746; 185 421.03 201 -733.306; 186 421.03 201 -687.056;187 421.03 201 -640.806; 188 421.03 201 -594.746; 189 440.06 201 -1138.75;190 440.06 201 -1078.75; 191 481.03 201 -1138.75; 192 481.03 201 -1119.5;193 481.03 201 -1099.5; 194 481.03 201 -1078.75; 195 529.03 201 -1138.75;196 529.03 201 -1119.5; 197 529.03 201 -1099.5; 198 529.03 201 -1078.75;199 529.03 201 -1029.75; 200 529.03 201 -970.74; 201 529.03 201 -844.246;202 529.03 201 -779.746; 203 529.03 201 -594.746; 204 529.032 201 -908.746;205 -631.22 471 -594.746; 206 -630.97 471 -1138.75; 207 -630.97 471 -1074.08;208 -630.97 471 -1011.62; 209 -630.97 471 -954.624; 210 -630.97 471 -892.992;211 -630.97 471 -840.084; 212 -630.97 471 -779.746; 213 -603.108 471 -1138.75;214 -603.106 471 -1074.08; 215 -566.448 471 -1138.75;216 -566.446 471 -1074.08; 217 -554.537 471 -1074.08;218 -554.537 471 -954.624; 219 -554.537 471 -892.992;220 -554.532 471 -1011.62; 221 -523.22 471 -779.746; 222 -523.22 471 -733.306;223 -523.22 471 -687.056; 224 -523.22 471 -640.806; 225 -523.22 471 -594.746;226 -519.359 471 -1074.08; 227 -519.359 471 -1011.62;228 -519.359 471 -954.624; 229 -519.359 471 -892.992;230 -516.636 471 -1138.75; 231 -516.63 471 -1074.08; 232 -479.976 471 -1138.75;233 -479.97 471 -1074.08; 234 -452.976 471 -1074.09; 235 -452.976 471 -1021.18;236 -452.97 471 -1138.75; 237 -452.97 471 -1011.62; 238 -452.97 471 -983.552;239 -452.97 471 -954.624; 240 -452.97 471 -930.637; 241 -452.97 471 -892.992;242 -452.97 471 -840.081; 243 -452.97 471 -838.624; 244 -452.97 471 -779.746;245 -452.97 471 -733.306; 246 -452.97 471 -711.904; 247 -452.97 471 -687.056;248 -452.97 471 -658.989; 249 -452.97 471 -640.806; 250 -452.97 471 -594.746;251 -412.441 471 -1074.09; 252 -412.441 471 -1021.18;253 -412.441 471 -983.552; 254 -412.441 471 -930.637;255 -412.441 471 -892.995; 256 -412.441 471 -840.081;257 -412.441 471 -779.746; 258 -412.441 471 -711.904;259 -412.441 471 -658.989; 260 -394.97 471 -1138.75; 261 -394.97 471 -1074.09;262 -355.239 471 -1074.09; 263 -355.239 471 -1021.18;264 -355.239 471 -983.552; 265 -355.239 471 -930.637;266 -355.239 471 -892.995; 267 -355.239 471 -840.081;268 -355.239 471 -779.746; 269 -355.239 471 -711.904;270 -355.239 471 -658.989; 271 -334.97 471 -1138.75; 272 -334.97 471 -1074.09;273 -300.975 471 -1138.75; 274 -300.975 471 -1074.09; 275 -259.97 471 -1138.75;276 -259.97 471 -1074.09; 277 -223.97 471 -1138.75; 278 -223.97 471 -1074.09;279 -188.976 471 -1074.09; 280 -188.97 471 -1138.75; 281 -188.97 471 -1021.18;282 -188.97 471 -983.552; 283 -188.97 471 -930.637; 284 -188.97 471 -925.536;285 -188.97 471 -892.995; 286 -188.97 471 -877.509; 287 -188.97 471 -840.081;288 -188.97 471 -828.533; 289 -188.97 471 -779.746; 290 -188.97 471 -733.306;291 -188.97 471 -711.904; 292 -188.97 471 -687.056; 293 -188.97 471 -658.989;294 -188.97 471 -640.806; 295 -188.97 471 -594.746; 296 10.03 471 -1138.75;297 10.03 471 -1068.36; 298 10.03 471 -1012.18; 299 10.03 471 -948.483;300 10.03 471 -925.532; 301 10.03 471 -877.509; 302 10.03 471 -875.746;303 10.03 471 -828.533; 304 10.03 471 -779.746; 305 10.03 471 -733.306;306 10.03 471 -687.056; 307 10.03 471 -640.806; 308 10.03 471 -594.746;309 42.5083 471 -1068.36; 310 42.5083 471 -1012.18; 311 42.5083 471 -992.119;312 42.5083 471 -948.483; 313 42.5083 471 -925.532; 314 42.5083 471 -875.746;315 42.5083 471 -849.458; 316 42.5083 471 -828.528; 317 42.5083 471 -779.746;318 50.03 471 -1138.75; 319 50.03 471 -1068.36; 320 78.528 471 -1068.36;321 78.528 471 -1012.18; 322 78.528 471 -992.119; 323 78.528 471 -948.483;324 78.528 471 -925.532; 325 78.528 471 -875.746; 326 78.528 471 -849.619;327 78.528 471 -827.746; 328 78.528 471 -779.746; 329 90.03 471 -1138.75;330 90.03 471 -1068.36; 331 123.66 471 -1138.75; 332 123.66 471 -1068.36;333 147.161 471 -1068.36; 334 147.161 471 -1012.18; 335 147.161 471 -948.483;336 147.161 471 -925.532; 337 147.161 471 -875.746; 338 147.161 471 -827.746;339 147.161 471 -779.746; 340 156.66 471 -1138.75; 341 156.66 471 -1068.36;342 175.465 471 -1068.36; 343 175.465 471 -998.006; 344 175.465 471 -970.887;345 175.465 471 -948.483; 346 175.465 471 -925.532; 347 175.465 471 -888.532;348 175.465 471 -855.506; 349 175.465 471 -828.387; 350 175.465 471 -779.746;351 190.524 471 -1068.36; 352 190.53 471 -1138.75; 353 224.38 471 -1138.75;354 224.38 471 -1068.36; 355 239.03 471 -1138.75; 356 239.03 471 -1078.75;357 239.03 471 -1068.36; 358 239.03 471 -1035.99; 359 239.03 471 -998.006;360 239.03 471 -970.887; 361 239.03 471 -948.483; 362 239.03 471 -925.532;363 239.03 471 -888.532; 364 239.03 471 -870.636; 365 239.03 471 -855.506;366 239.03 471 -836.581; 367 239.03 471 -828.387; 368 239.03 471 -779.746;369 239.03 471 -733.306; 370 239.03 471 -687.056; 371 239.03 471 -640.806;372 239.03 471 -594.746; 373 284.185 471 -1138.75; 374 284.185 471 -1078.75;375 315.208 471 -1138.75; 376 315.208 471 -1078.75; 377 346.239 471 -1138.75;378 346.239 471 -1078.75; 379 374.381 471 -1138.75; 380 374.381 471 -1078.75;381 408.03 471 -1138.75; 382 408.03 471 -1078.75; 383 421.03 471 -779.746;384 421.03 471 -733.306; 385 421.03 471 -687.056; 386 421.03 471 -640.806;387 421.03 471 -594.746; 388 440.06 471 -1138.75; 389 440.06 471 -1078.75;390 484.53 471 -1138.75; 391 484.53 471 -1078.75; 392 529.03 471 -1138.75;393 529.03 471 -1078.75; 394 529.03 471 -1035.99; 395 529.03 471 -998.004;396 529.03 471 -948.48; 397 529.03 471 -925.536; 398 529.03 471 -870.636;399 529.03 471 -836.581; 400 529.03 471 -779.746; 401 529.03 471 -594.746;402 -631.22 713 -594.746; 403 -630.97 713 -1138.75; 404 -630.97 713 -1074.46;405 -630.97 713 -1039.08; 406 -630.97 713 -987.078; 407 -630.97 713 -935.078;408 -630.97 713 -893.078; 409 -630.97 713 -855.972; 410 -630.97 713 -817.975;411 -630.97 713 -779.746; 412 -603.106 713 -1138.75; 413 -603.106 713 -1074.46;414 -566.446 713 -1138.75; 415 -566.446 713 -1074.46; 416 -558.35 713 -1039.08;417 -558.35 713 -987.078; 418 -558.35 713 -935.078; 419 -558.35 713 -893.078;420 -523.22 713 -779.746; 421 -523.22 713 -743.746; 422 -523.22 713 -705.246;423 -523.22 713 -649.996; 424 -523.22 713 -594.746; 425 -516.63 713 -1138.75;426 -516.63 713 -1074.46; 427 -485.865 713 -1039.08; 428 -485.865 713 -987.078;429 -485.865 713 -935.078; 430 -485.865 713 -893.078; 431 -479.97 713 -1138.75;432 -479.97 713 -1074.46; 433 -452.976 713 -1029.97; 434 -452.976 713 -851.475;435 -452.97 713 -1138.75; 436 -452.97 713 -1074.46; 437 -452.97 713 -1039.08;438 -452.97 713 -987.078; 439 -452.97 713 -975.975; 440 -452.97 713 -935.078;441 -452.97 713 -921.975; 442 -452.97 713 -893.078; 443 -452.97 713 -855.975;444 -452.97 713 -817.975; 445 -452.97 713 -779.746; 446 -452.97 713 -743.746;447 -452.97 713 -705.246; 448 -452.97 713 -649.996; 449 -452.97 713 -594.746;450 -404.26 713 -1029.97; 451 -404.26 713 -975.975; 452 -394.97 713 -1138.75;453 -394.97 713 -1074.46; 454 -375.396 713 -1029.97; 455 -375.396 713 -975.975;456 -334.97 713 -1138.75; 457 -334.968 713 -1074.46; 458 -311.699 713 -1029.97;459 -311.699 713 -975.975; 460 -311.699 713 -921.975;461 -311.699 713 -855.975; 462 -300.975 713 -1138.75;463 -300.975 713 -1074.46; 464 -296.97 713 -705.246; 465 -296.97 713 -671.246;466 -296.97 713 -649.996; 467 -296.97 713 -640.246; 468 -296.97 713 -594.746;469 -262.97 713 -705.246; 470 -259.97 713 -1138.75; 471 -259.97 713 -1074.46;472 -251.47 713 -594.746; 473 -240.473 713 -594.746; 474 -236.244 713 -921.975;475 -236.244 713 -855.975; 476 -236.225 713 -1029.97;477 -236.225 713 -975.975; 478 -228.973 713 -705.246; 479 -223.97 713 -1138.75;480 -223.97 713 -1074.46; 481 -188.97 713 -1138.75; 482 -188.97 713 -1109.75;483 -188.97 713 -1074.46; 484 -188.97 713 -1029.97; 485 -188.97 713 -975.975;486 -188.97 713 -921.975; 487 -188.97 713 -871.746; 488 -188.97 713 -855.975;489 -188.97 713 -817.975; 490 -188.97 713 -779.746; 491 -188.97 713 -743.746;492 -188.97 713 -705.246; 493 -188.97 713 -693.246; 494 -188.97 713 -665.243;495 -188.97 713 -646.249; 496 -188.97 713 -643.996; 497 -188.97 713 -594.746;498 -128.97 713 -693.246; 499 -128.97 713 -657.392; 500 -128.97 713 -643.996;501 -128.97 713 -634.1; 502 -128.97 713 -594.746; 503 -94.3461 713 -693.246;504 -90.9662 713 -594.746; 505 -86.9739 713 -594.746;506 -83.5939 713 -693.246; 507 -49.97 713 -693.246; 508 -49.97 713 -658.428;509 -49.97 713 -643.996; 510 -49.97 713 -633.065; 511 -49.97 713 -594.746;512 10.03 713 -1138.75; 513 10.03 713 -1109.75; 514 10.03 713 -1074.46;515 10.03 713 -1038.75; 516 10.03 713 -994.746; 517 10.03 713 -950.746;518 10.03 713 -921.972; 519 10.03 713 -896.084; 520 10.03 713 -871.746;521 10.03 713 -837.915; 522 10.03 713 -817.746; 523 10.03 713 -779.746;524 10.03 713 -743.746; 525 10.03 713 -705.246; 526 10.03 713 -693.246;527 10.03 713 -665.246; 528 10.03 713 -646.246; 529 10.03 713 -643.996;530 10.03 713 -594.746; 531 50.03 713 -1138.75; 532 50.03 713 -1074.46;533 50.03 713 -705.246; 534 61.53 713 -594.746; 535 72.5253 713 -594.746;536 84.0253 713 -705.246; 537 90.03 713 -1138.75; 538 90.03 713 -1074.46;539 123.66 713 -1138.75; 540 123.66 713 -1074.46; 541 126.03 713 -705.246;542 126.03 713 -664.314; 543 126.03 713 -663.242; 544 126.03 713 -648.251;545 126.03 713 -647.179; 546 126.03 713 -594.746; 547 147.03 713 -1038.75;548 147.03 713 -994.746; 549 147.03 713 -950.746; 550 147.03 713 -896.084;551 147.03 713 -837.915; 552 147.03 713 -779.746; 553 157.03 713 -1138.75;554 157.03 713 -1074.46; 555 164.2 713 -705.246; 556 174.924 713 -594.746;557 175.339 713 -896.084; 558 175.339 713 -855.344; 559 175.339 713 -828.225;560 175.339 713 -779.746; 561 175.415 713 -1038.75; 562 175.415 713 -997.996;563 175.415 713 -970.887; 564 175.415 713 -950.746; 565 189.136 713 -594.746;566 191.03 713 -1138.75; 567 191.03 713 -1074.46; 568 199.86 713 -705.246;569 223.88 713 -1138.75; 570 223.88 713 -1074.46; 571 239.03 713 -1138.75;572 239.03 713 -1094.75; 573 239.03 713 -1074.46; 574 239.03 713 -1050.75;575 239.03 713 -1038.76; 576 239.03 713 -997.996; 577 239.03 713 -970.887;578 239.03 713 -950.746; 579 239.03 713 -942.746; 580 239.03 713 -896.084;581 239.03 713 -855.344; 582 239.03 713 -837.915; 583 239.03 713 -828.225;584 239.03 713 -779.746; 585 239.03 713 -743.746; 586 239.03 713 -705.246;587 239.03 713 -663.242; 588 239.03 713 -649.996; 589 239.03 713 -594.746;590 299.03 713 -705.246; 591 299.03 713 -670.043; 592 299.03 713 -649.996;593 299.03 713 -641.449; 594 299.03 713 -594.746; 595 334.233 713 -705.246;596 345.733 713 -594.746; 597 356.327 713 -594.746; 598 367.827 713 -705.246;599 374.631 713 -1138.75; 600 374.631 713 -1094.75; 601 374.631 713 -1050.75;602 403.03 713 -705.246; 603 403.03 713 -670.043; 604 403.03 713 -641.449;605 403.03 713 -594.746; 606 408.03 713 -1138.75; 607 408.03 713 -1050.75;608 421.03 713 -779.746; 609 421.03 713 -743.746; 610 421.03 713 -705.246;611 421.03 713 -594.746; 612 439.31 713 -1138.75; 613 439.31 713 -1082.75;614 439.31 713 -1050.75; 615 461.53 713 -942.746; 616 461.53 713 -896.084;617 461.53 713 -837.915; 618 491.405 713 -942.746; 619 491.405 713 -896.084;620 491.405 713 -837.915; 621 529.03 713 -1138.75; 622 529.03 713 -1082.75;623 529.03 713 -1050.75; 624 529.03 713 -996.746; 625 529.03 713 -942.746;626 529.03 713 -896.084; 627 529.03 713 -837.915; 628 529.03 713 -779.746;629 529.03 713 -594.746; 630 -631.22 900 -594.746; 631 -630.972 900 -984.889;632 -630.97 900 -1138.75; 633 -630.97 900 -1074.46; 634 -630.97 900 -1036.17;635 -630.97 900 -933.603; 636 -630.97 900 -882.318; 637 -630.97 900 -831.032;638 -630.97 900 -779.746; 639 -603.106 900 -1138.75; 640 -603.106 900 -1074.46;641 -566.446 900 -1138.75; 642 -566.446 900 -1074.46; 643 -523.22 900 -779.746;644 -523.22 900 -733.496; 645 -523.22 900 -687.246; 646 -523.22 900 -640.996;647 -523.22 900 -594.746; 648 -516.63 900 -1138.75; 649 -516.63 900 -1074.46;650 -479.97 900 -1138.75; 651 -479.97 900 -1074.46; 652 -452.97 900 -1138.75;653 -452.97 900 -1074.46; 654 -452.97 900 -1036.17; 655 -452.97 900 -984.889;656 -452.97 900 -933.603; 657 -452.97 900 -882.318; 658 -452.97 900 -831.032;659 -452.97 900 -779.746; 660 -452.97 900 -733.496; 661 -452.97 900 -687.246;662 -452.97 900 -640.996; 663 -452.97 900 -594.746; 664 -394.97 900 -1138.75;665 -394.97 900 -1074.46; 666 -334.97 900 -1138.75; 667 -334.97 900 -1074.46;668 -300.975 900 -1138.75; 669 -300.975 900 -1074.46;670 -264.894 900 -687.246; 671 -264.894 900 -677.871;672 -264.894 900 -640.996; 673 -264.894 900 -622.622;674 -264.894 900 -594.746; 675 -259.97 900 -1138.75; 676 -259.97 900 -1074.46;677 -227.049 900 -687.246; 678 -227.049 900 -677.871;679 -227.049 900 -640.996; 680 -227.049 900 -622.622;681 -227.049 900 -594.746; 682 -223.97 900 -1138.75; 683 -223.97 900 -1074.46;684 -188.97 900 -1138.75; 685 -188.97 900 -1087.46; 686 -188.97 900 -1074.46;687 -188.97 900 -1036.17; 688 -188.97 900 -984.889; 689 -188.97 900 -933.603;690 -188.97 900 -882.318; 691 -188.97 900 -831.032; 692 -188.97 900 -779.746;693 -188.97 900 -733.496; 694 -188.97 900 -687.246; 695 -188.97 900 -640.996;696 -188.97 900 -594.746; 697 -112.957 900 -687.246; 698 -112.957 900 -640.996;699 -112.957 900 -594.746; 700 -103.97 900 -984.889; 701 -103.968 900 -933.603;702 -74.9732 900 -984.889; 703 -74.9732 900 -933.603;704 -65.9569 900 -687.246; 705 -65.9569 900 -640.996;706 -65.9569 900 -594.746; 707 10.03 900 -1138.75; 708 10.03 900 -1087.46;709 10.03 900 -1074.46; 710 10.03 900 -1036.17; 711 10.03 900 -984.889;712 10.03 900 -933.603; 713 10.03 900 -882.318; 714 10.03 900 -831.032;715 10.03 900 -779.746; 716 10.03 900 -733.496; 717 10.03 900 -687.246;718 10.03 900 -642.996; 719 10.03 900 -640.992; 720 10.03 900 -594.746;721 50.03 900 -1138.75; 722 50.03 900 -1074.46; 723 54.1676 900 -687.246;724 54.1676 900 -671.664; 725 54.1676 900 -640.992; 726 54.1676 900 -629.996;727 54.168 900 -594.746; 728 80.136 900 -594.746; 729 80.1376 900 -687.246;730 80.1376 900 -671.664; 731 80.1376 900 -640.992; 732 80.1376 900 -629.996;733 90.03 900 -1138.75; 734 90.03 900 -1074.46; 735 123.66 900 -1138.75;736 123.66 900 -1074.46; 737 157.03 900 -1138.75; 738 157.03 900 -1074.46;739 163.035 900 -687.246; 740 163.035 900 -673.496; 741 163.045 900 -640.992;742 163.045 900 -627.496; 743 163.045 900 -594.746; 744 191.03 900 -1138.75;745 191.03 900 -1074.46; 746 201.015 900 -687.246; 747 201.015 900 -673.496;748 201.015 900 -640.992; 749 201.015 900 -627.496; 750 201.015 900 -594.746;751 223.88 900 -1138.75; 752 223.88 900 -1074.46; 753 239.028 900 -733.496;754 239.03 900 -1138.75; 755 239.03 900 -1074.46; 756 239.03 900 -1052.46;757 239.03 900 -1036.18; 758 239.03 900 -984.889; 759 239.03 900 -933.603;760 239.03 900 -882.318; 761 239.03 900 -831.032; 762 239.03 900 -779.746;763 239.03 900 -687.246; 764 239.03 900 -640.996; 765 239.03 900 -594.746;766 267.302 900 -1052.46; 767 267.302 900 -933.603; 768 284.03 900 -1138.75;769 284.03 900 -1074.46; 770 327.68 900 -687.246; 771 327.68 900 -640.992;772 327.68 900 -594.746; 773 329.03 900 -1138.75; 774 329.03 900 -1074.46;775 345.247 900 -1052.46; 776 345.247 900 -993.032; 777 345.247 900 -933.603;778 374.03 900 -1138.75; 779 374.03 900 -1074.46; 780 374.68 900 -687.246;781 374.68 900 -640.996; 782 374.68 900 -594.746; 783 408.014 900 -1138.75;784 408.014 900 -1074.46; 785 421.03 900 -779.746; 786 421.03 900 -733.496;787 421.03 900 -687.246; 788 421.03 900 -640.996; 789 421.03 900 -594.746;790 440.014 900 -1138.75; 791 440.014 900 -1074.46; 792 484.014 900 -1138.75;793 484.014 900 -1074.46; 794 529.03 900 -1138.75; 795 529.03 900 -1074.46;796 529.03 900 -1052.46; 797 529.03 900 -993.032; 798 529.03 900 -933.603;799 529.03 900 -882.318; 800 529.03 900 -831.032; 801 529.03 900 -779.746;802 529.03 900 -594.746; 803 -630.972 1168 -839.746;804 -630.972 1168 -779.746; 805 -630.972 1168 -718.747;806 -630.972 1168 -656.746; 807 -630.972 1168 -594.746;808 -630.971 1168 -1019.75; 809 -630.971 1168 -959.746;810 -630.971 1168 -899.746; 811 -630.97 1168 -1138.75;812 -630.97 1168 -1079.75; 813 -452.97 1168 -1138.75;814 -452.97 1168 -1079.75; 815 -452.97 1168 -1019.75;816 -452.97 1168 -959.746; 817 -452.97 1168 -899.746;818 -452.97 1168 -839.746; 819 -452.97 1168 -779.746;820 -452.97 1168 -718.747; 821 -452.97 1168 -656.746;822 -452.97 1168 -594.746; 823 -188.97 1168 -1138.75;824 -188.97 1168 -1079.75; 825 -188.97 1168 -1019.75;826 -188.97 1168 -959.746; 827 -188.97 1168 -899.746;828 -188.97 1168 -839.746; 829 -188.97 1168 -779.746;830 -188.97 1168 -718.747; 831 -188.97 1168 -656.746;832 -188.97 1168 -594.746; 833 10.03 1168 -1138.75; 834 10.03 1168 -1079.75;835 10.03 1168 -1019.75; 836 10.03 1168 -959.746; 837 10.03 1168 -899.746;838 10.03 1168 -839.746; 839 10.03 1168 -779.746; 840 10.03 1168 -718.747;841 10.03 1168 -656.746; 842 10.03 1168 -594.746; 843 239.03 1168 -1138.75;844 239.03 1168 -1079.75; 845 239.03 1168 -1019.75; 846 239.03 1168 -959.746;847 239.03 1168 -899.746; 848 239.03 1168 -839.746; 849 239.03 1168 -779.746;850 239.03 1168 -718.747; 851 239.03 1168 -656.746; 852 239.03 1168 -594.746;853 529.03 1168 -1138.75; 854 529.03 1168 -1079.75; 855 529.03 1168 -1019.75;856 529.03 1168 -959.746; 857 529.03 1168 -899.746; 858 529.03 1168 -839.746;859 529.03 1168 -779.746; 860 529.03 1168 -718.747; 861 529.03 1168 -656.746;862 529.03 1168 -594.746;MEMBER INCIDENCES1 1 19; 2 27 1; 3 3 19; 4 2 20; 5 20 3; 6 2 27; 7 3 27; 8 4 41; 9 5 52;10 56 5; 11 52 6; 12 6 56; 13 4 76; 14 7 41; 15 6 89; 16 9 56; 17 7 76;18 8 85; 19 89 8; 20 85 9; 21 9 89; 22 10 76; 23 7 98; 24 12 89; 25 9 113;26 10 98; 27 11 109; 28 113 11; 29 109 12; 30 12 113; 31 13 153; 32 14 162;33 166 14; 34 162 15; 35 15 166; 36 16 195; 37 195 17; 38 16 202; 39 17 202;40 203 17; 41 18 202; 42 18 203; 43 27 19; 44 20 21; 45 21 22; 46 22 23;47 23 24; 48 24 25; 49 25 26; 50 26 27; 51 21 28; 52 22 29; 53 28 29; 54 28 30;55 29 31; 56 38 19; 57 27 34; 58 30 31; 59 30 32; 60 31 33; 61 20 41; 62 23 45;63 24 47; 64 25 49; 65 26 51; 66 32 33; 67 35 34; 68 36 35; 69 37 36; 70 38 37;71 32 39; 72 33 40; 73 39 40; 74 34 52; 75 35 53; 76 36 54; 77 37 55; 78 38 56;79 39 42; 80 40 43; 81 41 42; 82 42 43; 83 43 44; 84 44 45; 85 45 46; 86 46 47;87 47 48; 88 48 49; 89 49 50; 90 50 51; 91 51 52; 92 52 53; 93 53 54; 94 54 55;95 55 56; 96 41 57; 97 42 58; 98 57 58; 99 57 59; 100 58 60; 101 44 64;102 46 65; 103 66 48; 104 50 67; 105 59 60; 106 52 85; 107 53 86; 108 54 87;109 55 88; 110 56 89; 111 59 61; 112 60 62; 113 61 62; 114 62 63; 115 61 68;116 63 64; 117 64 65; 118 65 66; 119 66 67; 120 63 69; 121 68 69; 122 65 71;123 67 72; 124 69 70; 125 68 73; 126 70 71; 127 71 72; 128 70 74; 129 73 74;130 71 80; 131 72 83; 132 73 76; 133 74 78; 134 79 75; 135 75 80; 136 76 77;137 77 78; 138 78 79; 139 80 81; 140 81 82; 141 82 83; 142 83 84; 143 84 85;144 85 86; 145 86 87; 146 87 88; 147 88 89; 148 76 90; 149 77 91; 150 75 93;151 79 92; 152 90 91; 153 92 93; 154 81 104; 155 82 106; 156 84 107;157 85 109; 158 86 110; 159 87 111; 160 88 112; 161 89 113; 162 92 94;163 93 95; 164 90 96; 165 91 97; 166 94 95; 167 96 97; 168 94 101; 169 95 102;170 96 98; 171 97 99; 172 98 99; 173 99 100; 174 100 101; 175 101 102;176 102 103; 177 103 104; 178 104 105; 179 105 106; 180 106 107; 181 107 108;182 108 109; 183 109 110; 184 110 111; 185 111 112; 186 112 113; 187 114 105;188 117 108; 189 118 100; 190 122 103; 191 98 123; 192 114 115; 193 115 116;194 116 117; 195 118 119; 196 119 120; 197 120 121; 198 121 122; 199 124 118;200 123 124; 201 131 114; 202 115 132; 203 116 134; 204 135 117; 205 119 126;206 120 127; 207 121 129; 208 130 122; 209 125 124; 210 123 136; 211 125 126;212 126 127; 213 127 128; 214 128 129; 215 129 130; 216 131 132; 217 132 133;218 133 134; 219 134 135; 220 137 125; 221 136 137; 222 136 138; 223 139 137;224 128 140; 225 141 130; 226 138 139; 227 109 162; 228 110 163; 229 111 164;230 112 165; 231 113 166; 232 138 143; 233 144 139; 234 140 142; 235 142 141;236 143 144; 237 157 131; 238 133 159; 239 161 135; 240 140 145; 241 147 141;242 142 146; 243 143 148; 244 149 144; 245 145 146; 246 146 147; 247 148 149;248 148 150; 249 151 149; 250 145 152; 251 156 147; 252 150 151; 253 150 153;254 154 151; 255 154 152; 256 152 155; 257 153 154; 258 155 156; 259 156 157;260 157 158; 261 158 159; 262 159 160; 263 160 161; 264 161 162; 265 162 163;266 163 164; 267 164 165; 268 165 166; 269 153 167; 270 154 168; 271 152 169;272 155 170; 273 156 171; 274 158 172; 275 168 167; 276 167 173; 277 168 174;278 169 170; 279 170 171; 280 171 172; 281 174 173; 282 162 184; 283 163 185;284 164 186; 285 165 187; 286 166 188; 287 173 175; 288 174 176; 289 176 175;290 175 177; 291 176 178; 292 169 181; 293 171 182; 294 172 183; 295 178 177;296 160 201; 297 177 179; 298 178 180; 299 180 179; 300 181 182; 301 182 183;302 185 184; 303 186 185; 304 187 186; 305 188 187; 306 179 189; 307 180 190;308 190 189; 309 189 191; 310 190 194; 311 181 199; 312 182 200; 313 183 204;314 184 202; 315 188 203; 316 191 192; 317 192 193; 318 193 194; 319 191 195;320 192 196; 321 193 197; 322 194 198; 323 195 196; 324 196 197; 325 197 198;326 198 199; 327 199 200; 328 201 202; 329 202 203; 330 200 204; 331 204 201;332 19 205; 333 19 212; 334 205 27; 335 20 206; 336 206 27; 337 212 20;338 27 212; 339 41 236; 340 52 244; 341 244 56; 342 250 52; 343 56 250;344 76 236; 345 41 280; 346 89 250; 347 56 295; 348 76 280; 349 85 289;350 289 89; 351 295 85; 352 89 295; 353 280 98; 354 76 296; 355 295 113;356 89 308; 357 98 296; 358 109 304; 359 304 113; 360 308 109; 361 113 308;362 153 355; 363 162 368; 364 368 166; 365 372 162; 366 166 372; 367 195 392;368 392 202; 369 400 195; 370 202 400; 371 401 202; 372 203 400; 373 203 401;374 212 205; 375 206 207; 376 207 208; 377 208 209; 378 209 210; 379 210 211;380 211 212; 381 206 213; 382 207 214; 383 214 213; 384 209 218; 385 210 219;386 208 220; 387 213 215; 388 214 216; 389 225 205; 390 212 221; 391 216 215;392 216 217; 393 218 219; 394 217 220; 395 220 218; 396 211 242; 397 215 230;398 217 226; 399 218 228; 400 219 229; 401 220 227; 402 221 222; 403 222 223;404 223 224; 405 224 225; 406 226 227; 407 227 228; 408 228 229; 409 226 231;410 231 230; 411 230 232; 412 231 233; 413 221 244; 414 222 245; 415 223 247;416 224 249; 417 225 250; 418 227 237; 419 228 239; 420 229 241; 421 233 232;422 232 236; 423 234 233; 424 234 235; 425 236 234; 426 235 237; 427 237 238;428 238 239; 429 239 240; 430 240 241; 431 241 242; 432 242 243; 433 243 244;434 244 245; 435 245 246; 436 246 247; 437 247 248; 438 248 249; 439 249 250;440 251 234; 441 235 252; 442 238 253; 443 240 254; 444 241 255; 445 242 256;446 244 257; 447 246 258; 448 248 259; 449 236 260; 450 251 252; 451 253 254;452 255 256; 453 257 256; 454 257 258; 455 258 259; 456 251 261; 457 260 261;458 252 263; 459 253 264; 460 254 265; 461 255 266; 462 256 267; 463 257 268;464 258 269; 465 259 270; 466 261 262; 467 260 271; 468 262 263; 469 264 265;470 266 267; 471 268 267; 472 268 269; 473 269 270; 474 262 272; 475 271 272;476 250 295; 477 271 273; 478 272 274; 479 273 274; 480 273 275; 481 274 276;482 263 281; 483 264 282; 484 265 283; 485 266 285; 486 267 287; 487 268 289;488 269 291; 489 270 293; 490 275 276; 491 275 277; 492 276 278; 493 277 278;494 278 279; 495 277 280; 496 280 279; 497 279 281; 498 281 282; 499 282 283;500 283 284; 501 284 285; 502 285 286; 503 286 287; 504 287 288; 505 288 289;506 289 290; 507 290 291; 508 291 292; 509 292 293; 510 293 294; 511 294 295;512 280 296; 513 284 300; 514 286 301; 515 288 303; 516 289 304; 517 290 305;518 292 306; 519 294 307; 520 295 308; 521 296 297; 522 297 298; 523 298 299;524 299 300; 525 300 301; 526 301 302; 527 302 303; 528 303 304; 529 304 305;530 305 306; 531 306 307; 532 307 308; 533 297 309; 534 310 298; 535 299 312;536 300 313; 537 314 302; 538 316 303; 539 304 317; 540 296 318; 541 309 310;542 310 311; 543 311 312; 544 313 314; 545 314 315; 546 315 316; 547 316 317;548 309 319; 549 318 319; 550 311 322; 551 312 323; 552 313 324; 553 315 326;554 317 328; 555 319 320; 556 318 329; 557 320 321; 558 321 322; 559 322 323;560 324 325; 561 325 326; 562 326 327; 563 327 328; 564 320 330; 565 329 330;566 329 331; 567 330 332; 568 321 334; 569 323 335; 570 324 336; 571 325 337;572 327 338; 573 328 339; 574 331 332; 575 305 369; 576 306 370; 577 307 371;578 308 372; 579 332 333; 580 331 340; 581 333 334; 582 334 335; 583 336 337;584 337 338; 585 338 339; 586 333 341; 587 340 341; 588 335 345; 589 336 346;590 339 350; 591 341 342; 592 340 352; 593 342 343; 594 343 344; 595 344 345;596 346 347; 597 347 348; 598 348 349; 599 349 350; 600 342 351; 601 352 351;602 343 359; 603 344 360; 604 345 361; 605 346 362; 606 347 363; 607 348 365;608 349 367; 609 350 368; 610 351 354; 611 352 353; 612 353 354; 613 353 355;614 354 357; 615 355 356; 616 356 357; 617 357 358; 618 358 359; 619 359 360;620 360 361; 621 361 362; 622 362 363; 623 363 364; 624 364 365; 625 365 366;626 366 367; 627 367 368; 628 368 369; 629 369 370; 630 370 371; 631 371 372;632 355 373; 633 356 374; 634 374 373; 635 373 375; 636 374 376; 637 376 375;638 368 383; 639 369 384; 640 370 385; 641 371 386; 642 372 387; 643 375 377;644 376 378; 645 378 377; 646 377 379; 647 378 380; 648 380 379; 649 358 394;650 359 395; 651 361 396; 652 362 397; 653 364 398; 654 366 399; 655 379 381;656 380 382; 657 382 381; 658 383 384; 659 384 385; 660 385 386; 661 386 387;662 381 388; 663 382 389; 664 389 388; 665 388 390; 666 389 391; 667 383 400;668 401 387; 669 390 391; 670 390 392; 671 391 393; 672 392 393; 673 393 394;674 394 395; 675 395 396; 676 396 397; 677 397 398; 678 398 399; 679 399 400;680 400 401; 681 205 402; 682 205 411; 683 212 402; 684 206 403; 685 403 212;686 411 206; 687 212 411; 688 236 435; 689 244 435; 690 236 445; 691 244 445;692 250 449; 693 280 435; 694 236 481; 695 295 449; 696 250 497; 697 280 481;698 289 481; 699 280 490; 700 289 490; 701 295 497; 702 280 512; 703 296 481;704 295 530; 705 308 497; 706 296 512; 707 304 512; 708 296 523; 709 304 523;710 308 530; 711 355 571; 712 368 571; 713 355 584; 714 368 584; 715 372 589;716 392 621; 717 621 400; 718 628 392; 719 400 628; 720 629 400; 721 401 628;722 401 629; 723 411 402; 724 403 404; 725 404 405; 726 405 406; 727 406 407;728 407 408; 729 408 409; 730 409 410; 731 410 411; 732 403 412; 733 404 413;734 413 412; 735 416 405; 736 417 406; 737 418 407; 738 419 408; 739 412 414;740 413 415; 741 424 402; 742 411 420; 743 415 414; 744 417 416; 745 419 418;746 409 443; 747 410 444; 748 414 425; 749 415 426; 750 420 421; 751 421 422;752 422 423; 753 423 424; 754 427 416; 755 428 417; 756 429 418; 757 430 419;758 426 425; 759 425 431; 760 426 432; 761 420 445; 762 446 421; 763 422 447;764 423 448; 765 424 449; 766 428 427; 767 430 429; 768 432 431; 769 437 427;770 438 428; 771 440 429; 772 442 430; 773 431 435; 774 432 436; 775 437 433;776 433 438; 777 443 434; 778 434 444; 779 435 436; 780 436 437; 781 438 439;782 439 440; 783 440 441; 784 441 442; 785 442 443; 786 444 445; 787 445 446;788 446 447; 789 447 448; 790 448 449; 791 433 450; 792 439 451; 793 435 452;794 436 453; 795 450 451; 796 452 453; 797 450 454; 798 451 455; 799 441 460;800 443 461; 801 454 455; 802 447 464; 803 448 466; 804 449 468; 805 452 456;806 453 457; 807 454 458; 808 455 459; 809 456 457; 810 444 489; 811 445 490;812 446 491; 813 456 462; 814 457 463; 815 458 459; 816 460 461; 817 462 463;818 464 465; 819 465 466; 820 466 467; 821 467 468; 822 462 470; 823 463 471;824 464 469; 825 465 469; 826 467 472; 827 468 472; 828 460 474; 829 461 475;830 458 476; 831 459 477; 832 470 471; 833 469 478; 834 472 473; 835 470 479;836 471 480; 837 474 475; 838 476 477; 839 479 480; 840 496 473; 841 473 497;842 474 486; 843 475 488; 844 476 484; 845 477 485; 846 478 492; 847 494 478;848 479 481; 849 480 483; 850 481 482; 851 482 483; 852 483 484; 853 484 485;854 485 486; 855 486 487; 856 487 488; 857 488 489; 858 489 490; 859 490 491;860 491 492; 861 492 493; 862 493 494; 863 494 495; 864 495 496; 865 496 497;866 493 498; 867 500 496; 868 497 502; 869 498 499; 870 499 500; 871 500 501;872 501 502; 873 498 503; 874 499 503; 875 501 504; 876 502 504; 877 481 512;878 482 513; 879 486 518; 880 487 520; 881 489 522; 882 490 523; 883 491 524;884 504 505; 885 503 506; 886 510 505; 887 505 511; 888 506 507; 889 508 506;890 507 508; 891 508 509; 892 509 510; 893 510 511; 894 507 526; 895 509 529;896 511 530; 897 512 513; 898 513 514; 899 514 515; 900 515 516; 901 516 517;902 517 518; 903 518 519; 904 519 520; 905 520 521; 906 521 522; 907 522 523;908 523 524; 909 524 525; 910 525 526; 911 526 527; 912 527 528; 913 528 529;914 529 530; 915 512 531; 916 514 532; 917 525 533; 918 527 533; 919 529 534;920 530 534; 921 531 532; 922 533 536; 923 534 535; 924 531 537; 925 532 538;926 515 547; 927 516 548; 928 517 549; 929 519 550; 930 521 551; 931 523 552;932 537 538; 933 544 535; 934 535 546; 935 536 541; 936 543 536; 937 537 539;938 538 540; 939 539 540; 940 524 585; 941 542 541; 942 543 542; 943 544 543;944 545 544; 945 546 545; 946 539 553; 947 540 554; 948 541 555; 949 542 555;950 547 548; 951 548 549; 952 550 551; 953 551 552; 954 545 556; 955 546 556;956 553 554; 957 550 557; 958 552 560; 959 547 561; 960 549 564; 961 553 566;962 554 567; 963 557 558; 964 558 559; 965 559 560; 966 561 562; 967 562 563;968 563 564; 969 555 568; 970 556 565; 971 566 567; 972 557 580; 973 581 558;974 583 559; 975 560 584; 976 561 575; 977 576 562; 978 577 563; 979 564 578;980 566 569; 981 567 570; 982 588 565; 983 565 589; 984 568 586; 985 587 568;986 569 570; 987 569 571; 988 570 573; 989 571 572; 990 572 573; 991 573 574;992 574 575; 993 575 576; 994 576 577; 995 577 578; 996 578 579; 997 579 580;998 580 581; 999 581 582; 1000 582 583; 1001 583 584; 1002 584 585;1003 585 586; 1004 586 587; 1005 587 588; 1006 588 589; 1007 586 590;1008 592 588; 1009 589 594; 1010 590 591; 1011 591 592; 1012 592 593;1013 593 594; 1014 571 599; 1015 600 572; 1016 574 601; 1017 590 595;1018 595 591; 1019 596 593; 1020 594 596; 1021 584 608; 1022 585 609;1023 579 615; 1024 580 616; 1025 582 617; 1026 595 598; 1027 596 597;1028 600 599; 1029 601 600; 1030 597 604; 1031 597 605; 1032 576 624;1033 598 602; 1034 598 603; 1035 599 606; 1036 601 607; 1037 602 603;1038 603 604; 1039 604 605; 1040 607 606; 1041 602 610; 1042 605 611;1043 609 608; 1044 609 610; 1045 610 611; 1046 606 612; 1047 607 614;1048 613 612; 1049 614 613; 1050 615 616; 1051 617 616; 1052 608 628;1053 629 611; 1054 615 618; 1055 616 619; 1056 617 620; 1057 612 621;1058 613 622; 1059 614 623; 1060 618 619; 1061 620 619; 1062 618 625;1063 619 626; 1064 620 627; 1065 621 622; 1066 622 623; 1067 623 624;1068 624 625; 1069 625 626; 1070 626 627; 1071 627 628; 1072 628 629;1073 402 630; 1074 638 402; 1075 411 630; 1076 403 632; 1077 632 411;1078 403 638; 1079 411 638; 1080 435 652; 1081 435 659; 1082 445 652;1083 445 659; 1084 449 663; 1085 481 652; 1086 435 684; 1087 497 663;1088 449 696; 1089 481 684; 1090 481 692; 1091 490 684; 1092 490 692;1093 497 696; 1094 481 707; 1095 512 684; 1096 497 720; 1097 530 696;1098 512 707; 1099 512 715; 1100 523 707; 1101 523 715; 1102 530 720;1103 571 754; 1104 571 762; 1105 584 754; 1106 584 762; 1107 589 765;1108 621 794; 1109 794 628; 1110 621 801; 1111 628 801; 1112 802 628;1113 629 801; 1114 629 802; 1115 638 630; 1116 634 631; 1117 631 635;1118 632 633; 1119 633 634; 1120 635 636; 1121 636 637; 1122 637 638;1123 632 639; 1124 633 640; 1125 640 639; 1126 639 641; 1127 640 642;1128 647 630; 1129 638 643; 1130 642 641; 1131 631 655; 1132 634 654;1133 635 656; 1134 636 657; 1135 637 658; 1136 641 648; 1137 642 649;1138 643 644; 1139 644 645; 1140 645 646; 1141 646 647; 1142 649 648;1143 648 650; 1144 649 651; 1145 643 659; 1146 644 660; 1147 645 661;1148 646 662; 1149 647 663; 1150 651 650; 1151 650 652; 1152 651 653;1153 652 653; 1154 653 654; 1155 654 655; 1156 655 656; 1157 656 657;1158 657 658; 1159 658 659; 1160 659 660; 1161 660 661; 1162 661 662;1163 662 663; 1164 652 664; 1165 653 665; 1166 664 665; 1167 664 666;1168 665 667; 1169 661 670; 1170 662 672; 1171 663 674; 1172 666 667;1173 654 687; 1174 655 688; 1175 656 689; 1176 657 690; 1177 658 691;1178 659 692; 1179 660 693; 1180 666 668; 1181 667 669; 1182 668 669;1183 668 675; 1184 669 676; 1185 670 671; 1186 671 672; 1187 672 673;1188 673 674; 1189 675 676; 1190 670 677; 1191 678 671; 1192 672 679;1193 680 673; 1194 674 681; 1195 675 682; 1196 676 683; 1197 677 678;1198 678 679; 1199 679 680; 1200 680 681; 1201 682 683; 1202 677 694;1203 679 695; 1204 681 696; 1205 682 684; 1206 683 686; 1207 684 685;1208 685 686; 1209 686 687; 1210 687 688; 1211 688 689; 1212 689 690;1213 690 691; 1214 691 692; 1215 692 693; 1216 693 694; 1217 694 695;1218 695 696; 1219 694 697; 1220 695 698; 1221 696 699; 1222 688 700;1223 689 701; 1224 697 698; 1225 698 699; 1226 701 700; 1227 700 702;1228 701 703; 1229 684 707; 1230 685 708; 1231 687 710; 1232 690 713;1233 691 714; 1234 692 715; 1235 693 716; 1236 697 704; 1237 698 705;1238 699 706; 1239 703 702; 1240 704 705; 1241 705 706; 1242 702 711;1243 703 712; 1244 704 717; 1245 705 719; 1246 706 720; 1247 707 708;1248 708 709; 1249 709 710; 1250 710 711; 1251 711 712; 1252 712 713;1253 713 714; 1254 714 715; 1255 715 716; 1256 716 717; 1257 717 718;1258 718 719; 1259 719 720; 1260 707 721; 1261 709 722; 1262 717 723;1263 719 725; 1264 720 727; 1265 721 722; 1266 723 724; 1267 724 725;1268 725 726; 1269 726 727; 1270 727 728; 1271 723 729; 1272 730 724;1273 725 731; 1274 732 726; 1275 721 733; 1276 722 734; 1277 732 728;1278 729 730; 1279 730 731; 1280 731 732; 1281 733 734; 1282 733 735;1283 734 736; 1284 729 739; 1285 728 743; 1286 731 741; 1287 735 736;1288 716 753; 1289 710 757; 1290 711 758; 1291 712 759; 1292 713 760;1293 714 761; 1294 715 762; 1295 735 737; 1296 736 738; 1297 737 738;1298 739 740; 1299 740 741; 1300 741 742; 1301 742 743; 1302 737 744;1303 738 745; 1304 739 746; 1305 747 740; 1306 741 748; 1307 749 742;1308 743 750; 1309 744 745; 1310 746 747; 1311 747 748; 1312 748 749;1313 749 750; 1314 744 751; 1315 745 752; 1316 746 763; 1317 748 764;1318 750 765; 1319 751 752; 1320 751 754; 1321 752 755; 1322 762 753;1323 753 763; 1324 754 755; 1325 755 756; 1326 756 757; 1327 757 758;1328 758 759; 1329 759 760; 1330 760 761; 1331 761 762; 1332 763 764;1333 764 765; 1334 756 766; 1335 759 767; 1336 754 768; 1337 755 769;1338 766 767; 1339 763 770; 1340 764 771; 1341 765 772; 1342 768 769;1343 766 775; 1344 767 777; 1345 768 773; 1346 769 774; 1347 770 771;1348 771 772; 1349 773 774; 1350 753 786; 1351 762 785; 1352 775 776;1353 776 777; 1354 770 780; 1355 771 781; 1356 772 782; 1357 773 778;1358 774 779; 1359 778 779; 1360 780 781; 1361 781 782; 1362 760 799;1363 761 800; 1364 778 783; 1365 779 784; 1366 780 787; 1367 781 788;1368 782 789; 1369 784 783; 1370 785 786; 1371 786 787; 1372 787 788;1373 788 789; 1374 783 790; 1375 784 791; 1376 775 796; 1377 776 797;1378 777 798; 1379 790 791; 1380 790 792; 1381 791 793; 1382 785 801;1383 802 789; 1384 792 793; 1385 792 794; 1386 793 795; 1387 794 795;1388 795 796; 1389 796 797; 1390 797 798; 1391 798 799; 1392 799 800;1393 800 801; 1394 801 802; 1395 804 630; 1396 630 807; 1397 804 632;1398 638 804; 1399 807 638; 1400 632 811; 1401 811 638; 1402 652 813;1403 659 813; 1404 652 819; 1405 659 819; 1406 663 822; 1407 823 652;1408 684 813; 1409 832 663; 1410 696 822; 1411 684 823; 1412 692 823;1413 684 829; 1414 692 829; 1415 696 832; 1416 707 823; 1417 684 833;1418 720 832; 1419 696 842; 1420 707 833; 1421 715 833; 1422 707 839;1423 715 839; 1424 720 842; 1425 754 843; 1426 762 843; 1427 754 849;1428 762 849; 1429 765 852; 1430 794 853; 1431 853 801; 1432 859 794;1433 801 859; 1434 862 801; 1435 859 802; 1436 802 862; 1437 804 803;1438 805 804; 1439 806 805; 1440 807 806; 1441 803 810; 1442 809 808;1443 810 809; 1444 808 812; 1445 812 811; 1446 803 818; 1447 804 819;1448 805 820; 1449 806 821; 1450 822 807; 1451 808 815; 1452 809 816;1453 810 817; 1454 811 813; 1455 812 814; 1456 813 814; 1457 814 815;1458 815 816; 1459 816 817; 1460 817 818; 1461 818 819; 1462 819 820;1463 820 821; 1551 821 822; 1552 813 823; 1553 814 824; 1554 815 825;1555 816 826; 1556 817 827; 1557 818 828; 1558 819 829; 1559 820 830;1560 821 831; 1561 832 822; 1562 823 824; 1563 824 825; 1564 825 826;1565 826 827; 1566 827 828; 1567 828 829; 1568 829 830; 1569 830 831;1570 831 832; 1571 823 833; 1572 824 834; 1573 825 835; 1574 826 836;1575 827 837; 1576 828 838; 1577 829 839; 1578 830 840; 1579 831 841;1580 832 842; 1581 833 834; 1582 834 835; 1583 835 836; 1584 836 837;1585 837 838; 1586 838 839; 1587 839 840; 1588 840 841; 1589 841 842;1590 833 843; 1591 834 844; 1592 835 845; 1593 836 846; 1594 837 847;1595 838 848; 1596 839 849; 1597 840 850; 1598 841 851; 1599 842 852;1600 843 844; 1601 844 845; 1602 845 846; 1603 846 847; 1604 847 848;1605 848 849; 1606 849 850; 1607 850 851; 1608 851 852; 1609 843 853;1610 844 854; 1611 845 855; 1612 846 856; 1613 847 857; 1614 848 858;1615 849 859; 1616 850 860; 1617 851 861; 1618 852 862; 1619 853 854;1620 854 855; 1621 855 856; 1622 856 857; 1623 857 858; 1624 858 859;1625 860 859; 1626 861 860; 1627 862 861;ELEMENT INCIDENCES SHELL1464 811 804 819 813; 1465 813 823 829 819; 1466 804 807 822 819;1467 819 829 832 822; 1468 823 833 839 829; 1469 829 839 842 832;1470 833 843 849 839; 1471 839 849 852 842; 1472 843 853 859 849;1473 849 859 862 852;ELEMENT PROPERTY1466 THICKNESS 0.031251464 THICKNESS 0.031251465 THICKNESS 0.031251467 THICKNESS 0.031251468 THICKNESS 0.031251469 THICKNESS 0.031251470 THICKNESS 0.031251471 THICKNESS 0.031251472 THICKNESS 0.031251473 THICKNESS 0.03125DEFINE MATERIAL STARTISOTROPIC STEELE 29000POISSON 0.3DENSITY 0.000283ALPHA 6.5e-06DAMP 0.03TYPE STEELSTRENGTH FY 50 FU 65 RY 1 RT 1ISOTROPIC STEEL_ASTM_A992E 29000POISSON 0.3DENSITY 0.000283TYPE STEELSTRENGTH FY 50 FU 65 RY 1 RT 1ISOTROPIC STEEL_ASTM_A500_GRADE_B_RECTANGULAR_AND_SQUAREE 29000POISSON 0.3DENSITY 0.000283ISOTROPIC STEEL_50_KSIE 29000POISSON 0.3DENSITY 0.000283ALPHA 6.5e-06DAMP 0.03TYPE STEELSTRENGTH FY 50 FU 62 RY 1 RT 1G 11200ISOTROPIC STEEL_DECKE 29000POISSON 0.3DENSITY 0.000283ALPHA 6.5e-06DAMP 0.03G 11200TYPE STEELSTRENGTH FY 33 FU 45 RY 1 RT 1END DEFINE MATERIALMEMBER PROPERTY AMERICAN44 TO 50 81 TO 91 134 TO 143 172 TO 182 255 TO 264 323 TO 328 330 331 375 -376 TO 380 424 TO 433 672 TO 679 724 TO 731 1065 TO 1071 1116 TO 1122 1153 -1154 TO 1159 1207 TO 1214 1247 TO 1254 1324 TO 1331 1387 TO 1393 1437 1441 -1442 TO 1445 1456 TO 1461 1562 TO 1567 1581 TO 1586 1600 TO 1605 1619 TO 1623 -1624 TABLE ST W24X8443 92 TO 95 144 TO 147 183 TO 186 265 TO 268 329 374 434 TO 439 506 TO 511 -529 TO 532 628 TO 631 680 723 787 TO 790 859 TO 865 908 TO 914 1002 TO 1006 -1072 1115 1160 TO 1163 1215 TO 1218 1255 TO 1259 1322 1323 1332 1333 1394 -1462 1463 1551 1568 TO 1570 1587 TO 1589 1606 TO 1608 TABLE ST W24X5553 58 66 73 98 105 113 121 129 152 153 166 167 200 202 203 205 TO 207 221 -226 234 TO 236 242 245 TO 247 252 275 278 TO 281 289 295 299 TO 301 308 316 -317 TO 318 320 321 383 391 406 TO 408 410 421 450 TO 455 457 468 TO 473 475 -479 490 493 534 537 538 541 TO 547 549 550 553 557 TO 563 565 568 571 572 -574 587 601 TO 603 606 TO 608 612 634 637 645 648 657 664 669 734 743 758 -768 795 796 801 809 817 825 826 832 839 840 847 874 875 886 889 918 919 921 -932 933 936 939 949 954 956 971 973 974 977 978 982 985 986 1008 1018 1019 -1028 TO 1030 1034 1040 1048 TO 1051 1058 1060 1061 1125 1130 1142 1150 1166 -1172 1182 1185 TO 1189 1191 1193 1197 TO 1201 1224 TO 1226 1239 TO 1241 1265 -1266 TO 1269 1272 1274 1277 TO 1281 1287 1297 TO 1301 1305 1307 1309 TO 1313 -1319 1342 1347 TO 1349 1359 TO 1361 1369 1379 1384 TABLE ST W12X26116 TO 119 126 127 192 TO 198 211 TO 219 272 393 TO 395 581 TO 585 -593 TO 599 815 816 837 838 927 930 950 TO 953 963 TO 968 1015 1338 1352 1353 -1377 TABLE ST W12X40744 745 766 767 TABLE ST W12X5356 57 61 74 78 96 99 110 111 115 125 132 148 157 161 164 170 191 210 222 227 -231 232 243 248 253 269 276 282 286 287 290 297 306 309 314 315 319 381 387 -389 390 397 411 413 417 422 446 449 463 467 476 477 480 487 491 495 512 516 -520 539 540 554 556 566 573 578 580 590 592 609 611 613 632 635 638 642 643 -646 655 662 665 667 668 670 732 739 741 742 748 759 761 765 773 793 804 805 -811 813 822 827 834 835 841 848 868 876 877 882 884 887 896 915 920 923 924 -931 934 937 946 955 958 961 970 975 980 983 987 1009 1014 1020 1021 1027 -1031 1035 1042 1046 1052 1053 1057 1123 1126 1128 1129 1136 1143 1145 1149 -1151 1164 1167 1171 1178 1180 1183 1194 1195 1204 1205 1221 1229 1234 1238 -1246 1260 1264 1270 1275 1282 1285 1294 1295 1302 1308 1314 1318 1320 1336 -1341 1345 1351 1356 1357 1364 1368 1374 1380 1382 1383 1385 1438 TO 1440 -1447 1450 1454 1552 1558 1561 1571 1577 1580 1590 1596 1599 1609 1618 1625 -1626 TO 1627 TABLE ST W21X502 3 5 6 10 11 13 TO 16 19 20 22 TO 25 28 29 33 34 37 38 40 41 333 334 336 -337 341 342 344 TO 347 350 351 353 TO 356 359 360 364 365 368 369 371 372 -682 683 685 686 689 690 693 TO 696 698 699 702 TO 705 707 708 712 713 717 -718 720 721 1074 1075 1077 1078 1081 1082 1085 TO 1088 1090 1091 -1094 TO 1097 1099 1100 1104 1105 1109 1110 1112 1113 1395 1397 1399 1401 -1403 1404 1407 TO 1410 1412 1413 1416 TO 1419 1421 1422 1426 1427 1431 1432 -1434 1435 TABLE ST HSST6X6X0.375UNIT FEET KIPMEMBER PROPERTY AMERICAN67 TO 70 296 302 TO 305 402 TO 405 633 636 644 647 649 TO 654 656 658 TO 661 -663 666 671 750 TO 753 1043 TO 1045 1138 TO 1141 1335 1344 1370 TO 1373 -1378 TABLE ST W18X5051 52 54 55 59 60 62 TO 65 71 72 75 TO 77 79 80 97 100 TO 104 107 TO 109 112 -114 120 122 TO 124 128 130 131 133 149 TO 151 154 TO 156 158 TO 160 162 163 -165 168 169 171 187 TO 190 199 201 204 208 209 220 223 TO 225 228 TO 230 -233 237 TO 241 244 249 TO 251 254 270 271 273 274 277 283 TO 285 288 291 -292 TO 294 298 307 310 TO 313 382 384 TO 386 388 392 396 398 TO 401 409 412 -414 TO 416 418 TO 420 423 440 TO 445 447 448 456 458 TO 462 464 TO 466 474 -478 481 TO 486 488 489 492 494 513 TO 515 517 TO 519 533 535 536 548 551 -552 555 564 567 569 570 575 TO 577 579 586 588 589 591 600 604 605 610 614 -639 TO 641 733 735 TO 738 740 746 747 749 754 TO 757 760 762 TO 764 -769 TO 772 774 791 792 794 797 TO 800 802 803 806 TO 808 810 812 814 818 -819 TO 821 823 824 828 TO 831 833 836 842 TO 846 849 866 867 869 TO 873 878 -879 TO 881 883 885 888 890 TO 895 916 917 922 925 926 928 929 935 938 940 -941 TO 945 947 948 957 959 960 962 969 972 976 979 981 984 988 1007 -1010 TO 1013 1016 1017 1022 TO 1026 1032 1033 1036 TO 1039 1041 1047 1124 -1127 1131 TO 1135 1137 1144 1146 TO 1148 1152 1165 1168 TO 1170 -1173 TABLE ST W16X401174 TO 1177 1179 1181 1184 1190 1192 1196 1202 1203 1206 1219 1220 1222 1223 -1227 1228 1230 TO 1233 1235 TO 1237 1242 TO 1245 1261 TO 1263 1271 1273 1276 -1283 1284 1286 1288 TO 1293 1296 1303 1304 1306 1315 TO 1317 1321 1334 1337 -1339 1340 1343 1346 1350 1354 1355 1358 1362 1363 1365 TO 1367 1375 1376 -1381 TABLE ST W16X401613 1614 TABLE ST W16X40322 1054 TO 1056 1059 1062 TO 1064 1386 TABLE ST W16X40496 TO 505 521 TO 528 775 TO 786 TABLE ST W30X148615 TO 627 850 TO 858 897 TO 907 989 TO 1001 TABLE ST W27X102106 TABLE ST W21X681 4 7 TO 9 12 17 18 21 26 27 30 TO 32 35 36 39 42 332 335 338 TO 340 343 348 -349 352 357 358 361 TO 363 366 367 370 373 681 684 687 688 691 692 697 700 -701 706 709 TO 711 714 TO 716 719 722 1073 1076 1079 1080 1083 1084 1089 -1092 1093 1098 1101 TO 1103 1106 TO 1108 1111 1114 1396 1398 1400 1402 1405 -1406 1411 1414 1415 1420 1423 TO 1425 1428 TO 1430 1433 -1436 TABLE ST W18X971446 1448 1449 1451 TO 1453 1455 1553 TO 1557 1559 1560 1572 TO 1576 1578 -1579 1591 TO 1595 1597 1598 1610 TO 1612 1615 TO 1617 TABLE ST W16X26UNIT INCHES KIPCONSTANTSBETA 270 MEMB 1 4 8 12 17 21 26 30 31 35 36 42 332 335 339 343 348 352 357 -361 362 366 367 373 681 684 688 692 697 701 706 710 711 715 716 722 1073 -1076 1080 1084 1089 1093 1098 1102 1103 1107 1108 1114 1396 1400 1402 1406 -1411 1415 1420 1424 1425 1429 1430 1436MATERIAL STEEL_50_KSI MEMB 2 3 5 6 10 11 13 TO 16 19 20 22 TO 25 28 29 33 -34 37 38 40 41 333 334 336 337 341 342 344 TO 347 350 351 353 TO 356 359 -360 364 365 368 369 371 372 682 683 685 686 689 690 693 TO 696 698 699 702 -703 TO 705 707 708 712 713 717 718 720 721 1074 1075 1077 1078 1081 1082 1085 -1086 TO 1088 1090 1091 1094 TO 1097 1099 1100 1104 1105 1109 1110 1112 1113 -1395 1397 1399 1401 1403 1404 1407 TO 1410 1412 1413 1416 TO 1419 1421 1422 -1426 1427 1431 1432 1434 1435MATERIAL STEEL_ASTM_A992 MEMB 43 TO 105 107 TO 331 374 TO 495 506 TO 520 529 -530 TO 680 723 TO 774 787 TO 1072 1115 TO 1394 1437 TO 1463 1551 TO 1627MATERIAL STEEL_DECK MEMB 1464 TO 1473MATERIAL STEEL MEMB 1 4 7 TO 9 12 17 18 21 26 27 30 TO 32 35 36 39 42 106 -332 335 338 TO 340 343 348 349 352 357 358 361 TO 363 366 367 370 373 496 -497 TO 505 521 TO 528 681 684 687 688 691 692 697 700 701 706 709 TO 711 714 -715 TO 716 719 722 775 TO 786 1073 1076 1079 1080 1083 1084 1089 1092 1093 -1098 1101 TO 1103 1106 TO 1108 1111 1114 1396 1398 1400 1402 1405 1406 1411 -1414 1415 1420 1423 TO 1425 1428 TO 1430 1433 1436MEMBER OFFSET1263 START 0 0 01263 END 0 0 01273 START 0 0 01273 END 0 0 01286 START 0 0 01286 END 0 0 01306 START 0 0 01306 END 0 0 01317 START 0 0 0875 END 0 0 0919 START 0 0 0949 START 0 0 0954 START 0 0 0406 START 0 0 0461 END 0 0 0485 START 0 0 0513 START 0 0 0514 END 0 0 052 END 0 0 055 START 0 0 055 END 0 0 060 START 0 0 060 END 0 0 072 START 0 0 072 END 0 0 080 START 0 0 080 END 0 0 0206 END 0 0 0271 END 0 0 0292 START 0 0 0292 END 0 0 0311 START 0 0 0273 END 0 0 0293 START 0 0 0293 END 0 0 0312 START 0 0 01298 END 0 0 01299 START 0 0 0MEMBER RELEASE43 44 51 52 62 TO 66 70 73 75 TO 77 81 92 97 101 102 107 TO 109 116 126 136 -144 158 TO 160 172 183 206 221 228 TO 230 254 257 270 275 281 283 TO 285 -289 295 375 382 TO 386 391 393 TO 396 406 TO 408 410 414 TO 416 421 423 425 -434 441 TO 445 447 448 450 TO 455 457 468 TO 473 475 479 490 493 496 506 -513 TO 515 517 TO 519 521 529 533 TO 538 541 544 549 550 553 557 560 565 -568 571 572 574 TO 577 581 583 587 593 596 601 TO 603 606 TO 608 612 615 -628 633 634 637 639 TO 641 645 648 TO 654 724 732 TO 734 742 TO 747 758 762 -763 TO 764 766 TO 772 779 787 791 792 794 TO 796 799 TO 803 809 810 812 815 -816 TO 818 825 826 832 837 TO 840 847 850 859 866 868 874 875 878 TO 881 883 -886 889 895 897 908 916 TO 921 926 TO 933 936 939 940 945 949 950 952 954 -956 963 966 971 973 974 977 978 982 985 986 989 1002 1007 TO 1010 1015 1016 -1018 1019 1021 TO 1025 1029 1030 1032 1124 1125 1130 TO 1135 1142 -1146 TO 1148 1150 1165 1166 1169 1170 1172 TO 1177 1179 1182 1185 1187 1189 -1191 1193 1197 1199 1201 1207 1215 1219 1220 1222 TO 1226 1230 TO 1233 1235 -1239 TO 1241 1247 1255 1261 TO 1263 1265 1266 1268 1272 1274 1278 1280 1281 -1287 TO 1293 1297 START MY MZ1300 1305 1307 1309 1310 1312 1319 1322 1324 1334 1335 1337 TO 1340 1342 -1349 TO 1352 1359 1360 1362 1437 1440 1447 1456 1462 1562 1568 1581 1587 -1600 1606 START MY MZ1446 1448 1449 1451 TO 1453 1455 1553 TO 1557 1559 1560 1572 TO 1576 1578 -1579 1591 TO 1595 1597 1598 1610 TO 1614 1616 1617 START MY MZ299 305 308 316 323 329 657 664 669 1034 1037 1040 1049 TO 1051 1058 1060 -1061 1065 1072 1363 1369 1370 1377 1379 1383 1384 1387 1615 1618 1619 -1627 START MY MZ374 402 658 668 680 723 750 1053 1115 1394 START MY MZ104 149 152 167 200 226 236 247 252 START MY MZ53 57 58 61 96 98 103 105 110 113 118 121 127 129 148 150 151 153 TO 156 161 -166 191 192 195 202 203 205 207 211 216 224 227 231 234 237 TO 239 242 245 -251 269 271 TO 274 278 280 282 286 296 300 301 320 321 381 390 449 476 512 -520 539 540 578 632 638 642 793 804 877 915 1014 1118 1123 1129 1138 1153 -1160 1164 1171 1221 1229 1260 1264 1294 1298 1336 1341 1347 1450 1454 1552 -1561 1571 1580 1590 1596 1599 1609 START MY MZ43 50 56 62 TO 67 73 75 TO 80 91 95 101 107 TO 109 117 126 130 133 143 147 -158 TO 160 182 186 206 228 TO 230 264 268 283 TO 285 295 299 302 374 380 -383 389 391 393 TO 396 405 TO 408 410 414 TO 416 418 TO 421 433 439 440 450 -451 TO 455 457 468 TO 473 475 479 482 TO 486 488 TO 490 493 494 505 511 513 -514 TO 515 517 TO 519 532 534 537 538 543 547 549 550 553 559 563 565 568 -571 572 574 TO 577 582 585 587 595 599 601 TO 608 612 614 627 631 634 637 -639 TO 641 645 648 TO 654 657 723 731 734 TO 738 741 743 TO 747 753 758 762 -763 TO 764 766 TO 768 774 786 790 795 796 801 803 809 810 812 815 TO 817 821 -825 826 832 837 TO 840 842 TO 847 849 858 865 867 872 874 875 878 TO 881 -883 886 889 893 TO 896 907 914 918 919 921 927 930 932 933 936 939 TO 941 -949 951 953 954 956 965 968 971 TO 974 976 TO 979 982 TO 986 988 1001 1006 -1008 1013 1015 1018 1019 1022 1028 1030 1032 1034 1039 TO 1041 1043 1045 -1115 1122 1125 1130 TO 1135 1141 1142 1146 TO 1148 1150 1152 1159 1163 1166 -1172 TO 1177 1179 1182 1186 1188 1189 1191 1193 1198 1200 TO 1203 1206 1214 -1218 1224 TO 1226 1230 TO 1233 1235 1239 TO 1245 1254 1259 1265 1267 1269 -1272 1274 1277 1279 END MY MZ1281 1287 TO 1293 1297 1301 1305 1307 1309 1311 1313 1316 1317 1319 1321 -1331 1333 1338 1342 1348 TO 1350 1353 1359 1361 TO 1363 1366 1367 1369 1373 -1446 1450 1561 1618 END MY MZ1448 1449 1451 TO 1453 1455 1553 TO 1557 1559 1560 1572 TO 1576 1578 1579 -1591 TO 1595 1597 1598 1610 TO 1614 1616 1617 END MY MZ528 END MY MZ308 315 322 328 329 661 664 669 671 679 680 1048 1052 1058 1059 1062 TO 1064 -1071 1072 1376 TO 1379 1382 1384 1386 1393 END MY MZ1128 1438 1445 1447 1461 1551 1567 1570 1586 1589 1605 1608 1615 1624 -1625 END MY MZ53 58 61 74 98 103 105 110 113 119 121 127 129 131 132 152 TO 156 161 166 -167 TO 171 187 TO 190 194 198 200 202 203 205 207 215 219 221 226 227 231 -235 236 238 242 246 247 250 252 253 272 275 279 TO 281 289 296 300 301 311 -312 TO 314 318 TO 321 413 417 422 476 495 512 520 578 609 613 667 670 761 -765 773 841 848 877 975 987 1057 1145 1149 1151 1204 1205 1229 1246 1294 -1299 1318 1320 1385 1454 1552 1571 1580 1590 1596 1599 1609 END MY MZ1394 END MY MZSUPPORTS1 TO 18 PINNEDUNIT FEET KIPMEMBER TENSION 2 3 5 6 10 11 13 TO 16 19 20 22 TO 25 28 29 33 34 37 38 40 41 333 334 336 -337 341 342 344 TO 347 350 351 353 TO 356 359 360 364 365 368 369 371 372 -682 683 685 686 689 690 693 TO 696 698 699 702 TO 705 707 708 712 713 717 -718 720 721 1074 1075 1077 1078 1081 1082 1085 TO 1088 1090 1091 -1094 TO 1097 1099 1100 1104 1105 1109 1110 1112 1113 1395 1397 1399 1401 -1403 1404 1407 TO 1410 1412 1413 1416 TO 1419 1421 1422 1426 1427 1431 1432 -1434 1435UNIT INCHES KIPELEMENT PLANE STRESS1464 TO 1473LOAD 1 LOADTYPE Dead TITLE DEAD LOADSELFWEIGHT Y -1 UNIT FEET KIPMEMBER LOAD1289 TO 1292 CON GY -0.36JOINT LOAD736 FY -0.36671 673 678 680 724 726 730 732 740 742 747 749 FY -0.53MEMBER LOAD1224 1225 1240 1241 1347 1348 1360 1361 CON GY -0.53 1.251338 1352 1353 CON GY -2.2 2.51338 CON GY -2.2 7.5825 847 918 936 949 985 1018 1034 CON GY -2.9 2.5826 840 919 933 954 982 1019 1030 CON GY -2.9 3874 875 886 889 CON GY -1.5 1.51016 1023 TO 1025 1032 CON GY -0.45 61058 1059 CON GY -0.4 1.6671050 1051 1060 1061 CON GY -0.41058 1059 CON GY -0.4973 974 977 978 UNI GY -0.6585 595 599 950 952 963 965 966 968 CON GY -1.8 0.5951 CON GY -1.8 2.5953 CON GY -1.8 1.25926 TO 929 CON GY -0.4 4.25924 925 CON GY -0.4 1JOINT LOAD458 476 FY -0.8MEMBER LOAD815 816 837 838 CON GY -0.8816 837 CON GY -0.8 0.75JOINT LOAD451 455 FY -0.17MEMBER LOAD795 801 CON GY -0.17 1805 CON GY -0.4 0.667806 CON GY -0.644 0.667797 798 CON GY -0.65 1.41667799 800 803 CON GY -0.72 5.5802 804 810 TO 812 CON GY -0.465 5.5744 745 766 767 CON GY -3.65 1.25649 TO 654 CON GY -2.1 20649 TO 654 CON GY -2.1 5.5JOINT LOAD378 380 FY -0.21MEMBER LOAD656 CON GY -0.21 1.25649 TO 654 CON GY -0.4649 TO 652 CON GY -0.4 11.25649 TO 654 CON GY -0.4 8.667603 607 608 UNI GY -0.6581 583 593 596 CON GY -1.8 3582 CON GY -1.8 4541 544 557 560 CON GY -1 0.667541 544 557 560 CON GY -1 3.5JOINT LOAD311 315 322 326 FY -1MEMBER LOAD581 TO 585 593 TO 599 UNI GY -0.053496 521 523 CON GY -67.5 4.75499 CON GY -67.5 2.25513 TO 519 CON GY -0.28 1.5474 482 TO 489 CON GY -0.68 0.667466 CON GY -1.05 0.75458 TO 465 CON GY -1.086 2.25476 CON GY -0.6 5.667JOINT LOAD251 TO 256 258 259 262 TO 267 269 270 FY -1.05MEMBER LOAD454 472 CON GY -1.05 2.5453 471 CON GY -1.05 1.75394 406 CON GY -0.4 0.5394 406 CON GY -0.4 4.5394 CON GY -0.4 2.25393 395 CON GY -0.4 1.667395 CON GY -0.4 4407 CON GY -0.4 2.334408 CON GY -0.4 1.1667JOINT LOAD169 172 181 183 FY -0.75MEMBER LOAD300 CON GY -0.75 3.1667280 301 CON GY -0.75 1.8334279 CON GY -0.75 1292 TO 294 CON GY -0.57 0.334292 TO 294 CON GY -0.57 1.75292 TO 294 CON GY -0.57 7311 TO 313 CON GY -0.57 1277 CON GY -0.234 2.25288 CON GY -0.234 1.1667298 CON GY -0.234 1.334307 CON GY -0.234 1.5229 230 CON GY -0.23 16.0833JOINT LOAD140 142 145 146 FY -0.45114 TO 116 119 TO 121 126 127 129 131 132 134 FY -1MEMBER LOAD201 TO 208 CON GY -0.354 1.8334209 CON GY -0.354 1153 166 CON GY -0.275 1153 166 CON GY -0.275 3.75150 151 CON GY -0.65 2.8334116 126 CON GY -0.575 2.25126 CON GY -0.575 7.5118 127 CON GY -0.575 3.25127 CON GY -0.575 8.334126 127 UNI GY -0.125JOINT LOAD33 40 FY -0.4528 30 FY -0.28MEMBER LOAD66 73 CON GY -0.45 1.2553 58 CON GY -0.28 2.667ONEWAY LOADYRANGE 16 17.5 ONE -0.015 GYYRANGE 38 40 ONE -0.015 GYYRANGE 58 60 ONE -0.015 GYYRANGE 73 76 ONE -0.015 GYYRANGE 95 99 ONE -0.015 GY TOWARDS 1446JOINT LOAD450 451 454 455 FY -3.25UNIT INCHES KIPMEMBER LOAD117 119 CON GY -0.575 36UNIT FEET KIP602 UNI GY -0.6UNIT INCHES KIPLOAD 2 LOADTYPE Live TITLE FLOOR LIVEUNIT FEET KIPONEWAY LOADYRANGE 16 17.5 ONE -0.125 GYYRANGE 38 40 ONE -0.125 GYYRANGE 59 60 ONE -0.125 GYYRANGE 74 76 ONE -0.125 GYMEMBER LOAD394 CON GY -0.74 2.25406 CON GY -0.95 0.5406 CON GY -0.95 4.5395 CON GY -0.74 4407 CON GY -0.95 2.334408 CON GY -0.95 1.1667815 816 837 838 CON GY -2.1 3816 837 CON GY -2.1 0.75JOINT LOAD458 476 FY -2.1458 476 FX 2.2MEMBER LOAD816 837 CON GX 2.2 0.75815 816 837 838 CON GX 2.2 3744 745 766 767 CON GY -11.13 1.25744 745 766 767 CON GX 0.15 1.251338 1352 1353 CON GY -3.15 2.51338 CON GY -3.15 7.5LOAD 3 LOADTYPE Roof Live TITLE ROOF LIVE LOADONEWAY LOADYRANGE 95 99 ONE -0.02 GY TOWARDS 1446LOAD 4 LOADTYPE Wind TITLE WIND LOAD +XJOINT LOAD2 807 FX 4.63 19 205 402 630 FX 71 FX 2.4804 807 FX 11.7638 FX 19.927 411 FX 18.8212 FX 20.4811 FX 7.7206 632 FX 13.520 403 FX 12.4LOAD 5 LOADTYPE Wind TITLE WIND LOAD -XJOINT LOAD16 862 FX -4.6859 FX -11.7853 FX -7.7392 794 FX -13.5801 FX -19.917 203 401 629 802 FX -7195 621 FX -12.4202 628 FX -18.8400 FX -20.418 FX -2.4LOAD 6 LOADTYPE Wind TITLE WIND LOAD +ZJOINT LOAD16 811 FZ 4.6813 833 FZ 11.4195 621 823 FZ 12843 FZ 13.3853 FZ 7.813 206 632 FZ 8236 652 FZ 19.7280 684 FZ 20.676 296 481 707 FZ 19.1355 754 FZ 23.1392 794 FZ 137 20 403 FZ 7.341 435 FZ 18.198 512 FZ 17.6153 571 FZ 21.32 FZ 2.84 10 FZ 6.8LOAD 7 LOADTYPE Wind TITLE WIND LOAD -ZJOINT LOAD18 807 FZ -4.6822 842 FZ -11.4203 629 832 FZ -12852 FZ -13.3862 FZ -7.815 205 630 FZ -8250 663 FZ -19.7295 696 FZ -20.689 308 497 720 FZ -19.1372 765 FZ -23.1401 802 FZ -139 19 402 FZ -7.356 449 FZ -18.1113 530 FZ -17.6166 589 FZ -21.31 FZ -2.86 12 FZ -6.8LOAD 8 LOADTYPE Wind TITLE WIND UPLIFTMEMBER LOAD1446 1451 TO 1453 1455 1553 TO 1557 1572 TO 1576 1591 TO 1595 1610 TO 1613 -1614 UNI GY 0.2651447 TO 1449 1558 TO 1560 1577 TO 1579 1596 TO 1598 1615 TO 1617 UNI GY 0.2741450 1454 1552 1561 1571 1580 1590 1599 1609 1618 UNI GY 0.137LOAD COMB 9 DEAD1 1.0 LOAD COMB 10 DEAD + LIVE1 1.0 2 1.0 LOAD COMB 11 DEAD + LIVE ROOF1 1.0 3 1.0 LOAD COMB 12 DEAD + LIVE + LIVE ROOF1 1.0 2 0.75 3 0.75 LOAD COMB 13 DEAD + WIND (+X)1 0.6 4 0.6 8 0.6 LOAD COMB 14 DEAD + WIND(-X)1 0.6 5 0.6 8 0.6 LOAD COMB 15 DEAD + WIND (+Z)1 0.6 6 0.6 8 0.6 LOAD COMB 16 DEAD + WIND (-Z)1 0.6 7 0.6 8 0.6 LOAD COMB 17 DEAD + WIND(+X) + LIVE +LIVE ROOF1 1.0 2 0.75 3 0.75 4 0.45 8 0.45 LOAD COMB 18 DEAD + WIND (-X) + LIVE + LIVE ROOF1 1.0 2 0.75 3 0.75 5 0.45 8 0.45 LOAD COMB 19 DEAD + WIND(+Z) + LIVE + LIVE ROOF1 1.0 2 0.75 3 0.75 6 0.45 8 0.45 LOAD COMB 20 DEAD + WIND(-Z) + LIVE + LIVE ROOF1 1.0 2 0.75 3 0.75 7 0.45 8 0.45 LOAD COMB 21 D + 0.5L + 0.5 LR1 1.0 2 0.5 3 0.5 LOAD COMB 22 D+L+LR (DEFLECTION)1 1.0 2 1.0 3 1.0 LOAD COMB 23 DEAD LOAD (DEFLECTION)1 1.0 LOAD COMB 24 0.6D+0.6W (DEFLECTION)1 0.6 8 0.6 PERFORM ANALYSIS PRINT STATICS CHECKDEFINE ENVELOPE9 TO 21 ENVELOPE 1 TYPE STRENGTH22 TO 24 ENVELOPE 2 TYPE SERVICEABILITYEND DEFINE ENVELOPELOAD LIST ENV 1PARAMETER 1CODE AISC UNIFIED 2016METHOD ASDSGR 28 MEMB 1 4 7 TO 9 12 17 18 21 26 27 30 TO 32 35 36 39 42 TO 332 335 338 -339 TO 340 343 348 349 352 357 358 361 TO 363 366 367 370 373 TO 527 -529 TO 681 684 687 688 691 692 697 700 701 706 709 TO 711 714 TO 716 719 -722 TO 1073 1076 1079 1080 1083 1084 1089 1092 1093 1098 1101 TO 1103 1106 -1107 TO 1108 1111 1114 TO 1394 1396 1398 1400 1402 1405 1406 1411 1414 1415 -1420 1423 TO 1425 1428 TO 1430 1433 1436 TO 1463 1551 TO 1577 1579 TO 1627SGR 5 MEMB 2 3 5 6 10 11 13 TO 16 19 20 22 TO 25 28 29 33 34 37 38 40 41 333 -334 336 337 341 342 344 TO 347 350 351 353 TO 356 359 360 364 365 368 369 -371 372 682 683 685 686 689 690 693 TO 696 698 699 702 TO 705 707 708 712 -713 717 718 720 721 1074 1075 1077 1078 1081 1082 1085 TO 1088 1090 1091 -1094 TO 1097 1099 1100 1104 1105 1109 1110 1112 1113 1395 1397 1399 1401 -1403 1404 1407 TO 1410 1412 1413 1416 TO 1419 1421 1422 1426 1427 1431 1432 -1434 1435UNB 4 MEMB 1446 TO 1455 1552 TO 1561 1571 TO 1580 1590 TO 1599 1609 TO 1618UNT 4 MEMB 1446 TO 1455 1552 TO 1561 1571 TO 1580 1590 TO 1599 1609 TO 1618MAIN 1 MEMB 2 3 5 6 10 11 13 TO 16 19 20 22 TO 25 28 29 33 34 37 38 40 41 -43 TO 331 333 334 336 337 341 342 344 TO 347 350 351 353 TO 356 359 360 364 -365 368 369 371 372 374 TO 527 529 TO 680 682 683 685 686 689 690 -693 TO 696 698 699 702 TO 705 707 708 712 713 717 718 720 721 723 TO 1072 -1074 1075 1077 1078 1081 1082 1085 TO 1088 1090 1091 1094 TO 1097 1099 1100 -1104 1105 1109 1110 1112 1113 1115 TO 1395 1397 1399 1401 1403 1404 1407 -1408 TO 1410 1412 1413 1416 TO 1419 1421 1422 1426 1427 1431 1432 1434 1435 -1437 TO 1463 1551 TO 1627TMAIN 1 MEMB 2 3 5 6 10 11 13 TO 16 19 20 22 TO 25 28 29 33 34 37 38 40 41 -43 TO 331 333 334 336 337 341 342 344 TO 347 350 351 353 TO 356 359 360 364 -365 368 369 371 372 374 TO 527 529 TO 680 682 683 685 686 689 690 -693 TO 696 698 699 702 TO 705 707 708 712 713 717 718 720 721 723 TO 1072 -1074 1075 1077 1078 1081 1082 1085 TO 1088 1090 1091 1094 TO 1097 1099 1100 -1104 1105 1109 1110 1112 1113 1115 TO 1395 1397 1399 1401 1403 1404 1407 -1408 TO 1410 1412 1413 1416 TO 1419 1421 1422 1426 1427 1431 1432 1434 1435 -1437 TO 1463 1551 TO 1627RATIO 0.8 MEMB 1 4 7 TO 9 12 17 18 21 26 27 30 TO 32 35 36 39 42 332 335 338 -339 TO 340 343 348 349 352 357 358 361 TO 363 366 367 370 373 681 684 687 -688 691 692 697 700 701 706 709 TO 711 714 TO 716 719 722 1073 1076 1079 -1080 1083 1084 1089 1092 1093 1098 1101 TO 1103 1106 TO 1108 1111 1114 1396 -1398 1400 1402 1405 1406 1411 1414 1415 1420 1423 TO 1425 1428 TO 1430 1433 -1436RATIO 0.85 MEMB 2 3 5 6 10 11 13 TO 16 19 20 22 TO 25 28 29 33 34 37 38 40 -41 43 TO 331 333 334 336 337 341 342 344 TO 347 350 351 353 TO 356 359 360 -364 365 368 369 371 372 374 TO 680 682 683 685 686 689 690 693 TO 696 698 -699 702 TO 705 707 708 712 713 717 718 720 721 723 TO 1072 1074 1075 1077 -1078 1081 1082 1085 TO 1088 1090 1091 1094 TO 1097 1099 1100 1104 1105 1109 -1110 1112 1113 1115 TO 1395 1397 1399 1401 1403 1404 1407 TO 1410 1412 1413 -1416 TO 1419 1421 1422 1426 1427 1431 1432 1434 1435 1437 TO 1463 -1551 TO 1627CHECK CODE ALLLOAD LIST ENV 2PARAMETER 2CODE AISC UNIFIED 2016METHOD ASDDFF 240 ALLDJ1 632 MEMB 1116 TO 1123 1126 1136 1143 1151DJ1 633 MEMB 1124 1127 1137 1144 1152DJ1 638 MEMB 1129 1145DJ1 630 MEMB 1128 1149DJ2 652 MEMB 1123 1126 1136 1143 1151DJ2 653 MEMB 1124 1127 1137 1144 1152DJ2 659 MEMB 1129 1145 1153 TO 1159DJ2 663 MEMB 1128 1149 1160 TO 1163DJ2 638 MEMB 1116 TO 1122DJ1 659 MEMB 1160 TO 1163DJ1 652 MEMB 1153 TO 1159 1164 1167 1180 1183 1195 1205DJ1 653 MEMB 1165 1168 1181 1184 1196 1206DJ1 661 MEMB 1169 1190 1202DJ1 662 MEMB 1170 1192 1203DJ1 663 MEMB 1171 1194 1204DJ1 684 MEMB 1207 TO 1214DJ1 692 MEMB 1215 TO 1218DJ1 688 MEMB 1222 1227 1242DJ1 689 MEMB 1223 1228 1243DJ1 694 MEMB 1219 1236 1244DJ1 695 MEMB 1220 1237 1245DJ1 696 MEMB 1221 1238 1246DJ1 707 MEMB 1247 TO 1254 1260 1275 1282 1295 1302 1314 1320DJ1 715 MEMB 1255 TO 1259DJ2 684 MEMB 1164 1167 1180 1183 1195 1205DJ2 686 MEMB 1165 1168 1181 1184 1196 1206DJ2 694 MEMB 1169 1190 1202DJ2 695 MEMB 1170 1192 1203DJ2 696 MEMB 1171 1194 1204DJ2 692 MEMB 1207 TO 1214DJ2 696 MEMB 1215 TO 1218DJ2 711 MEMB 1222 1227 1242DJ2 712 MEMB 1223 1228 1243DJ2 715 MEMB 1247 TO 1254DJ2 717 MEMB 1219 1236 1244DJ2 720 MEMB 1221 1238 1246DJ2 719 MEMB 1220 1237 1245DJ1 709 MEMB 1261 1276 1283 1296 1303 1315 1321DJ1 717 MEMB 1262 1271 1284 1304 1316DJ1 719 MEMB 1263 1273 1286 1306 1317DJ1 720 MEMB 1264 1270 1285 1308 1318DJ1 754 MEMB 1324 TO 1331 1336 1345 1357 1364 1374 1380 1385DJ1 755 MEMB 1337 1346 1358 1365 1375 1381 1386DJ1 756 MEMB 1334 1343 1376DJ1 759 MEMB 1335 1344 1378DJ1 775 MEMB 1352 1353DJ1 762 MEMB 1351 1382DJ1 763 MEMB 1339 1354 1366DJ1 764 MEMB 1340 1355 1367DJ1 765 MEMB 1341 1356 1368 1383DJ1 785 MEMB 1370 TO 1373DJ1 794 MEMB 1387 TO 1393DJ2 754 MEMB 1260 1275 1282 1295 1302 1314 1320DJ2 755 MEMB 1261 1276 1283 1296 1303 1315 1321DJ2 762 MEMB 1324 TO 1331DJ2 765 MEMB 1264 1270 1285 1308 1318 1322 1323 1332 1333DJ2 764 MEMB 1263 1273 1286 1306 1317DJ2 763 MEMB 1262 1271 1284 1304 1316DJ2 794 MEMB 1336 1345 1357 1364 1374 1380 1385DJ2 795 MEMB 1337 1346 1358 1365 1375 1381 1386DJ2 796 MEMB 1334 1343 1376DJ2 798 MEMB 1335 1344 1378DJ2 777 MEMB 1352 1353DJ2 801 MEMB 1387 TO 1393DJ2 789 MEMB 1370 TO 1373DJ2 788 MEMB 1340 1355 1367DJ2 787 MEMB 1339 1354 1366DJ2 802 MEMB 1341 1356 1368 1383DJ1 403 MEMB 724 TO 732 739 748 759 773DJ1 404 MEMB 733 740 749 760 774DJ1 405 MEMB 735 754 769DJ1 406 MEMB 736 755 770DJ1 407 MEMB 737 756 771DJ1 408 MEMB 738 757 772DJ1 411 MEMB 742 761DJ1 402 MEMB 741 765DJ1 420 MEMB 750 TO 753DJ2 435 MEMB 732 739 748 759 773DJ2 436 MEMB 733 740 749 760 774DJ2 437 MEMB 735 754 769DJ2 438 MEMB 736 755 770DJ2 440 MEMB 737 756 771DJ2 442 MEMB 738 757 772DJ2 445 MEMB 742 761 775 TO 786DJ2 449 MEMB 741 765 787 TO 790DJ1 435 MEMB 775 TO 786 793 805 813 822 835 848DJ1 445 MEMB 787 TO 790DJ2 424 MEMB 750 TO 753DJ1 436 MEMB 794 806 814 823 836 849DJ1 433 MEMB 791 797 807 830 844DJ1 439 MEMB 792 798 808 831 845DJ1 441 MEMB 799 828 842DJ1 443 MEMB 800 829 843DJ1 447 MEMB 802 824 833 846DJ1 449 MEMB 804 827 834 841DJ1 464 MEMB 818 TO 821DJ1 481 MEMB 850 TO 858DJ1 490 MEMB 859 TO 865DJ2 481 MEMB 793 805 813 822 835 848DJ2 483 MEMB 794 806 814 823 836 849DJ2 484 MEMB 791 797 807 830 844DJ2 485 MEMB 792 798 808 831 845DJ2 486 MEMB 799 828 842DJ2 488 MEMB 800 829 843DJ2 492 MEMB 802 824 833 846DJ2 490 MEMB 850 TO 859DJ2 497 MEMB 804 827 834 841 859 TO 865DJ2 468 MEMB 818 TO 821DJ1 493 MEMB 866 873 885 888 894DJ1 497 MEMB 868 876 884 887 896DJ1 498 MEMB 869 TO 872DJ1 507 MEMB 890 TO 893DJ1 512 MEMB 897 TO 907 915 924 937 946 961 980 987DJ1 523 MEMB 908 TO 914DJ2 523 MEMB 897 TO 907DJ2 502 MEMB 869 TO 872DJ2 511 MEMB 890 TO 893DJ2 526 MEMB 866 873 885 888 894DJ2 530 MEMB 868 876 884 887 896 908 TO 914DJ1 514 MEMB 916 925 938 947 962 981 988DJ1 515 MEMB 926 959 976DJ1 517 MEMB 928 960 979DJ1 519 MEMB 929 957 972DJ1 523 MEMB 931 958 975DJ1 525 MEMB 917 922 935 948 969 984DJ1 530 MEMB 920 923 934 955 970 983DJ1 541 MEMB 941 TO 945DJ1 547 MEMB 950 951DJ1 550 MEMB 952 953DJ1 561 MEMB 966 TO 968DJ1 557 MEMB 963 TO 965DJ1 571 MEMB 989 TO 1001 1014 1035 1046 1057DJ1 584 MEMB 1002 TO 1006DJ2 571 MEMB 915 924 937 946 961 980 987DJ2 573 MEMB 916 925 938 947 962 981 988DJ2 575 MEMB 926 959 976DJ2 578 MEMB 928 960 979DJ2 580 MEMB 929 957 972DJ2 584 MEMB 931 958 975DJ2 586 MEMB 917 922 935 948 969 984DJ2 589 MEMB 920 923 934 955 970 983 1002 TO 1006DJ2 546 MEMB 941 TO 945DJ2 552 MEMB 952 953DJ2 560 MEMB 963 TO 965DJ2 549 MEMB 950 951DJ2 564 MEMB 966 TO 968DJ1 574 MEMB 1016 1036 1047 1059DJ1 579 MEMB 1023 1054 1062DJ1 580 MEMB 1024 1055 1063DJ1 582 MEMB 1025 1056 1064DJ1 584 MEMB 1002 TO 1006 1021 1052DJ1 586 MEMB 1007 1017 1026 1033 1041DJ1 589 MEMB 1009 1020 1027 1031 1042 1053DJ1 599 MEMB 1028 1029DJ1 612 MEMB 1048 1049DJ1 615 MEMB 1050 1051DJ1 618 MEMB 1060 1061DJ1 608 MEMB 1043 TO 1045DJ1 602 MEMB 1037 TO 1039DJ1 590 MEMB 1010 TO 1013DJ1 621 MEMB 1065 TO 1071DJ1 628 MEMB 1072DJ2 621 MEMB 1014 1035 1046 1057DJ2 623 MEMB 1016 1036 1047 1059DJ2 625 MEMB 1023 1054 1062DJ2 626 MEMB 1024 1055 1063DJ2 627 MEMB 1025 1056 1064DJ2 628 MEMB 1021 1052 1065 TO 1071DJ2 629 MEMB 1009 1020 1027 1031 1042 1053 1072DJ2 601 MEMB 1028 1029DJ2 614 MEMB 1048 1049DJ2 617 MEMB 1050 1051DJ2 620 MEMB 1060 1061DJ2 611 MEMB 1043 TO 1045DJ2 605 MEMB 1037 TO 1039DJ2 594 MEMB 1010 TO 1013DJ1 206 MEMB 375 TO 381 387 397 411 422DJ1 207 MEMB 382 388 392 398 409 412 423DJ1 208 MEMB 386 401 418DJ1 209 MEMB 384 399 419DJ1 210 MEMB 385 400 420DJ1 212 MEMB 390 413DJ1 205 MEMB 389 417DJ1 236 MEMB 424 TO 433 449 467 477 480 491 495DJ1 244 MEMB 434 TO 439 446 463 487DJ1 221 MEMB 402 TO 405DJ2 236 MEMB 381 387 397 411 422DJ2 234 MEMB 382 388 392 398 409 412 423DJ2 237 MEMB 386 401 418DJ2 239 MEMB 384 399 419DJ2 241 MEMB 385 400 420DJ2 244 MEMB 390 413DJ2 250 MEMB 389 417 434 TO 439DJ2 225 MEMB 402 TO 405DJ1 234 MEMB 440 456 466 474 478 481 492 494DJ1 235 MEMB 441 458 482DJ1 238 MEMB 442 459 483DJ1 240 MEMB 443 460 484DJ1 241 MEMB 444 461 485DJ1 242 MEMB 445 462 486DJ1 246 MEMB 447 464 488DJ1 248 MEMB 448 465 489DJ1 280 MEMB 496 TO 505DJ1 289 MEMB 506 TO 511DJ2 280 MEMB 449 467 477 480 491 495DJ2 279 MEMB 440 456 466 474 478 481 492 494DJ2 281 MEMB 441 458 482DJ2 282 MEMB 442 459 483DJ2 283 MEMB 443 460 484DJ2 285 MEMB 444 461 485DJ2 287 MEMB 445 462 486DJ2 289 MEMB 446 463 487 496 TO 505DJ2 291 MEMB 447 464 488DJ2 293 MEMB 448 465 489DJ2 295 MEMB 506 TO 511DJ1 296 MEMB 521 TO 528 540 556 566 580 592 611 613DJ1 297 MEMB 533 548 555 564 567 579 586 591 600 610 614DJ1 299 MEMB 535 551 569 588 604DJ1 300 MEMB 536 552 570 589 605DJ1 304 MEMB 529 TO 532 539 554 573 590 609DJ1 355 MEMB 615 TO 627DJ1 368 MEMB 628 TO 631 638 667DJ1 309 MEMB 541 TO 543DJ1 320 MEMB 557 TO 559DJ1 333 MEMB 581 582DJ1 342 MEMB 593 TO 595DJ1 313 MEMB 544 TO 547DJ1 324 MEMB 560 TO 563DJ1 336 MEMB 583 TO 585DJ1 346 MEMB 596 TO 599DJ2 355 MEMB 540 556 566 580 592 611 613DJ2 357 MEMB 533 548 555 564 567 579 586 591 600 610 614DJ2 361 MEMB 535 551 569 588 604DJ2 362 MEMB 536 552 570 589 605DJ2 368 MEMB 539 554 573 590 609 615 TO 627DJ2 312 MEMB 541 TO 543DJ2 323 MEMB 557 TO 559DJ2 335 MEMB 581 582DJ2 345 MEMB 593 TO 595DJ2 317 MEMB 544 TO 547DJ2 328 MEMB 560 TO 563DJ2 339 MEMB 583 TO 585DJ2 350 MEMB 596 TO 599DJ2 308 MEMB 529 TO 532DJ2 372 MEMB 628 TO 631DJ1 356 MEMB 633 636 644 647 656 663 666 671DJ1 392 MEMB 672 TO 679DJ1 383 MEMB 658 TO 661DJ2 392 MEMB 632 635 643 646 655 662 665 670DJ2 393 MEMB 633 636 644 647 656 663 666 671DJ2 400 MEMB 672 TO 679DJ2 387 MEMB 658 TO 661DJ1 20 MEMB 44 TO 50DJ1 21 MEMB 51 54 59 71 79DJ1 22 MEMB 52 55 60 72 80DJ1 27 MEMB 57 74DJ1 34 MEMB 67 TO 70DJ1 41 MEMB 81 TO 91 96 99 111 115 125 132DJ1 52 MEMB 92 TO 95DJ2 42 MEMB 51 54 59 71 79DJ2 43 MEMB 52 55 60 72 80DJ2 52 MEMB 57 74DJ2 38 MEMB 67 TO 70DJ2 56 MEMB 56 78 92 TO 95DJ1 19 MEMB 56 78DJ1 42 MEMB 97 100 112 114 120 124 128 133DJ1 46 MEMB 102 122 130DJ1 50 MEMB 104 123 131DJ1 76 MEMB 134 TO 143 148 164 170DJ1 63 MEMB 116 117DJ1 65 MEMB 118 119DJ1 85 MEMB 144 TO 147DJ2 76 MEMB 96 99 111 115 125 132DJ2 78 MEMB 97 100 112 114 120 124 128 133DJ2 65 MEMB 116 117DJ2 67 MEMB 118 119DJ2 85 MEMB 134 TO 143DJ2 89 MEMB 144 TO 147DJ1 77 MEMB 149 165 171DJ1 79 MEMB 151 162 168DJ1 75 MEMB 150 163 169DJ1 98 MEMB 172 TO 182 191 210 222 232 243 248 253DJ1 109 MEMB 183 TO 186DJ2 98 MEMB 148 164 170DJ2 99 MEMB 149 165 171DJ2 101 MEMB 151 162 168DJ2 102 MEMB 150 163 169DJ2 109 MEMB 172 TO 182DJ2 113 MEMB 183 TO 186DJ1 100 MEMB 189 199 209 220 223 233 244 249 254DJ1 103 MEMB 190 208 225 241 251DJ1 128 MEMB 224 240 250DJ1 105 MEMB 187 201 237DJ1 108 MEMB 188 204 239DJ1 153 MEMB 255 TO 264 269 276 287 290 297 306 309 319DJ1 162 MEMB 265 TO 268 282 314DJ1 118 MEMB 195 TO 198DJ1 125 MEMB 211 TO 215DJ1 140 MEMB 234 235DJ1 145 MEMB 245 246DJ1 114 MEMB 192 TO 194DJ1 131 MEMB 216 TO 219DJ2 153 MEMB 191 210 222 232 243 248 253DJ2 154 MEMB 189 199 209 220 223 233 244 249 254DJ2 152 MEMB 224 240 250DJ2 156 MEMB 190 208 225 241 251DJ2 157 MEMB 187 201 237DJ2 161 MEMB 188 204 239DJ2 166 MEMB 265 TO 268DJ2 122 MEMB 195 TO 198DJ2 130 MEMB 211 TO 215DJ2 117 MEMB 192 TO 194DJ2 135 MEMB 216 TO 219DJ2 162 MEMB 255 TO 264DJ2 141 MEMB 234 235DJ2 147 MEMB 245 246DJ1 154 MEMB 270 277 288 291 298 307 310 322DJ1 152 MEMB 271 292 311DJ1 156 MEMB 273 293 312DJ1 158 MEMB 274 294 313DJ1 195 MEMB 323 TO 328 330 331DJ1 191 MEMB 316 TO 318DJ1 169 MEMB 278 279DJ1 166 MEMB 286 315DJ1 184 MEMB 302 TO 305DJ2 195 MEMB 269 276 287 290 297 306 309 319DJ2 198 MEMB 254 270 277 288 291 298 307 310 322DJ2 194 MEMB 316 TO 318DJ2 199 MEMB 271 292 311DJ2 200 MEMB 273 293 312DJ2 204 MEMB 274 294 313DJ2 171 MEMB 278 279DJ2 202 MEMB 282 314 323 TO 328 330 331DJ2 188 MEMB 302 TO 305DJ2 203 MEMB 286 315DJ1 811 MEMB 1437 1441 TO 1445DJ1 804 MEMB 1438 TO 1440DJ1 813 MEMB 1456 TO 1461DJ1 819 MEMB 1462 1463 1551DJ1 823 MEMB 1562 TO 1567DJ1 829 MEMB 1568 TO 1570DJ1 833 MEMB 1581 TO 1586DJ1 839 MEMB 1587 TO 1589DJ1 843 MEMB 1600 TO 1605DJ1 849 MEMB 1606 TO 1608DJ1 853 MEMB 1619 TO 1624DJ1 859 MEMB 1625 TO 1627DJ2 804 MEMB 1437 1441 TO 1445DJ2 807 MEMB 1438 TO 1440DJ2 819 MEMB 1456 TO 1461DJ2 822 MEMB 1462 1463 1551DJ2 829 MEMB 1562 TO 1567DJ2 832 MEMB 1568 TO 1570DJ2 839 MEMB 1581 TO 1586DJ2 842 MEMB 1587 TO 1589DJ2 849 MEMB 1600 TO 1605DJ2 852 MEMB 1606 TO 1608DJ2 859 MEMB 1619 TO 1624DJ2 862 MEMB 1625 TO 1627TRACK 2 ALLCHECK CODE MEMB 43 TO 331 374 TO 680 723 TO 1072 1115 TO 1394 1437 TO 1463 -1551 TO 1627PRINT SECTION MAX DISPL ALLLOAD LIST ENV 1 2CHECK CODE MEMB 43 TO 331 374 TO 680 723 TO 1072 1115 TO 1394 1437 TO 1463 -1551 TO 1627FINISH
To clarify my question, is my model not telling STAAD which members to consider for deflection correctly? Looking at the results it is giving me different utilization ratios for different segments of the member.... when they should be one member with one utilization ratio for displacement.
You have defined 3 sets of design out of which the second one is the one which is only for deflection. If you look at the ratios for that design, the ratios would be same for all those segments which were assigned same DJ1 and DJ2. However in your last design set where you have both service and strength checks included, you will not get the same ratios for all segments as in some of those segments strength is governing and in some, deflection is governing.
Also on a different note, please do not paste the input commands in the forum thread. Instead you may upload the .std file directly.