Huge support reactions for support of shearwall (modeled using parametric)
Why do I keep having very big reactions for the support of modeled shearwall? When i modeled my structure, the reactions was around 1900Kn but when I incorporate a shear wall (which is modeled using parametric) it shows very large reactions which is 7000Kn. Can someone help me? Is this true for all cases that it has very large reactions? Or is there something wrong with my model?
  • Hello Zuhair,
    Your question will be more clear to me if I Can see your models. But, from the description it seems when you add the shearwall in your framed structure the reaction increases. If that is the case, please consider the selfweight of the shear wall. If still you have doubts, please upload the files here.
    Thanks & Regards,
    Abhisek Mandal
    Global Technical Support
  • STAAD SPACE
    START JOB INFORMATION
    ENGINEER DATE 05-Aug-21
    END JOB INFORMATION
    INPUT WIDTH 79
    UNIT METER KN
    JOINT COORDINATES
    1 0 0 0; 2 3.7 0 0; 3 8.925 0 0; 4 14.925 0 0; 5 20.15 0 0; 6 0 0 6; 7 3.7 0 6;
    8 8.925 0 6; 9 14.925 0 6; 10 20.15 0 6; 11 0 0 12; 12 3.7 0 12; 13 8.925 0 12;
    14 14.925 0 12; 15 20.15 0 12; 16 0 0 18; 17 3.7 0 18; 18 8.925 0 18;
    19 14.925 0 18; 20 20.15 0 18; 21 0 0 24; 22 3.7 0 24; 23 8.925 0 24;
    24 14.925 0 24; 25 20.15 0 24; 26 0 0 30; 27 3.7 0 30; 28 8.925 0 30;
    29 14.925 0 30; 30 20.15 0 30; 31 0 0 35.6; 32 3.7 0 35.6; 33 8.925 0 35.6;
    34 14.925 0 35.6; 35 20.15 0 35.6; 36 0 5.5 0; 37 3.7 5.5 0; 38 8.925 5.5 0;
    39 14.925 5.5 0; 40 20.15 5.5 0; 41 0 5.5 6; 42 3.7 5.5 6; 43 8.925 5.5 6;
    44 14.925 5.5 6; 45 20.15 5.5 6; 46 0 5.5 12; 47 3.7 5.5 12; 48 8.925 5.5 12;
    49 14.925 5.5 12; 50 20.15 5.5 12; 51 0 5.5 18; 52 3.7 5.5 18; 53 8.925 5.5 18;
    54 14.925 5.5 18; 55 20.15 5.5 18; 56 0 5.5 24; 57 3.7 5.5 24; 58 8.925 5.5 24;
    59 14.925 5.5 24; 60 20.15 5.5 24; 61 0 5.5 30; 62 3.7 5.5 30; 63 8.925 5.5 30;
    64 14.925 5.5 30; 65 20.15 5.5 30; 66 0 5.5 35.6; 67 3.7 5.5 35.6;
    68 8.925 5.5 35.6; 69 14.925 5.5 35.6; 70 20.15 5.5 35.6; 72 3.7 9 0;
    73 8.925 9 0; 74 14.925 9 0; 75 20.15 9 0; 77 3.7 9 6; 78 8.925 9 6;
    79 14.925 9 6; 80 20.15 9 6; 82 3.7 9 12; 83 8.925 9 12; 84 14.925 9 12;
    85 20.15 9 12; 87 3.7 9 18; 88 8.925 9 18; 89 14.925 9 18; 90 20.15 9 18;
    92 3.7 9 24; 93 8.925 9 24; 94 14.925 9 24; 95 20.15 9 24; 97 3.7 9 30;
    98 8.925 9 30; 99 14.925 9 30; 100 20.15 9 30; 102 3.7 9 35.6;
    103 8.925 9 35.6; 104 14.925 9 35.6; 105 20.15 9 35.6; 107 3.7 12.5 0;
    108 8.925 12.5 0; 109 14.925 12.5 0; 110 20.15 12.5 0; 112 3.7 12.5 6;
    113 8.925 12.5 6; 114 14.925 12.5 6; 115 20.15 12.5 6; 117 3.7 12.5 12;
    118 8.925 12.5 12; 119 14.925 12.5 12; 120 20.15 12.5 12; 122 3.7 12.5 18;
    123 8.925 12.5 18; 124 14.925 12.5 18; 125 20.15 12.5 18; 127 3.7 12.5 24;
    128 8.925 12.5 24; 129 14.925 12.5 24; 130 20.15 12.5 24; 132 3.7 12.5 30;
    133 8.925 12.5 30; 134 14.925 12.5 30; 135 20.15 12.5 30; 137 3.7 12.5 35.6;
    138 8.925 12.5 35.6; 139 14.925 12.5 35.6; 140 20.15 12.5 35.6; 142 3.7 17.5 0;
    143 8.925 17.5 0; 144 14.925 17.5 0; 145 20.15 17.5 0; 147 3.7 17.5 6;
    148 8.925 17.5 6; 149 14.925 17.5 6; 150 20.15 17.5 6; 152 3.7 17.5 12;
    153 8.925 17.5 12; 154 14.925 17.5 12; 155 20.15 17.5 12; 157 3.7 17.5 18;
    158 8.925 17.5 18; 159 14.925 17.5 18; 160 20.15 17.5 18; 162 3.7 17.5 24;
    163 8.925 17.5 24; 164 14.925 17.5 24; 165 20.15 17.5 24; 167 3.7 17.5 30;
    168 8.925 17.5 30; 169 14.925 17.5 30; 170 20.15 17.5 30; 172 3.7 17.5 35.6;
    173 8.925 17.5 35.6; 174 14.925 17.5 35.6; 175 20.15 17.5 35.6;
    211 6.3125 5.5 0; 212 11.925 5.5 0; 214 6.3125 5.5 6; 215 11.925 5.5 6;
    216 17.5375 5.5 6; 217 6.3125 5.5 12; 218 11.925 5.5 12; 219 17.5375 5.5 12;
    220 6.3125 5.5 18; 221 11.925 5.5 18; 222 17.5375 5.5 18; 223 6.3125 5.5 24;
    224 11.925 5.5 24; 225 17.5375 5.5 24; 226 6.3125 5.5 30; 227 11.925 5.5 30;
    228 17.5375 5.5 30; 229 6.3125 5.5 35.6; 230 11.925 5.5 35.6; 232 6.3125 9 0;
    233 11.925 9 0; 235 6.3125 9 6; 236 11.925 9 6; 237 17.5375 9 6;
    238 6.3125 9 12; 239 11.925 9 12; 240 17.5375 9 12; 241 6.3125 9 18;
    242 11.925 9 18; 243 17.5375 9 18; 244 6.3125 9 24; 245 11.925 9 24;
    246 17.5375 9 24; 247 6.3125 9 30; 248 11.925 9 30; 249 17.5375 9 30;
    250 6.3125 9 35.6; 251 11.925 9 35.6; 253 6.3125 12.5 0; 254 11.925 12.5 0;
    256 6.3125 12.5 6; 257 11.925 12.5 6; 258 17.5375 12.5 6; 259 6.3125 12.5 12;
    260 11.925 12.5 12; 261 17.5375 12.5 12; 262 6.3125 12.5 18;
    263 11.925 12.5 18; 264 17.5375 12.5 18; 265 6.3125 12.5 24;
    266 11.925 12.5 24; 267 17.5375 12.5 24; 268 6.3125 12.5 30;
    269 11.925 12.5 30; 270 17.5375 12.5 30; 271 6.3125 12.5 35.6;
    272 11.925 12.5 35.6; 274 6.3125 17.5 0; 275 11.925 17.5 0; 277 6.3125 17.5 6;
    278 11.925 17.5 6; 279 17.5375 17.5 6; 280 6.3125 17.5 12; 281 11.925 17.5 12;
    282 17.5375 17.5 12; 283 6.3125 17.5 18; 284 11.925 17.5 18;
    285 17.5375 17.5 18; 286 6.3125 17.5 24; 287 11.925 17.5 24;
    288 17.5375 17.5 24; 289 6.3125 17.5 30; 290 11.925 17.5 30;
    291 17.5375 17.5 30; 292 6.3125 17.5 35.6; 293 11.925 17.5 35.6; 295 0 -2.5 0;
    296 3.7 -2.5 0; 297 8.925 -2.5 0; 298 14.925 -2.5 0; 299 20.15 -2.5 0;
    300 0 -2.5 6; 301 3.7 -2.5 6; 302 8.925 -2.5 6; 303 14.925 -2.5 6;
    304 20.15 -2.5 6; 305 0 -2.5 12; 306 3.7 -2.5 12; 307 8.925 -2.5 12;
    308 14.925 -2.5 12; 309 20.15 -2.5 12; 310 0 -2.5 18; 311 3.7 -2.5 18;
    312 8.925 -2.5 18; 313 14.925 -2.5 18; 314 20.15 -2.5 18; 315 0 -2.5 24;
    316 3.7 -2.5 24; 317 8.925 -2.5 24; 318 14.925 -2.5 24; 319 20.15 -2.5 24;
    320 0 -2.5 30; 321 3.7 -2.5 30; 322 8.925 -2.5 30; 323 14.925 -2.5 30;
    324 20.15 -2.5 30; 325 0 -2.5 35.6; 326 3.7 -2.5 35.6; 327 8.925 -2.5 35.6;
    328 14.925 -2.5 35.6; 329 20.15 -2.5 35.6; 330 14.925 5.5 3.1;
    331 20.15 5.5 3.1; 332 14.925 9 3.1; 333 20.15 9 3.1; 334 14.925 12.5 3.1;
    335 20.15 12.5 3.1; 336 14.925 17.5 3.1; 337 20.15 17.5 3.1; 338 3.7 20.5 0;
    339 8.925 20.5 0; 340 14.925 20.5 0; 341 20.15 20.5 0; 342 3.7 20.5 6;
    343 8.925 20.5 6; 344 14.925 20.5 6; 345 20.15 20.5 6; 346 0 5.5 38;
    347 3.7 5.5 38; 348 8.925 5.5 38; 349 14.925 5.5 38; 350 20.15 5.5 38;
    351 6.3125 5.5 38; 352 11.925 5.5 38; 355 3.7 9 38; 356 8.925 9 38;
    357 14.925 9 38; 358 20.15 9 38; 359 6.3125 9 38; 360 11.925 9 38;
    363 3.7 12.5 38; 364 8.925 12.5 38; 365 14.925 12.5 38; 366 20.15 12.5 38;
    367 6.3125 12.5 38; 368 11.925 12.5 38; 369 18.125 0 30; 370 18.125 5.5 30;
    371 18.125 9 30; 372 18.125 12.5 30; 373 18.125 17.5 30; 374 18.125 -2.5 30;
    375 18.125 0 33.2; 376 18.125 5.5 33.2; 377 18.125 9 33.2;
    378 18.125 12.5 33.2; 379 18.125 17.5 33.2; 380 18.125 -2.5 33.2;
    381 14.925 0 33.2; 382 14.925 5.5 33.2; 383 14.925 9 33.2;
    384 14.925 12.5 33.2; 385 14.925 17.5 33.2; 386 14.925 -2.5 33.2;
    387 14.925 -2.29167 30; 388 14.925 -2.08333 30; 389 14.925 -1.875 30;
    390 14.925 -1.66667 30; 391 14.925 -1.45833 30; 392 14.925 -1.25 30;
    393 14.925 -1.04167 30; 394 14.925 -0.833333 30; 395 14.925 -0.625 30;
    396 14.925 -0.416667 30; 397 14.925 -0.208333 30; 398 15.125 0 30;
    399 15.325 0 30; 400 15.525 0 30; 401 15.725 0 30; 402 15.925 0 30;
    403 16.125 0 30; 404 16.325 0 30; 405 16.525 0 30; 406 16.725 0 30;
    407 16.925 0 30; 408 17.125 0 30; 409 17.325 0 30; 410 17.525 0 30;
    411 17.725 0 30; 412 17.925 0 30; 413 18.125 -0.208333 30;
    414 18.125 -0.416667 30; 415 18.125 -0.625 30; 416 18.125 -0.833333 30;
    417 18.125 -1.04167 30; 418 18.125 -1.25 30; 419 18.125 -1.45833 30;
    420 18.125 -1.66667 30; 421 18.125 -1.875 30; 422 18.125 -2.08333 30;
    423 18.125 -2.29167 30; 424 17.925 -2.5 30; 425 17.725 -2.5 30;
    426 17.525 -2.5 30; 427 17.325 -2.5 30; 428 17.125 -2.5 30; 429 16.925 -2.5 30;
    430 16.725 -2.5 30; 431 16.525 -2.5 30; 432 16.325 -2.5 30; 433 16.125 -2.5 30;
    434 15.925 -2.5 30; 435 15.725 -2.5 30; 436 15.525 -2.5 30; 437 15.325 -2.5 30;
    438 15.125 -2.5 30; 439 15.125 -2.29167 30; 440 15.325 -2.29167 30;
    441 15.525 -2.29167 30; 442 15.725 -2.29167 30; 443 15.925 -2.29167 30;
    444 16.125 -2.29167 30; 445 16.325 -2.29167 30; 446 16.525 -2.29167 30;
    447 16.725 -2.29167 30; 448 16.925 -2.29167 30; 449 17.125 -2.29167 30;
    450 17.325 -2.29167 30; 451 17.525 -2.29167 30; 452 17.725 -2.29167 30;
    453 17.925 -2.29167 30; 454 15.125 -2.08333 30; 455 15.325 -2.08333 30;
    456 15.525 -2.08333 30; 457 15.725 -2.08333 30; 458 15.925 -2.08333 30;
    459 16.125 -2.08333 30; 460 16.325 -2.08333 30; 461 16.525 -2.08333 30;
    462 16.725 -2.08333 30; 463 16.925 -2.08333 30; 464 17.125 -2.08333 30;
    465 17.325 -2.08333 30; 466 17.525 -2.08333 30; 467 17.725 -2.08333 30;
    468 17.925 -2.08333 30; 469 15.125 -1.875 30; 470 15.325 -1.875 30;
    471 15.525 -1.875 30; 472 15.725 -1.875 30; 473 15.925 -1.875 30;
    474 16.125 -1.875 30; 475 16.325 -1.875 30; 476 16.525 -1.875 30;
    477 16.725 -1.875 30; 478 16.925 -1.875 30; 479 17.125 -1.875 30;
    480 17.325 -1.875 30; 481 17.525 -1.875 30; 482 17.725 -1.875 30;
    483 17.925 -1.875 30; 484 15.125 -1.66667 30; 485 15.325 -1.66667 30;
    486 15.525 -1.66667 30; 487 15.725 -1.66667 30; 488 15.925 -1.66667 30;
    489 16.125 -1.66667 30; 490 16.325 -1.66667 30; 491 16.525 -1.66667 30;
    492 16.725 -1.66667 30; 493 16.925 -1.66667 30; 494 17.125 -1.66667 30;
    495 17.325 -1.66667 30; 496 17.525 -1.66667 30; 497 17.725 -1.66667 30;
    498 17.925 -1.66667 30; 499 15.125 -1.45833 30; 500 15.325 -1.45833 30;
    501 15.525 -1.45833 30; 502 15.725 -1.45833 30; 503 15.925 -1.45833 30;
    504 16.125 -1.45833 30; 505 16.325 -1.45833 30; 506 16.525 -1.45833 30;
    507 16.725 -1.45833 30; 508 16.925 -1.45833 30; 509 17.125 -1.45833 30;
    510 17.325 -1.45833 30; 511 17.525 -1.45833 30; 512 17.725 -1.45833 30;
    513 17.925 -1.45833 30; 514 15.125 -1.25 30; 515 15.325 -1.25 30;
    516 15.525 -1.25 30; 517 15.725 -1.25 30; 518 15.925 -1.25 30;
    519 16.125 -1.25 30; 520 16.325 -1.25 30; 521 16.525 -1.25 30;
    522 16.725 -1.25 30; 523 16.925 -1.25 30; 524 17.125 -1.25 30;
    525 17.325 -1.25 30; 526 17.525 -1.25 30; 527 17.725 -1.25 30;
    528 17.925 -1.25 30; 529 15.125 -1.04167 30; 530 15.325 -1.04167 30;
    531 15.525 -1.04167 30; 532 15.725 -1.04167 30; 533 15.925 -1.04167 30;
    534 16.125 -1.04167 30; 535 16.325 -1.04167 30; 536 16.525 -1.04167 30;
    537 16.725 -1.04167 30; 538 16.925 -1.04167 30; 539 17.125 -1.04167 30;
    540 17.325 -1.04167 30; 541 17.525 -1.04167 30; 542 17.725 -1.04167 30;
    543 17.925 -1.04167 30; 544 15.125 -0.833333 30; 545 15.325 -0.833333 30;
    546 15.525 -0.833333 30; 547 15.725 -0.833333 30; 548 15.925 -0.833333 30;
    549 16.125 -0.833333 30; 550 16.325 -0.833333 30; 551 16.525 -0.833333 30;
    552 16.725 -0.833333 30; 553 16.925 -0.833333 30; 554 17.125 -0.833333 30;
    555 17.325 -0.833333 30; 556 17.525 -0.833333 30; 557 17.725 -0.833333 30;
    558 17.925 -0.833333 30; 559 15.125 -0.625 30; 560 15.325 -0.625 30;
    561 15.525 -0.625 30; 562 15.725 -0.625 30; 563 15.925 -0.625 30;
    564 16.125 -0.625 30; 565 16.325 -0.625 30; 566 16.525 -0.625 30;
    567 16.725 -0.625 30; 568 16.925 -0.625 30; 569 17.125 -0.625 30;
    570 17.325 -0.625 30; 571 17.525 -0.625 30; 572 17.725 -0.625 30;
    573 17.925 -0.625 30; 574 15.125 -0.416667 30; 575 15.325 -0.416667 30;
    576 15.525 -0.416667 30; 577 15.725 -0.416667 30; 578 15.925 -0.416667 30;
    579 16.125 -0.416667 30; 580 16.325 -0.416667 30; 581 16.525 -0.416667 30;
    582 16.725 -0.416667 30; 583 16.925 -0.416667 30; 584 17.125 -0.416667 30;
    585 17.325 -0.416667 30; 586 17.525 -0.416667 30; 587 17.725 -0.416667 30;
    588 17.925 -0.416667 30; 589 15.125 -0.208333 30; 590 15.325 -0.208333 30;
    591 15.525 -0.208333 30; 592 15.725 -0.208333 30; 593 15.925 -0.208333 30;
    594 16.125 -0.208333 30; 595 16.325 -0.208333 30; 596 16.525 -0.208333 30;
    597 16.725 -0.208333 30; 598 16.925 -0.208333 30; 599 17.125 -0.208333 30;
    600 17.325 -0.208333 30; 601 17.525 -0.208333 30; 602 17.725 -0.208333 30;
    603 17.925 -0.208333 30; 604 18.125 0 30.2; 605 18.125 0 30.4;
    606 18.125 0 30.6; 607 18.125 0 30.8; 608 18.125 0 31; 609 18.125 0 31.2;
    610 18.125 0 31.4; 611 18.125 0 31.6; 612 18.125 0 31.8; 613 18.125 0 32;
    614 18.125 0 32.2; 615 18.125 0 32.4; 616 18.125 0 32.6; 617 18.125 0 32.8;
    618 18.125 0 33; 619 18.125 -0.208333 33.2; 620 18.125 -0.416667 33.2;
    621 18.125 -0.625 33.2; 622 18.125 -0.833333 33.2; 623 18.125 -1.04167 33.2;
    624 18.125 -1.25 33.2; 625 18.125 -1.45833 33.2; 626 18.125 -1.66667 33.2;
    627 18.125 -1.875 33.2; 628 18.125 -2.08333 33.2; 629 18.125 -2.29167 33.2;
    630 18.125 -2.5 33; 631 18.125 -2.5 32.8; 632 18.125 -2.5 32.6;
    633 18.125 -2.5 32.4; 634 18.125 -2.5 32.2; 635 18.125 -2.5 32;
    636 18.125 -2.5 31.8; 637 18.125 -2.5 31.6; 638 18.125 -2.5 31.4;
    639 18.125 -2.5 31.2; 640 18.125 -2.5 31; 641 18.125 -2.5 30.8;
    642 18.125 -2.5 30.6; 643 18.125 -2.5 30.4; 644 18.125 -2.5 30.2;
    645 18.125 -2.29167 30.2; 646 18.125 -2.29167 30.4; 647 18.125 -2.29167 30.6;
    648 18.125 -2.29167 30.8; 649 18.125 -2.29167 31; 650 18.125 -2.29167 31.2;
    651 18.125 -2.29167 31.4; 652 18.125 -2.29167 31.6; 653 18.125 -2.29167 31.8;
    654 18.125 -2.29167 32; 655 18.125 -2.29167 32.2; 656 18.125 -2.29167 32.4;
    657 18.125 -2.29167 32.6; 658 18.125 -2.29167 32.8; 659 18.125 -2.29167 33;
    660 18.125 -2.08333 30.2; 661 18.125 -2.08333 30.4; 662 18.125 -2.08333 30.6;
    663 18.125 -2.08333 30.8; 664 18.125 -2.08333 31; 665 18.125 -2.08333 31.2;
    666 18.125 -2.08333 31.4; 667 18.125 -2.08333 31.6; 668 18.125 -2.08333 31.8;
    669 18.125 -2.08333 32; 670 18.125 -2.08333 32.2; 671 18.125 -2.08333 32.4;
    672 18.125 -2.08333 32.6; 673 18.125 -2.08333 32.8; 674 18.125 -2.08333 33;
    675 18.125 -1.875 30.2; 676 18.125 -1.875 30.4; 677 18.125 -1.875 30.6;
    678 18.125 -1.875 30.8; 679 18.125 -1.875 31; 680 18.125 -1.875 31.2;
    681 18.125 -1.875 31.4; 682 18.125 -1.875 31.6; 683 18.125 -1.875 31.8;
    684 18.125 -1.875 32; 685 18.125 -1.875 32.2; 686 18.125 -1.875 32.4;
    687 18.125 -1.875 32.6; 688 18.125 -1.875 32.8; 689 18.125 -1.875 33;
    690 18.125 -1.66667 30.2; 691 18.125 -1.66667 30.4; 692 18.125 -1.66667 30.6;
    693 18.125 -1.66667 30.8; 694 18.125 -1.66667 31; 695 18.125 -1.66667 31.2;
    696 18.125 -1.66667 31.4; 697 18.125 -1.66667 31.6; 698 18.125 -1.66667 31.8;
    699 18.125 -1.66667 32; 700 18.125 -1.66667 32.2; 701 18.125 -1.66667 32.4;
    702 18.125 -1.66667 32.6; 703 18.125 -1.66667 32.8; 704 18.125 -1.66667 33;
    705 18.125 -1.45833 30.2; 706 18.125 -1.45833 30.4; 707 18.125 -1.45833 30.6;
    708 18.125 -1.45833 30.8; 709 18.125 -1.45833 31; 710 18.125 -1.45833 31.2;
    711 18.125 -1.45833 31.4; 712 18.125 -1.45833 31.6; 713 18.125 -1.45833 31.8;
    714 18.125 -1.45833 32; 715 18.125 -1.45833 32.2; 716 18.125 -1.45833 32.4;
    717 18.125 -1.45833 32.6; 718 18.125 -1.45833 32.8; 719 18.125 -1.45833 33;
    720 18.125 -1.25 30.2; 721 18.125 -1.25 30.4; 722 18.125 -1.25 30.6;
    723 18.125 -1.25 30.8; 724 18.125 -1.25 31; 725 18.125 -1.25 31.2;
    726 18.125 -1.25 31.4; 727 18.125 -1.25 31.6; 728 18.125 -1.25 31.8;
    729 18.125 -1.25 32; 730 18.125 -1.25 32.2; 731 18.125 -1.25 32.4;
    732 18.125 -1.25 32.6; 733 18.125 -1.25 32.8; 734 18.125 -1.25 33;
    735 18.125 -1.04167 30.2; 736 18.125 -1.04167 30.4; 737 18.125 -1.04167 30.6;
    738 18.125 -1.04167 30.8; 739 18.125 -1.04167 31; 740 18.125 -1.04167 31.2;
    741 18.125 -1.04167 31.4; 742 18.125 -1.04167 31.6; 743 18.125 -1.04167 31.8;
    744 18.125 -1.04167 32; 745 18.125 -1.04167 32.2; 746 18.125 -1.04167 32.4;
    747 18.125 -1.04167 32.6; 748 18.125 -1.04167 32.8; 749 18.125 -1.04167 33;
    750 18.125 -0.833333 30.2; 751 18.125 -0.833333 30.4;
    752 18.125 -0.833333 30.6; 753 18.125 -0.833333 30.8; 754 18.125 -0.833333 31;
    755 18.125 -0.833333 31.2; 756 18.125 -0.833333 31.4;
    757 18.125 -0.833333 31.6; 758 18.125 -0.833333 31.8; 759 18.125 -0.833333 32;
    760 18.125 -0.833333 32.2; 761 18.125 -0.833333 32.4;
    762 18.125 -0.833333 32.6; 763 18.125 -0.833333 32.8; 764 18.125 -0.833333 33;
    765 18.125 -0.625 30.2; 766 18.125 -0.625 30.4; 767 18.125 -0.625 30.6;
    768 18.125 -0.625 30.8; 769 18.125 -0.625 31; 770 18.125 -0.625 31.2;
    771 18.125 -0.625 31.4; 772 18.125 -0.625 31.6; 773 18.125 -0.625 31.8;
    774 18.125 -0.625 32; 775 18.125 -0.625 32.2; 776 18.125 -0.625 32.4;
    777 18.125 -0.625 32.6; 778 18.125 -0.625 32.8; 779 18.125 -0.625 33;
    780 18.125 -0.416667 30.2; 781 18.125 -0.416667 30.4;
    782 18.125 -0.416667 30.6; 783 18.125 -0.416667 30.8; 784 18.125 -0.416667 31;
    785 18.125 -0.416667 31.2; 786 18.125 -0.416667 31.4;
    787 18.125 -0.416667 31.6; 788 18.125 -0.416667 31.8; 789 18.125 -0.416667 32;
    790 18.125 -0.416667 32.2; 791 18.125 -0.416667 32.4;
    792 18.125 -0.416667 32.6; 793 18.125 -0.416667 32.8; 794 18.125 -0.416667 33;
    795 18.125 -0.208333 30.2; 796 18.125 -0.208333 30.4;
    797 18.125 -0.208333 30.6; 798 18.125 -0.208333 30.8; 799 18.125 -0.208333 31;
    800 18.125 -0.208333 31.2; 801 18.125 -0.208333 31.4;
    802 18.125 -0.208333 31.6; 803 18.125 -0.208333 31.8; 804 18.125 -0.208333 32;
    805 18.125 -0.208333 32.2; 806 18.125 -0.208333 32.4;
    807 18.125 -0.208333 32.6; 808 18.125 -0.208333 32.8; 809 18.125 -0.208333 33;
    810 14.925 -2.29167 33.2; 811 14.925 -2.08333 33.2; 812 14.925 -1.875 33.2;
    813 14.925 -1.66667 33.2; 814 14.925 -1.45833 33.2; 815 14.925 -1.25 33.2;
    816 14.925 -1.04167 33.2; 817 14.925 -0.833333 33.2; 818 14.925 -0.625 33.2;
    819 14.925 -0.416667 33.2; 820 14.925 -0.208333 33.2; 821 15.125 0 33.2;
    822 15.325 0 33.2; 823 15.525 0 33.2; 824 15.725 0 33.2; 825 15.925 0 33.2;
    826 16.125 0 33.2; 827 16.325 0 33.2; 828 16.525 0 33.2; 829 16.725 0 33.2;
    830 16.925 0 33.2; 831 17.125 0 33.2; 832 17.325 0 33.2; 833 17.525 0 33.2;
    834 17.725 0 33.2; 835 17.925 0 33.2; 836 17.925 -2.5 33.2;
    837 17.725 -2.5 33.2; 838 17.525 -2.5 33.2; 839 17.325 -2.5 33.2;
    840 17.125 -2.5 33.2; 841 16.925 -2.5 33.2; 842 16.725 -2.5 33.2;
    843 16.525 -2.5 33.2; 844 16.325 -2.5 33.2; 845 16.125 -2.5 33.2;
    846 15.925 -2.5 33.2; 847 15.725 -2.5 33.2; 848 15.525 -2.5 33.2;
    849 15.325 -2.5 33.2; 850 15.125 -2.5 33.2; 851 15.125 -2.29167 33.2;
    852 15.325 -2.29167 33.2; 853 15.525 -2.29167 33.2; 854 15.725 -2.29167 33.2;
    855 15.925 -2.29167 33.2; 856 16.125 -2.29167 33.2; 857 16.325 -2.29167 33.2;
    858 16.525 -2.29167 33.2; 859 16.725 -2.29167 33.2; 860 16.925 -2.29167 33.2;
    861 17.125 -2.29167 33.2; 862 17.325 -2.29167 33.2; 863 17.525 -2.29167 33.2;
    864 17.725 -2.29167 33.2; 865 17.925 -2.29167 33.2; 866 15.125 -2.08333 33.2;
    867 15.325 -2.08333 33.2; 868 15.525 -2.08333 33.2; 869 15.725 -2.08333 33.2;
    870 15.925 -2.08333 33.2; 871 16.125 -2.08333 33.2; 872 16.325 -2.08333 33.2;
    873 16.525 -2.08333 33.2; 874 16.725 -2.08333 33.2; 875 16.925 -2.08333 33.2;
    876 17.125 -2.08333 33.2; 877 17.325 -2.08333 33.2; 878 17.525 -2.08333 33.2;
    879 17.725 -2.08333 33.2; 880 17.925 -2.08333 33.2; 881 15.125 -1.875 33.2;
    882 15.325 -1.875 33.2; 883 15.525 -1.875 33.2; 884 15.725 -1.875 33.2;
    885 15.925 -1.875 33.2; 886 16.125 -1.875 33.2; 887 16.325 -1.875 33.2;
    888 16.525 -1.875 33.2; 889 16.725 -1.875 33.2; 890 16.925 -1.875 33.2;
    891 17.125 -1.875 33.2; 892 17.325 -1.875 33.2; 893 17.525 -1.875 33.2;
    894 17.725 -1.875 33.2; 895 17.925 -1.875 33.2; 896 15.125 -1.66667 33.2;
    897 15.325 -1.66667 33.2; 898 15.525 -1.66667 33.2; 899 15.725 -1.66667 33.2;
    900 15.925 -1.66667 33.2; 901 16.125 -1.66667 33.2; 902 16.325 -1.66667 33.2;
    903 16.525 -1.66667 33.2; 904 16.725 -1.66667 33.2; 905 16.925 -1.66667 33.2;
    906 17.125 -1.66667 33.2; 907 17.325 -1.66667 33.2; 908 17.525 -1.66667 33.2;
    909 17.725 -1.66667 33.2; 910 17.925 -1.66667 33.2; 911 15.125 -1.45833 33.2;
    912 15.325 -1.45833 33.2; 913 15.525 -1.45833 33.2; 914 15.725 -1.45833 33.2;
    915 15.925 -1.45833 33.2; 916 16.125 -1.45833 33.2; 917 16.325 -1.45833 33.2;
    918 16.525 -1.45833 33.2; 919 16.725 -1.45833 33.2; 920 16.925 -1.45833 33.2;
    921 17.125 -1.45833 33.2; 922 17.325 -1.45833 33.2; 923 17.525 -1.45833 33.2;
    924 17.725 -1.45833 33.2; 925 17.925 -1.45833 33.2; 926 15.125 -1.25 33.2;
    927 15.325 -1.25 33.2; 928 15.525 -1.25 33.2; 929 15.725 -1.25 33.2;
    930 15.925 -1.25 33.2; 931 16.125 -1.25 33.2; 932 16.325 -1.25 33.2;
    933 16.525 -1.25 33.2; 934 16.725 -1.25 33.2; 935 16.925 -1.25 33.2;
    936 17.125 -1.25 33.2; 937 17.325 -1.25 33.2; 938 17.525 -1.25 33.2;
    939 17.725 -1.25 33.2; 940 17.925 -1.25 33.2; 941 15.125 -1.04167 33.2;
    942 15.325 -1.04167 33.2; 943 15.525 -1.04167 33.2; 944 15.725 -1.04167 33.2;
    945 15.925 -1.04167 33.2; 946 16.125 -1.04167 33.2; 947 16.325 -1.04167 33.2;
    948 16.525 -1.04167 33.2; 949 16.725 -1.04167 33.2; 950 16.925 -1.04167 33.2;
    951 17.125 -1.04167 33.2; 952 17.325 -1.04167 33.2; 953 17.525 -1.04167 33.2;
    954 17.725 -1.04167 33.2; 955 17.925 -1.04167 33.2; 956 15.125 -0.833333 33.2;
    957 15.325 -0.833333 33.2; 958 15.525 -0.833333 33.2;
    959 15.725 -0.833333 33.2; 960 15.925 -0.833333 33.2;
    961 16.125 -0.833333 33.2; 962 16.325 -0.833333 33.2;
    963 16.525 -0.833333 33.2; 964 16.725 -0.833333 33.2;
    965 16.925 -0.833333 33.2; 966 17.125 -0.833333 33.2;
    967 17.325 -0.833333 33.2; 968 17.525 -0.833333 33.2;
    969 17.725 -0.833333 33.2; 970 17.925 -0.833333 33.2; 971 15.125 -0.625 33.2;
    972 15.325 -0.625 33.2; 973 15.525 -0.625 33.2; 974 15.725 -0.625 33.2;
    975 15.925 -0.625 33.2; 976 16.125 -0.625 33.2; 977 16.325 -0.625 33.2;
    978 16.525 -0.625 33.2; 979 16.725 -0.625 33.2; 980 16.925 -0.625 33.2;
    981 17.125 -0.625 33.2; 982 17.325 -0.625 33.2; 983 17.525 -0.625 33.2;
    984 17.725 -0.625 33.2; 985 17.925 -0.625 33.2; 986 15.125 -0.416667 33.2;
    987 15.325 -0.416667 33.2; 988 15.525 -0.416667 33.2;
    989 15.725 -0.416667 33.2; 990 15.925 -0.416667 33.2;
    991 16.125 -0.416667 33.2; 992 16.325 -0.416667 33.2;
    993 16.525 -0.416667 33.2; 994 16.725 -0.416667 33.2;
    995 16.925 -0.416667 33.2; 996 17.125 -0.416667 33.2;
    997 17.325 -0.416667 33.2; 998 17.525 -0.416667 33.2;
    999 17.725 -0.416667 33.2; 1000 17.925 -0.416667 33.2;
    1001 15.125 -0.208333 33.2; 1002 15.325 -0.208333 33.2;
    1003 15.525 -0.208333 33.2; 1004 15.725 -0.208333 33.2;
    1005 15.925 -0.208333 33.2; 1006 16.125 -0.208333 33.2;
    1007 16.325 -0.208333 33.2; 1008 16.525 -0.208333 33.2;
    1009 16.725 -0.208333 33.2; 1010 16.925 -0.208333 33.2;
    1011 17.125 -0.208333 33.2; 1012 17.325 -0.208333 33.2;
    1013 17.525 -0.208333 33.2; 1014 17.725 -0.208333 33.2;
    1015 17.925 -0.208333 33.2; 1016 14.925 2.75 30; 1017 15.1116 5.5 30;
    1018 15.2982 5.5 30; 1019 15.4848 5.5 30; 1020 15.6714 5.5 30;
    1021 15.858 5.5 30; 1022 16.0446 5.5 30; 1023 16.2313 5.5 30;
    1024 16.4179 5.5 30; 1025 16.6045 5.5 30; 1026 16.7911 5.5 30;
    1027 16.9777 5.5 30; 1028 17.1643 5.5 30; 1029 17.3509 5.5 30;
    1030 18.125 5.30357 30; 1031 18.125 5.10714 30; 1032 18.125 4.91071 30;
    1033 18.125 4.71429 30; 1034 18.125 4.51786 30; 1035 18.125 4.32143 30;
    1036 18.125 4.125 30; 1037 18.125 3.92857 30; 1038 18.125 3.73214 30;
    1039 18.125 3.53571 30; 1040 18.125 3.33929 30; 1041 18.125 3.14286 30;
    1042 18.125 2.94643 30; 1043 18.125 2.75 30; 1044 18.125 2.55357 30;
    1045 18.125 2.35714 30; 1046 18.125 2.16071 30; 1047 18.125 1.96429 30;
    1048 18.125 1.76786 30; 1049 18.125 1.57143 30; 1050 18.125 1.375 30;
    1051 18.125 1.17857 30; 1052 18.125 0.982143 30; 1053 18.125 0.785714 30;
    1054 18.125 0.589286 30; 1055 18.125 0.392857 30; 1056 18.125 0.196429 30;
    1057 17.3051 3.37449 30; 1058 17.5541 2.40047 30; 1059 17.5588 1.23819 30;
    1060 17.5613 1.58503 30; 1061 17.8749 4.95632 30; 1062 17.843 1.27655 30;
    1063 17.8026 3.62761 30; 1064 17.1931 3.76298 30; 1065 17.8467 1.11855 30;
    1066 16.5999 4.77182 30; 1067 17.7021 3.82589 30; 1068 17.648 3.67867 30;
    1069 15.4743 5.27575 30; 1070 15.797 5.36928 30; 1071 16.215 2.67298 30;
    1072 17.9941 0.176415 30; 1073 16.5587 0.889489 30; 1074 17.5825 4.643 30;
    1075 17.873 2.35871 30; 1076 17.4796 0.554409 30; 1077 16.9979 1.17037 30;
    1078 16.3107 1.01736 30; 1079 17.7985 0.593651 30; 1080 15.852 3.91884 30;
    1081 17.7555 5.02621 30; 1082 17.7018 4.8591 30; 1083 17.955 2.17111 30;
    1084 17.2266 4.52868 30; 1085 17.7123 4.95234 30; 1086 17.8609 5.05462 30;
    1087 17.7184 5.24243 30; 1088 17.6392 0.375696 30; 1089 17.3874 4.64827 30;
    1090 16.8688 0.640322 30; 1091 16.9368 2.05028 30; 1092 16.972 1.60497 30;
    1093 16.9854 2.43048 30; 1094 17.9681 1.23688 30; 1095 18.0112 0.362942 30;
    1096 17.8681 0.781209 30; 1097 16.7814 1.14039 30; 1098 17.6547 4.42796 30;
    1099 17.2858 0.238766 30; 1100 17.9674 0.862606 30; 1101 16.8265 5.33377 30;
    1102 17.0281 5.2725 30; 1103 17.9499 4.37149 30; 1104 17.9876 4.18349 30;
    1105 17.2442 4.61006 30; 1106 16.8867 2.66447 30; 1107 17.9081 0.610853 30;
    1108 17.1064 4.57865 30; 1109 17.9629 1.43265 30; 1110 17.8335 4.86681 30;
    1111 17.6249 4.96035 30; 1112 16.638 5.36856 30; 1113 17.683 5.00432 30;
    1114 17.7363 4.82512 30; 1115 17.2063 0.683957 30; 1116 16.6247 0.505332 30;
    1117 17.9848 1.06622 30; 1118 17.9906 4.89704 30; 1119 17.6287 5.05487 30;
    1120 17.3379 4.56444 30; 1121 16.9494 0.777899 30; 1122 17.6605 4.77316 30;
    1123 17.7697 4.89233 30; 1124 17.3339 4.87795 30; 1125 17.5049 0.718121 30;
    1126 16.8276 4.33643 30; 1127 17.6365 0.276773 30; 1128 17.4612 0.931546 30;
    1129 16.9757 4.25495 30; 1130 17.5149 2.13698 30; 1131 17.6083 1.99929 30;
    1132 17.388 4.47804 30; 1133 15.9644 0.196379 30; 1134 16.929 4.5234 30;
    1135 17.2271 1.90948 30; 1136 16.9817 3.81757 30; 1137 16.7643 4.65186 30;
    1138 17.6916 3.43989 30; 1139 17.6576 3.98214 30; 1140 16.1519 4.70127 30;
    1141 17.2998 4.6741 30; 1142 17.4119 0.705189 30; 1143 17.8875 4.55239 30;
    1144 17.3967 2.89712 30; 1145 16.0308 1.185 30; 1146 17.3567 2.24509 30;
    1147 17.7292 4.65541 30; 1148 16.2494 5.17298 30; 1149 16.008 5.24809 30;
    1150 17.5988 4.1116 30; 1151 17.3545 2.55274 30; 1152 17.4954 4.15121 30;
    1153 15.8673 5.00861 30; 1154 17.4512 4.85582 30; 1155 17.8594 3.81005 30;
    1156 17.6923 4.08124 30; 1157 17.9413 5.2089 30; 1158 16.8584 0.940548 30;
    1159 16.5296 5.18729 30; 1160 17.8989 4.83952 30; 1161 17.8726 0.46495 30;
    1162 17.1659 2.61514 30; 1163 17.4974 0.277659 30; 1164 16.8162 5.21206 30;
    1165 17.5631 4.51483 30; 1166 16.1671 3.50859 30; 1167 16.6532 4.02058 30;
    1168 17.4051 3.97412 30; 1169 16.4254 5.32183 30; 1170 17.8731 3.14823 30;
    1171 15.7862 2.83094 30; 1172 16.8348 0.438313 30; 1173 17.8378 0.53466 30;
    1174 17.8826 0.252813 30; 1175 17.9302 4.71111 30; 1176 17.7556 4.45483 30;
    1177 17.4834 0.162536 30; 1178 17.4245 0.538571 30; 1179 17.7787 0.1826 30;
    1180 17.5796 5.19308 30; 1181 17.1325 4.70855 30; 1182 18.0169 0.716727 30;
    1183 16.571 2.70591 30; 1184 17.5851 0.548341 30; 1185 16.6694 4.41057 30;
    1186 16.909 4.98546 30; 1187 16.793 1.47255 30; 1188 17.0003 0.467415 30;
    1189 17.9095 5.35622 30; 1190 17.2083 5.31342 30; 1191 17.9233 1.66331 30;
    1192 17.2499 5.14541 30; 1193 17.9985 0.537353 30; 1194 17.4255 0.473141 30;
    1195 17.5256 0.380355 30; 1196 16.5436 3.1801 30; 1197 17.9906 5.06489 30;
    1198 16.8691 4.11112 30; 1199 17.8034 5.15716 30; 1200 17.0508 4.98479 30;
    1201 17.6148 5.35633 30; 1202 16.9775 0.60215 30; 1203 17.3631 0.527855 30;
    1204 17.2947 4.42903 30; 1205 17.1463 0.167878 30; 1206 17.6285 0.737876 30;
    1207 17.2505 4.18107 30; 1208 17.6521 4.33371 30; 1209 16.7527 2.32413 30;
    1210 17.2471 0.586784 30; 1211 17.2271 1.15521 30; 1212 17.249 4.29956 30;
    1213 17.1608 4.18364 30; 1214 17.0984 1.79179 30; 1215 15.819 0.369919 30;
    1216 17.0315 2.20013 30; 1217 17.4937 3.55238 30; 1218 16.5752 0.236481 30;
    1219 17.254 4.79799 30; 1220 17.7768 4.95871 30; 1221 17.6262 1.46447 30;
    1222 17.3803 5.13256 30; 1223 17.9126 2.87418 30; 1224 17.7821 0.977656 30;
    1225 16.6681 5.21576 30; 1226 17.4654 4.42302 30; 1227 17.3771 3.78715 30;
    1228 16.3781 1.45982 30; 1229 17.3952 1.46356 30; 1230 17.3581 0.431268 30;
    1231 17.9931 2.01555 30; 1232 17.1221 0.550569 30; 1233 17.3381 0.611173 30;
    1234 17.2785 0.399762 30; 1235 17.2657 1.35887 30; 1236 17.4223 5.29793 30;
    1237 15.3858 3.1559 30; 1238 17.0971 4.29199 30; 1239 16.7979 5.07559 30;
    1240 15.6031 2.35335 30; 1241 17.7648 2.63007 30; 1242 15.3854 4.53702 30;
    1243 17.7656 1.58828 30; 1244 16.9569 5.1455 30; 1245 17.1808 1.65842 30;
    1246 17.4536 1.06348 30; 1247 17.4841 0.480022 30; 1248 16.9892 3.4946 30;
    1249 16.7375 0.764799 30; 1250 17.926 0.706098 30; 1251 17.8336 0.678827 30;
    1252 17.9955 3.9762 30; 1253 16.312 4.06373 30; 1254 16.9612 1.33464 30;
    1255 17.1178 1.41153 30; 1256 17.4348 4.28028 30; 1257 17.5727 1.76554 30;
    1258 17.6623 4.55985 30; 1259 17.1131 1.23109 30; 1260 16.4197 4.49243 30;
    1261 16.7948 0.232922 30; 1262 17.3716 1.89108 30; 1263 17.318 0.681323 30;
    1264 16.74 4.89712 30; 1265 17.4988 1.92952 30; 1266 17.743 4.26669 30;
    1267 16.6359 3.65793 30; 1268 15.9408 4.39746 30; 1269 17.7214 0.823566 30;
    1270 17.532 3.80947 30; 1271 17.0415 1.04755 30; 1272 17.0892 0.906735 30;
    1273 17.3755 2.01431 30; 1274 17.0272 4.00328 30; 1275 17.307 4.24755 30;
    1276 17.3526 4.16674 30; 1277 15.6532 5.2838 30; 1278 17.1828 2.33136 30;
    1279 17.5556 3.93583 30; 1280 16.6035 1.30671 30; 1281 17.7428 0.423629 30;
    1282 17.585 4.9018 30; 1283 17.2043 4.35774 30; 1284 17.3623 4.36315 30;
    1285 17.733 1.17453 30; 1286 17.1968 4.01616 30; 1287 17.769 2.08528 30;
    1288 16.4626 4.97706 30; 1289 17.058 0.693832 30; 1290 16.9815 4.82393 30;
    1291 17.6934 5.10943 30; 1292 16.6537 5.01565 30; 1293 17.6473 4.88898 30;
    1294 16.3698 0.642748 30; 1295 17.5669 4.83072 30; 1296 17.2716 1.0175 30;
    1297 17.4431 0.814955 30; 1298 17.48 0.63691 30; 1299 17.6171 0.467112 30;
    1300 17.8268 1.40369 30; 1301 17.5515 0.476232 30; 1302 17.4721 4.70936 30;
    1303 16.9735 4.68826 30; 1304 17.4881 1.38513 30; 1305 17.966 3.56558 30;
    1306 17.4255 1.75409 30; 1307 17.0629 2.95232 30; 1308 17.541 0.792165 30;
    1309 16.5982 2.00709 30; 1310 17.0645 4.42929 30; 1311 17.2714 1.53617 30;
    1312 17.0269 0.265519 30; 1313 17.5531 4.32562 30; 1314 17.0951 4.84339 30;
    1315 17.6807 1.32037 30; 1316 17.5171 4.93321 30; 1317 17.7137 4.90546 30;
    1318 17.2978 0.896331 30; 1319 16.2686 0.416275 30; 1320 17.8467 3.98895 30;
    1321 17.8101 4.7516 30; 1322 17.3942 4.99443 30; 1323 17.179 0.421731 30;
    1324 17.6356 3.01129 30; 1325 17.6428 4.83592 30; 1326 17.6202 0.602648 30;
    1327 17.7016 0.673288 30; 1328 17.6608 4.93256 30; 1329 16.5391 1.69165 30;
    1330 17.5904 4.25329 30; 1331 16.4055 0.163955 30; 1332 17.3896 0.632387 30;
    1333 16.1577 1.84945 30; 1334 17.2018 4.91862 30; 1335 15.8054 1.5249 30;
    1336 17.49 5.0157 30; 1337 16.2178 0.234863 30; 1338 17.5339 0.555905 30;
    1339 17.3769 0.581041 30; 1340 16.8308 4.79184 30; 1341 17.7218 0.577219 30;
    1342 17.8767 1.8935 30; 1343 17.7286 3.93583 30; 1344 17.9892 3.77253 30;
    1345 17.1534 0.798599 30; 1346 17.8933 0.363469 30; 1347 17.0681 4.1592 30;
    1348 15.9956 2.33334 30; 1349 17.6712 0.52252 30; 1350 17.1388 5.08154 30;
    1351 17.7673 0.520775 30; 1352 17.3971 0.321733 30; 1353 16.7617 2.07227 30;
    1354 17.6404 0.141911 30; 1355 17.3891 4.76008 30; 1356 16.7875 1.81428 30;
    1357 17.0017 1.90213 30; 1358 17.4548 0.402086 30; 1359 17.3061 0.779396 30;
    1360 17.4181 0.596717 30; 1361 17.588 0.903982 30; 1362 17.2993 0.546105 30;
    1363 16.9489 4.39399 30; 1364 16.3971 2.23226 30; 1365 17.2948 4.98401 30;
    1366 17.5562 0.647746 30; 1367 17.5143 5.10428 30; 1368 17.5693 4.99561 30;
    1369 16.051 0.676398 30; 1370 15.5339 4.95406 30; 1371 17.3773 1.31502 30;
    1372 15.621 0.641172 30; 1373 17.8089 4.16444 30; 1374 17.7503 0.317016 30;
    1375 17.7307 1.81213 30; 1376 17.4809 4.59061 30; 1377 17.5957 3.25071 30;
    1378 17.3887 1.18603 30; 1379 17.1839 2.06417 30; 1380 17.5451 4.75382 30;
    1381 17.3063 4.08468 30; 1382 17.1645 4.43247 30; 1383 17.6887 2.24881 30;
    1384 17.6042 1.08169 30; 1385 17.4 1.62751 30; 1386 17.2915 1.73697 30;
    1387 17.922 3.35843 30; 1388 15.4101 1.06509 30; 1389 18.125 5.5 30.2;
    1390 18.125 5.5 30.4; 1391 18.125 5.5 30.6; 1392 18.125 5.5 30.8;
    1393 18.125 5.5 31; 1394 18.125 5.5 31.2; 1395 18.125 5.5 31.4;
    1396 18.125 5.5 31.6; 1397 18.125 5.5 31.8; 1398 18.125 5.5 32;
    1399 18.125 5.5 32.2; 1400 18.125 5.5 32.4; 1401 18.125 5.5 32.6;
    1402 18.125 5.5 32.8; 1403 18.125 5.5 33; 1404 18.125 5.30357 33.2;
    1405 18.125 5.10714 33.2; 1406 18.125 4.91071 33.2; 1407 18.125 4.71429 33.2;
    1408 18.125 4.51786 33.2; 1409 18.125 4.32143 33.2; 1410 18.125 4.125 33.2;
    1411 18.125 3.92857 33.2; 1412 18.125 3.73214 33.2; 1413 18.125 3.53571 33.2;
    1414 18.125 3.33929 33.2; 1415 18.125 3.14286 33.2; 1416 18.125 2.94643 33.2;
    1417 18.125 2.75 33.2; 1418 18.125 2.55357 33.2; 1419 18.125 2.35714 33.2;
    1420 18.125 2.16071 33.2; 1421 18.125 1.96429 33.2; 1422 18.125 1.76786 33.2;
    1423 18.125 1.57143 33.2; 1424 18.125 1.375 33.2; 1425 18.125 1.17857 33.2;
    1426 18.125 0.982143 33.2; 1427 18.125 0.785714 33.2;
    1428 18.125 0.589286 33.2; 1429 18.125 0.392857 33.2;
    1430 18.125 0.196429 33.2; 1431 18.125 0.196429 30.2;
    1432 18.125 0.196429 30.4; 1433 18.125 0.196429 30.6;
    1434 18.125 0.196429 30.8; 1435 18.125 0.196429 31; 1436 18.125 0.196429 31.2;
    1437 18.125 0.196429 31.4; 1438 18.125 0.196429 31.6;
    1439 18.125 0.196429 31.8; 1440 18.125 0.196429 32; 1441 18.125 0.196429 32.2;
    1442 18.125 0.196429 32.4; 1443 18.125 0.196429 32.6;
    1444 18.125 0.196429 32.8; 1445 18.125 0.196429 33; 1446 18.125 0.392857 30.2;
    1447 18.125 0.392857 30.4; 1448 18.125 0.392857 30.6;
    1449 18.125 0.392857 30.8; 1450 18.125 0.392857 31; 1451 18.125 0.392857 31.2;
    1452 18.125 0.392857 31.4; 1453 18.125 0.392857 31.6;
    1454 18.125 0.392857 31.8; 1455 18.125 0.392857 32; 1456 18.125 0.392857 32.2;
    1457 18.125 0.392857 32.4; 1458 18.125 0.392857 32.6;
    1459 18.125 0.392857 32.8; 1460 18.125 0.392857 33; 1461 18.125 0.589286 30.2;
    1462 18.125 0.589286 30.4; 1463 18.125 0.589286 30.6;
    1464 18.125 0.589286 30.8; 1465 18.125 0.589286 31; 1466 18.125 0.589286 31.2;
    1467 18.125 0.589286 31.4; 1468 18.125 0.589286 31.6;
    1469 18.125 0.589286 31.8; 1470 18.125 0.589286 32; 1471 18.125 0.589286 32.2;
    1472 18.125 0.589286 32.4; 1473 18.125 0.589286 32.6;
    1474 18.125 0.589286 32.8; 1475 18.125 0.589286 33; 1476 18.125 0.785714 30.2;
    1477 18.125 0.785714 30.4; 1478 18.125 0.785714 30.6;
    1479 18.125 0.785714 30.8; 1480 18.125 0.785714 31; 1481 18.125 0.785714 31.2;
    1482 18.125 0.785714 31.4; 1483 18.125 0.785714 31.6;
    1484 18.125 0.785714 31.8; 1485 18.125 0.785714 32; 1486 18.125 0.785714 32.2;
    1487 18.125 0.785714 32.4; 1488 18.125 0.785714 32.6;
    1489 18.125 0.785714 32.8; 1490 18.125 0.785714 33; 1491 18.125 0.982143 30.2;
    1492 18.125 0.982143 30.4; 1493 18.125 0.982143 30.6;
    1494 18.125 0.982143 30.8; 1495 18.125 0.982143 31; 1496 18.125 0.982143 31.2;
    1497 18.125 0.982143 31.4; 1498 18.125 0.982143 31.6;
    1499 18.125 0.982143 31.8; 1500 18.125 0.982143 32; 1501 18.125 0.982143 32.2;
    1502 18.125 0.982143 32.4; 1503 18.125 0.982143 32.6;
    1504 18.125 0.982143 32.8; 1505 18.125 0.982143 33; 1506 18.125 1.17857 30.2;
    1507 18.125 1.17857 30.4; 1508 18.125 1.17857 30.6; 1509 18.125 1.17857 30.8;
    1510 18.125 1.17857 31; 1511 18.125 1.17857 31.2; 1512 18.125 1.17857 31.4;
    1513 18.125 1.17857 31.6; 1514 18.125 1.17857 31.8; 1515 18.125 1.17857 32;
    1516 18.125 1.17857 32.2; 1517 18.125 1.17857 32.4; 1518 18.125 1.17857 32.6;
    1519 18.125 1.17857 32.8; 1520 18.125 1.17857 33; 1521 18.125 1.375 30.2;
    1522 18.125 1.375 30.4; 1523 18.125 1.375 30.6; 1524 18.125 1.375 30.8;
    1525 18.125 1.375 31; 1526 18.125 1.375 31.2; 1527 18.125 1.375 31.4;
    1528 18.125 1.375 31.6; 1529 18.125 1.375 31.8; 1530 18.125 1.375 32;
    1531 18.125 1.375 32.2; 1532 18.125 1.375 32.4; 1533 18.125 1.375 32.6;
    1534 18.125 1.375 32.8; 1535 18.125 1.375 33; 1536 18.125 1.57143 30.2;
    1537 18.125 1.57143 30.4; 1538 18.125 1.57143 30.6; 1539 18.125 1.57143 30.8;
    1540 18.125 1.57143 31; 1541 18.125 1.57143 31.2; 1542 18.125 1.57143 31.4;
    1543 18.125 1.57143 31.6; 1544 18.125 1.57143 31.8; 1545 18.125 1.57143 32;
    1546 18.125 1.57143 32.2; 1547 18.125 1.57143 32.4; 1548 18.125 1.57143 32.6;
    1549 18.125 1.57143 32.8; 1550 18.125 1.57143 33; 1551 18.125 1.76786 30.2;
    1552 18.125 1.76786 30.4; 1553 18.125 1.76786 30.6; 1554 18.125 1.76786 30.8;
    1555 18.125 1.76786 31; 1556 18.125 1.76786 31.2; 1557 18.125 1.76786 31.4;
    1558 18.125 1.76786 31.6; 1559 18.125 1.76786 31.8; 1560 18.125 1.76786 32;
    1561 18.125 1.76786 32.2; 1562 18.125 1.76786 32.4; 1563 18.125 1.76786 32.6;
    1564 18.125 1.76786 32.8; 1565 18.125 1.76786 33; 1566 18.125 1.96429 30.2;
    1567 18.125 1.96429 30.4; 1568 18.125 1.96429 30.6; 1569 18.125 1.96429 30.8;
    1570 18.125 1.96429 31; 1571 18.125 1.96429 31.2; 1572 18.125 1.96429 31.4;
    1573 18.125 1.96429 31.6; 1574 18.125 1.96429 31.8; 1575 18.125 1.96429 32;
    1576 18.125 1.96429 32.2; 1577 18.125 1.96429 32.4; 1578 18.125 1.96429 32.6;
    1579 18.125 1.96429 32.8; 1580 18.125 1.96429 33; 1581 18.125 2.16071 30.2;
    1582 18.125 2.16071 30.4; 1583 18.125 2.16071 30.6; 1584 18.125 2.16071 30.8;
    1585 18.125 2.16071 31; 1586 18.125 2.16071 31.2; 1587 18.125 2.16071 31.4;
    1588 18.125 2.16071 31.6; 1589 18.125 2.16071 31.8; 1590 18.125 2.16071 32;
    1591 18.125 2.16071 32.2; 1592 18.125 2.16071 32.4; 1593 18.125 2.16071 32.6;
    1594 18.125 2.16071 32.8; 1595 18.125 2.16071 33; 1596 18.125 2.35714 30.2;
    1597 18.125 2.35714 30.4; 1598 18.125 2.35714 30.6; 1599 18.125 2.35714 30.8;
    1600 18.125 2.35714 31; 1601 18.125 2.35714 31.2; 1602 18.125 2.35714 31.4;
    1603 18.125 2.35714 31.6; 1604 18.125 2.35714 31.8; 1605 18.125 2.35714 32;
    1606 18.125 2.35714 32.2; 1607 18.125 2.35714 32.4; 1608 18.125 2.35714 32.6;
    1609 18.125 2.35714 32.8; 1610 18.125 2.35714 33; 1611 18.125 2.55357 30.2;
    1612 18.125 2.55357 30.4; 1613 18.125 2.55357 30.6; 1614 18.125 2.55357 30.8;
    1615 18.125 2.55357 31; 1616 18.125 2.55357 31.2; 1617 18.125 2.55357 31.4;
    1618 18.125 2.55357 31.6; 1619 18.125 2.55357 31.8; 1620 18.125 2.55357 32;
    1621 18.125 2.55357 32.2; 1622 18.125 2.55357 32.4; 1623 18.125 2.55357 32.6;
    1624 18.125 2.55357 32.8; 1625 18.125 2.55357 33; 1626 18.125 2.75 30.2;
    1627 18.125 2.75 30.4; 1628 18.125 2.75 30.6; 1629 18.125 2.75 30.8;
    1630 18.125 2.75 31; 1631 18.125 2.75 31.2; 1632 18.125 2.75 31.4;
    1633 18.125 2.75 31.6; 1634 18.125 2.75 31.8; 1635 18.125 2.75 32;
    1636 18.125 2.75 32.2; 1637 18.125 2.75 32.4; 1638 18.125 2.75 32.6;
    1639 18.125 2.75 32.8; 1640 18.125 2.75 33; 1641 18.125 2.94643 30.2;
    1642 18.125 2.94643 30.4; 1643 18.125 2.94643 30.6; 1644 18.125 2.94643 30.8;
    1645 18.125 2.94643 31; 1646 18.125 2.94643 31.2; 1647 18.125 2.94643 31.4;
    1648 18.125 2.94643 31.6; 1649 18.125 2.94643 31.8; 1650 18.125 2.94643 32;
    1651 18.125 2.94643 32.2; 1652 18.125 2.94643 32.4; 1653 18.125 2.94643 32.6;
    1654 18.125 2.94643 32.8; 1655 18.125 2.94643 33; 1656 18.125 3.14286 30.2;
    1657 18.125 3.14286 30.4; 1658 18.125 3.14286 30.6; 1659 18.125 3.14286 30.8;
    1660 18.125 3.14286 31; 1661 18.125 3.14286 31.2; 1662 18.125 3.14286 31.4;
    1663 18.125 3.14286 31.6; 1664 18.125 3.14286 31.8; 1665 18.125 3.14286 32;
    1666 18.125 3.14286 32.2; 1667 18.125 3.14286 32.4; 1668 18.125 3.14286 32.6;
    1669 18.125 3.14286 32.8; 1670 18.125 3.14286 33; 1671 18.125 3.33929 30.2;
    1672 18.125 3.33929 30.4; 1673 18.125 3.33929 30.6; 1674 18.125 3.33929 30.8;
    1675 18.125 3.33929 31; 1676 18.125 3.33929 31.2; 1677 18.125 3.33929 31.4;
    1678 18.125 3.33929 31.6; 1679 18.125 3.33929 31.8; 1680 18.125 3.33929 32;
    1681 18.125 3.33929 32.2; 1682 18.125 3.33929 32.4; 1683 18.125 3.33929 32.6;
    1684 18.125 3.33929 32.8; 1685 18.125 3.33929 33; 1686 18.125 3.53571 30.2;
    1687 18.125 3.53571 30.4; 1688 18.125 3.53571 30.6; 1689 18.125 3.53571 30.8;
    1690 18.125 3.53571 31; 1691 18.125 3.53571 31.2; 1692 18.125 3.53571 31.4;
    1693 18.125 3.53571 31.6; 1694 18.125 3.53571 31.8; 1695 18.125 3.53571 32;
    1696 18.125 3.53571 32.2; 1697 18.125 3.53571 32.4; 1698 18.125 3.53571 32.6;
    1699 18.125 3.53571 32.8; 1700 18.125 3.53571 33; 1701 18.125 3.73214 30.2;
    1702 18.125 3.73214 30.4; 1703 18.125 3.73214 30.6; 1704 18.125 3.73214 30.8;
    1705 18.125 3.73214 31; 1706 18.125 3.73214 31.2; 1707 18.125 3.73214 31.4;
    1708 18.125 3.73214 31.6; 1709 18.125 3.73214 31.8; 1710 18.125 3.73214 32;
    1711 18.125 3.73214 32.2; 1712 18.125 3.73214 32.4; 1713 18.125 3.73214 32.6;
    1714 18.125 3.73214 32.8; 1715 18.125 3.73214 33; 1716 18.125 3.92857 30.2;
    1717 18.125 3.92857 30.4; 1718 18.125 3.92857 30.6; 1719 18.125 3.92857 30.8;
    1720 18.125 3.92857 31; 1721 18.125 3.92857 31.2; 1722 18.125 3.92857 31.4;
    1723 18.125 3.92857 31.6; 1724 18.125 3.92857 31.8; 1725 18.125 3.92857 32;
    1726 18.125 3.92857 32.2; 1727 18.125 3.92857 32.4; 1728 18.125 3.92857 32.6;
    1729 18.125 3.92857 32.8; 1730 18.125 3.92857 33; 1731 18.125 4.125 30.2;
    1732 18.125 4.125 30.4; 1733 18.125 4.125 30.6; 1734 18.125 4.125 30.8;
    1735 18.125 4.125 31; 1736 18.125 4.125 31.2; 1737 18.125 4.125 31.4;
    1738 18.125 4.125 31.6; 1739 18.125 4.125 31.8; 1740 18.125 4.125 32;
    1741 18.125 4.125 32.2; 1742 18.125 4.125 32.4; 1743 18.125 4.125 32.6;
    1744 18.125 4.125 32.8; 1745 18.125 4.125 33; 1746 18.125 4.32143 30.2;
    1747 18.125 4.32143 30.4; 1748 18.125 4.32143 30.6; 1749 18.125 4.32143 30.8;
    1750 18.125 4.32143 31; 1751 18.125 4.32143 31.2; 1752 18.125 4.32143 31.4;
    1753 18.125 4.32143 31.6; 1754 18.125 4.32143 31.8; 1755 18.125 4.32143 32;
    1756 18.125 4.32143 32.2; 1757 18.125 4.32143 32.4; 1758 18.125 4.32143 32.6;
    1759 18.125 4.32143 32.8; 1760 18.125 4.32143 33; 1761 18.125 4.51786 30.2;
    1762 18.125 4.51786 30.4; 1763 18.125 4.51786 30.6; 1764 18.125 4.51786 30.8;
    1765 18.125 4.51786 31; 1766 18.125 4.51786 31.2; 1767 18.125 4.51786 31.4;
    1768 18.125 4.51786 31.6; 1769 18.125 4.51786 31.8; 1770 18.125 4.51786 32;
    1771 18.125 4.51786 32.2; 1772 18.125 4.51786 32.4; 1773 18.125 4.51786 32.6;
    1774 18.125 4.51786 32.8; 1775 18.125 4.51786 33; 1776 18.125 4.71429 30.2;
    1777 18.125 4.71429 30.4; 1778 18.125 4.71429 30.6; 1779 18.125 4.71429 30.8;
    1780 18.125 4.71429 31; 1781 18.125 4.71429 31.2; 1782 18.125 4.71429 31.4;
    1783 18.125 4.71429 31.6; 1784 18.125 4.71429 31.8; 1785 18.125 4.71429 32;
    1786 18.125 4.71429 32.2; 1787 18.125 4.71429 32.4; 1788 18.125 4.71429 32.6;
    1789 18.125 4.71429 32.8; 1790 18.125 4.71429 33; 1791 18.125 4.91071 30.2;
    1792 18.125 4.91071 30.4; 1793 18.125 4.91071 30.6; 1794 18.125 4.91071 30.8;
    1795 18.125 4.91071 31; 1796 18.125 4.91071 31.2; 1797 18.125 4.91071 31.4;
    1798 18.125 4.91071 31.6; 1799 18.125 4.91071 31.8; 1800 18.125 4.91071 32;
    1801 18.125 4.91071 32.2; 1802 18.125 4.91071 32.4; 1803 18.125 4.91071 32.6;
    1804 18.125 4.91071 32.8; 1805 18.125 4.91071 33; 1806 18.125 5.10714 30.2;
    1807 18.125 5.10714 30.4; 1808 18.125 5.10714 30.6; 1809 18.125 5.10714 30.8;
    1810 18.125 5.10714 31; 1811 18.125 5.10714 31.2; 1812 18.125 5.10714 31.4;
    1813 18.125 5.10714 31.6; 1814 18.125 5.10714 31.8; 1815 18.125 5.10714 32;
    1816 18.125 5.10714 32.2; 1817 18.125 5.10714 32.4; 1818 18.125 5.10714 32.6;
    1819 18.125 5.10714 32.8; 1820 18.125 5.10714 33; 1821 18.125 5.30357 30.2;
    1822 18.125 5.30357 30.4; 1823 18.125 5.30357 30.6; 1824 18.125 5.30357 30.8;
    1825 18.125 5.30357 31; 1826 18.125 5.30357 31.2; 1827 18.125 5.30357 31.4;
    1828 18.125 5.30357 31.6; 1829 18.125 5.30357 31.8; 1830 18.125 5.30357 32;
    1831 18.125 5.30357 32.2; 1832 18.125 5.30357 32.4; 1833 18.125 5.30357 32.6;
    1834 18.125 5.30357 32.8; 1835 18.125 5.30357 33; 1836 14.925 0.196429 33.2;
    1837 14.925 0.392857 33.2; 1838 14.925 0.589286 33.2;
    1839 14.925 0.785714 33.2; 1840 14.925 0.982143 33.2; 1841 14.925 1.17857 33.2;
    1842 14.925 1.375 33.2; 1843 14.925 1.57143 33.2; 1844 14.925 1.76786 33.2;
    1845 14.925 1.96429 33.2; 1846 14.925 2.16071 33.2; 1847 14.925 2.35714 33.2;
    1848 14.925 2.55357 33.2; 1849 14.925 2.75 33.2; 1850 14.925 2.94643 33.2;
    1851 14.925 3.14286 33.2; 1852 14.925 3.33929 33.2; 1853 14.925 3.53571 33.2;
    1854 14.925 3.73214 33.2; 1855 14.925 3.92857 33.2; 1856 14.925 4.125 33.2;
    1857 14.925 4.32143 33.2; 1858 14.925 4.51786 33.2; 1859 14.925 4.71429 33.2;
    1860 14.925 4.91071 33.2; 1861 14.925 5.10714 33.2; 1862 14.925 5.30357 33.2;
    1863 15.125 5.5 33.2; 1864 15.325 5.5 33.2; 1865 15.525 5.5 33.2;
    1866 15.725 5.5 33.2; 1867 15.925 5.5 33.2; 1868 16.125 5.5 33.2;
    1869 16.325 5.5 33.2; 1870 16.525 5.5 33.2; 1871 16.725 5.5 33.2;
    1872 16.925 5.5 33.2; 1873 17.125 5.5 33.2; 1874 17.325 5.5 33.2;
    1875 17.525 5.5 33.2; 1876 17.725 5.5 33.2; 1877 17.925 5.5 33.2;
    1878 15.125 0.196429 33.2; 1879 15.325 0.196429 33.2;
    1880 15.525 0.196429 33.2; 1881 15.725 0.196429 33.2;
    1882 15.925 0.196429 33.2; 1883 16.125 0.196429 33.2;
    1884 16.325 0.196429 33.2; 1885 16.525 0.196429 33.2;
    1886 16.725 0.196429 33.2; 1887 16.925 0.196429 33.2;
    1888 17.125 0.196429 33.2; 1889 17.325 0.196429 33.2;
    1890 17.525 0.196429 33.2; 1891 17.725 0.196429 33.2;
    1892 17.925 0.196429 33.2; 1893 15.125 0.392857 33.2;
    1894 15.325 0.392857 33.2; 1895 15.525 0.392857 33.2;
    1896 15.725 0.392857 33.2; 1897 15.925 0.392857 33.2;
    1898 16.125 0.392857 33.2; 1899 16.325 0.392857 33.2;
    1900 16.525 0.392857 33.2; 1901 16.725 0.392857 33.2;
    1902 16.925 0.392857 33.2; 1903 17.125 0.392857 33.2;
    1904 17.325 0.392857 33.2; 1905 17.525 0.392857 33.2;
    1906 17.725 0.392857 33.2; 1907 17.925 0.392857 33.2;
    1908 15.125 0.589286 33.2; 1909 15.325 0.589286 33.2;
    1910 15.525 0.589286 33.2; 1911 15.725 0.589286 33.2;
    1912 15.925 0.589286 33.2; 1913 16.125 0.589286 33.2;
    1914 16.325 0.589286 33.2; 1915 16.525 0.589286 33.2;
    1916 16.725 0.589286 33.2; 1917 16.925 0.589286 33.2;
    1918 17.125 0.589286 33.2; 1919 17.325 0.589286 33.2;
    1920 17.525 0.589286 33.2; 1921 17.725 0.589286 33.2;
    1922 17.925 0.589286 33.2; 1923 15.125 0.785714 33.2;
    1924 15.325 0.785714 33.2; 1925 15.525 0.785714 33.2;
    1926 15.725 0.785714 33.2; 1927 15.925 0.785714 33.2;
    1928 16.125 0.785714 33.2; 1929 16.325 0.785714 33.2;
    1930 16.525 0.785714 33.2; 1931 16.725 0.785714 33.2;
    1932 16.925 0.785714 33.2; 1933 17.125 0.785714 33.2;
    1934 17.325 0.785714 33.2; 1935 17.525 0.785714 33.2;
    1936 17.725 0.785714 33.2; 1937 17.925 0.785714 33.2;
    1938 15.125 0.982143 33.2; 1939 15.325 0.982143 33.2;
    1940 15.525 0.982143 33.2; 1941 15.725 0.982143 33.2;
    1942 15.925 0.982143 33.2; 1943 16.125 0.982143 33.2;
    1944 16.325 0.982143 33.2; 1945 16.525 0.982143 33.2;
    1946 16.725 0.982143 33.2; 1947 16.925 0.982143 33.2;
    1948 17.125 0.982143 33.2; 1949 17.325 0.982143 33.2;
    1950 17.525 0.982143 33.2; 1951 17.725 0.982143 33.2;
    1952 17.925 0.982143 33.2; 1953 15.125 1.17857 33.2; 1954 15.325 1.17857 33.2;
    1955 15.525 1.17857 33.2; 1956 15.725 1.17857 33.2; 1957 15.925 1.17857 33.2;
    1958 16.125 1.17857 33.2; 1959 16.325 1.17857 33.2; 1960 16.525 1.17857 33.2;
    1961 16.725 1.17857 33.2; 1962 16.925 1.17857 33.2; 1963 17.125 1.17857 33.2;
    1964 17.325 1.17857 33.2; 1965 17.525 1.17857 33.2; 1966 17.725 1.17857 33.2;
    1967 17.925 1.17857 33.2; 1968 15.125 1.375 33.2; 1969 15.325 1.375 33.2;
    1970 15.525 1.375 33.2; 1971 15.725 1.375 33.2; 1972 15.925 1.375 33.2;
    1973 16.125 1.375 33.2; 1974 16.325 1.375 33.2; 1975 16.525 1.375 33.2;
    1976 16.725 1.375 33.2; 1977 16.925 1.375 33.2; 1978 17.125 1.375 33.2;
    1979 17.325 1.375 33.2; 1980 17.525 1.375 33.2; 1981 17.725 1.375 33.2;
    1982 17.925 1.375 33.2; 1983 15.125 1.57143 33.2; 1984 15.325 1.57143 33.2;
    1985 15.525 1.57143 33.2; 1986 15.725 1.57143 33.2; 1987 15.925 1.57143 33.2;
    1988 16.125 1.57143 33.2; 1989 16.325 1.57143 33.2; 1990 16.525 1.57143 33.2;
    1991 16.725 1.57143 33.2; 1992 16.925 1.57143 33.2; 1993 17.125 1.57143 33.2;
    1994 17.325 1.57143 33.2; 1995 17.525 1.57143 33.2; 1996 17.725 1.57143 33.2;
    1997 17.925 1.57143 33.2; 1998 15.125 1.76786 33.2; 1999 15.325 1.76786 33.2;
    2000 15.525 1.76786 33.2; 2001 15.725 1.76786 33.2; 2002 15.925 1.76786 33.2;
    2003 16.125 1.76786 33.2; 2004 16.325 1.76786 33.2; 2005 16.525 1.76786 33.2;
    2006 16.725 1.76786 33.2; 2007 16.925 1.76786 33.2; 2008 17.125 1.76786 33.2;
    2009 17.325 1.76786 33.2; 2010 17.525 1.76786 33.2; 2011 17.725 1.76786 33.2;
    2012 17.925 1.76786 33.2; 2013 15.125 1.96429 33.2; 2014 15.325 1.96429 33.2;
    2015 15.525 1.96429 33.2; 2016 15.725 1.96429 33.2; 2017 15.925 1.96429 33.2;
    2018 16.125 1.96429 33.2; 2019 16.325 1.96429 33.2; 2020 16.525 1.96429 33.2;
    2021 16.725 1.96429 33.2; 2022 16.925 1.96429 33.2; 2023 17.125 1.96429 33.2;
    2024 17.325 1.96429 33.2; 2025 17.525 1.96429 33.2; 2026 17.725 1.96429 33.2;
    2027 17.925 1.96429 33.2; 2028 15.125 2.16071 33.2; 2029 15.325 2.16071 33.2;
    2030 15.525 2.16071 33.2; 2031 15.725 2.16071 33.2; 2032 15.925 2.16071 33.2;
    2033 16.125 2.16071 33.2; 2034 16.325 2.16071 33.2; 2035 16.525 2.16071 33.2;
    2036 16.725 2.16071 33.2; 2037 16.925 2.16071 33.2; 2038 17.125 2.16071 33.2;
    2039 17.325 2.16071 33.2; 2040 17.525 2.16071 33.2; 2041 17.725 2.16071 33.2;
    2042 17.925 2.16071 33.2; 2043 15.125 2.35714 33.2; 2044 15.325 2.35714 33.2;
    2045 15.525 2.35714 33.2; 2046 15.725 2.35714 33.2; 2047 15.925 2.35714 33.2;
    2048 16.125 2.35714 33.2; 2049 16.325 2.35714 33.2; 2050 16.525 2.35714 33.2;
    2051 16.725 2.35714 33.2; 2052 16.925 2.35714 33.2; 2053 17.125 2.35714 33.2;
    2054 17.325 2.35714 33.2; 2055 17.525 2.35714 33.2; 2056 17.725 2.35714 33.2;
    2057 17.925 2.35714 33.2; 2058 15.125 2.55357 33.2; 2059 15.325 2.55357 33.2;
    2060 15.525 2.55357 33.2; 2061 15.725 2.55357 33.2; 2062 15.925 2.55357 33.2;
    2063 16.125 2.55357 33.2; 2064 16.325 2.55357 33.2; 2065 16.525 2.55357 33.2;
    2066 16.725 2.55357 33.2; 2067 16.925 2.55357 33.2; 2068 17.125 2.55357 33.2;
    2069 17.325 2.55357 33.2; 2070 17.525 2.55357 33.2; 2071 17.725 2.55357 33.2;
    2072 17.925 2.55357 33.2; 2073 15.125 2.75 33.2; 2074 15.325 2.75 33.2;
    2075 15.525 2.75 33.2; 2076 15.725 2.75 33.2; 2077 15.925 2.75 33.2;
    2078 16.125 2.75 33.2; 2079 16.325 2.75 33.2; 2080 16.525 2.75 33.2;
    2081 16.725 2.75 33.2; 2082 16.925 2.75 33.2; 2083 17.125 2.75 33.2;
    2084 17.325 2.75 33.2; 2085 17.525 2.75 33.2; 2086 17.725 2.75 33.2;
    2087 17.925 2.75 33.2; 2088 15.125 2.94643 33.2; 2089 15.325 2.94643 33.2;
    2090 15.525 2.94643 33.2; 2091 15.725 2.94643 33.2; 2092 15.925 2.94643 33.2;
    2093 16.125 2.94643 33.2; 2094 16.325 2.94643 33.2; 2095 16.525 2.94643 33.2;
    2096 16.725 2.94643 33.2; 2097 16.925 2.94643 33.2; 2098 17.125 2.94643 33.2;
    2099 17.325 2.94643 33.2; 2100 17.525 2.94643 33.2; 2101 17.725 2.94643 33.2;
    2102 17.925 2.94643 33.2; 2103 15.125 3.14286 33.2; 2104 15.325 3.14286 33.2;
    2105 15.525 3.14286 33.2; 2106 15.725 3.14286 33.2; 2107 15.925 3.14286 33.2;
    2108 16.125 3.14286 33.2; 2109 16.325 3.14286 33.2; 2110 16.525 3.14286 33.2;
    2111 16.725 3.14286 33.2; 2112 16.925 3.14286 33.2; 2113 17.125 3.14286 33.2;
    2114 17.325 3.14286 33.2; 2115 17.525 3.14286 33.2; 2116 17.725 3.14286 33.2;
    2117 17.925 3.14286 33.2; 2118 15.125 3.33929 33.2; 2119 15.325 3.33929 33.2;
    2120 15.525 3.33929 33.2; 2121 15.725 3.33929 33.2; 2122 15.925 3.33929 33.2;
    2123 16.125 3.33929 33.2; 2124 16.325 3.33929 33.2; 2125 16.525 3.33929 33.2;
    2126 16.725 3.33929 33.2; 2127 16.925 3.33929 33.2; 2128 17.125 3.33929 33.2;
    2129 17.325 3.33929 33.2; 2130 17.525 3.33929 33.2; 2131 17.725 3.33929 33.2;
    2132 17.925 3.33929 33.2; 2133 15.125 3.53571 33.2; 2134 15.325 3.53571 33.2;
    2135 15.525 3.53571 33.2; 2136 15.725 3.53571 33.2; 2137 15.925 3.53571 33.2;
    2138 16.125 3.53571 33.2; 2139 16.325 3.53571 33.2; 2140 16.525 3.53571 33.2;
    2141 16.725 3.53571 33.2; 2142 16.925 3.53571 33.2; 2143 17.125 3.53571 33.2;
    2144 17.325 3.53571 33.2; 2145 17.525 3.53571 33.2; 2146 17.725 3.53571 33.2;
    2147 17.925 3.53571 33.2; 2148 15.125 3.73214 33.2; 2149 15.325 3.73214 33.2;
    2150 15.525 3.73214 33.2; 2151 15.725 3.73214 33.2; 2152 15.925 3.73214 33.2;
    2153 16.125 3.73214 33.2; 2154 16.325 3.73214 33.2; 2155 16.525 3.73214 33.2;
    2156 16.725 3.73214 33.2; 2157 16.925 3.73214 33.2; 2158 17.125 3.73214 33.2;
    2159 17.325 3.73214 33.2; 2160 17.525 3.73214 33.2; 2161 17.725 3.73214 33.2;
    2162 17.925 3.73214 33.2; 2163 15.125 3.92857 33.2; 2164 15.325 3.92857 33.2;
    2165 15.525 3.92857 33.2; 2166 15.725 3.92857 33.2; 2167 15.925 3.92857 33.2;
    2168 16.125 3.92857 33.2; 2169 16.325 3.92857 33.2; 2170 16.525 3.92857 33.2;
    2171 16.725 3.92857 33.2; 2172 16.925 3.92857 33.2; 2173 17.125 3.92857 33.2;
    2174 17.325 3.92857 33.2; 2175 17.525 3.92857 33.2; 2176 17.725 3.92857 33.2;
    2177 17.925 3.92857 33.2; 2178 15.125 4.125 33.2; 2179 15.325 4.125 33.2;
    2180 15.525 4.125 33.2; 2181 15.725 4.125 33.2; 2182 15.925 4.125 33.2;
    2183 16.125 4.125 33.2; 2184 16.325 4.125 33.2; 2185 16.525 4.125 33.2;
    2186 16.725 4.125 33.2; 2187 16.925 4.125 33.2; 2188 17.125 4.125 33.2;
    2189 17.325 4.125 33.2; 2190 17.525 4.125 33.2; 2191 17.725 4.125 33.2;
    2192 17.925 4.125 33.2; 2193 15.125 4.32143 33.2; 2194 15.325 4.32143 33.2;
    2195 15.525 4.32143 33.2; 2196 15.725 4.32143 33.2; 2197 15.925 4.32143 33.2;
    2198 16.125 4.32143 33.2; 2199 16.325 4.32143 33.2; 2200 16.525 4.32143 33.2;
    2201 16.725 4.32143 33.2; 2202 16.925 4.32143 33.2; 2203 17.125 4.32143 33.2;
    2204 17.325 4.32143 33.2; 2205 17.525 4.32143 33.2; 2206 17.725 4.32143 33.2;
    2207 17.925 4.32143 33.2; 2208 15.125 4.51786 33.2; 2209 15.325 4.51786 33.2;
    2210 15.525 4.51786 33.2; 2211 15.725 4.51786 33.2; 2212 15.925 4.51786 33.2;
    2213 16.125 4.51786 33.2; 2214 16.325 4.51786 33.2; 2215 16.525 4.51786 33.2;
    2216 16.725 4.51786 33.2; 2217 16.925 4.51786 33.2; 2218 17.125 4.51786 33.2;
    2219 17.325 4.51786 33.2; 2220 17.525 4.51786 33.2; 2221 17.725 4.51786 33.2;
    2222 17.925 4.51786 33.2; 2223 15.125 4.71429 33.2; 2224 15.325 4.71429 33.2;
    2225 15.525 4.71429 33.2; 2226 15.725 4.71429 33.2; 2227 15.925 4.71429 33.2;
    2228 16.125 4.71429 33.2; 2229 16.325 4.71429 33.2; 2230 16.525 4.71429 33.2;
    2231 16.725 4.71429 33.2; 2232 16.925 4.71429 33.2; 2233 17.125 4.71429 33.2;
    2234 17.325 4.71429 33.2; 2235 17.525 4.71429 33.2; 2236 17.725 4.71429 33.2;
    2237 17.925 4.71429 33.2; 2238 15.125 4.91071 33.2; 2239 15.325 4.91071 33.2;
    2240 15.525 4.91071 33.2; 2241 15.725 4.91071 33.2; 2242 15.925 4.91071 33.2;
    2243 16.125 4.91071 33.2; 2244 16.325 4.91071 33.2; 2245 16.525 4.91071 33.2;
    2246 16.725 4.91071 33.2; 2247 16.925 4.91071 33.2; 2248 17.125 4.91071 33.2;
    2249 17.325 4.91071 33.2; 2250 17.525 4.91071 33.2; 2251 17.725 4.91071 33.2;
    2252 17.925 4.91071 33.2; 2253 15.125 5.10714 33.2; 2254 15.325 5.10714 33.2;
    2255 15.525 5.10714 33.2; 2256 15.725 5.10714 33.2; 2257 15.925 5.10714 33.2;
    2258 16.125 5.10714 33.2; 2259 16.325 5.10714 33.2; 2260 16.525 5.10714 33.2;
    2261 16.725 5.10714 33.2; 2262 16.925 5.10714 33.2; 2263 17.125 5.10714 33.2;
    2264 17.325 5.10714 33.2; 2265 17.525 5.10714 33.2; 2266 17.725 5.10714 33.2;
    2267 17.925 5.10714 33.2; 2268 15.125 5.30357 33.2; 2269 15.325 5.30357 33.2;
    2270 15.525 5.30357 33.2; 2271 15.725 5.30357 33.2; 2272 15.925 5.30357 33.2;
    2273 16.125 5.30357 33.2; 2274 16.325 5.30357 33.2; 2275 16.525 5.30357 33.2;
    2276 16.725 5.30357 33.2; 2277 16.925 5.30357 33.2; 2278 17.125 5.30357 33.2;
    2279 17.325 5.30357 33.2; 2280 17.525 5.30357 33.2; 2281 17.725 5.30357 33.2;
    2282 17.925 5.30357 33.2; 2283 14.925 7.25 30; 2284 15.1116 9 30;
    2285 15.2982 9 30; 2286 15.4848 9 30; 2287 15.6714 9 30; 2288 15.858 9 30;
    2289 16.0446 9 30; 2290 16.2313 9 30; 2291 16.4179 9 30; 2292 16.6045 9 30;
    2293 16.7911 9 30; 2294 16.9777 9 30; 2295 17.1643 9 30; 2296 17.3509 9 30;
    2297 18.125 8.80556 30; 2298 18.125 8.61111 30; 2299 18.125 8.41667 30;
    2300 18.125 8.22222 30; 2301 18.125 8.02778 30; 2302 18.125 7.83333 30;
    2303 18.125 7.63889 30; 2304 18.125 7.44444 30; 2305 18.125 7.25 30;
    2306 18.125 7.05556 30; 2307 18.125 6.86111 30; 2308 18.125 6.66667 30;
    2309 18.125 6.47222 30; 2310 18.125 6.27778 30; 2311 18.125 6.08333 30;
    2312 18.125 5.88889 30; 2313 18.125 5.69444 30; 2314 17.7748 8.41053 30;
    2315 16.4242 7.06328 30; 2316 16.9571 6.4992 30; 2317 15.9884 7.31256 30;
    2318 17.4895 8.36013 30; 2319 17.4388 6.13779 30; 2320 17.3047 8.85919 30;
    2321 17.8 8.34717 30; 2322 17.7672 8.27962 30; 2323 15.2786 7.13895 30;
    2324 15.5333 5.68447 30; 2325 17.0907 8.02965 30; 2326 17.1441 8.84047 30;
    2327 16.861 7.43857 30; 2328 17.3312 8.1831 30; 2329 17.9082 6.89156 30;
    2330 17.4534 8.78595 30; 2331 17.2521 7.62229 30; 2332 15.2681 6.053 30;
    2333 17.3126 8.67439 30; 2334 16.8804 6.26123 30; 2335 17.5881 6.03779 30;
    2336 17.6202 8.47612 30; 2337 17.2279 6.43726 30; 2338 17.1696 6.12785 30;
    2339 17.7085 8.3873 30; 2340 17.9565 8.65406 30; 2341 15.3854 8.29228 30;
    2342 17.4114 5.83853 30; 2343 16.9943 6.08509 30; 2344 16.8023 6.46843 30;
    2345 17.9885 7.34552 30; 2346 16.8102 8.77099 30; 2347 17.9062 6.30452 30;
    2348 17.9632 6.11499 30; 2349 17.2439 5.72594 30; 2350 16.9831 8.81273 30;
    2351 17.2002 7.82843 30; 2352 17.9104 6.49674 30; 2353 17.0156 5.66608 30;
    2354 16.5566 8.24684 30; 2355 15.5695 8.56443 30; 2356 16.7321 7.66656 30;
    2357 16.8768 6.12246 30; 2358 17.9583 6.68191 30; 2359 16.8274 5.6163 30;
    2360 17.3772 8.44552 30; 2361 15.6966 7.22948 30; 2362 17.3479 5.64039 30;
    2363 16.4889 8.08816 30; 2364 15.967 6.99979 30; 2365 17.2819 8.05266 30;
    2366 17.3439 5.93479 30; 2367 17.0392 8.27512 30; 2368 17.2098 8.00448 30;
    2369 16.3463 6.603 30; 2370 17.1 8.16128 30; 2371 15.9318 8.29993 30;
    2372 16.9662 7.78486 30; 2373 16.6861 8.15376 30; 2374 16.7635 7.17404 30;
    2375 15.4007 5.79885 30; 2376 17.4955 5.84214 30; 2377 17.0422 7.01722 30;
    2378 17.5382 8.50033 30; 2379 17.5146 6.79452 30; 2380 17.5054 8.54032 30;
    2381 16.6395 7.93752 30; 2382 16.7107 7.30172 30; 2383 16.8244 7.10026 30;
    2384 16.7931 6.90385 30; 2385 15.7822 8.77504 30; 2386 17.2486 8.1771 30;
    2387 15.9592 6.70152 30; 2388 17.0637 6.27506 30; 2389 17.3052 8.55169 30;
    2390 16.8148 7.84385 30; 2391 17.4101 7.5287 30; 2392 16.8985 8.24992 30;
    2393 16.6075 6.65404 30; 2394 16.2176 8.81304 30; 2395 16.2431 5.71772 30;
    2396 16.4492 5.97855 30; 2397 17.5814 7.73672 30; 2398 17.503 7.87347 30;
    2399 16.5692 7.47525 30; 2400 17.795 7.49206 30; 2401 16.7566 8.42959 30;
    2402 18.0309 7.64911 30; 2403 16.7123 5.72009 30; 2404 17.08 7.87712 30;
    2405 17.6028 7.115 30; 2406 17.6212 7.42763 30; 2407 16.4174 6.28098 30;
    2408 17.9841 8.49079 30; 2409 16.7613 5.82787 30; 2410 17.5114 7.35994 30;
    2411 16.9199 7.94297 30; 2412 17.2479 8.69314 30; 2413 17.8072 8.50475 30;
    2414 17.8652 7.36437 30; 2415 16.8811 7.01227 30; 2416 17.3303 8.36592 30;
    2417 17.5004 8.30842 30; 2418 17.5706 7.26168 30; 2419 18.0253 7.0127 30;
    2420 18.0037 7.54278 30; 2421 17.2732 8.64425 30; 2422 17.3618 6.0625 30;
    2423 17.6084 8.30171 30; 2424 17.703 7.66703 30; 2425 17.5762 8.41361 30;
    2426 16.4654 7.67014 30; 2427 16.9316 5.94967 30; 2428 17.9204 5.90839 30;
    2429 16.8595 6.01355 30; 2430 15.604 6.2342 30; 2431 16.5967 8.40294 30;
    2432 17.5994 6.25344 30; 2433 16.9451 8.36167 30; 2434 17.9701 7.14629 30;
    2435 17.5639 5.83199 30; 2436 17.1812 8.29729 30; 2437 17.3058 8.72477 30;
    2438 17.1272 7.50982 30; 2439 17.1635 6.61612 30; 2440 17.3748 8.66634 30;
    2441 17.4802 8.87928 30; 2442 17.0216 8.64574 30; 2443 17.4633 5.64369 30;
    2444 16.2031 8.28633 30; 2445 15.7283 7.66559 30; 2446 17.6628 8.59944 30;
    2447 17.2588 6.14375 30; 2448 17.0797 6.16188 30; 2449 17.719 6.39303 30;
    2450 15.7448 5.76557 30; 2451 15.3138 7.85223 30; 2452 16.9668 8.07227 30;
    2453 16.7148 6.11274 30; 2454 16.8061 8.00819 30; 2455 17.5989 5.96011 30;
    2456 17.69 8.23249 30; 2457 17.3633 8.76934 30; 2458 17.8994 7.97718 30;
    2459 16.536 7.16521 30; 2460 17.8168 6.08835 30; 2461 17.5057 8.72422 30;
    2462 17.8722 8.43445 30; 2463 17.1988 5.95751 30; 2464 17.7748 6.86548 30;
    2465 17.4218 8.56492 30; 2466 17.4756 8.23105 30; 2467 17.4484 6.06184 30;
    2468 17.3712 6.24123 30; 2469 16.7017 8.29047 30; 2470 17.3532 7.36902 30;
    2471 15.7748 8.14379 30; 2472 16.3896 8.28298 30; 2473 15.9221 6.39565 30;
    2474 17.2542 8.41784 30; 2475 17.5901 7.62506 30; 2476 17.3945 8.49762 30;
    2477 16.8066 8.2868 30; 2478 17.7915 8.71806 30; 2479 17.2013 6.80538 30;
    2480 17.5482 6.95325 30; 2481 17.5137 7.5643 30; 2482 17.6596 7.5705 30;
    2483 17.4138 5.74703 30; 2484 17.9145 8.761 30; 2485 17.2799 6.27411 30;
    2486 17.89 8.56724 30; 2487 17.54 6.34573 30; 2488 18.0012 8.35734 30;
    2489 17.3117 8.62027 30; 2490 17.6729 6.5508 30; 2491 15.6289 6.80705 30;
    2492 17.3294 7.16303 30; 2493 16.6185 7.30188 30; 2494 18.019 6.85253 30;
    2495 17.0006 8.17883 30; 2496 17.5193 6.05291 30; 2497 17.6628 6.82401 30;
    2498 16.6162 6.46934 30; 2499 16.5597 6.16755 30; 2500 15.9645 5.7045 30;
    2501 17.6467 5.9199 30; 2502 17.8223 5.71915 30; 2503 17.018 5.88861 30;
    2504 17.2997 5.85751 30; 2505 17.4654 7.23383 30; 2506 17.3423 6.14802 30;
    2507 17.3079 7.89047 30; 2508 17.4513 8.51961 30; 2509 16.0181 7.67192 30;
    2510 17.7146 8.46335 30; 2511 17.0968 7.36263 30; 2512 16.723 5.92845 30;
    2513 17.3888 5.99555 30; 2514 16.4187 8.73197 30; 2515 16.6745 6.31001 30;
    2516 17.7989 7.61268 30; 2517 16.6202 5.80643 30; 2518 16.5945 8.70813 30;
    2519 17.7382 8.33923 30; 2520 17.4467 7.08972 30; 2521 17.9029 7.62386 30;
    2522 17.1322 8.67484 30; 2523 17.1812 7.21649 30; 2524 16.9697 7.34825 30;
    2525 17.3617 6.9309 30; 2526 17.7391 8.09565 30; 2527 17.1731 8.55246 30;
    2528 17.6236 5.86672 30; 2529 17.2268 7.05937 30; 2530 17.808 8.85054 30;
    2531 17.2349 8.59167 30; 2532 17.853 7.04791 30; 2533 17.5678 7.50072 30;
    2534 17.5265 8.40127 30; 2535 17.7895 7.73276 30; 2536 17.8668 7.20765 30;
    2537 17.7555 7.24692 30; 2538 16.3127 7.4116 30; 2539 17.6088 6.12123 30;
    2540 17.4316 7.95315 30; 2541 16.6701 7.14031 30; 2542 17.6108 8.53573 30;
    2543 17.5826 8.61451 30; 2544 17.075 6.37755 30; 2545 17.5863 5.74422 30;
    2546 16.9925 6.60751 30; 2547 17.1403 5.8149 30; 2548 17.5825 8.24586 30;
    2549 17.6512 8.18309 30; 2550 16.6504 6.8531 30; 2551 17.716 5.82062 30;
    2552 17.3047 7.74899 30; 2553 17.6515 5.6916 30; 2554 17.5081 5.78114 30;
    2555 17.0877 6.00534 30; 2556 17.9251 6.9808 30; 2557 17.2076 8.65534 30;
    2558 17.4128 8.39081 30; 2559 16.1621 7.8287 30; 2560 17.8951 7.48163 30;
    2561 17.3477 8.10032 30; 2562 17.5182 6.14989 30; 2563 17.7002 6.09728 30;
    2564 17.4751 6.47539 30; 2565 16.1831 7.29889 30; 2566 17.0846 7.19538 30;
    2567 16.4833 5.70625 30; 2568 17.8213 7.55562 30; 2569 17.7969 6.21104 30;
    2570 17.9687 8.18081 30; 2571 16.272 6.0189 30; 2572 17.8644 7.55837 30;
    2573 17.392 7.64675 30; 2574 16.9047 7.64442 30; 2575 17.259 7.2714 30;
    2576 16.0172 8.69244 30; 2577 17.6319 8.37397 30; 2578 17.4906 8.5911 30;
    2579 17.6884 8.51008 30; 2580 17.388 6.68714 30; 2581 17.7583 7.41485 30;
    2582 17.5429 8.36109 30; 2583 17.7343 7.08446 30; 2584 17.487 8.44128 30;
    2585 17.684 7.33765 30; 2586 17.437 6.29205 30; 2587 17.5966 8.35756 30;
    2588 17.5071 8.04158 30; 2589 16.7866 6.28743 30; 2590 17.5523 5.97293 30;
    2591 17.651 7.88381 30; 2592 16.1942 6.3559 30; 2593 17.4951 7.64172 30;
    2594 17.5067 5.98073 30; 2595 16.8238 8.14284 30; 2596 16.4689 7.35969 30;
    2597 17.45 5.99033 30; 2598 17.6676 6.01873 30; 2599 17.5313 5.91274 30;
    2600 17.2134 7.3825 30; 2601 17.5783 5.91819 30; 2602 17.4461 7.43609 30;
    2603 16.8093 6.64579 30; 2604 16.8141 5.73174 30; 2605 17.1145 6.4867 30;
    2606 16.8858 8.58292 30; 2607 17.9541 7.77684 30; 2608 17.6729 6.17883 30;
    2609 17.8091 8.63716 30; 2610 17.2904 8.4922 30; 2611 17.8575 6.7922 30;
    2612 17.752 8.57109 30; 2613 17.5574 8.56554 30; 2614 17.4924 8.65782 30;
    2615 17.4035 8.32521 30; 2616 17.0161 7.559 30; 2617 17.4034 7.29451 30;
    2618 17.4281 5.92439 30; 2619 17.7557 6.69079 30; 2620 17.7064 8.29253 30;
    2621 16.66 5.6196 30; 2622 17.4788 5.91776 30; 2623 17.3083 6.55226 30;
    2624 17.2929 7.47711 30; 2625 17.6983 6.28992 30; 2626 17.8072 8.20576 30;
    2627 17.3647 8.56891 30; 2628 15.8994 6.14904 30; 2629 15.6539 5.98634 30;
    2630 17.4387 7.78517 30; 2631 17.4238 8.62715 30; 2632 17.5469 8.45354 30;
    2633 17.35 6.38659 30; 2634 17.4989 8.15119 30; 2635 17.4733 8.47749 30;
    2636 17.3297 8.27451 30; 2637 16.3287 7.97076 30; 2638 17.2816 6.01699 30;
    2639 17.7547 5.94555 30; 2640 17.7417 7.56475 30; 2641 16.8035 7.28766 30;
    2642 17.6635 6.96976 30; 2643 16.0526 6.04753 30; 2644 16.6899 8.55159 30;
    2645 17.019 6.7277 30; 2646 16.2617 8.54396 30; 2647 16.7105 7.48922 30;
    2648 17.6674 8.3361 30; 2649 17.6728 8.6801 30; 2650 17.6987 7.49117 30;
    2651 17.6163 8.78752 30; 2652 16.8572 8.43735 30; 2653 17.174 6.29564 30;
    2654 17.0875 7.69504 30; 2655 17.5802 8.66551 30; 2656 16.9717 6.24727 30;
    2657 17.1853 8.11774 30; 2658 17.8795 8.32965 30; 2659 16.9198 6.8142 30;
    2660 16.9816 6.38953 30; 2661 16.448 8.44982 30; 2662 16.8514 5.87555 30;
    2663 17.0343 8.43956 30; 2664 17.2671 8.7633 30; 2665 16.9246 7.20019 30;
    2666 16.9398 5.77586 30; 2667 17.1964 8.74816 30; 2668 16.7788 5.98962 30;
    2669 16.8909 6.37385 30; 2670 16.3516 6.8855 30; 2671 17.7904 6.96097 30;
    2672 17.1095 8.50341 30; 2673 16.6803 7.01013 30; 2674 17.642 8.43062 30;
    2675 16.6004 5.96573 30; 2676 18.125 9 30.2; 2677 18.125 9 30.4;
    2678 18.125 9 30.6; 2679 18.125 9 30.8; 2680 18.125 9 31; 2681 18.125 9 31.2;
    2682 18.125 9 31.4; 2683 18.125 9 31.6; 2684 18.125 9 31.8; 2685 18.125 9 32;
    2686 18.125 9 32.2; 2687 18.125 9 32.4; 2688 18.125 9 32.6; 2689 18.125 9 32.8;
    2690 18.125 9 33; 2691 18.125 8.80556 33.2; 2692 18.125 8.61111 33.2;
    2693 18.125 8.41667 33.2; 2694 18.125 8.22222 33.2; 2695 18.125 8.02778 33.2;
    2696 18.125 7.83333 33.2; 2697 18.125 7.63889 33.2; 2698 18.125 7.44444 33.2;
    2699 18.125 7.25 33.2; 2700 18.125 7.05556 33.2; 2701 18.125 6.86111 33.2;
    2702 18.125 6.66667 33.2; 2703 18.125 6.47222 33.2; 2704 18.125 6.27778 33.2;
    2705 18.125 6.08333 33.2; 2706 18.125 5.88889 33.2; 2707 18.125 5.69444 33.2;
    2708 18.125 5.69444 30.2; 2709 18.125 5.69444 30.4; 2710 18.125 5.69444 30.6;
    2711 18.125 5.69444 30.8; 2712 18.125 5.69444 31; 2713 18.125 5.69444 31.2;
    2714 18.125 5.69444 31.4; 2715 18.125 5.69444 31.6; 2716 18.125 5.69444 31.8;
    2717 18.125 5.69444 32; 2718 18.125 5.69444 32.2; 2719 18.125 5.69444 32.4;
    2720 18.125 5.69444 32.6; 2721 18.125 5.69444 32.8; 2722 18.125 5.69444 33;
    2723 18.125 5.88889 30.2; 2724 18.125 5.88889 30.4; 2725 18.125 5.88889 30.6;
    2726 18.125 5.88889 30.8; 2727 18.125 5.88889 31; 2728 18.125 5.88889 31.2;
    2729 18.125 5.88889 31.4; 2730 18.125 5.88889 31.6; 2731 18.125 5.88889 31.8;
    2732 18.125 5.88889 32; 2733 18.125 5.88889 32.2; 2734 18.125 5.88889 32.4;
    2735 18.125 5.88889 32.6; 2736 18.125 5.88889 32.8; 2737 18.125 5.88889 33;
    2738 18.125 6.08333 30.2; 2739 18.125 6.08333 30.4; 2740 18.125 6.08333 30.6;
    2741 18.125 6.08333 30.8; 2742 18.125 6.08333 31; 2743 18.125 6.08333 31.2;
    2744 18.125 6.08333 31.4; 2745 18.125 6.08333 31.6; 2746 18.125 6.08333 31.8;
    2747 18.125 6.08333 32; 2748 18.125 6.08333 32.2; 2749 18.125 6.08333 32.4;
    2750 18.125 6.08333 32.6; 2751 18.125 6.08333 32.8; 2752 18.125 6.08333 33;
    2753 18.125 6.27778 30.2; 2754 18.125 6.27778 30.4; 2755 18.125 6.27778 30.6;
    2756 18.125 6.27778 30.8; 2757 18.125 6.27778 31; 2758 18.125 6.27778 31.2;
    2759 18.125 6.27778 31.4; 2760 18.125 6.27778 31.6; 2761 18.125 6.27778 31.8;
    2762 18.125 6.27778 32; 2763 18.125 6.27778 32.2; 2764 18.125 6.27778 32.4;
    2765 18.125 6.27778 32.6; 2766 18.125 6.27778 32.8; 2767 18.125 6.27778 33;
    2768 18.125 6.47222 30.2; 2769 18.125 6.47222 30.4; 2770 18.125 6.47222 30.6;
    2771 18.125 6.47222 30.8; 2772 18.125 6.47222 31; 2773 18.125 6.47222 31.2;
    2774 18.125 6.47222 31.4; 2775 18.125 6.47222 31.6; 2776 18.125 6.47222 31.8;
    2777 18.125 6.47222 32; 2778 18.125 6.47222 32.2; 2779 18.125 6.47222 32.4;
    2780 18.125 6.47222 32.6; 2781 18.125 6.47222 32.8; 2782 18.125 6.47222 33;
    2783 18.125 6.66667 30.2; 2784 18.125 6.66667 30.4; 2785 18.125 6.66667 30.6;
    2786 18.125 6.66667 30.8; 2787 18.125 6.66667 31; 2788 18.125 6.66667 31.2;
    2789 18.125 6.66667 31.4; 2790 18.125 6.66667 31.6; 2791 18.125 6.66667 31.8;
    2792 18.125 6.66667 32; 2793 18.125 6.66667 32.2; 2794 18.125 6.66667 32.4;
    2795 18.125 6.66667 32.6; 2796 18.125 6.66667 32.8; 2797 18.125 6.66667 33;
    2798 18.125 6.86111 30.2; 2799 18.125 6.86111 30.4; 2800 18.125 6.86111 30.6;
    2801 18.125 6.86111 30.8; 2802 18.125 6.86111 31; 2803 18.125 6.86111 31.2;
    2804 18.125 6.86111 31.4; 2805 18.125 6.86111 31.6; 2806 18.125 6.86111 31.8;
    2807 18.125 6.86111 32; 2808 18.125 6.86111 32.2; 2809 18.125 6.86111 32.4;
    2810 18.125 6.86111 32.6; 2811 18.125 6.86111 32.8; 2812 18.125 6.86111 33;
    2813 18.125 7.05556 30.2; 2814 18.125 7.05556 30.4; 2815 18.125 7.05556 30.6;
    2816 18.125 7.05556 30.8; 2817 18.125 7.05556 31; 2818 18.125 7.05556 31.2;
    2819 18.125 7.05556 31.4; 2820 18.125 7.05556 31.6; 2821 18.125 7.05556 31.8;
    2822 18.125 7.05556 32; 2823 18.125 7.05556 32.2; 2824 18.125 7.05556 32.4;
    2825 18.125 7.05556 32.6; 2826 18.125 7.05556 32.8; 2827 18.125 7.05556 33;
    2828 18.125 7.25 30.2; 2829 18.125 7.25 30.4; 2830 18.125 7.25 30.6;
    2831 18.125 7.25 30.8; 2832 18.125 7.25 31; 2833 18.125 7.25 31.2;
    2834 18.125 7.25 31.4; 2835 18.125 7.25 31.6; 2836 18.125 7.25 31.8;
    2837 18.125 7.25 32; 2838 18.125 7.25 32.2; 2839 18.125 7.25 32.4;
    2840 18.125 7.25 32.6; 2841 18.125 7.25 32.8; 2842 18.125 7.25 33;
    2843 18.125 7.44444 30.2; 2844 18.125 7.44444 30.4; 2845 18.125 7.44444 30.6;
    2846 18.125 7.44444 30.8; 2847 18.125 7.44444 31; 2848 18.125 7.44444 31.2;
    2849 18.125 7.44444 31.4; 2850 18.125 7.44444 31.6; 2851 18.125 7.44444 31.8;
    2852 18.125 7.44444 32; 2853 18.125 7.44444 32.2; 2854 18.125 7.44444 32.4;
    2855 18.125 7.44444 32.6; 2856 18.125 7.44444 32.8; 2857 18.125 7.44444 33;
    2858 18.125 7.63889 30.2; 2859 18.125 7.63889 30.4; 2860 18.125 7.63889 30.6;
    2861 18.125 7.63889 30.8; 2862 18.125 7.63889 31; 2863 18.125 7.63889 31.2;
    2864 18.125 7.63889 31.4; 2865 18.125 7.63889 31.6; 2866 18.125 7.63889 31.8;
    2867 18.125 7.63889 32; 2868 18.125 7.63889 32.2; 2869 18.125 7.63889 32.4;
    2870 18.125 7.63889 32.6; 2871 18.125 7.63889 32.8; 2872 18.125 7.63889 33;
    2873 18.125 7.83333 30.2; 2874 18.125 7.83333 30.4; 2875 18.125 7.83333 30.6;
    2876 18.125 7.83333 30.8; 2877 18.125 7.83333 31; 2878 18.125 7.83333 31.2;
    2879 18.125 7.83333 31.4; 2880 18.125 7.83333 31.6; 2881 18.125 7.83333 31.8;
    2882 18.125 7.83333 32; 2883 18.125 7.83333 32.2; 2884 18.125 7.83333 32.4;
    2885 18.125 7.83333 32.6; 2886 18.125 7.83333 32.8; 2887 18.125 7.83333 33;
    2888 18.125 8.02778 30.2; 2889 18.125 8.02778 30.4; 2890 18.125 8.02778 30.6;
    2891 18.125 8.02778 30.8; 2892 18.125 8.02778 31; 2893 18.125 8.02778 31.2;
    2894 18.125 8.02778 31.4; 2895 18.125 8.02778 31.6; 2896 18.125 8.02778 31.8;
    2897 18.125 8.02778 32; 2898 18.125 8.02778 32.2; 2899 18.125 8.02778 32.4;
    2900 18.125 8.02778 32.6; 2901 18.125 8.02778 32.8; 2902 18.125 8.02778 33;
    2903 18.125 8.22222 30.2; 2904 18.125 8.22222 30.4; 2905 18.125 8.22222 30.6;
    2906 18.125 8.22222 30.8; 2907 18.125 8.22222 31; 2908 18.125 8.22222 31.2;
    2909 18.125 8.22222 31.4; 2910 18.125 8.22222 31.6; 2911 18.125 8.22222 31.8;
    2912 18.125 8.22222 32; 2913 18.125 8.22222 32.2; 2914 18.125 8.22222 32.4;
    2915 18.125 8.22222 32.6; 2916 18.125 8.22222 32.8; 2917 18.125 8.22222 33;
    2918 18.125 8.41667 30.2; 2919 18.125 8.41667 30.4; 2920 18.125 8.41667 30.6;
    2921 18.125 8.41667 30.8; 2922 18.125 8.41667 31; 2923 18.125 8.41667 31.2;
    2924 18.125 8.41667 31.4; 2925 18.125 8.41667 31.6; 2926 18.125 8.41667 31.8;
    2927 18.125 8.41667 32; 2928 18.125 8.41667 32.2; 2929 18.125 8.41667 32.4;
    2930 18.125 8.41667 32.6; 2931 18.125 8.41667 32.8; 2932 18.125 8.41667 33;
    2933 18.125 8.61111 30.2; 2934 18.125 8.61111 30.4; 2935 18.125 8.61111 30.6;
    2936 18.125 8.61111 30.8; 2937 18.125 8.61111 31; 2938 18.125 8.61111 31.2;
    2939 18.125 8.61111 31.4; 2940 18.125 8.61111 31.6; 2941 18.125 8.61111 31.8;
    2942 18.125 8.61111 32; 2943 18.125 8.61111 32.2; 2944 18.125 8.61111 32.4;
    2945 18.125 8.61111 32.6; 2946 18.125 8.61111 32.8; 2947 18.125 8.61111 33;
    2948 18.125 8.80556 30.2; 2949 18.125 8.80556 30.4; 2950 18.125 8.80556 30.6;
    2951 18.125 8.80556 30.8; 2952 18.125 8.80556 31; 2953 18.125 8.80556 31.2;
    2954 18.125 8.80556 31.4; 2955 18.125 8.80556 31.6; 2956 18.125 8.80556 31.8;
    2957 18.125 8.80556 32; 2958 18.125 8.80556 32.2; 2959 18.125 8.80556 32.4;
    2960 18.125 8.80556 32.6; 2961 18.125 8.80556 32.8; 2962 18.125 8.80556 33;
    2963 14.925 5.69444 33.2; 2964 14.925 5.88889 33.2; 2965 14.925 6.08333 33.2;
    2966 14.925 6.27778 33.2; 2967 14.925 6.47222 33.2; 2968 14.925 6.66667 33.2;
    2969 14.925 6.86111 33.2; 2970 14.925 7.05556 33.2; 2971 14.925 7.25 33.2;
    2972 14.925 7.44444 33.2; 2973 14.925 7.63889 33.2; 2974 14.925 7.83333 33.2;
    2975 14.925 8.02778 33.2; 2976 14.925 8.22222 33.2; 2977 14.925 8.41667 33.2;
    2978 14.925 8.61111 33.2; 2979 14.925 8.80556 33.2; 2980 15.125 9 33.2;
    2981 15.325 9 33.2; 2982 15.525 9 33.2; 2983 15.725 9 33.2; 2984 15.925 9 33.2;
    2985 16.125 9 33.2; 2986 16.325 9 33.2; 2987 16.525 9 33.2; 2988 16.725 9 33.2;
    2989 16.925 9 33.2; 2990 17.125 9 33.2; 2991 17.325 9 33.2; 2992 17.525 9 33.2;
    2993 17.725 9 33.2; 2994 17.925 9 33.2; 2995 15.125 5.69444 33.2;
    2996 15.325 5.69444 33.2; 2997 15.525 5.69444 33.2; 2998 15.725 5.69444 33.2;
    2999 15.925 5.69444 33.2; 3000 16.125 5.69444 33.2; 3001 16.325 5.69444 33.2;
    3002 16.525 5.69444 33.2; 3003 16.725 5.69444 33.2; 3004 16.925 5.69444 33.2;
    3005 17.125 5.69444 33.2; 3006 17.325 5.69444 33.2; 3007 17.525 5.69444 33.2;
    3008 17.725 5.69444 33.2; 3009 17.925 5.69444 33.2; 3010 15.125 5.88889 33.2;
    3011 15.325 5.88889 33.2; 3012 15.525 5.88889 33.2; 3013 15.725 5.88889 33.2;
    3014 15.925 5.88889 33.2; 3015 16.125 5.88889 33.2; 3016 16.325 5.88889 33.2;
    3017 16.525 5.88889 33.2; 3018 16.725 5.88889 33.2; 3019 16.925 5.88889 33.2;
    3020 17.125 5.88889 33.2; 3021 17.325 5.88889 33.2; 3022 17.525 5.88889 33.2;
    3023 17.725 5.88889 33.2; 3024 17.925 5.88889 33.2; 3025 15.125 6.08333 33.2;
    3026 15.325 6.08333 33.2; 3027 15.525 6.08333 33.2; 3028 15.725 6.08333 33.2;
    3029 15.925 6.08333 33.2; 3030 16.125 6.08333 33.2; 3031 16.325 6.08333 33.2;
    3032 16.525 6.08333 33.2; 3033 16.725 6.08333 33.2; 3034 16.925 6.08333 33.2;
    3035 17.125 6.08333 33.2; 3036 17.325 6.08333 33.2; 3037 17.525 6.08333 33.2;
    3038 17.725 6.08333 33.2; 3039 17.925 6.08333 33.2; 3040 15.125 6.27778 33.2;
    3041 15.325 6.27778 33.2; 3042 15.525 6.27778 33.2; 3043 15.725 6.27778 33.2;
    3044 15.925 6.27778 33.2; 3045 16.125 6.27778 33.2; 3046 16.325 6.27778 33.2;
    3047 16.525 6.27778 33.2; 3048 16.725 6.27778 33.2; 3049 16.925 6.27778 33.2;
    3050 17.125 6.27778 33.2; 3051 17.325 6.27778 33.2; 3052 17.525 6.27778 33.2;
    3053 17.725 6.27778 33.2; 3054 17.925 6.27778 33.2; 3055 15.125 6.47222 33.2;
    3056 15.325 6.47222 33.2; 3057 15.525 6.47222 33.2; 3058 15.725 6.47222 33.2;
    3059 15.925 6.47222 33.2; 3060 16.125 6.47222 33.2; 3061 16.325 6.47222 33.2;
    3062 16.525 6.47222 33.2; 3063 16.725 6.47222 33.2; 3064 16.925 6.47222 33.2;
    3065 17.125 6.47222 33.2; 3066 17.325 6.47222 33.2; 3067 17.525 6.47222 33.2;
    3068 17.725 6.47222 33.2; 3069 17.925 6.47222 33.2; 3070 15.125 6.66667 33.2;
    3071 15.325 6.66667 33.2; 3072 15.525 6.66667 33.2; 3073 15.725 6.66667 33.2;
    3074 15.925 6.66667 33.2; 3075 16.125 6.66667 33.2; 3076 16.325 6.66667 33.2;
    3077 16.525 6.66667 33.2; 3078 16.725 6.66667 33.2; 3079 16.925 6.66667 33.2;
    3080 17.125 6.66667 33.2; 3081 17.325 6.66667 33.2; 3082 17.525 6.66667 33.2;
    3083 17.725 6.66667 33.2; 3084 17.925 6.66667 33.2; 3085 15.125 6.86111 33.2;
    3086 15.325 6.86111 33.2; 3087 15.525 6.86111 33.2; 3088 15.725 6.86111 33.2;
    3089 15.925 6.86111 33.2; 3090 16.125 6.86111 33.2; 3091 16.325 6.86111 33.2;
    3092 16.525 6.86111 33.2; 3093 16.725 6.86111 33.2; 3094 16.925 6.86111 33.2;
    3095 17.125 6.86111 33.2; 3096 17.325 6.86111 33.2; 3097 17.525 6.86111 33.2;
    3098 17.725 6.86111 33.2; 3099 17.925 6.86111 33.2; 3100 15.125 7.05556 33.2;
    3101 15.325 7.05556 33.2; 3102 15.525 7.05556 33.2; 3103 15.725 7.05556 33.2;
    3104 15.925 7.05556 33.2; 3105 16.125 7.05556 33.2; 3106 16.325 7.05556 33.2;
    3107 16.525 7.05556 33.2; 3108 16.725 7.05556 33.2; 3109 16.925 7.05556 33.2;
    3110 17.125 7.05556 33.2; 3111 17.325 7.05556 33.2; 3112 17.525 7.05556 33.2;
    3113 17.725 7.05556 33.2; 3114 17.925 7.05556 33.2; 3115 15.125 7.25 33.2;
    3116 15.325 7.25 33.2; 3117 15.525 7.25 33.2; 3118 15.725 7.25 33.2;
    3119 15.925 7.25 33.2; 3120 16.125 7.25 33.2; 3121 16.325 7.25 33.2;
    3122 16.525 7.25 33.2; 3123 16.725 7.25 33.2; 3124 16.925 7.25 33.2;
    3125 17.125 7.25 33.2; 3126 17.325 7.25 33.2; 3127 17.525 7.25 33.2;
    3128 17.725 7.25 33.2; 3129 17.925 7.25 33.2; 3130 15.125 7.44444 33.2;
    3131 15.325 7.44444 33.2; 3132 15.525 7.44444 33.2; 3133 15.725 7.44444 33.2;
    3134 15.925 7.44444 33.2; 3135 16.125 7.44444 33.2; 3136 16.325 7.44444 33.2;
    3137 16.525 7.44444 33.2; 3138 16.725 7.44444 33.2; 3139 16.925 7.44444 33.2;
    3140 17.125 7.44444 33.2; 3141 17.325 7.44444 33.2; 3142 17.525 7.44444 33.2;
    3143 17.725 7.44444 33.2; 3144 17.925 7.44444 33.2; 3145 15.125 7.63889 33.2;
    3146 15.325 7.63889 33.2; 3147 15.525 7.63889 33.2; 3148 15.725 7.63889 33.2;
    3149 15.925 7.63889 33.2; 3150 16.125 7.63889 33.2; 3151 16.325 7.63889 33.2;
    3152 16.525 7.63889 33.2; 3153 16.725 7.63889 33.2; 3154 16.925 7.63889 33.2;
    3155 17.125 7.63889 33.2; 3156 17.325 7.63889 33.2; 3157 17.525 7.63889 33.2;
    3158 17.725 7.63889 33.2; 3159 17.925 7.63889 33.2; 3160 15.125 7.83333 33.2;
    3161 15.325 7.83333 33.2; 3162 15.525 7.83333 33.2; 3163 15.725 7.83333 33.2;
    3164 15.925 7.83333 33.2; 3165 16.125 7.83333 33.2; 3166 16.325 7.83333 33.2;
    3167 16.525 7.83333 33.2; 3168 16.725 7.83333 33.2; 3169 16.925 7.83333 33.2;
    3170 17.125 7.83333 33.2; 3171 17.325 7.83333 33.2; 3172 17.525 7.83333 33.2;
    3173 17.725 7.83333 33.2; 3174 17.925 7.83333 33.2; 3175 15.125 8.02778 33.2;
    3176 15.325 8.02778 33.2; 3177 15.525 8.02778 33.2; 3178 15.725 8.02778 33.2;
    3179 15.925 8.02778 33.2; 3180 16.125 8.02778 33.2; 3181 16.325 8.02778 33.2;
    3182 16.525 8.02778 33.2; 3183 16.725 8.02778 33.2; 3184 16.925 8.02778 33.2;
    3185 17.125 8.02778 33.2; 3186 17.325 8.02778 33.2; 3187 17.525 8.02778 33.2;
    3188 17.725 8.02778 33.2; 3189 17.925 8.02778 33.2; 3190 15.125 8.22222 33.2;
    3191 15.325 8.22222 33.2; 3192 15.525 8.22222 33.2; 3193 15.725 8.22222 33.2;
    3194 15.925 8.22222 33.2; 3195 16.125 8.22222 33.2; 3196 16.325 8.22222 33.2;
    3197 16.525 8.22222 33.2; 3198 16.725 8.22222 33.2; 3199 16.925 8.22222 33.2;
    3200 17.125 8.22222 33.2; 3201 17.325 8.22222 33.2; 3202 17.525 8.22222 33.2;
    3203 17.725 8.22222 33.2; 3204 17.925 8.22222 33.2; 3205 15.125 8.41667 33.2;
    3206 15.325 8.41667 33.2; 3207 15.525 8.41667 33.2; 3208 15.725 8.41667 33.2;
    3209 15.925 8.41667 33.2; 3210 16.125 8.41667 33.2; 3211 16.325 8.41667 33.2;
    3212 16.525 8.41667 33.2; 3213 16.725 8.41667 33.2; 3214 16.925 8.41667 33.2;
    3215 17.125 8.41667 33.2; 3216 17.325 8.41667 33.2; 3217 17.525 8.41667 33.2;
    3218 17.725 8.41667 33.2; 3219 17.925 8.41667 33.2; 3220 15.125 8.61111 33.2;
    3221 15.325 8.61111 33.2; 3222 15.525 8.61111 33.2; 3223 15.725 8.61111 33.2;
    3224 15.925 8.61111 33.2; 3225 16.125 8.61111 33.2; 3226 16.325 8.61111 33.2;
    3227 16.525 8.61111 33.2; 3228 16.725 8.61111 33.2; 3229 16.925 8.61111 33.2;
    3230 17.125 8.61111 33.2; 3231 17.325 8.61111 33.2; 3232 17.525 8.61111 33.2;
    3233 17.725 8.61111 33.2; 3234 17.925 8.61111 33.2; 3235 15.125 8.80556 33.2;
    3236 15.325 8.80556 33.2; 3237 15.525 8.80556 33.2; 3238 15.725 8.80556 33.2;
    3239 15.925 8.80556 33.2; 3240 16.125 8.80556 33.2; 3241 16.325 8.80556 33.2;
    3242 16.525 8.80556 33.2; 3243 16.725 8.80556 33.2; 3244 16.925 8.80556 33.2;
    3245 17.125 8.80556 33.2; 3246 17.325 8.80556 33.2; 3247 17.525 8.80556 33.2;
    3248 17.725 8.80556 33.2; 3249 17.925 8.80556 33.2; 3250 14.925 10.75 30;
    3251 15.1116 12.5 30; 3252 15.2982 12.5 30; 3253 15.4848 12.5 30;
    3254 15.6714 12.5 30; 3255 15.858 12.5 30; 3256 16.0446 12.5 30;
    3257 16.2313 12.5 30; 3258 16.4179 12.5 30; 3259 16.6045 12.5 30;
    3260 16.7911 12.5 30; 3261 16.9777 12.5 30; 3262 17.1643 12.5 30;
    3263 17.3509 12.5 30; 3264 18.125 12.3056 30; 3265 18.125 12.1111 30;
    3266 18.125 11.9167 30; 3267 18.125 11.7222 30; 3268 18.125 11.5278 30;
    3269 18.125 11.3333 30; 3270 18.125 11.1389 30; 3271 18.125 10.9444 30;
    3272 18.125 10.75 30; 3273 18.125 10.5556 30; 3274 18.125 10.3611 30;
    3275 18.125 10.1667 30; 3276 18.125 9.97222 30; 3277 18.125 9.77778 30;
    3278 18.125 9.58333 30; 3279 18.125 9.38889 30; 3280 18.125 9.19444 30;
    3281 17.7748 11.9105 30; 3282 16.4242 10.5633 30; 3283 16.9571 9.9992 30;
    3284 15.9884 10.8126 30; 3285 17.4895 11.8601 30; 3286 17.4388 9.63779 30;
    3287 17.3047 12.3592 30; 3288 17.8 11.8472 30; 3289 17.7672 11.7796 30;
    3290 15.2786 10.639 30; 3291 15.5333 9.18447 30; 3292 17.0907 11.5296 30;
    3293 17.1441 12.3405 30; 3294 16.861 10.9386 30; 3295 17.3312 11.6831 30;
    3296 17.9082 10.3916 30; 3297 17.4534 12.2859 30; 3298 17.2521 11.1223 30;
    3299 15.2681 9.553 30; 3300 17.3126 12.1744 30; 3301 16.8804 9.76123 30;
    3302 17.5881 9.53779 30; 3303 17.6202 11.9761 30; 3304 17.2279 9.93726 30;
    3305 17.1696 9.62785 30; 3306 17.7085 11.8873 30; 3307 17.9565 12.1541 30;
    3308 15.3854 11.7923 30; 3309 17.4114 9.33853 30; 3310 16.9943 9.58509 30;
    3311 16.8023 9.96843 30; 3312 17.9885 10.8455 30; 3313 16.8102 12.271 30;
    3314 17.9062 9.80452 30; 3315 17.9632 9.61499 30; 3316 17.2439 9.22594 30;
    3317 16.9831 12.3127 30; 3318 17.2002 11.3284 30; 3319 17.9104 9.99674 30;
    3320 17.0156 9.16608 30; 3321 16.5566 11.7468 30; 3322 15.5695 12.0644 30;
    3323 16.7321 11.1666 30; 3324 16.8768 9.62246 30; 3325 17.9583 10.1819 30;
    3326 16.8274 9.1163 30; 3327 17.3772 11.9455 30; 3328 15.6966 10.7295 30;
    3329 17.3479 9.14039 30; 3330 16.4889 11.5882 30; 3331 15.967 10.4998 30;
    3332 17.2819 11.5527 30; 3333 17.3439 9.43479 30; 3334 17.0392 11.7751 30;
    3335 17.2098 11.5045 30; 3336 16.3463 10.103 30; 3337 17.1 11.6613 30;
    3338 15.9318 11.7999 30; 3339 16.9662 11.2849 30; 3340 16.6861 11.6538 30;
    3341 16.7635 10.674 30; 3342 15.4007 9.29885 30; 3343 17.4955 9.34214 30;
    3344 17.0422 10.5172 30; 3345 17.5382 12.0003 30; 3346 17.5146 10.2945 30;
    3347 17.5054 12.0403 30; 3348 16.6395 11.4375 30; 3349 16.7107 10.8017 30;
    3350 16.8244 10.6003 30; 3351 16.7931 10.4039 30; 3352 15.7822 12.275 30;
    3353 17.2486 11.6771 30; 3354 15.9592 10.2015 30; 3355 17.0637 9.77506 30;
    3356 17.3052 12.0517 30; 3357 16.8148 11.3438 30; 3358 17.4101 11.0287 30;
    3359 16.8985 11.7499 30; 3360 16.6075 10.154 30; 3361 16.2176 12.313 30;
    3362 16.2431 9.21772 30; 3363 16.4492 9.47855 30; 3364 17.5814 11.2367 30;
    3365 17.503 11.3735 30; 3366 16.5692 10.9752 30; 3367 17.795 10.9921 30;
    3368 16.7566 11.9296 30; 3369 18.0309 11.1491 30; 3370 16.7123 9.22009 30;
    3371 17.08 11.3771 30; 3372 17.6028 10.615 30; 3373 17.6212 10.9276 30;
    3374 16.4174 9.78098 30; 3375 17.9841 11.9908 30; 3376 16.7613 9.32787 30;
    3377 17.5114 10.8599 30; 3378 16.9199 11.443 30; 3379 17.2479 12.1931 30;
    3380 17.8072 12.0048 30; 3381 17.8652 10.8644 30; 3382 16.8811 10.5123 30;
    3383 17.3303 11.8659 30; 3384 17.5004 11.8084 30; 3385 17.5706 10.7617 30;
    3386 18.0253 10.5127 30; 3387 18.0037 11.0428 30; 3388 17.2732 12.1443 30;
    3389 17.3618 9.5625 30; 3390 17.6084 11.8017 30; 3391 17.703 11.167 30;
    3392 17.5762 11.9136 30; 3393 16.4654 11.1701 30; 3394 16.9316 9.44967 30;
    3395 17.9204 9.40839 30; 3396 16.8595 9.51355 30; 3397 15.604 9.7342 30;
    3398 16.5967 11.9029 30; 3399 17.5994 9.75344 30; 3400 16.9451 11.8617 30;
    3401 17.9701 10.6463 30; 3402 17.5639 9.33199 30; 3403 17.1812 11.7973 30;
    3404 17.3058 12.2248 30; 3405 17.1272 11.0098 30; 3406 17.1635 10.1161 30;
    3407 17.3748 12.1663 30; 3408 17.4802 12.3793 30; 3409 17.0216 12.1457 30;
    3410 17.4633 9.14369 30; 3411 16.2031 11.7863 30; 3412 15.7283 11.1656 30;
    3413 17.6628 12.0994 30; 3414 17.2588 9.64375 30; 3415 17.0797 9.66188 30;
    3416 17.719 9.89303 30; 3417 15.7448 9.26557 30; 3418 15.3138 11.3522 30;
    3419 16.9668 11.5723 30; 3420 16.7148 9.61274 30; 3421 16.8061 11.5082 30;
    3422 17.5989 9.46011 30; 3423 17.69 11.7325 30; 3424 17.3633 12.2693 30;
    3425 17.8994 11.4772 30; 3426 16.536 10.6652 30; 3427 17.8168 9.58835 30;
    3428 17.5057 12.2242 30; 3429 17.8722 11.9344 30; 3430 17.1988 9.45751 30;
    3431 17.7748 10.3655 30; 3432 17.4218 12.0649 30; 3433 17.4756 11.731 30;
    3434 17.4484 9.56184 30; 3435 17.3712 9.74123 30; 3436 16.7017 11.7905 30;
    3437 17.3532 10.869 30; 3438 15.7748 11.6438 30; 3439 16.3896 11.783 30;
    3440 15.9221 9.89565 30; 3441 17.2542 11.9178 30; 3442 17.5901 11.1251 30;
    3443 17.3945 11.9976 30; 3444 16.8066 11.7868 30; 3445 17.7915 12.2181 30;
    3446 17.2013 10.3054 30; 3447 17.5482 10.4533 30; 3448 17.5137 11.0643 30;
    3449 17.6596 11.0705 30; 3450 17.4138 9.24703 30; 3451 17.9145 12.261 30;
    3452 17.2799 9.77411 30; 3453 17.89 12.0672 30; 3454 17.54 9.84573 30;
    3455 18.0012 11.8573 30; 3456 17.3117 12.1203 30; 3457 17.6729 10.0508 30;
    3458 15.6289 10.307 30; 3459 17.3294 10.663 30; 3460 16.6185 10.8019 30;
    3461 18.019 10.3525 30; 3462 17.0006 11.6788 30; 3463 17.5193 9.55291 30;
    3464 17.6628 10.324 30; 3465 16.6162 9.96934 30; 3466 16.5597 9.66755 30;
    3467 15.9645 9.2045 30; 3468 17.6467 9.4199 30; 3469 17.8223 9.21915 30;
    3470 17.018 9.38861 30; 3471 17.2997 9.35751 30; 3472 17.4654 10.7338 30;
    3473 17.3423 9.64802 30; 3474 17.3079 11.3905 30; 3475 17.4513 12.0196 30;
    3476 16.0181 11.1719 30; 3477 17.7146 11.9634 30; 3478 17.0968 10.8626 30;
    3479 16.723 9.42845 30; 3480 17.3888 9.49555 30; 3481 16.4187 12.232 30;
    3482 16.6745 9.81001 30; 3483 17.7989 11.1127 30; 3484 16.6202 9.30643 30;
    3485 16.5945 12.2081 30; 3486 17.7382 11.8392 30; 3487 17.4467 10.5897 30;
    3488 17.9029 11.1239 30; 3489 17.1322 12.1748 30; 3490 17.1812 10.7165 30;
    3491 16.9697 10.8482 30; 3492 17.3617 10.4309 30; 3493 17.7391 11.5957 30;
    3494 17.1731 12.0525 30; 3495 17.6236 9.36672 30; 3496 17.2268 10.5594 30;
    3497 17.808 12.3505 30; 3498 17.2349 12.0917 30; 3499 17.853 10.5479 30;
    3500 17.5678 11.0007 30; 3501 17.5265 11.9013 30; 3502 17.7895 11.2328 30;
    3503 17.8668 10.7076 30; 3504 17.7555 10.7469 30; 3505 16.3127 10.9116 30;
    3506 17.6088 9.62123 30; 3507 17.4316 11.4532 30; 3508 16.6701 10.6403 30;
    3509 17.6108 12.0357 30; 3510 17.5826 12.1145 30; 3511 17.075 9.87755 30;
    3512 17.5863 9.24422 30; 3513 16.9925 10.1075 30; 3514 17.1403 9.3149 30;
    3515 17.5825 11.7459 30; 3516 17.6512 11.6831 30; 3517 16.6504 10.3531 30;
    3518 17.716 9.32062 30; 3519 17.3047 11.249 30; 3520 17.6515 9.1916 30;
    3521 17.5081 9.28114 30; 3522 17.0877 9.50534 30; 3523 17.9251 10.4808 30;
    3524 17.2076 12.1553 30; 3525 17.4128 11.8908 30; 3526 16.1621 11.3287 30;
    3527 17.8951 10.9816 30; 3528 17.3477 11.6003 30; 3529 17.5182 9.64989 30;
    3530 17.7002 9.59728 30; 3531 17.4751 9.97539 30; 3532 16.1831 10.7989 30;
    3533 17.0846 10.6954 30; 3534 16.4833 9.20625 30; 3535 17.8213 11.0556 30;
    3536 17.7969 9.71104 30; 3537 17.9687 11.6808 30; 3538 16.272 9.5189 30;
    3539 17.8644 11.0584 30; 3540 17.392 11.1468 30; 3541 16.9047 11.1444 30;
    3542 17.259 10.7714 30; 3543 16.0172 12.1924 30; 3544 17.6319 11.874 30;
    3545 17.4906 12.0911 30; 3546 17.6884 12.0101 30; 3547 17.388 10.1871 30;
    3548 17.7583 10.9149 30; 3549 17.5429 11.8611 30; 3550 17.7343 10.5845 30;
    3551 17.487 11.9413 30; 3552 17.684 10.8376 30; 3553 17.437 9.79205 30;
    3554 17.5966 11.8576 30; 3555 17.5071 11.5416 30; 3556 16.7866 9.78743 30;
    3557 17.5523 9.47293 30; 3558 17.651 11.3838 30; 3559 16.1942 9.8559 30;
    3560 17.4951 11.1417 30; 3561 17.5067 9.48073 30; 3562 16.8238 11.6428 30;
    3563 16.4689 10.8597 30; 3564 17.45 9.49034 30; 3565 17.6676 9.51873 30;
    3566 17.5313 9.41274 30; 3567 17.2134 10.8825 30; 3568 17.5783 9.41819 30;
    3569 17.4461 10.9361 30; 3570 16.8093 10.1458 30; 3571 16.8141 9.23174 30;
    3572 17.1145 9.9867 30; 3573 16.8858 12.0829 30; 3574 17.9541 11.2768 30;
    3575 17.6729 9.67883 30; 3576 17.8091 12.1372 30; 3577 17.2904 11.9922 30;
    3578 17.8575 10.2922 30; 3579 17.752 12.0711 30; 3580 17.5574 12.0655 30;
    3581 17.4924 12.1578 30; 3582 17.4035 11.8252 30; 3583 17.0161 11.059 30;
    3584 17.4034 10.7945 30; 3585 17.4281 9.42439 30; 3586 17.7557 10.1908 30;
    3587 17.7064 11.7925 30; 3588 16.66 9.1196 30; 3589 17.4788 9.41776 30;
    3590 17.3083 10.0523 30; 3591 17.2929 10.9771 30; 3592 17.6983 9.78992 30;
    3593 17.8072 11.7058 30; 3594 17.3647 12.0689 30; 3595 15.8994 9.64904 30;
    3596 15.6539 9.48634 30; 3597 17.4387 11.2852 30; 3598 17.4238 12.1271 30;
    3599 17.5469 11.9535 30; 3600 17.35 9.88659 30; 3601 17.4989 11.6512 30;
    3602 17.4733 11.9775 30; 3603 17.3297 11.7745 30; 3604 16.3287 11.4708 30;
    3605 17.2816 9.51699 30; 3606 17.7547 9.44555 30; 3607 17.7417 11.0648 30;
    3608 16.8035 10.7877 30; 3609 17.6635 10.4698 30; 3610 16.0526 9.54753 30;
    3611 16.6899 12.0516 30; 3612 17.019 10.2277 30; 3613 16.2617 12.044 30;
    3614 16.7105 10.9892 30; 3615 17.6674 11.8361 30; 3616 17.6728 12.1801 30;
    3617 17.6987 10.9912 30; 3618 17.6163 12.2875 30; 3619 16.8572 11.9374 30;
    3620 17.174 9.79564 30; 3621 17.0875 11.195 30; 3622 17.5802 12.1655 30;
    3623 16.9717 9.74727 30; 3624 17.1853 11.6177 30; 3625 17.8795 11.8296 30;
    3626 16.9198 10.3142 30; 3627 16.9816 9.88953 30; 3628 16.448 11.9498 30;
    3629 16.8514 9.37555 30; 3630 17.0343 11.9396 30; 3631 17.2671 12.2633 30;
    3632 16.9246 10.7002 30; 3633 16.9398 9.27586 30; 3634 17.1964 12.2482 30;
    3635 16.7788 9.48962 30; 3636 16.8909 9.87385 30; 3637 16.3516 10.3855 30;
    3638 17.7904 10.461 30; 3639 17.1095 12.0034 30; 3640 16.6803 10.5101 30;
    3641 17.642 11.9306 30; 3642 16.6004 9.46573 30; 3643 18.125 12.5 30.2;
    3644 18.125 12.5 30.4; 3645 18.125 12.5 30.6; 3646 18.125 12.5 30.8;
    3647 18.125 12.5 31; 3648 18.125 12.5 31.2; 3649 18.125 12.5 31.4;
    3650 18.125 12.5 31.6; 3651 18.125 12.5 31.8; 3652 18.125 12.5 32;
    3653 18.125 12.5 32.2; 3654 18.125 12.5 32.4; 3655 18.125 12.5 32.6;
    3656 18.125 12.5 32.8; 3657 18.125 12.5 33; 3658 18.125 12.3056 33.2;
    3659 18.125 12.1111 33.2; 3660 18.125 11.9167 33.2; 3661 18.125 11.7222 33.2;
    3662 18.125 11.5278 33.2; 3663 18.125 11.3333 33.2; 3664 18.125 11.1389 33.2;
    3665 18.125 10.9444 33.2; 3666 18.125 10.75 33.2; 3667 18.125 10.5556 33.2;
    3668 18.125 10.3611 33.2; 3669 18.125 10.1667 33.2; 3670 18.125 9.97222 33.2;
    3671 18.125 9.77778 33.2; 3672 18.125 9.58333 33.2; 3673 18.125 9.38889 33.2;
    3674 18.125 9.19444 33.2; 3675 18.125 9.19444 30.2; 3676 18.125 9.19444 30.4;
    3677 18.125 9.19444 30.6; 3678 18.125 9.19444 30.8; 3679 18.125 9.19444 31;
    3680 18.125 9.19444 31.2; 3681 18.125 9.19444 31.4; 3682 18.125 9.19444 31.6;
    3683 18.125 9.19444 31.8; 3684 18.125 9.19444 32; 3685 18.125 9.19444 32.2;
    3686 18.125 9.19444 32.4; 3687 18.125 9.19444 32.6; 3688 18.125 9.19444 32.8;
    3689 18.125 9.19444 33; 3690 18.125 9.38889 30.2; 3691 18.125 9.38889 30.4;
    3692 18.125 9.38889 30.6; 3693 18.125 9.38889 30.8; 3694 18.125 9.38889 31;
    3695 18.125 9.38889 31.2; 3696 18.125 9.38889 31.4; 3697 18.125 9.38889 31.6;
    3698 18.125 9.38889 31.8; 3699 18.125 9.38889 32; 3700 18.125 9.38889 32.2;
    3701 18.125 9.38889 32.4; 3702 18.125 9.38889 32.6; 3703 18.125 9.38889 32.8;
    3704 18.125 9.38889 33; 3705 18.125 9.58333 30.2; 3706 18.125 9.58333 30.4;
    3707 18.125 9.58333 30.6; 3708 18.125 9.58333 30.8; 3709 18.125 9.58333 31;
    3710 18.125 9.58333 31.2; 3711 18.125 9.58333 31.4; 3712 18.125 9.58333 31.6;
    3713 18.125 9.58333 31.8; 3714 18.125 9.58333 32; 3715 18.125 9.58333 32.2;
    3716 18.125 9.58333 32.4; 3717 18.125 9.58333 32.6; 3718 18.125 9.58333 32.8;
    3719 18.125 9.58333 33; 3720 18.125 9.77778 30.2; 3721 18.125 9.77778 30.4;
    3722 18.125 9.77778 30.6; 3723 18.125 9.77778 30.8; 3724 18.125 9.77778 31;
    3725 18.125 9.77778 31.2; 3726 18.125 9.77778 31.4; 3727 18.125 9.77778 31.6;
    3728 18.125 9.77778 31.8; 3729 18.125 9.77778 32; 3730 18.125 9.77778 32.2;
    3731 18.125 9.77778 32.4; 3732 18.125 9.77778 32.6; 3733 18.125 9.77778 32.8;
    3734 18.125 9.77778 33; 3735 18.125 9.97222 30.2; 3736 18.125 9.97222 30.4;
    3737 18.125 9.97222 30.6; 3738 18.125 9.97222 30.8; 3739 18.125 9.97222 31;
    3740 18.125 9.97222 31.2; 3741 18.125 9.97222 31.4; 3742 18.125 9.97222 31.6;
    3743 18.125 9.97222 31.8; 3744 18.125 9.97222 32; 3745 18.125 9.97222 32.2;
    3746 18.125 9.97222 32.4; 3747 18.125 9.97222 32.6; 3748 18.125 9.97222 32.8;
    3749 18.125 9.97222 33; 3750 18.125 10.1667 30.2; 3751 18.125 10.1667 30.4;
    3752 18.125 10.1667 30.6; 3753 18.125 10.1667 30.8; 3754 18.125 10.1667 31;
    3755 18.125 10.1667 31.2; 3756 18.125 10.1667 31.4; 3757 18.125 10.1667 31.6;
    3758 18.125 10.1667 31.8; 3759 18.125 10.1667 32; 3760 18.125 10.1667 32.2;
    3761 18.125 10.1667 32.4; 3762 18.125 10.1667 32.6; 3763 18.125 10.1667 32.8;
    3764 18.125 10.1667 33; 3765 18.125 10.3611 30.2; 3766 18.125 10.3611 30.4;
    3767 18.125 10.3611 30.6; 3768 18.125 10.3611 30.8; 3769 18.125 10.3611 31;
    3770 18.125 10.3611 31.2; 3771 18.125 10.3611 31.4; 3772 18.125 10.3611 31.6;
    3773 18.125 10.3611 31.8; 3774 18.125 10.3611 32; 3775 18.125 10.3611 32.2;
    3776 18.125 10.3611 32.4; 3777 18.125 10.3611 32.6; 3778 18.125 10.3611 32.8;
    3779 18.125 10.3611 33; 3780 18.125 10.5556 30.2; 3781 18.125 10.5556 30.4;
    3782 18.125 10.5556 30.6; 3783 18.125 10.5556 30.8; 3784 18.125 10.5556 31;
    3785 18.125 10.5556 31.2; 3786 18.125 10.5556 31.4; 3787 18.125 10.5556 31.6;
    3788 18.125 10.5556 31.8; 3789 18.125 10.5556 32; 3790 18.125 10.5556 32.2;
    3791 18.125 10.5556 32.4; 3792 18.125 10.5556 32.6; 3793 18.125 10.5556 32.8;
    3794 18.125 10.5556 33; 3795 18.125 10.75 30.2; 3796 18.125 10.75 30.4;
    3797 18.125 10.75 30.6; 3798 18.125 10.75 30.8; 3799 18.125 10.75 31;
    3800 18.125 10.75 31.2; 3801 18.125 10.75 31.4; 3802 18.125 10.75 31.6;
    3803 18.125 10.75 31.8; 3804 18.125 10.75 32; 3805 18.125 10.75 32.2;
    3806 18.125 10.75 32.4; 3807 18.125 10.75 32.6; 3808 18.125 10.75 32.8;
    3809 18.125 10.75 33; 3810 18.125 10.9444 30.2; 3811 18.125 10.9444 30.4;
    3812 18.125 10.9444 30.6; 3813 18.125 10.9444 30.8; 3814 18.125 10.9444 31;
    3815 18.125 10.9444 31.2; 3816 18.125 10.9444 31.4; 3817 18.125 10.9444 31.6;
    3818 18.125 10.9444 31.8; 3819 18.125 10.9444 32; 3820 18.125 10.9444 32.2;
    3821 18.125 10.9444 32.4; 3822 18.125 10.9444 32.6; 3823 18.125 10.9444 32.8;
    3824 18.125 10.9444 33; 3825 18.125 11.1389 30.2; 3826 18.125 11.1389 30.4;
    3827 18.125 11.1389 30.6; 3828 18.125 11.1389 30.8; 3829 18.125 11.1389 31;
    3830 18.125 11.1389 31.2; 3831 18.125 11.1389 31.4; 3832 18.125 11.1389 31.6;
    3833 18.125 11.1389 31.8; 3834 18.125 11.1389 32; 3835 18.125 11.1389 32.2;
    3836 18.125 11.1389 32.4; 3837 18.125 11.1389 32.6; 3838 18.125 11.1389 32.8;
    3839 18.125 11.1389 33; 3840 18.125 11.3333 30.2; 3841 18.125 11.3333 30.4;
    3842 18.125 11.3333 30.6; 3843 18.125 11.3333 30.8; 3844 18.125 11.3333 31;
    3845 18.125 11.3333 31.2; 3846 18.125 11.3333 31.4; 3847 18.125 11.3333 31.6;
    3848 18.125 11.3333 31.8; 3849 18.125 11.3333 32; 3850 18.125 11.3333 32.2;
    3851 18.125 11.3333 32.4; 3852 18.125 11.3333 32.6; 3853 18.125 11.3333 32.8;
    3854 18.125 11.3333 33; 3855 18.125 11.5278 30.2; 3856 18.125 11.5278 30.4;
    3857 18.125 11.5278 30.6; 3858 18.125 11.5278 30.8; 3859 18.125 11.5278 31;
    3860 18.125 11.5278 31.2; 3861 18.125 11.5278 31.4; 3862 18.125 11.5278 31.6;
    3863 18.125 11.5278 31.8; 3864 18.125 11.5278 32; 3865 18.125 11.5278 32.2;
    3866 18.125 11.5278 32.4; 3867 18.125 11.5278 32.6; 3868 18.125 11.5278 32.8;
    3869 18.125 11.5278 33; 3870 18.125 11.7222 30.2; 3871 18.125 11.7222 30.4;
    3872 18.125 11.7222 30.6; 3873 18.125 11.7222 30.8; 3874 18.125 11.7222 31;
    3875 18.125 11.7222 31.2; 3876 18.125 11.7222 31.4; 3877 18.125 11.7222 31.6;
    3878 18.125 11.7222 31.8; 3879 18.125 11.7222 32; 3880 18.125 11.7222 32.2;
    3881 18.125 11.7222 32.4; 3882 18.125 11.7222 32.6; 3883 18.125 11.7222 32.8;
    3884 18.125 11.7222 33; 3885 18.125 11.9167 30.2; 3886 18.125 11.9167 30.4;
    3887 18.125 11.9167 30.6; 3888 18.125 11.9167 30.8; 3889 18.125 11.9167 31;
    3890 18.125 11.9167 31.2; 3891 18.125 11.9167 31.4; 3892 18.125 11.9167 31.6;
    3893 18.125 11.9167 31.8; 3894 18.125 11.9167 32; 3895 18.125 11.9167 32.2;
    3896 18.125 11.9167 32.4; 3897 18.125 11.9167 32.6; 3898 18.125 11.9167 32.8;
    3899 18.125 11.9167 33; 3900 18.125 12.1111 30.2; 3901 18.125 12.1111 30.4;
    3902 18.125 12.1111 30.6; 3903 18.125 12.1111 30.8; 3904 18.125 12.1111 31;
    3905 18.125 12.1111 31.2; 3906 18.125 12.1111 31.4; 3907 18.125 12.1111 31.6;
    3908 18.125 12.1111 31.8; 3909 18.125 12.1111 32; 3910 18.125 12.1111 32.2;
    3911 18.125 12.1111 32.4; 3912 18.125 12.1111 32.6; 3913 18.125 12.1111 32.8;
    3914 18.125 12.1111 33; 3915 18.125 12.3056 30.2; 3916 18.125 12.3056 30.4;
    3917 18.125 12.3056 30.6; 3918 18.125 12.3056 30.8; 3919 18.125 12.3056 31;
    3920 18.125 12.3056 31.2; 3921 18.125 12.3056 31.4; 3922 18.125 12.3056 31.6;
    3923 18.125 12.3056 31.8; 3924 18.125 12.3056 32; 3925 18.125 12.3056 32.2;
    3926 18.125 12.3056 32.4; 3927 18.125 12.3056 32.6; 3928 18.125 12.3056 32.8;
    3929 18.125 12.3056 33; 3930 14.925 9.19444 33.2; 3931 14.925 9.38889 33.2;
    3932 14.925 9.58333 33.2; 3933 14.925 9.77778 33.2; 3934 14.925 9.97222 33.2;
    3935 14.925 10.1667 33.2; 3936 14.925 10.3611 33.2; 3937 14.925 10.5556 33.2;
    3938 14.925 10.75 33.2; 3939 14.925 10.9444 33.2; 3940 14.925 11.1389 33.2;
    3941 14.925 11.3333 33.2; 3942 14.925 11.5278 33.2; 3943 14.925 11.7222 33.2;
    3944 14.925 11.9167 33.2; 3945 14.925 12.1111 33.2; 3946 14.925 12.3056 33.2;
    3947 15.125 12.5 33.2; 3948 15.325 12.5 33.2; 3949 15.525 12.5 33.2;
    3950 15.725 12.5 33.2; 3951 15.925 12.5 33.2; 3952 16.125 12.5 33.2;
    3953 16.325 12.5 33.2; 3954 16.525 12.5 33.2; 3955 16.725 12.5 33.2;
    3956 16.925 12.5 33.2; 3957 17.125 12.5 33.2; 3958 17.325 12.5 33.2;
    3959 17.525 12.5 33.2; 3960 17.725 12.5 33.2; 3961 17.925 12.5 33.2;
    3962 15.125 9.19444 33.2; 3963 15.325 9.19444 33.2; 3964 15.525 9.19444 33.2;
    3965 15.725 9.19444 33.2; 3966 15.925 9.19444 33.2; 3967 16.125 9.19444 33.2;
    3968 16.325 9.19444 33.2; 3969 16.525 9.19444 33.2; 3970 16.725 9.19444 33.2;
    3971 16.925 9.19444 33.2; 3972 17.125 9.19444 33.2; 3973 17.325 9.19444 33.2;
    3974 17.525 9.19444 33.2; 3975 17.725 9.19444 33.2; 3976 17.925 9.19444 33.2;
    3977 15.125 9.38889 33.2; 3978 15.325 9.38889 33.2; 3979 15.525 9.38889 33.2;
    3980 15.725 9.38889 33.2; 3981 15.925 9.38889 33.2; 3982 16.125 9.38889 33.2;
    3983 16.325 9.38889 33.2; 3984 16.525 9.38889 33.2; 3985 16.725 9.38889 33.2;
    3986 16.925 9.38889 33.2; 3987 17.125 9.38889 33.2; 3988 17.325 9.38889 33.2;
    3989 17.525 9.38889 33.2; 3990 17.725 9.38889 33.2; 3991 17.925 9.38889 33.2;
    3992 15.125 9.58333 33.2; 3993 15.325 9.58333 33.2; 3994 15.525 9.58333 33.2;
    3995 15.725 9.58333 33.2; 3996 15.925 9.58333 33.2; 3997 16.125 9.58333 33.2;
    3998 16.325 9.58333 33.2; 3999 16.525 9.58333 33.2; 4000 16.725 9.58333 33.2;
    4001 16.925 9.58333 33.2; 4002 17.125 9.58333 33.2; 4003 17.325 9.58333 33.2;
    4004 17.525 9.58333 33.2; 4005 17.725 9.58333 33.2; 4006 17.925 9.58333 33.2;
    4007 15.125 9.77778 33.2; 4008 15.325 9.77778 33.2; 4009 15.525 9.77778 33.2;
    4010 15.725 9.77778 33.2; 4011 15.925 9.77778 33.2; 4012 16.125 9.77778 33.2;
    4013 16.325 9.77778 33.2; 4014 16.525 9.77778 33.2; 4015 16.725 9.77778 33.2;
    4016 16.925 9.77778 33.2; 4017 17.125 9.77778 33.2; 4018 17.325 9.77778 33.2;
    4019 17.525 9.77778 33.2; 4020 17.725 9.77778 33.2; 4021 17.925 9.77778 33.2;
    4022 15.125 9.97222 33.2; 4023 15.325 9.97222 33.2; 4024 15.525 9.97222 33.2;
    4025 15.725 9.97222 33.2; 4026 15.925 9.97222 33.2; 4027 16.125 9.97222 33.2;
    4028 16.325 9.97222 33.2; 4029 16.525 9.97222 33.2; 4030 16.725 9.97222 33.2;
    4031 16.925 9.97222 33.2; 4032 17.125 9.97222 33.2; 4033 17.325 9.97222 33.2;
    4034 17.525 9.97222 33.2; 4035 17.725 9.97222 33.2; 4036 17.925 9.97222 33.2;
    4037 15.125 10.1667 33.2; 4038 15.325 10.1667 33.2; 4039 15.525 10.1667 33.2;
    4040 15.725 10.1667 33.2; 4041 15.925 10.1667 33.2; 4042 16.125 10.1667 33.2;
    4043 16.325 10.1667 33.2; 4044 16.525 10.1667 33.2; 4045 16.725 10.1667 33.2;
    4046 16.925 10.1667 33.2; 4047 17.125 10.1667 33.2; 4048 17.325 10.1667 33.2;
    4049 17.525 10.1667 33.2; 4050 17.725 10.1667 33.2; 4051 17.925 10.1667 33.2;
    4052 15.125 10.3611 33.2; 4053 15.325 10.3611 33.2; 4054 15.525 10.3611 33.2;
    4055 15.725 10.3611 33.2; 4056 15.925 10.3611 33.2; 4057 16.125 10.3611 33.2;
    4058 16.325 10.3611 33.2; 4059 16.525 10.3611 33.2; 4060 16.725 10.3611 33.2;
    4061 16.925 10.3611 33.2; 4062 17.125 10.3611 33.2; 4063 17.325 10.3611 33.2;
    4064 17.525 10.3611 33.2; 4065 17.725 10.3611 33.2; 4066 17.925 10.3611 33.2;
    4067 15.125 10.5556 33.2; 4068 15.325 10.5556 33.2; 4069 15.525 10.5556 33.2;
    4070 15.725 10.5556 33.2; 4071 15.925 10.5556 33.2; 4072 16.125 10.5556 33.2;
    4073 16.325 10.5556 33.2; 4074 16.525 10.5556 33.2; 4075 16.725 10.5556 33.2;
    4076 16.925 10.5556 33.2; 4077 17.125 10.5556 33.2; 4078 17.325 10.5556 33.2;
    4079 17.525 10.5556 33.2; 4080 17.725 10.5556 33.2; 4081 17.925 10.5556 33.2;
    4082 15.125 10.75 33.2; 4083 15.325 10.75 33.2; 4084 15.525 10.75 33.2;
    4085 15.725 10.75 33.2; 4086 15.925 10.75 33.2; 4087 16.125 10.75 33.2;
    4088 16.325 10.75 33.2; 4089 16.525 10.75 33.2; 4090 16.725 10.75 33.2;
    4091 16.925 10.75 33.2; 4092 17.125 10.75 33.2; 4093 17.325 10.75 33.2;
    4094 17.525 10.75 33.2; 4095 17.725 10.75 33.2; 4096 17.925 10.75 33.2;
    4097 15.125 10.9444 33.2; 4098 15.325 10.9444 33.2; 4099 15.525 10.9444 33.2;
    4100 15.725 10.9444 33.2; 4101 15.925 10.9444 33.2; 4102 16.125 10.9444 33.2;
    4103 16.325 10.9444 33.2; 4104 16.525 10.9444 33.2; 4105 16.725 10.9444 33.2;
    4106 16.925 10.9444 33.2; 4107 17.125 10.9444 33.2; 4108 17.325 10.9444 33.2;
    4109 17.525 10.9444 33.2; 4110 17.725 10.9444 33.2; 4111 17.925 10.9444 33.2;
    4112 15.125 11.1389 33.2; 4113 15.325 11.1389 33.2; 4114 15.525 11.1389 33.2;
    4115 15.725 11.1389 33.2; 4116 15.925 11.1389 33.2; 4117 16.125 11.1389 33.2;
    4118 16.325 11.1389 33.2; 4119 16.525 11.1389 33.2; 4120 16.725 11.1389 33.2;
    4121 16.925 11.1389 33.2; 4122 17.125 11.1389 33.2; 4123 17.325 11.1389 33.2;
    4124 17.525 11.1389 33.2; 4125 17.725 11.1389 33.2; 4126 17.925 11.1389 33.2;
    4127 15.125 11.3333 33.2; 4128 15.325 11.3333 33.2; 4129 15.525 11.3333 33.2;
    4130 15.725 11.3333 33.2; 4131 15.925 11.3333 33.2; 4132 16.125 11.3333 33.2;
    4133 16.325 11.3333 33.2; 4134 16.525 11.3333 33.2; 4135 16.725 11.3333 33.2;
    4136 16.925 11.3333 33.2; 4137 17.125 11.3333 33.2; 4138 17.325 11.3333 33.2;
    4139 17.525 11.3333 33.2; 4140 17.725 11.3333 33.2; 4141 17.925 11.3333 33.2;
    4142 15.125 11.5278 33.2; 4143 15.325 11.5278 33.2; 4144 15.525 11.5278 33.2;
    4145 15.725 11.5278 33.2; 4146 15.925 11.5278 33.2; 4147 16.125 11.5278 33.2;
    4148 16.325 11.5278 33.2; 4149 16.525 11.5278 33.2; 4150 16.725 11.5278 33.2;
    4151 16.925 11.5278 33.2; 4152 17.125 11.5278 33.2; 4153 17.325 11.5278 33.2;
    4154 17.525 11.5278 33.2; 4155 17.725 11.5278 33.2; 4156 17.925 11.5278 33.2;
    4157 15.125 11.7222 33.2; 4158 15.325 11.7222 33.2; 4159 15.525 11.7222 33.2;
    4160 15.725 11.7222 33.2; 4161 15.925 11.7222 33.2; 4162 16.125 11.7222 33.2;
    4163 16.325 11.7222 33.2; 4164 16.525 11.7222 33.2; 4165 16.725 11.7222 33.2;
    4166 16.925 11.7222 33.2; 4167 17.125 11.7222 33.2; 4168 17.325 11.7222 33.2;
    4169 17.525 11.7222 33.2; 4170 17.725 11.7222 33.2; 4171 17.925 11.7222 33.2;
    4172 15.125 11.9167 33.2; 4173 15.325 11.9167 33.2; 4174 15.525 11.9167 33.2;
    4175 15.725 11.9167 33.2; 4176 15.925 11.9167 33.2; 4177 16.125 11.9167 33.2;
    4178 16.325 11.9167 33.2; 4179 16.525 11.9167 33.2; 4180 16.725 11.9167 33.2;
    4181 16.925 11.9167 33.2; 4182 17.125 11.9167 33.2; 4183 17.325 11.9167 33.2;
    4184 17.525 11.9167 33.2; 4185 17.725 11.9167 33.2; 4186 17.925 11.9167 33.2;
    4187 15.125 12.1111 33.2; 4188 15.325 12.1111 33.2; 4189 15.525 12.1111 33.2;
    4190 15.725 12.1111 33.2; 4191 15.925 12.1111 33.2; 4192 16.125 12.1111 33.2;
    4193 16.325 12.1111 33.2; 4194 16.525 12.1111 33.2; 4195 16.725 12.1111 33.2;
    4196 16.925 12.1111 33.2; 4197 17.125 12.1111 33.2; 4198 17.325 12.1111 33.2;
    4199 17.525 12.1111 33.2; 4200 17.725 12.1111 33.2; 4201 17.925 12.1111 33.2;
    4202 15.125 12.3056 33.2; 4203 15.325 12.3056 33.2; 4204 15.525 12.3056 33.2;
    4205 15.725 12.3056 33.2; 4206 15.925 12.3056 33.2; 4207 16.125 12.3056 33.2;
    4208 16.325 12.3056 33.2; 4209 16.525 12.3056 33.2; 4210 16.725 12.3056 33.2;
    4211 16.925 12.3056 33.2; 4212 17.125 12.3056 33.2; 4213 17.325 12.3056 33.2;
    4214 17.525 12.3056 33.2; 4215 17.725 12.3056 33.2; 4216 17.925 12.3056 33.2;
    4217 14.925 15 30; 4218 15.1116 17.5 30; 4219 15.2982 17.5 30;
    4220 15.4848 17.5 30; 4221 15.6714 17.5 30; 4222 15.858 17.5 30;
    4223 16.0446 17.5 30; 4224 16.2313 17.5 30; 4225 16.4179 17.5 30;
    4226 16.6045 17.5 30; 4227 16.7911 17.5 30; 4228 16.9777 17.5 30;
    4229 17.1643 17.5 30; 4230 17.3509 17.5 30; 4231 18.125 17.3077 30;
    4232 18.125 17.1154 30; 4233 18.125 16.9231 30; 4234 18.125 16.7308 30;
    4235 18.125 16.5385 30; 4236 18.125 16.3462 30; 4237 18.125 16.1538 30;
    4238 18.125 15.9615 30; 4239 18.125 15.7692 30; 4240 18.125 15.5769 30;
    4241 18.125 15.3846 30; 4242 18.125 15.1923 30; 4243 18.125 15 30;
    4244 18.125 14.8077 30; 4245 18.125 14.6154 30; 4246 18.125 14.4231 30;
    4247 18.125 14.2308 30; 4248 18.125 14.0385 30; 4249 18.125 13.8462 30;
    4250 18.125 13.6538 30; 4251 18.125 13.4615 30; 4252 18.125 13.2692 30;
    4253 18.125 13.0769 30; 4254 18.125 12.8846 30; 4255 18.125 12.6923 30;
    4256 17.643 16.092 30; 4257 17.3344 13.305 30; 4258 17.7673 16.9326 30;
    4259 17.8767 14.2878 30; 4260 17.5959 17.0048 30; 4261 15.4052 17.2703 30;
    4262 17.9773 12.8042 30; 4263 15.7108 17.3409 30; 4264 15.645 12.7188 30;
    4265 15.5347 17.3082 30; 4266 15.5159 12.7675 30; 4267 17.364 13.6448 30;
    4268 17.1662 17.1958 30; 4269 17.1528 16.8809 30; 4270 17.627 17.3857 30;
    4271 15.9129 17.3063 30; 4272 17.2732 16.8923 30; 4273 17.0915 13.1647 30;
    4274 17.3379 16.6095 30; 4275 17.8959 14.9736 30; 4276 17.7789 16.4459 30;
    4277 16.6293 14.9222 30; 4278 17.9675 13.3446 30; 4279 15.4943 13.2775 30;
    4280 15.3147 16.568 30; 4281 17.5515 12.9686 30; 4282 16.8035 15.9836 30;
    4283 17.2172 12.9152 30; 4284 16.4081 12.6926 30; 4285 17.0755 13.7712 30;
    4286 16.8293 15.8194 30; 4287 17.5952 13.5105 30; 4288 17.0389 15.7417 30;
    4289 17.1866 17.0449 30; 4290 17.9559 17.3878 30; 4291 17.3141 15.2532 30;
    4292 16.9654 15.168 30; 4293 17.1476 12.6441 30; 4294 17.9594 13.4609 30;
    4295 18.0195 13.2155 30; 4296 17.0801 16.7843 30; 4297 16.528 16.8819 30;
    4298 17.456 13.2749 30; 4299 17.166 17.327 30; 4300 17.5325 16.4811 30;
    4301 17.6182 17.0687 30; 4302 17.9302 16.7746 30; 4303 18.0118 16.5201 30;
    4304 16.9444 16.5177 30; 4305 17.937 16.1657 30; 4306 17.7578 13.0806 30;
    4307 17.4891 16.9821 30; 4308 17.0181 12.7787 30; 4309 17.3474 17.1832 30;
    4310 17.0176 16.4383 30; 4311 17.9446 13.8229 30; 4312 16.985 15.9318 30;
    4313 16.439 16.577 30; 4314 17.3704 17.3458 30; 4315 17.1259 16.4137 30;
    4316 17.5165 17.2749 30; 4317 16.852 16.3847 30; 4318 17.2762 13.9998 30;
    4319 17.7253 17.1992 30; 4320 16.591 17.3707 30; 4321 17.1058 16.5158 30;
    4322 17.0793 16.5918 30; 4323 17.4738 15.538 30; 4324 16.8785 13.6338 30;
    4325 16.9994 14.2129 30; 4326 16.3536 16.4078 30; 4327 15.7841 12.8775 30;
    4328 15.5506 17.0931 30; 4329 15.3613 16.9553 30; 4330 17.5924 15.6405 30;
    4331 16.7373 13.8403 30; 4332 17.6161 14.0835 30; 4333 17.1913 16.5983 30;
    4334 15.7079 17.1797 30; 4335 17.5314 13.097 30; 4336 17.6312 12.9655 30;
    4337 17.0169 13.5018 30; 4338 17.2858 14.1667 30; 4339 17.8618 16.8394 30;
    4340 16.671 14.1618 30; 4341 16.9731 16.3129 30; 4342 17.4783 13.0145 30;
    4343 17.0604 13.3514 30; 4344 17.904 15.1452 30; 4345 17.4921 14.497 30;
    4346 17.7095 17.1292 30; 4347 16.342 13.3998 30; 4348 17.0323 16.6654 30;
    4349 17.5966 13.0699 30; 4350 16.1773 16.9227 30; 4351 16.2194 12.7211 30;
    4352 17.735 12.8878 30; 4353 17.7234 13.1619 30; 4354 17.8365 14.6794 30;
    4355 17.263 16.6555 30; 4356 16.7434 16.6628 30; 4357 17.6785 13.2416 30;
    4358 17.8156 13.1731 30; 4359 17.7774 17.112 30; 4360 17.8898 14.1627 30;
    4361 17.8222 12.8738 30; 4362 17.0807 14.4726 30; 4363 16.1747 17.3074 30;
    4364 16.2133 13.1603 30; 4365 17.311 16.7073 30; 4366 17.9043 13.1836 30;
    4367 17.3187 16.3578 30; 4368 17.8678 13.0868 30; 4369 17.7996 12.7999 30;
    4370 17.5492 16.9618 30; 4371 16.5671 15.9565 30; 4372 17.7506 16.5603 30;
    4373 17.9425 15.9906 30; 4374 17.9724 16.3531 30; 4375 17.9161 13.2606 30;
    4376 17.1752 13.4876 30; 4377 17.6843 12.9056 30; 4378 16.4245 17.2859 30;
    4379 16.9081 16.6497 30; 4380 16.7402 14.5276 30; 4381 17.8829 13.9219 30;
    4382 17.6532 12.88 30; 4383 17.9856 16.6554 30; 4384 17.6572 13.0551 30;
    4385 16.9914 15.471 30; 4386 17.4811 17.1605 30; 4387 17.8465 16.3487 30;
    4388 17.193 16.4857 30; 4389 16.891 16.1628 30; 4390 16.7732 16.5378 30;
    4391 17.6094 13.697 30; 4392 17.2518 16.118 30; 4393 17.2736 16.5714 30;
    4394 17.5528 13.0378 30; 4395 17.2633 13.825 30; 4396 17.244 13.3332 30;
    4397 17.3759 17.0602 30; 4398 16.9069 13.0598 30; 4399 15.4816 12.9588 30;
    4400 17.117 16.2688 30; 4401 17.6195 12.8546 30; 4402 17.0133 13.9662 30;
    4403 17.5912 12.8971 30; 4404 17.594 12.944 30; 4405 16.0365 14.5544 30;
    4406 17.6974 17.2957 30; 4407 17.7134 12.7145 30; 4408 17.6831 16.6901 30;
    4409 17.5727 13.1337 30; 4410 15.7257 16.961 30; 4411 17.5152 16.3472 30;
    4412 15.8884 16.8173 30; 4413 16.9276 17.017 30; 4414 16.6463 16.4735 30;
    4415 15.8996 17.0552 30; 4416 17.3343 16.5169 30; 4417 17.5763 12.8207 30;
    4418 17.6979 12.8421 30; 4419 16.4403 13.1004 30; 4420 16.7367 17.2834 30;
    4421 16.6041 12.6932 30; 4422 16.0058 12.8106 30; 4423 17.8481 14.0589 30;
    4424 17.8215 13.3531 30; 4425 17.2761 16.4628 30; 4426 17.4888 13.5827 30;
    4427 17.388 16.6659 30; 4428 17.9204 14.4805 30; 4429 17.5961 17.2369 30;
    4430 17.4868 12.8668 30; 4431 17.3499 13.1646 30; 4432 17.5969 12.7543 30;
    4433 16.3973 12.8934 30; 4434 17.5139 13.1895 30; 4435 17.3372 12.9081 30;
    4436 17.5057 12.7995 30; 4437 18.0016 13.9956 30; 4438 17.6471 13.1492 30;
    4439 18.0036 17.0929 30; 4440 16.9766 12.6423 30; 4441 17.835 13.4523 30;
    4442 16.5376 12.8713 30; 4443 17.9893 14.2739 30; 4444 17.6825 16.8223 30;
    4445 17.3203 13.4734 30; 4446 17.9431 12.7139 30; 4447 16.2423 16.0017 30;
    4448 17.4582 12.9394 30; 4449 17.4309 16.8221 30; 4450 17.2559 15.5054 30;
    4451 17.9244 15.3865 30; 4452 17.6437 17.1278 30; 4453 17.3249 16.8252 30;
    4454 16.4544 13.6679 30; 4455 17.4042 16.5713 30; 4456 17.8608 13.605 30;
    4457 17.5107 17.0599 30; 4458 17.7604 13.0205 30; 4459 16.9743 13.2245 30;
    4460 17.481 16.9012 30; 4461 17.1427 12.8148 30; 4462 17.4504 15.754 30;
    4463 17.1031 16.0505 30; 4464 17.4858 15.3633 30; 4465 17.5829 15.913 30;
    4466 17.6922 17.0405 30; 4467 17.1497 13.3445 30; 4468 17.2067 16.3999 30;
    4469 18.0012 16.9206 30; 4470 16.7019 13.4659 30; 4471 17.8911 16.944 30;
    4472 17.8604 12.9976 30; 4473 16.5826 16.6844 30; 4474 17.357 14.8777 30;
    4475 17.782 16.8189 30; 4476 17.6037 13.0047 30; 4477 17.5617 17.0952 30;
    4478 16.4852 16.2521 30; 4479 16.2171 12.9126 30; 4480 16.7164 12.8357 30;
    4481 17.1703 16.6897 30; 4482 17.5452 16.6122 30; 4483 16.6891 16.2288 30;
    4484 15.963 13.8489 30; 4485 17.3932 14.3506 30; 4486 15.6899 16.7135 30;
    4487 17.6782 12.9472 30; 4488 17.6982 15.201 30; 4489 16.2084 17.0969 30;
    4490 17.7203 15.5457 30; 4491 17.5591 17.1564 30; 4492 17.7326 12.9516 30;
    4493 16.8614 13.3423 30; 4494 17.4162 16.0078 30; 4495 16.8703 16.8287 30;
    4496 17.643 14.9308 30; 4497 17.6952 15.4058 30; 4498 15.8402 15.2494 30;
    4499 17.2503 13.6457 30; 4500 15.7913 13.2716 30; 4501 17.9633 12.9235 30;
    4502 17.1225 13.6472 30; 4503 15.4959 14.337 30; 4504 17.6249 14.3965 30;
    4505 16.2226 16.5312 30; 4506 16.9747 17.2436 30; 4507 16.5324 16.4509 30;
    4508 17.4844 13.9768 30; 4509 17.9557 14.815 30; 4510 17.6625 16.9552 30;
    4511 16.2089 16.2892 30; 4512 17.8443 16.5998 30; 4513 17.4839 14.125 30;
    4514 16.1196 13.5383 30; 4515 15.9625 16.5234 30; 4516 17.4206 13.8329 30;
    4517 17.7886 12.9354 30; 4518 17.7999 16.0347 30; 4519 17.3728 16.7441 30;
    4520 17.8982 16.4896 30; 4521 16.8115 12.6999 30; 4522 16.6298 13.0103 30;
    4523 15.8259 16.2203 30; 4524 17.9238 14.0464 30; 4525 16.3424 16.6894 30;
    4526 17.7389 14.2473 30; 4527 17.7556 14.4592 30; 4528 17.8892 17.0553 30;
    4529 17.6863 13.3294 30; 4530 16.7666 13.1271 30; 4531 17.6818 13.0008 30;
    4532 17.2539 16.2595 30; 4533 17.4658 16.5246 30; 4534 17.7866 13.9223 30;
    4535 17.7796 17.0264 30; 4536 17.7475 13.7127 30; 4537 17.6328 12.9191 30;
    4538 16.3912 15.4728 30; 4539 17.7817 13.8201 30; 4540 17.655 17.1828 30;
    4541 17.3369 13.0274 30; 4542 17.8855 15.6156 30; 4543 17.5392 12.9243 30;
    4544 17.571 13.309 30; 4545 17.2067 13.1746 30; 4546 17.2531 15.8338 30;
    4547 17.5899 13.2225 30; 4548 17.9946 14.135 30; 4549 17.6367 16.5309 30;
    4550 17.4229 16.9834 30; 4551 17.993 13.0946 30; 4552 17.7017 13.5577 30;
    4553 17.4333 13.4072 30; 4554 17.7096 13.4324 30; 4555 17.1615 14.7273 30;
    4556 17.8012 13.2628 30; 4557 17.4823 16.1915 30; 4558 17.4604 13.1177 30;
    4559 17.486 16.7302 30; 4560 17.3902 16.4333 30; 4561 17.4499 16.6504 30;
    4562 17.2284 16.7721 30; 4563 17.3912 16.9009 30; 4564 16.8086 12.9297 30;
    4565 16.2659 14.0718 30; 4566 17.5779 13.4042 30; 4567 16.1602 16.7102 30;
    4568 16.0131 13.2045 30; 4569 17.4103 12.756 30; 4570 17.5653 16.8942 30;
    4571 17.5043 16.8147 30; 4572 17.6183 14.6242 30; 4573 16.6389 15.6407 30;
    4574 17.5815 16.7088 30; 4575 17.4117 12.8506 30; 4576 17.6682 16.3378 30;
    4577 16.5686 13.2843 30; 4578 17.6939 13.9893 30; 4579 17.2931 12.7747 30;
    4580 17.7975 16.2338 30; 4581 17.6567 12.8009 30; 4582 17.5524 12.866 30;
    4583 17.5844 16.8101 30; 4584 17.6071 14.2691 30; 4585 17.4592 12.6462 30;
    4586 17.6515 13.8494 30; 4587 16.5567 17.091 30; 4588 17.9343 17.2653 30;
    4589 17.0658 12.962 30; 4590 17.3023 12.635 30; 4591 17.1786 13.0156 30;
    4592 17.3047 16.9688 30; 4593 17.8485 17.1683 30; 4594 17.7899 14.1219 30;
    4595 17.831 15.817 30; 4596 17.8211 16.7044 30; 4597 16.9281 12.8725 30;
    4598 18.125 17.5 30.2; 4599 18.125 17.5 30.4; 4600 18.125 17.5 30.6;
    4601 18.125 17.5 30.8; 4602 18.125 17.5 31; 4603 18.125 17.5 31.2;
    4604 18.125 17.5 31.4; 4605 18.125 17.5 31.6; 4606 18.125 17.5 31.8;
    4607 18.125 17.5 32; 4608 18.125 17.5 32.2; 4609 18.125 17.5 32.4;
    4610 18.125 17.5 32.6; 4611 18.125 17.5 32.8; 4612 18.125 17.5 33;
    4613 18.125 17.3077 33.2; 4614 18.125 17.1154 33.2; 4615 18.125 16.9231 33.2;
    4616 18.125 16.7308 33.2; 4617 18.125 16.5385 33.2; 4618 18.125 16.3462 33.2;
    4619 18.125 16.1538 33.2; 4620 18.125 15.9615 33.2; 4621 18.125 15.7692 33.2;
    4622 18.125 15.5769 33.2; 4623 18.125 15.3846 33.2; 4624 18.125 15.1923 33.2;
    4625 18.125 15 33.2; 4626 18.125 14.8077 33.2; 4627 18.125 14.6154 33.2;
    4628 18.125 14.4231 33.2; 4629 18.125 14.2308 33.2; 4630 18.125 14.0385 33.2;
    4631 18.125 13.8462 33.2; 4632 18.125 13.6538 33.2; 4633 18.125 13.4615 33.2;
    4634 18.125 13.2692 33.2; 4635 18.125 13.0769 33.2; 4636 18.125 12.8846 33.2;
    4637 18.125 12.6923 33.2; 4638 18.125 12.6923 30.2; 4639 18.125 12.6923 30.4;
    4640 18.125 12.6923 30.6; 4641 18.125 12.6923 30.8; 4642 18.125 12.6923 31;
    4643 18.125 12.6923 31.2; 4644 18.125 12.6923 31.4; 4645 18.125 12.6923 31.6;
    4646 18.125 12.6923 31.8; 4647 18.125 12.6923 32; 4648 18.125 12.6923 32.2;
    4649 18.125 12.6923 32.4; 4650 18.125 12.6923 32.6; 4651 18.125 12.6923 32.8;
    4652 18.125 12.6923 33; 4653 18.125 12.8846 30.2; 4654 18.125 12.8846 30.4;
    4655 18.125 12.8846 30.6; 4656 18.125 12.8846 30.8; 4657 18.125 12.8846 31;
    4658 18.125 12.8846 31.2; 4659 18.125 12.8846 31.4; 4660 18.125 12.8846 31.6;
    4661 18.125 12.8846 31.8; 4662 18.125 12.8846 32; 4663 18.125 12.8846 32.2;
    4664 18.125 12.8846 32.4; 4665 18.125 12.8846 32.6; 4666 18.125 12.8846 32.8;
    4667 18.125 12.8846 33; 4668 18.125 13.0769 30.2; 4669 18.125 13.0769 30.4;
    4670 18.125 13.0769 30.6; 4671 18.125 13.0769 30.8; 4672 18.125 13.0769 31;
    4673 18.125 13.0769 31.2; 4674 18.125 13.0769 31.4; 4675 18.125 13.0769 31.6;
    4676 18.125 13.0769 31.8; 4677 18.125 13.0769 32; 4678 18.125 13.0769 32.2;
    4679 18.125 13.0769 32.4; 4680 18.125 13.0769 32.6; 4681 18.125 13.0769 32.8;
    4682 18.125 13.0769 33; 4683 18.125 13.2692 30.2; 4684 18.125 13.2692 30.4;
    4685 18.125 13.2692 30.6; 4686 18.125 13.2692 30.8; 4687 18.125 13.2692 31;
    4688 18.125 13.2692 31.2; 4689 18.125 13.2692 31.4; 4690 18.125 13.2692 31.6;
    4691 18.125 13.2692 31.8; 4692 18.125 13.2692 32; 4693 18.125 13.2692 32.2;
    4694 18.125 13.2692 32.4; 4695 18.125 13.2692 32.6; 4696 18.125 13.2692 32.8;
    4697 18.125 13.2692 33; 4698 18.125 13.4615 30.2; 4699 18.125 13.4615 30.4;
    4700 18.125 13.4615 30.6; 4701 18.125 13.4615 30.8; 4702 18.125 13.4615 31;
    4703 18.125 13.4615 31.2; 4704 18.125 13.4615 31.4; 4705 18.125 13.4615 31.6;
    4706 18.125 13.4615 31.8; 4707 18.125 13.4615 32; 4708 18.125 13.4615 32.2;
    4709 18.125 13.4615 32.4; 4710 18.125 13.4615 32.6; 4711 18.125 13.4615 32.8;
    4712 18.125 13.4615 33; 4713 18.125 13.6538 30.2; 4714 18.125 13.6538 30.4;
    4715 18.125 13.6538 30.6; 4716 18.125 13.6538 30.8; 4717 18.125 13.6538 31;
    4718 18.125 13.6538 31.2; 4719 18.125 13.6538 31.4; 4720 18.125 13.6538 31.6;
    4721 18.125 13.6538 31.8; 4722 18.125 13.6538 32; 4723 18.125 13.6538 32.2;
    4724 18.125 13.6538 32.4; 4725 18.125 13.6538 32.6; 4726 18.125 13.6538 32.8;
    4727 18.125 13.6538 33; 4728 18.125 13.8462 30.2; 4729 18.125 13.8462 30.4;
    4730 18.125 13.8462 30.6; 4731 18.125 13.8462 30.8; 4732 18.125 13.8462 31;
    4733 18.125 13.8462 31.2; 4734 18.125 13.8462 31.4; 4735 18.125 13.8462 31.6;
    4736 18.125 13.8462 31.8; 4737 18.125 13.8462 32; 4738 18.125 13.8462 32.2;
    4739 18.125 13.8462 32.4; 4740 18.125 13.8462 32.6; 4741 18.125 13.8462 32.8;
    4742 18.125 13.8462 33; 4743 18.125 14.0385 30.2; 4744 18.125 14.0385 30.4;
    4745 18.125 14.0385 30.6; 4746 18.125 14.0385 30.8; 4747 18.125 14.0385 31;
    4748 18.125 14.0385 31.2; 4749 18.125 14.0385 31.4; 4750 18.125 14.0385 31.6;
    4751 18.125 14.0385 31.8; 4752 18.125 14.0385 32; 4753 18.125 14.0385 32.2;
    4754 18.125 14.0385 32.4; 4755 18.125 14.0385 32.6; 4756 18.125 14.0385 32.8;
    4757 18.125 14.0385 33; 4758 18.125 14.2308 30.2; 4759 18.125 14.2308 30.4;
    4760 18.125 14.2308 30.6; 4761 18.125 14.2308 30.8; 4762 18.125 14.2308 31;
    4763 18.125 14.2308 31.2; 4764 18.125 14.2308 31.4; 4765 18.125 14.2308 31.6;
    4766 18.125 14.2308 31.8; 4767 18.125 14.2308 32; 4768 18.125 14.2308 32.2;
    4769 18.125 14.2308 32.4; 4770 18.125 14.2308 32.6; 4771 18.125 14.2308 32.8;
    4772 18.125 14.2308 33; 4773 18.125 14.4231 30.2; 4774 18.125 14.4231 30.4;
    4775 18.125 14.4231 30.6; 4776 18.125 14.4231 30.8; 4777 18.125 14.4231 31;
    4778 18.125 14.4231 31.2; 4779 18.125 14.4231 31.4; 4780 18.125 14.4231 31.6;
    4781 18.125 14.4231 31.8; 4782 18.125 14.4231 32; 4783 18.125 14.4231 32.2;
    4784 18.125 14.4231 32.4; 4785 18.125 14.4231 32.6; 4786 18.125 14.4231 32.8;
    4787 18.125 14.4231 33; 4788 18.125 14.6154 30.2; 4789 18.125 14.6154 30.4;
    4790 18.125 14.6154 30.6; 4791 18.125 14.6154 30.8; 4792 18.125 14.6154 31;
    4793 18.125 14.6154 31.2; 4794 18.125 14.6154 31.4; 4795 18.125 14.6154 31.6;
    4796 18.125 14.6154 31.8; 4797 18.125 14.6154 32; 4798 18.125 14.6154 32.2;
    4799 18.125 14.6154 32.4; 4800 18.125 14.6154 32.6; 4801 18.125 14.6154 32.8;
    4802 18.125 14.6154 33; 4803 18.125 14.8077 30.2; 4804 18.125 14.8077 30.4;
    4805 18.125 14.8077 30.6; 4806 18.125 14.8077 30.8; 4807 18.125 14.8077 31;
    4808 18.125 14.8077 31.2; 4809 18.125 14.8077 31.4; 4810 18.125 14.8077 31.6;
    4811 18.125 14.8077 31.8; 4812 18.125 14.8077 32; 4813 18.125 14.8077 32.2;
    4814 18.125 14.8077 32.4; 4815 18.125 14.8077 32.6; 4816 18.125 14.8077 32.8;
    4817 18.125 14.8077 33; 4818 18.125 15 30.2; 4819 18.125 15 30.4;
    4820 18.125 15 30.6; 4821 18.125 15 30.8; 4822 18.125 15 31;
    4823 18.125 15 31.2; 4824 18.125 15 31.4; 4825 18.125 15 31.6;
    4826 18.125 15 31.8; 4827 18.125 15 32; 4828 18.125 15 32.2;
    4829 18.125 15 32.4; 4830 18.125 15 32.6; 4831 18.125 15 32.8;
    4832 18.125 15 33; 4833 18.125 15.1923 30.2; 4834 18.125 15.1923 30.4;
    4835 18.125 15.1923 30.6; 4836 18.125 15.1923 30.8; 4837 18.125 15.1923 31;
    4838 18.125 15.1923 31.2; 4839 18.125 15.1923 31.4; 4840 18.125 15.1923 31.6;
    4841 18.125 15.1923 31.8; 4842 18.125 15.1923 32; 4843 18.125 15.1923 32.2;
    4844 18.125 15.1923 32.4; 4845 18.125 15.1923 32.6; 4846 18.125 15.1923 32.8;
    4847 18.125 15.1923 33; 4848 18.125 15.3846 30.2; 4849 18.125 15.3846 30.4;
    4850 18.125 15.3846 30.6; 4851 18.125 15.3846 30.8; 4852 18.125 15.3846 31;
    4853 18.125 15.3846 31.2; 4854 18.125 15.3846 31.4; 4855 18.125 15.3846 31.6;
    4856 18.125 15.3846 31.8; 4857 18.125 15.3846 32; 4858 18.125 15.3846 32.2;
    4859 18.125 15.3846 32.4; 4860 18.125 15.3846 32.6; 4861 18.125 15.3846 32.8;
    4862 18.125 15.3846 33; 4863 18.125 15.5769 30.2; 4864 18.125 15.5769 30.4;
    4865 18.125 15.5769 30.6; 4866 18.125 15.5769 30.8; 4867 18.125 15.5769 31;
    4868 18.125 15.5769 31.2; 4869 18.125 15.5769 31.4; 4870 18.125 15.5769 31.6;
    4871 18.125 15.5769 31.8; 4872 18.125 15.5769 32; 4873 18.125 15.5769 32.2;
    4874 18.125 15.5769 32.4; 4875 18.125 15.5769 32.6; 4876 18.125 15.5769 32.8;
    4877 18.125 15.5769 33; 4878 18.125 15.7692 30.2; 4879 18.125 15.7692 30.4;
    4880 18.125 15.7692 30.6; 4881 18.125 15.7692 30.8; 4882 18.125 15.7692 31;
    4883 18.125 15.7692 31.2; 4884 18.125 15.7692 31.4; 4885 18.125 15.7692 31.6;
    4886 18.125 15.7692 31.8; 4887 18.125 15.7692 32; 4888 18.125 15.7692 32.2;
    4889 18.125 15.7692 32.4; 4890 18.125 15.7692 32.6; 4891 18.125 15.7692 32.8;
    4892 18.125 15.7692 33; 4893 18.125 15.9615 30.2; 4894 18.125 15.9615 30.4;
    4895 18.125 15.9615 30.6; 4896 18.125 15.9615 30.8; 4897 18.125 15.9615 31;
    4898 18.125 15.9615 31.2; 4899 18.125 15.9615 31.4; 4900 18.125 15.9615 31.6;
    4901 18.125 15.9615 31.8; 4902 18.125 15.9615 32; 4903 18.125 15.9615 32.2;
    4904 18.125 15.9615 32.4; 4905 18.125 15.9615 32.6; 4906 18.125 15.9615 32.8;
    4907 18.125 15.9615 33; 4908 18.125 16.1538 30.2; 4909 18.125 16.1538 30.4;
    4910 18.125 16.1538 30.6; 4911 18.125 16.1538 30.8; 4912 18.125 16.1538 31;
    4913 18.125 16.1538 31.2; 4914 18.125 16.1538 31.4; 4915 18.125 16.1538 31.6;
    4916 18.125 16.1538 31.8; 4917 18.125 16.1538 32; 4918 18.125 16.1538 32.2;
    4919 18.125 16.1538 32.4; 4920 18.125 16.1538 32.6; 4921 18.125 16.1538 32.8;
    4922 18.125 16.1538 33; 4923 18.125 16.3462 30.2; 4924 18.125 16.3462 30.4;
    4925 18.125 16.3462 30.6; 4926 18.125 16.3462 30.8; 4927 18.125 16.3462 31;
    4928 18.125 16.3462 31.2; 4929 18.125 16.3462 31.4; 4930 18.125 16.3462 31.6;
    4931 18.125 16.3462 31.8; 4932 18.125 16.3462 32; 4933 18.125 16.3462 32.2;
    4934 18.125 16.3462 32.4; 4935 18.125 16.3462 32.6; 4936 18.125 16.3462 32.8;
    4937 18.125 16.3462 33; 4938 18.125 16.5385 30.2; 4939 18.125 16.5385 30.4;
    4940 18.125 16.5385 30.6; 4941 18.125 16.5385 30.8; 4942 18.125 16.5385 31;
    4943 18.125 16.5385 31.2; 4944 18.125 16.5385 31.4; 4945 18.125 16.5385 31.6;
    4946 18.125 16.5385 31.8; 4947 18.125 16.5385 32; 4948 18.125 16.5385 32.2;
    4949 18.125 16.5385 32.4; 4950 18.125 16.5385 32.6; 4951 18.125 16.5385 32.8;
    4952 18.125 16.5385 33; 4953 18.125 16.7308 30.2; 4954 18.125 16.7308 30.4;
    4955 18.125 16.7308 30.6; 4956 18.125 16.7308 30.8; 4957 18.125 16.7308 31;
    4958 18.125 16.7308 31.2; 4959 18.125 16.7308 31.4; 4960 18.125 16.7308 31.6;
    4961 18.125 16.7308 31.8; 4962 18.125 16.7308 32; 4963 18.125 16.7308 32.2;
    4964 18.125 16.7308 32.4; 4965 18.125 16.7308 32.6; 4966 18.125 16.7308 32.8;
    4967 18.125 16.7308 33; 4968 18.125 16.9231 30.2; 4969 18.125 16.9231 30.4;
    4970 18.125 16.9231 30.6; 4971 18.125 16.9231 30.8; 4972 18.125 16.9231 31;
    4973 18.125 16.9231 31.2; 4974 18.125 16.9231 31.4; 4975 18.125 16.9231 31.6;
    4976 18.125 16.9231 31.8; 4977 18.125 16.9231 32; 4978 18.125 16.9231 32.2;
    4979 18.125 16.9231 32.4; 4980 18.125 16.9231 32.6; 4981 18.125 16.9231 32.8;
    4982 18.125 16.9231 33; 4983 18.125 17.1154 30.2; 4984 18.125 17.1154 30.4;
    4985 18.125 17.1154 30.6; 4986 18.125 17.1154 30.8; 4987 18.125 17.1154 31;
    4988 18.125 17.1154 31.2; 4989 18.125 17.1154 31.4; 4990 18.125 17.1154 31.6;
    4991 18.125 17.1154 31.8; 4992 18.125 17.1154 32; 4993 18.125 17.1154 32.2;
    4994 18.125 17.1154 32.4; 4995 18.125 17.1154 32.6; 4996 18.125 17.1154 32.8;
    4997 18.125 17.1154 33; 4998 18.125 17.3077 30.2; 4999 18.125 17.3077 30.4;
    5000 18.125 17.3077 30.6; 5001 18.125 17.3077 30.8; 5002 18.125 17.3077 31;
    5003 18.125 17.3077 31.2; 5004 18.125 17.3077 31.4; 5005 18.125 17.3077 31.6;
    5006 18.125 17.3077 31.8; 5007 18.125 17.3077 32; 5008 18.125 17.3077 32.2;
    5009 18.125 17.3077 32.4; 5010 18.125 17.3077 32.6; 5011 18.125 17.3077 32.8;
    5012 18.125 17.3077 33; 5013 14.925 12.6923 33.2; 5014 14.925 12.8846 33.2;
    5015 14.925 13.0769 33.2; 5016 14.925 13.2692 33.2; 5017 14.925 13.4615 33.2;
    5018 14.925 13.6538 33.2; 5019 14.925 13.8462 33.2; 5020 14.925 14.0385 33.2;
    5021 14.925 14.2308 33.2; 5022 14.925 14.4231 33.2; 5023 14.925 14.6154 33.2;
    5024 14.925 14.8077 33.2; 5025 14.925 15 33.2; 5026 14.925 15.1923 33.2;
    5027 14.925 15.3846 33.2; 5028 14.925 15.5769 33.2; 5029 14.925 15.7692 33.2;
    5030 14.925 15.9615 33.2; 5031 14.925 16.1538 33.2; 5032 14.925 16.3462 33.2;
    5033 14.925 16.5385 33.2; 5034 14.925 16.7308 33.2; 5035 14.925 16.9231 33.2;
    5036 14.925 17.1154 33.2; 5037 14.925 17.3077 33.2; 5038 15.125 17.5 33.2;
    5039 15.325 17.5 33.2; 5040 15.525 17.5 33.2; 5041 15.725 17.5 33.2;
    5042 15.925 17.5 33.2; 5043 16.125 17.5 33.2; 5044 16.325 17.5 33.2;
    5045 16.525 17.5 33.2; 5046 16.725 17.5 33.2; 5047 16.925 17.5 33.2;
    5048 17.125 17.5 33.2; 5049 17.325 17.5 33.2; 5050 17.525 17.5 33.2;
    5051 17.725 17.5 33.2; 5052 17.925 17.5 33.2; 5053 15.125 12.6923 33.2;
    5054 15.325 12.6923 33.2; 5055 15.525 12.6923 33.2; 5056 15.725 12.6923 33.2;
    5057 15.925 12.6923 33.2; 5058 16.125 12.6923 33.2; 5059 16.325 12.6923 33.2;
    5060 16.525 12.6923 33.2; 5061 16.725 12.6923 33.2; 5062 16.925 12.6923 33.2;
    5063 17.125 12.6923 33.2; 5064 17.325 12.6923 33.2; 5065 17.525 12.6923 33.2;
    5066 17.725 12.6923 33.2; 5067 17.925 12.6923 33.2; 5068 15.125 12.8846 33.2;
    5069 15.325 12.8846 33.2; 5070 15.525 12.8846 33.2; 5071 15.725 12.8846 33.2;
    5072 15.925 12.8846 33.2; 5073 16.125 12.8846 33.2; 5074 16.325 12.8846 33.2;
    5075 16.525 12.8846 33.2; 5076 16.725 12.8846 33.2; 5077 16.925 12.8846 33.2;
    5078 17.125 12.8846 33.2; 5079 17.325 12.8846 33.2; 5080 17.525 12.8846 33.2;
    5081 17.725 12.8846 33.2; 5082 17.925 12.8846 33.2; 5083 15.125 13.0769 33.2;
    5084 15.325 13.0769 33.2; 5085 15.525 13.0769 33.2; 5086 15.725 13.0769 33.2;
    5087 15.925 13.0769 33.2; 5088 16.125 13.0769 33.2; 5089 16.325 13.0769 33.2;
    5090 16.525 13.0769 33.2; 5091 16.725 13.0769 33.2; 5092 16.925 13.0769 33.2;
    5093 17.125 13.0769 33.2; 5094 17.325 13.0769 33.2; 5095 17.525 13.0769 33.2;
    5096 17.725 13.0769 33.2; 5097 17.925 13.0769 33.2; 5098 15.125 13.2692 33.2;
    5099 15.325 13.2692 33.2; 5100 15.525 13.2692 33.2; 5101 15.725 13.2692 33.2;
    5102 15.925 13.2692 33.2; 5103 16.125 13.2692 33.2; 5104 16.325 13.2692 33.2;
    5105 16.525 13.2692 33.2; 5106 16.725 13.2692 33.2; 5107 16.925 13.2692 33.2;
    5108 17.125 13.2692 33.2; 5109 17.325 13.2692 33.2; 5110 17.525 13.2692 33.2;
    5111 17.725 13.2692 33.2; 5112 17.925 13.2692 33.2; 5113 15.125 13.4615 33.2;
    5114 15.325 13.4615 33.2; 5115 15.525 13.4615 33.2; 5116 15.725 13.4615 33.2;
    5117 15.925 13.4615 33.2; 5118 16.125 13.4615 33.2; 5119 16.325 13.4615 33.2;
    5120 16.525 13.4615 33.2; 5121 16.725 13.4615 33.2; 5122 16.925 13.4615 33.2;
    5123 17.125 13.4615 33.2; 5124 17.325 13.4615 33.2; 5125 17.525 13.4615 33.2;
    5126 17.725 13.4615 33.2; 5127 17.925 13.4615 33.2; 5128 15.125 13.6538 33.2;
    5129 15.325 13.6538 33.2; 5130 15.525 13.6538 33.2; 5131 15.725 13.6538 33.2;
    5132 15.925 13.6538 33.2; 5133 16.125 13.6538 33.2; 5134 16.325 13.6538 33.2;
    5135 16.525 13.6538 33.2; 5136 16.725 13.6538 33.2; 5137 16.925 13.6538 33.2;
    5138 17.125 13.6538 33.2; 5139 17.325 13.6538 33.2; 5140 17.525 13.6538 33.2;
    5141 17.725 13.6538 33.2; 5142 17.925 13.6538 33.2; 5143 15.125 13.8462 33.2;
    5144 15.325 13.8462 33.2; 5145 15.525 13.8462 33.2; 5146 15.725 13.8462 33.2;
    5147 15.925 13.8462 33.2; 5148 16.125 13.8462 33.2; 5149 16.325 13.8462 33.2;
    5150 16.525 13.8462 33.2; 5151 16.725 13.8462 33.2; 5152 16.925 13.8462 33.2;
    5153 17.125 13.8462 33.2; 5154 17.325 13.8462 33.2; 5155 17.525 13.8462 33.2;
    5156 17.725 13.8462 33.2; 5157 17.925 13.8462 33.2; 5158 15.125 14.0385 33.2;
    5159 15.325 14.0385 33.2; 5160 15.525 14.0385 33.2; 5161 15.725 14.0385 33.2;
    5162 15.925 14.0385 33.2; 5163 16.125 14.0385 33.2; 5164 16.325 14.0385 33.2;
    5165 16.525 14.0385 33.2; 5166 16.725 14.0385 33.2; 5167 16.925 14.0385 33.2;
    5168 17.125 14.0385 33.2; 5169 17.325 14.0385 33.2; 5170 17.525 14.0385 33.2;
    5171 17.725 14.0385 33.2; 5172 17.925 14.0385 33.2; 5173 15.125 14.2308 33.2;
    5174 15.325 14.2308 33.2; 5175 15.525 14.2308 33.2; 5176 15.725 14.2308 33.2;
    5177 15.925 14.2308 33.2; 5178 16.125 14.2308 33.2; 5179 16.325 14.2308 33.2;
    5180 16.525 14.2308 33.2; 5181 16.725 14.2308 33.2; 5182 16.925 14.2308 33.2;
    5183 17.125 14.2308 33.2; 5184 17.325 14.2308 33.2; 5185 17.525 14.2308 33.2;
    5186 17.725 14.2308 33.2; 5187 17.925 14.2308 33.2; 5188 15.125 14.4231 33.2;
    5189 15.325 14.4231 33.2; 5190 15.525 14.4231 33.2; 5191 15.725 14.4231 33.2;
    5192 15.925 14.4231 33.2; 5193 16.125 14.4231 33.2; 5194 16.325 14.4231 33.2;
    5195 16.525 14.4231 33.2; 5196 16.725 14.4231 33.2; 5197 16.925 14.4231 33.2;
    5198 17.125 14.4231 33.2; 5199 17.325 14.4231 33.2; 5200 17.525 14.4231 33.2;
    5201 17.725 14.4231 33.2; 5202 17.925 14.4231 33.2; 5203 15.125 14.6154 33.2;
    5204 15.325 14.6154 33.2; 5205 15.525 14.6154 33.2; 5206 15.725 14.6154 33.2;
    5207 15.925 14.6154 33.2; 5208 16.125 14.6154 33.2; 5209 16.325 14.6154 33.2;
    5210 16.525 14.6154 33.2; 5211 16.725 14.6154 33.2; 5212 16.925 14.6154 33.2;
    5213 17.125 14.6154 33.2; 5214 17.325 14.6154 33.2; 5215 17.525 14.6154 33.2;
    5216 17.725 14.6154 33.2; 5217 17.925 14.6154 33.2; 5218 15.125 14.8077 33.2;
    5219 15.325 14.8077 33.2; 5220 15.525 14.8077 33.2; 5221 15.725 14.8077 33.2;
    5222 15.925 14.8077 33.2; 5223 16.125 14.8077 33.2; 5224 16.325 14.8077 33.2;
    5225 16.525 14.8077 33.2; 5226 16.725 14.8077 33.2; 5227 16.925 14.8077 33.2;
    5228 17.125 14.8077 33.2; 5229 17.325 14.8077 33.2; 5230 17.525 14.8077 33.2;
    5231 17.725 14.8077 33.2; 5232 17.925 14.8077 33.2; 5233 15.125 15 33.2;
    5234 15.325 15 33.2; 5235 15.525 15 33.2; 5236 15.725 15 33.2;
    5237 15.925 15 33.2; 5238 16.125 15 33.2; 5239 16.325 15 33.2;
    5240 16.525 15 33.2; 5241 16.725 15 33.2; 5242 16.925 15 33.2;
    5243 17.125 15 33.2; 5244 17.325 15 33.2; 5245 17.525 15 33.2;
    5246 17.725 15 33.2; 5247 17.925 15 33.2; 5248 15.125 15.1923 33.2;
    5249 15.325 15.1923 33.2; 5250 15.525 15.1923 33.2; 5251 15.725 15.1923 33.2;
    5252 15.925 15.1923 33.2; 5253 16.125 15.1923 33.2; 5254 16.325 15.1923 33.2;
    5255 16.525 15.1923 33.2; 5256 16.725 15.1923 33.2; 5257 16.925 15.1923 33.2;
    5258 17.125 15.1923 33.2; 5259 17.325 15.1923 33.2; 5260 17.525 15.1923 33.2;
    5261 17.725 15.1923 33.2; 5262 17.925 15.1923 33.2; 5263 15.125 15.3846 33.2;
    5264 15.325 15.3846 33.2; 5265 15.525 15.3846 33.2; 5266 15.725 15.3846 33.2;
    5267 15.925 15.3846 33.2; 5268 16.125 15.3846 33.2; 5269 16.325 15.3846 33.2;
    5270 16.525 15.3846 33.2; 5271 16.725 15.3846 33.2; 5272 16.925 15.3846 33.2;
    5273 17.125 15.3846 33.2; 5274 17.325 15.3846 33.2; 5275 17.525 15.3846 33.2;
    5276 17.725 15.3846 33.2; 5277 17.925 15.3846 33.2; 5278 15.125 15.5769 33.2;
    5279 15.325 15.5769 33.2; 5280 15.525 15.5769 33.2; 5281 15.725 15.5769 33.2;
    5282 15.925 15.5769 33.2; 5283 16.125 15.5769 33.2; 5284 16.325 15.5769 33.2;
    5285 16.525 15.5769 33.2; 5286 16.725 15.5769 33.2; 5287 16.925 15.5769 33.2;
    5288 17.125 15.5769 33.2; 5289 17.325 15.5769 33.2; 5290 17.525 15.5769 33.2;
    5291 17.725 15.5769 33.2; 5292 17.925 15.5769 33.2; 5293 15.125 15.7692 33.2;
    5294 15.325 15.7692 33.2; 5295 15.525 15.7692 33.2; 5296 15.725 15.7692 33.2;
    5297 15.925 15.7692 33.2; 5298 16.125 15.7692 33.2; 5299 16.325 15.7692 33.2;
    5300 16.525 15.7692 33.2; 5301 16.725 15.7692 33.2; 5302 16.925 15.7692 33.2;
    5303 17.125 15.7692 33.2; 5304 17.325 15.7692 33.2; 5305 17.525 15.7692 33.2;
    5306 17.725 15.7692 33.2; 5307 17.925 15.7692 33.2; 5308 15.125 15.9615 33.2;
    5309 15.325 15.9615 33.2; 5310 15.525 15.9615 33.2; 5311 15.725 15.9615 33.2;
    5312 15.925 15.9615 33.2; 5313 16.125 15.9615 33.2; 5314 16.325 15.9615 33.2;
    5315 16.525 15.9615 33.2; 5316 16.725 15.9615 33.2; 5317 16.925 15.9615 33.2;
    5318 17.125 15.9615 33.2; 5319 17.325 15.9615 33.2; 5320 17.525 15.9615 33.2;
    5321 17.725 15.9615 33.2; 5322 17.925 15.9615 33.2; 5323 15.125 16.1538 33.2;
    5324 15.325 16.1538 33.2; 5325 15.525 16.1538 33.2; 5326 15.725 16.1538 33.2;
    5327 15.925 16.1538 33.2; 5328 16.125 16.1538 33.2; 5329 16.325 16.1538 33.2;
    5330 16.525 16.1538 33.2; 5331 16.725 16.1538 33.2; 5332 16.925 16.1538 33.2;
    5333 17.125 16.1538 33.2; 5334 17.325 16.1538 33.2; 5335 17.525 16.1538 33.2;
    5336 17.725 16.1538 33.2; 5337 17.925 16.1538 33.2; 5338 15.125 16.3462 33.2;
    5339 15.325 16.3462 33.2; 5340 15.525 16.3462 33.2; 5341 15.725 16.3462 33.2;
    5342 15.925 16.3462 33.2; 5343 16.125 16.3462 33.2; 5344 16.325 16.3462 33.2;
    5345 16.525 16.3462 33.2; 5346 16.725 16.3462 33.2; 5347 16.925 16.3462 33.2;
    5348 17.125 16.3462 33.2; 5349 17.325 16.3462 33.2; 5350 17.525 16.3462 33.2;
    5351 17.725 16.3462 33.2; 5352 17.925 16.3462 33.2; 5353 15.125 16.5385 33.2;
    5354 15.325 16.5385 33.2; 5355 15.525 16.5385 33.2; 5356 15.725 16.5385 33.2;
    5357 15.925 16.5385 33.2; 5358 16.125 16.5385 33.2; 5359 16.325 16.5385 33.2;
    5360 16.525 16.5385 33.2; 5361 16.725 16.5385 33.2; 5362 16.925 16.5385 33.2;
    5363 17.125 16.5385 33.2; 5364 17.325 16.5385 33.2; 5365 17.525 16.5385 33.2;
    5366 17.725 16.5385 33.2; 5367 17.925 16.5385 33.2; 5368 15.125 16.7308 33.2;
    5369 15.325 16.7308 33.2; 5370 15.525 16.7308 33.2; 5371 15.725 16.7308 33.2;
    5372 15.925 16.7308 33.2; 5373 16.125 16.7308 33.2; 5374 16.325 16.7308 33.2;
    5375 16.525 16.7308 33.2; 5376 16.725 16.7308 33.2; 5377 16.925 16.7308 33.2;
    5378 17.125 16.7308 33.2; 5379 17.325 16.7308 33.2; 5380 17.525 16.7308 33.2;
    5381 17.725 16.7308 33.2; 5382 17.925 16.7308 33.2; 5383 15.125 16.9231 33.2;
    5384 15.325 16.9231 33.2; 5385 15.525 16.9231 33.2; 5386 15.725 16.9231 33.2;
    5387 15.925 16.9231 33.2; 5388 16.125 16.9231 33.2; 5389 16.325 16.9231 33.2;
    5390 16.525 16.9231 33.2; 5391 16.725 16.9231 33.2; 5392 16.925 16.9231 33.2;
    5393 17.125 16.9231 33.2; 5394 17.325 16.9231 33.2; 5395 17.525 16.9231 33.2;
    5396 17.725 16.9231 33.2; 5397 17.925 16.9231 33.2; 5398 15.125 17.1154 33.2;
    5399 15.325 17.1154 33.2; 5400 15.525 17.1154 33.2; 5401 15.725 17.1154 33.2;
    5402 15.925 17.1154 33.2; 5403 16.125 17.1154 33.2; 5404 16.325 17.1154 33.2;
    5405 16.525 17.1154 33.2; 5406 16.725 17.1154 33.2; 5407 16.925 17.1154 33.2;
    5408 17.125 17.1154 33.2; 5409 17.325 17.1154 33.2; 5410 17.525 17.1154 33.2;
    5411 17.725 17.1154 33.2; 5412 17.925 17.1154 33.2; 5413 15.125 17.3077 33.2;
    5414 15.325 17.3077 33.2; 5415 15.525 17.3077 33.2; 5416 15.725 17.3077 33.2;
    5417 15.925 17.3077 33.2; 5418 16.125 17.3077 33.2; 5419 16.325 17.3077 33.2;
    5420 16.525 17.3077 33.2; 5421 16.725 17.3077 33.2; 5422 16.925 17.3077 33.2;
    5423 17.125 17.3077 33.2; 5424 17.325 17.3077 33.2; 5425 17.525 17.3077 33.2;
    5426 17.725 17.3077 33.2; 5427 17.925 17.3077 33.2;
    MEMBER INCIDENCES
    1 1 2; 2 2 3; 3 3 4; 4 4 5; 5 1 6; 6 2 7; 7 3 8; 8 4 9; 9 5 10; 10 6 7; 11 7 8;
    12 8 9; 13 9 10; 14 6 11; 15 7 12; 16 8 13; 17 9 14; 18 10 15; 19 11 12;
    20 12 13; 21 13 14; 22 14 15; 23 11 16; 24 12 17; 25 13 18; 26 14 19; 27 15 20;
    28 16 17; 29 17 18; 30 18 19; 31 19 20; 32 16 21; 33 17 22; 34 18 23; 35 19 24;
    36 20 25; 37 21 22; 38 22 23; 39 23 24; 40 24 25; 41 21 26; 42 22 27; 43 23 28;
    44 24 29; 45 25 30; 46 26 27; 47 27 28; 48 28 29; 50 26 31; 51 27 32; 52 28 33;
    54 30 35; 55 31 32; 56 32 33; 57 33 34; 58 34 35; 59 1 36; 60 2 37; 61 3 38;
    62 4 39; 63 5 40; 64 6 41; 65 7 42; 66 8 43; 67 9 44; 68 10 45; 69 11 46;
    70 12 47; 71 13 48; 72 14 49; 73 15 50; 74 16 51; 75 17 52; 76 18 53; 77 19 54;
    78 20 55; 79 21 56; 80 22 57; 81 23 58; 82 24 59; 83 25 60; 84 26 61; 85 27 62;
    86 28 63; 87 29 1016; 88 30 65; 89 31 66; 90 32 67; 91 33 68; 92 34 69;
    93 35 70; 94 36 37; 95 37 211; 96 38 212; 97 39 40; 98 36 41; 99 37 42;
    100 38 43; 101 39 330; 102 40 331; 103 41 42; 104 42 214; 105 43 215;
    106 44 216; 107 41 46; 108 42 47; 109 43 48; 110 44 49; 111 45 50; 112 46 47;
    113 47 217; 114 48 218; 115 49 219; 116 46 51; 117 47 52; 118 48 53; 119 49 54;
    120 50 55; 121 51 52; 122 52 220; 123 53 221; 124 54 222; 125 51 56; 126 52 57;
    127 53 58; 128 54 59; 129 55 60; 130 56 57; 131 57 223; 132 58 224; 133 59 225;
    134 56 61; 135 57 62; 136 58 63; 137 59 64; 138 60 65; 139 61 62; 140 62 226;
    141 63 227; 143 61 66; 144 62 67; 145 63 68; 147 65 70; 148 66 67; 149 67 229;
    150 68 230; 151 69 70; 153 37 72; 154 38 73; 155 39 74; 156 40 75; 158 42 77;
    159 43 78; 160 44 79; 161 45 80; 163 47 82; 164 48 83; 165 49 84; 166 50 85;
    168 52 87; 169 53 88; 170 54 89; 171 55 90; 173 57 92; 174 58 93; 175 59 94;
    176 60 95; 178 62 97; 179 63 98; 180 64 2283; 181 65 100; 183 67 102;
    184 68 103; 185 69 104; 186 70 105; 188 72 232; 189 73 233; 190 74 75;
    192 72 77; 193 73 78; 194 74 332; 195 75 333; 197 77 235; 198 78 236;
    199 79 237; 201 77 82; 202 78 83; 203 79 84; 204 80 85; 206 82 238; 207 83 239;
    208 84 240; 210 82 87; 211 83 88; 212 84 89; 213 85 90; 215 87 241; 216 88 242;
    217 89 243; 219 87 92; 220 88 93; 221 89 94; 222 90 95; 224 92 244; 225 93 245;
    226 94 246; 228 92 97; 229 93 98; 230 94 99; 231 95 100; 233 97 247;
    234 98 248; 237 97 102; 238 98 103; 240 100 105; 242 102 250; 243 103 251;
    244 104 105; 246 72 107; 247 73 108; 248 74 109; 249 75 110; 251 77 112;
    252 78 113; 253 79 114; 254 80 115; 256 82 117; 257 83 118; 258 84 119;
    259 85 120; 261 87 122; 262 88 123; 263 89 124; 264 90 125; 266 92 127;
    267 93 128; 268 94 129; 269 95 130; 271 97 132; 272 98 133; 273 99 3250;
    274 100 135; 276 102 137; 277 103 138; 278 104 139; 279 105 140; 281 107 253;
    282 108 254; 283 109 110; 285 107 112; 286 108 113; 287 109 334; 288 110 335;
    290 112 256; 291 113 257; 292 114 258; 294 112 117; 295 113 118; 296 114 119;
    297 115 120; 299 117 259; 300 118 260; 301 119 261; 303 117 122; 304 118 123;
    305 119 124; 306 120 125; 308 122 262; 309 123 263; 310 124 264; 312 122 127;
    313 123 128; 314 124 129; 315 125 130; 317 127 265; 318 128 266; 319 129 267;
    321 127 132; 322 128 133; 323 129 134; 324 130 135; 326 132 268; 327 133 269;
    330 132 137; 331 133 138; 333 135 140; 335 137 271; 336 138 272; 337 139 140;
    339 107 142; 340 108 143; 341 109 144; 342 110 145; 344 112 147; 345 113 148;
    346 114 149; 347 115 150; 349 117 152; 352 120 155; 354 122 157; 357 125 160;
    359 127 162; 362 130 165; 364 132 167; 367 135 170; 369 137 172; 370 138 173;
    371 139 174; 372 140 175; 374 142 274; 375 143 275; 376 144 145; 378 142 147;
    379 143 148; 380 144 336; 381 145 337; 383 147 277; 384 148 278; 385 149 279;
    387 147 152; 388 148 153; 389 149 154; 390 150 155; 392 152 280; 393 153 281;
    394 154 282; 396 152 157; 397 153 158; 398 154 159; 399 155 160; 401 157 283;
    402 158 284; 403 159 285; 405 157 162; 406 158 163; 407 159 164; 408 160 165;
    410 162 286; 411 163 287; 412 164 288; 414 162 167; 415 163 168; 416 164 169;
    417 165 170; 419 167 289; 420 168 290; 423 167 172; 424 168 173; 426 170 175;
    428 172 292; 429 173 293; 430 174 175; 524 211 38; 525 212 39; 527 214 43;
    528 215 44; 529 216 45; 530 217 48; 531 218 49; 532 219 50; 533 220 53;
    534 221 54; 535 222 55; 536 223 58; 537 224 59; 538 225 60; 539 226 63;
    540 227 64; 542 229 68; 543 230 69; 545 211 214; 546 214 217; 547 217 220;
    548 220 223; 549 223 226; 550 226 229; 551 212 215; 552 215 218; 553 218 221;
    554 221 224; 555 224 227; 556 227 230; 558 216 219; 559 219 222; 560 222 225;
    561 225 228; 563 232 73; 564 233 74; 566 235 78; 567 236 79; 568 237 80;
    569 238 83; 570 239 84; 571 240 85; 572 241 88; 573 242 89; 574 243 90;
    575 244 93; 576 245 94; 577 246 95; 578 247 98; 579 248 99; 581 250 103;
    582 251 104; 584 232 235; 585 235 238; 586 238 241; 587 241 244; 588 244 247;
    589 247 250; 590 233 236; 591 236 239; 592 239 242; 593 242 245; 594 245 248;
    595 248 251; 597 237 240; 598 240 243; 599 243 246; 600 246 249; 602 253 108;
    603 254 109; 605 256 113; 606 257 114; 607 258 115; 608 259 118; 609 260 119;
    610 261 120; 611 262 123; 612 263 124; 613 264 125; 614 265 128; 615 266 129;
    616 267 130; 617 268 133; 618 269 134; 620 271 138; 621 272 139; 623 253 256;
    624 256 259; 625 259 262; 626 262 265; 627 265 268; 628 268 271; 629 254 257;
    630 257 260; 631 260 263; 632 263 266; 633 266 269; 634 269 272; 636 258 261;
    637 261 264; 638 264 267; 639 267 270; 641 274 143; 642 275 144; 644 277 148;
    645 278 149; 646 279 150; 647 280 153; 648 281 154; 649 282 155; 650 283 158;
    651 284 159; 652 285 160; 653 286 163; 654 287 164; 655 288 165; 656 289 168;
    657 290 169; 659 292 173; 660 293 174; 662 274 277; 663 277 280; 664 280 283;
    665 283 286; 666 286 289; 667 289 292; 668 275 278; 669 278 281; 670 281 284;
    671 284 287; 672 287 290; 673 290 293; 675 279 282; 676 282 285; 677 285 288;
    678 288 291; 680 1 295; 681 2 296; 682 3 297; 683 4 298; 684 5 299; 685 6 300;
    686 7 301; 687 8 302; 688 9 303; 689 10 304; 690 11 305; 691 12 306;
    692 13 307; 693 14 308; 694 15 309; 695 16 310; 696 17 311; 697 18 312;
    698 19 313; 699 20 314; 700 21 315; 701 22 316; 702 23 317; 703 24 318;
    704 25 319; 705 26 320; 706 27 321; 707 28 322; 708 29 397; 709 30 324;
    710 31 325; 711 32 326; 712 33 327; 713 34 328; 714 35 329; 715 330 44;
    716 331 45; 717 330 331; 720 332 333; 723 334 335; 726 336 337; 727 332 79;
    728 333 80; 729 334 114; 730 335 115; 731 336 149; 732 337 150; 733 142 338;
    734 143 339; 735 144 340; 736 145 341; 737 147 342; 738 148 343; 739 149 344;
    740 150 345; 741 338 342; 742 339 343; 743 340 344; 744 341 345; 745 338 339;
    746 339 340; 747 340 341; 748 342 343; 749 343 344; 750 344 345; 751 66 346;
    752 67 347; 753 68 348; 754 69 349; 755 70 350; 756 229 351; 757 230 352;
    758 346 347; 759 347 351; 760 348 352; 761 349 350; 762 351 348; 763 352 349;
    765 102 355; 766 103 356; 767 104 357; 768 105 358; 769 250 359; 770 251 360;
    772 355 359; 773 356 360; 774 357 358; 775 359 356; 776 360 357; 778 137 363;
    779 138 364; 780 139 365; 781 140 366; 782 271 367; 783 272 368; 785 363 367;
    786 364 368; 787 365 366; 788 367 364; 789 368 365; 790 134 4217; 791 369 30;
    792 370 65; 793 371 100; 794 372 135; 795 373 170; 796 369 1056; 797 370 2313;
    798 371 3280; 799 369 413; 800 372 4255; 807 375 1430; 808 376 2707;
    809 377 3674; 810 375 619; 811 378 4637; 812 381 34; 814 382 69; 816 383 104;
    818 384 139; 820 385 174; 823 381 1836; 824 382 2963; 825 383 3930;
    826 381 820; 827 384 5013; 828 387 323; 829 388 387; 830 389 388; 831 390 389;
    832 391 390; 833 392 391; 834 393 392; 835 394 393; 836 395 394; 837 396 395;
    838 397 396; 854 413 414; 855 414 415; 856 415 416; 857 416 417; 858 417 418;
    859 418 419; 860 419 420; 861 420 421; 862 421 422; 863 422 423; 864 423 374;
    1072 619 620; 1073 620 621; 1074 621 622; 1075 622 623; 1076 623 624;
    1077 624 625; 1078 625 626; 1079 626 627; 1080 627 628; 1081 628 629;
    1082 629 380; 1275 810 386; 1276 811 810; 1277 812 811; 1278 813 812;
    1279 814 813; 1280 815 814; 1281 816 815; 1282 817 816; 1283 818 817;
    1284 819 818; 1285 820 819; 1493 1016 64; 1507 1030 370; 1508 1031 1030;
    1509 1032 1031; 1510 1033 1032; 1511 1034 1033; 1512 1035 1034; 1513 1036 1035;
    1514 1037 1036; 1515 1038 1037; 1516 1039 1038; 1517 1040 1039; 1518 1041 1040;
    1519 1042 1041; 1520 1043 1042; 1521 1044 1043; 1522 1045 1044; 1523 1046 1045;
    1524 1047 1046; 1525 1048 1047; 1526 1049 1048; 1527 1050 1049; 1528 1051 1050;
    1529 1052 1051; 1530 1053 1052; 1531 1054 1053; 1532 1055 1054; 1533 1056 1055;
    1924 1404 376; 1925 1405 1404; 1926 1406 1405; 1927 1407 1406; 1928 1408 1407;
    1929 1409 1408; 1930 1410 1409; 1931 1411 1410; 1932 1412 1411; 1933 1413 1412;
    1934 1414 1413; 1935 1415 1414; 1936 1416 1415; 1937 1417 1416; 1938 1418 1417;
    1939 1419 1418; 1940 1420 1419; 1941 1421 1420; 1942 1422 1421; 1943 1423 1422;
    1944 1424 1423; 1945 1425 1424; 1946 1426 1425; 1947 1427 1426; 1948 1428 1427;
    1949 1429 1428; 1950 1430 1429; 2399 1836 1837; 2400 1837 1838; 2401 1838 1839;
    2402 1839 1840; 2403 1840 1841; 2404 1841 1842; 2405 1842 1843; 2406 1843 1844;
    2407 1844 1845; 2408 1845 1846; 2409 1846 1847; 2410 1847 1848; 2411 1848 1849;
    2412 1849 1850; 2413 1850 1851; 2414 1851 1852; 2415 1852 1853; 2416 1853 1854;
    2417 1854 1855; 2418 1855 1856; 2419 1856 1857; 2420 1857 1858; 2421 1858 1859;
    2422 1859 1860; 2423 1860 1861; 2424 1861 1862; 2425 1862 382; 2889 2283 99;
    2903 2297 371; 2904 2298 2297; 2905 2299 2298; 2906 2300 2299; 2907 2301 2300;
    2908 2302 2301; 2909 2303 2302; 2910 2304 2303; 2911 2305 2304; 2912 2306 2305;
    2913 2307 2306; 2914 2308 2307; 2915 2309 2308; 2916 2310 2309; 2917 2311 2310;
    2918 2312 2311; 2919 2313 2312; 3333 2691 377; 3334 2692 2691; 3335 2693 2692;
    3336 2694 2693; 3337 2695 2694; 3338 2696 2695; 3339 2697 2696; 3340 2698 2697;
    3341 2699 2698; 3342 2700 2699; 3343 2701 2700; 3344 2702 2701; 3345 2703 2702;
    3346 2704 2703; 3347 2705 2704; 3348 2706 2705; 3349 2707 2706; 3638 2963 2964;
    3639 2964 2965; 3640 2965 2966; 3641 2966 2967; 3642 2967 2968; 3643 2968 2969;
    3644 2969 2970; 3645 2970 2971; 3646 2971 2972; 3647 2972 2973; 3648 2973 2974;
    3649 2974 2975; 3650 2975 2976; 3651 2976 2977; 3652 2977 2978; 3653 2978 2979;
    3654 2979 383; 3958 3250 134; 3972 3264 372; 3973 3265 3264; 3974 3266 3265;
    3975 3267 3266; 3976 3268 3267; 3977 3269 3268; 3978 3270 3269; 3979 3271 3270;
    3980 3272 3271; 3981 3273 3272; 3982 3274 3273; 3983 3275 3274; 3984 3276 3275;
    3985 3277 3276; 3986 3278 3277; 3987 3279 3278; 3988 3280 3279; 4402 3658 378;
    4403 3659 3658; 4404 3660 3659; 4405 3661 3660; 4406 3662 3661; 4407 3663 3662;
    4408 3664 3663; 4409 3665 3664; 4410 3666 3665; 4411 3667 3666; 4412 3668 3667;
    4413 3669 3668; 4414 3670 3669; 4415 3671 3670; 4416 3672 3671; 4417 3673 3672;
    4418 3674 3673; 4707 3930 3931; 4708 3931 3932; 4709 3932 3933; 4710 3933 3934;
    4711 3934 3935; 4712 3935 3936; 4713 3936 3937; 4714 3937 3938; 4715 3938 3939;
    4716 3939 3940; 4717 3940 3941; 4718 3941 3942; 4719 3942 3943; 4720 3943 3944;
    4721 3944 3945; 4722 3945 3946; 4723 3946 384; 5027 4217 169; 5041 4231 373;
    5042 4232 4231; 5043 4233 4232; 5044 4234 4233; 5045 4235 4234; 5046 4236 4235;
    5047 4237 4236; 5048 4238 4237; 5049 4239 4238; 5050 4240 4239; 5051 4241 4240;
    5052 4242 4241; 5053 4243 4242; 5054 4244 4243; 5055 4245 4244; 5056 4246 4245;
    5057 4247 4246; 5058 4248 4247; 5059 4249 4248; 5060 4250 4249; 5061 4251 4250;
    5062 4252 4251; 5063 4253 4252; 5064 4254 4253; 5065 4255 4254; 5463 4613 379;
    5464 4614 4613; 5465 4615 4614; 5466 4616 4615; 5467 4617 4616; 5468 4618 4617;
    5469 4619 4618; 5470 4620 4619; 5471 4621 4620; 5472 4622 4621; 5473 4623 4622;
    5474 4624 4623; 5475 4625 4624; 5476 4626 4625; 5477 4627 4626; 5478 4628 4627;
    5479 4629 4628; 5480 4630 4629; 5481 4631 4630; 5482 4632 4631; 5483 4633 4632;
    5484 4634 4633; 5485 4635 4634; 5486 4636 4635; 5487 4637 4636; 5904 5013 5014;
    5905 5014 5015; 5906 5015 5016; 5907 5016 5017; 5908 5017 5018; 5909 5018 5019;
    5910 5019 5020; 5911 5020 5021; 5912 5021 5022; 5913 5022 5023; 5914 5023 5024;
    5915 5024 5025; 5916 5025 5026; 5917 5026 5027; 5918 5027 5028; 5919 5028 5029;
    5920 5029 5030; 5921 5030 5031; 5922 5031 5032; 5923 5032 5033; 5924 5033 5034;
    5925 5034 5035; 5926 5035 5036; 5927 5036 5037; 5928 5037 385;
    ELEMENT INCIDENCES SHELL
    865 387 439 438 323; 866 439 440 437 438; 867 440 441 436 437;
    868 441 442 435 436; 869 442 443 434 435; 870 443 444 433 434;
    871 444 445 432 433; 872 445 446 431 432; 873 446 447 430 431;
    874 447 448 429 430; 875 448 449 428 429; 876 449 450 427 428;
    877 450 451 426 427; 878 451 452 425 426; 879 452 453 424 425;
    880 453 423 374 424; 881 388 454 439 387; 882 454 455 440 439;
    883 455 456 441 440; 884 456 457 442 441; 885 457 458 443 442;
    886 458 459 444 443; 887 459 460 445 444; 888 460 461 446 445;
    889 461 462 447 446; 890 462 463 448 447; 891 463 464 449 448;
    892 464 465 450 449; 893 465 466 451 450; 894 466 467 452 451;
    895 467 468 453 452; 896 468 422 423 453; 897 389 469 454 388;
    898 469 470 455 454; 899 470 471 456 455; 900 471 472 457 456;
    901 472 473 458 457; 902 473 474 459 458; 903 474 475 460 459;
    904 475 476 461 460; 905 476 477 462 461; 906 477 478 463 462;
    907 478 479 464 463; 908 479 480 465 464; 909 480 481 466 465;
    910 481 482 467 466; 911 482 483 468 467; 912 483 421 422 468;
    913 390 484 469 389; 914 484 485 470 469; 915 485 486 471 470;
    916 486 487 472 471; 917 487 488 473 472; 918 488 489 474 473;
    919 489 490 475 474; 920 490 491 476 475; 921 491 492 477 476;
    922 492 493 478 477; 923 493 494 479 478; 924 494 495 480 479;
    925 495 496 481 480; 926 496 497 482 481; 927 497 498 483 482;
    928 498 420 421 483; 929 391 499 484 390; 930 499 500 485 484;
    931 500 501 486 485; 932 501 502 487 486; 933 502 503 488 487;
    934 503 504 489 488; 935 504 505 490 489; 936 505 506 491 490;
    937 506 507 492 491; 938 507 508 493 492; 939 508 509 494 493;
    940 509 510 495 494; 941 510 511 496 495; 942 511 512 497 496;
    943 512 513 498 497; 944 513 419 420 498; 945 392 514 499 391;
    946 514 515 500 499; 947 515 516 501 500; 948 516 517 502 501;
    949 517 518 503 502; 950 518 519 504 503; 951 519 520 505 504;
    952 520 521 506 505; 953 521 522 507 506; 954 522 523 508 507;
    955 523 524 509 508; 956 524 525 510 509; 957 525 526 511 510;
    958 526 527 512 511; 959 527 528 513 512; 960 528 418 419 513;
    961 393 529 514 392; 962 529 530 515 514; 963 530 531 516 515;
    964 531 532 517 516; 965 532 533 518 517; 966 533 534 519 518;
    967 534 535 520 519; 968 535 536 521 520; 969 536 537 522 521;
    970 537 538 523 522; 971 538 539 524 523; 972 539 540 525 524;
    973 540 541 526 525; 974 541 542 527 526; 975 542 543 528 527;
    976 543 417 418 528; 977 394 544 529 393; 978 544 545 530 529;
    979 545 546 531 530; 980 546 547 532 531; 981 547 548 533 532;
    982 548 549 534 533; 983 549 550 535 534; 984 550 551 536 535;
    985 551 552 537 536; 986 552 553 538 537; 987 553 554 539 538;
    988 554 555 540 539; 989 555 556 541 540; 990 556 557 542 541;
    991 557 558 543 542; 992 558 416 417 543; 993 395 559 544 394;
    994 559 560 545 544; 995 560 561 546 545; 996 561 562 547 546;
    997 562 563 548 547; 998 563 564 549 548; 999 564 565 550 549;
    1000 565 566 551 550; 1001 566 567 552 551; 1002 567 568 553 552;
    1003 568 569 554 553; 1004 569 570 555 554; 1005 570 571 556 555;
    1006 571 572 557 556; 1007 572 573 558 557; 1008 573 415 416 558;
    1009 396 574 559 395; 1010 574 575 560 559; 1011 575 576 561 560;
    1012 576 577 562 561; 1013 577 578 563 562; 1014 578 579 564 563;
    1015 579 580 565 564; 1016 580 581 566 565; 1017 581 582 567 566;
    1018 582 583 568 567; 1019 583 584 569 568; 1020 584 585 570 569;
    1021 585 586 571 570; 1022 586 587 572 571; 1023 587 588 573 572;
    1024 588 414 415 573; 1025 397 589 574 396; 1026 589 590 575 574;
    1027 590 591 576 575; 1028 591 592 577 576; 1029 592 593 578 577;
    1030 593 594 579 578; 1031 594 595 580 579; 1032 595 596 581 580;
    1033 596 597 582 581; 1034 597 598 583 582; 1035 598 599 584 583;
    1036 599 600 585 584; 1037 600 601 586 585; 1038 601 602 587 586;
    1039 602 603 588 587; 1040 603 413 414 588; 1041 29 398 589 397;
    1042 398 399 590 589; 1043 399 400 591 590; 1044 400 401 592 591;
    1045 401 402 593 592; 1046 402 403 594 593; 1047 403 404 595 594;
    1048 404 405 596 595; 1049 405 406 597 596; 1050 406 407 598 597;
    1051 407 408 599 598; 1052 408 409 600 599; 1053 409 410 601 600;
    1054 410 411 602 601; 1055 411 412 603 602; 1056 412 369 413 603;
    1083 423 645 644 374; 1084 645 646 643 644; 1085 646 647 642 643;
    1086 647 648 641 642; 1087 648 649 640 641; 1088 649 650 639 640;
    1089 650 651 638 639; 1090 651 652 637 638; 1091 652 653 636 637;
    1092 653 654 635 636; 1093 654 655 634 635; 1094 655 656 633 634;
    1095 656 657 632 633; 1096 657 658 631 632; 1097 658 659 630 631;
    1098 659 629 380 630; 1099 422 660 645 423; 1100 660 661 646 645;
    1101 661 662 647 646; 1102 662 663 648 647; 1103 663 664 649 648;
    1104 664 665 650 649; 1105 665 666 651 650; 1106 666 667 652 651;
    1107 667 668 653 652; 1108 668 669 654 653; 1109 669 670 655 654;
    1110 670 671 656 655; 1111 671 672 657 656; 1112 672 673 658 657;
    1113 673 674 659 658; 1114 674 628 629 659; 1115 421 675 660 422;
    1116 675 676 661 660; 1117 676 677 662 661; 1118 677 678 663 662;
    1119 678 679 664 663; 1120 679 680 665 664; 1121 680 681 666 665;
    1122 681 682 667 666; 1123 682 683 668 667; 1124 683 684 669 668;
    1125 684 685 670 669; 1126 685 686 671 670; 1127 686 687 672 671;
    1128 687 688 673 672; 1129 688 689 674 673; 1130 689 627 628 674;
    1131 420 690 675 421; 1132 690 691 676 675; 1133 691 692 677 676;
    1134 692 693 678 677; 1135 693 694 679 678; 1136 694 695 680 679;
    1137 695 696 681 680; 1138 696 697 682 681; 1139 697 698 683 682;
    1140 698 699 684 683; 1141 699 700 685 684; 1142 700 701 686 685;
    1143 701 702 687 686; 1144 702 703 688 687; 1145 703 704 689 688;
    1146 704 626 627 689; 1147 419 705 690 420; 1148 705 706 691 690;
    1149 706 707 692 691; 1150 707 708 693 692; 1151 708 709 694 693;
    1152 709 710 695 694; 1153 710 711 696 695; 1154 711 712 697 696;
    1155 712 713 698 697; 1156 713 714 699 698; 1157 714 715 700 699;
    1158 715 716 701 700; 1159 716 717 702 701; 1160 717 718 703 702;
    1161 718 719 704 703; 1162 719 625 626 704; 1163 418 720 705 419;
    1164 720 721 706 705; 1165 721 722 707 706; 1166 722 723 708 707;
    1167 723 724 709 708; 1168 724 725 710 709; 1169 725 726 711 710;
    1170 726 727 712 711; 1171 727 728 713 712; 1172 728 729 714 713;
    1173 729 730 715 714; 1174 730 731 716 715; 1175 731 732 717 716;
    1176 732 733 718 717; 1177 733 734 719 718; 1178 734 624 625 719;
    1179 417 735 720 418; 1180 735 736 721 720; 1181 736 737 722 721;
    1182 737 738 723 722; 1183 738 739 724 723; 1184 739 740 725 724;
    1185 740 741 726 725; 1186 741 742 727 726; 1187 742 743 728 727;
    1188 743 744 729 728; 1189 744 745 730 729; 1190 745 746 731 730;
    1191 746 747 732 731; 1192 747 748 733 732; 1193 748 749 734 733;
    1194 749 623 624 734; 1195 416 750 735 417; 1196 750 751 736 735;
    1197 751 752 737 736; 1198 752 753 738 737; 1199 753 754 739 738;
    1200 754 755 740 739; 1201 755 756 741 740; 1202 756 757 742 741;
    1203 757 758 743 742; 1204 758 759 744 743; 1205 759 760 745 744;
    1206 760 761 746 745; 1207 761 762 747 746; 1208 762 763 748 747;
    1209 763 764 749 748; 1210 764 622 623 749; 1211 415 765 750 416;
    1212 765 766 751 750; 1213 766 767 752 751; 1214 767 768 753 752;
    1215 768 769 754 753; 1216 769 770 755 754; 1217 770 771 756 755;
    1218 771 772 757 756; 1219 772 773 758 757; 1220 773 774 759 758;
    1221 774 775 760 759; 1222 775 776 761 760; 1223 776 777 762 761;
    1224 777 778 763 762; 1225 778 779 764 763; 1226 779 621 622 764;
    1227 414 780 765 415; 1228 780 781 766 765; 1229 781 782 767 766;
    1230 782 783 768 767; 1231 783 784 769 768; 1232 784 785 770 769;
    1233 785 786 771 770; 1234 786 787 772 771; 1235 787 788 773 772;
    1236 788 789 774 773; 1237 789 790 775 774; 1238 790 791 776 775;
    1239 791 792 777 776; 1240 792 793 778 777; 1241 793 794 779 778;
    1242 794 620 621 779; 1243 413 795 780 414; 1244 795 796 781 780;
    1245 796 797 782 781; 1246 797 798 783 782; 1247 798 799 784 783;
    1248 799 800 785 784; 1249 800 801 786 785; 1250 801 802 787 786;
    1251 802 803 788 787; 1252 803 804 789 788; 1253 804 805 790 789;
    1254 805 806 791 790; 1255 806 807 792 791; 1256 807 808 793 792;
    1257 808 809 794 793; 1258 809 619 620 794; 1259 369 604 795 413;
    1260 604 605 796 795; 1261 605 606 797 796; 1262 606 607 798 797;
    1263 607 608 799 798; 1264 608 609 800 799; 1265 609 610 801 800;
    1266 610 611 802 801; 1267 611 612 803 802; 1268 612 613 804 803;
    1269 613 614 805 804; 1270 614 615 806 805; 1271 615 616 807 806;
    1272 616 617 808 807; 1273 617 618 809 808; 1274 618 375 619 809;
    1301 810 851 850 386; 1302 851 852 849 850; 1303 852 853 848 849;
    1304 853 854 847 848; 1305 854 855 846 847; 1306 855 856 845 846;
    1307 856 857 844 845; 1308 857 858 843 844; 1309 858 859 842 843;
    1310 859 860 841 842; 1311 860 861 840 841; 1312 861 862 839 840;
    1313 862 863 838 839; 1314 863 864 837 838; 1315 864 865 836 837;
    1316 865 629 380 836; 1317 811 866 851 810; 1318 866 867 852 851;
    1319 867 868 853 852; 1320 868 869 854 853; 1321 869 870 855 854;
    1322 870 871 856 855; 1323 871 872 857 856; 1324 872 873 858 857;
    1325 873 874 859 858; 1326 874 875 860 859; 1327 875 876 861 860;
    1328 876 877 862 861; 1329 877 878 863 862; 1330 878 879 864 863;
    1331 879 880 865 864; 1332 880 628 629 865; 1333 812 881 866 811;
    1334 881 882 867 866; 1335 882 883 868 867; 1336 883 884 869 868;
    1337 884 885 870 869; 1338 885 886 871 870; 1339 886 887 872 871;
    1340 887 888 873 872; 1341 888 889 874 873; 1342 889 890 875 874;
    1343 890 891 876 875; 1344 891 892 877 876; 1345 892 893 878 877;
    1346 893 894 879 878; 1347 894 895 880 879; 1348 895 627 628 880;
    1349 813 896 881 812; 1350 896 897 882 881; 1351 897 898 883 882;
    1352 898 899 884 883; 1353 899 900 885 884; 1354 900 901 886 885;
    1355 901 902 887 886; 1356 902 903 888 887; 1357 903 904 889 888;
    1358 904 905 890 889; 1359 905 906 891 890; 1360 906 907 892 891;
    1361 907 908 893 892; 1362 908 909 894 893; 1363 909 910 895 894;
    1364 910 626 627 895; 1365 814 911 896 813; 1366 911 912 897 896;
    1367 912 913 898 897; 1368 913 914 899 898; 1369 914 915 900 899;
    1370 915 916 901 900; 1371 916 917 902 901; 1372 917 918 903 902;
    1373 918 919 904 903; 1374 919 920 905 904; 1375 920 921 906 905;
    1376 921 922 907 906; 1377 922 923 908 907; 1378 923 924 909 908;
    1379 924 925 910 909; 1380 925 625 626 910; 1381 815 926 911 814;
    1382 926 927 912 911; 1383 927 928 913 912; 1384 928 929 914 913;
    1385 929 930 915 914; 1386 930 931 916 915; 1387 931 932 917 916;
    1388 932 933 918 917; 1389 933 934 919 918; 1390 934 935 920 919;
    1391 935 936 921 920; 1392 936 937 922 921; 1393 937 938 923 922;
    1394 938 939 924 923; 1395 939 940 925 924; 1396 940 624 625 925;
    1397 816 941 926 815; 1398 941 942 927 926; 1399 942 943 928 927;
    1400 943 944 929 928; 1401 944 945 930 929; 1402 945 946 931 930;
    1403 946 947 932 931; 1404 947 948 933 932; 1405 948 949 934 933;
    1406 949 950 935 934; 1407 950 951 936 935; 1408 951 952 937 936;
    1409 952 953 938 937; 1410 953 954 939 938; 1411 954 955 940 939;
    1412 955 623 624 940; 1413 817 956 941 816; 1414 956 957 942 941;
    1415 957 958 943 942; 1416 958 959 944 943; 1417 959 960 945 944;
    1418 960 961 946 945; 1419 961 962 947 946; 1420 962 963 948 947;
    1421 963 964 949 948; 1422 964 965 950 949; 1423 965 966 951 950;
    1424 966 967 952 951; 1425 967 968 953 952; 1426 968 969 954 953;
    1427 969 970 955 954; 1428 970 622 623 955; 1429 818 971 956 817;
    1430 971 972 957 956; 1431 972 973 958 957; 1432 973 974 959 958;
    1433 974 975 960 959; 1434 975 976 961 960; 1435 976 977 962 961;
    1436 977 978 963 962; 1437 978 979 964 963; 1438 979 980 965 964;
    1439 980 981 966 965; 1440 981 982 967 966; 1441 982 983 968 967;
    1442 983 984 969 968; 1443 984 985 970 969; 1444 985 621 622 970;
    1445 819 986 971 818; 1446 986 987 972 971; 1447 987 988 973 972;
    1448 988 989 974 973; 1449 989 990 975 974; 1450 990 991 976 975;
    1451 991 992 977 976; 1452 992 993 978 977; 1453 993 994 979 978;
    1454 994 995 980 979; 1455 995 996 981 980; 1456 996 997 982 981;
    1457 997 998 983 982; 1458 998 999 984 983; 1459 999 1000 985 984;
    1460 1000 620 621 985; 1461 820 1001 986 819; 1462 1001 1002 987 986;
    1463 1002 1003 988 987; 1464 1003 1004 989 988; 1465 1004 1005 990 989;
    1466 1005 1006 991 990; 1467 1006 1007 992 991; 1468 1007 1008 993 992;
    1469 1008 1009 994 993; 1470 1009 1010 995 994; 1471 1010 1011 996 995;
    1472 1011 1012 997 996; 1473 1012 1013 998 997; 1474 1013 1014 999 998;
    1475 1014 1015 1000 999; 1476 1015 619 620 1000; 1477 381 821 1001 820;
    1478 821 822 1002 1001; 1479 822 823 1003 1002; 1480 823 824 1004 1003;
    1481 824 825 1005 1004; 1482 825 826 1006 1005; 1483 826 827 1007 1006;
    1484 827 828 1008 1007; 1485 828 829 1009 1008; 1486 829 830 1010 1009;
    1487 830 831 1011 1010; 1488 831 832 1012 1011; 1489 832 833 1013 1012;
    1490 833 834 1014 1013; 1491 834 835 1015 1014; 1492 835 375 619 1015;
    1534 1148 1288 1140 1153; 1535 1260 1185 1167 1253; 1536 1110 1160 1175 1321;
    1537 1078 1073 1294 1369; 1538 1062 1094 1065 1285; 1539 1086 1197 1118 1061;
    1540 1175 1033 1034 1143; 1541 1181 1105 1084 1108; 1542 1288 1292 1264 1066;
    1543 1095 1055 1056 1072; 1544 1304 1221 1315 1059; 1545 1205 1099 409 408;
    1546 1102 1190 1192 1350; 1547 1089 1376 1132 1120; 1548 1026 1027 1102 1101;
    1549 1237 1171 1240 1016; 1550 1099 1177 410 409; 1551 1284 1226 1313 1256;
    1552 1157 1030 1031 1197; 1553 1251 1107 1173 1079; 1554 64 1242 1237 1016;
    1555 1315 1300 1062 1285; 1556 1123 1110 1321 1114; 1557 1185 1126 1198 1167;
    1558 1268 1253 1166 1080; 1559 1161 1193 1095 1346; 1560 1359 1297 1142 1263;
    1561 1117 1051 1052 1100; 1562 1297 1308 1125 1142; 1563 1288 1066 1260 1140;
    1564 1018 1019 1277 1069; 1565 1349 1341 1351 1281; 1566 1071 1183 1209 1364;
    1567 1233 1339 1203 1362; 1568 1198 1274 1136 1167; 1569 1350 1192 1365 1334;
    1570 1219 1355 1089 1141; 1571 1183 1106 1093 1209; 1572 1103 1035 1036 1104;
    1573 1185 1134 1363 1126; 1574 1312 1205 408 407; 1575 1115 1210 1323 1232;
    1576 1361 1269 1206 1308; 1577 1240 1348 1333 1335; 1578 1295 1325 1122 1380;
    1579 1352 1163 1177 1099; 1580 1081 1086 1061 1220; 1581 1177 1354 411 410;
    1582 1220 1061 1110 1123; 1583 1182 1053 1054 1193; 1584 1140 1260 1253 1268;
    1585 1217 1138 1377 1057; 1586 1264 1340 1137 1066; 1587 1299 1349 1281 1088;
    1588 1142 1125 1366 1298; 1589 1224 1100 1096 1269; 1590 1225 1164 1239 1292;
    1591 1076 1338 1301 1247; 1592 1212 1275 1207 1213; 1593 1144 1241 1058 1151;
    1594 1215 1133 402 401; 1595 1152 1150 1279 1168; 1596 1312 1323 1099 1205;
    1597 1335 1145 1372 1388; 1598 1229 1060 1221 1304; 1599 1319 1218 1331 1337;
    1600 1365 1322 1154 1124; 1601 1343 1320 1155 1067; 1602 1124 1154 1355 1219;
    1603 1249 1090 1172 1116; 1604 1165 1098 1313 1226; 1605 1072 1056 369 412;
    1606 1222 1367 1336 1322; 1607 1127 1374 1179 1354; 1608 1067 1155 1063 1068;
    1609 1354 1179 412 411; 1610 1248 1057 1144 1307; 1611 1215 1319 1337 1133;
    1612 1096 1250 1107 1251; 1613 1167 1136 1248 1267; 1614 1023 1024 1169 1148;
    1615 1065 1117 1100 1224; 1616 1192 1222 1322 1365; 1617 1197 1031 1032 1118;
    1618 1179 1174 1072 412; 1619 1021 1022 1149 1070; 1620 1137 1303 1134 1185;
    1621 1316 1282 1295 1154; 1622 1024 1025 1112 1169; 1623 1121 1289 1202 1090;
    1624 1073 1249 1116 1294; 1625 1087 1189 1157 1199; 1626 1285 1065 1224 1384;
    1627 1190 1236 1222 1192; 1628 1145 1078 1369 1372; 1629 1171 1071 1348 1240;
    1630 1307 1144 1151 1162; 1631 1162 1151 1278 1093; 1632 1360 1298 1076 1178;
    1633 1344 1038 1039 1305; 1634 1313 1208 1266 1330; 1635 1092 1245 1311 1255;
    1636 1236 1180 1367 1222; 1637 1025 1026 1101 1112; 1638 1068 1063 1138 1217;
    1639 1322 1336 1316 1154; 1640 1372 1369 1319 1215; 1641 1111 1113 1085 1328;
    1642 1118 1032 1033 1175; 1643 1291 1199 1086 1081; 1644 1382 1084 1204 1283;
    1645 1283 1212 1213 1238; 1646 1166 1196 1071 1171; 1647 1380 1122 1147 1074;
    1648 1372 1215 401 400; 1649 1378 1059 1384 1246; 1650 1286 1168 1227 1064;
    1651 1367 1119 1368 1336; 1652 1158 1271 1272 1121; 1653 1142 1298 1360 1332;
    1654 1101 1102 1244 1164; 1655 1234 1230 1352 1099; 1656 1385 1060 1229 1311;
    1657 1341 1079 1173 1351; 1658 1186 1200 1314 1290; 1659 228 370 1189 1201;
    1660 1116 1172 1261 1218; 1661 1335 1333 1228 1145; 1662 1169 1159 1288 1148;
    1663 1263 1142 1332 1233; 1664 1388 1372 399 398; 1665 1294 1116 1218 1319;
    1666 1180 1087 1199 1291; 1667 1104 1036 1037 1252; 1668 1264 1186 1290 1340;
    1669 1274 1286 1064 1136; 1670 1302 1380 1074 1376; 1671 1227 1270 1068 1217;
    1672 1058 1241 1075 1383; 1673 1258 1147 1143 1176; 1674 1189 370 1030 1157;
    1675 1196 1307 1106 1183; 1676 1301 1299 1088 1195; 1677 1199 1157 1197 1086;
    1678 1236 1201 1087 1180; 1679 1261 1312 407 406; 1680 1180 1291 1119 1367;
    1681 1281 1161 1346 1374; 1682 1327 1251 1079 1341; 1683 1094 1051 1117 1065;
    1684 1059 1315 1285 1384; 1685 1168 1279 1270 1227; 1686 1098 1176 1266 1208;
    1687 1289 1345 1115 1232; 1688 1252 1037 1038 1344; 1689 1287 1083 1231 1342;
    1690 1357 1214 1092 1356; 1691 1163 1127 1354 1177; 1692 1265 1131 1375 1257;
    1693 1279 1067 1068 1270; 1694 1272 1345 1289 1121; 1695 1383 1075 1083 1287;
    1696 1216 1379 1357 1091; 1697 1376 1074 1258 1165; 1698 1155 1344 1305 1063;
    1699 1073 1097 1158 1249; 1700 1256 1313 1330 1152; 1701 1326 1327 1341 1349;
    1702 1115 1359 1263 1210; 1703 1376 1165 1226 1132; 1704 1373 1104 1252 1320;
    1705 1320 1252 1344 1155; 1706 1342 1048 1049 1191; 1707 1187 1092 1255 1254;
    1708 1195 1088 1127 1163; 1709 1331 1218 405 404; 1710 1057 1377 1324 1144;
    1711 1075 1045 1046 1083; 1712 1269 1096 1251 1327; 1713 1184 1326 1349 1299;
    1714 1077 1259 1211 1271; 1715 1028 1029 1236 1190; 1716 1375 1342 1191 1243;
    1717 1271 1211 1296 1272; 1718 1016 1240 1335 1388; 1719 1016 1388 398 29;
    1720 1266 1103 1104 1373; 1721 1176 1143 1103 1266; 1722 1221 1243 1300 1315;
    1723 1254 1255 1259 1077; 1724 1321 1175 1143 1147; 1725 1214 1135 1386 1245;
    1726 1308 1206 1366 1125; 1727 1119 1291 1081 1113; 1728 1017 1018 1069 1370;
    1729 1066 1137 1185 1260; 1730 1085 1220 1123 1317; 1731 1083 1046 1047 1231;
    1732 1300 1109 1094 1062; 1733 1334 1365 1124 1219; 1734 1243 1191 1109 1300;
    1735 1370 1153 1140 1268; 1736 1090 1202 1188 1172; 1737 1156 1320 1343 1139;
    1738 1187 1254 1097 1280; 1739 1345 1318 1359 1115; 1740 1377 1170 1223 1324;
    1741 1088 1281 1374 1127; 1742 1209 1216 1091 1353; 1743 1170 1041 1042 1223;
    1744 1257 1375 1243 1060; 1745 1093 1278 1216 1209; 1746 1305 1039 1040 1387;
    1747 1131 1287 1342 1375; 1748 1249 1158 1121 1090; 1749 1244 1102 1350 1200;
    1750 1129 1347 1274 1198; 1751 1058 1383 1130 1146; 1752 1384 1224 1269 1361;
    1753 1371 1304 1059 1378; 1754 1374 1346 1174 1179; 1755 1165 1258 1176 1098;
    1756 1228 1280 1078 1145; 1757 1122 1114 1321 1147; 1758 1255 1235 1211 1259;
    1759 1246 1384 1361 1128; 1760 1218 1261 406 405; 1761 1241 1044 1045 1075;
    1762 1351 1173 1161 1281; 1763 1387 1040 1041 1170; 1764 1143 1034 1035 1103;
    1765 1330 1266 1150 1152; 1766 1348 1071 1364 1333; 1767 1311 1229 1235 1255;
    1768 1318 1128 1297 1359; 1769 1210 1362 1234 1323; 1770 1340 1290 1303 1137;
    1771 1061 1118 1160 1110; 1772 1135 1262 1306 1386; 1773 1355 1302 1376 1089;
    1774 1223 1043 1044 1241; 1775 1273 1130 1131 1265; 1776 1213 1207 1381 1286;
    1777 1154 1380 1302 1355; 1778 1027 1028 1190 1102; 1779 1082 1114 1122 1325;
    1780 1193 1054 1055 1095; 1781 1230 1194 1358 1352; 1782 1150 1156 1139 1279;
    1783 1362 1203 1230 1234; 1784 1266 1373 1156 1150; 1785 1069 1277 1153 1370;
    1786 1133 1337 403 402; 1787 1280 1097 1073 1078; 1788 1126 1363 1129 1198;
    1789 1346 1095 1072 1174; 1790 1309 1353 1356 1329; 1791 1329 1356 1092 1187;
    1792 1022 1023 1148 1149; 1793 1353 1091 1357 1356; 1794 1277 1070 1149 1153;
    1795 1106 1307 1162 1093; 1796 1357 1379 1135 1214; 1797 64 1017 1370 1242;
    1798 1119 1113 1111 1368; 1799 1139 1343 1067 1279; 1800 1159 1225 1292 1288;
    1801 1347 1213 1286 1274; 1802 1202 1289 1232 1188; 1803 1134 1108 1310 1363;
    1804 1275 1256 1152 1276; 1805 1063 1305 1387 1138; 1806 1200 1350 1334 1314;
    1807 1141 1089 1120 1105; 1808 1144 1324 1223 1241; 1809 1229 1304 1371 1235;
    1810 1368 1111 1282 1316; 1811 1204 1284 1212 1283; 1812 1296 1246 1128 1318;
    1813 1129 1238 1213 1347; 1814 1298 1366 1338 1076; 1815 1019 1020 1070 1277;
    1816 1206 1327 1326 1366; 1817 1303 1181 1108 1134; 1818 1231 1047 1048 1342;
    1819 1132 1226 1284 1204; 1820 1290 1314 1181 1303; 1821 1338 1184 1299 1301;
    1822 1164 1244 1186 1239; 1823 1169 1112 1225 1159; 1824 1282 1293 1325 1295;
    1825 1276 1152 1168 1381; 1826 1366 1326 1184 1338; 1827 1207 1275 1276 1381;
    1828 1267 1248 1307 1196; 1829 1113 1081 1220 1085; 1830 1364 1209 1353 1309;
    1831 1292 1239 1186 1264; 1832 1235 1371 1378 1211; 1833 1211 1378 1246 1296;
    1834 1188 1232 1323 1312; 1835 1363 1310 1238 1129; 1836 1337 1331 404 403;
    1837 1278 1146 1379 1216; 1838 1233 1332 1360 1339; 1839 1084 1120 1132 1204;
    1840 1080 1166 1171 1237; 1841 1097 1077 1271 1158; 1842 1317 1123 1114 1082;
    1843 1250 1182 1193 1107; 1844 1293 1317 1082 1325; 1845 1151 1058 1146 1278;
    1846 1064 1227 1217 1057; 1847 1112 1101 1164 1225; 1848 1310 1382 1283 1238;
    1849 1111 1328 1293 1282; 1850 1136 1064 1057 1248; 1851 1306 1257 1060 1385;
    1852 1178 1076 1247 1194; 1853 1358 1195 1163 1352; 1854 1146 1130 1273 1379;
    1855 1379 1273 1262 1135; 1856 1272 1296 1318 1345; 1857 1100 1052 1053 1182;
    1858 1172 1188 1312 1261; 1859 1108 1084 1382 1310; 1860 1370 1268 1080 1242;
    1861 1138 1387 1170 1377; 1862 1130 1383 1287 1131; 1863 1107 1193 1161 1173;
    1864 1181 1219 1141 1105; 1865 1329 1187 1280 1228; 1866 1191 1049 1050 1109;
    1867 1029 228 1201 1236; 1868 1314 1334 1219 1181; 1869 1328 1085 1317 1293;
    1870 1212 1284 1256 1275; 1871 1096 1100 1182 1250; 1872 1339 1360 1178 1203;
    1873 1128 1361 1308 1297; 1874 1253 1267 1196 1166; 1875 1109 1050 1051 1094;
    1876 1245 1386 1385 1311; 1877 1364 1309 1329 1333; 1878 1247 1301 1195 1358;
    1879 1203 1178 1194 1230; 1880 1210 1263 1233 1362; 1881 1262 1265 1257 1306;
    1882 1323 1234 1099; 1883 1253 1167 1267; 1884 1313 1098 1208;
    1885 1336 1368 1316; 1886 1223 1042 1043; 1887 1369 1294 1319;
    1888 1160 1118 1175; 1889 1074 1147 1258; 1890 1201 1189 1087;
    1891 1206 1269 1327; 1892 1060 1243 1221; 1893 399 1372 400;
    1894 1097 1254 1077; 1895 1149 1148 1153; 1896 1154 1295 1380;
    1897 1194 1247 1358; 1898 1273 1265 1262; 1899 1020 1021 1070;
    1900 1244 1200 1186; 1901 1333 1329 1228; 1902 1286 1381 1168;
    1903 1214 1245 1092; 1904 1105 1120 1084; 1905 1386 1306 1385;
    1906 1242 1080 1237; 1907 1156 1373 1320; 1908 1071 1196 1183;
    1951 1056 1431 604 369; 1952 1431 1432 605 604; 1953 1432 1433 606 605;
    1954 1433 1434 607 606; 1955 1434 1435 608 607; 1956 1435 1436 609 608;
    1957 1436 1437 610 609; 1958 1437 1438 611 610; 1959 1438 1439 612 611;
    1960 1439 1440 613 612; 1961 1440 1441 614 613; 1962 1441 1442 615 614;
    1963 1442 1443 616 615; 1964 1443 1444 617 616; 1965 1444 1445 618 617;
    1966 1445 1430 375 618; 1967 1055 1446 1431 1056; 1968 1446 1447 1432 1431;
    1969 1447 1448 1433 1432; 1970 1448 1449 1434 1433; 1971 1449 1450 1435 1434;
    1972 1450 1451 1436 1435; 1973 1451 1452 1437 1436; 1974 1452 1453 1438 1437;
    1975 1453 1454 1439 1438; 1976 1454 1455 1440 1439; 1977 1455 1456 1441 1440;
    1978 1456 1457 1442 1441; 1979 1457 1458 1443 1442; 1980 1458 1459 1444 1443;
    1981 1459 1460 1445 1444; 1982 1460 1429 1430 1445; 1983 1054 1461 1446 1055;
    1984 1461 1462 1447 1446; 1985 1462 1463 1448 1447; 1986 1463 1464 1449 1448;
    1987 1464 1465 1450 1449; 1988 1465 1466 1451 1450; 1989 1466 1467 1452 1451;
    1990 1467 1468 1453 1452; 1991 1468 1469 1454 1453; 1992 1469 1470 1455 1454;
    1993 1470 1471 1456 1455; 1994 1471 1472 1457 1456; 1995 1472 1473 1458 1457;
    1996 1473 1474 1459 1458; 1997 1474 1475 1460 1459; 1998 1475 1428 1429 1460;
    1999 1053 1476 1461 1054; 2000 1476 1477 1462 1461; 2001 1477 1478 1463 1462;
    2002 1478 1479 1464 1463; 2003 1479 1480 1465 1464; 2004 1480 1481 1466 1465;
    2005 1481 1482 1467 1466; 2006 1482 1483 1468 1467; 2007 1483 1484 1469 1468;
    2008 1484 1485 1470 1469; 2009 1485 1486 1471 1470; 2010 1486 1487 1472 1471;
    2011 1487 1488 1473 1472; 2012 1488 1489 1474 1473; 2013 1489 1490 1475 1474;
    2014 1490 1427 1428 1475; 2015 1052 1491 1476 1053; 2016 1491 1492 1477 1476;
    2017 1492 1493 1478 1477; 2018 1493 1494 1479 1478; 2019 1494 1495 1480 1479;
    2020 1495 1496 1481 1480; 2021 1496 1497 1482 1481; 2022 1497 1498 1483 1482;
    2023 1498 1499 1484 1483; 2024 1499 1500 1485 1484; 2025 1500 1501 1486 1485;
    2026 1501 1502 1487 1486; 2027 1502 1503 1488 1487; 2028 1503 1504 1489 1488;
    2029 1504 1505 1490 1489; 2030 1505 1426 1427 1490; 2031 1051 1506 1491 1052;
    2032 1506 1507 1492 1491; 2033 1507 1508 1493 1492; 2034 1508 1509 1494 1493;
    2035 1509 1510 1495 1494; 2036 1510 1511 1496 1495; 2037 1511 1512 1497 1496;
    2038 1512 1513 1498 1497; 2039 1513 1514 1499 1498; 2040 1514 1515 1500 1499;
    2041 1515 1516 1501 1500; 2042 1516 1517 1502 1501; 2043 1517 1518 1503 1502;
    2044 1518 1519 1504 1503; 2045 1519 1520 1505 1504; 2046 1520 1425 1426 1505;
    2047 1050 1521 1506 1051; 2048 1521 1522 1507 1506; 2049 1522 1523 1508 1507;
    2050 1523 1524 1509 1508; 2051 1524 1525 1510 1509; 2052 1525 1526 1511 1510;
    2053 1526 1527 1512 1511; 2054 1527 1528 1513 1512; 2055 1528 1529 1514 1513;
    2056 1529 1530 1515 1514; 2057 1530 1531 1516 1515; 2058 1531 1532 1517 1516;
    2059 1532 1533 1518 1517; 2060 1533 1534 1519 1518; 2061 1534 1535 1520 1519;
    2062 1535 1424 1425 1520; 2063 1049 1536 1521 1050; 2064 1536 1537 1522 1521;
    2065 1537 1538 1523 1522; 2066 1538 1539 1524 1523; 2067 1539 1540 1525 1524;
    2068 1540 1541 1526 1525; 2069 1541 1542 1527 1526; 2070 1542 1543 1528 1527;
    2071 1543 1544 1529 1528; 2072 1544 1545 1530 1529; 2073 1545 1546 1531 1530;
    2074 1546 1547 1532 1531; 2075 1547 1548 1533 1532; 2076 1548 1549 1534 1533;
    2077 1549 1550 1535 1534; 2078 1550 1423 1424 1535; 2079 1048 1551 1536 1049;
    2080 1551 1552 1537 1536; 2081 1552 1553 1538 1537; 2082 1553 1554 1539 1538;
    2083 1554 1555 1540 1539; 2084 1555 1556 1541 1540; 2085 1556 1557 1542 1541;
    2086 1557 1558 1543 1542; 2087 1558 1559 1544 1543; 2088 1559 1560 1545 1544;
    2089 1560 1561 1546 1545; 2090 1561 1562 1547 1546; 2091 1562 1563 1548 1547;
    2092 1563 1564 1549 1548; 2093 1564 1565 1550 1549; 2094 1565 1422 1423 1550;
    2095 1047 1566 1551 1048; 2096 1566 1567 1552 1551; 2097 1567 1568 1553 1552;
    2098 1568 1569 1554 1553; 2099 1569 1570 1555 1554; 2100 1570 1571 1556 1555;
    2101 1571 1572 1557 1556; 2102 1572 1573 1558 1557; 2103 1573 1574 1559 1558;
    2104 1574 1575 1560 1559; 2105 1575 1576 1561 1560; 2106 1576 1577 1562 1561;
    2107 1577 1578 1563 1562; 2108 1578 1579 1564 1563; 2109 1579 1580 1565 1564;
    2110 1580 1421 1422 1565; 2111 1046 1581 1566 1047; 2112 1581 1582 1567 1566;
    2113 1582 1583 1568 1567; 2114 1583 1584 1569 1568; 2115 1584 1585 1570 1569;
    2116 1585 1586 1571 1570; 2117 1586 1587 1572 1571; 2118 1587 1588 1573 1572;
    2119 1588 1589 1574 1573; 2120 1589 1590 1575 1574; 2121 1590 1591 1576 1575;
    2122 1591 1592 1577 1576; 2123 1592 1593 1578 1577; 2124 1593 1594 1579 1578;
    2125 1594 1595 1580 1579; 2126 1595 1420 1421 1580; 2127 1045 1596 1581 1046;
    2128 1596 1597 1582 1581; 2129 1597 1598 1583 1582; 2130 1598 1599 1584 1583;
    2131 1599 1600 1585 1584; 2132 1600 1601 1586 1585; 2133 1601 1602 1587 1586;
    2134 1602 1603 1588 1587; 2135 1603 1604 1589 1588; 2136 1604 1605 1590 1589;
    2137 1605 1606 1591 1590; 2138 1606 1607 1592 1591; 2139 1607 1608 1593 1592;
    2140 1608 1609 1594 1593; 2141 1609 1610 1595 1594; 2142 1610 1419 1420 1595;
    2143 1044 1611 1596 1045; 2144 1611 1612 1597 1596; 2145 1612 1613 1598 1597;
    2146 1613 1614 1599 1598; 2147 1614 1615 1600 1599; 2148 1615 1616 1601 1600;
    2149 1616 1617 1602 1601; 2150 1617 1618 1603 1602; 2151 1618 1619 1604 1603;
    2152 1619 1620 1605 1604; 2153 1620 1621 1606 1605; 2154 1621 1622 1607 1606;
    2155 1622 1623 1608 1607; 2156 1623 1624 1609 1608; 2157 1624 1625 1610 1609;
    2158 1625 1418 1419 1610; 2159 1043 1626 1611 1044; 2160 1626 1627 1612 1611;
    2161 1627 1628 1613 1612; 2162 1628 1629 1614 1613; 2163 1629 1630 1615 1614;
    2164 1630 1631 1616 1615; 2165 1631 1632 1617 1616; 2166 1632 1633 1618 1617;
    2167 1633 1634 1619 1618; 2168 1634 1635 1620 1619; 2169 1635 1636 1621 1620;
    2170 1636 1637 1622 1621; 2171 1637 1638 1623 1622; 2172 1638 1639 1624 1623;
    2173 1639 1640 1625 1624; 2174 1640 1417 1418 1625; 2175 1042 1641 1626 1043;
    2176 1641 1642 1627 1626; 2177 1642 1643 1628 1627; 2178 1643 1644 1629 1628;
    2179 1644 1645 1630 1629; 2180 1645 1646 1631 1630; 2181 1646 1647 1632 1631;
    2182 1647 1648 1633 1632; 2183 1648 1649 1634 1633; 2184 1649 1650 1635 1634;
    2185 1650 1651 1636 1635; 2186 1651 1652 1637 1636; 2187 1652 1653 1638 1637;
    2188 1653 1654 1639 1638; 2189 1654 1655 1640 1639; 2190 1655 1416 1417 1640;
    2191 1041 1656 1641 1042; 2192 1656 1657 1642 1641; 2193 1657 1658 1643 1642;
    2194 1658 1659 1644 1643; 2195 1659 1660 1645 1644; 2196 1660 1661 1646 1645;
    2197 1661 1662 1647 1646; 2198 1662 1663 1648 1647; 2199 1663 1664 1649 1648;
    2200 1664 1665 1650 1649; 2201 1665 1666 1651 1650; 2202 1666 1667 1652 1651;
    2203 1667 1668 1653 1652; 2204 1668 1669 1654 1653; 2205 1669 1670 1655 1654;
    2206 1670 1415 1416 1655; 2207 1040 1671 1656 1041; 2208 1671 1672 1657 1656;
    2209 1672 1673 1658 1657; 2210 1673 1674 1659 1658; 2211 1674 1675 1660 1659;
    2212 1675 1676 1661 1660; 2213 1676 1677 1662 1661; 2214 1677 1678 1663 1662;
    2215 1678 1679 1664 1663; 2216 1679 1680 1665 1664; 2217 1680 1681 1666 1665;
    2218 1681 1682 1667 1666; 2219 1682 1683 1668 1667; 2220 1683 1684 1669 1668;
    2221 1684 1685 1670 1669; 2222 1685 1414 1415 1670; 2223 1039 1686 1671 1040;
    2224 1686 1687 1672 1671; 2225 1687 1688 1673 1672; 2226 1688 1689 1674 1673;
    2227 1689 1690 1675 1674; 2228 1690 1691 1676 1675; 2229 1691 1692 1677 1676;
    2230 1692 1693 1678 1677; 2231 1693 1694 1679 1678; 2232 1694 1695 1680 1679;
    2233 1695 1696 1681 1680; 2234 1696 1697 1682 1681; 2235 1697 1698 1683 1682;
    2236 1698 1699 1684 1683; 2237 1699 1700 1685 1684; 2238 1700 1413 1414 1685;
    2239 1038 1701 1686 1039; 2240 1701 1702 1687 1686; 2241 1702 1703 1688 1687;
    2242 1703 1704 1689 1688; 2243 1704 1705 1690 1689; 2244 1705 1706 1691 1690;
    2245 1706 1707 1692 1691; 2246 1707 1708 1693 1692; 2247 1708 1709 1694 1693;
    2248 1709 1710 1695 1694; 2249 1710 1711 1696 1695; 2250 1711 1712 1697 1696;
    2251 1712 1713 1698 1697; 2252 1713 1714 1699 1698; 2253 1714 1715 1700 1699;
    2254 1715 1412 1413 1700; 2255 1037 1716 1701 1038; 2256 1716 1717 1702 1701;
    2257 1717 1718 1703 1702; 2258 1718 1719 1704 1703; 2259 1719 1720 1705 1704;
    2260 1720 1721 1706 1705; 2261 1721 1722 1707 1706; 2262 1722 1723 1708 1707;
    2263 1723 1724 1709 1708; 2264 1724 1725 1710 1709; 2265 1725 1726 1711 1710;
    2266 1726 1727 1712 1711; 2267 1727 1728 1713 1712; 2268 1728 1729 1714 1713;
    2269 1729 1730 1715 1714; 2270 1730 1411 1412 1715; 2271 1036 1731 1716 1037;
    2272 1731 1732 1717 1716; 2273 1732 1733 1718 1717; 2274 1733 1734 1719 1718;
    2275 1734 1735 1720 1719; 2276 1735 1736 1721 1720; 2277 1736 1737 1722 1721;
    2278 1737 1738 1723 1722; 2279 1738 1739 1724 1723; 2280 1739 1740 1725 1724;
    2281 1740 1741 1726 1725; 2282 1741 1742 1727 1726; 2283 1742 1743 1728 1727;
    2284 1743 1744 1729 1728; 2285 1744 1745 1730 1729; 2286 1745 1410 1411 1730;
    2287 1035 1746 1731 1036; 2288 1746 1747 1732 1731; 2289 1747 1748 1733 1732;
    2290 1748 1749 1734 1733; 2291 1749 1750 1735 1734; 2292 1750 1751 1736 1735;
    2293 1751 1752 1737 1736; 2294 1752 1753 1738 1737; 2295 1753 1754 1739 1738;
    2296 1754 1755 1740 1739; 2297 1755 1756 1741 1740; 2298 1756 1757 1742 1741;
    2299 1757 1758 1743 1742; 2300 1758 1759 1744 1743; 2301 1759 1760 1745 1744;
    2302 1760 1409 1410 1745; 2303 1034 1761 1746 1035; 2304 1761 1762 1747 1746;
    2305 1762 1763 1748 1747; 2306 1763 1764 1749 1748; 2307 1764 1765 1750 1749;
    2308 1765 1766 1751 1750; 2309 1766 1767 1752 1751; 2310 1767 1768 1753 1752;
    2311 1768 1769 1754 1753; 2312 1769 1770 1755 1754; 2313 1770 1771 1756 1755;
    2314 1771 1772 1757 1756; 2315 1772 1773 1758 1757; 2316 1773 1774 1759 1758;
    2317 1774 1775 1760 1759; 2318 1775 1408 1409 1760; 2319 1033 1776 1761 1034;
    2320 1776 1777 1762 1761; 2321 1777 1778 1763 1762; 2322 1778 1779 1764 1763;
    2323 1779 1780 1765 1764; 2324 1780 1781 1766 1765; 2325 1781 1782 1767 1766;
    2326 1782 1783 1768 1767; 2327 1783 1784 1769 1768; 2328 1784 1785 1770 1769;
    2329 1785 1786 1771 1770; 2330 1786 1787 1772 1771; 2331 1787 1788 1773 1772;
    2332 1788 1789 1774 1773; 2333 1789 1790 1775 1774; 2334 1790 1407 1408 1775;
    2335 1032 1791 1776 1033; 2336 1791 1792 1777 1776; 2337 1792 1793 1778 1777;
    2338 1793 1794 1779 1778; 2339 1794 1795 1780 1779; 2340 1795 1796 1781 1780;
    2341 1796 1797 1782 1781; 2342 1797 1798 1783 1782; 2343 1798 1799 1784 1783;
    2344 1799 1800 1785 1784; 2345 1800 1801 1786 1785; 2346 1801 1802 1787 1786;
    2347 1802 1803 1788 1787; 2348 1803 1804 1789 1788; 2349 1804 1805 1790 1789;
    2350 1805 1406 1407 1790; 2351 1031 1806 1791 1032; 2352 1806 1807 1792 1791;
    2353 1807 1808 1793 1792; 2354 1808 1809 1794 1793; 2355 1809 1810 1795 1794;
    2356 1810 1811 1796 1795; 2357 1811 1812 1797 1796; 2358 1812 1813 1798 1797;
    2359 1813 1814 1799 1798; 2360 1814 1815 1800 1799; 2361 1815 1816 1801 1800;
    2362 1816 1817 1802 1801; 2363 1817 1818 1803 1802; 2364 1818 1819 1804 1803;
    2365 1819 1820 1805 1804; 2366 1820 1405 1406 1805; 2367 1030 1821 1806 1031;
    2368 1821 1822 1807 1806; 2369 1822 1823 1808 1807; 2370 1823 1824 1809 1808;
    2371 1824 1825 1810 1809; 2372 1825 1826 1811 1810; 2373 1826 1827 1812 1811;
    2374 1827 1828 1813 1812; 2375 1828 1829 1814 1813; 2376 1829 1830 1815 1814;
    2377 1830 1831 1816 1815; 2378 1831 1832 1817 1816; 2379 1832 1833 1818 1817;
    2380 1833 1834 1819 1818; 2381 1834 1835 1820 1819; 2382 1835 1404 1405 1820;
    2383 370 1389 1821 1030; 2384 1389 1390 1822 1821; 2385 1390 1391 1823 1822;
    2386 1391 1392 1824 1823; 2387 1392 1393 1825 1824; 2388 1393 1394 1826 1825;
    2389 1394 1395 1827 1826; 2390 1395 1396 1828 1827; 2391 1396 1397 1829 1828;
    2392 1397 1398 1830 1829; 2393 1398 1399 1831 1830; 2394 1399 1400 1832 1831;
    2395 1400 1401 1833 1832; 2396 1401 1402 1834 1833; 2397 1402 1403 1835 1834;
    2398 1403 376 1404 1835; 2441 1836 1878 821 381; 2442 1878 1879 822 821;
    2443 1879 1880 823 822; 2444 1880 1881 824 823; 2445 1881 1882 825 824;
    2446 1882 1883 826 825; 2447 1883 1884 827 826; 2448 1884 1885 828 827;
    2449 1885 1886 829 828; 2450 1886 1887 830 829; 2451 1887 1888 831 830;
    2452 1888 1889 832 831; 2453 1889 1890 833 832; 2454 1890 1891 834 833;
    2455 1891 1892 835 834; 2456 1892 1430 375 835; 2457 1837 1893 1878 1836;
    2458 1893 1894 1879 1878; 2459 1894 1895 1880 1879; 2460 1895 1896 1881 1880;
    2461 1896 1897 1882 1881; 2462 1897 1898 1883 1882; 2463 1898 1899 1884 1883;
    2464 1899 1900 1885 1884; 2465 1900 1901 1886 1885; 2466 1901 1902 1887 1886;
    2467 1902 1903 1888 1887; 2468 1903 1904 1889 1888; 2469 1904 1905 1890 1889;
    2470 1905 1906 1891 1890; 2471 1906 1907 1892 1891; 2472 1907 1429 1430 1892;
    2473 1838 1908 1893 1837; 2474 1908 1909 1894 1893; 2475 1909 1910 1895 1894;
    2476 1910 1911 1896 1895; 2477 1911 1912 1897 1896; 2478 1912 1913 1898 1897;
    2479 1913 1914 1899 1898; 2480 1914 1915 1900 1899; 2481 1915 1916 1901 1900;
    2482 1916 1917 1902 1901; 2483 1917 1918 1903 1902; 2484 1918 1919 1904 1903;
    2485 1919 1920 1905 1904; 2486 1920 1921 1906 1905; 2487 1921 1922 1907 1906;
    2488 1922 1428 1429 1907; 2489 1839 1923 1908 1838; 2490 1923 1924 1909 1908;
    2491 1924 1925 1910 1909; 2492 1925 1926 1911 1910; 2493 1926 1927 1912 1911;
    2494 1927 1928 1913 1912; 2495 1928 1929 1914 1913; 2496 1929 1930 1915 1914;
    2497 1930 1931 1916 1915; 2498 1931 1932 1917 1916; 2499 1932 1933 1918 1917;
    2500 1933 1934 1919 1918; 2501 1934 1935 1920 1919; 2502 1935 1936 1921 1920;
    2503 1936 1937 1922 1921; 2504 1937 1427 1428 1922; 2505 1840 1938 1923 1839;
    2506 1938 1939 1924 1923; 2507 1939 1940 1925 1924; 2508 1940 1941 1926 1925;
    2509 1941 1942 1927 1926; 2510 1942 1943 1928 1927; 2511 1943 1944 1929 1928;
    2512 1944 1945 1930 1929; 2513 1945 1946 1931 1930; 2514 1946 1947 1932 1931;
    2515 1947 1948 1933 1932; 2516 1948 1949 1934 1933; 2517 1949 1950 1935 1934;
    2518 1950 1951 1936 1935; 2519 1951 1952 1937 1936; 2520 1952 1426 1427 1937;
    2521 1841 1953 1938 1840; 2522 1953 1954 1939 1938; 2523 1954 1955 1940 1939;
    2524 1955 1956 1941 1940; 2525 1956 1957 1942 1941; 2526 1957 1958 1943 1942;
    2527 1958 1959 1944 1943; 2528 1959 1960 1945 1944; 2529 1960 1961 1946 1945;
    2530 1961 1962 1947 1946; 2531 1962 1963 1948 1947; 2532 1963 1964 1949 1948;
    2533 1964 1965 1950 1949; 2534 1965 1966 1951 1950; 2535 1966 1967 1952 1951;
    2536 1967 1425 1426 1952; 2537 1842 1968 1953 1841; 2538 1968 1969 1954 1953;
    2539 1969 1970 1955 1954; 2540 1970 1971 1956 1955; 2541 1971 1972 1957 1956;
    2542 1972 1973 1958 1957; 2543 1973 1974 1959 1958; 2544 1974 1975 1960 1959;
    2545 1975 1976 1961 1960; 2546 1976 1977 1962 1961; 2547 1977 1978 1963 1962;
    2548 1978 1979 1964 1963; 2549 1979 1980 1965 1964; 2550 1980 1981 1966 1965;
    2551 1981 1982 1967 1966; 2552 1982 1424 1425 1967; 2553 1843 1983 1968 1842;
    2554 1983 1984 1969 1968; 2555 1984 1985 1970 1969; 2556 1985 1986 1971 1970;
    2557 1986 1987 1972 1971; 2558 1987 1988 1973 1972; 2559 1988 1989 1974 1973;
    2560 1989 1990 1975 1974; 2561 1990 1991 1976 1975; 2562 1991 1992 1977 1976;
    2563 1992 1993 1978 1977; 2564 1993 1994 1979 1978; 2565 1994 1995 1980 1979;
    2566 1995 1996 1981 1980; 2567 1996 1997 1982 1981; 2568 1997 1423 1424 1982;
    2569 1844 1998 1983 1843; 2570 1998 1999 1984 1983; 2571 1999 2000 1985 1984;
    2572 2000 2001 1986 1985; 2573 2001 2002 1987 1986; 2574 2002 2003 1988 1987;
    2575 2003 2004 1989 1988; 2576 2004 2005 1990 1989; 2577 2005 2006 1991 1990;
    2578 2006 2007 1992 1991; 2579 2007 2008 1993 1992; 2580 2008 2009 1994 1993;
    2581 2009 2010 1995 1994; 2582 2010 2011 1996 1995; 2583 2011 2012 1997 1996;
    2584 2012 1422 1423 1997; 2585 1845 2013 1998 1844; 2586 2013 2014 1999 1998;
    2587 2014 2015 2000 1999; 2588 2015 2016 2001 2000; 2589 2016 2017 2002 2001;
    2590 2017 2018 2003 2002; 2591 2018 2019 2004 2003; 2592 2019 2020 2005 2004;
    2593 2020 2021 2006 2005; 2594 2021 2022 2007 2006; 2595 2022 2023 2008 2007;
    2596 2023 2024 2009 2008; 2597 2024 2025 2010 2009; 2598 2025 2026 2011 2010;
    2599 2026 2027 2012 2011; 2600 2027 1421 1422 2012; 2601 1846 2028 2013 1845;
    2602 2028 2029 2014 2013; 2603 2029 2030 2015 2014; 2604 2030 2031 2016 2015;
    2605 2031 2032 2017 2016; 2606 2032 2033 2018 2017; 2607 2033 2034 2019 2018;
    2608 2034 2035 2020 2019; 2609 2035 2036 2021 2020; 2610 2036 2037 2022 2021;
    2611 2037 2038 2023 2022; 2612 2038 2039 2024 2023; 2613 2039 2040 2025 2024;
    2614 2040 2041 2026 2025; 2615 2041 2042 2027 2026; 2616 2042 1420 1421 2027;
    2617 1847 2043 2028 1846; 2618 2043 2044 2029 2028; 2619 2044 2045 2030 2029;
    2620 2045 2046 2031 2030; 2621 2046 2047 2032 2031; 2622 2047 2048 2033 2032;
    2623 2048 2049 2034 2033; 2624 2049 2050 2035 2034; 2625 2050 2051 2036 2035;
    2626 2051 2052 2037 2036; 2627 2052 2053 2038 2037; 2628 2053 2054 2039 2038;
    2629 2054 2055 2040 2039; 2630 2055 2056 2041 2040; 2631 2056 2057 2042 2041;
    2632 2057 1419 1420 2042; 2633 1848 2058 2043 1847; 2634 2058 2059 2044 2043;
    2635 2059 2060 2045 2044; 2636 2060 2061 2046 2045; 2637 2061 2062 2047 2046;
    2638 2062 2063 2048 2047; 2639 2063 2064 2049 2048; 2640 2064 2065 2050 2049;
    2641 2065 2066 2051 2050; 2642 2066 2067 2052 2051; 2643 2067 2068 2053 2052;
    2644 2068 2069 2054 2053; 2645 2069 2070 2055 2054; 2646 2070 2071 2056 2055;
    2647 2071 2072 2057 2056; 2648 2072 1418 1419 2057; 2649 1849 2073 2058 1848;
    2650 2073 2074 2059 2058; 2651 2074 2075 2060 2059; 2652 2075 2076 2061 2060;
    2653 2076 2077 2062 2061; 2654 2077 2078 2063 2062; 2655 2078 2079 2064 2063;
    2656 2079 2080 2065 2064; 2657 2080 2081 2066 2065; 2658 2081 2082 2067 2066;
    2659 2082 2083 2068 2067; 2660 2083 2084 2069 2068; 2661 2084 2085 2070 2069;
    2662 2085 2086 2071 2070; 2663 2086 2087 2072 2071; 2664 2087 1417 1418 2072;
    2665 1850 2088 2073 1849; 2666 2088 2089 2074 2073; 2667 2089 2090 2075 2074;
    2668 2090 2091 2076 2075; 2669 2091 2092 2077 2076; 2670 2092 2093 2078 2077;
    2671 2093 2094 2079 2078; 2672 2094 2095 2080 2079; 2673 2095 2096 2081 2080;
    2674 2096 2097 2082 2081; 2675 2097 2098 2083 2082; 2676 2098 2099 2084 2083;
    2677 2099 2100 2085 2084; 2678 2100 2101 2086 2085; 2679 2101 2102 2087 2086;
    2680 2102 1416 1417 2087; 2681 1851 2103 2088 1850; 2682 2103 2104 2089 2088;
    2683 2104 2105 2090 2089; 2684 2105 2106 2091 2090; 2685 2106 2107 2092 2091;
    2686 2107 2108 2093 2092; 2687 2108 2109 2094 2093; 2688 2109 2110 2095 2094;
    2689 2110 2111 2096 2095; 2690 2111 2112 2097 2096; 2691 2112 2113 2098 2097;
    2692 2113 2114 2099 2098; 2693 2114 2115 2100 2099; 2694 2115 2116 2101 2100;
    2695 2116 2117 2102 2101; 2696 2117 1415 1416 2102; 2697 1852 2118 2103 1851;
    2698 2118 2119 2104 2103; 2699 2119 2120 2105 2104; 2700 2120 2121 2106 2105;
    2701 2121 2122 2107 2106; 2702 2122 2123 2108 2107; 2703 2123 2124 2109 2108;
    2704 2124 2125 2110 2109; 2705 2125 2126 2111 2110; 2706 2126 2127 2112 2111;
    2707 2127 2128 2113 2112; 2708 2128 2129 2114 2113; 2709 2129 2130 2115 2114;
    2710 2130 2131 2116 2115; 2711 2131 2132 2117 2116; 2712 2132 1414 1415 2117;
    2713 1853 2133 2118 1852; 2714 2133 2134 2119 2118; 2715 2134 2135 2120 2119;
    2716 2135 2136 2121 2120; 2717 2136 2137 2122 2121; 2718 2137 2138 2123 2122;
    2719 2138 2139 2124 2123; 2720 2139 2140 2125 2124; 2721 2140 2141 2126 2125;
    2722 2141 2142 2127 2126; 2723 2142 2143 2128 2127; 2724 2143 2144 2129 2128;
    2725 2144 2145 2130 2129; 2726 2145 2146 2131 2130; 2727 2146 2147 2132 2131;
    2728 2147 1413 1414 2132; 2729 1854 2148 2133 1853; 2730 2148 2149 2134 2133;
    2731 2149 2150 2135 2134; 2732 2150 2151 2136 2135; 2733 2151 2152 2137 2136;
    2734 2152 2153 2138 2137; 2735 2153 2154 2139 2138; 2736 2154 2155 2140 2139;
    2737 2155 2156 2141 2140; 2738 2156 2157 2142 2141; 2739 2157 2158 2143 2142;
    2740 2158 2159 2144 2143; 2741 2159 2160 2145 2144; 2742 2160 2161 2146 2145;
    2743 2161 2162 2147 2146; 2744 2162 1412 1413 2147; 2745 1855 2163 2148 1854;
    2746 2163 2164 2149 2148; 2747 2164 2165 2150 2149; 2748 2165 2166 2151 2150;
    2749 2166 2167 2152 2151; 2750 2167 2168 2153 2152; 2751 2168 2169 2154 2153;
    2752 2169 2170 2155 2154; 2753 2170 2171 2156 2155; 2754 2171 2172 2157 2156;
    2755 2172 2173 2158 2157; 2756 2173 2174 2159 2158; 2757 2174 2175 2160 2159;
    2758 2175 2176 2161 2160; 2759 2176 2177 2162 2161; 2760 2177 1411 1412 2162;
    2761 1856 2178 2163 1855; 2762 2178 2179 2164 2163; 2763 2179 2180 2165 2164;
    2764 2180 2181 2166 2165; 2765 2181 2182 2167 2166; 2766 2182 2183 2168 2167;
    2767 2183 2184 2169 2168; 2768 2184 2185 2170 2169; 2769 2185 2186 2171 2170;
    2770 2186 2187 2172 2171; 2771 2187 2188 2173 2172; 2772 2188 2189 2174 2173;
    2773 2189 2190 2175 2174; 2774 2190 2191 2176 2175; 2775 2191 2192 2177 2176;
    2776 2192 1410 1411 2177; 2777 1857 2193 2178 1856; 2778 2193 2194 2179 2178;
    2779 2194 2195 2180 2179; 2780 2195 2196 2181 2180; 2781 2196 2197 2182 2181;
    2782 2197 2198 2183 2182; 2783 2198 2199 2184 2183; 2784 2199 2200 2185 2184;
    2785 2200 2201 2186 2185; 2786 2201 2202 2187 2186; 2787 2202 2203 2188 2187;
    2788 2203 2204 2189 2188; 2789 2204 2205 2190 2189; 2790 2205 2206 2191 2190;
    2791 2206 2207 2192 2191; 2792 2207 1409 1410 2192; 2793 1858 2208 2193 1857;
    2794 2208 2209 2194 2193; 2795 2209 2210 2195 2194; 2796 2210 2211 2196 2195;
    2797 2211 2212 2197 2196; 2798 2212 2213 2198 2197; 2799 2213 2214 2199 2198;
    2800 2214 2215 2200 2199; 2801 2215 2216 2201 2200; 2802 2216 2217 2202 2201;
    2803 2217 2218 2203 2202; 2804 2218 2219 2204 2203; 2805 2219 2220 2205 2204;
    2806 2220 2221 2206 2205; 2807 2221 2222 2207 2206; 2808 2222 1408 1409 2207;
    2809 1859 2223 2208 1858; 2810 2223 2224 2209 2208; 2811 2224 2225 2210 2209;
    2812 2225 2226 2211 2210; 2813 2226 2227 2212 2211; 2814 2227 2228 2213 2212;
    2815 2228 2229 2214 2213; 2816 2229 2230 2215 2214; 2817 2230 2231 2216 2215;
    2818 2231 2232 2217 2216; 2819 2232 2233 2218 2217; 2820 2233 2234 2219 2218;
    2821 2234 2235 2220 2219; 2822 2235 2236 2221 2220; 2823 2236 2237 2222 2221;
    2824 2237 1407 1408 2222; 2825 1860 2238 2223 1859; 2826 2238 2239 2224 2223;
    2827 2239 2240 2225 2224; 2828 2240 2241 2226 2225; 2829 2241 2242 2227 2226;
    2830 2242 2243 2228 2227; 2831 2243 2244 2229 2228; 2832 2244 2245 2230 2229;
    2833 2245 2246 2231 2230; 2834 2246 2247 2232 2231; 2835 2247 2248 2233 2232;
    2836 2248 2249 2234 2233; 2837 2249 2250 2235 2234; 2838 2250 2251 2236 2235;
    2839 2251 2252 2237 2236; 2840 2252 1406 1407 2237; 2841 1861 2253 2238 1860;
    2842 2253 2254 2239 2238; 2843 2254 2255 2240 2239; 2844 2255 2256 2241 2240;
    2845 2256 2257 2242 2241; 2846 2257 2258 2243 2242; 2847 2258 2259 2244 2243;
    2848 2259 2260 2245 2244; 2849 2260 2261 2246 2245; 2850 2261 2262 2247 2246;
    2851 2262 2263 2248 2247; 2852 2263 2264 2249 2248; 2853 2264 2265 2250 2249;
    2854 2265 2266 2251 2250; 2855 2266 2267 2252 2251; 2856 2267 1405 1406 2252;
    2857 1862 2268 2253 1861; 2858 2268 2269 2254 2253; 2859 2269 2270 2255 2254;
    2860 2270 2271 2256 2255; 2861 2271 2272 2257 2256; 2862 2272 2273 2258 2257;
    2863 2273 2274 2259 2258; 2864 2274 2275 2260 2259; 2865 2275 2276 2261 2260;
    2866 2276 2277 2262 2261; 2867 2277 2278 2263 2262; 2868 2278 2279 2264 2263;
    2869 2279 2280 2265 2264; 2870 2280 2281 2266 2265; 2871 2281 2282 2267 2266;
    2872 2282 1404 1405 2267; 2873 382 1863 2268 1862; 2874 1863 1864 2269 2268;
    2875 1864 1865 2270 2269; 2876 1865 1866 2271 2270; 2877 1866 1867 2272 2271;
    2878 1867 1868 2273 2272; 2879 1868 1869 2274 2273; 2880 1869 1870 2275 2274;
    2881 1870 1871 2276 2275; 2882 1871 1872 2277 2276; 2883 1872 1873 2278 2277;
    2884 1873 1874 2279 2278; 2885 1874 1875 2280 2279; 2886 1875 1876 2281 2280;
    2887 1876 1877 2282 2281; 2888 1877 376 1404 2282; 2920 99 2451 2323 2283;
    2921 2506 2319 2467 2422; 2922 2587 2577 2648 2423; 2923 2606 2663 2433 2652;
    2924 2404 2351 2654 2372; 2925 2496 2335 2590 2594; 2926 2515 2589 2453 2499;
    2927 2612 2609 2486 2413; 2928 2383 2415 2384 2673; 2929 2608 2569 2460 2563;
    2930 2641 2665 2383 2374; 2931 2580 2379 2490 2564; 2932 2323 2491 2430 2332;
    2933 2349 2483 2443 2362; 2934 2621 2359 1026 1025; 2935 2541 2374 2383 2673;
    2936 2375 2629 2450 2324; 2937 2563 2460 2639 2598; 2938 2503 2547 2353 2666;
    2939 2347 2310 2311 2348; 2940 2579 2612 2413 2510; 2941 2406 2650 2581 2585;
    2942 2349 2362 1029 1028; 2943 2362 2443 228 1029; 2944 2392 2495 2452 2595;
    2945 2480 2642 2497 2379; 2946 2539 2563 2598 2335; 2947 2284 2285 2355 2341;
    2948 2459 2541 2673 2315; 2949 2329 2494 2358 2611; 2950 2556 2419 2494 2329;
    2951 2344 2316 2660 2669; 2952 2488 2299 2300 2570; 2953 2360 2558 2416 2474;
    2954 2555 2463 2547 2503; 2955 2381 2390 2356 2426; 2956 2360 2635 2584 2558;
    2957 2415 2377 2659 2384; 2958 2489 2440 2627 2389; 2959 2352 2309 2310 2347;
    2960 2616 2438 2511 2524; 2961 2419 2306 2307 2494; 2962 2636 2466 2634 2328;
    2963 2335 2598 2455 2590; 2964 2326 2320 2664 2667; 2965 2367 2436 2370 2495;
    2966 2427 2503 2666 2662; 2967 2369 2498 2407 2592; 2968 2324 2450 1020 1019;
    2969 2353 2349 1028 1027; 2970 2337 2633 2485 2653; 2971 2401 2652 2477 2469;
    2972 2574 2616 2524 2327; 2973 2460 2348 2428 2639; 2974 2325 2368 2351 2404;
    2975 2416 2558 2615 2636; 2976 2411 2404 2372 2390; 2977 2634 2549 2526 2588;
    2978 2314 2462 2658 2321; 2979 2565 2538 2315 2670; 2980 2476 2508 2635 2360;
    2981 2479 2525 2379 2580; 2982 2332 2430 2629 2375; 2983 2502 2313 370 228;
    2984 2407 2498 2515 2499; 2985 2408 2298 2299 2488; 2986 2505 2418 2405 2520;
    2987 2439 2623 2337 2605; 2988 2430 2473 2628 2629; 2989 2588 2526 2458 2591;
    2990 2364 2670 2369 2387; 2991 2519 2321 2322 2620; 2992 2358 2308 2309 2352;
    2993 2292 2293 2346 2518; 2994 2643 2571 2395 2500; 2995 2447 2506 2422 2638;
    2996 2417 2423 2548 2466; 2997 2431 2469 2373 2354; 2998 2293 2294 2350 2346;
    2999 2375 2324 1019 1018; 3000 2441 2651 2461 2330; 3001 2520 2480 2379 2525;
    3002 2479 2580 2623 2439; 3003 2628 2643 2450 2629; 3004 2320 2441 2330 2457;
    3005 2290 2291 2514 2394; 3006 2633 2564 2487 2586; 3007 2291 2292 2518 2514;
    3008 2518 2644 2431 2661; 3009 2342 2376 2554 2483; 3010 2424 2535 2516 2640;
    3011 2403 2604 2359 2621; 3012 2283 2323 2332 64; 3013 2604 2666 2353 2359;
    3014 2391 2481 2533 2602; 3015 2463 2504 2349 2547; 3016 2453 2668 2512 2675;
    3017 2336 2579 2510 2674; 3018 2644 2401 2469 2431; 3019 2572 2521 2420 2560;
    3020 2518 2346 2606 2644; 3021 2517 2409 2604 2403; 3022 2623 2564 2633 2337;
    3023 2492 2520 2525 2529; 3024 2426 2356 2647 2399; 3025 2356 2574 2327 2647;
    3026 2653 2485 2447 2338; 3027 2654 2331 2438 2616; 3028 2331 2573 2391 2624;
    3029 2550 2384 2659 2603; 3030 2433 2663 2436 2367; 3031 2499 2453 2675 2396;
    3032 2468 2586 2562 2319; 3033 2520 2405 2642 2480; 3034 2373 2595 2454 2381;
    3035 2606 2442 2672 2663; 3036 2596 2399 2493 2459; 3037 2617 2505 2520 2492;
    3038 2428 2312 2313 2502; 3039 2413 2486 2408 2462; 3040 2530 371 2297 2484;
    3041 2622 2599 2435 2376; 3042 2584 2534 2318 2558; 3043 2660 2544 2388 2656;
    3044 2540 2588 2591 2398; 3045 2289 2290 2394 2576; 3046 2530 2484 2478 2651;
    3047 2446 2612 2579 2542; 3048 2543 2446 2542 2613; 3049 2390 2372 2574 2356;
    3050 2632 2336 2674 2425; 3051 2626 2570 2458 2526; 3052 2534 2425 2587 2582;
    3053 2562 2539 2335 2496; 3054 2466 2548 2549 2634; 3055 2607 2302 2303 2402;
    3056 2516 2521 2572 2568; 3057 2442 2522 2527 2672; 3058 2440 2631 2465 2627;
    3059 2359 2353 1027 1026; 3060 2453 2357 2429 2668; 3061 2507 2540 2398 2630;
    3062 2595 2452 2411 2454; 3063 2584 2632 2425 2534; 3064 2398 2591 2397 2630;
    3065 99 2284 2341 2451; 3066 2379 2497 2619 2490; 3067 2581 2414 2537 2585;
    3068 2614 2543 2613 2578; 3069 2450 2500 1021 1020; 3070 2432 2625 2569 2608;
    3071 2389 2627 2476 2610; 3072 2536 2434 2532 2583; 3073 2288 2289 2576 2385;
    3074 2350 2326 2522 2442; 3075 2491 2387 2473 2430; 3076 2394 2514 2646 2576;
    3077 2470 2617 2492 2575; 3078 2388 2653 2338 2448; 3079 2658 2488 2570 2626;
    3080 2436 2386 2657 2370; 3081 2570 2300 2301 2458; 3082 2339 2314 2321 2519;
    3083 2368 2365 2540 2507; 3084 2318 2534 2582 2417; 3085 2332 2375 1018 1017;
    3086 2517 2403 2621 2567; 3087 2435 2528 2551 2545; 3088 2354 2373 2381 2363;
    3089 2454 2411 2390 2381; 3090 2500 2395 1023 1022; 3091 2433 2367 2495 2392;
    3092 2535 2607 2521 2516; 3093 2593 2397 2475 2481; 3094 2537 2536 2583 2405;
    3095 2385 2576 2371 2355; 3096 2545 2553 228 2443; 3097 2458 2301 2302 2607;
    3098 2376 2435 2545 2554; 3099 2512 2668 2662 2409; 3100 2474 2416 2636 2436;
    3101 2639 2428 2502 2551; 3102 2436 2636 2328 2386; 3103 2320 2457 2437 2664;
    3104 2538 2596 2459 2315; 3105 2672 2527 2610 2474; 3106 2501 2639 2551 2528;
    3107 2533 2482 2650 2406; 3108 2667 2412 2557 2522; 3109 2504 2342 2483 2349;
    3110 2478 2484 2340 2609; 3111 2319 2562 2496 2467; 3112 2469 2477 2595 2373;
    3113 2423 2648 2620 2456; 3114 2445 2509 2565 2317; 3115 2533 2406 2410 2602;
    3116 2668 2429 2427 2662; 3117 2372 2654 2616 2574; 3118 2471 2371 2559 2509;
    3119 2426 2399 2596 2538; 3120 2345 2305 2434 2536; 3121 2590 2455 2601 2599;
    3122 2414 2345 2536 2537; 3123 2321 2658 2626 2322; 3124 2671 2329 2611 2464;
    3125 2627 2465 2508 2476; 3126 2432 2608 2539 2562; 3127 2527 2531 2389 2610;
    3128 2583 2532 2671 2642; 3129 2395 2567 1024 1023; 3130 2642 2671 2464 2497;
    3131 2546 2439 2605 2316; 3132 2670 2550 2603 2393; 3133 2484 2297 2298 2340;
    3134 2420 2304 2305 2345; 3135 2343 2555 2503 2427; 3136 2610 2476 2360 2474;
    3137 2524 2511 2523 2566; 3138 2545 2551 2502 2553; 3139 2532 2556 2329 2671;
    3140 2341 2445 2361 2451; 3141 2475 2482 2533 2481; 3142 2485 2468 2506 2447;
    3143 2552 2630 2573 2331; 3144 2370 2657 2368 2325; 3145 2571 2396 2567 2395;
    3146 2652 2433 2392 2477; 3147 2620 2322 2626 2456; 3148 2340 2298 2408 2486;
    3149 2399 2647 2382 2493; 3150 2422 2467 2597 2513; 3151 2286 2287 2385 2355;
    3152 2633 2586 2468 2485; 3153 2656 2388 2448 2343; 3154 2348 2311 2312 2428;
    3155 2568 2572 2560 2400; 3156 2655 2649 2446 2543; 3157 2591 2535 2424 2397;
    3158 2582 2587 2423 2417; 3159 2509 2559 2538 2565; 3160 2591 2458 2607 2535;
    3161 2667 2664 2437 2412; 3162 2674 2339 2648 2577; 3163 2558 2318 2417 2615;
    3164 2549 2456 2626 2526; 3165 2365 2561 2588 2540; 3166 2554 2545 2443 2483;
    3167 2467 2496 2594 2597; 3168 2514 2518 2661 2646; 3169 2351 2552 2331 2654;
    3170 2397 2424 2482 2475; 3171 2564 2490 2449 2487; 3172 2437 2457 2440 2333;
    3173 2425 2674 2577 2587; 3174 2573 2593 2481 2391; 3175 2645 2479 2439 2546;
    3176 2674 2510 2314 2339; 3177 2396 2675 2517 2567; 3178 2617 2410 2418 2505;
    3179 2605 2337 2653 2544; 3180 2355 2371 2471 2341; 3181 2640 2516 2568 2400;
    3182 2603 2546 2316 2344; 3183 2663 2672 2474 2436; 3184 2644 2606 2652 2401;
    3185 2510 2413 2462 2314; 3186 2487 2449 2625 2432; 3187 2567 2621 1025 1024;
    3188 2607 2402 2420 2521; 3189 2482 2424 2640 2650; 3190 2638 2422 2513 2366;
    3191 2669 2660 2656 2334; 3192 2378 2542 2336 2632; 3193 2338 2447 2638 2463;
    3194 2315 2673 2550 2670; 3195 2646 2661 2472 2444; 3196 2522 2557 2531 2527;
    3197 2657 2386 2365 2368; 3198 2651 2478 2609 2649; 3199 2380 2613 2542 2378;
    3200 2661 2354 2363 2472; 3201 2383 2665 2377 2415; 3202 2675 2512 2409 2517;
    3203 2438 2331 2624 2600; 3204 2423 2456 2549 2548; 3205 2328 2634 2588 2561;
    3206 2586 2487 2432 2562; 3207 2630 2397 2593 2573; 3208 2296 249 2441 2320;
    3209 2327 2524 2665 2641; 3210 2409 2662 2666 2604; 3211 2371 2444 2637 2559;
    3212 2444 2472 2363 2637; 3213 2366 2618 2342 2504; 3214 2566 2523 2529 2377;
    3215 2597 2594 2622 2618; 3216 2465 2578 2380 2508; 3217 2402 2303 2304 2420;
    3218 2410 2406 2585 2418; 3219 2576 2646 2444 2371; 3220 2497 2464 2611 2619;
    3221 2473 2592 2643 2628; 3222 2648 2339 2519 2620; 3223 2441 249 2530 2651;
    3224 2624 2391 2602 2470; 3225 2524 2566 2377 2665; 3226 2334 2656 2343 2357;
    3227 2457 2330 2461 2440; 3228 2393 2603 2344 2498; 3229 2440 2461 2614 2631;
    3230 2495 2370 2325 2452; 3231 2351 2507 2630 2552; 3232 2569 2347 2348 2460;
    3233 2637 2363 2381 2426; 3234 2619 2358 2352 2490; 3235 2498 2344 2589 2515;
    3236 2341 2471 2509 2445; 3237 2346 2350 2442 2606; 3238 2463 2638 2366 2504;
    3239 2387 2369 2592 2473; 3240 2451 2361 2491 2323; 3241 2560 2420 2345 2414;
    3242 2594 2590 2599 2622; 3243 2445 2317 2364 2361; 3244 2455 2598 2639 2501;
    3245 2452 2325 2404 2411; 3246 2461 2651 2649 2655; 3247 2631 2614 2578 2465;
    3248 2470 2602 2410 2617; 3249 2386 2328 2561 2365; 3250 2295 2296 2320 2326;
    3251 2649 2609 2612 2446; 3252 2294 2295 2326 2350; 3253 2448 2338 2555 2343;
    3254 2455 2501 2528 2601; 3255 2434 2305 2306 2419; 3256 2640 2400 2581 2650;
    3257 2357 2343 2427 2429; 3258 2513 2597 2618 2366; 3259 2344 2669 2334 2589;
    3260 2559 2637 2426 2538; 3261 2421 2489 2389 2531; 3262 2490 2352 2347 2449;
    3263 2317 2565 2670 2364; 3264 2592 2407 2571 2643; 3265 2407 2499 2396 2571;
    3266 2647 2327 2641 2382; 3267 2494 2307 2308 2358; 3268 2508 2380 2378 2635;
    3269 2618 2622 2376 2342; 3270 2400 2560 2414 2581; 3271 2377 2529 2525 2479;
    3272 2599 2601 2528 2435; 3273 2461 2655 2543 2614; 3274 2532 2434 2419 2556;
    3275 2462 2408 2488 2658; 3276 2361 2364 2387 2491; 3277 2316 2605 2544 2660;
    3278 2412 2437 2333 2421; 3279 2418 2585 2537 2405; 3280 2382 2641 2374 2541;
    3281 2600 2624 2470 2575; 3282 2589 2334 2357 2453; 3283 2615 2417 2466 2636;
    3284 2449 2347 2569 2625; 3285 2377 2479 2645 2659; 3286 2635 2378 2632 2584;
    3287 2523 2575 2492 2529; 3288 2670 2393 2498 2369; 3289 2659 2645 2546 2603;
    3290 2511 2600 2575 2523; 3291 2421 2333 2440 2489; 3292 2493 2382 2541 2459;
    3293 2557 2412 2421 2531; 3294 64 2332 1017; 3295 2578 2613 2380;
    3296 2609 2340 2486; 3297 2368 2507 2351; 3298 2539 2608 2563;
    3299 2477 2392 2595; 3300 2468 2319 2506; 3301 2555 2338 2463;
    3302 2553 2502 228; 3303 2287 2288 2385; 3304 2673 2384 2550;
    3305 2661 2431 2354; 3306 2623 2580 2564; 3307 2450 2643 2500;
    3308 2326 2667 2522; 3309 2542 2579 2336; 3310 2438 2600 2511;
    3311 2619 2611 2358; 3312 2544 2653 2388; 3313 2405 2583 2642;
    3314 2547 2349 2353; 3315 2285 2286 2355; 3316 249 371 2530;
    3317 1021 2500 1022; 3350 2313 2708 1389 370; 3351 2708 2709 1390 1389;
    3352 2709 2710 1391 1390; 3353 2710 2711 1392 1391; 3354 2711 2712 1393 1392;
    3355 2712 2713 1394 1393; 3356 2713 2714 1395 1394; 3357 2714 2715 1396 1395;
    3358 2715 2716 1397 1396; 3359 2716 2717 1398 1397; 3360 2717 2718 1399 1398;
    3361 2718 2719 1400 1399; 3362 2719 2720 1401 1400; 3363 2720 2721 1402 1401;
    3364 2721 2722 1403 1402; 3365 2722 2707 376 1403; 3366 2312 2723 2708 2313;
    3367 2723 2724 2709 2708; 3368 2724 2725 2710 2709; 3369 2725 2726 2711 2710;
    3370 2726 2727 2712 2711; 3371 2727 2728 2713 2712; 3372 2728 2729 2714 2713;
    3373 2729 2730 2715 2714; 3374 2730 2731 2716 2715; 3375 2731 2732 2717 2716;
    3376 2732 2733 2718 2717; 3377 2733 2734 2719 2718; 3378 2734 2735 2720 2719;
    3379 2735 2736 2721 2720; 3380 2736 2737 2722 2721; 3381 2737 2706 2707 2722;
    3382 2311 2738 2723 2312; 3383 2738 2739 2724 2723; 3384 2739 2740 2725 2724;
    3385 2740 2741 2726 2725; 3386 2741 2742 2727 2726; 3387 2742 2743 2728 2727;
    3388 2743 2744 2729 2728; 3389 2744 2745 2730 2729; 3390 2745 2746 2731 2730;
    3391 2746 2747 2732 2731; 3392 2747 2748 2733 2732; 3393 2748 2749 2734 2733;
    3394 2749 2750 2735 2734; 3395 2750 2751 2736 2735; 3396 2751 2752 2737 2736;
    3397 2752 2705 2706 2737; 3398 2310 2753 2738 2311; 3399 2753 2754 2739 2738;
    3400 2754 2755 2740 2739; 3401 2755 2756 2741 2740; 3402 2756 2757 2742 2741;
    3403 2757 2758 2743 2742; 3404 2758 2759 2744 2743; 3405 2759 2760 2745 2744;
    3406 2760 2761 2746 2745; 3407 2761 2762 2747 2746; 3408 2762 2763 2748 2747;
    3409 2763 2764 2749 2748; 3410 2764 2765 2750 2749; 3411 2765 2766 2751 2750;
    3412 2766 2767 2752 2751; 3413 2767 2704 2705 2752; 3414 2309 2768 2753 2310;
    3415 2768 2769 2754 2753; 3416 2769 2770 2755 2754; 3417 2770 2771 2756 2755;
    3418 2771 2772 2757 2756; 3419 2772 2773 2758 2757; 3420 2773 2774 2759 2758;
    3421 2774 2775 2760 2759; 3422 2775 2776 2761 2760; 3423 2776 2777 2762 2761;
    3424 2777 2778 2763 2762; 3425 2778 2779 2764 2763; 3426 2779 2780 2765 2764;
    3427 2780 2781 2766 2765; 3428 2781 2782 2767 2766; 3429 2782 2703 2704 2767;
    3430 2308 2783 2768 2309; 3431 2783 2784 2769 2768; 3432 2784 2785 2770 2769;
    3433 2785 2786 2771 2770; 3434 2786 2787 2772 2771; 3435 2787 2788 2773 2772;
    3436 2788 2789 2774 2773; 3437 2789 2790 2775 2774; 3438 2790 2791 2776 2775;
    3439 2791 2792 2777 2776; 3440 2792 2793 2778 2777; 3441 2793 2794 2779 2778;
    3442 2794 2795 2780 2779; 3443 2795 2796 2781 2780; 3444 2796 2797 2782 2781;
    3445 2797 2702 2703 2782; 3446 2307 2798 2783 2308; 3447 2798 2799 2784 2783;
    3448 2799 2800 2785 2784; 3449 2800 2801 2786 2785; 3450 2801 2802 2787 2786;
    3451 2802 2803 2788 2787; 3452 2803 2804 2789 2788; 3453 2804 2805 2790 2789;
    3454 2805 2806 2791 2790; 3455 2806 2807 2792 2791; 3456 2807 2808 2793 2792;
    3457 2808 2809 2794 2793; 3458 2809 2810 2795 2794; 3459 2810 2811 2796 2795;
    3460 2811 2812 2797 2796; 3461 2812 2701 2702 2797; 3462 2306 2813 2798 2307;
    3463 2813 2814 2799 2798; 3464 2814 2815 2800 2799; 3465 2815 2816 2801 2800;
    3466 2816 2817 2802 2801; 3467 2817 2818 2803 2802; 3468 2818 2819 2804 2803;
    3469 2819 2820 2805 2804; 3470 2820 2821 2806 2805; 3471 2821 2822 2807 2806;
    3472 2822 2823 2808 2807; 3473 2823 2824 2809 2808; 3474 2824 2825 2810 2809;
    3475 2825 2826 2811 2810; 3476 2826 2827 2812 2811; 3477 2827 2700 2701 2812;
    3478 2305 2828 2813 2306; 3479 2828 2829 2814 2813; 3480 2829 2830 2815 2814;
    3481 2830 2831 2816 2815; 3482 2831 2832 2817 2816; 3483 2832 2833 2818 2817;
    3484 2833 2834 2819 2818; 3485 2834 2835 2820 2819; 3486 2835 2836 2821 2820;
    3487 2836 2837 2822 2821; 3488 2837 2838 2823 2822; 3489 2838 2839 2824 2823;
    3490 2839 2840 2825 2824; 3491 2840 2841 2826 2825; 3492 2841 2842 2827 2826;
    3493 2842 2699 2700 2827; 3494 2304 2843 2828 2305; 3495 2843 2844 2829 2828;
    3496 2844 2845 2830 2829; 3497 2845 2846 2831 2830; 3498 2846 2847 2832 2831;
    3499 2847 2848 2833 2832; 3500 2848 2849 2834 2833; 3501 2849 2850 2835 2834;
    3502 2850 2851 2836 2835; 3503 2851 2852 2837 2836; 3504 2852 2853 2838 2837;
    3505 2853 2854 2839 2838; 3506 2854 2855 2840 2839; 3507 2855 2856 2841 2840;
    3508 2856 2857 2842 2841; 3509 2857 2698 2699 2842; 3510 2303 2858 2843 2304;
    3511 2858 2859 2844 2843; 3512 2859 2860 2845 2844; 3513 2860 2861 2846 2845;
    3514 2861 2862 2847 2846; 3515 2862 2863 2848 2847; 3516 2863 2864 2849 2848;
    3517 2864 2865 2850 2849; 3518 2865 2866 2851 2850; 3519 2866 2867 2852 2851;
    3520 2867 2868 2853 2852; 3521 2868 2869 2854 2853; 3522 2869 2870 2855 2854;
    3523 2870 2871 2856 2855; 3524 2871 2872 2857 2856; 3525 2872 2697 2698 2857;
    3526 2302 2873 2858 2303; 3527 2873 2874 2859 2858; 3528 2874 2875 2860 2859;
    3529 2875 2876 2861 2860; 3530 2876 2877 2862 2861; 3531 2877 2878 2863 2862;
    3532 2878 2879 2864 2863; 3533 2879 2880 2865 2864; 3534 2880 2881 2866 2865;
    3535 2881 2882 2867 2866; 3536 2882 2883 2868 2867; 3537 2883 2884 2869 2868;
    3538 2884 2885 2870 2869; 3539 2885 2886 2871 2870; 3540 2886 2887 2872 2871;
    3541 2887 2696 2697 2872; 3542 2301 2888 2873 2302; 3543 2888 2889 2874 2873;
    3544 2889 2890 2875 2874; 3545 2890 2891 2876 2875; 3546 2891 2892 2877 2876;
    3547 2892 2893 2878 2877; 3548 2893 2894 2879 2878; 3549 2894 2895 2880 2879;
    3550 2895 2896 2881 2880; 3551 2896 2897 2882 2881; 3552 2897 2898 2883 2882;
    3553 2898 2899 2884 2883; 3554 2899 2900 2885 2884; 3555 2900 2901 2886 2885;
    3556 2901 2902 2887 2886; 3557 2902 2695 2696 2887; 3558 2300 2903 2888 2301;
    3559 2903 2904 2889 2888; 3560 2904 2905 2890 2889; 3561 2905 2906 2891 2890;
    3562 2906 2907 2892 2891; 3563 2907 2908 2893 2892; 3564 2908 2909 2894 2893;
    3565 2909 2910 2895 2894; 3566 2910 2911 2896 2895; 3567 2911 2912 2897 2896;
    3568 2912 2913 2898 2897; 3569 2913 2914 2899 2898; 3570 2914 2915 2900 2899;
    3571 2915 2916 2901 2900; 3572 2916 2917 2902 2901; 3573 2917 2694 2695 2902;
    3574 2299 2918 2903 2300; 3575 2918 2919 2904 2903; 3576 2919 2920 2905 2904;
    3577 2920 2921 2906 2905; 3578 2921 2922 2907 2906; 3579 2922 2923 2908 2907;
    3580 2923 2924 2909 2908; 3581 2924 2925 2910 2909; 3582 2925 2926 2911 2910;
    3583 2926 2927 2912 2911; 3584 2927 2928 2913 2912; 3585 2928 2929 2914 2913;
    3586 2929 2930 2915 2914; 3587 2930 2931 2916 2915; 3588 2931 2932 2917 2916;
    3589 2932 2693 2694 2917; 3590 2298 2933 2918 2299; 3591 2933 2934 2919 2918;
    3592 2934 2935 2920 2919; 3593 2935 2936 2921 2920; 3594 2936 2937 2922 2921;
    3595 2937 2938 2923 2922; 3596 2938 2939 2924 2923; 3597 2939 2940 2925 2924;
    3598 2940 2941 2926 2925; 3599 2941 2942 2927 2926; 3600 2942 2943 2928 2927;
    3601 2943 2944 2929 2928; 3602 2944 2945 2930 2929; 3603 2945 2946 2931 2930;
    3604 2946 2947 2932 2931; 3605 2947 2692 2693 2932; 3606 2297 2948 2933 2298;
    3607 2948 2949 2934 2933; 3608 2949 2950 2935 2934; 3609 2950 2951 2936 2935;
    3610 2951 2952 2937 2936; 3611 2952 2953 2938 2937; 3612 2953 2954 2939 2938;
    3613 2954 2955 2940 2939; 3614 2955 2956 2941 2940; 3615 2956 2957 2942 2941;
    3616 2957 2958 2943 2942; 3617 2958 2959 2944 2943; 3618 2959 2960 2945 2944;
    3619 2960 2961 2946 2945; 3620 2961 2962 2947 2946; 3621 2962 2691 2692 2947;
    3622 371 2676 2948 2297; 3623 2676 2677 2949 2948; 3624 2677 2678 2950 2949;
    3625 2678 2679 2951 2950; 3626 2679 2680 2952 2951; 3627 2680 2681 2953 2952;
    3628 2681 2682 2954 2953; 3629 2682 2683 2955 2954; 3630 2683 2684 2956 2955;
    3631 2684 2685 2957 2956; 3632 2685 2686 2958 2957; 3633 2686 2687 2959 2958;
    3634 2687 2688 2960 2959; 3635 2688 2689 2961 2960; 3636 2689 2690 2962 2961;
    3637 2690 377 2691 2962; 3670 2963 2995 1863 382; 3671 2995 2996 1864 1863;
    3672 2996 2997 1865 1864; 3673 2997 2998 1866 1865; 3674 2998 2999 1867 1866;
    3675 2999 3000 1868 1867; 3676 3000 3001 1869 1868; 3677 3001 3002 1870 1869;
    3678 3002 3003 1871 1870; 3679 3003 3004 1872 1871; 3680 3004 3005 1873 1872;
    3681 3005 3006 1874 1873; 3682 3006 3007 1875 1874; 3683 3007 3008 1876 1875;
    3684 3008 3009 1877 1876; 3685 3009 2707 376 1877; 3686 2964 3010 2995 2963;
    3687 3010 3011 2996 2995; 3688 3011 3012 2997 2996; 3689 3012 3013 2998 2997;
    3690 3013 3014 2999 2998; 3691 3014 3015 3000 2999; 3692 3015 3016 3001 3000;
    3693 3016 3017 3002 3001; 3694 3017 3018 3003 3002; 3695 3018 3019 3004 3003;
    3696 3019 3020 3005 3004; 3697 3020 3021 3006 3005; 3698 3021 3022 3007 3006;
    3699 3022 3023 3008 3007; 3700 3023 3024 3009 3008; 3701 3024 2706 2707 3009;
    3702 2965 3025 3010 2964; 3703 3025 3026 3011 3010; 3704 3026 3027 3012 3011;
    3705 3027 3028 3013 3012; 3706 3028 3029 3014 3013; 3707 3029 3030 3015 3014;
    3708 3030 3031 3016 3015; 3709 3031 3032 3017 3016; 3710 3032 3033 3018 3017;
    3711 3033 3034 3019 3018; 3712 3034 3035 3020 3019; 3713 3035 3036 3021 3020;
    3714 3036 3037 3022 3021; 3715 3037 3038 3023 3022; 3716 3038 3039 3024 3023;
    3717 3039 2705 2706 3024; 3718 2966 3040 3025 2965; 3719 3040 3041 3026 3025;
    3720 3041 3042 3027 3026; 3721 3042 3043 3028 3027; 3722 3043 3044 3029 3028;
    3723 3044 3045 3030 3029; 3724 3045 3046 3031 3030; 3725 3046 3047 3032 3031;
    3726 3047 3048 3033 3032; 3727 3048 3049 3034 3033; 3728 3049 3050 3035 3034;
    3729 3050 3051 3036 3035; 3730 3051 3052 3037 3036; 3731 3052 3053 3038 3037;
    3732 3053 3054 3039 3038; 3733 3054 2704 2705 3039; 3734 2967 3055 3040 2966;
    3735 3055 3056 3041 3040; 3736 3056 3057 3042 3041; 3737 3057 3058 3043 3042;
    3738 3058 3059 3044 3043; 3739 3059 3060 3045 3044; 3740 3060 3061 3046 3045;
    3741 3061 3062 3047 3046; 3742 3062 3063 3048 3047; 3743 3063 3064 3049 3048;
    3744 3064 3065 3050 3049; 3745 3065 3066 3051 3050; 3746 3066 3067 3052 3051;
    3747 3067 3068 3053 3052; 3748 3068 3069 3054 3053; 3749 3069 2703 2704 3054;
    3750 2968 3070 3055 2967; 3751 3070 3071 3056 3055; 3752 3071 3072 3057 3056;
    3753 3072 3073 3058 3057; 3754 3073 3074 3059 3058; 3755 3074 3075 3060 3059;
    3756 3075 3076 3061 3060; 3757 3076 3077 3062 3061; 3758 3077 3078 3063 3062;
    3759 3078 3079 3064 3063; 3760 3079 3080 3065 3064; 3761 3080 3081 3066 3065;
    3762 3081 3082 3067 3066; 3763 3082 3083 3068 3067; 3764 3083 3084 3069 3068;
    3765 3084 2702 2703 3069; 3766 2969 3085 3070 2968; 3767 3085 3086 3071 3070;
    3768 3086 3087 3072 3071; 3769 3087 3088 3073 3072; 3770 3088 3089 3074 3073;
    3771 3089 3090 3075 3074; 3772 3090 3091 3076 3075; 3773 3091 3092 3077 3076;
    3774 3092 3093 3078 3077; 3775 3093 3094 3079 3078; 3776 3094 3095 3080 3079;
    3777 3095 3096 3081 3080; 3778 3096 3097 3082 3081; 3779 3097 3098 3083 3082;
    3780 3098 3099 3084 3083; 3781 3099 2701 2702 3084; 3782 2970 3100 3085 2969;
    3783 3100 3101 3086 3085; 3784 3101 3102 3087 3086; 3785 3102 3103 3088 3087;
    3786 3103 3104 3089 3088; 3787 3104 3105 3090 3089; 3788 3105 3106 3091 3090;
    3789 3106 3107 3092 3091; 3790 3107 3108 3093 3092; 3791 3108 3109 3094 3093;
    3792 3109 3110 3095 3094; 3793 3110 3111 3096 3095; 3794 3111 3112 3097 3096;
    3795 3112 3113 3098 3097; 3796 3113 3114 3099 3098; 3797 3114 2700 2701 3099;
    3798 2971 3115 3100 2970; 3799 3115 3116 3101 3100; 3800 3116 3117 3102 3101;
    3801 3117 3118 3103 3102; 3802 3118 3119 3104 3103; 3803 3119 3120 3105 3104;
    3804 3120 3121 3106 3105; 3805 3121 3122 3107 3106; 3806 3122 3123 3108 3107;
    3807 3123 3124 3109 3108; 3808 3124 3125 3110 3109; 3809 3125 3126 3111 3110;
    3810 3126 3127 3112 3111; 3811 3127 3128 3113 3112; 3812 3128 3129 3114 3113;
    3813 3129 2699 2700 3114; 3814 2972 3130 3115 2971; 3815 3130 3131 3116 3115;
    3816 3131 3132 3117 3116; 3817 3132 3133 3118 3117; 3818 3133 3134 3119 3118;
    3819 3134 3135 3120 3119; 3820 3135 3136 3121 3120; 3821 3136 3137 3122 3121;
    3822 3137 3138 3123 3122; 3823 3138 3139 3124 3123; 3824 3139 3140 3125 3124;
    3825 3140 3141 3126 3125; 3826 3141 3142 3127 3126; 3827 3142 3143 3128 3127;
    3828 3143 3144 3129 3128; 3829 3144 2698 2699 3129; 3830 2973 3145 3130 2972;
    3831 3145 3146 3131 3130; 3832 3146 3147 3132 3131; 3833 3147 3148 3133 3132;
    3834 3148 3149 3134 3133; 3835 3149 3150 3135 3134; 3836 3150 3151 3136 3135;
    3837 3151 3152 3137 3136; 3838 3152 3153 3138 3137; 3839 3153 3154 3139 3138;
    3840 3154 3155 3140 3139; 3841 3155 3156 3141 3140; 3842 3156 3157 3142 3141;
    3843 3157 3158 3143 3142; 3844 3158 3159 3144 3143; 3845 3159 2697 2698 3144;
    3846 2974 3160 3145 2973; 3847 3160 3161 3146 3145; 3848 3161 3162 3147 3146;
    3849 3162 3163 3148 3147; 3850 3163 3164 3149 3148; 3851 3164 3165 3150 3149;
    3852 3165 3166 3151 3150; 3853 3166 3167 3152 3151; 3854 3167 3168 3153 3152;
    3855 3168 3169 3154 3153; 3856 3169 3170 3155 3154; 3857 3170 3171 3156 3155;
    3858 3171 3172 3157 3156; 3859 3172 3173 3158 3157; 3860 3173 3174 3159 3158;
    3861 3174 2696 2697 3159; 3862 2975 3175 3160 2974; 3863 3175 3176 3161 3160;
    3864 3176 3177 3162 3161; 3865 3177 3178 3163 3162; 3866 3178 3179 3164 3163;
    3867 3179 3180 3165 3164; 3868 3180 3181 3166 3165; 3869 3181 3182 3167 3166;
    3870 3182 3183 3168 3167; 3871 3183 3184 3169 3168; 3872 3184 3185 3170 3169;
    3873 3185 3186 3171 3170; 3874 3186 3187 3172 3171; 3875 3187 3188 3173 3172;
    3876 3188 3189 3174 3173; 3877 3189 2695 2696 3174; 3878 2976 3190 3175 2975;
    3879 3190 3191 3176 3175; 3880 3191 3192 3177 3176; 3881 3192 3193 3178 3177;
    3882 3193 3194 3179 3178; 3883 3194 3195 3180 3179; 3884 3195 3196 3181 3180;
    3885 3196 3197 3182 3181; 3886 3197 3198 3183 3182; 3887 3198 3199 3184 3183;
    3888 3199 3200 3185 3184; 3889 3200 3201 3186 3185; 3890 3201 3202 3187 3186;
    3891 3202 3203 3188 3187; 3892 3203 3204 3189 3188; 3893 3204 2694 2695 3189;
    3894 2977 3205 3190 2976; 3895 3205 3206 3191 3190; 3896 3206 3207 3192 3191;
    3897 3207 3208 3193 3192; 3898 3208 3209 3194 3193; 3899 3209 3210 3195 3194;
    3900 3210 3211 3196 3195; 3901 3211 3212 3197 3196; 3902 3212 3213 3198 3197;
    3903 3213 3214 3199 3198; 3904 3214 3215 3200 3199; 3905 3215 3216 3201 3200;
    3906 3216 3217 3202 3201; 3907 3217 3218 3203 3202; 3908 3218 3219 3204 3203;
    3909 3219 2693 2694 3204; 3910 2978 3220 3205 2977; 3911 3220 3221 3206 3205;
    3912 3221 3222 3207 3206; 3913 3222 3223 3208 3207; 3914 3223 3224 3209 3208;
    3915 3224 3225 3210 3209; 3916 3225 3226 3211 3210; 3917 3226 3227 3212 3211;
    3918 3227 3228 3213 3212; 3919 3228 3229 3214 3213; 3920 3229 3230 3215 3214;
    3921 3230 3231 3216 3215; 3922 3231 3232 3217 3216; 3923 3232 3233 3218 3217;
    3924 3233 3234 3219 3218; 3925 3234 2692 2693 3219; 3926 2979 3235 3220 2978;
    3927 3235 3236 3221 3220; 3928 3236 3237 3222 3221; 3929 3237 3238 3223 3222;
    3930 3238 3239 3224 3223; 3931 3239 3240 3225 3224; 3932 3240 3241 3226 3225;
    3933 3241 3242 3227 3226; 3934 3242 3243 3228 3227; 3935 3243 3244 3229 3228;
    3936 3244 3245 3230 3229; 3937 3245 3246 3231 3230; 3938 3246 3247 3232 3231;
    3939 3247 3248 3233 3232; 3940 3248 3249 3234 3233; 3941 3249 2691 2692 3234;
    3942 383 2980 3235 2979; 3943 2980 2981 3236 3235; 3944 2981 2982 3237 3236;
    3945 2982 2983 3238 3237; 3946 2983 2984 3239 3238; 3947 2984 2985 3240 3239;
    3948 2985 2986 3241 3240; 3949 2986 2987 3242 3241; 3950 2987 2988 3243 3242;
    3951 2988 2989 3244 3243; 3952 2989 2990 3245 3244; 3953 2990 2991 3246 3245;
    3954 2991 2992 3247 3246; 3955 2992 2993 3248 3247; 3956 2993 2994 3249 3248;
    3957 2994 377 2691 3249; 3989 134 3418 3290 3250; 3990 3473 3286 3434 3389;
    3991 3554 3544 3615 3390; 3992 3573 3630 3400 3619; 3993 3371 3318 3621 3339;
    3994 3463 3302 3557 3561; 3995 3482 3556 3420 3466; 3996 3579 3576 3453 3380;
    3997 3350 3382 3351 3640; 3998 3575 3536 3427 3530; 3999 3608 3632 3350 3341;
    4000 3547 3346 3457 3531; 4001 3290 3458 3397 3299; 4002 3316 3450 3410 3329;
    4003 3588 3326 2293 2292; 4004 3508 3341 3350 3640; 4005 3342 3596 3417 3291;
    4006 3530 3427 3606 3565; 4007 3470 3514 3320 3633; 4008 3314 3277 3278 3315;
    4009 3546 3579 3380 3477; 4010 3373 3617 3548 3552; 4011 3316 3329 2296 2295;
    4012 3329 3410 249 2296; 4013 3359 3462 3419 3562; 4014 3447 3609 3464 3346;
    4015 3506 3530 3565 3302; 4016 3251 3252 3322 3308; 4017 3426 3508 3640 3282;
    4018 3296 3461 3325 3578; 4019 3523 3386 3461 3296; 4020 3311 3283 3627 3636;
    4021 3455 3266 3267 3537; 4022 3327 3525 3383 3441; 4023 3522 3430 3514 3470;
    4024 3348 3357 3323 3393; 4025 3327 3602 3551 3525; 4026 3382 3344 3626 3351;
    4027 3456 3407 3594 3356; 4028 3319 3276 3277 3314; 4029 3583 3405 3478 3491;
    4030 3386 3273 3274 3461; 4031 3603 3433 3601 3295; 4032 3302 3565 3422 3557;
    4033 3293 3287 3631 3634; 4034 3334 3403 3337 3462; 4035 3394 3470 3633 3629;
    4036 3336 3465 3374 3559; 4037 3291 3417 2287 2286; 4038 3320 3316 2295 2294;
    4039 3304 3600 3452 3620; 4040 3368 3619 3444 3436; 4041 3541 3583 3491 3294;
    4042 3427 3315 3395 3606; 4043 3292 3335 3318 3371; 4044 3383 3525 3582 3603;
    4045 3378 3371 3339 3357; 4046 3601 3516 3493 3555; 4047 3281 3429 3625 3288;
    4048 3532 3505 3282 3637; 4049 3443 3475 3602 3327; 4050 3446 3492 3346 3547;
    4051 3299 3397 3596 3342; 4052 3469 3280 371 249; 4053 3374 3465 3482 3466;
    4054 3375 3265 3266 3455; 4055 3472 3385 3372 3487; 4056 3406 3590 3304 3572;
    4057 3397 3440 3595 3596; 4058 3555 3493 3425 3558; 4059 3331 3637 3336 3354;
    4060 3486 3288 3289 3587; 4061 3325 3275 3276 3319; 4062 3259 3260 3313 3485;
    4063 3610 3538 3362 3467; 4064 3414 3473 3389 3605; 4065 3384 3390 3515 3433;
    4066 3398 3436 3340 3321; 4067 3260 3261 3317 3313; 4068 3342 3291 2286 2285;
    4069 3408 3618 3428 3297; 4070 3487 3447 3346 3492; 4071 3446 3547 3590 3406;
    4072 3595 3610 3417 3596; 4073 3287 3408 3297 3424; 4074 3257 3258 3481 3361;
    4075 3600 3531 3454 3553; 4076 3258 3259 3485 3481; 4077 3485 3611 3398 3628;
    4078 3309 3343 3521 3450; 4079 3391 3502 3483 3607; 4080 3370 3571 3326 3588;
    4081 3250 3290 3299 99; 4082 3571 3633 3320 3326; 4083 3358 3448 3500 3569;
    4084 3430 3471 3316 3514; 4085 3420 3635 3479 3642; 4086 3303 3546 3477 3641;
    4087 3611 3368 3436 3398; 4088 3539 3488 3387 3527; 4089 3485 3313 3573 3611;
    4090 3484 3376 3571 3370; 4091 3590 3531 3600 3304; 4092 3459 3487 3492 3496;
    4093 3393 3323 3614 3366; 4094 3323 3541 3294 3614; 4095 3620 3452 3414 3305;
    4096 3621 3298 3405 3583; 4097 3298 3540 3358 3591; 4098 3517 3351 3626 3570;
    4099 3400 3630 3403 3334; 4100 3466 3420 3642 3363; 4101 3435 3553 3529 3286;
    4102 3487 3372 3609 3447; 4103 3340 3562 3421 3348; 4104 3573 3409 3639 3630;
    4105 3563 3366 3460 3426; 4106 3584 3472 3487 3459; 4107 3395 3279 3280 3469;
    4108 3380 3453 3375 3429; 4109 3497 372 3264 3451; 4110 3589 3566 3402 3343;
    4111 3551 3501 3285 3525; 4112 3627 3511 3355 3623; 4113 3507 3555 3558 3365;
    4114 3256 3257 3361 3543; 4115 3497 3451 3445 3618; 4116 3413 3579 3546 3509;
    4117 3510 3413 3509 3580; 4118 3357 3339 3541 3323; 4119 3599 3303 3641 3392;
    4120 3593 3537 3425 3493; 4121 3501 3392 3554 3549; 4122 3529 3506 3302 3463;
    4123 3433 3515 3516 3601; 4124 3574 3269 3270 3369; 4125 3483 3488 3539 3535;
    4126 3409 3489 3494 3639; 4127 3407 3598 3432 3594; 4128 3326 3320 2294 2293;
    4129 3420 3324 3396 3635; 4130 3474 3507 3365 3597; 4131 3562 3419 3378 3421;
    4132 3551 3599 3392 3501; 4133 3365 3558 3364 3597; 4134 134 3251 3308 3418;
    4135 3346 3464 3586 3457; 4136 3548 3381 3504 3552; 4137 3581 3510 3580 3545;
    4138 3417 3467 2288 2287; 4139 3399 3592 3536 3575; 4140 3356 3594 3443 3577;
    4141 3503 3401 3499 3550; 4142 3255 3256 3543 3352; 4143 3317 3293 3489 3409;
    4144 3458 3354 3440 3397; 4145 3361 3481 3613 3543; 4146 3437 3584 3459 3542;
    4147 3355 3620 3305 3415; 4148 3625 3455 3537 3593; 4149 3403 3353 3624 3337;
    4150 3537 3267 3268 3425; 4151 3306 3281 3288 3486; 4152 3335 3332 3507 3474;
    4153 3285 3501 3549 3384; 4154 3299 3342 2285 2284; 4155 3484 3370 3588 3534;
    4156 3402 3495 3518 3512; 4157 3321 3340 3348 3330; 4158 3421 3378 3357 3348;
    4159 3467 3362 2290 2289; 4160 3400 3334 3462 3359; 4161 3502 3574 3488 3483;
    4162 3560 3364 3442 3448; 4163 3504 3503 3550 3372; 4164 3352 3543 3338 3322;
    4165 3512 3520 249 3410; 4166 3425 3268 3269 3574; 4167 3343 3402 3512 3521;
    4168 3479 3635 3629 3376; 4169 3441 3383 3603 3403; 4170 3606 3395 3469 3518;
    4171 3403 3603 3295 3353; 4172 3287 3424 3404 3631; 4173 3505 3563 3426 3282;
    4174 3639 3494 3577 3441; 4175 3468 3606 3518 3495; 4176 3500 3449 3617 3373;
    4177 3634 3379 3524 3489; 4178 3471 3309 3450 3316; 4179 3445 3451 3307 3576;
    4180 3286 3529 3463 3434; 4181 3436 3444 3562 3340; 4182 3390 3615 3587 3423;
    4183 3412 3476 3532 3284; 4184 3500 3373 3377 3569; 4185 3635 3396 3394 3629;
    4186 3339 3621 3583 3541; 4187 3438 3338 3526 3476; 4188 3393 3366 3563 3505;
    4189 3312 3272 3401 3503; 4190 3557 3422 3568 3566; 4191 3381 3312 3503 3504;
    4192 3288 3625 3593 3289; 4193 3638 3296 3578 3431; 4194 3594 3432 3475 3443;
    4195 3399 3575 3506 3529; 4196 3494 3498 3356 3577; 4197 3550 3499 3638 3609;
    4198 3362 3534 2291 2290; 4199 3609 3638 3431 3464; 4200 3513 3406 3572 3283;
    4201 3637 3517 3570 3360; 4202 3451 3264 3265 3307; 4203 3387 3271 3272 3312;
    4204 3310 3522 3470 3394; 4205 3577 3443 3327 3441; 4206 3491 3478 3490 3533;
    4207 3512 3518 3469 3520; 4208 3499 3523 3296 3638; 4209 3308 3412 3328 3418;
    4210 3442 3449 3500 3448; 4211 3452 3435 3473 3414; 4212 3519 3597 3540 3298;
    4213 3337 3624 3335 3292; 4214 3538 3363 3534 3362; 4215 3619 3400 3359 3444;
    4216 3587 3289 3593 3423; 4217 3307 3265 3375 3453; 4218 3366 3614 3349 3460;
    4219 3389 3434 3564 3480; 4220 3253 3254 3352 3322; 4221 3600 3553 3435 3452;
    4222 3623 3355 3415 3310; 4223 3315 3278 3279 3395; 4224 3535 3539 3527 3367;
    4225 3622 3616 3413 3510; 4226 3558 3502 3391 3364; 4227 3549 3554 3390 3384;
    4228 3476 3526 3505 3532; 4229 3558 3425 3574 3502; 4230 3634 3631 3404 3379;
    4231 3641 3306 3615 3544; 4232 3525 3285 3384 3582; 4233 3516 3423 3593 3493;
    4234 3332 3528 3555 3507; 4235 3521 3512 3410 3450; 4236 3434 3463 3561 3564;
    4237 3481 3485 3628 3613; 4238 3318 3519 3298 3621; 4239 3364 3391 3449 3442;
    4240 3531 3457 3416 3454; 4241 3404 3424 3407 3300; 4242 3392 3641 3544 3554;
    4243 3540 3560 3448 3358; 4244 3612 3446 3406 3513; 4245 3641 3477 3281 3306;
    4246 3363 3642 3484 3534; 4247 3584 3377 3385 3472; 4248 3572 3304 3620 3511;
    4249 3322 3338 3438 3308; 4250 3607 3483 3535 3367; 4251 3570 3513 3283 3311;
    4252 3630 3639 3441 3403; 4253 3611 3573 3619 3368; 4254 3477 3380 3429 3281;
    4255 3454 3416 3592 3399; 4256 3534 3588 2292 2291; 4257 3574 3369 3387 3488;
    4258 3449 3391 3607 3617; 4259 3605 3389 3480 3333; 4260 3636 3627 3623 3301;
    4261 3345 3509 3303 3599; 4262 3305 3414 3605 3430; 4263 3282 3640 3517 3637;
    4264 3613 3628 3439 3411; 4265 3489 3524 3498 3494; 4266 3624 3353 3332 3335;
    4267 3618 3445 3576 3616; 4268 3347 3580 3509 3345; 4269 3628 3321 3330 3439;
    4270 3350 3632 3344 3382; 4271 3642 3479 3376 3484; 4272 3405 3298 3591 3567;
    4273 3390 3423 3516 3515; 4274 3295 3601 3555 3528; 4275 3553 3454 3399 3529;
    4276 3597 3364 3560 3540; 4277 3263 270 3408 3287; 4278 3294 3491 3632 3608;
    4279 3376 3629 3633 3571; 4280 3338 3411 3604 3526; 4281 3411 3439 3330 3604;
    4282 3333 3585 3309 3471; 4283 3533 3490 3496 3344; 4284 3564 3561 3589 3585;
    4285 3432 3545 3347 3475; 4286 3369 3270 3271 3387; 4287 3377 3373 3552 3385;
    4288 3543 3613 3411 3338; 4289 3464 3431 3578 3586; 4290 3440 3559 3610 3595;
    4291 3615 3306 3486 3587; 4292 3408 270 3497 3618; 4293 3591 3358 3569 3437;
    4294 3491 3533 3344 3632; 4295 3301 3623 3310 3324; 4296 3424 3297 3428 3407;
    4297 3360 3570 3311 3465; 4298 3407 3428 3581 3598; 4299 3462 3337 3292 3419;
    4300 3318 3474 3597 3519; 4301 3536 3314 3315 3427; 4302 3604 3330 3348 3393;
    4303 3586 3325 3319 3457; 4304 3465 3311 3556 3482; 4305 3308 3438 3476 3412;
    4306 3313 3317 3409 3573; 4307 3430 3605 3333 3471; 4308 3354 3336 3559 3440;
    4309 3418 3328 3458 3290; 4310 3527 3387 3312 3381; 4311 3561 3557 3566 3589;
    4312 3412 3284 3331 3328; 4313 3422 3565 3606 3468; 4314 3419 3292 3371 3378;
    4315 3428 3618 3616 3622; 4316 3598 3581 3545 3432; 4317 3437 3569 3377 3584;
    4318 3353 3295 3528 3332; 4319 3262 3263 3287 3293; 4320 3616 3576 3579 3413;
    4321 3261 3262 3293 3317; 4322 3415 3305 3522 3310; 4323 3422 3468 3495 3568;
    4324 3401 3272 3273 3386; 4325 3607 3367 3548 3617; 4326 3324 3310 3394 3396;
    4327 3480 3564 3585 3333; 4328 3311 3636 3301 3556; 4329 3526 3604 3393 3505;
    4330 3388 3456 3356 3498; 4331 3457 3319 3314 3416; 4332 3284 3532 3637 3331;
    4333 3559 3374 3538 3610; 4334 3374 3466 3363 3538; 4335 3614 3294 3608 3349;
    4336 3461 3274 3275 3325; 4337 3475 3347 3345 3602; 4338 3585 3589 3343 3309;
    4339 3367 3527 3381 3548; 4340 3344 3496 3492 3446; 4341 3566 3568 3495 3402;
    4342 3428 3622 3510 3581; 4343 3499 3401 3386 3523; 4344 3429 3375 3455 3625;
    4345 3328 3331 3354 3458; 4346 3283 3572 3511 3627; 4347 3379 3404 3300 3388;
    4348 3385 3552 3504 3372; 4349 3349 3608 3341 3508; 4350 3567 3591 3437 3542;
    4351 3556 3301 3324 3420; 4352 3582 3384 3433 3603; 4353 3416 3314 3536 3592;
    4354 3344 3446 3612 3626; 4355 3602 3345 3599 3551; 4356 3490 3542 3459 3496;
    4357 3637 3360 3465 3336; 4358 3626 3612 3513 3570; 4359 3478 3567 3542 3490;
    4360 3388 3300 3407 3456; 4361 3460 3349 3508 3426; 4362 3524 3379 3388 3498;
    4363 99 3299 2284; 4364 3545 3580 3347; 4365 3576 3307 3453;
    4366 3335 3474 3318; 4367 3506 3575 3530; 4368 3444 3359 3562;
    4369 3435 3286 3473; 4370 3522 3305 3430; 4371 3520 3469 249;
    4372 3254 3255 3352; 4373 3640 3351 3517; 4374 3628 3398 3321;
    4375 3590 3547 3531; 4376 3417 3610 3467; 4377 3293 3634 3489;
    4378 3509 3546 3303; 4379 3405 3567 3478; 4380 3586 3578 3325;
    4381 3511 3620 3355; 4382 3372 3550 3609; 4383 3514 3316 3320;
    4384 3252 3253 3322; 4385 270 372 3497; 4386 2288 3467 2289;
    4419 3280 3675 2676 371; 4420 3675 3676 2677 2676; 4421 3676 3677 2678 2677;
    4422 3677 3678 2679 2678; 4423 3678 3679 2680 2679; 4424 3679 3680 2681 2680;
    4425 3680 3681 2682 2681; 4426 3681 3682 2683 2682; 4427 3682 3683 2684 2683;
    4428 3683 3684 2685 2684; 4429 3684 3685 2686 2685; 4430 3685 3686 2687 2686;
    4431 3686 3687 2688 2687; 4432 3687 3688 2689 2688; 4433 3688 3689 2690 2689;
    4434 3689 3674 377 2690; 4435 3279 3690 3675 3280; 4436 3690 3691 3676 3675;
    4437 3691 3692 3677 3676; 4438 3692 3693 3678 3677; 4439 3693 3694 3679 3678;
    4440 3694 3695 3680 3679; 4441 3695 3696 3681 3680; 4442 3696 3697 3682 3681;
    4443 3697 3698 3683 3682; 4444 3698 3699 3684 3683; 4445 3699 3700 3685 3684;
    4446 3700 3701 3686 3685; 4447 3701 3702 3687 3686; 4448 3702 3703 3688 3687;
    4449 3703 3704 3689 3688; 4450 3704 3673 3674 3689; 4451 3278 3705 3690 3279;
    4452 3705 3706 3691 3690; 4453 3706 3707 3692 3691; 4454 3707 3708 3693 3692;
    4455 3708 3709 3694 3693; 4456 3709 3710 3695 3694; 4457 3710 3711 3696 3695;
    4458 3711 3712 3697 3696; 4459 3712 3713 3698 3697; 4460 3713 3714 3699 3698;
    4461 3714 3715 3700 3699; 4462 3715 3716 3701 3700; 4463 3716 3717 3702 3701;
    4464 3717 3718 3703 3702; 4465 3718 3719 3704 3703; 4466 3719 3672 3673 3704;
    4467 3277 3720 3705 3278; 4468 3720 3721 3706 3705; 4469 3721 3722 3707 3706;
    4470 3722 3723 3708 3707; 4471 3723 3724 3709 3708; 4472 3724 3725 3710 3709;
    4473 3725 3726 3711 3710; 4474 3726 3727 3712 3711; 4475 3727 3728 3713 3712;
    4476 3728 3729 3714 3713; 4477 3729 3730 3715 3714; 4478 3730 3731 3716 3715;
    4479 3731 3732 3717 3716; 4480 3732 3733 3718 3717; 4481 3733 3734 3719 3718;
    4482 3734 3671 3672 3719; 4483 3276 3735 3720 3277; 4484 3735 3736 3721 3720;
    4485 3736 3737 3722 3721; 4486 3737 3738 3723 3722; 4487 3738 3739 3724 3723;
    4488 3739 3740 3725 3724; 4489 3740 3741 3726 3725; 4490 3741 3742 3727 3726;
    4491 3742 3743 3728 3727; 4492 3743 3744 3729 3728; 4493 3744 3745 3730 3729;
    4494 3745 3746 3731 3730; 4495 3746 3747 3732 3731; 4496 3747 3748 3733 3732;
    4497 3748 3749 3734 3733; 4498 3749 3670 3671 3734; 4499 3275 3750 3735 3276;
    4500 3750 3751 3736 3735; 4501 3751 3752 3737 3736; 4502 3752 3753 3738 3737;
    4503 3753 3754 3739 3738; 4504 3754 3755 3740 3739; 4505 3755 3756 3741 3740;
    4506 3756 3757 3742 3741; 4507 3757 3758 3743 3742; 4508 3758 3759 3744 3743;
    4509 3759 3760 3745 3744; 4510 3760 3761 3746 3745; 4511 3761 3762 3747 3746;
    4512 3762 3763 3748 3747; 4513 3763 3764 3749 3748; 4514 3764 3669 3670 3749;
    4515 3274 3765 3750 3275; 4516 3765 3766 3751 3750; 4517 3766 3767 3752 3751;
    4518 3767 3768 3753 3752; 4519 3768 3769 3754 3753; 4520 3769 3770 3755 3754;
    4521 3770 3771 3756 3755; 4522 3771 3772 3757 3756; 4523 3772 3773 3758 3757;
    4524 3773 3774 3759 3758; 4525 3774 3775 3760 3759; 4526 3775 3776 3761 3760;
    4527 3776 3777 3762 3761; 4528 3777 3778 3763 3762; 4529 3778 3779 3764 3763;
    4530 3779 3668 3669 3764; 4531 3273 3780 3765 3274; 4532 3780 3781 3766 3765;
    4533 3781 3782 3767 3766; 4534 3782 3783 3768 3767; 4535 3783 3784 3769 3768;
    4536 3784 3785 3770 3769; 4537 3785 3786 3771 3770; 4538 3786 3787 3772 3771;
    4539 3787 3788 3773 3772; 4540 3788 3789 3774 3773; 4541 3789 3790 3775 3774;
    4542 3790 3791 3776 3775; 4543 3791 3792 3777 3776; 4544 3792 3793 3778 3777;
    4545 3793 3794 3779 3778; 4546 3794 3667 3668 3779; 4547 3272 3795 3780 3273;
    4548 3795 3796 3781 3780; 4549 3796 3797 3782 3781; 4550 3797 3798 3783 3782;
    4551 3798 3799 3784 3783; 4552 3799 3800 3785 3784; 4553 3800 3801 3786 3785;
    4554 3801 3802 3787 3786; 4555 3802 3803 3788 3787; 4556 3803 3804 3789 3788;
    4557 3804 3805 3790 3789; 4558 3805 3806 3791 3790; 4559 3806 3807 3792 3791;
    4560 3807 3808 3793 3792; 4561 3808 3809 3794 3793; 4562 3809 3666 3667 3794;
    4563 3271 3810 3795 3272; 4564 3810 3811 3796 3795; 4565 3811 3812 3797 3796;
    4566 3812 3813 3798 3797; 4567 3813 3814 3799 3798; 4568 3814 3815 3800 3799;
    4569 3815 3816 3801 3800; 4570 3816 3817 3802 3801; 4571 3817 3818 3803 3802;
    4572 3818 3819 3804 3803; 4573 3819 3820 3805 3804; 4574 3820 3821 3806 3805;
    4575 3821 3822 3807 3806; 4576 3822 3823 3808 3807; 4577 3823 3824 3809 3808;
    4578 3824 3665 3666 3809; 4579 3270 3825 3810 3271; 4580 3825 3826 3811 3810;
    4581 3826 3827 3812 3811; 4582 3827 3828 3813 3812; 4583 3828 3829 3814 3813;
    4584 3829 3830 3815 3814; 4585 3830 3831 3816 3815; 4586 3831 3832 3817 3816;
    4587 3832 3833 3818 3817; 4588 3833 3834 3819 3818; 4589 3834 3835 3820 3819;
    4590 3835 3836 3821 3820; 4591 3836 3837 3822 3821; 4592 3837 3838 3823 3822;
    4593 3838 3839 3824 3823; 4594 3839 3664 3665 3824; 4595 3269 3840 3825 3270;
    4596 3840 3841 3826 3825; 4597 3841 3842 3827 3826; 4598 3842 3843 3828 3827;
    4599 3843 3844 3829 3828; 4600 3844 3845 3830 3829; 4601 3845 3846 3831 3830;
    4602 3846 3847 3832 3831; 4603 3847 3848 3833 3832; 4604 3848 3849 3834 3833;
    4605 3849 3850 3835 3834; 4606 3850 3851 3836 3835; 4607 3851 3852 3837 3836;
    4608 3852 3853 3838 3837; 4609 3853 3854 3839 3838; 4610 3854 3663 3664 3839;
    4611 3268 3855 3840 3269; 4612 3855 3856 3841 3840; 4613 3856 3857 3842 3841;
    4614 3857 3858 3843 3842; 4615 3858 3859 3844 3843; 4616 3859 3860 3845 3844;
    4617 3860 3861 3846 3845; 4618 3861 3862 3847 3846; 4619 3862 3863 3848 3847;
    4620 3863 3864 3849 3848; 4621 3864 3865 3850 3849; 4622 3865 3866 3851 3850;
    4623 3866 3867 3852 3851; 4624 3867 3868 3853 3852; 4625 3868 3869 3854 3853;
    4626 3869 3662 3663 3854; 4627 3267 3870 3855 3268; 4628 3870 3871 3856 3855;
    4629 3871 3872 3857 3856; 4630 3872 3873 3858 3857; 4631 3873 3874 3859 3858;
    4632 3874 3875 3860 3859; 4633 3875 3876 3861 3860; 4634 3876 3877 3862 3861;
    4635 3877 3878 3863 3862; 4636 3878 3879 3864 3863; 4637 3879 3880 3865 3864;
    4638 3880 3881 3866 3865; 4639 3881 3882 3867 3866; 4640 3882 3883 3868 3867;
    4641 3883 3884 3869 3868; 4642 3884 3661 3662 3869; 4643 3266 3885 3870 3267;
    4644 3885 3886 3871 3870; 4645 3886 3887 3872 3871; 4646 3887 3888 3873 3872;
    4647 3888 3889 3874 3873; 4648 3889 3890 3875 3874; 4649 3890 3891 3876 3875;
    4650 3891 3892 3877 3876; 4651 3892 3893 3878 3877; 4652 3893 3894 3879 3878;
    4653 3894 3895 3880 3879; 4654 3895 3896 3881 3880; 4655 3896 3897 3882 3881;
    4656 3897 3898 3883 3882; 4657 3898 3899 3884 3883; 4658 3899 3660 3661 3884;
    4659 3265 3900 3885 3266; 4660 3900 3901 3886 3885; 4661 3901 3902 3887 3886;
    4662 3902 3903 3888 3887; 4663 3903 3904 3889 3888; 4664 3904 3905 3890 3889;
    4665 3905 3906 3891 3890; 4666 3906 3907 3892 3891; 4667 3907 3908 3893 3892;
    4668 3908 3909 3894 3893; 4669 3909 3910 3895 3894; 4670 3910 3911 3896 3895;
    4671 3911 3912 3897 3896; 4672 3912 3913 3898 3897; 4673 3913 3914 3899 3898;
    4674 3914 3659 3660 3899; 4675 3264 3915 3900 3265; 4676 3915 3916 3901 3900;
    4677 3916 3917 3902 3901; 4678 3917 3918 3903 3902; 4679 3918 3919 3904 3903;
    4680 3919 3920 3905 3904; 4681 3920 3921 3906 3905; 4682 3921 3922 3907 3906;
    4683 3922 3923 3908 3907; 4684 3923 3924 3909 3908; 4685 3924 3925 3910 3909;
    4686 3925 3926 3911 3910; 4687 3926 3927 3912 3911; 4688 3927 3928 3913 3912;
    4689 3928 3929 3914 3913; 4690 3929 3658 3659 3914; 4691 372 3643 3915 3264;
    4692 3643 3644 3916 3915; 4693 3644 3645 3917 3916; 4694 3645 3646 3918 3917;
    4695 3646 3647 3919 3918; 4696 3647 3648 3920 3919; 4697 3648 3649 3921 3920;
    4698 3649 3650 3922 3921; 4699 3650 3651 3923 3922; 4700 3651 3652 3924 3923;
    4701 3652 3653 3925 3924; 4702 3653 3654 3926 3925; 4703 3654 3655 3927 3926;
    4704 3655 3656 3928 3927; 4705 3656 3657 3929 3928; 4706 3657 378 3658 3929;
    4739 3930 3962 2980 383; 4740 3962 3963 2981 2980; 4741 3963 3964 2982 2981;
    4742 3964 3965 2983 2982; 4743 3965 3966 2984 2983; 4744 3966 3967 2985 2984;
    4745 3967 3968 2986 2985; 4746 3968 3969 2987 2986; 4747 3969 3970 2988 2987;
    4748 3970 3971 2989 2988; 4749 3971 3972 2990 2989; 4750 3972 3973 2991 2990;
    4751 3973 3974 2992 2991; 4752 3974 3975 2993 2992; 4753 3975 3976 2994 2993;
    4754 3976 3674 377 2994; 4755 3931 3977 3962 3930; 4756 3977 3978 3963 3962;
    4757 3978 3979 3964 3963; 4758 3979 3980 3965 3964; 4759 3980 3981 3966 3965;
    4760 3981 3982 3967 3966; 4761 3982 3983 3968 3967; 4762 3983 3984 3969 3968;
    4763 3984 3985 3970 3969; 4764 3985 3986 3971 3970; 4765 3986 3987 3972 3971;
    4766 3987 3988 3973 3972; 4767 3988 3989 3974 3973; 4768 3989 3990 3975 3974;
    4769 3990 3991 3976 3975; 4770 3991 3673 3674 3976; 4771 3932 3992 3977 3931;
    4772 3992 3993 3978 3977; 4773 3993 3994 3979 3978; 4774 3994 3995 3980 3979;
    4775 3995 3996 3981 3980; 4776 3996 3997 3982 3981; 4777 3997 3998 3983 3982;
    4778 3998 3999 3984 3983; 4779 3999 4000 3985 3984; 4780 4000 4001 3986 3985;
    4781 4001 4002 3987 3986; 4782 4002 4003 3988 3987; 4783 4003 4004 3989 3988;
    4784 4004 4005 3990 3989; 4785 4005 4006 3991 3990; 4786 4006 3672 3673 3991;
    4787 3933 4007 3992 3932; 4788 4007 4008 3993 3992; 4789 4008 4009 3994 3993;
    4790 4009 4010 3995 3994; 4791 4010 4011 3996 3995; 4792 4011 4012 3997 3996;
    4793 4012 4013 3998 3997; 4794 4013 4014 3999 3998; 4795 4014 4015 4000 3999;
    4796 4015 4016 4001 4000; 4797 4016 4017 4002 4001; 4798 4017 4018 4003 4002;
    4799 4018 4019 4004 4003; 4800 4019 4020 4005 4004; 4801 4020 4021 4006 4005;
    4802 4021 3671 3672 4006; 4803 3934 4022 4007 3933; 4804 4022 4023 4008 4007;
    4805 4023 4024 4009 4008; 4806 4024 4025 4010 4009; 4807 4025 4026 4011 4010;
    4808 4026 4027 4012 4011; 4809 4027 4028 4013 4012; 4810 4028 4029 4014 4013;
    4811 4029 4030 4015 4014; 4812 4030 4031 4016 4015; 4813 4031 4032 4017 4016;
    4814 4032 4033 4018 4017; 4815 4033 4034 4019 4018; 4816 4034 4035 4020 4019;
    4817 4035 4036 4021 4020; 4818 4036 3670 3671 4021; 4819 3935 4037 4022 3934;
    4820 4037 4038 4023 4022; 4821 4038 4039 4024 4023; 4822 4039 4040 4025 4024;
    4823 4040 4041 4026 4025; 4824 4041 4042 4027 4026; 4825 4042 4043 4028 4027;
    4826 4043 4044 4029 4028; 4827 4044 4045 4030 4029; 4828 4045 4046 4031 4030;
    4829 4046 4047 4032 4031; 4830 4047 4048 4033 4032; 4831 4048 4049 4034 4033;
    4832 4049 4050 4035 4034; 4833 4050 4051 4036 4035; 4834 4051 3669 3670 4036;
    4835 3936 4052 4037 3935; 4836 4052 4053 4038 4037; 4837 4053 4054 4039 4038;
    4838 4054 4055 4040 4039; 4839 4055 4056 4041 4040; 4840 4056 4057 4042 4041;
    4841 4057 4058 4043 4042; 4842 4058 4059 4044 4043; 4843 4059 4060 4045 4044;
    4844 4060 4061 4046 4045; 4845 4061 4062 4047 4046; 4846 4062 4063 4048 4047;
    4847 4063 4064 4049 4048; 4848 4064 4065 4050 4049; 4849 4065 4066 4051 4050;
    4850 4066 3668 3669 4051; 4851 3937 4067 4052 3936; 4852 4067 4068 4053 4052;
    4853 4068 4069 4054 4053; 4854 4069 4070 4055 4054; 4855 4070 4071 4056 4055;
    4856 4071 4072 4057 4056; 4857 4072 4073 4058 4057; 4858 4073 4074 4059 4058;
    4859 4074 4075 4060 4059; 4860 4075 4076 4061 4060; 4861 4076 4077 4062 4061;
    4862 4077 4078 4063 4062; 4863 4078 4079 4064 4063; 4864 4079 4080 4065 4064;
    4865 4080 4081 4066 4065; 4866 4081 3667 3668 4066; 4867 3938 4082 4067 3937;
    4868 4082 4083 4068 4067; 4869 4083 4084 4069 4068; 4870 4084 4085 4070 4069;
    4871 4085 4086 4071 4070; 4872 4086 4087 4072 4071; 4873 4087 4088 4073 4072;
    4874 4088 4089 4074 4073; 4875 4089 4090 4075 4074; 4876 4090 4091 4076 4075;
    4877 4091 4092 4077 4076; 4878 4092 4093 4078 4077; 4879 4093 4094 4079 4078;
    4880 4094 4095 4080 4079; 4881 4095 4096 4081 4080; 4882 4096 3666 3667 4081;
    4883 3939 4097 4082 3938; 4884 4097 4098 4083 4082; 4885 4098 4099 4084 4083;
    4886 4099 4100 4085 4084; 4887 4100 4101 4086 4085; 4888 4101 4102 4087 4086;
    4889 4102 4103 4088 4087; 4890 4103 4104 4089 4088; 4891 4104 4105 4090 4089;
    4892 4105 4106 4091 4090; 4893 4106 4107 4092 4091; 4894 4107 4108 4093 4092;
    4895 4108 4109 4094 4093; 4896 4109 4110 4095 4094; 4897 4110 4111 4096 4095;
    4898 4111 3665 3666 4096; 4899 3940 4112 4097 3939; 4900 4112 4113 4098 4097;
    4901 4113 4114 4099 4098; 4902 4114 4115 4100 4099; 4903 4115 4116 4101 4100;
    4904 4116 4117 4102 4101; 4905 4117 4118 4103 4102; 4906 4118 4119 4104 4103;
    4907 4119 4120 4105 4104; 4908 4120 4121 4106 4105; 4909 4121 4122 4107 4106;
    4910 4122 4123 4108 4107; 4911 4123 4124 4109 4108; 4912 4124 4125 4110 4109;
    4913 4125 4126 4111 4110; 4914 4126 3664 3665 4111; 4915 3941 4127 4112 3940;
    4916 4127 4128 4113 4112; 4917 4128 4129 4114 4113; 4918 4129 4130 4115 4114;
    4919 4130 4131 4116 4115; 4920 4131 4132 4117 4116; 4921 4132 4133 4118 4117;
    4922 4133 4134 4119 4118; 4923 4134 4135 4120 4119; 4924 4135 4136 4121 4120;
    4925 4136 4137 4122 4121; 4926 4137 4138 4123 4122; 4927 4138 4139 4124 4123;
    4928 4139 4140 4125 4124; 4929 4140 4141 4126 4125; 4930 4141 3663 3664 4126;
    4931 3942 4142 4127 3941; 4932 4142 4143 4128 4127; 4933 4143 4144 4129 4128;
    4934 4144 4145 4130 4129; 4935 4145 4146 4131 4130; 4936 4146 4147 4132 4131;
    4937 4147 4148 4133 4132; 4938 4148 4149 4134 4133; 4939 4149 4150 4135 4134;
    4940 4150 4151 4136 4135; 4941 4151 4152 4137 4136; 4942 4152 4153 4138 4137;
    4943 4153 4154 4139 4138; 4944 4154 4155 4140 4139; 4945 4155 4156 4141 4140;
    4946 4156 3662 3663 4141; 4947 3943 4157 4142 3942; 4948 4157 4158 4143 4142;
    4949 4158 4159 4144 4143; 4950 4159 4160 4145 4144; 4951 4160 4161 4146 4145;
    4952 4161 4162 4147 4146; 4953 4162 4163 4148 4147; 4954 4163 4164 4149 4148;
    4955 4164 4165 4150 4149; 4956 4165 4166 4151 4150; 4957 4166 4167 4152 4151;
    4958 4167 4168 4153 4152; 4959 4168 4169 4154 4153; 4960 4169 4170 4155 4154;
    4961 4170 4171 4156 4155; 4962 4171 3661 3662 4156; 4963 3944 4172 4157 3943;
    4964 4172 4173 4158 4157; 4965 4173 4174 4159 4158; 4966 4174 4175 4160 4159;
    4967 4175 4176 4161 4160; 4968 4176 4177 4162 4161; 4969 4177 4178 4163 4162;
    4970 4178 4179 4164 4163; 4971 4179 4180 4165 4164; 4972 4180 4181 4166 4165;
    4973 4181 4182 4167 4166; 4974 4182 4183 4168 4167; 4975 4183 4184 4169 4168;
    4976 4184 4185 4170 4169; 4977 4185 4186 4171 4170; 4978 4186 3660 3661 4171;
    4979 3945 4187 4172 3944; 4980 4187 4188 4173 4172; 4981 4188 4189 4174 4173;
    4982 4189 4190 4175 4174; 4983 4190 4191 4176 4175; 4984 4191 4192 4177 4176;
    4985 4192 4193 4178 4177; 4986 4193 4194 4179 4178; 4987 4194 4195 4180 4179;
    4988 4195 4196 4181 4180; 4989 4196 4197 4182 4181; 4990 4197 4198 4183 4182;
    4991 4198 4199 4184 4183; 4992 4199 4200 4185 4184; 4993 4200 4201 4186 4185;
    4994 4201 3659 3660 4186; 4995 3946 4202 4187 3945; 4996 4202 4203 4188 4187;
    4997 4203 4204 4189 4188; 4998 4204 4205 4190 4189; 4999 4205 4206 4191 4190;
    5000 4206 4207 4192 4191; 5001 4207 4208 4193 4192; 5002 4208 4209 4194 4193;
    5003 4209 4210 4195 4194; 5004 4210 4211 4196 4195; 5005 4211 4212 4197 4196;
    5006 4212 4213 4198 4197; 5007 4213 4214 4199 4198; 5008 4214 4215 4200 4199;
    5009 4215 4216 4201 4200; 5010 4216 3658 3659 4201; 5011 384 3947 4202 3946;
    5012 3947 3948 4203 4202; 5013 3948 3949 4204 4203; 5014 3949 3950 4205 4204;
    5015 3950 3951 4206 4205; 5016 3951 3952 4207 4206; 5017 3952 3953 4208 4207;
    5018 3953 3954 4209 4208; 5019 3954 3955 4210 4209; 5020 3955 3956 4211 4210;
    5021 3956 3957 4212 4211; 5022 3957 3958 4213 4212; 5023 3958 3959 4214 4213;
    5024 3959 3960 4215 4214; 5025 3960 3961 4216 4215; 5026 3961 378 3658 4216;
    5066 4555 4345 4485 4362; 5067 4516 4391 4426 4267; 5068 4349 4384 4476 4394;
    5069 4471 4469 4302 4339; 5070 4294 4251 4252 4278; 5071 4555 4474 4572 4345;
    5072 134 4279 4399 3251; 5073 4355 4365 4274 4393; 5074 4433 4442 4421 4284;
    5075 4547 4357 4353 4438; 5076 4375 4278 4252 4295; 5077 4345 4572 4527 4504;
    5078 4456 4250 4251 4294; 5079 4554 4441 4424 4529; 5080 4524 4548 4248 4437;
    5081 4458 4472 4517 4492; 5082 4304 4322 4321 4310; 5083 4494 4465 4462 4546;
    5084 4293 4590 3263 3262; 5085 4438 4353 4306 4384; 5086 4267 4426 4553 4445;
    5087 4420 4506 4413 4587; 5088 4358 4366 4551 4368; 5089 4407 4369 4262 4446;
    5090 4531 4458 4492 4487; 5091 4295 4252 4253 4551; 5092 4460 4570 4583 4571;
    5093 4430 4582 4417 4436; 5094 4533 4300 4411 4560; 5095 4393 4416 4425 4388;
    5096 4411 4576 4256 4557; 5097 4256 4518 4595 4465; 5098 4346 4359 4535 4466;
    5099 4493 4337 4343 4459; 5100 4219 4220 4265 4261; 5101 4311 4249 4250 4456;
    5102 4383 4234 4235 4303; 5103 4341 4400 4463 4389; 5104 4374 4236 4237 4305;
    5105 4497 4451 4344 4488; 5106 4441 4294 4278 4424; 5107 4347 4577 4419 4364;
    5108 4452 4346 4466 4301; 5109 4434 4409 4335 4558; 5110 4324 4285 4502 4337;
    5111 4229 4230 4314 4299; 5112 4273 4545 4591 4589; 5113 4329 4486 4523 4280;
    5114 4491 4452 4301 4477; 5115 4594 4423 4534 4578; 5116 4448 4543 4582 4430;
    5117 4264 4327 3255 3254; 5118 4292 4291 4496 4474; 5119 4493 4459 4398 4530;
    5120 4386 4491 4477 4457; 5121 4529 4424 4556 4357; 5122 4332 4526 4594 4578;
    5123 4450 4323 4464 4291; 5124 4589 4591 4283 4461; 5125 4597 4308 4440 4521;
    5126 4221 4222 4271 4263; 5127 4479 4433 4284 4351; 5128 4345 4504 4584 4485;
    5129 4230 291 4270 4314; 5130 291 373 4290 4270; 5131 4429 4540 4452 4491;
    5132 4330 4595 4542 4490; 5133 4530 4398 4597 4564; 5134 4217 4503 4279 134;
    5135 4356 4495 4379 4390; 5136 4305 4237 4238 4373; 5137 4226 4227 4420 4320;
    5138 4429 4406 4319 4540; 5139 4587 4413 4495 4297; 5140 4592 4563 4453 4272;
    5141 4540 4319 4346 4452; 5142 4509 4244 4245 4354; 5143 4222 4223 4363 4271;
    5144 4324 4337 4493 4470; 5145 4384 4306 4458 4531; 5146 4506 4268 4289 4413;
    5147 4320 4420 4587 4378; 5148 4549 4372 4276 4576; 5149 4453 4563 4449 4519;
    5150 4466 4535 4258 4510; 5151 4220 4221 4263 4265; 5152 4568 4364 4479 4422;
    5153 4523 4447 4538 4498; 5154 4412 4350 4567 4515; 5155 4303 4235 4236 4374;
    5156 4301 4466 4510 4260; 5157 4315 4468 4532 4400; 5158 4426 4287 4566 4553;
    5159 4228 4229 4299 4506; 5160 4581 4418 4369 4407; 5161 4325 4338 4318 4402;
    5162 4342 4281 4543 4448; 5163 4510 4258 4475 4444; 5164 4351 4284 3258 3257;
    5165 4318 4508 4516 4395; 5166 4343 4467 4273 4459; 5167 4437 4248 4249 4311;
    5168 4539 4311 4456 4536; 5169 4298 4434 4558 4431; 5170 4584 4526 4332 4513;
    5171 4257 4553 4298 4431; 5172 4279 4500 4327 4399; 5173 4476 4384 4531 4336;
    5174 4372 4512 4520 4276; 5175 4505 4326 4511 4515; 5176 4596 4302 4383 4512;
    5177 4333 4393 4388 4321; 5178 4534 4381 4311 4539; 5179 4263 4271 4415 4334;
    5180 4399 4327 4264 4266; 5181 4499 4267 4445 4376; 5182 4498 4538 4292 4277;
    5183 4576 4580 4518 4256; 5184 4265 4263 4334 4328; 5185 4566 4554 4529 4544;
    5186 4357 4556 4358 4353; 5187 4287 4552 4554 4566; 5188 4271 4363 4489 4415;
    5189 4562 4365 4355 4481; 5190 4545 4431 4541 4591; 5191 4501 4254 4255 4262;
    5192 4328 4334 4415 4410; 5193 4261 4265 4328 4329; 5194 4522 4530 4564 4480;
    5195 4300 4549 4576 4411; 5196 4473 4356 4390 4414; 5197 4338 4513 4508 4318;
    5198 4597 4589 4461 4308; 5199 4344 4242 4243 4275; 5200 4565 4340 4331 4454;
    5201 4423 4524 4381 4534; 5202 4328 4410 4486 4329; 5203 4364 4419 4433 4479;
    5204 4313 4507 4478 4326; 5205 4313 4473 4414 4507; 5206 4563 4460 4571 4449;
    5207 4268 4309 4397 4289; 5208 4409 4438 4384 4349; 5209 4538 4573 4385 4292;
    5210 4336 4531 4487 4537; 5211 4413 4269 4296 4495; 5212 4546 4462 4323 4450;
    5213 4310 4315 4400 4341; 5214 4442 4522 4480 4421; 5215 4484 4565 4454 4514;
    5216 4512 4383 4303 4520; 5217 4390 4379 4304 4317; 5218 4316 4429 4491 4386;
    5219 4488 4344 4275 4496; 5220 4445 4553 4257 4396; 5221 4402 4318 4395 4285;
    5222 4541 4342 4448 4435; 5223 4424 4278 4375 4556; 5224 4467 4396 4545 4273;
    5225 4291 4464 4488 4496; 5226 4595 4239 4240 4542; 5227 4459 4273 4589 4398;
    5228 4385 4450 4291 4292; 5229 4281 4476 4336 4404; 5230 4465 4595 4330 4462;
    5231 4376 4445 4396 4467; 5232 4306 4368 4472 4458; 5233 4514 4347 4364 4568;
    5234 4285 4395 4499 4502; 5235 4558 4335 4394 4342; 5236 4361 4501 4262 4369;
    5237 4557 4256 4465 4494; 5238 4270 4290 4588 4406; 5239 4421 4521 3260 3259;
    5240 4436 4432 4585 4569; 5241 4275 4243 4244 4509; 5242 4434 4547 4438 4409;
    5243 4435 4448 4430 4575; 5244 4556 4375 4366 4358; 5245 4564 4597 4521 4480;
    5246 4298 4544 4547 4434; 5247 4227 4228 4506 4420; 5248 4284 4421 3259 3258;
    5249 4359 4593 4528 4535; 5250 4317 4341 4389 4483; 5251 4422 4351 3257 3256;
    5252 4508 4586 4391 4516; 5253 4288 4546 4450 4385; 5254 4277 4555 4362 4380;
    5255 4387 4374 4305 4580; 5256 4474 4496 4354 4572; 5257 4496 4275 4509 4354;
    5258 4551 4253 4254 4501; 5259 4323 4497 4488 4464; 5260 4352 4361 4369 4418;
    5261 4500 4568 4422 4327; 5262 4373 4238 4239 4595; 5263 4570 4510 4444 4583;
    5264 4591 4541 4435 4283; 5265 4586 4539 4536 4391; 5266 4410 4415 4412 4486;
    5267 4331 4402 4285 4324; 5268 4503 4484 4500 4279; 5269 4580 4305 4373 4518;
    5270 4414 4390 4317 4483; 5271 4370 4260 4510 4570; 5272 4447 4371 4573 4538;
    5273 4519 4559 4561 4427; 5274 4330 4490 4497 4323; 5275 4553 4566 4544 4298;
    5276 4578 4534 4539 4586; 5277 4490 4542 4451 4497; 5278 4368 4551 4501 4472;
    5279 4286 4288 4385 4573; 5280 4444 4475 4596 4408; 5281 4367 4411 4557 4532;
    5282 4577 4530 4522 4419; 5283 4419 4522 4442 4433; 5284 4475 4339 4302 4596;
    5285 4391 4536 4456 4552; 5286 4485 4584 4513 4338; 5287 4521 4440 3261 3260;
    5288 4297 4495 4356 4473; 5289 4426 4391 4552 4287; 5290 4468 4425 4367 4532;
    5291 4502 4499 4376 4337; 5292 4454 4331 4324 4470; 5293 4314 4316 4386 4309;
    5294 4528 4439 4469 4471; 5295 4224 4225 4378 4363; 5296 4525 4313 4326 4505;
    5297 4415 4489 4350 4412; 5298 4432 4407 270 4585; 5299 4454 4470 4577 4347;
    5300 4258 4471 4339 4475; 5301 4524 4437 4311 4381; 5302 4470 4493 4530 4577;
    5303 4503 4405 4565 4484; 5304 4283 4435 4579 4461; 5305 4487 4492 4352 4377;
    5306 4397 4457 4307 4550; 5307 4308 4461 4293 4440; 5308 4363 4378 4587 4489;
    5309 4337 4376 4467 4343; 5310 4389 4463 4312 4282; 5311 4354 4245 4246 4428;
    5312 4396 4257 4431 4545; 5313 4262 4255 372 4446; 5314 4484 4514 4568 4500;
    5315 4504 4527 4526 4584; 5316 4319 4593 4359 4346; 5317 4526 4259 4360 4594;
    5318 4561 4482 4533 4455; 5319 4455 4533 4560 4416; 5320 4379 4348 4322 4304;
    5321 4486 4412 4515 4523; 5322 4380 4362 4325 4340; 5323 4371 4282 4286 4573;
    5324 4400 4532 4392 4463; 5325 4562 4453 4519 4365; 5326 4321 4388 4315 4310;
    5327 4583 4444 4408 4574; 5328 4388 4425 4468 4315; 5329 4407 4446 372 270;
    5330 4535 4528 4471 4258; 5331 4394 4476 4281 4342; 5332 4463 4392 4494 4546;
    5333 4590 4585 270 3263; 5334 4489 4587 4297 4350; 5335 4408 4596 4372 4549;
    5336 4277 4292 4474 4555; 5337 4457 4260 4370 4307; 5338 4395 4516 4267 4499;
    5339 4266 4264 3253 3252; 5340 4290 373 4231 4588; 5341 4340 4325 4402 4331;
    5342 4588 4231 4232 4439; 5343 4481 4355 4393 4333; 5344 4593 4588 4439 4528;
    5345 4431 4558 4342 4541; 5346 4281 4404 4403 4543; 5347 4544 4529 4357 4547;
    5348 4498 4277 4380 4405; 5349 4299 4314 4309 4268; 5350 4582 4403 4401 4417;
    5351 4507 4414 4483 4478; 5352 4296 4269 4562 4481; 5353 4375 4295 4551 4366;
    5354 4525 4297 4473 4313; 5355 4417 4401 4581 4432; 5356 4572 4354 4428 4527;
    5357 4296 4481 4322 4348; 5358 4397 4550 4563 4592; 5359 4350 4297 4525 4567;
    5360 4478 4483 4371 4447; 5361 4451 4241 4242 4344; 5362 4495 4296 4348 4379;
    5363 3251 4399 4266 3252; 5364 4428 4246 4247 4443; 5365 4427 4561 4455 4274;
    5366 4217 4498 4405 4503; 5367 4440 4293 3262 3261; 5368 169 4218 4329 4280;
    5369 4322 4481 4333 4321; 5370 4483 4389 4282 4371; 5371 4405 4380 4340 4565;
    5372 4552 4456 4441 4554; 5373 4362 4485 4338 4325; 5374 4550 4307 4460 4563;
    5375 4567 4525 4505 4515; 5376 4309 4386 4457 4397; 5377 4259 4443 4548 4360;
    5378 4393 4274 4455 4416; 5379 4559 4574 4482 4561; 5380 4532 4557 4494 4392;
    5381 4511 4326 4478 4447; 5382 4439 4232 4233 4469; 5383 4404 4336 4537 4403;
    5384 4517 4472 4501 4361; 5385 4515 4511 4447 4523; 5386 4327 4422 3256 3255;
    5387 4276 4520 4374 4387; 5388 4353 4358 4368 4306; 5389 4492 4517 4361 4352;
    5390 4574 4408 4549 4482; 5391 4449 4571 4559 4519; 5392 4579 4569 4585 4590;
    5393 4365 4519 4427 4274; 5394 4482 4549 4300 4533; 5395 4425 4416 4560 4367;
    5396 4218 4219 4261 4329; 5397 4269 4272 4453 4562; 5398 4360 4548 4524 4423;
    5399 4435 4575 4569 4579; 5400 4469 4233 4234 4302; 5401 4335 4409 4349 4394;
    5402 4270 4406 4429 4316; 5403 4527 4428 4259 4526; 5404 4537 4487 4377 4382;
    5405 4307 4370 4570 4460; 5406 4403 4537 4382 4401; 5407 4542 4240 4241 4451;
    5408 4225 4226 4320 4378; 5409 4282 4312 4288 4286; 5410 4276 4387 4580 4576;
    5411 4571 4583 4574 4559; 5412 4575 4430 4436 4569; 5413 4443 4247 4248 4548;
    5414 4312 4463 4546 4288; 5415 4304 4310 4341 4317; 5416 4280 4523 4498 4217;
    5417 4332 4578 4586 4508; 5418 4289 4592 4272 4269; 5419 4382 4377 4352 4418;
    5420 4477 4301 4260 4457; 5421 4406 4588 4593 4319; 5422 4401 4382 4418 4581;
    5423 4461 4579 4590 4293; 5424 4518 4373 4595; 5425 4436 4417 4432;
    5426 4456 4294 4441; 5427 3253 4264 3254; 5428 4314 4270 4316;
    5429 4543 4403 4582; 5430 4398 4589 4597; 5431 4513 4332 4508;
    5432 4506 4299 4268; 5433 4432 4581 4407; 5434 4480 4521 4421;
    5435 4462 4330 4323; 5436 4367 4560 4411; 5437 4514 4454 4347;
    5438 4413 4289 4269; 5439 4594 4360 4423; 5440 4428 4443 4259;
    5441 4289 4397 4592; 5442 4422 4479 4351; 5443 169 4280 4217;
    5444 4372 4596 4512; 5445 4520 4303 4374; 5446 4223 4224 4363;
    5447 4302 4234 4383; 5488 4255 4638 3643 372; 5489 4638 4639 3644 3643;
    5490 4639 4640 3645 3644; 5491 4640 4641 3646 3645; 5492 4641 4642 3647 3646;
    5493 4642 4643 3648 3647; 5494 4643 4644 3649 3648; 5495 4644 4645 3650 3649;
    5496 4645 4646 3651 3650; 5497 4646 4647 3652 3651; 5498 4647 4648 3653 3652;
    5499 4648 4649 3654 3653; 5500 4649 4650 3655 3654; 5501 4650 4651 3656 3655;
    5502 4651 4652 3657 3656; 5503 4652 4637 378 3657; 5504 4254 4653 4638 4255;
    5505 4653 4654 4639 4638; 5506 4654 4655 4640 4639; 5507 4655 4656 4641 4640;
    5508 4656 4657 4642 4641; 5509 4657 4658 4643 4642; 5510 4658 4659 4644 4643;
    5511 4659 4660 4645 4644; 5512 4660 4661 4646 4645; 5513 4661 4662 4647 4646;
    5514 4662 4663 4648 4647; 5515 4663 4664 4649 4648; 5516 4664 4665 4650 4649;
    5517 4665 4666 4651 4650; 5518 4666 4667 4652 4651; 5519 4667 4636 4637 4652;
    5520 4253 4668 4653 4254; 5521 4668 4669 4654 4653; 5522 4669 4670 4655 4654;
    5523 4670 4671 4656 4655; 5524 4671 4672 4657 4656; 5525 4672 4673 4658 4657;
    5526 4673 4674 4659 4658; 5527 4674 4675 4660 4659; 5528 4675 4676 4661 4660;
    5529 4676 4677 4662 4661; 5530 4677 4678 4663 4662; 5531 4678 4679 4664 4663;
    5532 4679 4680 4665 4664; 5533 4680 4681 4666 4665; 5534 4681 4682 4667 4666;
    5535 4682 4635 4636 4667; 5536 4252 4683 4668 4253; 5537 4683 4684 4669 4668;
    5538 4684 4685 4670 4669; 5539 4685 4686 4671 4670; 5540 4686 4687 4672 4671;
    5541 4687 4688 4673 4672; 5542 4688 4689 4674 4673; 5543 4689 4690 4675 4674;
    5544 4690 4691 4676 4675; 5545 4691 4692 4677 4676; 5546 4692 4693 4678 4677;
    5547 4693 4694 4679 4678; 5548 4694 4695 4680 4679; 5549 4695 4696 4681 4680;
    5550 4696 4697 4682 4681; 5551 4697 4634 4635 4682; 5552 4251 4698 4683 4252;
    5553 4698 4699 4684 4683; 5554 4699 4700 4685 4684; 5555 4700 4701 4686 4685;
    5556 4701 4702 4687 4686; 5557 4702 4703 4688 4687; 5558 4703 4704 4689 4688;
    5559 4704 4705 4690 4689; 5560 4705 4706 4691 4690; 5561 4706 4707 4692 4691;
    5562 4707 4708 4693 4692; 5563 4708 4709 4694 4693; 5564 4709 4710 4695 4694;
    5565 4710 4711 4696 4695; 5566 4711 4712 4697 4696; 5567 4712 4633 4634 4697;
    5568 4250 4713 4698 4251; 5569 4713 4714 4699 4698; 5570 4714 4715 4700 4699;
    5571 4715 4716 4701 4700; 5572 4716 4717 4702 4701; 5573 4717 4718 4703 4702;
    5574 4718 4719 4704 4703; 5575 4719 4720 4705 4704; 5576 4720 4721 4706 4705;
    5577 4721 4722 4707 4706; 5578 4722 4723 4708 4707; 5579 4723 4724 4709 4708;
    5580 4724 4725 4710 4709; 5581 4725 4726 4711 4710; 5582 4726 4727 4712 4711;
    5583 4727 4632 4633 4712; 5584 4249 4728 4713 4250; 5585 4728 4729 4714 4713;
    5586 4729 4730 4715 4714; 5587 4730 4731 4716 4715; 5588 4731 4732 4717 4716;
    5589 4732 4733 4718 4717; 5590 4733 4734 4719 4718; 5591 4734 4735 4720 4719;
    5592 4735 4736 4721 4720; 5593 4736 4737 4722 4721; 5594 4737 4738 4723 4722;
    5595 4738 4739 4724 4723; 5596 4739 4740 4725 4724; 5597 4740 4741 4726 4725;
    5598 4741 4742 4727 4726; 5599 4742 4631 4632 4727; 5600 4248 4743 4728 4249;
    5601 4743 4744 4729 4728; 5602 4744 4745 4730 4729; 5603 4745 4746 4731 4730;
    5604 4746 4747 4732 4731; 5605 4747 4748 4733 4732; 5606 4748 4749 4734 4733;
    5607 4749 4750 4735 4734; 5608 4750 4751 4736 4735; 5609 4751 4752 4737 4736;
    5610 4752 4753 4738 4737; 5611 4753 4754 4739 4738; 5612 4754 4755 4740 4739;
    5613 4755 4756 4741 4740; 5614 4756 4757 4742 4741; 5615 4757 4630 4631 4742;
    5616 4247 4758 4743 4248; 5617 4758 4759 4744 4743; 5618 4759 4760 4745 4744;
    5619 4760 4761 4746 4745; 5620 4761 4762 4747 4746; 5621 4762 4763 4748 4747;
    5622 4763 4764 4749 4748; 5623 4764 4765 4750 4749; 5624 4765 4766 4751 4750;
    5625 4766 4767 4752 4751; 5626 4767 4768 4753 4752; 5627 4768 4769 4754 4753;
    5628 4769 4770 4755 4754; 5629 4770 4771 4756 4755; 5630 4771 4772 4757 4756;
    5631 4772 4629 4630 4757; 5632 4246 4773 4758 4247; 5633 4773 4774 4759 4758;
    5634 4774 4775 4760 4759; 5635 4775 4776 4761 4760; 5636 4776 4777 4762 4761;
    5637 4777 4778 4763 4762; 5638 4778 4779 4764 4763; 5639 4779 4780 4765 4764;
    5640 4780 4781 4766 4765; 5641 4781 4782 4767 4766; 5642 4782 4783 4768 4767;
    5643 4783 4784 4769 4768; 5644 4784 4785 4770 4769; 5645 4785 4786 4771 4770;
    5646 4786 4787 4772 4771; 5647 4787 4628 4629 4772; 5648 4245 4788 4773 4246;
    5649 4788 4789 4774 4773; 5650 4789 4790 4775 4774; 5651 4790 4791 4776 4775;
    5652 4791 4792 4777 4776; 5653 4792 4793 4778 4777; 5654 4793 4794 4779 4778;
    5655 4794 4795 4780 4779; 5656 4795 4796 4781 4780; 5657 4796 4797 4782 4781;
    5658 4797 4798 4783 4782; 5659 4798 4799 4784 4783; 5660 4799 4800 4785 4784;
    5661 4800 4801 4786 4785; 5662 4801 4802 4787 4786; 5663 4802 4627 4628 4787;
    5664 4244 4803 4788 4245; 5665 4803 4804 4789 4788; 5666 4804 4805 4790 4789;
    5667 4805 4806 4791 4790; 5668 4806 4807 4792 4791; 5669 4807 4808 4793 4792;
    5670 4808 4809 4794 4793; 5671 4809 4810 4795 4794; 5672 4810 4811 4796 4795;
    5673 4811 4812 4797 4796; 5674 4812 4813 4798 4797; 5675 4813 4814 4799 4798;
    5676 4814 4815 4800 4799; 5677 4815 4816 4801 4800; 5678 4816 4817 4802 4801;
    5679 4817 4626 4627 4802; 5680 4243 4818 4803 4244; 5681 4818 4819 4804 4803;
    5682 4819 4820 4805 4804; 5683 4820 4821 4806 4805; 5684 4821 4822 4807 4806;
    5685 4822 4823 4808 4807; 5686 4823 4824 4809 4808; 5687 4824 4825 4810 4809;
    5688 4825 4826 4811 4810; 5689 4826 4827 4812 4811; 5690 4827 4828 4813 4812;
    5691 4828 4829 4814 4813; 5692 4829 4830 4815 4814; 5693 4830 4831 4816 4815;
    5694 4831 4832 4817 4816; 5695 4832 4625 4626 4817; 5696 4242 4833 4818 4243;
    5697 4833 4834 4819 4818; 5698 4834 4835 4820 4819; 5699 4835 4836 4821 4820;
    5700 4836 4837 4822 4821; 5701 4837 4838 4823 4822; 5702 4838 4839 4824 4823;
    5703 4839 4840 4825 4824; 5704 4840 4841 4826 4825; 5705 4841 4842 4827 4826;
    5706 4842 4843 4828 4827; 5707 4843 4844 4829 4828; 5708 4844 4845 4830 4829;
    5709 4845 4846 4831 4830; 5710 4846 4847 4832 4831; 5711 4847 4624 4625 4832;
    5712 4241 4848 4833 4242; 5713 4848 4849 4834 4833; 5714 4849 4850 4835 4834;
    5715 4850 4851 4836 4835; 5716 4851 4852 4837 4836; 5717 4852 4853 4838 4837;
    5718 4853 4854 4839 4838; 5719 4854 4855 4840 4839; 5720 4855 4856 4841 4840;
    5721 4856 4857 4842 4841; 5722 4857 4858 4843 4842; 5723 4858 4859 4844 4843;
    5724 4859 4860 4845 4844; 5725 4860 4861 4846 4845; 5726 4861 4862 4847 4846;
    5727 4862 4623 4624 4847; 5728 4240 4863 4848 4241; 5729 4863 4864 4849 4848;
    5730 4864 4865 4850 4849; 5731 4865 4866 4851 4850; 5732 4866 4867 4852 4851;
    5733 4867 4868 4853 4852; 5734 4868 4869 4854 4853; 5735 4869 4870 4855 4854;
    5736 4870 4871 4856 4855; 5737 4871 4872 4857 4856; 5738 4872 4873 4858 4857;
    5739 4873 4874 4859 4858; 5740 4874 4875 4860 4859; 5741 4875 4876 4861 4860;
    5742 4876 4877 4862 4861; 5743 4877 4622 4623 4862; 5744 4239 4878 4863 4240;
    5745 4878 4879 4864 4863; 5746 4879 4880 4865 4864; 5747 4880 4881 4866 4865;
    5748 4881 4882 4867 4866; 5749 4882 4883 4868 4867; 5750 4883 4884 4869 4868;
    5751 4884 4885 4870 4869; 5752 4885 4886 4871 4870; 5753 4886 4887 4872 4871;
    5754 4887 4888 4873 4872; 5755 4888 4889 4874 4873; 5756 4889 4890 4875 4874;
    5757 4890 4891 4876 4875; 5758 4891 4892 4877 4876; 5759 4892 4621 4622 4877;
    5760 4238 4893 4878 4239; 5761 4893 4894 4879 4878; 5762 4894 4895 4880 4879;
    5763 4895 4896 4881 4880; 5764 4896 4897 4882 4881; 5765 4897 4898 4883 4882;
    5766 4898 4899 4884 4883; 5767 4899 4900 4885 4884; 5768 4900 4901 4886 4885;
    5769 4901 4902 4887 4886; 5770 4902 4903 4888 4887; 5771 4903 4904 4889 4888;
    5772 4904 4905 4890 4889; 5773 4905 4906 4891 4890; 5774 4906 4907 4892 4891;
    5775 4907 4620 4621 4892; 5776 4237 4908 4893 4238; 5777 4908 4909 4894 4893;
    5778 4909 4910 4895 4894; 5779 4910 4911 4896 4895; 5780 4911 4912 4897 4896;
    5781 4912 4913 4898 4897; 5782 4913 4914 4899 4898; 5783 4914 4915 4900 4899;
    5784 4915 4916 4901 4900; 5785 4916 4917 4902 4901; 5786 4917 4918 4903 4902;
    5787 4918 4919 4904 4903; 5788 4919 4920 4905 4904; 5789 4920 4921 4906 4905;
    5790 4921 4922 4907 4906; 5791 4922 4619 4620 4907; 5792 4236 4923 4908 4237;
    5793 4923 4924 4909 4908; 5794 4924 4925 4910 4909; 5795 4925 4926 4911 4910;
    5796 4926 4927 4912 4911; 5797 4927 4928 4913 4912; 5798 4928 4929 4914 4913;
    5799 4929 4930 4915 4914; 5800 4930 4931 4916 4915; 5801 4931 4932 4917 4916;
    5802 4932 4933 4918 4917; 5803 4933 4934 4919 4918; 5804 4934 4935 4920 4919;
    5805 4935 4936 4921 4920; 5806 4936 4937 4922 4921; 5807 4937 4618 4619 4922;
    5808 4235 4938 4923 4236; 5809 4938 4939 4924 4923; 5810 4939 4940 4925 4924;
    5811 4940 4941 4926 4925; 5812 4941 4942 4927 4926; 5813 4942 4943 4928 4927;
    5814 4943 4944 4929 4928; 5815 4944 4945 4930 4929; 5816 4945 4946 4931 4930;
    5817 4946 4947 4932 4931; 5818 4947 4948 4933 4932; 5819 4948 4949 4934 4933;
    5820 4949 4950 4935 4934; 5821 4950 4951 4936 4935; 5822 4951 4952 4937 4936;
    5823 4952 4617 4618 4937; 5824 4234 4953 4938 4235; 5825 4953 4954 4939 4938;
    5826 4954 4955 4940 4939; 5827 4955 4956 4941 4940; 5828 4956 4957 4942 4941;
    5829 4957 4958 4943 4942; 5830 4958 4959 4944 4943; 5831 4959 4960 4945 4944;
    5832 4960 4961 4946 4945; 5833 4961 4962 4947 4946; 5834 4962 4963 4948 4947;
    5835 4963 4964 4949 4948; 5836 4964 4965 4950 4949; 5837 4965 4966 4951 4950;
    5838 4966 4967 4952 4951; 5839 4967 4616 4617 4952; 5840 4233 4968 4953 4234;
    5841 4968 4969 4954 4953; 5842 4969 4970 4955 4954; 5843 4970 4971 4956 4955;
    5844 4971 4972 4957 4956; 5845 4972 4973 4958 4957; 5846 4973 4974 4959 4958;
    5847 4974 4975 4960 4959; 5848 4975 4976 4961 4960; 5849 4976 4977 4962 4961;
    5850 4977 4978 4963 4962; 5851 4978 4979 4964 4963; 5852 4979 4980 4965 4964;
    5853 4980 4981 4966 4965; 5854 4981 4982 4967 4966; 5855 4982 4615 4616 4967;
    5856 4232 4983 4968 4233; 5857 4983 4984 4969 4968; 5858 4984 4985 4970 4969;
    5859 4985 4986 4971 4970; 5860 4986 4987 4972 4971; 5861 4987 4988 4973 4972;
    5862 4988 4989 4974 4973; 5863 4989 4990 4975 4974; 5864 4990 4991 4976 4975;
    5865 4991 4992 4977 4976; 5866 4992 4993 4978 4977; 5867 4993 4994 4979 4978;
    5868 4994 4995 4980 4979; 5869 4995 4996 4981 4980; 5870 4996 4997 4982 4981;
    5871 4997 4614 4615 4982; 5872 4231 4998 4983 4232; 5873 4998 4999 4984 4983;
    5874 4999 5000 4985 4984; 5875 5000 5001 4986 4985; 5876 5001 5002 4987 4986;
    5877 5002 5003 4988 4987; 5878 5003 5004 4989 4988; 5879 5004 5005 4990 4989;
    5880 5005 5006 4991 4990; 5881 5006 5007 4992 4991; 5882 5007 5008 4993 4992;
    5883 5008 5009 4994 4993; 5884 5009 5010 4995 4994; 5885 5010 5011 4996 4995;
    5886 5011 5012 4997 4996; 5887 5012 4613 4614 4997; 5888 373 4598 4998 4231;
    5889 4598 4599 4999 4998; 5890 4599 4600 5000 4999; 5891 4600 4601 5001 5000;
    5892 4601 4602 5002 5001; 5893 4602 4603 5003 5002; 5894 4603 4604 5004 5003;
    5895 4604 4605 5005 5004; 5896 4605 4606 5006 5005; 5897 4606 4607 5007 5006;
    5898 4607 4608 5008 5007; 5899 4608 4609 5009 5008; 5900 4609 4610 5010 5009;
    5901 4610 4611 5011 5010; 5902 4611 4612 5012 5011; 5903 4612 379 4613 5012;
    5944 5013 5053 3947 384; 5945 5053 5054 3948 3947; 5946 5054 5055 3949 3948;
    5947 5055 5056 3950 3949; 5948 5056 5057 3951 3950; 5949 5057 5058 3952 3951;
    5950 5058 5059 3953 3952; 5951 5059 5060 3954 3953; 5952 5060 5061 3955 3954;
    5953 5061 5062 3956 3955; 5954 5062 5063 3957 3956; 5955 5063 5064 3958 3957;
    5956 5064 5065 3959 3958; 5957 5065 5066 3960 3959; 5958 5066 5067 3961 3960;
    5959 5067 4637 378 3961; 5960 5014 5068 5053 5013; 5961 5068 5069 5054 5053;
    5962 5069 5070 5055 5054; 5963 5070 5071 5056 5055; 5964 5071 5072 5057 5056;
    5965 5072 5073 5058 5057; 5966 5073 5074 5059 5058; 5967 5074 5075 5060 5059;
    5968 5075 5076 5061 5060; 5969 5076 5077 5062 5061; 5970 5077 5078 5063 5062;
    5971 5078 5079 5064 5063; 5972 5079 5080 5065 5064; 5973 5080 5081 5066 5065;
    5974 5081 5082 5067 5066; 5975 5082 4636 4637 5067; 5976 5015 5083 5068 5014;
    5977 5083 5084 5069 5068; 5978 5084 5085 5070 5069; 5979 5085 5086 5071 5070;
    5980 5086 5087 5072 5071; 5981 5087 5088 5073 5072; 5982 5088 5089 5074 5073;
    5983 5089 5090 5075 5074; 5984 5090 5091 5076 5075; 5985 5091 5092 5077 5076;
    5986 5092 5093 5078 5077; 5987 5093 5094 5079 5078; 5988 5094 5095 5080 5079;
    5989 5095 5096 5081 5080; 5990 5096 5097 5082 5081; 5991 5097 4635 4636 5082;
    5992 5016 5098 5083 5015; 5993 5098 5099 5084 5083; 5994 5099 5100 5085 5084;
    5995 5100 5101 5086 5085; 5996 5101 5102 5087 5086; 5997 5102 5103 5088 5087;
    5998 5103 5104 5089 5088; 5999 5104 5105 5090 5089; 6000 5105 5106 5091 5090;
    6001 5106 5107 5092 5091; 6002 5107 5108 5093 5092; 6003 5108 5109 5094 5093;
    6004 5109 5110 5095 5094; 6005 5110 5111 5096 5095; 6006 5111 5112 5097 5096;
    6007 5112 4634 4635 5097; 6008 5017 5113 5098 5016; 6009 5113 5114 5099 5098;
    6010 5114 5115 5100 5099; 6011 5115 5116 5101 5100; 6012 5116 5117 5102 5101;
    6013 5117 5118 5103 5102; 6014 5118 5119 5104 5103; 6015 5119 5120 5105 5104;
    6016 5120 5121 5106 5105; 6017 5121 5122 5107 5106; 6018 5122 5123 5108 5107;
    6019 5123 5124 5109 5108; 6020 5124 5125 5110 5109; 6021 5125 5126 5111 5110;
    6022 5126 5127 5112 5111; 6023 5127 4633 4634 5112; 6024 5018 5128 5113 5017;
    6025 5128 5129 5114 5113; 6026 5129 5130 5115 5114; 6027 5130 5131 5116 5115;
    6028 5131 5132 5117 5116; 6029 5132 5133 5118 5117; 6030 5133 5134 5119 5118;
    6031 5134 5135 5120 5119; 6032 5135 5136 5121 5120; 6033 5136 5137 5122 5121;
    6034 5137 5138 5123 5122; 6035 5138 5139 5124 5123; 6036 5139 5140 5125 5124;
    6037 5140 5141 5126 5125; 6038 5141 5142 5127 5126; 6039 5142 4632 4633 5127;
    6040 5019 5143 5128 5018; 6041 5143 5144 5129 5128; 6042 5144 5145 5130 5129;
    6043 5145 5146 5131 5130; 6044 5146 5147 5132 5131; 6045 5147 5148 5133 5132;
    6046 5148 5149 5134 5133; 6047 5149 5150 5135 5134; 6048 5150 5151 5136 5135;
    6049 5151 5152 5137 5136; 6050 5152 5153 5138 5137; 6051 5153 5154 5139 5138;
    6052 5154 5155 5140 5139; 6053 5155 5156 5141 5140; 6054 5156 5157 5142 5141;
    6055 5157 4631 4632 5142; 6056 5020 5158 5143 5019; 6057 5158 5159 5144 5143;
    6058 5159 5160 5145 5144; 6059 5160 5161 5146 5145; 6060 5161 5162 5147 5146;
    6061 5162 5163 5148 5147; 6062 5163 5164 5149 5148; 6063 5164 5165 5150 5149;
    6064 5165 5166 5151 5150; 6065 5166 5167 5152 5151; 6066 5167 5168 5153 5152;
    6067 5168 5169 5154 5153; 6068 5169 5170 5155 5154; 6069 5170 5171 5156 5155;
    6070 5171 5172 5157 5156; 6071 5172 4630 4631 5157; 6072 5021 5173 5158 5020;
    6073 5173 5174 5159 5158; 6074 5174 5175 5160 5159; 6075 5175 5176 5161 5160;
    6076 5176 5177 5162 5161; 6077 5177 5178 5163 5162; 6078 5178 5179 5164 5163;
    6079 5179 5180 5165 5164; 6080 5180 5181 5166 5165; 6081 5181 5182 5167 5166;
    6082 5182 5183 5168 5167; 6083 5183 5184 5169 5168; 6084 5184 5185 5170 5169;
    6085 5185 5186 5171 5170; 6086 5186 5187 5172 5171; 6087 5187 4629 4630 5172;
    6088 5022 5188 5173 5021; 6089 5188 5189 5174 5173; 6090 5189 5190 5175 5174;
    6091 5190 5191 5176 5175; 6092 5191 5192 5177 5176; 6093 5192 5193 5178 5177;
    6094 5193 5194 5179 5178; 6095 5194 5195 5180 5179; 6096 5195 5196 5181 5180;
    6097 5196 5197 5182 5181; 6098 5197 5198 5183 5182; 6099 5198 5199 5184 5183;
    6100 5199 5200 5185 5184; 6101 5200 5201 5186 5185; 6102 5201 5202 5187 5186;
    6103 5202 4628 4629 5187; 6104 5023 5203 5188 5022; 6105 5203 5204 5189 5188;
    6106 5204 5205 5190 5189; 6107 5205 5206 5191 5190; 6108 5206 5207 5192 5191;
    6109 5207 5208 5193 5192; 6110 5208 5209 5194 5193; 6111 5209 5210 5195 5194;
    6112 5210 5211 5196 5195; 6113 5211 5212 5197 5196; 6114 5212 5213 5198 5197;
    6115 5213 5214 5199 5198; 6116 5214 5215 5200 5199; 6117 5215 5216 5201 5200;
    6118 5216 5217 5202 5201; 6119 5217 4627 4628 5202; 6120 5024 5218 5203 5023;
    6121 5218 5219 5204 5203; 6122 5219 5220 5205 5204; 6123 5220 5221 5206 5205;
    6124 5221 5222 5207 5206; 6125 5222 5223 5208 5207; 6126 5223 5224 5209 5208;
    6127 5224 5225 5210 5209; 6128 5225 5226 5211 5210; 6129 5226 5227 5212 5211;
    6130 5227 5228 5213 5212; 6131 5228 5229 5214 5213; 6132 5229 5230 5215 5214;
    6133 5230 5231 5216 5215; 6134 5231 5232 5217 5216; 6135 5232 4626 4627 5217;
    6136 5025 5233 5218 5024; 6137 5233 5234 5219 5218; 6138 5234 5235 5220 5219;
    6139 5235 5236 5221 5220; 6140 5236 5237 5222 5221; 6141 5237 5238 5223 5222;
    6142 5238 5239 5224 5223; 6143 5239 5240 5225 5224; 6144 5240 5241 5226 5225;
    6145 5241 5242 5227 5226; 6146 5242 5243 5228 5227; 6147 5243 5244 5229 5228;
    6148 5244 5245 5230 5229; 6149 5245 5246 5231 5230; 6150 5246 5247 5232 5231;
    6151 5247 4625 4626 5232; 6152 5026 5248 5233 5025; 6153 5248 5249 5234 5233;
    6154 5249 5250 5235 5234; 6155 5250 5251 5236 5235; 6156 5251 5252 5237 5236;
    6157 5252 5253 5238 5237; 6158 5253 5254 5239 5238; 6159 5254 5255 5240 5239;
    6160 5255 5256 5241 5240; 6161 5256 5257 5242 5241; 6162 5257 5258 5243 5242;
    6163 5258 5259 5244 5243; 6164 5259 5260 5245 5244; 6165 5260 5261 5246 5245;
    6166 5261 5262 5247 5246; 6167 5262 4624 4625 5247; 6168 5027 5263 5248 5026;
    6169 5263 5264 5249 5248; 6170 5264 5265 5250 5249; 6171 5265 5266 5251 5250;
    6172 5266 5267 5252 5251; 6173 5267 5268 5253 5252; 6174 5268 5269 5254 5253;
    6175 5269 5270 5255 5254; 6176 5270 5271 5256 5255; 6177 5271 5272 5257 5256;
    6178 5272 5273 5258 5257; 6179 5273 5274 5259 5258; 6180 5274 5275 5260 5259;
    6181 5275 5276 5261 5260; 6182 5276 5277 5262 5261; 6183 5277 4623 4624 5262;
    6184 5028 5278 5263 5027; 6185 5278 5279 5264 5263; 6186 5279 5280 5265 5264;
    6187 5280 5281 5266 5265; 6188 5281 5282 5267 5266; 6189 5282 5283 5268 5267;
    6190 5283 5284 5269 5268; 6191 5284 5285 5270 5269; 6192 5285 5286 5271 5270;
    6193 5286 5287 5272 5271; 6194 5287 5288 5273 5272; 6195 5288 5289 5274 5273;
    6196 5289 5290 5275 5274; 6197 5290 5291 5276 5275; 6198 5291 5292 5277 5276;
    6199 5292 4622 4623 5277; 6200 5029 5293 5278 5028; 6201 5293 5294 5279 5278;
    6202 5294 5295 5280 5279; 6203 5295 5296 5281 5280; 6204 5296 5297 5282 5281;
    6205 5297 5298 5283 5282; 6206 5298 5299 5284 5283; 6207 5299 5300 5285 5284;
    6208 5300 5301 5286 5285; 6209 5301 5302 5287 5286; 6210 5302 5303 5288 5287;
    6211 5303 5304 5289 5288; 6212 5304 5305 5290 5289; 6213 5305 5306 5291 5290;
    6214 5306 5307 5292 5291; 6215 5307 4621 4622 5292; 6216 5030 5308 5293 5029;
    6217 5308 5309 5294 5293; 6218 5309 5310 5295 5294; 6219 5310 5311 5296 5295;
    6220 5311 5312 5297 5296; 6221 5312 5313 5298 5297; 6222 5313 5314 5299 5298;
    6223 5314 5315 5300 5299; 6224 5315 5316 5301 5300; 6225 5316 5317 5302 5301;
    6226 5317 5318 5303 5302; 6227 5318 5319 5304 5303; 6228 5319 5320 5305 5304;
    6229 5320 5321 5306 5305; 6230 5321 5322 5307 5306; 6231 5322 4620 4621 5307;
    6232 5031 5323 5308 5030; 6233 5323 5324 5309 5308; 6234 5324 5325 5310 5309;
    6235 5325 5326 5311 5310; 6236 5326 5327 5312 5311; 6237 5327 5328 5313 5312;
    6238 5328 5329 5314 5313; 6239 5329 5330 5315 5314; 6240 5330 5331 5316 5315;
    6241 5331 5332 5317 5316; 6242 5332 5333 5318 5317; 6243 5333 5334 5319 5318;
    6244 5334 5335 5320 5319; 6245 5335 5336 5321 5320; 6246 5336 5337 5322 5321;
    6247 5337 4619 4620 5322; 6248 5032 5338 5323 5031; 6249 5338 5339 5324 5323;
    6250 5339 5340 5325 5324; 6251 5340 5341 5326 5325; 6252 5341 5342 5327 5326;
    6253 5342 5343 5328 5327; 6254 5343 5344 5329 5328; 6255 5344 5345 5330 5329;
    6256 5345 5346 5331 5330; 6257 5346 5347 5332 5331; 6258 5347 5348 5333 5332;
    6259 5348 5349 5334 5333; 6260 5349 5350 5335 5334; 6261 5350 5351 5336 5335;
    6262 5351 5352 5337 5336; 6263 5352 4618 4619 5337; 6264 5033 5353 5338 5032;
    6265 5353 5354 5339 5338; 6266 5354 5355 5340 5339; 6267 5355 5356 5341 5340;
    6268 5356 5357 5342 5341; 6269 5357 5358 5343 5342; 6270 5358 5359 5344 5343;
    6271 5359 5360 5345 5344; 6272 5360 5361 5346 5345; 6273 5361 5362 5347 5346;
    6274 5362 5363 5348 5347; 6275 5363 5364 5349 5348; 6276 5364 5365 5350 5349;
    6277 5365 5366 5351 5350; 6278 5366 5367 5352 5351; 6279 5367 4617 4618 5352;
    6280 5034 5368 5353 5033; 6281 5368 5369 5354 5353; 6282 5369 5370 5355 5354;
    6283 5370 5371 5356 5355; 6284 5371 5372 5357 5356; 6285 5372 5373 5358 5357;
    6286 5373 5374 5359 5358; 6287 5374 5375 5360 5359; 6288 5375 5376 5361 5360;
    6289 5376 5377 5362 5361; 6290 5377 5378 5363 5362; 6291 5378 5379 5364 5363;
    6292 5379 5380 5365 5364; 6293 5380 5381 5366 5365; 6294 5381 5382 5367 5366;
    6295 5382 4616 4617 5367; 6296 5035 5383 5368 5034; 6297 5383 5384 5369 5368;
    6298 5384 5385 5370 5369; 6299 5385 5386 5371 5370; 6300 5386 5387 5372 5371;
    6301 5387 5388 5373 5372; 6302 5388 5389 5374 5373; 6303 5389 5390 5375 5374;
    6304 5390 5391 5376 5375; 6305 5391 5392 5377 5376; 6306 5392 5393 5378 5377;
    6307 5393 5394 5379 5378; 6308 5394 5395 5380 5379; 6309 5395 5396 5381 5380;
    6310 5396 5397 5382 5381; 6311 5397 4615 4616 5382; 6312 5036 5398 5383 5035;
    6313 5398 5399 5384 5383; 6314 5399 5400 5385 5384; 6315 5400 5401 5386 5385;
    6316 5401 5402 5387 5386; 6317 5402 5403 5388 5387; 6318 5403 5404 5389 5388;
    6319 5404 5405 5390 5389; 6320 5405 5406 5391 5390; 6321 5406 5407 5392 5391;
    6322 5407 5408 5393 5392; 6323 5408 5409 5394 5393; 6324 5409 5410 5395 5394;
    6325 5410 5411 5396 5395; 6326 5411 5412 5397 5396; 6327 5412 4614 4615 5397;
    6328 5037 5413 5398 5036; 6329 5413 5414 5399 5398; 6330 5414 5415 5400 5399;
    6331 5415 5416 5401 5400; 6332 5416 5417 5402 5401; 6333 5417 5418 5403 5402;
    6334 5418 5419 5404 5403; 6335 5419 5420 5405 5404; 6336 5420 5421 5406 5405;
    6337 5421 5422 5407 5406; 6338 5422 5423 5408 5407; 6339 5423 5424 5409 5408;
    6340 5424 5425 5410 5409; 6341 5425 5426 5411 5410; 6342 5426 5427 5412 5411;
    6343 5427 4613 4614 5412; 6344 385 5038 5413 5037; 6345 5038 5039 5414 5413;
    6346 5039 5040 5415 5414; 6347 5040 5041 5416 5415; 6348 5041 5042 5417 5416;
    6349 5042 5043 5418 5417; 6350 5043 5044 5419 5418; 6351 5044 5045 5420 5419;
    6352 5045 5046 5421 5420; 6353 5046 5047 5422 5421; 6354 5047 5048 5423 5422;
    6355 5048 5049 5424 5423; 6356 5049 5050 5425 5424; 6357 5050 5051 5426 5425;
    6358 5051 5052 5427 5426; 6359 5052 379 4613 5427;
    <! STAAD PRO GENERATED DATA DO NOT MODIFY !!!
    PARAMETRIC MODEL SWALL 15
    TYPE WALL
    MESH PARAM 0.2 4 1 1
    MESH ORG 1 2 3
    BOUNDARY 4
    384 0 0 385 0 0 379 0 0 378 0 0
    GENERATED NODES 5013 TO 5427
    GENERATED PLATES PLATE 5944 TO 6359
    END
    !> END GENERATED DATA BLOCK
    PARAMETRIC MODEL SWALL 14
    TYPE WALL
    MESH ORG 1 2 3
    BOUNDARY 4
    372 0 0 373 0 0 379 0 0 378 0 0
    GENERATED NODES 4598 TO 5012
    GENERATED PLATES PLATE 5488 TO 5903
    END
    PARAMETRIC MODEL SWALL 13
    TYPE WALL
    MESH ORG 1 3 4
    BOUNDARY 6
    134 0 0 169 0 0 291 0 0 373 0 0 372 0 0 270 0 0
    GENERATED NODES 4217 TO 4597
    GENERATED PLATES PLATE 5066 TO 5447
    END
    PARAMETRIC MODEL SWALL 12
    TYPE WALL
    MESH ORG 1 2 3
    BOUNDARY 4
    383 0 0 384 0 0 378 0 0 377 0 0
    GENERATED NODES 3930 TO 4216
    GENERATED PLATES PLATE 4739 TO 5026
    END
    PARAMETRIC MODEL SWALL 11
    TYPE WALL
    MESH ORG 1 2 3
    BOUNDARY 4
    371 0 0 372 0 0 378 0 0 377 0 0
    GENERATED NODES 3643 TO 3929
    GENERATED PLATES PLATE 4419 TO 4706
    END
    PARAMETRIC MODEL SWALL 10
    TYPE WALL
    MESH ORG 1 3 4
    BOUNDARY 6
    99 0 0 134 0 0 270 0 0 372 0 0 371 0 0 249 0 0
    GENERATED NODES 3250 TO 3642
    GENERATED PLATES PLATE 3989 TO 4386
    END
    PARAMETRIC MODEL SWALL 9
    TYPE WALL
    MESH ORG 1 2 3
    BOUNDARY 4
    382 0 0 383 0 0 377 0 0 376 0 0
    GENERATED NODES 2963 TO 3249
    GENERATED PLATES PLATE 3670 TO 3957
    END
    PARAMETRIC MODEL SWALL 8
    TYPE WALL
    MESH ORG 1 2 3
    BOUNDARY 4
    370 0 0 371 0 0 377 0 0 376 0 0
    GENERATED NODES 2676 TO 2962
    GENERATED PLATES PLATE 3350 TO 3637
    END
    PARAMETRIC MODEL SWALL 7
    TYPE WALL
    MESH ORG 1 3 4
    BOUNDARY 6
    64 0 0 99 0 0 249 0 0 371 0 0 370 0 0 228 0 0
    GENERATED NODES 2283 TO 2675
    GENERATED PLATES PLATE 2920 TO 3317
    END
    PARAMETRIC MODEL SWALL 6
    TYPE WALL
    MESH ORG 1 2 3
    BOUNDARY 4
    381 0 0 382 0 0 376 0 0 375 0 0
    GENERATED NODES 1836 TO 2282
    GENERATED PLATES PLATE 2441 TO 2888
    END
    PARAMETRIC MODEL SWALL 5
    TYPE WALL
    MESH ORG 1 2 3
    BOUNDARY 4
    369 0 0 370 0 0 376 0 0 375 0 0
    GENERATED NODES 1389 TO 1835
    GENERATED PLATES PLATE 1951 TO 2398
    END
    PARAMETRIC MODEL SWALL 4
    TYPE WALL
    MESH ORG 1 3 4
    BOUNDARY 5
    29 0 0 64 0 0 228 0 0 370 0 0 369 0 0
    GENERATED NODES 1016 TO 1388
    GENERATED PLATES PLATE 1534 TO 1908
    END
    PARAMETRIC MODEL SWALL 3
    TYPE WALL
    MESH ORG 1 2 3
    BOUNDARY 4
    386 0 0 381 0 0 375 0 0 380 0 0
    GENERATED NODES 810 TO 1015
    GENERATED PLATES PLATE 1301 TO 1492
    END
    PARAMETRIC MODEL SWALL 2
    TYPE WALL
    MESH ORG 1 2 3
    BOUNDARY 4
    374 0 0 369 0 0 375 0 0 380 0 0
    GENERATED NODES 604 TO 809
    GENERATED PLATES PLATE 1083 TO 1274
    END
    TYPE WALL
    MESH ORG 1 2 3
    BOUNDARY 4
    323 0 0 29 0 0 369 0 0 374 0 0
    GENERATED NODES 387 TO 603
    GENERATED PLATES PLATE 865 TO 1056
    END
    START GROUP DEFINITION
    FLOOR
    _2FLR_DL 95 96 99 TO 101 104 TO 106 108 TO 111 113 TO 115 117 TO 120 -
    122 TO 124 126 TO 129 131 TO 133 135 TO 138 140 141 144 145 149 150 524 525 -
    527 TO 540 542 543 545 TO 556 558 TO 561 715 792 814
    _2FLR_DL_2WAY 94 98 99 103 106 TO 108 112 116 117 121 125 126 130 134 135 -
    139 143 144 148 529 715 TO 717
    _3FLR_DL 188 189 192 TO 194 197 TO 199 201 TO 204 206 TO 208 210 TO 213 215 -
    216 TO 217 219 TO 222 224 TO 226 228 TO 231 233 234 237 238 242 243 563 564 -
    566 TO 579 581 582 584 TO 595 597 TO 600 720 727 728 793 816
    _4FLR_DL 281 282 285 TO 287 290 TO 292 294 TO 297 299 TO 301 303 TO 306 308 -
    309 TO 310 312 TO 315 317 TO 319 321 TO 324 326 327 330 331 335 336 602 603 -
    605 TO 618 620 621 623 TO 634 636 TO 639 723 729 730 794 818
    _5FLR_DL 374 375 378 TO 380 383 TO 385 641 642 644 TO 646 662 668 726 731 732
    _2FLR_LL_OFFICE 96 100 101 104 TO 106 108 TO 111 113 TO 115 119 120 124 128 -
    129 131 TO 133 135 TO 138 140 141 144 145 149 150 525 527 TO 532 535 TO 540 -
    542 543 546 549 TO 552 555 556 558 TO 561 715 792 814
    _2FLR_LL_ASSMBLY 122 123 126 TO 128 131 132 533 534 536 537 548 554
    _2FLR_LL_STORAGE 95 99 100 104 113 114 117 TO 119 122 123 524 527 530 531 -
    533 534 545 547 553
    _2FLR_LL_OFFICE2 94 98 99 103 106 TO 108 112 116 117 121 125 126 130 134 135 -
    _3FLR_LL_QUARTER 188 189 192 TO 194 197 198 201 TO 203 206 TO 208 210 TO 213 -
    215 TO 217 219 TO 222 224 TO 226 228 TO 230 233 234 237 238 242 243 563 564 -
    566 567 569 TO 579 581 582 584 TO 595 598 599 727 816
    _3FLR_LL_GYM 199 203 204 208 568 571 597
    _3FR_LL_STORAGE 226 230 231 577 600 793
    _3FLR_LL_GYM2 199 568 720 727 728
    _4FLR_LL_ASSMBLY 281 282 285 TO 287 290 TO 292 294 TO 297 299 TO 301 -
    303 TO 306 308 TO 310 312 TO 315 317 TO 319 321 TO 324 326 327 330 331 335 -
    336 602 603 605 TO 618 620 621 623 TO 634 636 TO 639 723 729 730 794 818
    _5TH_LL_STORAGE 375 379 380 384 641 642 644 645 662 668 731
    _2FLR_BALCONY 148 TO 150 542 543 751 TO 754 756 TO 760 762 763
    _3FLR_BALCONY 242 243 581 582 765 TO 767 769 770 772 773 775 776
    _4FLR_BALCONY 335 TO 337 620 621 778 TO 783 785 TO 789
    JOINT
    END GROUP DEFINITION
    ELEMENT PROPERTY
    865 TO 1056 1083 TO 1274 1301 TO 1492 1534 TO 1908 1951 TO 2398 2441 TO 2888 -
    2920 TO 3317 3350 TO 3637 3670 TO 3957 3989 TO 4386 4419 TO 4706 -
    4739 TO 5026 5066 TO 5447 5488 TO 5903 5944 TO 6359 THICKNESS 0.25
    DEFINE MATERIAL START
    ISOTROPIC CONCRETE
    E 2.17185e+07
    POISSON 0.17
    DENSITY 23.5616
    ALPHA 1e-05
    DAMP 0.05
    TYPE CONCRETE
    STRENGTH FCU 27579
    END DEFINE MATERIAL
    MEMBER PROPERTY AMERICAN
    153 TO 156 158 TO 161 163 TO 166 168 TO 171 173 TO 176 178 TO 181 183 TO 186 -
    246 TO 249 251 TO 254 256 TO 259 261 TO 264 266 TO 269 271 TO 274 -
    276 TO 279 797 798 808 809 824 825 2889 2903 TO 2919 3333 TO 3349 -
    3638 TO 3654 3958 3972 TO 3988 4402 TO 4418 4707 TO 4722 -
    4723 PRIS YD 0.45 ZD 0.45
    188 TO 190 192 TO 195 197 TO 199 201 TO 204 206 TO 208 210 TO 213 215 TO 217 -
    219 TO 222 224 TO 226 228 TO 231 233 234 237 238 240 281 TO 283 285 TO 288 -
    290 TO 292 294 TO 297 299 TO 301 303 TO 306 308 TO 310 312 TO 315 -
    317 TO 319 321 TO 324 326 327 330 331 333 374 TO 376 378 TO 381 383 TO 385 -
    387 TO 390 392 TO 394 396 TO 399 401 TO 403 405 TO 408 410 TO 412 -
    414 TO 417 419 420 423 424 426 428 TO 430 563 564 566 TO 579 602 603 605 -
    606 TO 618 641 642 644 TO 657 659 660 727 TO 732 793 TO 795 816 818 -
    820 PRIS YD 0.4 ZD 0.3
    1 TO 48 50 TO 52 54 TO 58 94 TO 141 143 TO 145 147 TO 151 242 TO 244 -
    335 TO 337 524 525 527 TO 540 542 543 545 TO 556 558 TO 561 581 582 -
    584 TO 595 597 TO 600 620 621 623 TO 634 636 TO 639 662 TO 673 675 TO 678 -
    715 TO 717 720 723 726 741 TO 763 765 TO 770 772 TO 776 778 TO 783 -
    785 TO 789 791 792 812 814 PRIS YD 0.3 ZD 0.25
    339 TO 342 344 TO 347 349 352 354 357 359 362 364 367 369 TO 372 733 TO 740 -
    790 800 811 827 5027 5041 TO 5065 5463 TO 5487 5904 TO 5927 -
    5928 PRIS YD 0.3 ZD 0.3
    59 TO 93 680 TO 714 796 799 807 810 823 826 828 TO 838 854 TO 864 -
    1072 TO 1082 1275 TO 1285 1493 1507 TO 1533 1924 TO 1950 2399 TO 2424 -
    2425 PRIS YD 0.5 ZD 0.5
    CONSTANTS
    MATERIAL CONCRETE ALL
    MEMBER RELEASE
    545 TO 556 558 TO 561 584 TO 595 597 TO 600 623 TO 634 636 TO 639 662 TO 673 -
    675 TO 678 START MY MZ
    675 TO 678 END MY MZ
    SUPPORTS
    295 TO 329 374 380 386 424 TO 438 630 TO 644 836 TO 850 FIXED
    MEMBER CRACKED
    59 TO 93 153 TO 156 158 TO 161 163 TO 166 168 TO 171 173 TO 176 178 TO 181 -
    183 TO 186 246 TO 249 251 TO 254 256 TO 259 261 TO 264 266 TO 269 -
    271 TO 274 276 TO 279 339 TO 342 344 TO 347 349 352 354 357 359 362 364 367 -
    369 TO 372 680 TO 714 733 TO 740 REDUCTION RIY 0.7 RIZ 0.7
    1 TO 48 50 TO 52 54 TO 58 94 TO 141 143 TO 145 147 TO 151 188 TO 190 -
    219 TO 222 224 TO 226 228 TO 231 233 234 237 238 240 242 TO 244 281 TO 283 -
    285 TO 288 290 TO 292 294 TO 297 299 TO 301 303 TO 306 308 TO 310 -
    312 TO 315 317 TO 319 321 TO 324 326 327 330 331 333 335 TO 337 374 TO 376 -
    378 TO 381 383 TO 385 387 TO 390 392 TO 394 396 TO 399 401 TO 403 -
    405 TO 408 410 TO 412 414 TO 417 419 420 423 424 426 428 TO 430 524 525 527 -
    528 TO 540 542 543 545 TO 556 558 TO 561 563 564 566 TO 579 581 582 -
    584 TO 595 597 TO 600 602 603 605 TO 618 620 621 623 TO 634 636 TO 639 641 -
    642 644 TO 657 659 660 662 TO 673 675 TO 678 715 TO 717 720 723 726 TO 732 -
    741 TO 763 765 TO 770 772 TO 776 778 TO 783 785 TO 788 -
    789 REDUCTION RIY 0.35 RIZ 0.35
    DEFINE REFERENCE LOADS
    LOAD R1 LOADTYPE Dead TITLE DL1
    ONEWAY LOAD
    _2FLR_DL ONE -2.5 GY
    _3FLR_DL ONE -2.5 GY
    _4FLR_DL ONE -2.5 GY
    _5FLR_DL ONE -2.5 GY
    FLOOR LOAD
    _2FLR_DL_2WAY FLOAD -2.5 GY
    SELFWEIGHT Y -1
    ONEWAY LOAD
    _2FLR_BALCONY ONE -2.5 GY
    _3FLR_BALCONY ONE -2.5 GY
    _4FLR_BALCONY ONE -2.5 GY
    LOAD R2 LOADTYPE Dead TITLE DL2
    ONEWAY LOAD
    _2FLR_DL ONE -3.32 GY
    _3FLR_DL ONE -3.32 GY
    _4FLR_DL ONE -3.32 GY
    _5FLR_DL ONE -3.32 GY
    FLOOR LOAD
    _2FLR_DL_2WAY FLOAD -3.32 GY
    END DEFINE REFERENCE LOADS
    FLOOR DIAPHRAGM
    DIA 1 TYPE RIG HEI 5.5
    DIA 2 TYPE RIG HEI 9
    DIA 3 TYPE RIG HEI 12.5
    CHECK SOFT STORY ASCE7
    DEFINE UBC LOAD
    ZONE 0.4 I 1.5 RWX 8.55 RWZ 8.5 STYP 4 CT 0.0731 NA 1.2 NV 1.6
    DEFINE WIND LOAD
    TYPE 1 W1
    ASCE-7-2010:PARAMS 85.000 MPH 0 1 1 0 0.000 FT 0.000 FT 0.000 FT 1 2 20.500 -
    M 20.150 M 35.600 M 2.000 0.010 0 0 0 0 0 0.882 1.000 1.000 0.850 0 0 0 0 -
    0.831 0.800 -0.180
    INT 0.407075 0.407075 0.427257 0.444583 0.459866 0.473603 0.486123 0.497658 -
    0.508373 0.518398 0.52783 0.536746 0.545209 0.553272 0.560977 HEIG 0 4.572 -
    5.79723 7.02246 8.24769 9.47292 10.6981 11.9234 13.1486 14.3738 15.5991 -
    16.8243 18.0495 19.2748 20.5
    EXP 1 JOINT 1 TO 70 72 TO 75 77 TO 80 82 TO 85 87 TO 90 92 TO 95 97 TO 100 -
    102 TO 105 107 TO 110 112 TO 115 117 TO 120 122 TO 125 127 TO 130 -
    132 TO 135 137 TO 140 142 TO 145 147 TO 150 152 TO 155 157 TO 160 -
    162 TO 165 167 TO 170 172 TO 175 211 212 214 TO 230 232 233 235 TO 251 253 -
    254 256 TO 272 274 275 277 TO 293 295 TO 345 374 380 386
    LOAD 1 LOADTYPE Seismic TITLE EX
    UBC LOAD X 1 DEC 1 ACC 0.05
    PERFORM ANALYSIS PRINT LOAD DATA
    CHANGE
    LOAD 2 LOADTYPE Seismic TITLE EZ
    UBC LOAD Z 1 DEC 1 ACC 0.05
    CHANGE
    LOAD 3 LOADTYPE Dead TITLE DL1
    REFERENCE LOAD
    R1 1.0
    LOAD 4 LOADTYPE Dead TITLE DL2
    REFERENCE LOAD
    R2 1.0
    LOAD 5 LOADTYPE Live TITLE LL1
    ONEWAY LOAD
    _2FLR_LL_OFFICE ONE -2.4 GY
    FLOOR LOAD
    _2FLR_LL_OFFICE2 FLOAD -2.4 GY
    ONEWAY LOAD
    _3FLR_LL_QUARTER ONE -1.9 GY
    _2FLR_BALCONY ONE -2.9 GY
    _3FLR_BALCONY ONE -2.9 GY
    _4FLR_BALCONY ONE -2.9 GY
    LOAD 6 LOADTYPE Live TITLE LL2
    ONEWAY LOAD
    _2FLR_LL_ASSMBLY ONE -4.8 GY
    _2FLR_LL_STORAGE ONE -6 GY
    _3FLR_LL_GYM ONE -6 GY
    _3FR_LL_STORAGE ONE -6 GY
    FLOOR LOAD
    _3FLR_LL_GYM2 FLOAD -6 GY
    ONEWAY LOAD
    _4FLR_LL_ASSMBLY ONE -4.8 GY
    _5TH_LL_STORAGE ONE -6 GY
    LOAD 7 LOADTYPE Roof Live TITLE LLR
    JOINT LOAD
    152 155 157 160 162 165 167 170 172 TO 175 338 TO 345 FY -30
    LOAD 8 LOADTYPE Wind TITLE WZ1
    WIND LOAD Z 1 TYPE 1
    LOAD 9 LOADTYPE Wind TITLE WZ2
    WIND LOAD Z -1 TYPE 1
    LOAD 10 LOADTYPE Wind TITLE WX1
    WIND LOAD X 1 TYPE 1
    LOAD 11 LOADTYPE Wind TITLE WX2
    WIND LOAD X -1 TYPE 1
    **DESIGN LOAD COMBINATIONS - LRFD
    LOAD COMB 101 1.4DL
    1 0.0 2 0.0 3 1.4 4 1.4 5 0.0 6 0.0 7 0.0 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 102 1.2DL + 1.6LL + 0.5LLR
    1 0.0 2 0.0 3 1.2 4 1.2 5 1.6 6 1.6 7 0.5 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 103 1.2DL + 1.6LLR + F1LL
    1 0.0 2 0.0 3 1.2 4 1.2 5 0.5 6 1.0 7 1.6 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 104 (1.2 + 0.5CAI)DL + F1LL + 1.0EX + 0.3EZ
    1 1.0 2 0.3 3 1.42 4 1.42 5 0.5 6 1.0 7 0.5 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 105 (1.2 + 0.5CAI)DL + F1LL + 1.0EX - 0.3EZ
    1 1.0 2 -0.3 3 1.42 4 1.42 5 0.5 6 1.0 7 0.5 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 106 (1.2 + 0.5CAI)DL + F1LL - 1.0EX + 0.3EZ
    1 -1.0 2 0.3 3 1.42 4 1.42 5 0.5 6 1.0 7 0.5 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 107 (1.2 + 0.5CAI)DL + F1LL - 1.0EX - 0.3EZ
    1 -1.0 2 -0.3 3 1.42 4 1.42 5 0.5 6 1.0 7 0.5 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 108 (1.2 + 0.5CAI)DL + F1LL + 1.0EZ + 0.3EX
    1 0.3 2 1.0 3 1.42 4 1.42 5 0.5 6 1.0 7 0.5 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 109 (1.2 + 0.5CAI)DL + F1LL + 1.0EZ - 0.3EX
    1 -0.3 2 1.0 3 1.42 4 1.42 5 0.5 6 1.0 7 0.5 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 110 (1.2 + 0.5CAI)DL + F1LL - 1.0EZ + 0.3EX
    1 0.3 2 -1.0 3 1.42 4 1.42 5 0.5 6 1.0 7 0.5 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 111 (1.2 + 0.5CAI)DL + F1LL - 1.0EZ - 0.3EX
    1 -0.3 2 -1.0 3 1.42 4 1.42 5 0.5 6 1.0 7 0.5 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 112 (0.9 + 0.5CAI)DL + 1.0EX + 0.3EZ
    1 1.0 2 0.3 3 1.12 4 1.12 5 0.0 6 0.0 7 0.0 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 113 (0.9 + 0.5CAI)DL + 1.0EX - 0.3EZ
    1 1.0 2 -0.3 3 1.12 4 1.12 5 0.0 6 0.0 7 0.0 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 114 (0.9 + 0.5CAI)DL - 1.0EX + 0.3EZ
    1 -1.0 2 0.3 3 1.12 4 1.12 5 0.0 6 0.0 7 0.0 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 115 (0.9 + 0.5CAI)DL - 1.0EX - 0.3EZ
    1 -1.0 2 -0.3 3 1.12 4 1.12 5 0.0 6 0.0 7 0.0 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 116 (0.9 + 0.5CAI)DL + 1.0EZ + 0.3EX
    1 0.3 2 1.0 3 1.12 4 1.12 5 0.0 6 0.0 7 0.0 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 117 (0.9 + 0.5CAI)DL + 1.0EZ - 0.3EX
    1 -0.3 2 1.0 3 1.12 4 1.12 5 0.0 6 0.0 7 0.0 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 118 (0.9 + 0.5CAI)DL - 1.0EZ + 0.3EX
    1 0.3 2 -1.0 3 1.12 4 1.12 5 0.0 6 0.0 7 0.0 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 119 (0.9 + 0.5CAI)DL - 1.0EZ - 0.3EX
    1 -0.3 2 -1.0 3 1.12 4 1.12 5 0.0 6 0.0 7 0.0 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 120 1.2DL + F1LL + 0.5LLR + 1.0WZ1
    1 0.0 2 0.0 3 1.2 4 1.2 5 0.5 6 1.0 7 0.5 8 1.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 121 1.2DL + F1LL + 0.5LLR + 1.0WZ2
    1 0.0 2 0.0 3 1.2 4 1.2 5 0.5 6 1.0 7 0.5 8 0.0 9 1.0 10 0.0 11 0.0
    LOAD COMB 122 1.2DL + F1LL + 0.5LLR + 1.0WX1
    1 0.0 2 0.0 3 1.2 4 1.2 5 0.5 6 1.0 7 0.5 8 0.0 9 0.0 10 1.0 11 0.0
    LOAD COMB 123 1.2DL + F1LL + 0.5LLR + 1.0WX2
    1 0.0 2 0.0 3 1.2 4 1.2 5 0.5 6 1.0 7 0.5 8 0.0 9 0.0 10 0.0 11 1.0
    LOAD COMB 124 0.9DL + 1.0WZ1
    1 0.0 2 0.0 3 0.9 4 0.9 5 0.0 6 0.0 7 0.0 8 1.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 125 0.9DL + 1.0WZ2
    1 0.0 2 0.0 3 0.9 4 0.9 5 0.0 6 0.0 7 0.0 8 0.0 9 1.0 10 0.0 11 0.0
    LOAD COMB 126 0.9DL + 1.0WX1
    1 0.0 2 0.0 3 0.9 4 0.9 5 0.0 6 0.0 7 0.0 8 0.0 9 0.0 10 1.0 11 0.0
    LOAD COMB 127 0.9DL + 1.0WX2
    1 0.0 2 0.0 3 0.9 4 0.9 5 0.0 6 0.0 7 0.0 8 0.0 9 0.0 10 0.0 11 1.0
    LOAD COMB 128 (0.9 - 0.5CAI)DL + 1.0EX + 0.3EZ
    1 1.0 2 0.3 3 0.68 4 0.68 5 0.0 6 0.0 7 0.0 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 129 (0.9 - 0.5CAI)DL + 1.0EX - 0.3EZ
    1 1.0 2 -0.3 3 0.68 4 0.68 5 0.0 6 0.0 7 0.0 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 130 (0.9 - 0.5CAI)DL - 1.0EX + 0.3EZ
    1 -1.0 2 0.3 3 0.68 4 0.68 5 0.0 6 0.0 7 0.0 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 131 (0.9 - 0.5CAI)DL - 1.0EX - 0.3EZ
    1 -1.0 2 -0.3 3 0.68 4 0.68 5 0.0 6 0.0 7 0.0 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 132 (0.9 - 0.5CAI)DL + 1.0EZ + 0.3EX
    1 0.3 2 1.0 3 0.68 4 0.68 5 0.0 6 0.0 7 0.0 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 133 (0.9 - 0.5CAI)DL + 1.0EZ - 0.3EX
    1 -0.3 2 1.0 3 0.68 4 0.68 5 0.0 6 0.0 7 0.0 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 134 (0.9 - 0.5CAI)DL - 1.0EZ + 0.3EX
    1 0.3 2 -1.0 3 0.68 4 0.68 5 0.0 6 0.0 7 0.0 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 135 (0.9 - 0.5CAI)DL - 1.0EZ - 0.3EX
    1 -0.3 2 -1.0 3 0.68 4 0.68 5 0.0 6 0.0 7 0.0 8 0.0 9 0.0 10 0.0 11 0.0
    PERFORM ANALYSIS
    PRINT STORY DRIFT 0.003361
    FINISH
    The support reactions became very unrealistic.
Reply
  • STAAD SPACE
    START JOB INFORMATION
    ENGINEER DATE 05-Aug-21
    END JOB INFORMATION
    INPUT WIDTH 79
    UNIT METER KN
    JOINT COORDINATES
    1 0 0 0; 2 3.7 0 0; 3 8.925 0 0; 4 14.925 0 0; 5 20.15 0 0; 6 0 0 6; 7 3.7 0 6;
    8 8.925 0 6; 9 14.925 0 6; 10 20.15 0 6; 11 0 0 12; 12 3.7 0 12; 13 8.925 0 12;
    14 14.925 0 12; 15 20.15 0 12; 16 0 0 18; 17 3.7 0 18; 18 8.925 0 18;
    19 14.925 0 18; 20 20.15 0 18; 21 0 0 24; 22 3.7 0 24; 23 8.925 0 24;
    24 14.925 0 24; 25 20.15 0 24; 26 0 0 30; 27 3.7 0 30; 28 8.925 0 30;
    29 14.925 0 30; 30 20.15 0 30; 31 0 0 35.6; 32 3.7 0 35.6; 33 8.925 0 35.6;
    34 14.925 0 35.6; 35 20.15 0 35.6; 36 0 5.5 0; 37 3.7 5.5 0; 38 8.925 5.5 0;
    39 14.925 5.5 0; 40 20.15 5.5 0; 41 0 5.5 6; 42 3.7 5.5 6; 43 8.925 5.5 6;
    44 14.925 5.5 6; 45 20.15 5.5 6; 46 0 5.5 12; 47 3.7 5.5 12; 48 8.925 5.5 12;
    49 14.925 5.5 12; 50 20.15 5.5 12; 51 0 5.5 18; 52 3.7 5.5 18; 53 8.925 5.5 18;
    54 14.925 5.5 18; 55 20.15 5.5 18; 56 0 5.5 24; 57 3.7 5.5 24; 58 8.925 5.5 24;
    59 14.925 5.5 24; 60 20.15 5.5 24; 61 0 5.5 30; 62 3.7 5.5 30; 63 8.925 5.5 30;
    64 14.925 5.5 30; 65 20.15 5.5 30; 66 0 5.5 35.6; 67 3.7 5.5 35.6;
    68 8.925 5.5 35.6; 69 14.925 5.5 35.6; 70 20.15 5.5 35.6; 72 3.7 9 0;
    73 8.925 9 0; 74 14.925 9 0; 75 20.15 9 0; 77 3.7 9 6; 78 8.925 9 6;
    79 14.925 9 6; 80 20.15 9 6; 82 3.7 9 12; 83 8.925 9 12; 84 14.925 9 12;
    85 20.15 9 12; 87 3.7 9 18; 88 8.925 9 18; 89 14.925 9 18; 90 20.15 9 18;
    92 3.7 9 24; 93 8.925 9 24; 94 14.925 9 24; 95 20.15 9 24; 97 3.7 9 30;
    98 8.925 9 30; 99 14.925 9 30; 100 20.15 9 30; 102 3.7 9 35.6;
    103 8.925 9 35.6; 104 14.925 9 35.6; 105 20.15 9 35.6; 107 3.7 12.5 0;
    108 8.925 12.5 0; 109 14.925 12.5 0; 110 20.15 12.5 0; 112 3.7 12.5 6;
    113 8.925 12.5 6; 114 14.925 12.5 6; 115 20.15 12.5 6; 117 3.7 12.5 12;
    118 8.925 12.5 12; 119 14.925 12.5 12; 120 20.15 12.5 12; 122 3.7 12.5 18;
    123 8.925 12.5 18; 124 14.925 12.5 18; 125 20.15 12.5 18; 127 3.7 12.5 24;
    128 8.925 12.5 24; 129 14.925 12.5 24; 130 20.15 12.5 24; 132 3.7 12.5 30;
    133 8.925 12.5 30; 134 14.925 12.5 30; 135 20.15 12.5 30; 137 3.7 12.5 35.6;
    138 8.925 12.5 35.6; 139 14.925 12.5 35.6; 140 20.15 12.5 35.6; 142 3.7 17.5 0;
    143 8.925 17.5 0; 144 14.925 17.5 0; 145 20.15 17.5 0; 147 3.7 17.5 6;
    148 8.925 17.5 6; 149 14.925 17.5 6; 150 20.15 17.5 6; 152 3.7 17.5 12;
    153 8.925 17.5 12; 154 14.925 17.5 12; 155 20.15 17.5 12; 157 3.7 17.5 18;
    158 8.925 17.5 18; 159 14.925 17.5 18; 160 20.15 17.5 18; 162 3.7 17.5 24;
    163 8.925 17.5 24; 164 14.925 17.5 24; 165 20.15 17.5 24; 167 3.7 17.5 30;
    168 8.925 17.5 30; 169 14.925 17.5 30; 170 20.15 17.5 30; 172 3.7 17.5 35.6;
    173 8.925 17.5 35.6; 174 14.925 17.5 35.6; 175 20.15 17.5 35.6;
    211 6.3125 5.5 0; 212 11.925 5.5 0; 214 6.3125 5.5 6; 215 11.925 5.5 6;
    216 17.5375 5.5 6; 217 6.3125 5.5 12; 218 11.925 5.5 12; 219 17.5375 5.5 12;
    220 6.3125 5.5 18; 221 11.925 5.5 18; 222 17.5375 5.5 18; 223 6.3125 5.5 24;
    224 11.925 5.5 24; 225 17.5375 5.5 24; 226 6.3125 5.5 30; 227 11.925 5.5 30;
    228 17.5375 5.5 30; 229 6.3125 5.5 35.6; 230 11.925 5.5 35.6; 232 6.3125 9 0;
    233 11.925 9 0; 235 6.3125 9 6; 236 11.925 9 6; 237 17.5375 9 6;
    238 6.3125 9 12; 239 11.925 9 12; 240 17.5375 9 12; 241 6.3125 9 18;
    242 11.925 9 18; 243 17.5375 9 18; 244 6.3125 9 24; 245 11.925 9 24;
    246 17.5375 9 24; 247 6.3125 9 30; 248 11.925 9 30; 249 17.5375 9 30;
    250 6.3125 9 35.6; 251 11.925 9 35.6; 253 6.3125 12.5 0; 254 11.925 12.5 0;
    256 6.3125 12.5 6; 257 11.925 12.5 6; 258 17.5375 12.5 6; 259 6.3125 12.5 12;
    260 11.925 12.5 12; 261 17.5375 12.5 12; 262 6.3125 12.5 18;
    263 11.925 12.5 18; 264 17.5375 12.5 18; 265 6.3125 12.5 24;
    266 11.925 12.5 24; 267 17.5375 12.5 24; 268 6.3125 12.5 30;
    269 11.925 12.5 30; 270 17.5375 12.5 30; 271 6.3125 12.5 35.6;
    272 11.925 12.5 35.6; 274 6.3125 17.5 0; 275 11.925 17.5 0; 277 6.3125 17.5 6;
    278 11.925 17.5 6; 279 17.5375 17.5 6; 280 6.3125 17.5 12; 281 11.925 17.5 12;
    282 17.5375 17.5 12; 283 6.3125 17.5 18; 284 11.925 17.5 18;
    285 17.5375 17.5 18; 286 6.3125 17.5 24; 287 11.925 17.5 24;
    288 17.5375 17.5 24; 289 6.3125 17.5 30; 290 11.925 17.5 30;
    291 17.5375 17.5 30; 292 6.3125 17.5 35.6; 293 11.925 17.5 35.6; 295 0 -2.5 0;
    296 3.7 -2.5 0; 297 8.925 -2.5 0; 298 14.925 -2.5 0; 299 20.15 -2.5 0;
    300 0 -2.5 6; 301 3.7 -2.5 6; 302 8.925 -2.5 6; 303 14.925 -2.5 6;
    304 20.15 -2.5 6; 305 0 -2.5 12; 306 3.7 -2.5 12; 307 8.925 -2.5 12;
    308 14.925 -2.5 12; 309 20.15 -2.5 12; 310 0 -2.5 18; 311 3.7 -2.5 18;
    312 8.925 -2.5 18; 313 14.925 -2.5 18; 314 20.15 -2.5 18; 315 0 -2.5 24;
    316 3.7 -2.5 24; 317 8.925 -2.5 24; 318 14.925 -2.5 24; 319 20.15 -2.5 24;
    320 0 -2.5 30; 321 3.7 -2.5 30; 322 8.925 -2.5 30; 323 14.925 -2.5 30;
    324 20.15 -2.5 30; 325 0 -2.5 35.6; 326 3.7 -2.5 35.6; 327 8.925 -2.5 35.6;
    328 14.925 -2.5 35.6; 329 20.15 -2.5 35.6; 330 14.925 5.5 3.1;
    331 20.15 5.5 3.1; 332 14.925 9 3.1; 333 20.15 9 3.1; 334 14.925 12.5 3.1;
    335 20.15 12.5 3.1; 336 14.925 17.5 3.1; 337 20.15 17.5 3.1; 338 3.7 20.5 0;
    339 8.925 20.5 0; 340 14.925 20.5 0; 341 20.15 20.5 0; 342 3.7 20.5 6;
    343 8.925 20.5 6; 344 14.925 20.5 6; 345 20.15 20.5 6; 346 0 5.5 38;
    347 3.7 5.5 38; 348 8.925 5.5 38; 349 14.925 5.5 38; 350 20.15 5.5 38;
    351 6.3125 5.5 38; 352 11.925 5.5 38; 355 3.7 9 38; 356 8.925 9 38;
    357 14.925 9 38; 358 20.15 9 38; 359 6.3125 9 38; 360 11.925 9 38;
    363 3.7 12.5 38; 364 8.925 12.5 38; 365 14.925 12.5 38; 366 20.15 12.5 38;
    367 6.3125 12.5 38; 368 11.925 12.5 38; 369 18.125 0 30; 370 18.125 5.5 30;
    371 18.125 9 30; 372 18.125 12.5 30; 373 18.125 17.5 30; 374 18.125 -2.5 30;
    375 18.125 0 33.2; 376 18.125 5.5 33.2; 377 18.125 9 33.2;
    378 18.125 12.5 33.2; 379 18.125 17.5 33.2; 380 18.125 -2.5 33.2;
    381 14.925 0 33.2; 382 14.925 5.5 33.2; 383 14.925 9 33.2;
    384 14.925 12.5 33.2; 385 14.925 17.5 33.2; 386 14.925 -2.5 33.2;
    387 14.925 -2.29167 30; 388 14.925 -2.08333 30; 389 14.925 -1.875 30;
    390 14.925 -1.66667 30; 391 14.925 -1.45833 30; 392 14.925 -1.25 30;
    393 14.925 -1.04167 30; 394 14.925 -0.833333 30; 395 14.925 -0.625 30;
    396 14.925 -0.416667 30; 397 14.925 -0.208333 30; 398 15.125 0 30;
    399 15.325 0 30; 400 15.525 0 30; 401 15.725 0 30; 402 15.925 0 30;
    403 16.125 0 30; 404 16.325 0 30; 405 16.525 0 30; 406 16.725 0 30;
    407 16.925 0 30; 408 17.125 0 30; 409 17.325 0 30; 410 17.525 0 30;
    411 17.725 0 30; 412 17.925 0 30; 413 18.125 -0.208333 30;
    414 18.125 -0.416667 30; 415 18.125 -0.625 30; 416 18.125 -0.833333 30;
    417 18.125 -1.04167 30; 418 18.125 -1.25 30; 419 18.125 -1.45833 30;
    420 18.125 -1.66667 30; 421 18.125 -1.875 30; 422 18.125 -2.08333 30;
    423 18.125 -2.29167 30; 424 17.925 -2.5 30; 425 17.725 -2.5 30;
    426 17.525 -2.5 30; 427 17.325 -2.5 30; 428 17.125 -2.5 30; 429 16.925 -2.5 30;
    430 16.725 -2.5 30; 431 16.525 -2.5 30; 432 16.325 -2.5 30; 433 16.125 -2.5 30;
    434 15.925 -2.5 30; 435 15.725 -2.5 30; 436 15.525 -2.5 30; 437 15.325 -2.5 30;
    438 15.125 -2.5 30; 439 15.125 -2.29167 30; 440 15.325 -2.29167 30;
    441 15.525 -2.29167 30; 442 15.725 -2.29167 30; 443 15.925 -2.29167 30;
    444 16.125 -2.29167 30; 445 16.325 -2.29167 30; 446 16.525 -2.29167 30;
    447 16.725 -2.29167 30; 448 16.925 -2.29167 30; 449 17.125 -2.29167 30;
    450 17.325 -2.29167 30; 451 17.525 -2.29167 30; 452 17.725 -2.29167 30;
    453 17.925 -2.29167 30; 454 15.125 -2.08333 30; 455 15.325 -2.08333 30;
    456 15.525 -2.08333 30; 457 15.725 -2.08333 30; 458 15.925 -2.08333 30;
    459 16.125 -2.08333 30; 460 16.325 -2.08333 30; 461 16.525 -2.08333 30;
    462 16.725 -2.08333 30; 463 16.925 -2.08333 30; 464 17.125 -2.08333 30;
    465 17.325 -2.08333 30; 466 17.525 -2.08333 30; 467 17.725 -2.08333 30;
    468 17.925 -2.08333 30; 469 15.125 -1.875 30; 470 15.325 -1.875 30;
    471 15.525 -1.875 30; 472 15.725 -1.875 30; 473 15.925 -1.875 30;
    474 16.125 -1.875 30; 475 16.325 -1.875 30; 476 16.525 -1.875 30;
    477 16.725 -1.875 30; 478 16.925 -1.875 30; 479 17.125 -1.875 30;
    480 17.325 -1.875 30; 481 17.525 -1.875 30; 482 17.725 -1.875 30;
    483 17.925 -1.875 30; 484 15.125 -1.66667 30; 485 15.325 -1.66667 30;
    486 15.525 -1.66667 30; 487 15.725 -1.66667 30; 488 15.925 -1.66667 30;
    489 16.125 -1.66667 30; 490 16.325 -1.66667 30; 491 16.525 -1.66667 30;
    492 16.725 -1.66667 30; 493 16.925 -1.66667 30; 494 17.125 -1.66667 30;
    495 17.325 -1.66667 30; 496 17.525 -1.66667 30; 497 17.725 -1.66667 30;
    498 17.925 -1.66667 30; 499 15.125 -1.45833 30; 500 15.325 -1.45833 30;
    501 15.525 -1.45833 30; 502 15.725 -1.45833 30; 503 15.925 -1.45833 30;
    504 16.125 -1.45833 30; 505 16.325 -1.45833 30; 506 16.525 -1.45833 30;
    507 16.725 -1.45833 30; 508 16.925 -1.45833 30; 509 17.125 -1.45833 30;
    510 17.325 -1.45833 30; 511 17.525 -1.45833 30; 512 17.725 -1.45833 30;
    513 17.925 -1.45833 30; 514 15.125 -1.25 30; 515 15.325 -1.25 30;
    516 15.525 -1.25 30; 517 15.725 -1.25 30; 518 15.925 -1.25 30;
    519 16.125 -1.25 30; 520 16.325 -1.25 30; 521 16.525 -1.25 30;
    522 16.725 -1.25 30; 523 16.925 -1.25 30; 524 17.125 -1.25 30;
    525 17.325 -1.25 30; 526 17.525 -1.25 30; 527 17.725 -1.25 30;
    528 17.925 -1.25 30; 529 15.125 -1.04167 30; 530 15.325 -1.04167 30;
    531 15.525 -1.04167 30; 532 15.725 -1.04167 30; 533 15.925 -1.04167 30;
    534 16.125 -1.04167 30; 535 16.325 -1.04167 30; 536 16.525 -1.04167 30;
    537 16.725 -1.04167 30; 538 16.925 -1.04167 30; 539 17.125 -1.04167 30;
    540 17.325 -1.04167 30; 541 17.525 -1.04167 30; 542 17.725 -1.04167 30;
    543 17.925 -1.04167 30; 544 15.125 -0.833333 30; 545 15.325 -0.833333 30;
    546 15.525 -0.833333 30; 547 15.725 -0.833333 30; 548 15.925 -0.833333 30;
    549 16.125 -0.833333 30; 550 16.325 -0.833333 30; 551 16.525 -0.833333 30;
    552 16.725 -0.833333 30; 553 16.925 -0.833333 30; 554 17.125 -0.833333 30;
    555 17.325 -0.833333 30; 556 17.525 -0.833333 30; 557 17.725 -0.833333 30;
    558 17.925 -0.833333 30; 559 15.125 -0.625 30; 560 15.325 -0.625 30;
    561 15.525 -0.625 30; 562 15.725 -0.625 30; 563 15.925 -0.625 30;
    564 16.125 -0.625 30; 565 16.325 -0.625 30; 566 16.525 -0.625 30;
    567 16.725 -0.625 30; 568 16.925 -0.625 30; 569 17.125 -0.625 30;
    570 17.325 -0.625 30; 571 17.525 -0.625 30; 572 17.725 -0.625 30;
    573 17.925 -0.625 30; 574 15.125 -0.416667 30; 575 15.325 -0.416667 30;
    576 15.525 -0.416667 30; 577 15.725 -0.416667 30; 578 15.925 -0.416667 30;
    579 16.125 -0.416667 30; 580 16.325 -0.416667 30; 581 16.525 -0.416667 30;
    582 16.725 -0.416667 30; 583 16.925 -0.416667 30; 584 17.125 -0.416667 30;
    585 17.325 -0.416667 30; 586 17.525 -0.416667 30; 587 17.725 -0.416667 30;
    588 17.925 -0.416667 30; 589 15.125 -0.208333 30; 590 15.325 -0.208333 30;
    591 15.525 -0.208333 30; 592 15.725 -0.208333 30; 593 15.925 -0.208333 30;
    594 16.125 -0.208333 30; 595 16.325 -0.208333 30; 596 16.525 -0.208333 30;
    597 16.725 -0.208333 30; 598 16.925 -0.208333 30; 599 17.125 -0.208333 30;
    600 17.325 -0.208333 30; 601 17.525 -0.208333 30; 602 17.725 -0.208333 30;
    603 17.925 -0.208333 30; 604 18.125 0 30.2; 605 18.125 0 30.4;
    606 18.125 0 30.6; 607 18.125 0 30.8; 608 18.125 0 31; 609 18.125 0 31.2;
    610 18.125 0 31.4; 611 18.125 0 31.6; 612 18.125 0 31.8; 613 18.125 0 32;
    614 18.125 0 32.2; 615 18.125 0 32.4; 616 18.125 0 32.6; 617 18.125 0 32.8;
    618 18.125 0 33; 619 18.125 -0.208333 33.2; 620 18.125 -0.416667 33.2;
    621 18.125 -0.625 33.2; 622 18.125 -0.833333 33.2; 623 18.125 -1.04167 33.2;
    624 18.125 -1.25 33.2; 625 18.125 -1.45833 33.2; 626 18.125 -1.66667 33.2;
    627 18.125 -1.875 33.2; 628 18.125 -2.08333 33.2; 629 18.125 -2.29167 33.2;
    630 18.125 -2.5 33; 631 18.125 -2.5 32.8; 632 18.125 -2.5 32.6;
    633 18.125 -2.5 32.4; 634 18.125 -2.5 32.2; 635 18.125 -2.5 32;
    636 18.125 -2.5 31.8; 637 18.125 -2.5 31.6; 638 18.125 -2.5 31.4;
    639 18.125 -2.5 31.2; 640 18.125 -2.5 31; 641 18.125 -2.5 30.8;
    642 18.125 -2.5 30.6; 643 18.125 -2.5 30.4; 644 18.125 -2.5 30.2;
    645 18.125 -2.29167 30.2; 646 18.125 -2.29167 30.4; 647 18.125 -2.29167 30.6;
    648 18.125 -2.29167 30.8; 649 18.125 -2.29167 31; 650 18.125 -2.29167 31.2;
    651 18.125 -2.29167 31.4; 652 18.125 -2.29167 31.6; 653 18.125 -2.29167 31.8;
    654 18.125 -2.29167 32; 655 18.125 -2.29167 32.2; 656 18.125 -2.29167 32.4;
    657 18.125 -2.29167 32.6; 658 18.125 -2.29167 32.8; 659 18.125 -2.29167 33;
    660 18.125 -2.08333 30.2; 661 18.125 -2.08333 30.4; 662 18.125 -2.08333 30.6;
    663 18.125 -2.08333 30.8; 664 18.125 -2.08333 31; 665 18.125 -2.08333 31.2;
    666 18.125 -2.08333 31.4; 667 18.125 -2.08333 31.6; 668 18.125 -2.08333 31.8;
    669 18.125 -2.08333 32; 670 18.125 -2.08333 32.2; 671 18.125 -2.08333 32.4;
    672 18.125 -2.08333 32.6; 673 18.125 -2.08333 32.8; 674 18.125 -2.08333 33;
    675 18.125 -1.875 30.2; 676 18.125 -1.875 30.4; 677 18.125 -1.875 30.6;
    678 18.125 -1.875 30.8; 679 18.125 -1.875 31; 680 18.125 -1.875 31.2;
    681 18.125 -1.875 31.4; 682 18.125 -1.875 31.6; 683 18.125 -1.875 31.8;
    684 18.125 -1.875 32; 685 18.125 -1.875 32.2; 686 18.125 -1.875 32.4;
    687 18.125 -1.875 32.6; 688 18.125 -1.875 32.8; 689 18.125 -1.875 33;
    690 18.125 -1.66667 30.2; 691 18.125 -1.66667 30.4; 692 18.125 -1.66667 30.6;
    693 18.125 -1.66667 30.8; 694 18.125 -1.66667 31; 695 18.125 -1.66667 31.2;
    696 18.125 -1.66667 31.4; 697 18.125 -1.66667 31.6; 698 18.125 -1.66667 31.8;
    699 18.125 -1.66667 32; 700 18.125 -1.66667 32.2; 701 18.125 -1.66667 32.4;
    702 18.125 -1.66667 32.6; 703 18.125 -1.66667 32.8; 704 18.125 -1.66667 33;
    705 18.125 -1.45833 30.2; 706 18.125 -1.45833 30.4; 707 18.125 -1.45833 30.6;
    708 18.125 -1.45833 30.8; 709 18.125 -1.45833 31; 710 18.125 -1.45833 31.2;
    711 18.125 -1.45833 31.4; 712 18.125 -1.45833 31.6; 713 18.125 -1.45833 31.8;
    714 18.125 -1.45833 32; 715 18.125 -1.45833 32.2; 716 18.125 -1.45833 32.4;
    717 18.125 -1.45833 32.6; 718 18.125 -1.45833 32.8; 719 18.125 -1.45833 33;
    720 18.125 -1.25 30.2; 721 18.125 -1.25 30.4; 722 18.125 -1.25 30.6;
    723 18.125 -1.25 30.8; 724 18.125 -1.25 31; 725 18.125 -1.25 31.2;
    726 18.125 -1.25 31.4; 727 18.125 -1.25 31.6; 728 18.125 -1.25 31.8;
    729 18.125 -1.25 32; 730 18.125 -1.25 32.2; 731 18.125 -1.25 32.4;
    732 18.125 -1.25 32.6; 733 18.125 -1.25 32.8; 734 18.125 -1.25 33;
    735 18.125 -1.04167 30.2; 736 18.125 -1.04167 30.4; 737 18.125 -1.04167 30.6;
    738 18.125 -1.04167 30.8; 739 18.125 -1.04167 31; 740 18.125 -1.04167 31.2;
    741 18.125 -1.04167 31.4; 742 18.125 -1.04167 31.6; 743 18.125 -1.04167 31.8;
    744 18.125 -1.04167 32; 745 18.125 -1.04167 32.2; 746 18.125 -1.04167 32.4;
    747 18.125 -1.04167 32.6; 748 18.125 -1.04167 32.8; 749 18.125 -1.04167 33;
    750 18.125 -0.833333 30.2; 751 18.125 -0.833333 30.4;
    752 18.125 -0.833333 30.6; 753 18.125 -0.833333 30.8; 754 18.125 -0.833333 31;
    755 18.125 -0.833333 31.2; 756 18.125 -0.833333 31.4;
    757 18.125 -0.833333 31.6; 758 18.125 -0.833333 31.8; 759 18.125 -0.833333 32;
    760 18.125 -0.833333 32.2; 761 18.125 -0.833333 32.4;
    762 18.125 -0.833333 32.6; 763 18.125 -0.833333 32.8; 764 18.125 -0.833333 33;
    765 18.125 -0.625 30.2; 766 18.125 -0.625 30.4; 767 18.125 -0.625 30.6;
    768 18.125 -0.625 30.8; 769 18.125 -0.625 31; 770 18.125 -0.625 31.2;
    771 18.125 -0.625 31.4; 772 18.125 -0.625 31.6; 773 18.125 -0.625 31.8;
    774 18.125 -0.625 32; 775 18.125 -0.625 32.2; 776 18.125 -0.625 32.4;
    777 18.125 -0.625 32.6; 778 18.125 -0.625 32.8; 779 18.125 -0.625 33;
    780 18.125 -0.416667 30.2; 781 18.125 -0.416667 30.4;
    782 18.125 -0.416667 30.6; 783 18.125 -0.416667 30.8; 784 18.125 -0.416667 31;
    785 18.125 -0.416667 31.2; 786 18.125 -0.416667 31.4;
    787 18.125 -0.416667 31.6; 788 18.125 -0.416667 31.8; 789 18.125 -0.416667 32;
    790 18.125 -0.416667 32.2; 791 18.125 -0.416667 32.4;
    792 18.125 -0.416667 32.6; 793 18.125 -0.416667 32.8; 794 18.125 -0.416667 33;
    795 18.125 -0.208333 30.2; 796 18.125 -0.208333 30.4;
    797 18.125 -0.208333 30.6; 798 18.125 -0.208333 30.8; 799 18.125 -0.208333 31;
    800 18.125 -0.208333 31.2; 801 18.125 -0.208333 31.4;
    802 18.125 -0.208333 31.6; 803 18.125 -0.208333 31.8; 804 18.125 -0.208333 32;
    805 18.125 -0.208333 32.2; 806 18.125 -0.208333 32.4;
    807 18.125 -0.208333 32.6; 808 18.125 -0.208333 32.8; 809 18.125 -0.208333 33;
    810 14.925 -2.29167 33.2; 811 14.925 -2.08333 33.2; 812 14.925 -1.875 33.2;
    813 14.925 -1.66667 33.2; 814 14.925 -1.45833 33.2; 815 14.925 -1.25 33.2;
    816 14.925 -1.04167 33.2; 817 14.925 -0.833333 33.2; 818 14.925 -0.625 33.2;
    819 14.925 -0.416667 33.2; 820 14.925 -0.208333 33.2; 821 15.125 0 33.2;
    822 15.325 0 33.2; 823 15.525 0 33.2; 824 15.725 0 33.2; 825 15.925 0 33.2;
    826 16.125 0 33.2; 827 16.325 0 33.2; 828 16.525 0 33.2; 829 16.725 0 33.2;
    830 16.925 0 33.2; 831 17.125 0 33.2; 832 17.325 0 33.2; 833 17.525 0 33.2;
    834 17.725 0 33.2; 835 17.925 0 33.2; 836 17.925 -2.5 33.2;
    837 17.725 -2.5 33.2; 838 17.525 -2.5 33.2; 839 17.325 -2.5 33.2;
    840 17.125 -2.5 33.2; 841 16.925 -2.5 33.2; 842 16.725 -2.5 33.2;
    843 16.525 -2.5 33.2; 844 16.325 -2.5 33.2; 845 16.125 -2.5 33.2;
    846 15.925 -2.5 33.2; 847 15.725 -2.5 33.2; 848 15.525 -2.5 33.2;
    849 15.325 -2.5 33.2; 850 15.125 -2.5 33.2; 851 15.125 -2.29167 33.2;
    852 15.325 -2.29167 33.2; 853 15.525 -2.29167 33.2; 854 15.725 -2.29167 33.2;
    855 15.925 -2.29167 33.2; 856 16.125 -2.29167 33.2; 857 16.325 -2.29167 33.2;
    858 16.525 -2.29167 33.2; 859 16.725 -2.29167 33.2; 860 16.925 -2.29167 33.2;
    861 17.125 -2.29167 33.2; 862 17.325 -2.29167 33.2; 863 17.525 -2.29167 33.2;
    864 17.725 -2.29167 33.2; 865 17.925 -2.29167 33.2; 866 15.125 -2.08333 33.2;
    867 15.325 -2.08333 33.2; 868 15.525 -2.08333 33.2; 869 15.725 -2.08333 33.2;
    870 15.925 -2.08333 33.2; 871 16.125 -2.08333 33.2; 872 16.325 -2.08333 33.2;
    873 16.525 -2.08333 33.2; 874 16.725 -2.08333 33.2; 875 16.925 -2.08333 33.2;
    876 17.125 -2.08333 33.2; 877 17.325 -2.08333 33.2; 878 17.525 -2.08333 33.2;
    879 17.725 -2.08333 33.2; 880 17.925 -2.08333 33.2; 881 15.125 -1.875 33.2;
    882 15.325 -1.875 33.2; 883 15.525 -1.875 33.2; 884 15.725 -1.875 33.2;
    885 15.925 -1.875 33.2; 886 16.125 -1.875 33.2; 887 16.325 -1.875 33.2;
    888 16.525 -1.875 33.2; 889 16.725 -1.875 33.2; 890 16.925 -1.875 33.2;
    891 17.125 -1.875 33.2; 892 17.325 -1.875 33.2; 893 17.525 -1.875 33.2;
    894 17.725 -1.875 33.2; 895 17.925 -1.875 33.2; 896 15.125 -1.66667 33.2;
    897 15.325 -1.66667 33.2; 898 15.525 -1.66667 33.2; 899 15.725 -1.66667 33.2;
    900 15.925 -1.66667 33.2; 901 16.125 -1.66667 33.2; 902 16.325 -1.66667 33.2;
    903 16.525 -1.66667 33.2; 904 16.725 -1.66667 33.2; 905 16.925 -1.66667 33.2;
    906 17.125 -1.66667 33.2; 907 17.325 -1.66667 33.2; 908 17.525 -1.66667 33.2;
    909 17.725 -1.66667 33.2; 910 17.925 -1.66667 33.2; 911 15.125 -1.45833 33.2;
    912 15.325 -1.45833 33.2; 913 15.525 -1.45833 33.2; 914 15.725 -1.45833 33.2;
    915 15.925 -1.45833 33.2; 916 16.125 -1.45833 33.2; 917 16.325 -1.45833 33.2;
    918 16.525 -1.45833 33.2; 919 16.725 -1.45833 33.2; 920 16.925 -1.45833 33.2;
    921 17.125 -1.45833 33.2; 922 17.325 -1.45833 33.2; 923 17.525 -1.45833 33.2;
    924 17.725 -1.45833 33.2; 925 17.925 -1.45833 33.2; 926 15.125 -1.25 33.2;
    927 15.325 -1.25 33.2; 928 15.525 -1.25 33.2; 929 15.725 -1.25 33.2;
    930 15.925 -1.25 33.2; 931 16.125 -1.25 33.2; 932 16.325 -1.25 33.2;
    933 16.525 -1.25 33.2; 934 16.725 -1.25 33.2; 935 16.925 -1.25 33.2;
    936 17.125 -1.25 33.2; 937 17.325 -1.25 33.2; 938 17.525 -1.25 33.2;
    939 17.725 -1.25 33.2; 940 17.925 -1.25 33.2; 941 15.125 -1.04167 33.2;
    942 15.325 -1.04167 33.2; 943 15.525 -1.04167 33.2; 944 15.725 -1.04167 33.2;
    945 15.925 -1.04167 33.2; 946 16.125 -1.04167 33.2; 947 16.325 -1.04167 33.2;
    948 16.525 -1.04167 33.2; 949 16.725 -1.04167 33.2; 950 16.925 -1.04167 33.2;
    951 17.125 -1.04167 33.2; 952 17.325 -1.04167 33.2; 953 17.525 -1.04167 33.2;
    954 17.725 -1.04167 33.2; 955 17.925 -1.04167 33.2; 956 15.125 -0.833333 33.2;
    957 15.325 -0.833333 33.2; 958 15.525 -0.833333 33.2;
    959 15.725 -0.833333 33.2; 960 15.925 -0.833333 33.2;
    961 16.125 -0.833333 33.2; 962 16.325 -0.833333 33.2;
    963 16.525 -0.833333 33.2; 964 16.725 -0.833333 33.2;
    965 16.925 -0.833333 33.2; 966 17.125 -0.833333 33.2;
    967 17.325 -0.833333 33.2; 968 17.525 -0.833333 33.2;
    969 17.725 -0.833333 33.2; 970 17.925 -0.833333 33.2; 971 15.125 -0.625 33.2;
    972 15.325 -0.625 33.2; 973 15.525 -0.625 33.2; 974 15.725 -0.625 33.2;
    975 15.925 -0.625 33.2; 976 16.125 -0.625 33.2; 977 16.325 -0.625 33.2;
    978 16.525 -0.625 33.2; 979 16.725 -0.625 33.2; 980 16.925 -0.625 33.2;
    981 17.125 -0.625 33.2; 982 17.325 -0.625 33.2; 983 17.525 -0.625 33.2;
    984 17.725 -0.625 33.2; 985 17.925 -0.625 33.2; 986 15.125 -0.416667 33.2;
    987 15.325 -0.416667 33.2; 988 15.525 -0.416667 33.2;
    989 15.725 -0.416667 33.2; 990 15.925 -0.416667 33.2;
    991 16.125 -0.416667 33.2; 992 16.325 -0.416667 33.2;
    993 16.525 -0.416667 33.2; 994 16.725 -0.416667 33.2;
    995 16.925 -0.416667 33.2; 996 17.125 -0.416667 33.2;
    997 17.325 -0.416667 33.2; 998 17.525 -0.416667 33.2;
    999 17.725 -0.416667 33.2; 1000 17.925 -0.416667 33.2;
    1001 15.125 -0.208333 33.2; 1002 15.325 -0.208333 33.2;
    1003 15.525 -0.208333 33.2; 1004 15.725 -0.208333 33.2;
    1005 15.925 -0.208333 33.2; 1006 16.125 -0.208333 33.2;
    1007 16.325 -0.208333 33.2; 1008 16.525 -0.208333 33.2;
    1009 16.725 -0.208333 33.2; 1010 16.925 -0.208333 33.2;
    1011 17.125 -0.208333 33.2; 1012 17.325 -0.208333 33.2;
    1013 17.525 -0.208333 33.2; 1014 17.725 -0.208333 33.2;
    1015 17.925 -0.208333 33.2; 1016 14.925 2.75 30; 1017 15.1116 5.5 30;
    1018 15.2982 5.5 30; 1019 15.4848 5.5 30; 1020 15.6714 5.5 30;
    1021 15.858 5.5 30; 1022 16.0446 5.5 30; 1023 16.2313 5.5 30;
    1024 16.4179 5.5 30; 1025 16.6045 5.5 30; 1026 16.7911 5.5 30;
    1027 16.9777 5.5 30; 1028 17.1643 5.5 30; 1029 17.3509 5.5 30;
    1030 18.125 5.30357 30; 1031 18.125 5.10714 30; 1032 18.125 4.91071 30;
    1033 18.125 4.71429 30; 1034 18.125 4.51786 30; 1035 18.125 4.32143 30;
    1036 18.125 4.125 30; 1037 18.125 3.92857 30; 1038 18.125 3.73214 30;
    1039 18.125 3.53571 30; 1040 18.125 3.33929 30; 1041 18.125 3.14286 30;
    1042 18.125 2.94643 30; 1043 18.125 2.75 30; 1044 18.125 2.55357 30;
    1045 18.125 2.35714 30; 1046 18.125 2.16071 30; 1047 18.125 1.96429 30;
    1048 18.125 1.76786 30; 1049 18.125 1.57143 30; 1050 18.125 1.375 30;
    1051 18.125 1.17857 30; 1052 18.125 0.982143 30; 1053 18.125 0.785714 30;
    1054 18.125 0.589286 30; 1055 18.125 0.392857 30; 1056 18.125 0.196429 30;
    1057 17.3051 3.37449 30; 1058 17.5541 2.40047 30; 1059 17.5588 1.23819 30;
    1060 17.5613 1.58503 30; 1061 17.8749 4.95632 30; 1062 17.843 1.27655 30;
    1063 17.8026 3.62761 30; 1064 17.1931 3.76298 30; 1065 17.8467 1.11855 30;
    1066 16.5999 4.77182 30; 1067 17.7021 3.82589 30; 1068 17.648 3.67867 30;
    1069 15.4743 5.27575 30; 1070 15.797 5.36928 30; 1071 16.215 2.67298 30;
    1072 17.9941 0.176415 30; 1073 16.5587 0.889489 30; 1074 17.5825 4.643 30;
    1075 17.873 2.35871 30; 1076 17.4796 0.554409 30; 1077 16.9979 1.17037 30;
    1078 16.3107 1.01736 30; 1079 17.7985 0.593651 30; 1080 15.852 3.91884 30;
    1081 17.7555 5.02621 30; 1082 17.7018 4.8591 30; 1083 17.955 2.17111 30;
    1084 17.2266 4.52868 30; 1085 17.7123 4.95234 30; 1086 17.8609 5.05462 30;
    1087 17.7184 5.24243 30; 1088 17.6392 0.375696 30; 1089 17.3874 4.64827 30;
    1090 16.8688 0.640322 30; 1091 16.9368 2.05028 30; 1092 16.972 1.60497 30;
    1093 16.9854 2.43048 30; 1094 17.9681 1.23688 30; 1095 18.0112 0.362942 30;
    1096 17.8681 0.781209 30; 1097 16.7814 1.14039 30; 1098 17.6547 4.42796 30;
    1099 17.2858 0.238766 30; 1100 17.9674 0.862606 30; 1101 16.8265 5.33377 30;
    1102 17.0281 5.2725 30; 1103 17.9499 4.37149 30; 1104 17.9876 4.18349 30;
    1105 17.2442 4.61006 30; 1106 16.8867 2.66447 30; 1107 17.9081 0.610853 30;
    1108 17.1064 4.57865 30; 1109 17.9629 1.43265 30; 1110 17.8335 4.86681 30;
    1111 17.6249 4.96035 30; 1112 16.638 5.36856 30; 1113 17.683 5.00432 30;
    1114 17.7363 4.82512 30; 1115 17.2063 0.683957 30; 1116 16.6247 0.505332 30;
    1117 17.9848 1.06622 30; 1118 17.9906 4.89704 30; 1119 17.6287 5.05487 30;
    1120 17.3379 4.56444 30; 1121 16.9494 0.777899 30; 1122 17.6605 4.77316 30;
    1123 17.7697 4.89233 30; 1124 17.3339 4.87795 30; 1125 17.5049 0.718121 30;
    1126 16.8276 4.33643 30; 1127 17.6365 0.276773 30; 1128 17.4612 0.931546 30;
    1129 16.9757 4.25495 30; 1130 17.5149 2.13698 30; 1131 17.6083 1.99929 30;
    1132 17.388 4.47804 30; 1133 15.9644 0.196379 30; 1134 16.929 4.5234 30;
    1135 17.2271 1.90948 30; 1136 16.9817 3.81757 30; 1137 16.7643 4.65186 30;
    1138 17.6916 3.43989 30; 1139 17.6576 3.98214 30; 1140 16.1519 4.70127 30;
    1141 17.2998 4.6741 30; 1142 17.4119 0.705189 30; 1143 17.8875 4.55239 30;
    1144 17.3967 2.89712 30; 1145 16.0308 1.185 30; 1146 17.3567 2.24509 30;
    1147 17.7292 4.65541 30; 1148 16.2494 5.17298 30; 1149 16.008 5.24809 30;
    1150 17.5988 4.1116 30; 1151 17.3545 2.55274 30; 1152 17.4954 4.15121 30;
    1153 15.8673 5.00861 30; 1154 17.4512 4.85582 30; 1155 17.8594 3.81005 30;
    1156 17.6923 4.08124 30; 1157 17.9413 5.2089 30; 1158 16.8584 0.940548 30;
    1159 16.5296 5.18729 30; 1160 17.8989 4.83952 30; 1161 17.8726 0.46495 30;
    1162 17.1659 2.61514 30; 1163 17.4974 0.277659 30; 1164 16.8162 5.21206 30;
    1165 17.5631 4.51483 30; 1166 16.1671 3.50859 30; 1167 16.6532 4.02058 30;
    1168 17.4051 3.97412 30; 1169 16.4254 5.32183 30; 1170 17.8731 3.14823 30;
    1171 15.7862 2.83094 30; 1172 16.8348 0.438313 30; 1173 17.8378 0.53466 30;
    1174 17.8826 0.252813 30; 1175 17.9302 4.71111 30; 1176 17.7556 4.45483 30;
    1177 17.4834 0.162536 30; 1178 17.4245 0.538571 30; 1179 17.7787 0.1826 30;
    1180 17.5796 5.19308 30; 1181 17.1325 4.70855 30; 1182 18.0169 0.716727 30;
    1183 16.571 2.70591 30; 1184 17.5851 0.548341 30; 1185 16.6694 4.41057 30;
    1186 16.909 4.98546 30; 1187 16.793 1.47255 30; 1188 17.0003 0.467415 30;
    1189 17.9095 5.35622 30; 1190 17.2083 5.31342 30; 1191 17.9233 1.66331 30;
    1192 17.2499 5.14541 30; 1193 17.9985 0.537353 30; 1194 17.4255 0.473141 30;
    1195 17.5256 0.380355 30; 1196 16.5436 3.1801 30; 1197 17.9906 5.06489 30;
    1198 16.8691 4.11112 30; 1199 17.8034 5.15716 30; 1200 17.0508 4.98479 30;
    1201 17.6148 5.35633 30; 1202 16.9775 0.60215 30; 1203 17.3631 0.527855 30;
    1204 17.2947 4.42903 30; 1205 17.1463 0.167878 30; 1206 17.6285 0.737876 30;
    1207 17.2505 4.18107 30; 1208 17.6521 4.33371 30; 1209 16.7527 2.32413 30;
    1210 17.2471 0.586784 30; 1211 17.2271 1.15521 30; 1212 17.249 4.29956 30;
    1213 17.1608 4.18364 30; 1214 17.0984 1.79179 30; 1215 15.819 0.369919 30;
    1216 17.0315 2.20013 30; 1217 17.4937 3.55238 30; 1218 16.5752 0.236481 30;
    1219 17.254 4.79799 30; 1220 17.7768 4.95871 30; 1221 17.6262 1.46447 30;
    1222 17.3803 5.13256 30; 1223 17.9126 2.87418 30; 1224 17.7821 0.977656 30;
    1225 16.6681 5.21576 30; 1226 17.4654 4.42302 30; 1227 17.3771 3.78715 30;
    1228 16.3781 1.45982 30; 1229 17.3952 1.46356 30; 1230 17.3581 0.431268 30;
    1231 17.9931 2.01555 30; 1232 17.1221 0.550569 30; 1233 17.3381 0.611173 30;
    1234 17.2785 0.399762 30; 1235 17.2657 1.35887 30; 1236 17.4223 5.29793 30;
    1237 15.3858 3.1559 30; 1238 17.0971 4.29199 30; 1239 16.7979 5.07559 30;
    1240 15.6031 2.35335 30; 1241 17.7648 2.63007 30; 1242 15.3854 4.53702 30;
    1243 17.7656 1.58828 30; 1244 16.9569 5.1455 30; 1245 17.1808 1.65842 30;
    1246 17.4536 1.06348 30; 1247 17.4841 0.480022 30; 1248 16.9892 3.4946 30;
    1249 16.7375 0.764799 30; 1250 17.926 0.706098 30; 1251 17.8336 0.678827 30;
    1252 17.9955 3.9762 30; 1253 16.312 4.06373 30; 1254 16.9612 1.33464 30;
    1255 17.1178 1.41153 30; 1256 17.4348 4.28028 30; 1257 17.5727 1.76554 30;
    1258 17.6623 4.55985 30; 1259 17.1131 1.23109 30; 1260 16.4197 4.49243 30;
    1261 16.7948 0.232922 30; 1262 17.3716 1.89108 30; 1263 17.318 0.681323 30;
    1264 16.74 4.89712 30; 1265 17.4988 1.92952 30; 1266 17.743 4.26669 30;
    1267 16.6359 3.65793 30; 1268 15.9408 4.39746 30; 1269 17.7214 0.823566 30;
    1270 17.532 3.80947 30; 1271 17.0415 1.04755 30; 1272 17.0892 0.906735 30;
    1273 17.3755 2.01431 30; 1274 17.0272 4.00328 30; 1275 17.307 4.24755 30;
    1276 17.3526 4.16674 30; 1277 15.6532 5.2838 30; 1278 17.1828 2.33136 30;
    1279 17.5556 3.93583 30; 1280 16.6035 1.30671 30; 1281 17.7428 0.423629 30;
    1282 17.585 4.9018 30; 1283 17.2043 4.35774 30; 1284 17.3623 4.36315 30;
    1285 17.733 1.17453 30; 1286 17.1968 4.01616 30; 1287 17.769 2.08528 30;
    1288 16.4626 4.97706 30; 1289 17.058 0.693832 30; 1290 16.9815 4.82393 30;
    1291 17.6934 5.10943 30; 1292 16.6537 5.01565 30; 1293 17.6473 4.88898 30;
    1294 16.3698 0.642748 30; 1295 17.5669 4.83072 30; 1296 17.2716 1.0175 30;
    1297 17.4431 0.814955 30; 1298 17.48 0.63691 30; 1299 17.6171 0.467112 30;
    1300 17.8268 1.40369 30; 1301 17.5515 0.476232 30; 1302 17.4721 4.70936 30;
    1303 16.9735 4.68826 30; 1304 17.4881 1.38513 30; 1305 17.966 3.56558 30;
    1306 17.4255 1.75409 30; 1307 17.0629 2.95232 30; 1308 17.541 0.792165 30;
    1309 16.5982 2.00709 30; 1310 17.0645 4.42929 30; 1311 17.2714 1.53617 30;
    1312 17.0269 0.265519 30; 1313 17.5531 4.32562 30; 1314 17.0951 4.84339 30;
    1315 17.6807 1.32037 30; 1316 17.5171 4.93321 30; 1317 17.7137 4.90546 30;
    1318 17.2978 0.896331 30; 1319 16.2686 0.416275 30; 1320 17.8467 3.98895 30;
    1321 17.8101 4.7516 30; 1322 17.3942 4.99443 30; 1323 17.179 0.421731 30;
    1324 17.6356 3.01129 30; 1325 17.6428 4.83592 30; 1326 17.6202 0.602648 30;
    1327 17.7016 0.673288 30; 1328 17.6608 4.93256 30; 1329 16.5391 1.69165 30;
    1330 17.5904 4.25329 30; 1331 16.4055 0.163955 30; 1332 17.3896 0.632387 30;
    1333 16.1577 1.84945 30; 1334 17.2018 4.91862 30; 1335 15.8054 1.5249 30;
    1336 17.49 5.0157 30; 1337 16.2178 0.234863 30; 1338 17.5339 0.555905 30;
    1339 17.3769 0.581041 30; 1340 16.8308 4.79184 30; 1341 17.7218 0.577219 30;
    1342 17.8767 1.8935 30; 1343 17.7286 3.93583 30; 1344 17.9892 3.77253 30;
    1345 17.1534 0.798599 30; 1346 17.8933 0.363469 30; 1347 17.0681 4.1592 30;
    1348 15.9956 2.33334 30; 1349 17.6712 0.52252 30; 1350 17.1388 5.08154 30;
    1351 17.7673 0.520775 30; 1352 17.3971 0.321733 30; 1353 16.7617 2.07227 30;
    1354 17.6404 0.141911 30; 1355 17.3891 4.76008 30; 1356 16.7875 1.81428 30;
    1357 17.0017 1.90213 30; 1358 17.4548 0.402086 30; 1359 17.3061 0.779396 30;
    1360 17.4181 0.596717 30; 1361 17.588 0.903982 30; 1362 17.2993 0.546105 30;
    1363 16.9489 4.39399 30; 1364 16.3971 2.23226 30; 1365 17.2948 4.98401 30;
    1366 17.5562 0.647746 30; 1367 17.5143 5.10428 30; 1368 17.5693 4.99561 30;
    1369 16.051 0.676398 30; 1370 15.5339 4.95406 30; 1371 17.3773 1.31502 30;
    1372 15.621 0.641172 30; 1373 17.8089 4.16444 30; 1374 17.7503 0.317016 30;
    1375 17.7307 1.81213 30; 1376 17.4809 4.59061 30; 1377 17.5957 3.25071 30;
    1378 17.3887 1.18603 30; 1379 17.1839 2.06417 30; 1380 17.5451 4.75382 30;
    1381 17.3063 4.08468 30; 1382 17.1645 4.43247 30; 1383 17.6887 2.24881 30;
    1384 17.6042 1.08169 30; 1385 17.4 1.62751 30; 1386 17.2915 1.73697 30;
    1387 17.922 3.35843 30; 1388 15.4101 1.06509 30; 1389 18.125 5.5 30.2;
    1390 18.125 5.5 30.4; 1391 18.125 5.5 30.6; 1392 18.125 5.5 30.8;
    1393 18.125 5.5 31; 1394 18.125 5.5 31.2; 1395 18.125 5.5 31.4;
    1396 18.125 5.5 31.6; 1397 18.125 5.5 31.8; 1398 18.125 5.5 32;
    1399 18.125 5.5 32.2; 1400 18.125 5.5 32.4; 1401 18.125 5.5 32.6;
    1402 18.125 5.5 32.8; 1403 18.125 5.5 33; 1404 18.125 5.30357 33.2;
    1405 18.125 5.10714 33.2; 1406 18.125 4.91071 33.2; 1407 18.125 4.71429 33.2;
    1408 18.125 4.51786 33.2; 1409 18.125 4.32143 33.2; 1410 18.125 4.125 33.2;
    1411 18.125 3.92857 33.2; 1412 18.125 3.73214 33.2; 1413 18.125 3.53571 33.2;
    1414 18.125 3.33929 33.2; 1415 18.125 3.14286 33.2; 1416 18.125 2.94643 33.2;
    1417 18.125 2.75 33.2; 1418 18.125 2.55357 33.2; 1419 18.125 2.35714 33.2;
    1420 18.125 2.16071 33.2; 1421 18.125 1.96429 33.2; 1422 18.125 1.76786 33.2;
    1423 18.125 1.57143 33.2; 1424 18.125 1.375 33.2; 1425 18.125 1.17857 33.2;
    1426 18.125 0.982143 33.2; 1427 18.125 0.785714 33.2;
    1428 18.125 0.589286 33.2; 1429 18.125 0.392857 33.2;
    1430 18.125 0.196429 33.2; 1431 18.125 0.196429 30.2;
    1432 18.125 0.196429 30.4; 1433 18.125 0.196429 30.6;
    1434 18.125 0.196429 30.8; 1435 18.125 0.196429 31; 1436 18.125 0.196429 31.2;
    1437 18.125 0.196429 31.4; 1438 18.125 0.196429 31.6;
    1439 18.125 0.196429 31.8; 1440 18.125 0.196429 32; 1441 18.125 0.196429 32.2;
    1442 18.125 0.196429 32.4; 1443 18.125 0.196429 32.6;
    1444 18.125 0.196429 32.8; 1445 18.125 0.196429 33; 1446 18.125 0.392857 30.2;
    1447 18.125 0.392857 30.4; 1448 18.125 0.392857 30.6;
    1449 18.125 0.392857 30.8; 1450 18.125 0.392857 31; 1451 18.125 0.392857 31.2;
    1452 18.125 0.392857 31.4; 1453 18.125 0.392857 31.6;
    1454 18.125 0.392857 31.8; 1455 18.125 0.392857 32; 1456 18.125 0.392857 32.2;
    1457 18.125 0.392857 32.4; 1458 18.125 0.392857 32.6;
    1459 18.125 0.392857 32.8; 1460 18.125 0.392857 33; 1461 18.125 0.589286 30.2;
    1462 18.125 0.589286 30.4; 1463 18.125 0.589286 30.6;
    1464 18.125 0.589286 30.8; 1465 18.125 0.589286 31; 1466 18.125 0.589286 31.2;
    1467 18.125 0.589286 31.4; 1468 18.125 0.589286 31.6;
    1469 18.125 0.589286 31.8; 1470 18.125 0.589286 32; 1471 18.125 0.589286 32.2;
    1472 18.125 0.589286 32.4; 1473 18.125 0.589286 32.6;
    1474 18.125 0.589286 32.8; 1475 18.125 0.589286 33; 1476 18.125 0.785714 30.2;
    1477 18.125 0.785714 30.4; 1478 18.125 0.785714 30.6;
    1479 18.125 0.785714 30.8; 1480 18.125 0.785714 31; 1481 18.125 0.785714 31.2;
    1482 18.125 0.785714 31.4; 1483 18.125 0.785714 31.6;
    1484 18.125 0.785714 31.8; 1485 18.125 0.785714 32; 1486 18.125 0.785714 32.2;
    1487 18.125 0.785714 32.4; 1488 18.125 0.785714 32.6;
    1489 18.125 0.785714 32.8; 1490 18.125 0.785714 33; 1491 18.125 0.982143 30.2;
    1492 18.125 0.982143 30.4; 1493 18.125 0.982143 30.6;
    1494 18.125 0.982143 30.8; 1495 18.125 0.982143 31; 1496 18.125 0.982143 31.2;
    1497 18.125 0.982143 31.4; 1498 18.125 0.982143 31.6;
    1499 18.125 0.982143 31.8; 1500 18.125 0.982143 32; 1501 18.125 0.982143 32.2;
    1502 18.125 0.982143 32.4; 1503 18.125 0.982143 32.6;
    1504 18.125 0.982143 32.8; 1505 18.125 0.982143 33; 1506 18.125 1.17857 30.2;
    1507 18.125 1.17857 30.4; 1508 18.125 1.17857 30.6; 1509 18.125 1.17857 30.8;
    1510 18.125 1.17857 31; 1511 18.125 1.17857 31.2; 1512 18.125 1.17857 31.4;
    1513 18.125 1.17857 31.6; 1514 18.125 1.17857 31.8; 1515 18.125 1.17857 32;
    1516 18.125 1.17857 32.2; 1517 18.125 1.17857 32.4; 1518 18.125 1.17857 32.6;
    1519 18.125 1.17857 32.8; 1520 18.125 1.17857 33; 1521 18.125 1.375 30.2;
    1522 18.125 1.375 30.4; 1523 18.125 1.375 30.6; 1524 18.125 1.375 30.8;
    1525 18.125 1.375 31; 1526 18.125 1.375 31.2; 1527 18.125 1.375 31.4;
    1528 18.125 1.375 31.6; 1529 18.125 1.375 31.8; 1530 18.125 1.375 32;
    1531 18.125 1.375 32.2; 1532 18.125 1.375 32.4; 1533 18.125 1.375 32.6;
    1534 18.125 1.375 32.8; 1535 18.125 1.375 33; 1536 18.125 1.57143 30.2;
    1537 18.125 1.57143 30.4; 1538 18.125 1.57143 30.6; 1539 18.125 1.57143 30.8;
    1540 18.125 1.57143 31; 1541 18.125 1.57143 31.2; 1542 18.125 1.57143 31.4;
    1543 18.125 1.57143 31.6; 1544 18.125 1.57143 31.8; 1545 18.125 1.57143 32;
    1546 18.125 1.57143 32.2; 1547 18.125 1.57143 32.4; 1548 18.125 1.57143 32.6;
    1549 18.125 1.57143 32.8; 1550 18.125 1.57143 33; 1551 18.125 1.76786 30.2;
    1552 18.125 1.76786 30.4; 1553 18.125 1.76786 30.6; 1554 18.125 1.76786 30.8;
    1555 18.125 1.76786 31; 1556 18.125 1.76786 31.2; 1557 18.125 1.76786 31.4;
    1558 18.125 1.76786 31.6; 1559 18.125 1.76786 31.8; 1560 18.125 1.76786 32;
    1561 18.125 1.76786 32.2; 1562 18.125 1.76786 32.4; 1563 18.125 1.76786 32.6;
    1564 18.125 1.76786 32.8; 1565 18.125 1.76786 33; 1566 18.125 1.96429 30.2;
    1567 18.125 1.96429 30.4; 1568 18.125 1.96429 30.6; 1569 18.125 1.96429 30.8;
    1570 18.125 1.96429 31; 1571 18.125 1.96429 31.2; 1572 18.125 1.96429 31.4;
    1573 18.125 1.96429 31.6; 1574 18.125 1.96429 31.8; 1575 18.125 1.96429 32;
    1576 18.125 1.96429 32.2; 1577 18.125 1.96429 32.4; 1578 18.125 1.96429 32.6;
    1579 18.125 1.96429 32.8; 1580 18.125 1.96429 33; 1581 18.125 2.16071 30.2;
    1582 18.125 2.16071 30.4; 1583 18.125 2.16071 30.6; 1584 18.125 2.16071 30.8;
    1585 18.125 2.16071 31; 1586 18.125 2.16071 31.2; 1587 18.125 2.16071 31.4;
    1588 18.125 2.16071 31.6; 1589 18.125 2.16071 31.8; 1590 18.125 2.16071 32;
    1591 18.125 2.16071 32.2; 1592 18.125 2.16071 32.4; 1593 18.125 2.16071 32.6;
    1594 18.125 2.16071 32.8; 1595 18.125 2.16071 33; 1596 18.125 2.35714 30.2;
    1597 18.125 2.35714 30.4; 1598 18.125 2.35714 30.6; 1599 18.125 2.35714 30.8;
    1600 18.125 2.35714 31; 1601 18.125 2.35714 31.2; 1602 18.125 2.35714 31.4;
    1603 18.125 2.35714 31.6; 1604 18.125 2.35714 31.8; 1605 18.125 2.35714 32;
    1606 18.125 2.35714 32.2; 1607 18.125 2.35714 32.4; 1608 18.125 2.35714 32.6;
    1609 18.125 2.35714 32.8; 1610 18.125 2.35714 33; 1611 18.125 2.55357 30.2;
    1612 18.125 2.55357 30.4; 1613 18.125 2.55357 30.6; 1614 18.125 2.55357 30.8;
    1615 18.125 2.55357 31; 1616 18.125 2.55357 31.2; 1617 18.125 2.55357 31.4;
    1618 18.125 2.55357 31.6; 1619 18.125 2.55357 31.8; 1620 18.125 2.55357 32;
    1621 18.125 2.55357 32.2; 1622 18.125 2.55357 32.4; 1623 18.125 2.55357 32.6;
    1624 18.125 2.55357 32.8; 1625 18.125 2.55357 33; 1626 18.125 2.75 30.2;
    1627 18.125 2.75 30.4; 1628 18.125 2.75 30.6; 1629 18.125 2.75 30.8;
    1630 18.125 2.75 31; 1631 18.125 2.75 31.2; 1632 18.125 2.75 31.4;
    1633 18.125 2.75 31.6; 1634 18.125 2.75 31.8; 1635 18.125 2.75 32;
    1636 18.125 2.75 32.2; 1637 18.125 2.75 32.4; 1638 18.125 2.75 32.6;
    1639 18.125 2.75 32.8; 1640 18.125 2.75 33; 1641 18.125 2.94643 30.2;
    1642 18.125 2.94643 30.4; 1643 18.125 2.94643 30.6; 1644 18.125 2.94643 30.8;
    1645 18.125 2.94643 31; 1646 18.125 2.94643 31.2; 1647 18.125 2.94643 31.4;
    1648 18.125 2.94643 31.6; 1649 18.125 2.94643 31.8; 1650 18.125 2.94643 32;
    1651 18.125 2.94643 32.2; 1652 18.125 2.94643 32.4; 1653 18.125 2.94643 32.6;
    1654 18.125 2.94643 32.8; 1655 18.125 2.94643 33; 1656 18.125 3.14286 30.2;
    1657 18.125 3.14286 30.4; 1658 18.125 3.14286 30.6; 1659 18.125 3.14286 30.8;
    1660 18.125 3.14286 31; 1661 18.125 3.14286 31.2; 1662 18.125 3.14286 31.4;
    1663 18.125 3.14286 31.6; 1664 18.125 3.14286 31.8; 1665 18.125 3.14286 32;
    1666 18.125 3.14286 32.2; 1667 18.125 3.14286 32.4; 1668 18.125 3.14286 32.6;
    1669 18.125 3.14286 32.8; 1670 18.125 3.14286 33; 1671 18.125 3.33929 30.2;
    1672 18.125 3.33929 30.4; 1673 18.125 3.33929 30.6; 1674 18.125 3.33929 30.8;
    1675 18.125 3.33929 31; 1676 18.125 3.33929 31.2; 1677 18.125 3.33929 31.4;
    1678 18.125 3.33929 31.6; 1679 18.125 3.33929 31.8; 1680 18.125 3.33929 32;
    1681 18.125 3.33929 32.2; 1682 18.125 3.33929 32.4; 1683 18.125 3.33929 32.6;
    1684 18.125 3.33929 32.8; 1685 18.125 3.33929 33; 1686 18.125 3.53571 30.2;
    1687 18.125 3.53571 30.4; 1688 18.125 3.53571 30.6; 1689 18.125 3.53571 30.8;
    1690 18.125 3.53571 31; 1691 18.125 3.53571 31.2; 1692 18.125 3.53571 31.4;
    1693 18.125 3.53571 31.6; 1694 18.125 3.53571 31.8; 1695 18.125 3.53571 32;
    1696 18.125 3.53571 32.2; 1697 18.125 3.53571 32.4; 1698 18.125 3.53571 32.6;
    1699 18.125 3.53571 32.8; 1700 18.125 3.53571 33; 1701 18.125 3.73214 30.2;
    1702 18.125 3.73214 30.4; 1703 18.125 3.73214 30.6; 1704 18.125 3.73214 30.8;
    1705 18.125 3.73214 31; 1706 18.125 3.73214 31.2; 1707 18.125 3.73214 31.4;
    1708 18.125 3.73214 31.6; 1709 18.125 3.73214 31.8; 1710 18.125 3.73214 32;
    1711 18.125 3.73214 32.2; 1712 18.125 3.73214 32.4; 1713 18.125 3.73214 32.6;
    1714 18.125 3.73214 32.8; 1715 18.125 3.73214 33; 1716 18.125 3.92857 30.2;
    1717 18.125 3.92857 30.4; 1718 18.125 3.92857 30.6; 1719 18.125 3.92857 30.8;
    1720 18.125 3.92857 31; 1721 18.125 3.92857 31.2; 1722 18.125 3.92857 31.4;
    1723 18.125 3.92857 31.6; 1724 18.125 3.92857 31.8; 1725 18.125 3.92857 32;
    1726 18.125 3.92857 32.2; 1727 18.125 3.92857 32.4; 1728 18.125 3.92857 32.6;
    1729 18.125 3.92857 32.8; 1730 18.125 3.92857 33; 1731 18.125 4.125 30.2;
    1732 18.125 4.125 30.4; 1733 18.125 4.125 30.6; 1734 18.125 4.125 30.8;
    1735 18.125 4.125 31; 1736 18.125 4.125 31.2; 1737 18.125 4.125 31.4;
    1738 18.125 4.125 31.6; 1739 18.125 4.125 31.8; 1740 18.125 4.125 32;
    1741 18.125 4.125 32.2; 1742 18.125 4.125 32.4; 1743 18.125 4.125 32.6;
    1744 18.125 4.125 32.8; 1745 18.125 4.125 33; 1746 18.125 4.32143 30.2;
    1747 18.125 4.32143 30.4; 1748 18.125 4.32143 30.6; 1749 18.125 4.32143 30.8;
    1750 18.125 4.32143 31; 1751 18.125 4.32143 31.2; 1752 18.125 4.32143 31.4;
    1753 18.125 4.32143 31.6; 1754 18.125 4.32143 31.8; 1755 18.125 4.32143 32;
    1756 18.125 4.32143 32.2; 1757 18.125 4.32143 32.4; 1758 18.125 4.32143 32.6;
    1759 18.125 4.32143 32.8; 1760 18.125 4.32143 33; 1761 18.125 4.51786 30.2;
    1762 18.125 4.51786 30.4; 1763 18.125 4.51786 30.6; 1764 18.125 4.51786 30.8;
    1765 18.125 4.51786 31; 1766 18.125 4.51786 31.2; 1767 18.125 4.51786 31.4;
    1768 18.125 4.51786 31.6; 1769 18.125 4.51786 31.8; 1770 18.125 4.51786 32;
    1771 18.125 4.51786 32.2; 1772 18.125 4.51786 32.4; 1773 18.125 4.51786 32.6;
    1774 18.125 4.51786 32.8; 1775 18.125 4.51786 33; 1776 18.125 4.71429 30.2;
    1777 18.125 4.71429 30.4; 1778 18.125 4.71429 30.6; 1779 18.125 4.71429 30.8;
    1780 18.125 4.71429 31; 1781 18.125 4.71429 31.2; 1782 18.125 4.71429 31.4;
    1783 18.125 4.71429 31.6; 1784 18.125 4.71429 31.8; 1785 18.125 4.71429 32;
    1786 18.125 4.71429 32.2; 1787 18.125 4.71429 32.4; 1788 18.125 4.71429 32.6;
    1789 18.125 4.71429 32.8; 1790 18.125 4.71429 33; 1791 18.125 4.91071 30.2;
    1792 18.125 4.91071 30.4; 1793 18.125 4.91071 30.6; 1794 18.125 4.91071 30.8;
    1795 18.125 4.91071 31; 1796 18.125 4.91071 31.2; 1797 18.125 4.91071 31.4;
    1798 18.125 4.91071 31.6; 1799 18.125 4.91071 31.8; 1800 18.125 4.91071 32;
    1801 18.125 4.91071 32.2; 1802 18.125 4.91071 32.4; 1803 18.125 4.91071 32.6;
    1804 18.125 4.91071 32.8; 1805 18.125 4.91071 33; 1806 18.125 5.10714 30.2;
    1807 18.125 5.10714 30.4; 1808 18.125 5.10714 30.6; 1809 18.125 5.10714 30.8;
    1810 18.125 5.10714 31; 1811 18.125 5.10714 31.2; 1812 18.125 5.10714 31.4;
    1813 18.125 5.10714 31.6; 1814 18.125 5.10714 31.8; 1815 18.125 5.10714 32;
    1816 18.125 5.10714 32.2; 1817 18.125 5.10714 32.4; 1818 18.125 5.10714 32.6;
    1819 18.125 5.10714 32.8; 1820 18.125 5.10714 33; 1821 18.125 5.30357 30.2;
    1822 18.125 5.30357 30.4; 1823 18.125 5.30357 30.6; 1824 18.125 5.30357 30.8;
    1825 18.125 5.30357 31; 1826 18.125 5.30357 31.2; 1827 18.125 5.30357 31.4;
    1828 18.125 5.30357 31.6; 1829 18.125 5.30357 31.8; 1830 18.125 5.30357 32;
    1831 18.125 5.30357 32.2; 1832 18.125 5.30357 32.4; 1833 18.125 5.30357 32.6;
    1834 18.125 5.30357 32.8; 1835 18.125 5.30357 33; 1836 14.925 0.196429 33.2;
    1837 14.925 0.392857 33.2; 1838 14.925 0.589286 33.2;
    1839 14.925 0.785714 33.2; 1840 14.925 0.982143 33.2; 1841 14.925 1.17857 33.2;
    1842 14.925 1.375 33.2; 1843 14.925 1.57143 33.2; 1844 14.925 1.76786 33.2;
    1845 14.925 1.96429 33.2; 1846 14.925 2.16071 33.2; 1847 14.925 2.35714 33.2;
    1848 14.925 2.55357 33.2; 1849 14.925 2.75 33.2; 1850 14.925 2.94643 33.2;
    1851 14.925 3.14286 33.2; 1852 14.925 3.33929 33.2; 1853 14.925 3.53571 33.2;
    1854 14.925 3.73214 33.2; 1855 14.925 3.92857 33.2; 1856 14.925 4.125 33.2;
    1857 14.925 4.32143 33.2; 1858 14.925 4.51786 33.2; 1859 14.925 4.71429 33.2;
    1860 14.925 4.91071 33.2; 1861 14.925 5.10714 33.2; 1862 14.925 5.30357 33.2;
    1863 15.125 5.5 33.2; 1864 15.325 5.5 33.2; 1865 15.525 5.5 33.2;
    1866 15.725 5.5 33.2; 1867 15.925 5.5 33.2; 1868 16.125 5.5 33.2;
    1869 16.325 5.5 33.2; 1870 16.525 5.5 33.2; 1871 16.725 5.5 33.2;
    1872 16.925 5.5 33.2; 1873 17.125 5.5 33.2; 1874 17.325 5.5 33.2;
    1875 17.525 5.5 33.2; 1876 17.725 5.5 33.2; 1877 17.925 5.5 33.2;
    1878 15.125 0.196429 33.2; 1879 15.325 0.196429 33.2;
    1880 15.525 0.196429 33.2; 1881 15.725 0.196429 33.2;
    1882 15.925 0.196429 33.2; 1883 16.125 0.196429 33.2;
    1884 16.325 0.196429 33.2; 1885 16.525 0.196429 33.2;
    1886 16.725 0.196429 33.2; 1887 16.925 0.196429 33.2;
    1888 17.125 0.196429 33.2; 1889 17.325 0.196429 33.2;
    1890 17.525 0.196429 33.2; 1891 17.725 0.196429 33.2;
    1892 17.925 0.196429 33.2; 1893 15.125 0.392857 33.2;
    1894 15.325 0.392857 33.2; 1895 15.525 0.392857 33.2;
    1896 15.725 0.392857 33.2; 1897 15.925 0.392857 33.2;
    1898 16.125 0.392857 33.2; 1899 16.325 0.392857 33.2;
    1900 16.525 0.392857 33.2; 1901 16.725 0.392857 33.2;
    1902 16.925 0.392857 33.2; 1903 17.125 0.392857 33.2;
    1904 17.325 0.392857 33.2; 1905 17.525 0.392857 33.2;
    1906 17.725 0.392857 33.2; 1907 17.925 0.392857 33.2;
    1908 15.125 0.589286 33.2; 1909 15.325 0.589286 33.2;
    1910 15.525 0.589286 33.2; 1911 15.725 0.589286 33.2;
    1912 15.925 0.589286 33.2; 1913 16.125 0.589286 33.2;
    1914 16.325 0.589286 33.2; 1915 16.525 0.589286 33.2;
    1916 16.725 0.589286 33.2; 1917 16.925 0.589286 33.2;
    1918 17.125 0.589286 33.2; 1919 17.325 0.589286 33.2;
    1920 17.525 0.589286 33.2; 1921 17.725 0.589286 33.2;
    1922 17.925 0.589286 33.2; 1923 15.125 0.785714 33.2;
    1924 15.325 0.785714 33.2; 1925 15.525 0.785714 33.2;
    1926 15.725 0.785714 33.2; 1927 15.925 0.785714 33.2;
    1928 16.125 0.785714 33.2; 1929 16.325 0.785714 33.2;
    1930 16.525 0.785714 33.2; 1931 16.725 0.785714 33.2;
    1932 16.925 0.785714 33.2; 1933 17.125 0.785714 33.2;
    1934 17.325 0.785714 33.2; 1935 17.525 0.785714 33.2;
    1936 17.725 0.785714 33.2; 1937 17.925 0.785714 33.2;
    1938 15.125 0.982143 33.2; 1939 15.325 0.982143 33.2;
    1940 15.525 0.982143 33.2; 1941 15.725 0.982143 33.2;
    1942 15.925 0.982143 33.2; 1943 16.125 0.982143 33.2;
    1944 16.325 0.982143 33.2; 1945 16.525 0.982143 33.2;
    1946 16.725 0.982143 33.2; 1947 16.925 0.982143 33.2;
    1948 17.125 0.982143 33.2; 1949 17.325 0.982143 33.2;
    1950 17.525 0.982143 33.2; 1951 17.725 0.982143 33.2;
    1952 17.925 0.982143 33.2; 1953 15.125 1.17857 33.2; 1954 15.325 1.17857 33.2;
    1955 15.525 1.17857 33.2; 1956 15.725 1.17857 33.2; 1957 15.925 1.17857 33.2;
    1958 16.125 1.17857 33.2; 1959 16.325 1.17857 33.2; 1960 16.525 1.17857 33.2;
    1961 16.725 1.17857 33.2; 1962 16.925 1.17857 33.2; 1963 17.125 1.17857 33.2;
    1964 17.325 1.17857 33.2; 1965 17.525 1.17857 33.2; 1966 17.725 1.17857 33.2;
    1967 17.925 1.17857 33.2; 1968 15.125 1.375 33.2; 1969 15.325 1.375 33.2;
    1970 15.525 1.375 33.2; 1971 15.725 1.375 33.2; 1972 15.925 1.375 33.2;
    1973 16.125 1.375 33.2; 1974 16.325 1.375 33.2; 1975 16.525 1.375 33.2;
    1976 16.725 1.375 33.2; 1977 16.925 1.375 33.2; 1978 17.125 1.375 33.2;
    1979 17.325 1.375 33.2; 1980 17.525 1.375 33.2; 1981 17.725 1.375 33.2;
    1982 17.925 1.375 33.2; 1983 15.125 1.57143 33.2; 1984 15.325 1.57143 33.2;
    1985 15.525 1.57143 33.2; 1986 15.725 1.57143 33.2; 1987 15.925 1.57143 33.2;
    1988 16.125 1.57143 33.2; 1989 16.325 1.57143 33.2; 1990 16.525 1.57143 33.2;
    1991 16.725 1.57143 33.2; 1992 16.925 1.57143 33.2; 1993 17.125 1.57143 33.2;
    1994 17.325 1.57143 33.2; 1995 17.525 1.57143 33.2; 1996 17.725 1.57143 33.2;
    1997 17.925 1.57143 33.2; 1998 15.125 1.76786 33.2; 1999 15.325 1.76786 33.2;
    2000 15.525 1.76786 33.2; 2001 15.725 1.76786 33.2; 2002 15.925 1.76786 33.2;
    2003 16.125 1.76786 33.2; 2004 16.325 1.76786 33.2; 2005 16.525 1.76786 33.2;
    2006 16.725 1.76786 33.2; 2007 16.925 1.76786 33.2; 2008 17.125 1.76786 33.2;
    2009 17.325 1.76786 33.2; 2010 17.525 1.76786 33.2; 2011 17.725 1.76786 33.2;
    2012 17.925 1.76786 33.2; 2013 15.125 1.96429 33.2; 2014 15.325 1.96429 33.2;
    2015 15.525 1.96429 33.2; 2016 15.725 1.96429 33.2; 2017 15.925 1.96429 33.2;
    2018 16.125 1.96429 33.2; 2019 16.325 1.96429 33.2; 2020 16.525 1.96429 33.2;
    2021 16.725 1.96429 33.2; 2022 16.925 1.96429 33.2; 2023 17.125 1.96429 33.2;
    2024 17.325 1.96429 33.2; 2025 17.525 1.96429 33.2; 2026 17.725 1.96429 33.2;
    2027 17.925 1.96429 33.2; 2028 15.125 2.16071 33.2; 2029 15.325 2.16071 33.2;
    2030 15.525 2.16071 33.2; 2031 15.725 2.16071 33.2; 2032 15.925 2.16071 33.2;
    2033 16.125 2.16071 33.2; 2034 16.325 2.16071 33.2; 2035 16.525 2.16071 33.2;
    2036 16.725 2.16071 33.2; 2037 16.925 2.16071 33.2; 2038 17.125 2.16071 33.2;
    2039 17.325 2.16071 33.2; 2040 17.525 2.16071 33.2; 2041 17.725 2.16071 33.2;
    2042 17.925 2.16071 33.2; 2043 15.125 2.35714 33.2; 2044 15.325 2.35714 33.2;
    2045 15.525 2.35714 33.2; 2046 15.725 2.35714 33.2; 2047 15.925 2.35714 33.2;
    2048 16.125 2.35714 33.2; 2049 16.325 2.35714 33.2; 2050 16.525 2.35714 33.2;
    2051 16.725 2.35714 33.2; 2052 16.925 2.35714 33.2; 2053 17.125 2.35714 33.2;
    2054 17.325 2.35714 33.2; 2055 17.525 2.35714 33.2; 2056 17.725 2.35714 33.2;
    2057 17.925 2.35714 33.2; 2058 15.125 2.55357 33.2; 2059 15.325 2.55357 33.2;
    2060 15.525 2.55357 33.2; 2061 15.725 2.55357 33.2; 2062 15.925 2.55357 33.2;
    2063 16.125 2.55357 33.2; 2064 16.325 2.55357 33.2; 2065 16.525 2.55357 33.2;
    2066 16.725 2.55357 33.2; 2067 16.925 2.55357 33.2; 2068 17.125 2.55357 33.2;
    2069 17.325 2.55357 33.2; 2070 17.525 2.55357 33.2; 2071 17.725 2.55357 33.2;
    2072 17.925 2.55357 33.2; 2073 15.125 2.75 33.2; 2074 15.325 2.75 33.2;
    2075 15.525 2.75 33.2; 2076 15.725 2.75 33.2; 2077 15.925 2.75 33.2;
    2078 16.125 2.75 33.2; 2079 16.325 2.75 33.2; 2080 16.525 2.75 33.2;
    2081 16.725 2.75 33.2; 2082 16.925 2.75 33.2; 2083 17.125 2.75 33.2;
    2084 17.325 2.75 33.2; 2085 17.525 2.75 33.2; 2086 17.725 2.75 33.2;
    2087 17.925 2.75 33.2; 2088 15.125 2.94643 33.2; 2089 15.325 2.94643 33.2;
    2090 15.525 2.94643 33.2; 2091 15.725 2.94643 33.2; 2092 15.925 2.94643 33.2;
    2093 16.125 2.94643 33.2; 2094 16.325 2.94643 33.2; 2095 16.525 2.94643 33.2;
    2096 16.725 2.94643 33.2; 2097 16.925 2.94643 33.2; 2098 17.125 2.94643 33.2;
    2099 17.325 2.94643 33.2; 2100 17.525 2.94643 33.2; 2101 17.725 2.94643 33.2;
    2102 17.925 2.94643 33.2; 2103 15.125 3.14286 33.2; 2104 15.325 3.14286 33.2;
    2105 15.525 3.14286 33.2; 2106 15.725 3.14286 33.2; 2107 15.925 3.14286 33.2;
    2108 16.125 3.14286 33.2; 2109 16.325 3.14286 33.2; 2110 16.525 3.14286 33.2;
    2111 16.725 3.14286 33.2; 2112 16.925 3.14286 33.2; 2113 17.125 3.14286 33.2;
    2114 17.325 3.14286 33.2; 2115 17.525 3.14286 33.2; 2116 17.725 3.14286 33.2;
    2117 17.925 3.14286 33.2; 2118 15.125 3.33929 33.2; 2119 15.325 3.33929 33.2;
    2120 15.525 3.33929 33.2; 2121 15.725 3.33929 33.2; 2122 15.925 3.33929 33.2;
    2123 16.125 3.33929 33.2; 2124 16.325 3.33929 33.2; 2125 16.525 3.33929 33.2;
    2126 16.725 3.33929 33.2; 2127 16.925 3.33929 33.2; 2128 17.125 3.33929 33.2;
    2129 17.325 3.33929 33.2; 2130 17.525 3.33929 33.2; 2131 17.725 3.33929 33.2;
    2132 17.925 3.33929 33.2; 2133 15.125 3.53571 33.2; 2134 15.325 3.53571 33.2;
    2135 15.525 3.53571 33.2; 2136 15.725 3.53571 33.2; 2137 15.925 3.53571 33.2;
    2138 16.125 3.53571 33.2; 2139 16.325 3.53571 33.2; 2140 16.525 3.53571 33.2;
    2141 16.725 3.53571 33.2; 2142 16.925 3.53571 33.2; 2143 17.125 3.53571 33.2;
    2144 17.325 3.53571 33.2; 2145 17.525 3.53571 33.2; 2146 17.725 3.53571 33.2;
    2147 17.925 3.53571 33.2; 2148 15.125 3.73214 33.2; 2149 15.325 3.73214 33.2;
    2150 15.525 3.73214 33.2; 2151 15.725 3.73214 33.2; 2152 15.925 3.73214 33.2;
    2153 16.125 3.73214 33.2; 2154 16.325 3.73214 33.2; 2155 16.525 3.73214 33.2;
    2156 16.725 3.73214 33.2; 2157 16.925 3.73214 33.2; 2158 17.125 3.73214 33.2;
    2159 17.325 3.73214 33.2; 2160 17.525 3.73214 33.2; 2161 17.725 3.73214 33.2;
    2162 17.925 3.73214 33.2; 2163 15.125 3.92857 33.2; 2164 15.325 3.92857 33.2;
    2165 15.525 3.92857 33.2; 2166 15.725 3.92857 33.2; 2167 15.925 3.92857 33.2;
    2168 16.125 3.92857 33.2; 2169 16.325 3.92857 33.2; 2170 16.525 3.92857 33.2;
    2171 16.725 3.92857 33.2; 2172 16.925 3.92857 33.2; 2173 17.125 3.92857 33.2;
    2174 17.325 3.92857 33.2; 2175 17.525 3.92857 33.2; 2176 17.725 3.92857 33.2;
    2177 17.925 3.92857 33.2; 2178 15.125 4.125 33.2; 2179 15.325 4.125 33.2;
    2180 15.525 4.125 33.2; 2181 15.725 4.125 33.2; 2182 15.925 4.125 33.2;
    2183 16.125 4.125 33.2; 2184 16.325 4.125 33.2; 2185 16.525 4.125 33.2;
    2186 16.725 4.125 33.2; 2187 16.925 4.125 33.2; 2188 17.125 4.125 33.2;
    2189 17.325 4.125 33.2; 2190 17.525 4.125 33.2; 2191 17.725 4.125 33.2;
    2192 17.925 4.125 33.2; 2193 15.125 4.32143 33.2; 2194 15.325 4.32143 33.2;
    2195 15.525 4.32143 33.2; 2196 15.725 4.32143 33.2; 2197 15.925 4.32143 33.2;
    2198 16.125 4.32143 33.2; 2199 16.325 4.32143 33.2; 2200 16.525 4.32143 33.2;
    2201 16.725 4.32143 33.2; 2202 16.925 4.32143 33.2; 2203 17.125 4.32143 33.2;
    2204 17.325 4.32143 33.2; 2205 17.525 4.32143 33.2; 2206 17.725 4.32143 33.2;
    2207 17.925 4.32143 33.2; 2208 15.125 4.51786 33.2; 2209 15.325 4.51786 33.2;
    2210 15.525 4.51786 33.2; 2211 15.725 4.51786 33.2; 2212 15.925 4.51786 33.2;
    2213 16.125 4.51786 33.2; 2214 16.325 4.51786 33.2; 2215 16.525 4.51786 33.2;
    2216 16.725 4.51786 33.2; 2217 16.925 4.51786 33.2; 2218 17.125 4.51786 33.2;
    2219 17.325 4.51786 33.2; 2220 17.525 4.51786 33.2; 2221 17.725 4.51786 33.2;
    2222 17.925 4.51786 33.2; 2223 15.125 4.71429 33.2; 2224 15.325 4.71429 33.2;
    2225 15.525 4.71429 33.2; 2226 15.725 4.71429 33.2; 2227 15.925 4.71429 33.2;
    2228 16.125 4.71429 33.2; 2229 16.325 4.71429 33.2; 2230 16.525 4.71429 33.2;
    2231 16.725 4.71429 33.2; 2232 16.925 4.71429 33.2; 2233 17.125 4.71429 33.2;
    2234 17.325 4.71429 33.2; 2235 17.525 4.71429 33.2; 2236 17.725 4.71429 33.2;
    2237 17.925 4.71429 33.2; 2238 15.125 4.91071 33.2; 2239 15.325 4.91071 33.2;
    2240 15.525 4.91071 33.2; 2241 15.725 4.91071 33.2; 2242 15.925 4.91071 33.2;
    2243 16.125 4.91071 33.2; 2244 16.325 4.91071 33.2; 2245 16.525 4.91071 33.2;
    2246 16.725 4.91071 33.2; 2247 16.925 4.91071 33.2; 2248 17.125 4.91071 33.2;
    2249 17.325 4.91071 33.2; 2250 17.525 4.91071 33.2; 2251 17.725 4.91071 33.2;
    2252 17.925 4.91071 33.2; 2253 15.125 5.10714 33.2; 2254 15.325 5.10714 33.2;
    2255 15.525 5.10714 33.2; 2256 15.725 5.10714 33.2; 2257 15.925 5.10714 33.2;
    2258 16.125 5.10714 33.2; 2259 16.325 5.10714 33.2; 2260 16.525 5.10714 33.2;
    2261 16.725 5.10714 33.2; 2262 16.925 5.10714 33.2; 2263 17.125 5.10714 33.2;
    2264 17.325 5.10714 33.2; 2265 17.525 5.10714 33.2; 2266 17.725 5.10714 33.2;
    2267 17.925 5.10714 33.2; 2268 15.125 5.30357 33.2; 2269 15.325 5.30357 33.2;
    2270 15.525 5.30357 33.2; 2271 15.725 5.30357 33.2; 2272 15.925 5.30357 33.2;
    2273 16.125 5.30357 33.2; 2274 16.325 5.30357 33.2; 2275 16.525 5.30357 33.2;
    2276 16.725 5.30357 33.2; 2277 16.925 5.30357 33.2; 2278 17.125 5.30357 33.2;
    2279 17.325 5.30357 33.2; 2280 17.525 5.30357 33.2; 2281 17.725 5.30357 33.2;
    2282 17.925 5.30357 33.2; 2283 14.925 7.25 30; 2284 15.1116 9 30;
    2285 15.2982 9 30; 2286 15.4848 9 30; 2287 15.6714 9 30; 2288 15.858 9 30;
    2289 16.0446 9 30; 2290 16.2313 9 30; 2291 16.4179 9 30; 2292 16.6045 9 30;
    2293 16.7911 9 30; 2294 16.9777 9 30; 2295 17.1643 9 30; 2296 17.3509 9 30;
    2297 18.125 8.80556 30; 2298 18.125 8.61111 30; 2299 18.125 8.41667 30;
    2300 18.125 8.22222 30; 2301 18.125 8.02778 30; 2302 18.125 7.83333 30;
    2303 18.125 7.63889 30; 2304 18.125 7.44444 30; 2305 18.125 7.25 30;
    2306 18.125 7.05556 30; 2307 18.125 6.86111 30; 2308 18.125 6.66667 30;
    2309 18.125 6.47222 30; 2310 18.125 6.27778 30; 2311 18.125 6.08333 30;
    2312 18.125 5.88889 30; 2313 18.125 5.69444 30; 2314 17.7748 8.41053 30;
    2315 16.4242 7.06328 30; 2316 16.9571 6.4992 30; 2317 15.9884 7.31256 30;
    2318 17.4895 8.36013 30; 2319 17.4388 6.13779 30; 2320 17.3047 8.85919 30;
    2321 17.8 8.34717 30; 2322 17.7672 8.27962 30; 2323 15.2786 7.13895 30;
    2324 15.5333 5.68447 30; 2325 17.0907 8.02965 30; 2326 17.1441 8.84047 30;
    2327 16.861 7.43857 30; 2328 17.3312 8.1831 30; 2329 17.9082 6.89156 30;
    2330 17.4534 8.78595 30; 2331 17.2521 7.62229 30; 2332 15.2681 6.053 30;
    2333 17.3126 8.67439 30; 2334 16.8804 6.26123 30; 2335 17.5881 6.03779 30;
    2336 17.6202 8.47612 30; 2337 17.2279 6.43726 30; 2338 17.1696 6.12785 30;
    2339 17.7085 8.3873 30; 2340 17.9565 8.65406 30; 2341 15.3854 8.29228 30;
    2342 17.4114 5.83853 30; 2343 16.9943 6.08509 30; 2344 16.8023 6.46843 30;
    2345 17.9885 7.34552 30; 2346 16.8102 8.77099 30; 2347 17.9062 6.30452 30;
    2348 17.9632 6.11499 30; 2349 17.2439 5.72594 30; 2350 16.9831 8.81273 30;
    2351 17.2002 7.82843 30; 2352 17.9104 6.49674 30; 2353 17.0156 5.66608 30;
    2354 16.5566 8.24684 30; 2355 15.5695 8.56443 30; 2356 16.7321 7.66656 30;
    2357 16.8768 6.12246 30; 2358 17.9583 6.68191 30; 2359 16.8274 5.6163 30;
    2360 17.3772 8.44552 30; 2361 15.6966 7.22948 30; 2362 17.3479 5.64039 30;
    2363 16.4889 8.08816 30; 2364 15.967 6.99979 30; 2365 17.2819 8.05266 30;
    2366 17.3439 5.93479 30; 2367 17.0392 8.27512 30; 2368 17.2098 8.00448 30;
    2369 16.3463 6.603 30; 2370 17.1 8.16128 30; 2371 15.9318 8.29993 30;
    2372 16.9662 7.78486 30; 2373 16.6861 8.15376 30; 2374 16.7635 7.17404 30;
    2375 15.4007 5.79885 30; 2376 17.4955 5.84214 30; 2377 17.0422 7.01722 30;
    2378 17.5382 8.50033 30; 2379 17.5146 6.79452 30; 2380 17.5054 8.54032 30;
    2381 16.6395 7.93752 30; 2382 16.7107 7.30172 30; 2383 16.8244 7.10026 30;
    2384 16.7931 6.90385 30; 2385 15.7822 8.77504 30; 2386 17.2486 8.1771 30;
    2387 15.9592 6.70152 30; 2388 17.0637 6.27506 30; 2389 17.3052 8.55169 30;
    2390 16.8148 7.84385 30; 2391 17.4101 7.5287 30; 2392 16.8985 8.24992 30;
    2393 16.6075 6.65404 30; 2394 16.2176 8.81304 30; 2395 16.2431 5.71772 30;
    2396 16.4492 5.97855 30; 2397 17.5814 7.73672 30; 2398 17.503 7.87347 30;
    2399 16.5692 7.47525 30; 2400 17.795 7.49206 30; 2401 16.7566 8.42959 30;
    2402 18.0309 7.64911 30; 2403 16.7123 5.72009 30; 2404 17.08 7.87712 30;
    2405 17.6028 7.115 30; 2406 17.6212 7.42763 30; 2407 16.4174 6.28098 30;
    2408 17.9841 8.49079 30; 2409 16.7613 5.82787 30; 2410 17.5114 7.35994 30;
    2411 16.9199 7.94297 30; 2412 17.2479 8.69314 30; 2413 17.8072 8.50475 30;
    2414 17.8652 7.36437 30; 2415 16.8811 7.01227 30; 2416 17.3303 8.36592 30;
    2417 17.5004 8.30842 30; 2418 17.5706 7.26168 30; 2419 18.0253 7.0127 30;
    2420 18.0037 7.54278 30; 2421 17.2732 8.64425 30; 2422 17.3618 6.0625 30;
    2423 17.6084 8.30171 30; 2424 17.703 7.66703 30; 2425 17.5762 8.41361 30;
    2426 16.4654 7.67014 30; 2427 16.9316 5.94967 30; 2428 17.9204 5.90839 30;
    2429 16.8595 6.01355 30; 2430 15.604 6.2342 30; 2431 16.5967 8.40294 30;
    2432 17.5994 6.25344 30; 2433 16.9451 8.36167 30; 2434 17.9701 7.14629 30;
    2435 17.5639 5.83199 30; 2436 17.1812 8.29729 30; 2437 17.3058 8.72477 30;
    2438 17.1272 7.50982 30; 2439 17.1635 6.61612 30; 2440 17.3748 8.66634 30;
    2441 17.4802 8.87928 30; 2442 17.0216 8.64574 30; 2443 17.4633 5.64369 30;
    2444 16.2031 8.28633 30; 2445 15.7283 7.66559 30; 2446 17.6628 8.59944 30;
    2447 17.2588 6.14375 30; 2448 17.0797 6.16188 30; 2449 17.719 6.39303 30;
    2450 15.7448 5.76557 30; 2451 15.3138 7.85223 30; 2452 16.9668 8.07227 30;
    2453 16.7148 6.11274 30; 2454 16.8061 8.00819 30; 2455 17.5989 5.96011 30;
    2456 17.69 8.23249 30; 2457 17.3633 8.76934 30; 2458 17.8994 7.97718 30;
    2459 16.536 7.16521 30; 2460 17.8168 6.08835 30; 2461 17.5057 8.72422 30;
    2462 17.8722 8.43445 30; 2463 17.1988 5.95751 30; 2464 17.7748 6.86548 30;
    2465 17.4218 8.56492 30; 2466 17.4756 8.23105 30; 2467 17.4484 6.06184 30;
    2468 17.3712 6.24123 30; 2469 16.7017 8.29047 30; 2470 17.3532 7.36902 30;
    2471 15.7748 8.14379 30; 2472 16.3896 8.28298 30; 2473 15.9221 6.39565 30;
    2474 17.2542 8.41784 30; 2475 17.5901 7.62506 30; 2476 17.3945 8.49762 30;
    2477 16.8066 8.2868 30; 2478 17.7915 8.71806 30; 2479 17.2013 6.80538 30;
    2480 17.5482 6.95325 30; 2481 17.5137 7.5643 30; 2482 17.6596 7.5705 30;
    2483 17.4138 5.74703 30; 2484 17.9145 8.761 30; 2485 17.2799 6.27411 30;
    2486 17.89 8.56724 30; 2487 17.54 6.34573 30; 2488 18.0012 8.35734 30;
    2489 17.3117 8.62027 30; 2490 17.6729 6.5508 30; 2491 15.6289 6.80705 30;
    2492 17.3294 7.16303 30; 2493 16.6185 7.30188 30; 2494 18.019 6.85253 30;
    2495 17.0006 8.17883 30; 2496 17.5193 6.05291 30; 2497 17.6628 6.82401 30;
    2498 16.6162 6.46934 30; 2499 16.5597 6.16755 30; 2500 15.9645 5.7045 30;
    2501 17.6467 5.9199 30; 2502 17.8223 5.71915 30; 2503 17.018 5.88861 30;
    2504 17.2997 5.85751 30; 2505 17.4654 7.23383 30; 2506 17.3423 6.14802 30;
    2507 17.3079 7.89047 30; 2508 17.4513 8.51961 30; 2509 16.0181 7.67192 30;
    2510 17.7146 8.46335 30; 2511 17.0968 7.36263 30; 2512 16.723 5.92845 30;
    2513 17.3888 5.99555 30; 2514 16.4187 8.73197 30; 2515 16.6745 6.31001 30;
    2516 17.7989 7.61268 30; 2517 16.6202 5.80643 30; 2518 16.5945 8.70813 30;
    2519 17.7382 8.33923 30; 2520 17.4467 7.08972 30; 2521 17.9029 7.62386 30;
    2522 17.1322 8.67484 30; 2523 17.1812 7.21649 30; 2524 16.9697 7.34825 30;
    2525 17.3617 6.9309 30; 2526 17.7391 8.09565 30; 2527 17.1731 8.55246 30;
    2528 17.6236 5.86672 30; 2529 17.2268 7.05937 30; 2530 17.808 8.85054 30;
    2531 17.2349 8.59167 30; 2532 17.853 7.04791 30; 2533 17.5678 7.50072 30;
    2534 17.5265 8.40127 30; 2535 17.7895 7.73276 30; 2536 17.8668 7.20765 30;
    2537 17.7555 7.24692 30; 2538 16.3127 7.4116 30; 2539 17.6088 6.12123 30;
    2540 17.4316 7.95315 30; 2541 16.6701 7.14031 30; 2542 17.6108 8.53573 30;
    2543 17.5826 8.61451 30; 2544 17.075 6.37755 30; 2545 17.5863 5.74422 30;
    2546 16.9925 6.60751 30; 2547 17.1403 5.8149 30; 2548 17.5825 8.24586 30;
    2549 17.6512 8.18309 30; 2550 16.6504 6.8531 30; 2551 17.716 5.82062 30;
    2552 17.3047 7.74899 30; 2553 17.6515 5.6916 30; 2554 17.5081 5.78114 30;
    2555 17.0877 6.00534 30; 2556 17.9251 6.9808 30; 2557 17.2076 8.65534 30;
    2558 17.4128 8.39081 30; 2559 16.1621 7.8287 30; 2560 17.8951 7.48163 30;
    2561 17.3477 8.10032 30; 2562 17.5182 6.14989 30; 2563 17.7002 6.09728 30;
    2564 17.4751 6.47539 30; 2565 16.1831 7.29889 30; 2566 17.0846 7.19538 30;
    2567 16.4833 5.70625 30; 2568 17.8213 7.55562 30; 2569 17.7969 6.21104 30;
    2570 17.9687 8.18081 30; 2571 16.272 6.0189 30; 2572 17.8644 7.55837 30;
    2573 17.392 7.64675 30; 2574 16.9047 7.64442 30; 2575 17.259 7.2714 30;
    2576 16.0172 8.69244 30; 2577 17.6319 8.37397 30; 2578 17.4906 8.5911 30;
    2579 17.6884 8.51008 30; 2580 17.388 6.68714 30; 2581 17.7583 7.41485 30;
    2582 17.5429 8.36109 30; 2583 17.7343 7.08446 30; 2584 17.487 8.44128 30;
    2585 17.684 7.33765 30; 2586 17.437 6.29205 30; 2587 17.5966 8.35756 30;
    2588 17.5071 8.04158 30; 2589 16.7866 6.28743 30; 2590 17.5523 5.97293 30;
    2591 17.651 7.88381 30; 2592 16.1942 6.3559 30; 2593 17.4951 7.64172 30;
    2594 17.5067 5.98073 30; 2595 16.8238 8.14284 30; 2596 16.4689 7.35969 30;
    2597 17.45 5.99033 30; 2598 17.6676 6.01873 30; 2599 17.5313 5.91274 30;
    2600 17.2134 7.3825 30; 2601 17.5783 5.91819 30; 2602 17.4461 7.43609 30;
    2603 16.8093 6.64579 30; 2604 16.8141 5.73174 30; 2605 17.1145 6.4867 30;
    2606 16.8858 8.58292 30; 2607 17.9541 7.77684 30; 2608 17.6729 6.17883 30;
    2609 17.8091 8.63716 30; 2610 17.2904 8.4922 30; 2611 17.8575 6.7922 30;
    2612 17.752 8.57109 30; 2613 17.5574 8.56554 30; 2614 17.4924 8.65782 30;
    2615 17.4035 8.32521 30; 2616 17.0161 7.559 30; 2617 17.4034 7.29451 30;
    2618 17.4281 5.92439 30; 2619 17.7557 6.69079 30; 2620 17.7064 8.29253 30;
    2621 16.66 5.6196 30; 2622 17.4788 5.91776 30; 2623 17.3083 6.55226 30;
    2624 17.2929 7.47711 30; 2625 17.6983 6.28992 30; 2626 17.8072 8.20576 30;
    2627 17.3647 8.56891 30; 2628 15.8994 6.14904 30; 2629 15.6539 5.98634 30;
    2630 17.4387 7.78517 30; 2631 17.4238 8.62715 30; 2632 17.5469 8.45354 30;
    2633 17.35 6.38659 30; 2634 17.4989 8.15119 30; 2635 17.4733 8.47749 30;
    2636 17.3297 8.27451 30; 2637 16.3287 7.97076 30; 2638 17.2816 6.01699 30;
    2639 17.7547 5.94555 30; 2640 17.7417 7.56475 30; 2641 16.8035 7.28766 30;
    2642 17.6635 6.96976 30; 2643 16.0526 6.04753 30; 2644 16.6899 8.55159 30;
    2645 17.019 6.7277 30; 2646 16.2617 8.54396 30; 2647 16.7105 7.48922 30;
    2648 17.6674 8.3361 30; 2649 17.6728 8.6801 30; 2650 17.6987 7.49117 30;
    2651 17.6163 8.78752 30; 2652 16.8572 8.43735 30; 2653 17.174 6.29564 30;
    2654 17.0875 7.69504 30; 2655 17.5802 8.66551 30; 2656 16.9717 6.24727 30;
    2657 17.1853 8.11774 30; 2658 17.8795 8.32965 30; 2659 16.9198 6.8142 30;
    2660 16.9816 6.38953 30; 2661 16.448 8.44982 30; 2662 16.8514 5.87555 30;
    2663 17.0343 8.43956 30; 2664 17.2671 8.7633 30; 2665 16.9246 7.20019 30;
    2666 16.9398 5.77586 30; 2667 17.1964 8.74816 30; 2668 16.7788 5.98962 30;
    2669 16.8909 6.37385 30; 2670 16.3516 6.8855 30; 2671 17.7904 6.96097 30;
    2672 17.1095 8.50341 30; 2673 16.6803 7.01013 30; 2674 17.642 8.43062 30;
    2675 16.6004 5.96573 30; 2676 18.125 9 30.2; 2677 18.125 9 30.4;
    2678 18.125 9 30.6; 2679 18.125 9 30.8; 2680 18.125 9 31; 2681 18.125 9 31.2;
    2682 18.125 9 31.4; 2683 18.125 9 31.6; 2684 18.125 9 31.8; 2685 18.125 9 32;
    2686 18.125 9 32.2; 2687 18.125 9 32.4; 2688 18.125 9 32.6; 2689 18.125 9 32.8;
    2690 18.125 9 33; 2691 18.125 8.80556 33.2; 2692 18.125 8.61111 33.2;
    2693 18.125 8.41667 33.2; 2694 18.125 8.22222 33.2; 2695 18.125 8.02778 33.2;
    2696 18.125 7.83333 33.2; 2697 18.125 7.63889 33.2; 2698 18.125 7.44444 33.2;
    2699 18.125 7.25 33.2; 2700 18.125 7.05556 33.2; 2701 18.125 6.86111 33.2;
    2702 18.125 6.66667 33.2; 2703 18.125 6.47222 33.2; 2704 18.125 6.27778 33.2;
    2705 18.125 6.08333 33.2; 2706 18.125 5.88889 33.2; 2707 18.125 5.69444 33.2;
    2708 18.125 5.69444 30.2; 2709 18.125 5.69444 30.4; 2710 18.125 5.69444 30.6;
    2711 18.125 5.69444 30.8; 2712 18.125 5.69444 31; 2713 18.125 5.69444 31.2;
    2714 18.125 5.69444 31.4; 2715 18.125 5.69444 31.6; 2716 18.125 5.69444 31.8;
    2717 18.125 5.69444 32; 2718 18.125 5.69444 32.2; 2719 18.125 5.69444 32.4;
    2720 18.125 5.69444 32.6; 2721 18.125 5.69444 32.8; 2722 18.125 5.69444 33;
    2723 18.125 5.88889 30.2; 2724 18.125 5.88889 30.4; 2725 18.125 5.88889 30.6;
    2726 18.125 5.88889 30.8; 2727 18.125 5.88889 31; 2728 18.125 5.88889 31.2;
    2729 18.125 5.88889 31.4; 2730 18.125 5.88889 31.6; 2731 18.125 5.88889 31.8;
    2732 18.125 5.88889 32; 2733 18.125 5.88889 32.2; 2734 18.125 5.88889 32.4;
    2735 18.125 5.88889 32.6; 2736 18.125 5.88889 32.8; 2737 18.125 5.88889 33;
    2738 18.125 6.08333 30.2; 2739 18.125 6.08333 30.4; 2740 18.125 6.08333 30.6;
    2741 18.125 6.08333 30.8; 2742 18.125 6.08333 31; 2743 18.125 6.08333 31.2;
    2744 18.125 6.08333 31.4; 2745 18.125 6.08333 31.6; 2746 18.125 6.08333 31.8;
    2747 18.125 6.08333 32; 2748 18.125 6.08333 32.2; 2749 18.125 6.08333 32.4;
    2750 18.125 6.08333 32.6; 2751 18.125 6.08333 32.8; 2752 18.125 6.08333 33;
    2753 18.125 6.27778 30.2; 2754 18.125 6.27778 30.4; 2755 18.125 6.27778 30.6;
    2756 18.125 6.27778 30.8; 2757 18.125 6.27778 31; 2758 18.125 6.27778 31.2;
    2759 18.125 6.27778 31.4; 2760 18.125 6.27778 31.6; 2761 18.125 6.27778 31.8;
    2762 18.125 6.27778 32; 2763 18.125 6.27778 32.2; 2764 18.125 6.27778 32.4;
    2765 18.125 6.27778 32.6; 2766 18.125 6.27778 32.8; 2767 18.125 6.27778 33;
    2768 18.125 6.47222 30.2; 2769 18.125 6.47222 30.4; 2770 18.125 6.47222 30.6;
    2771 18.125 6.47222 30.8; 2772 18.125 6.47222 31; 2773 18.125 6.47222 31.2;
    2774 18.125 6.47222 31.4; 2775 18.125 6.47222 31.6; 2776 18.125 6.47222 31.8;
    2777 18.125 6.47222 32; 2778 18.125 6.47222 32.2; 2779 18.125 6.47222 32.4;
    2780 18.125 6.47222 32.6; 2781 18.125 6.47222 32.8; 2782 18.125 6.47222 33;
    2783 18.125 6.66667 30.2; 2784 18.125 6.66667 30.4; 2785 18.125 6.66667 30.6;
    2786 18.125 6.66667 30.8; 2787 18.125 6.66667 31; 2788 18.125 6.66667 31.2;
    2789 18.125 6.66667 31.4; 2790 18.125 6.66667 31.6; 2791 18.125 6.66667 31.8;
    2792 18.125 6.66667 32; 2793 18.125 6.66667 32.2; 2794 18.125 6.66667 32.4;
    2795 18.125 6.66667 32.6; 2796 18.125 6.66667 32.8; 2797 18.125 6.66667 33;
    2798 18.125 6.86111 30.2; 2799 18.125 6.86111 30.4; 2800 18.125 6.86111 30.6;
    2801 18.125 6.86111 30.8; 2802 18.125 6.86111 31; 2803 18.125 6.86111 31.2;
    2804 18.125 6.86111 31.4; 2805 18.125 6.86111 31.6; 2806 18.125 6.86111 31.8;
    2807 18.125 6.86111 32; 2808 18.125 6.86111 32.2; 2809 18.125 6.86111 32.4;
    2810 18.125 6.86111 32.6; 2811 18.125 6.86111 32.8; 2812 18.125 6.86111 33;
    2813 18.125 7.05556 30.2; 2814 18.125 7.05556 30.4; 2815 18.125 7.05556 30.6;
    2816 18.125 7.05556 30.8; 2817 18.125 7.05556 31; 2818 18.125 7.05556 31.2;
    2819 18.125 7.05556 31.4; 2820 18.125 7.05556 31.6; 2821 18.125 7.05556 31.8;
    2822 18.125 7.05556 32; 2823 18.125 7.05556 32.2; 2824 18.125 7.05556 32.4;
    2825 18.125 7.05556 32.6; 2826 18.125 7.05556 32.8; 2827 18.125 7.05556 33;
    2828 18.125 7.25 30.2; 2829 18.125 7.25 30.4; 2830 18.125 7.25 30.6;
    2831 18.125 7.25 30.8; 2832 18.125 7.25 31; 2833 18.125 7.25 31.2;
    2834 18.125 7.25 31.4; 2835 18.125 7.25 31.6; 2836 18.125 7.25 31.8;
    2837 18.125 7.25 32; 2838 18.125 7.25 32.2; 2839 18.125 7.25 32.4;
    2840 18.125 7.25 32.6; 2841 18.125 7.25 32.8; 2842 18.125 7.25 33;
    2843 18.125 7.44444 30.2; 2844 18.125 7.44444 30.4; 2845 18.125 7.44444 30.6;
    2846 18.125 7.44444 30.8; 2847 18.125 7.44444 31; 2848 18.125 7.44444 31.2;
    2849 18.125 7.44444 31.4; 2850 18.125 7.44444 31.6; 2851 18.125 7.44444 31.8;
    2852 18.125 7.44444 32; 2853 18.125 7.44444 32.2; 2854 18.125 7.44444 32.4;
    2855 18.125 7.44444 32.6; 2856 18.125 7.44444 32.8; 2857 18.125 7.44444 33;
    2858 18.125 7.63889 30.2; 2859 18.125 7.63889 30.4; 2860 18.125 7.63889 30.6;
    2861 18.125 7.63889 30.8; 2862 18.125 7.63889 31; 2863 18.125 7.63889 31.2;
    2864 18.125 7.63889 31.4; 2865 18.125 7.63889 31.6; 2866 18.125 7.63889 31.8;
    2867 18.125 7.63889 32; 2868 18.125 7.63889 32.2; 2869 18.125 7.63889 32.4;
    2870 18.125 7.63889 32.6; 2871 18.125 7.63889 32.8; 2872 18.125 7.63889 33;
    2873 18.125 7.83333 30.2; 2874 18.125 7.83333 30.4; 2875 18.125 7.83333 30.6;
    2876 18.125 7.83333 30.8; 2877 18.125 7.83333 31; 2878 18.125 7.83333 31.2;
    2879 18.125 7.83333 31.4; 2880 18.125 7.83333 31.6; 2881 18.125 7.83333 31.8;
    2882 18.125 7.83333 32; 2883 18.125 7.83333 32.2; 2884 18.125 7.83333 32.4;
    2885 18.125 7.83333 32.6; 2886 18.125 7.83333 32.8; 2887 18.125 7.83333 33;
    2888 18.125 8.02778 30.2; 2889 18.125 8.02778 30.4; 2890 18.125 8.02778 30.6;
    2891 18.125 8.02778 30.8; 2892 18.125 8.02778 31; 2893 18.125 8.02778 31.2;
    2894 18.125 8.02778 31.4; 2895 18.125 8.02778 31.6; 2896 18.125 8.02778 31.8;
    2897 18.125 8.02778 32; 2898 18.125 8.02778 32.2; 2899 18.125 8.02778 32.4;
    2900 18.125 8.02778 32.6; 2901 18.125 8.02778 32.8; 2902 18.125 8.02778 33;
    2903 18.125 8.22222 30.2; 2904 18.125 8.22222 30.4; 2905 18.125 8.22222 30.6;
    2906 18.125 8.22222 30.8; 2907 18.125 8.22222 31; 2908 18.125 8.22222 31.2;
    2909 18.125 8.22222 31.4; 2910 18.125 8.22222 31.6; 2911 18.125 8.22222 31.8;
    2912 18.125 8.22222 32; 2913 18.125 8.22222 32.2; 2914 18.125 8.22222 32.4;
    2915 18.125 8.22222 32.6; 2916 18.125 8.22222 32.8; 2917 18.125 8.22222 33;
    2918 18.125 8.41667 30.2; 2919 18.125 8.41667 30.4; 2920 18.125 8.41667 30.6;
    2921 18.125 8.41667 30.8; 2922 18.125 8.41667 31; 2923 18.125 8.41667 31.2;
    2924 18.125 8.41667 31.4; 2925 18.125 8.41667 31.6; 2926 18.125 8.41667 31.8;
    2927 18.125 8.41667 32; 2928 18.125 8.41667 32.2; 2929 18.125 8.41667 32.4;
    2930 18.125 8.41667 32.6; 2931 18.125 8.41667 32.8; 2932 18.125 8.41667 33;
    2933 18.125 8.61111 30.2; 2934 18.125 8.61111 30.4; 2935 18.125 8.61111 30.6;
    2936 18.125 8.61111 30.8; 2937 18.125 8.61111 31; 2938 18.125 8.61111 31.2;
    2939 18.125 8.61111 31.4; 2940 18.125 8.61111 31.6; 2941 18.125 8.61111 31.8;
    2942 18.125 8.61111 32; 2943 18.125 8.61111 32.2; 2944 18.125 8.61111 32.4;
    2945 18.125 8.61111 32.6; 2946 18.125 8.61111 32.8; 2947 18.125 8.61111 33;
    2948 18.125 8.80556 30.2; 2949 18.125 8.80556 30.4; 2950 18.125 8.80556 30.6;
    2951 18.125 8.80556 30.8; 2952 18.125 8.80556 31; 2953 18.125 8.80556 31.2;
    2954 18.125 8.80556 31.4; 2955 18.125 8.80556 31.6; 2956 18.125 8.80556 31.8;
    2957 18.125 8.80556 32; 2958 18.125 8.80556 32.2; 2959 18.125 8.80556 32.4;
    2960 18.125 8.80556 32.6; 2961 18.125 8.80556 32.8; 2962 18.125 8.80556 33;
    2963 14.925 5.69444 33.2; 2964 14.925 5.88889 33.2; 2965 14.925 6.08333 33.2;
    2966 14.925 6.27778 33.2; 2967 14.925 6.47222 33.2; 2968 14.925 6.66667 33.2;
    2969 14.925 6.86111 33.2; 2970 14.925 7.05556 33.2; 2971 14.925 7.25 33.2;
    2972 14.925 7.44444 33.2; 2973 14.925 7.63889 33.2; 2974 14.925 7.83333 33.2;
    2975 14.925 8.02778 33.2; 2976 14.925 8.22222 33.2; 2977 14.925 8.41667 33.2;
    2978 14.925 8.61111 33.2; 2979 14.925 8.80556 33.2; 2980 15.125 9 33.2;
    2981 15.325 9 33.2; 2982 15.525 9 33.2; 2983 15.725 9 33.2; 2984 15.925 9 33.2;
    2985 16.125 9 33.2; 2986 16.325 9 33.2; 2987 16.525 9 33.2; 2988 16.725 9 33.2;
    2989 16.925 9 33.2; 2990 17.125 9 33.2; 2991 17.325 9 33.2; 2992 17.525 9 33.2;
    2993 17.725 9 33.2; 2994 17.925 9 33.2; 2995 15.125 5.69444 33.2;
    2996 15.325 5.69444 33.2; 2997 15.525 5.69444 33.2; 2998 15.725 5.69444 33.2;
    2999 15.925 5.69444 33.2; 3000 16.125 5.69444 33.2; 3001 16.325 5.69444 33.2;
    3002 16.525 5.69444 33.2; 3003 16.725 5.69444 33.2; 3004 16.925 5.69444 33.2;
    3005 17.125 5.69444 33.2; 3006 17.325 5.69444 33.2; 3007 17.525 5.69444 33.2;
    3008 17.725 5.69444 33.2; 3009 17.925 5.69444 33.2; 3010 15.125 5.88889 33.2;
    3011 15.325 5.88889 33.2; 3012 15.525 5.88889 33.2; 3013 15.725 5.88889 33.2;
    3014 15.925 5.88889 33.2; 3015 16.125 5.88889 33.2; 3016 16.325 5.88889 33.2;
    3017 16.525 5.88889 33.2; 3018 16.725 5.88889 33.2; 3019 16.925 5.88889 33.2;
    3020 17.125 5.88889 33.2; 3021 17.325 5.88889 33.2; 3022 17.525 5.88889 33.2;
    3023 17.725 5.88889 33.2; 3024 17.925 5.88889 33.2; 3025 15.125 6.08333 33.2;
    3026 15.325 6.08333 33.2; 3027 15.525 6.08333 33.2; 3028 15.725 6.08333 33.2;
    3029 15.925 6.08333 33.2; 3030 16.125 6.08333 33.2; 3031 16.325 6.08333 33.2;
    3032 16.525 6.08333 33.2; 3033 16.725 6.08333 33.2; 3034 16.925 6.08333 33.2;
    3035 17.125 6.08333 33.2; 3036 17.325 6.08333 33.2; 3037 17.525 6.08333 33.2;
    3038 17.725 6.08333 33.2; 3039 17.925 6.08333 33.2; 3040 15.125 6.27778 33.2;
    3041 15.325 6.27778 33.2; 3042 15.525 6.27778 33.2; 3043 15.725 6.27778 33.2;
    3044 15.925 6.27778 33.2; 3045 16.125 6.27778 33.2; 3046 16.325 6.27778 33.2;
    3047 16.525 6.27778 33.2; 3048 16.725 6.27778 33.2; 3049 16.925 6.27778 33.2;
    3050 17.125 6.27778 33.2; 3051 17.325 6.27778 33.2; 3052 17.525 6.27778 33.2;
    3053 17.725 6.27778 33.2; 3054 17.925 6.27778 33.2; 3055 15.125 6.47222 33.2;
    3056 15.325 6.47222 33.2; 3057 15.525 6.47222 33.2; 3058 15.725 6.47222 33.2;
    3059 15.925 6.47222 33.2; 3060 16.125 6.47222 33.2; 3061 16.325 6.47222 33.2;
    3062 16.525 6.47222 33.2; 3063 16.725 6.47222 33.2; 3064 16.925 6.47222 33.2;
    3065 17.125 6.47222 33.2; 3066 17.325 6.47222 33.2; 3067 17.525 6.47222 33.2;
    3068 17.725 6.47222 33.2; 3069 17.925 6.47222 33.2; 3070 15.125 6.66667 33.2;
    3071 15.325 6.66667 33.2; 3072 15.525 6.66667 33.2; 3073 15.725 6.66667 33.2;
    3074 15.925 6.66667 33.2; 3075 16.125 6.66667 33.2; 3076 16.325 6.66667 33.2;
    3077 16.525 6.66667 33.2; 3078 16.725 6.66667 33.2; 3079 16.925 6.66667 33.2;
    3080 17.125 6.66667 33.2; 3081 17.325 6.66667 33.2; 3082 17.525 6.66667 33.2;
    3083 17.725 6.66667 33.2; 3084 17.925 6.66667 33.2; 3085 15.125 6.86111 33.2;
    3086 15.325 6.86111 33.2; 3087 15.525 6.86111 33.2; 3088 15.725 6.86111 33.2;
    3089 15.925 6.86111 33.2; 3090 16.125 6.86111 33.2; 3091 16.325 6.86111 33.2;
    3092 16.525 6.86111 33.2; 3093 16.725 6.86111 33.2; 3094 16.925 6.86111 33.2;
    3095 17.125 6.86111 33.2; 3096 17.325 6.86111 33.2; 3097 17.525 6.86111 33.2;
    3098 17.725 6.86111 33.2; 3099 17.925 6.86111 33.2; 3100 15.125 7.05556 33.2;
    3101 15.325 7.05556 33.2; 3102 15.525 7.05556 33.2; 3103 15.725 7.05556 33.2;
    3104 15.925 7.05556 33.2; 3105 16.125 7.05556 33.2; 3106 16.325 7.05556 33.2;
    3107 16.525 7.05556 33.2; 3108 16.725 7.05556 33.2; 3109 16.925 7.05556 33.2;
    3110 17.125 7.05556 33.2; 3111 17.325 7.05556 33.2; 3112 17.525 7.05556 33.2;
    3113 17.725 7.05556 33.2; 3114 17.925 7.05556 33.2; 3115 15.125 7.25 33.2;
    3116 15.325 7.25 33.2; 3117 15.525 7.25 33.2; 3118 15.725 7.25 33.2;
    3119 15.925 7.25 33.2; 3120 16.125 7.25 33.2; 3121 16.325 7.25 33.2;
    3122 16.525 7.25 33.2; 3123 16.725 7.25 33.2; 3124 16.925 7.25 33.2;
    3125 17.125 7.25 33.2; 3126 17.325 7.25 33.2; 3127 17.525 7.25 33.2;
    3128 17.725 7.25 33.2; 3129 17.925 7.25 33.2; 3130 15.125 7.44444 33.2;
    3131 15.325 7.44444 33.2; 3132 15.525 7.44444 33.2; 3133 15.725 7.44444 33.2;
    3134 15.925 7.44444 33.2; 3135 16.125 7.44444 33.2; 3136 16.325 7.44444 33.2;
    3137 16.525 7.44444 33.2; 3138 16.725 7.44444 33.2; 3139 16.925 7.44444 33.2;
    3140 17.125 7.44444 33.2; 3141 17.325 7.44444 33.2; 3142 17.525 7.44444 33.2;
    3143 17.725 7.44444 33.2; 3144 17.925 7.44444 33.2; 3145 15.125 7.63889 33.2;
    3146 15.325 7.63889 33.2; 3147 15.525 7.63889 33.2; 3148 15.725 7.63889 33.2;
    3149 15.925 7.63889 33.2; 3150 16.125 7.63889 33.2; 3151 16.325 7.63889 33.2;
    3152 16.525 7.63889 33.2; 3153 16.725 7.63889 33.2; 3154 16.925 7.63889 33.2;
    3155 17.125 7.63889 33.2; 3156 17.325 7.63889 33.2; 3157 17.525 7.63889 33.2;
    3158 17.725 7.63889 33.2; 3159 17.925 7.63889 33.2; 3160 15.125 7.83333 33.2;
    3161 15.325 7.83333 33.2; 3162 15.525 7.83333 33.2; 3163 15.725 7.83333 33.2;
    3164 15.925 7.83333 33.2; 3165 16.125 7.83333 33.2; 3166 16.325 7.83333 33.2;
    3167 16.525 7.83333 33.2; 3168 16.725 7.83333 33.2; 3169 16.925 7.83333 33.2;
    3170 17.125 7.83333 33.2; 3171 17.325 7.83333 33.2; 3172 17.525 7.83333 33.2;
    3173 17.725 7.83333 33.2; 3174 17.925 7.83333 33.2; 3175 15.125 8.02778 33.2;
    3176 15.325 8.02778 33.2; 3177 15.525 8.02778 33.2; 3178 15.725 8.02778 33.2;
    3179 15.925 8.02778 33.2; 3180 16.125 8.02778 33.2; 3181 16.325 8.02778 33.2;
    3182 16.525 8.02778 33.2; 3183 16.725 8.02778 33.2; 3184 16.925 8.02778 33.2;
    3185 17.125 8.02778 33.2; 3186 17.325 8.02778 33.2; 3187 17.525 8.02778 33.2;
    3188 17.725 8.02778 33.2; 3189 17.925 8.02778 33.2; 3190 15.125 8.22222 33.2;
    3191 15.325 8.22222 33.2; 3192 15.525 8.22222 33.2; 3193 15.725 8.22222 33.2;
    3194 15.925 8.22222 33.2; 3195 16.125 8.22222 33.2; 3196 16.325 8.22222 33.2;
    3197 16.525 8.22222 33.2; 3198 16.725 8.22222 33.2; 3199 16.925 8.22222 33.2;
    3200 17.125 8.22222 33.2; 3201 17.325 8.22222 33.2; 3202 17.525 8.22222 33.2;
    3203 17.725 8.22222 33.2; 3204 17.925 8.22222 33.2; 3205 15.125 8.41667 33.2;
    3206 15.325 8.41667 33.2; 3207 15.525 8.41667 33.2; 3208 15.725 8.41667 33.2;
    3209 15.925 8.41667 33.2; 3210 16.125 8.41667 33.2; 3211 16.325 8.41667 33.2;
    3212 16.525 8.41667 33.2; 3213 16.725 8.41667 33.2; 3214 16.925 8.41667 33.2;
    3215 17.125 8.41667 33.2; 3216 17.325 8.41667 33.2; 3217 17.525 8.41667 33.2;
    3218 17.725 8.41667 33.2; 3219 17.925 8.41667 33.2; 3220 15.125 8.61111 33.2;
    3221 15.325 8.61111 33.2; 3222 15.525 8.61111 33.2; 3223 15.725 8.61111 33.2;
    3224 15.925 8.61111 33.2; 3225 16.125 8.61111 33.2; 3226 16.325 8.61111 33.2;
    3227 16.525 8.61111 33.2; 3228 16.725 8.61111 33.2; 3229 16.925 8.61111 33.2;
    3230 17.125 8.61111 33.2; 3231 17.325 8.61111 33.2; 3232 17.525 8.61111 33.2;
    3233 17.725 8.61111 33.2; 3234 17.925 8.61111 33.2; 3235 15.125 8.80556 33.2;
    3236 15.325 8.80556 33.2; 3237 15.525 8.80556 33.2; 3238 15.725 8.80556 33.2;
    3239 15.925 8.80556 33.2; 3240 16.125 8.80556 33.2; 3241 16.325 8.80556 33.2;
    3242 16.525 8.80556 33.2; 3243 16.725 8.80556 33.2; 3244 16.925 8.80556 33.2;
    3245 17.125 8.80556 33.2; 3246 17.325 8.80556 33.2; 3247 17.525 8.80556 33.2;
    3248 17.725 8.80556 33.2; 3249 17.925 8.80556 33.2; 3250 14.925 10.75 30;
    3251 15.1116 12.5 30; 3252 15.2982 12.5 30; 3253 15.4848 12.5 30;
    3254 15.6714 12.5 30; 3255 15.858 12.5 30; 3256 16.0446 12.5 30;
    3257 16.2313 12.5 30; 3258 16.4179 12.5 30; 3259 16.6045 12.5 30;
    3260 16.7911 12.5 30; 3261 16.9777 12.5 30; 3262 17.1643 12.5 30;
    3263 17.3509 12.5 30; 3264 18.125 12.3056 30; 3265 18.125 12.1111 30;
    3266 18.125 11.9167 30; 3267 18.125 11.7222 30; 3268 18.125 11.5278 30;
    3269 18.125 11.3333 30; 3270 18.125 11.1389 30; 3271 18.125 10.9444 30;
    3272 18.125 10.75 30; 3273 18.125 10.5556 30; 3274 18.125 10.3611 30;
    3275 18.125 10.1667 30; 3276 18.125 9.97222 30; 3277 18.125 9.77778 30;
    3278 18.125 9.58333 30; 3279 18.125 9.38889 30; 3280 18.125 9.19444 30;
    3281 17.7748 11.9105 30; 3282 16.4242 10.5633 30; 3283 16.9571 9.9992 30;
    3284 15.9884 10.8126 30; 3285 17.4895 11.8601 30; 3286 17.4388 9.63779 30;
    3287 17.3047 12.3592 30; 3288 17.8 11.8472 30; 3289 17.7672 11.7796 30;
    3290 15.2786 10.639 30; 3291 15.5333 9.18447 30; 3292 17.0907 11.5296 30;
    3293 17.1441 12.3405 30; 3294 16.861 10.9386 30; 3295 17.3312 11.6831 30;
    3296 17.9082 10.3916 30; 3297 17.4534 12.2859 30; 3298 17.2521 11.1223 30;
    3299 15.2681 9.553 30; 3300 17.3126 12.1744 30; 3301 16.8804 9.76123 30;
    3302 17.5881 9.53779 30; 3303 17.6202 11.9761 30; 3304 17.2279 9.93726 30;
    3305 17.1696 9.62785 30; 3306 17.7085 11.8873 30; 3307 17.9565 12.1541 30;
    3308 15.3854 11.7923 30; 3309 17.4114 9.33853 30; 3310 16.9943 9.58509 30;
    3311 16.8023 9.96843 30; 3312 17.9885 10.8455 30; 3313 16.8102 12.271 30;
    3314 17.9062 9.80452 30; 3315 17.9632 9.61499 30; 3316 17.2439 9.22594 30;
    3317 16.9831 12.3127 30; 3318 17.2002 11.3284 30; 3319 17.9104 9.99674 30;
    3320 17.0156 9.16608 30; 3321 16.5566 11.7468 30; 3322 15.5695 12.0644 30;
    3323 16.7321 11.1666 30; 3324 16.8768 9.62246 30; 3325 17.9583 10.1819 30;
    3326 16.8274 9.1163 30; 3327 17.3772 11.9455 30; 3328 15.6966 10.7295 30;
    3329 17.3479 9.14039 30; 3330 16.4889 11.5882 30; 3331 15.967 10.4998 30;
    3332 17.2819 11.5527 30; 3333 17.3439 9.43479 30; 3334 17.0392 11.7751 30;
    3335 17.2098 11.5045 30; 3336 16.3463 10.103 30; 3337 17.1 11.6613 30;
    3338 15.9318 11.7999 30; 3339 16.9662 11.2849 30; 3340 16.6861 11.6538 30;
    3341 16.7635 10.674 30; 3342 15.4007 9.29885 30; 3343 17.4955 9.34214 30;
    3344 17.0422 10.5172 30; 3345 17.5382 12.0003 30; 3346 17.5146 10.2945 30;
    3347 17.5054 12.0403 30; 3348 16.6395 11.4375 30; 3349 16.7107 10.8017 30;
    3350 16.8244 10.6003 30; 3351 16.7931 10.4039 30; 3352 15.7822 12.275 30;
    3353 17.2486 11.6771 30; 3354 15.9592 10.2015 30; 3355 17.0637 9.77506 30;
    3356 17.3052 12.0517 30; 3357 16.8148 11.3438 30; 3358 17.4101 11.0287 30;
    3359 16.8985 11.7499 30; 3360 16.6075 10.154 30; 3361 16.2176 12.313 30;
    3362 16.2431 9.21772 30; 3363 16.4492 9.47855 30; 3364 17.5814 11.2367 30;
    3365 17.503 11.3735 30; 3366 16.5692 10.9752 30; 3367 17.795 10.9921 30;
    3368 16.7566 11.9296 30; 3369 18.0309 11.1491 30; 3370 16.7123 9.22009 30;
    3371 17.08 11.3771 30; 3372 17.6028 10.615 30; 3373 17.6212 10.9276 30;
    3374 16.4174 9.78098 30; 3375 17.9841 11.9908 30; 3376 16.7613 9.32787 30;
    3377 17.5114 10.8599 30; 3378 16.9199 11.443 30; 3379 17.2479 12.1931 30;
    3380 17.8072 12.0048 30; 3381 17.8652 10.8644 30; 3382 16.8811 10.5123 30;
    3383 17.3303 11.8659 30; 3384 17.5004 11.8084 30; 3385 17.5706 10.7617 30;
    3386 18.0253 10.5127 30; 3387 18.0037 11.0428 30; 3388 17.2732 12.1443 30;
    3389 17.3618 9.5625 30; 3390 17.6084 11.8017 30; 3391 17.703 11.167 30;
    3392 17.5762 11.9136 30; 3393 16.4654 11.1701 30; 3394 16.9316 9.44967 30;
    3395 17.9204 9.40839 30; 3396 16.8595 9.51355 30; 3397 15.604 9.7342 30;
    3398 16.5967 11.9029 30; 3399 17.5994 9.75344 30; 3400 16.9451 11.8617 30;
    3401 17.9701 10.6463 30; 3402 17.5639 9.33199 30; 3403 17.1812 11.7973 30;
    3404 17.3058 12.2248 30; 3405 17.1272 11.0098 30; 3406 17.1635 10.1161 30;
    3407 17.3748 12.1663 30; 3408 17.4802 12.3793 30; 3409 17.0216 12.1457 30;
    3410 17.4633 9.14369 30; 3411 16.2031 11.7863 30; 3412 15.7283 11.1656 30;
    3413 17.6628 12.0994 30; 3414 17.2588 9.64375 30; 3415 17.0797 9.66188 30;
    3416 17.719 9.89303 30; 3417 15.7448 9.26557 30; 3418 15.3138 11.3522 30;
    3419 16.9668 11.5723 30; 3420 16.7148 9.61274 30; 3421 16.8061 11.5082 30;
    3422 17.5989 9.46011 30; 3423 17.69 11.7325 30; 3424 17.3633 12.2693 30;
    3425 17.8994 11.4772 30; 3426 16.536 10.6652 30; 3427 17.8168 9.58835 30;
    3428 17.5057 12.2242 30; 3429 17.8722 11.9344 30; 3430 17.1988 9.45751 30;
    3431 17.7748 10.3655 30; 3432 17.4218 12.0649 30; 3433 17.4756 11.731 30;
    3434 17.4484 9.56184 30; 3435 17.3712 9.74123 30; 3436 16.7017 11.7905 30;
    3437 17.3532 10.869 30; 3438 15.7748 11.6438 30; 3439 16.3896 11.783 30;
    3440 15.9221 9.89565 30; 3441 17.2542 11.9178 30; 3442 17.5901 11.1251 30;
    3443 17.3945 11.9976 30; 3444 16.8066 11.7868 30; 3445 17.7915 12.2181 30;
    3446 17.2013 10.3054 30; 3447 17.5482 10.4533 30; 3448 17.5137 11.0643 30;
    3449 17.6596 11.0705 30; 3450 17.4138 9.24703 30; 3451 17.9145 12.261 30;
    3452 17.2799 9.77411 30; 3453 17.89 12.0672 30; 3454 17.54 9.84573 30;
    3455 18.0012 11.8573 30; 3456 17.3117 12.1203 30; 3457 17.6729 10.0508 30;
    3458 15.6289 10.307 30; 3459 17.3294 10.663 30; 3460 16.6185 10.8019 30;
    3461 18.019 10.3525 30; 3462 17.0006 11.6788 30; 3463 17.5193 9.55291 30;
    3464 17.6628 10.324 30; 3465 16.6162 9.96934 30; 3466 16.5597 9.66755 30;
    3467 15.9645 9.2045 30; 3468 17.6467 9.4199 30; 3469 17.8223 9.21915 30;
    3470 17.018 9.38861 30; 3471 17.2997 9.35751 30; 3472 17.4654 10.7338 30;
    3473 17.3423 9.64802 30; 3474 17.3079 11.3905 30; 3475 17.4513 12.0196 30;
    3476 16.0181 11.1719 30; 3477 17.7146 11.9634 30; 3478 17.0968 10.8626 30;
    3479 16.723 9.42845 30; 3480 17.3888 9.49555 30; 3481 16.4187 12.232 30;
    3482 16.6745 9.81001 30; 3483 17.7989 11.1127 30; 3484 16.6202 9.30643 30;
    3485 16.5945 12.2081 30; 3486 17.7382 11.8392 30; 3487 17.4467 10.5897 30;
    3488 17.9029 11.1239 30; 3489 17.1322 12.1748 30; 3490 17.1812 10.7165 30;
    3491 16.9697 10.8482 30; 3492 17.3617 10.4309 30; 3493 17.7391 11.5957 30;
    3494 17.1731 12.0525 30; 3495 17.6236 9.36672 30; 3496 17.2268 10.5594 30;
    3497 17.808 12.3505 30; 3498 17.2349 12.0917 30; 3499 17.853 10.5479 30;
    3500 17.5678 11.0007 30; 3501 17.5265 11.9013 30; 3502 17.7895 11.2328 30;
    3503 17.8668 10.7076 30; 3504 17.7555 10.7469 30; 3505 16.3127 10.9116 30;
    3506 17.6088 9.62123 30; 3507 17.4316 11.4532 30; 3508 16.6701 10.6403 30;
    3509 17.6108 12.0357 30; 3510 17.5826 12.1145 30; 3511 17.075 9.87755 30;
    3512 17.5863 9.24422 30; 3513 16.9925 10.1075 30; 3514 17.1403 9.3149 30;
    3515 17.5825 11.7459 30; 3516 17.6512 11.6831 30; 3517 16.6504 10.3531 30;
    3518 17.716 9.32062 30; 3519 17.3047 11.249 30; 3520 17.6515 9.1916 30;
    3521 17.5081 9.28114 30; 3522 17.0877 9.50534 30; 3523 17.9251 10.4808 30;
    3524 17.2076 12.1553 30; 3525 17.4128 11.8908 30; 3526 16.1621 11.3287 30;
    3527 17.8951 10.9816 30; 3528 17.3477 11.6003 30; 3529 17.5182 9.64989 30;
    3530 17.7002 9.59728 30; 3531 17.4751 9.97539 30; 3532 16.1831 10.7989 30;
    3533 17.0846 10.6954 30; 3534 16.4833 9.20625 30; 3535 17.8213 11.0556 30;
    3536 17.7969 9.71104 30; 3537 17.9687 11.6808 30; 3538 16.272 9.5189 30;
    3539 17.8644 11.0584 30; 3540 17.392 11.1468 30; 3541 16.9047 11.1444 30;
    3542 17.259 10.7714 30; 3543 16.0172 12.1924 30; 3544 17.6319 11.874 30;
    3545 17.4906 12.0911 30; 3546 17.6884 12.0101 30; 3547 17.388 10.1871 30;
    3548 17.7583 10.9149 30; 3549 17.5429 11.8611 30; 3550 17.7343 10.5845 30;
    3551 17.487 11.9413 30; 3552 17.684 10.8376 30; 3553 17.437 9.79205 30;
    3554 17.5966 11.8576 30; 3555 17.5071 11.5416 30; 3556 16.7866 9.78743 30;
    3557 17.5523 9.47293 30; 3558 17.651 11.3838 30; 3559 16.1942 9.8559 30;
    3560 17.4951 11.1417 30; 3561 17.5067 9.48073 30; 3562 16.8238 11.6428 30;
    3563 16.4689 10.8597 30; 3564 17.45 9.49034 30; 3565 17.6676 9.51873 30;
    3566 17.5313 9.41274 30; 3567 17.2134 10.8825 30; 3568 17.5783 9.41819 30;
    3569 17.4461 10.9361 30; 3570 16.8093 10.1458 30; 3571 16.8141 9.23174 30;
    3572 17.1145 9.9867 30; 3573 16.8858 12.0829 30; 3574 17.9541 11.2768 30;
    3575 17.6729 9.67883 30; 3576 17.8091 12.1372 30; 3577 17.2904 11.9922 30;
    3578 17.8575 10.2922 30; 3579 17.752 12.0711 30; 3580 17.5574 12.0655 30;
    3581 17.4924 12.1578 30; 3582 17.4035 11.8252 30; 3583 17.0161 11.059 30;
    3584 17.4034 10.7945 30; 3585 17.4281 9.42439 30; 3586 17.7557 10.1908 30;
    3587 17.7064 11.7925 30; 3588 16.66 9.1196 30; 3589 17.4788 9.41776 30;
    3590 17.3083 10.0523 30; 3591 17.2929 10.9771 30; 3592 17.6983 9.78992 30;
    3593 17.8072 11.7058 30; 3594 17.3647 12.0689 30; 3595 15.8994 9.64904 30;
    3596 15.6539 9.48634 30; 3597 17.4387 11.2852 30; 3598 17.4238 12.1271 30;
    3599 17.5469 11.9535 30; 3600 17.35 9.88659 30; 3601 17.4989 11.6512 30;
    3602 17.4733 11.9775 30; 3603 17.3297 11.7745 30; 3604 16.3287 11.4708 30;
    3605 17.2816 9.51699 30; 3606 17.7547 9.44555 30; 3607 17.7417 11.0648 30;
    3608 16.8035 10.7877 30; 3609 17.6635 10.4698 30; 3610 16.0526 9.54753 30;
    3611 16.6899 12.0516 30; 3612 17.019 10.2277 30; 3613 16.2617 12.044 30;
    3614 16.7105 10.9892 30; 3615 17.6674 11.8361 30; 3616 17.6728 12.1801 30;
    3617 17.6987 10.9912 30; 3618 17.6163 12.2875 30; 3619 16.8572 11.9374 30;
    3620 17.174 9.79564 30; 3621 17.0875 11.195 30; 3622 17.5802 12.1655 30;
    3623 16.9717 9.74727 30; 3624 17.1853 11.6177 30; 3625 17.8795 11.8296 30;
    3626 16.9198 10.3142 30; 3627 16.9816 9.88953 30; 3628 16.448 11.9498 30;
    3629 16.8514 9.37555 30; 3630 17.0343 11.9396 30; 3631 17.2671 12.2633 30;
    3632 16.9246 10.7002 30; 3633 16.9398 9.27586 30; 3634 17.1964 12.2482 30;
    3635 16.7788 9.48962 30; 3636 16.8909 9.87385 30; 3637 16.3516 10.3855 30;
    3638 17.7904 10.461 30; 3639 17.1095 12.0034 30; 3640 16.6803 10.5101 30;
    3641 17.642 11.9306 30; 3642 16.6004 9.46573 30; 3643 18.125 12.5 30.2;
    3644 18.125 12.5 30.4; 3645 18.125 12.5 30.6; 3646 18.125 12.5 30.8;
    3647 18.125 12.5 31; 3648 18.125 12.5 31.2; 3649 18.125 12.5 31.4;
    3650 18.125 12.5 31.6; 3651 18.125 12.5 31.8; 3652 18.125 12.5 32;
    3653 18.125 12.5 32.2; 3654 18.125 12.5 32.4; 3655 18.125 12.5 32.6;
    3656 18.125 12.5 32.8; 3657 18.125 12.5 33; 3658 18.125 12.3056 33.2;
    3659 18.125 12.1111 33.2; 3660 18.125 11.9167 33.2; 3661 18.125 11.7222 33.2;
    3662 18.125 11.5278 33.2; 3663 18.125 11.3333 33.2; 3664 18.125 11.1389 33.2;
    3665 18.125 10.9444 33.2; 3666 18.125 10.75 33.2; 3667 18.125 10.5556 33.2;
    3668 18.125 10.3611 33.2; 3669 18.125 10.1667 33.2; 3670 18.125 9.97222 33.2;
    3671 18.125 9.77778 33.2; 3672 18.125 9.58333 33.2; 3673 18.125 9.38889 33.2;
    3674 18.125 9.19444 33.2; 3675 18.125 9.19444 30.2; 3676 18.125 9.19444 30.4;
    3677 18.125 9.19444 30.6; 3678 18.125 9.19444 30.8; 3679 18.125 9.19444 31;
    3680 18.125 9.19444 31.2; 3681 18.125 9.19444 31.4; 3682 18.125 9.19444 31.6;
    3683 18.125 9.19444 31.8; 3684 18.125 9.19444 32; 3685 18.125 9.19444 32.2;
    3686 18.125 9.19444 32.4; 3687 18.125 9.19444 32.6; 3688 18.125 9.19444 32.8;
    3689 18.125 9.19444 33; 3690 18.125 9.38889 30.2; 3691 18.125 9.38889 30.4;
    3692 18.125 9.38889 30.6; 3693 18.125 9.38889 30.8; 3694 18.125 9.38889 31;
    3695 18.125 9.38889 31.2; 3696 18.125 9.38889 31.4; 3697 18.125 9.38889 31.6;
    3698 18.125 9.38889 31.8; 3699 18.125 9.38889 32; 3700 18.125 9.38889 32.2;
    3701 18.125 9.38889 32.4; 3702 18.125 9.38889 32.6; 3703 18.125 9.38889 32.8;
    3704 18.125 9.38889 33; 3705 18.125 9.58333 30.2; 3706 18.125 9.58333 30.4;
    3707 18.125 9.58333 30.6; 3708 18.125 9.58333 30.8; 3709 18.125 9.58333 31;
    3710 18.125 9.58333 31.2; 3711 18.125 9.58333 31.4; 3712 18.125 9.58333 31.6;
    3713 18.125 9.58333 31.8; 3714 18.125 9.58333 32; 3715 18.125 9.58333 32.2;
    3716 18.125 9.58333 32.4; 3717 18.125 9.58333 32.6; 3718 18.125 9.58333 32.8;
    3719 18.125 9.58333 33; 3720 18.125 9.77778 30.2; 3721 18.125 9.77778 30.4;
    3722 18.125 9.77778 30.6; 3723 18.125 9.77778 30.8; 3724 18.125 9.77778 31;
    3725 18.125 9.77778 31.2; 3726 18.125 9.77778 31.4; 3727 18.125 9.77778 31.6;
    3728 18.125 9.77778 31.8; 3729 18.125 9.77778 32; 3730 18.125 9.77778 32.2;
    3731 18.125 9.77778 32.4; 3732 18.125 9.77778 32.6; 3733 18.125 9.77778 32.8;
    3734 18.125 9.77778 33; 3735 18.125 9.97222 30.2; 3736 18.125 9.97222 30.4;
    3737 18.125 9.97222 30.6; 3738 18.125 9.97222 30.8; 3739 18.125 9.97222 31;
    3740 18.125 9.97222 31.2; 3741 18.125 9.97222 31.4; 3742 18.125 9.97222 31.6;
    3743 18.125 9.97222 31.8; 3744 18.125 9.97222 32; 3745 18.125 9.97222 32.2;
    3746 18.125 9.97222 32.4; 3747 18.125 9.97222 32.6; 3748 18.125 9.97222 32.8;
    3749 18.125 9.97222 33; 3750 18.125 10.1667 30.2; 3751 18.125 10.1667 30.4;
    3752 18.125 10.1667 30.6; 3753 18.125 10.1667 30.8; 3754 18.125 10.1667 31;
    3755 18.125 10.1667 31.2; 3756 18.125 10.1667 31.4; 3757 18.125 10.1667 31.6;
    3758 18.125 10.1667 31.8; 3759 18.125 10.1667 32; 3760 18.125 10.1667 32.2;
    3761 18.125 10.1667 32.4; 3762 18.125 10.1667 32.6; 3763 18.125 10.1667 32.8;
    3764 18.125 10.1667 33; 3765 18.125 10.3611 30.2; 3766 18.125 10.3611 30.4;
    3767 18.125 10.3611 30.6; 3768 18.125 10.3611 30.8; 3769 18.125 10.3611 31;
    3770 18.125 10.3611 31.2; 3771 18.125 10.3611 31.4; 3772 18.125 10.3611 31.6;
    3773 18.125 10.3611 31.8; 3774 18.125 10.3611 32; 3775 18.125 10.3611 32.2;
    3776 18.125 10.3611 32.4; 3777 18.125 10.3611 32.6; 3778 18.125 10.3611 32.8;
    3779 18.125 10.3611 33; 3780 18.125 10.5556 30.2; 3781 18.125 10.5556 30.4;
    3782 18.125 10.5556 30.6; 3783 18.125 10.5556 30.8; 3784 18.125 10.5556 31;
    3785 18.125 10.5556 31.2; 3786 18.125 10.5556 31.4; 3787 18.125 10.5556 31.6;
    3788 18.125 10.5556 31.8; 3789 18.125 10.5556 32; 3790 18.125 10.5556 32.2;
    3791 18.125 10.5556 32.4; 3792 18.125 10.5556 32.6; 3793 18.125 10.5556 32.8;
    3794 18.125 10.5556 33; 3795 18.125 10.75 30.2; 3796 18.125 10.75 30.4;
    3797 18.125 10.75 30.6; 3798 18.125 10.75 30.8; 3799 18.125 10.75 31;
    3800 18.125 10.75 31.2; 3801 18.125 10.75 31.4; 3802 18.125 10.75 31.6;
    3803 18.125 10.75 31.8; 3804 18.125 10.75 32; 3805 18.125 10.75 32.2;
    3806 18.125 10.75 32.4; 3807 18.125 10.75 32.6; 3808 18.125 10.75 32.8;
    3809 18.125 10.75 33; 3810 18.125 10.9444 30.2; 3811 18.125 10.9444 30.4;
    3812 18.125 10.9444 30.6; 3813 18.125 10.9444 30.8; 3814 18.125 10.9444 31;
    3815 18.125 10.9444 31.2; 3816 18.125 10.9444 31.4; 3817 18.125 10.9444 31.6;
    3818 18.125 10.9444 31.8; 3819 18.125 10.9444 32; 3820 18.125 10.9444 32.2;
    3821 18.125 10.9444 32.4; 3822 18.125 10.9444 32.6; 3823 18.125 10.9444 32.8;
    3824 18.125 10.9444 33; 3825 18.125 11.1389 30.2; 3826 18.125 11.1389 30.4;
    3827 18.125 11.1389 30.6; 3828 18.125 11.1389 30.8; 3829 18.125 11.1389 31;
    3830 18.125 11.1389 31.2; 3831 18.125 11.1389 31.4; 3832 18.125 11.1389 31.6;
    3833 18.125 11.1389 31.8; 3834 18.125 11.1389 32; 3835 18.125 11.1389 32.2;
    3836 18.125 11.1389 32.4; 3837 18.125 11.1389 32.6; 3838 18.125 11.1389 32.8;
    3839 18.125 11.1389 33; 3840 18.125 11.3333 30.2; 3841 18.125 11.3333 30.4;
    3842 18.125 11.3333 30.6; 3843 18.125 11.3333 30.8; 3844 18.125 11.3333 31;
    3845 18.125 11.3333 31.2; 3846 18.125 11.3333 31.4; 3847 18.125 11.3333 31.6;
    3848 18.125 11.3333 31.8; 3849 18.125 11.3333 32; 3850 18.125 11.3333 32.2;
    3851 18.125 11.3333 32.4; 3852 18.125 11.3333 32.6; 3853 18.125 11.3333 32.8;
    3854 18.125 11.3333 33; 3855 18.125 11.5278 30.2; 3856 18.125 11.5278 30.4;
    3857 18.125 11.5278 30.6; 3858 18.125 11.5278 30.8; 3859 18.125 11.5278 31;
    3860 18.125 11.5278 31.2; 3861 18.125 11.5278 31.4; 3862 18.125 11.5278 31.6;
    3863 18.125 11.5278 31.8; 3864 18.125 11.5278 32; 3865 18.125 11.5278 32.2;
    3866 18.125 11.5278 32.4; 3867 18.125 11.5278 32.6; 3868 18.125 11.5278 32.8;
    3869 18.125 11.5278 33; 3870 18.125 11.7222 30.2; 3871 18.125 11.7222 30.4;
    3872 18.125 11.7222 30.6; 3873 18.125 11.7222 30.8; 3874 18.125 11.7222 31;
    3875 18.125 11.7222 31.2; 3876 18.125 11.7222 31.4; 3877 18.125 11.7222 31.6;
    3878 18.125 11.7222 31.8; 3879 18.125 11.7222 32; 3880 18.125 11.7222 32.2;
    3881 18.125 11.7222 32.4; 3882 18.125 11.7222 32.6; 3883 18.125 11.7222 32.8;
    3884 18.125 11.7222 33; 3885 18.125 11.9167 30.2; 3886 18.125 11.9167 30.4;
    3887 18.125 11.9167 30.6; 3888 18.125 11.9167 30.8; 3889 18.125 11.9167 31;
    3890 18.125 11.9167 31.2; 3891 18.125 11.9167 31.4; 3892 18.125 11.9167 31.6;
    3893 18.125 11.9167 31.8; 3894 18.125 11.9167 32; 3895 18.125 11.9167 32.2;
    3896 18.125 11.9167 32.4; 3897 18.125 11.9167 32.6; 3898 18.125 11.9167 32.8;
    3899 18.125 11.9167 33; 3900 18.125 12.1111 30.2; 3901 18.125 12.1111 30.4;
    3902 18.125 12.1111 30.6; 3903 18.125 12.1111 30.8; 3904 18.125 12.1111 31;
    3905 18.125 12.1111 31.2; 3906 18.125 12.1111 31.4; 3907 18.125 12.1111 31.6;
    3908 18.125 12.1111 31.8; 3909 18.125 12.1111 32; 3910 18.125 12.1111 32.2;
    3911 18.125 12.1111 32.4; 3912 18.125 12.1111 32.6; 3913 18.125 12.1111 32.8;
    3914 18.125 12.1111 33; 3915 18.125 12.3056 30.2; 3916 18.125 12.3056 30.4;
    3917 18.125 12.3056 30.6; 3918 18.125 12.3056 30.8; 3919 18.125 12.3056 31;
    3920 18.125 12.3056 31.2; 3921 18.125 12.3056 31.4; 3922 18.125 12.3056 31.6;
    3923 18.125 12.3056 31.8; 3924 18.125 12.3056 32; 3925 18.125 12.3056 32.2;
    3926 18.125 12.3056 32.4; 3927 18.125 12.3056 32.6; 3928 18.125 12.3056 32.8;
    3929 18.125 12.3056 33; 3930 14.925 9.19444 33.2; 3931 14.925 9.38889 33.2;
    3932 14.925 9.58333 33.2; 3933 14.925 9.77778 33.2; 3934 14.925 9.97222 33.2;
    3935 14.925 10.1667 33.2; 3936 14.925 10.3611 33.2; 3937 14.925 10.5556 33.2;
    3938 14.925 10.75 33.2; 3939 14.925 10.9444 33.2; 3940 14.925 11.1389 33.2;
    3941 14.925 11.3333 33.2; 3942 14.925 11.5278 33.2; 3943 14.925 11.7222 33.2;
    3944 14.925 11.9167 33.2; 3945 14.925 12.1111 33.2; 3946 14.925 12.3056 33.2;
    3947 15.125 12.5 33.2; 3948 15.325 12.5 33.2; 3949 15.525 12.5 33.2;
    3950 15.725 12.5 33.2; 3951 15.925 12.5 33.2; 3952 16.125 12.5 33.2;
    3953 16.325 12.5 33.2; 3954 16.525 12.5 33.2; 3955 16.725 12.5 33.2;
    3956 16.925 12.5 33.2; 3957 17.125 12.5 33.2; 3958 17.325 12.5 33.2;
    3959 17.525 12.5 33.2; 3960 17.725 12.5 33.2; 3961 17.925 12.5 33.2;
    3962 15.125 9.19444 33.2; 3963 15.325 9.19444 33.2; 3964 15.525 9.19444 33.2;
    3965 15.725 9.19444 33.2; 3966 15.925 9.19444 33.2; 3967 16.125 9.19444 33.2;
    3968 16.325 9.19444 33.2; 3969 16.525 9.19444 33.2; 3970 16.725 9.19444 33.2;
    3971 16.925 9.19444 33.2; 3972 17.125 9.19444 33.2; 3973 17.325 9.19444 33.2;
    3974 17.525 9.19444 33.2; 3975 17.725 9.19444 33.2; 3976 17.925 9.19444 33.2;
    3977 15.125 9.38889 33.2; 3978 15.325 9.38889 33.2; 3979 15.525 9.38889 33.2;
    3980 15.725 9.38889 33.2; 3981 15.925 9.38889 33.2; 3982 16.125 9.38889 33.2;
    3983 16.325 9.38889 33.2; 3984 16.525 9.38889 33.2; 3985 16.725 9.38889 33.2;
    3986 16.925 9.38889 33.2; 3987 17.125 9.38889 33.2; 3988 17.325 9.38889 33.2;
    3989 17.525 9.38889 33.2; 3990 17.725 9.38889 33.2; 3991 17.925 9.38889 33.2;
    3992 15.125 9.58333 33.2; 3993 15.325 9.58333 33.2; 3994 15.525 9.58333 33.2;
    3995 15.725 9.58333 33.2; 3996 15.925 9.58333 33.2; 3997 16.125 9.58333 33.2;
    3998 16.325 9.58333 33.2; 3999 16.525 9.58333 33.2; 4000 16.725 9.58333 33.2;
    4001 16.925 9.58333 33.2; 4002 17.125 9.58333 33.2; 4003 17.325 9.58333 33.2;
    4004 17.525 9.58333 33.2; 4005 17.725 9.58333 33.2; 4006 17.925 9.58333 33.2;
    4007 15.125 9.77778 33.2; 4008 15.325 9.77778 33.2; 4009 15.525 9.77778 33.2;
    4010 15.725 9.77778 33.2; 4011 15.925 9.77778 33.2; 4012 16.125 9.77778 33.2;
    4013 16.325 9.77778 33.2; 4014 16.525 9.77778 33.2; 4015 16.725 9.77778 33.2;
    4016 16.925 9.77778 33.2; 4017 17.125 9.77778 33.2; 4018 17.325 9.77778 33.2;
    4019 17.525 9.77778 33.2; 4020 17.725 9.77778 33.2; 4021 17.925 9.77778 33.2;
    4022 15.125 9.97222 33.2; 4023 15.325 9.97222 33.2; 4024 15.525 9.97222 33.2;
    4025 15.725 9.97222 33.2; 4026 15.925 9.97222 33.2; 4027 16.125 9.97222 33.2;
    4028 16.325 9.97222 33.2; 4029 16.525 9.97222 33.2; 4030 16.725 9.97222 33.2;
    4031 16.925 9.97222 33.2; 4032 17.125 9.97222 33.2; 4033 17.325 9.97222 33.2;
    4034 17.525 9.97222 33.2; 4035 17.725 9.97222 33.2; 4036 17.925 9.97222 33.2;
    4037 15.125 10.1667 33.2; 4038 15.325 10.1667 33.2; 4039 15.525 10.1667 33.2;
    4040 15.725 10.1667 33.2; 4041 15.925 10.1667 33.2; 4042 16.125 10.1667 33.2;
    4043 16.325 10.1667 33.2; 4044 16.525 10.1667 33.2; 4045 16.725 10.1667 33.2;
    4046 16.925 10.1667 33.2; 4047 17.125 10.1667 33.2; 4048 17.325 10.1667 33.2;
    4049 17.525 10.1667 33.2; 4050 17.725 10.1667 33.2; 4051 17.925 10.1667 33.2;
    4052 15.125 10.3611 33.2; 4053 15.325 10.3611 33.2; 4054 15.525 10.3611 33.2;
    4055 15.725 10.3611 33.2; 4056 15.925 10.3611 33.2; 4057 16.125 10.3611 33.2;
    4058 16.325 10.3611 33.2; 4059 16.525 10.3611 33.2; 4060 16.725 10.3611 33.2;
    4061 16.925 10.3611 33.2; 4062 17.125 10.3611 33.2; 4063 17.325 10.3611 33.2;
    4064 17.525 10.3611 33.2; 4065 17.725 10.3611 33.2; 4066 17.925 10.3611 33.2;
    4067 15.125 10.5556 33.2; 4068 15.325 10.5556 33.2; 4069 15.525 10.5556 33.2;
    4070 15.725 10.5556 33.2; 4071 15.925 10.5556 33.2; 4072 16.125 10.5556 33.2;
    4073 16.325 10.5556 33.2; 4074 16.525 10.5556 33.2; 4075 16.725 10.5556 33.2;
    4076 16.925 10.5556 33.2; 4077 17.125 10.5556 33.2; 4078 17.325 10.5556 33.2;
    4079 17.525 10.5556 33.2; 4080 17.725 10.5556 33.2; 4081 17.925 10.5556 33.2;
    4082 15.125 10.75 33.2; 4083 15.325 10.75 33.2; 4084 15.525 10.75 33.2;
    4085 15.725 10.75 33.2; 4086 15.925 10.75 33.2; 4087 16.125 10.75 33.2;
    4088 16.325 10.75 33.2; 4089 16.525 10.75 33.2; 4090 16.725 10.75 33.2;
    4091 16.925 10.75 33.2; 4092 17.125 10.75 33.2; 4093 17.325 10.75 33.2;
    4094 17.525 10.75 33.2; 4095 17.725 10.75 33.2; 4096 17.925 10.75 33.2;
    4097 15.125 10.9444 33.2; 4098 15.325 10.9444 33.2; 4099 15.525 10.9444 33.2;
    4100 15.725 10.9444 33.2; 4101 15.925 10.9444 33.2; 4102 16.125 10.9444 33.2;
    4103 16.325 10.9444 33.2; 4104 16.525 10.9444 33.2; 4105 16.725 10.9444 33.2;
    4106 16.925 10.9444 33.2; 4107 17.125 10.9444 33.2; 4108 17.325 10.9444 33.2;
    4109 17.525 10.9444 33.2; 4110 17.725 10.9444 33.2; 4111 17.925 10.9444 33.2;
    4112 15.125 11.1389 33.2; 4113 15.325 11.1389 33.2; 4114 15.525 11.1389 33.2;
    4115 15.725 11.1389 33.2; 4116 15.925 11.1389 33.2; 4117 16.125 11.1389 33.2;
    4118 16.325 11.1389 33.2; 4119 16.525 11.1389 33.2; 4120 16.725 11.1389 33.2;
    4121 16.925 11.1389 33.2; 4122 17.125 11.1389 33.2; 4123 17.325 11.1389 33.2;
    4124 17.525 11.1389 33.2; 4125 17.725 11.1389 33.2; 4126 17.925 11.1389 33.2;
    4127 15.125 11.3333 33.2; 4128 15.325 11.3333 33.2; 4129 15.525 11.3333 33.2;
    4130 15.725 11.3333 33.2; 4131 15.925 11.3333 33.2; 4132 16.125 11.3333 33.2;
    4133 16.325 11.3333 33.2; 4134 16.525 11.3333 33.2; 4135 16.725 11.3333 33.2;
    4136 16.925 11.3333 33.2; 4137 17.125 11.3333 33.2; 4138 17.325 11.3333 33.2;
    4139 17.525 11.3333 33.2; 4140 17.725 11.3333 33.2; 4141 17.925 11.3333 33.2;
    4142 15.125 11.5278 33.2; 4143 15.325 11.5278 33.2; 4144 15.525 11.5278 33.2;
    4145 15.725 11.5278 33.2; 4146 15.925 11.5278 33.2; 4147 16.125 11.5278 33.2;
    4148 16.325 11.5278 33.2; 4149 16.525 11.5278 33.2; 4150 16.725 11.5278 33.2;
    4151 16.925 11.5278 33.2; 4152 17.125 11.5278 33.2; 4153 17.325 11.5278 33.2;
    4154 17.525 11.5278 33.2; 4155 17.725 11.5278 33.2; 4156 17.925 11.5278 33.2;
    4157 15.125 11.7222 33.2; 4158 15.325 11.7222 33.2; 4159 15.525 11.7222 33.2;
    4160 15.725 11.7222 33.2; 4161 15.925 11.7222 33.2; 4162 16.125 11.7222 33.2;
    4163 16.325 11.7222 33.2; 4164 16.525 11.7222 33.2; 4165 16.725 11.7222 33.2;
    4166 16.925 11.7222 33.2; 4167 17.125 11.7222 33.2; 4168 17.325 11.7222 33.2;
    4169 17.525 11.7222 33.2; 4170 17.725 11.7222 33.2; 4171 17.925 11.7222 33.2;
    4172 15.125 11.9167 33.2; 4173 15.325 11.9167 33.2; 4174 15.525 11.9167 33.2;
    4175 15.725 11.9167 33.2; 4176 15.925 11.9167 33.2; 4177 16.125 11.9167 33.2;
    4178 16.325 11.9167 33.2; 4179 16.525 11.9167 33.2; 4180 16.725 11.9167 33.2;
    4181 16.925 11.9167 33.2; 4182 17.125 11.9167 33.2; 4183 17.325 11.9167 33.2;
    4184 17.525 11.9167 33.2; 4185 17.725 11.9167 33.2; 4186 17.925 11.9167 33.2;
    4187 15.125 12.1111 33.2; 4188 15.325 12.1111 33.2; 4189 15.525 12.1111 33.2;
    4190 15.725 12.1111 33.2; 4191 15.925 12.1111 33.2; 4192 16.125 12.1111 33.2;
    4193 16.325 12.1111 33.2; 4194 16.525 12.1111 33.2; 4195 16.725 12.1111 33.2;
    4196 16.925 12.1111 33.2; 4197 17.125 12.1111 33.2; 4198 17.325 12.1111 33.2;
    4199 17.525 12.1111 33.2; 4200 17.725 12.1111 33.2; 4201 17.925 12.1111 33.2;
    4202 15.125 12.3056 33.2; 4203 15.325 12.3056 33.2; 4204 15.525 12.3056 33.2;
    4205 15.725 12.3056 33.2; 4206 15.925 12.3056 33.2; 4207 16.125 12.3056 33.2;
    4208 16.325 12.3056 33.2; 4209 16.525 12.3056 33.2; 4210 16.725 12.3056 33.2;
    4211 16.925 12.3056 33.2; 4212 17.125 12.3056 33.2; 4213 17.325 12.3056 33.2;
    4214 17.525 12.3056 33.2; 4215 17.725 12.3056 33.2; 4216 17.925 12.3056 33.2;
    4217 14.925 15 30; 4218 15.1116 17.5 30; 4219 15.2982 17.5 30;
    4220 15.4848 17.5 30; 4221 15.6714 17.5 30; 4222 15.858 17.5 30;
    4223 16.0446 17.5 30; 4224 16.2313 17.5 30; 4225 16.4179 17.5 30;
    4226 16.6045 17.5 30; 4227 16.7911 17.5 30; 4228 16.9777 17.5 30;
    4229 17.1643 17.5 30; 4230 17.3509 17.5 30; 4231 18.125 17.3077 30;
    4232 18.125 17.1154 30; 4233 18.125 16.9231 30; 4234 18.125 16.7308 30;
    4235 18.125 16.5385 30; 4236 18.125 16.3462 30; 4237 18.125 16.1538 30;
    4238 18.125 15.9615 30; 4239 18.125 15.7692 30; 4240 18.125 15.5769 30;
    4241 18.125 15.3846 30; 4242 18.125 15.1923 30; 4243 18.125 15 30;
    4244 18.125 14.8077 30; 4245 18.125 14.6154 30; 4246 18.125 14.4231 30;
    4247 18.125 14.2308 30; 4248 18.125 14.0385 30; 4249 18.125 13.8462 30;
    4250 18.125 13.6538 30; 4251 18.125 13.4615 30; 4252 18.125 13.2692 30;
    4253 18.125 13.0769 30; 4254 18.125 12.8846 30; 4255 18.125 12.6923 30;
    4256 17.643 16.092 30; 4257 17.3344 13.305 30; 4258 17.7673 16.9326 30;
    4259 17.8767 14.2878 30; 4260 17.5959 17.0048 30; 4261 15.4052 17.2703 30;
    4262 17.9773 12.8042 30; 4263 15.7108 17.3409 30; 4264 15.645 12.7188 30;
    4265 15.5347 17.3082 30; 4266 15.5159 12.7675 30; 4267 17.364 13.6448 30;
    4268 17.1662 17.1958 30; 4269 17.1528 16.8809 30; 4270 17.627 17.3857 30;
    4271 15.9129 17.3063 30; 4272 17.2732 16.8923 30; 4273 17.0915 13.1647 30;
    4274 17.3379 16.6095 30; 4275 17.8959 14.9736 30; 4276 17.7789 16.4459 30;
    4277 16.6293 14.9222 30; 4278 17.9675 13.3446 30; 4279 15.4943 13.2775 30;
    4280 15.3147 16.568 30; 4281 17.5515 12.9686 30; 4282 16.8035 15.9836 30;
    4283 17.2172 12.9152 30; 4284 16.4081 12.6926 30; 4285 17.0755 13.7712 30;
    4286 16.8293 15.8194 30; 4287 17.5952 13.5105 30; 4288 17.0389 15.7417 30;
    4289 17.1866 17.0449 30; 4290 17.9559 17.3878 30; 4291 17.3141 15.2532 30;
    4292 16.9654 15.168 30; 4293 17.1476 12.6441 30; 4294 17.9594 13.4609 30;
    4295 18.0195 13.2155 30; 4296 17.0801 16.7843 30; 4297 16.528 16.8819 30;
    4298 17.456 13.2749 30; 4299 17.166 17.327 30; 4300 17.5325 16.4811 30;
    4301 17.6182 17.0687 30; 4302 17.9302 16.7746 30; 4303 18.0118 16.5201 30;
    4304 16.9444 16.5177 30; 4305 17.937 16.1657 30; 4306 17.7578 13.0806 30;
    4307 17.4891 16.9821 30; 4308 17.0181 12.7787 30; 4309 17.3474 17.1832 30;
    4310 17.0176 16.4383 30; 4311 17.9446 13.8229 30; 4312 16.985 15.9318 30;
    4313 16.439 16.577 30; 4314 17.3704 17.3458 30; 4315 17.1259 16.4137 30;
    4316 17.5165 17.2749 30; 4317 16.852 16.3847 30; 4318 17.2762 13.9998 30;
    4319 17.7253 17.1992 30; 4320 16.591 17.3707 30; 4321 17.1058 16.5158 30;
    4322 17.0793 16.5918 30; 4323 17.4738 15.538 30; 4324 16.8785 13.6338 30;
    4325 16.9994 14.2129 30; 4326 16.3536 16.4078 30; 4327 15.7841 12.8775 30;
    4328 15.5506 17.0931 30; 4329 15.3613 16.9553 30; 4330 17.5924 15.6405 30;
    4331 16.7373 13.8403 30; 4332 17.6161 14.0835 30; 4333 17.1913 16.5983 30;
    4334 15.7079 17.1797 30; 4335 17.5314 13.097 30; 4336 17.6312 12.9655 30;
    4337 17.0169 13.5018 30; 4338 17.2858 14.1667 30; 4339 17.8618 16.8394 30;
    4340 16.671 14.1618 30; 4341 16.9731 16.3129 30; 4342 17.4783 13.0145 30;
    4343 17.0604 13.3514 30; 4344 17.904 15.1452 30; 4345 17.4921 14.497 30;
    4346 17.7095 17.1292 30; 4347 16.342 13.3998 30; 4348 17.0323 16.6654 30;
    4349 17.5966 13.0699 30; 4350 16.1773 16.9227 30; 4351 16.2194 12.7211 30;
    4352 17.735 12.8878 30; 4353 17.7234 13.1619 30; 4354 17.8365 14.6794 30;
    4355 17.263 16.6555 30; 4356 16.7434 16.6628 30; 4357 17.6785 13.2416 30;
    4358 17.8156 13.1731 30; 4359 17.7774 17.112 30; 4360 17.8898 14.1627 30;
    4361 17.8222 12.8738 30; 4362 17.0807 14.4726 30; 4363 16.1747 17.3074 30;
    4364 16.2133 13.1603 30; 4365 17.311 16.7073 30; 4366 17.9043 13.1836 30;
    4367 17.3187 16.3578 30; 4368 17.8678 13.0868 30; 4369 17.7996 12.7999 30;
    4370 17.5492 16.9618 30; 4371 16.5671 15.9565 30; 4372 17.7506 16.5603 30;
    4373 17.9425 15.9906 30; 4374 17.9724 16.3531 30; 4375 17.9161 13.2606 30;
    4376 17.1752 13.4876 30; 4377 17.6843 12.9056 30; 4378 16.4245 17.2859 30;
    4379 16.9081 16.6497 30; 4380 16.7402 14.5276 30; 4381 17.8829 13.9219 30;
    4382 17.6532 12.88 30; 4383 17.9856 16.6554 30; 4384 17.6572 13.0551 30;
    4385 16.9914 15.471 30; 4386 17.4811 17.1605 30; 4387 17.8465 16.3487 30;
    4388 17.193 16.4857 30; 4389 16.891 16.1628 30; 4390 16.7732 16.5378 30;
    4391 17.6094 13.697 30; 4392 17.2518 16.118 30; 4393 17.2736 16.5714 30;
    4394 17.5528 13.0378 30; 4395 17.2633 13.825 30; 4396 17.244 13.3332 30;
    4397 17.3759 17.0602 30; 4398 16.9069 13.0598 30; 4399 15.4816 12.9588 30;
    4400 17.117 16.2688 30; 4401 17.6195 12.8546 30; 4402 17.0133 13.9662 30;
    4403 17.5912 12.8971 30; 4404 17.594 12.944 30; 4405 16.0365 14.5544 30;
    4406 17.6974 17.2957 30; 4407 17.7134 12.7145 30; 4408 17.6831 16.6901 30;
    4409 17.5727 13.1337 30; 4410 15.7257 16.961 30; 4411 17.5152 16.3472 30;
    4412 15.8884 16.8173 30; 4413 16.9276 17.017 30; 4414 16.6463 16.4735 30;
    4415 15.8996 17.0552 30; 4416 17.3343 16.5169 30; 4417 17.5763 12.8207 30;
    4418 17.6979 12.8421 30; 4419 16.4403 13.1004 30; 4420 16.7367 17.2834 30;
    4421 16.6041 12.6932 30; 4422 16.0058 12.8106 30; 4423 17.8481 14.0589 30;
    4424 17.8215 13.3531 30; 4425 17.2761 16.4628 30; 4426 17.4888 13.5827 30;
    4427 17.388 16.6659 30; 4428 17.9204 14.4805 30; 4429 17.5961 17.2369 30;
    4430 17.4868 12.8668 30; 4431 17.3499 13.1646 30; 4432 17.5969 12.7543 30;
    4433 16.3973 12.8934 30; 4434 17.5139 13.1895 30; 4435 17.3372 12.9081 30;
    4436 17.5057 12.7995 30; 4437 18.0016 13.9956 30; 4438 17.6471 13.1492 30;
    4439 18.0036 17.0929 30; 4440 16.9766 12.6423 30; 4441 17.835 13.4523 30;
    4442 16.5376 12.8713 30; 4443 17.9893 14.2739 30; 4444 17.6825 16.8223 30;
    4445 17.3203 13.4734 30; 4446 17.9431 12.7139 30; 4447 16.2423 16.0017 30;
    4448 17.4582 12.9394 30; 4449 17.4309 16.8221 30; 4450 17.2559 15.5054 30;
    4451 17.9244 15.3865 30; 4452 17.6437 17.1278 30; 4453 17.3249 16.8252 30;
    4454 16.4544 13.6679 30; 4455 17.4042 16.5713 30; 4456 17.8608 13.605 30;
    4457 17.5107 17.0599 30; 4458 17.7604 13.0205 30; 4459 16.9743 13.2245 30;
    4460 17.481 16.9012 30; 4461 17.1427 12.8148 30; 4462 17.4504 15.754 30;
    4463 17.1031 16.0505 30; 4464 17.4858 15.3633 30; 4465 17.5829 15.913 30;
    4466 17.6922 17.0405 30; 4467 17.1497 13.3445 30; 4468 17.2067 16.3999 30;
    4469 18.0012 16.9206 30; 4470 16.7019 13.4659 30; 4471 17.8911 16.944 30;
    4472 17.8604 12.9976 30; 4473 16.5826 16.6844 30; 4474 17.357 14.8777 30;
    4475 17.782 16.8189 30; 4476 17.6037 13.0047 30; 4477 17.5617 17.0952 30;
    4478 16.4852 16.2521 30; 4479 16.2171 12.9126 30; 4480 16.7164 12.8357 30;
    4481 17.1703 16.6897 30; 4482 17.5452 16.6122 30; 4483 16.6891 16.2288 30;
    4484 15.963 13.8489 30; 4485 17.3932 14.3506 30; 4486 15.6899 16.7135 30;
    4487 17.6782 12.9472 30; 4488 17.6982 15.201 30; 4489 16.2084 17.0969 30;
    4490 17.7203 15.5457 30; 4491 17.5591 17.1564 30; 4492 17.7326 12.9516 30;
    4493 16.8614 13.3423 30; 4494 17.4162 16.0078 30; 4495 16.8703 16.8287 30;
    4496 17.643 14.9308 30; 4497 17.6952 15.4058 30; 4498 15.8402 15.2494 30;
    4499 17.2503 13.6457 30; 4500 15.7913 13.2716 30; 4501 17.9633 12.9235 30;
    4502 17.1225 13.6472 30; 4503 15.4959 14.337 30; 4504 17.6249 14.3965 30;
    4505 16.2226 16.5312 30; 4506 16.9747 17.2436 30; 4507 16.5324 16.4509 30;
    4508 17.4844 13.9768 30; 4509 17.9557 14.815 30; 4510 17.6625 16.9552 30;
    4511 16.2089 16.2892 30; 4512 17.8443 16.5998 30; 4513 17.4839 14.125 30;
    4514 16.1196 13.5383 30; 4515 15.9625 16.5234 30; 4516 17.4206 13.8329 30;
    4517 17.7886 12.9354 30; 4518 17.7999 16.0347 30; 4519 17.3728 16.7441 30;
    4520 17.8982 16.4896 30; 4521 16.8115 12.6999 30; 4522 16.6298 13.0103 30;
    4523 15.8259 16.2203 30; 4524 17.9238 14.0464 30; 4525 16.3424 16.6894 30;
    4526 17.7389 14.2473 30; 4527 17.7556 14.4592 30; 4528 17.8892 17.0553 30;
    4529 17.6863 13.3294 30; 4530 16.7666 13.1271 30; 4531 17.6818 13.0008 30;
    4532 17.2539 16.2595 30; 4533 17.4658 16.5246 30; 4534 17.7866 13.9223 30;
    4535 17.7796 17.0264 30; 4536 17.7475 13.7127 30; 4537 17.6328 12.9191 30;
    4538 16.3912 15.4728 30; 4539 17.7817 13.8201 30; 4540 17.655 17.1828 30;
    4541 17.3369 13.0274 30; 4542 17.8855 15.6156 30; 4543 17.5392 12.9243 30;
    4544 17.571 13.309 30; 4545 17.2067 13.1746 30; 4546 17.2531 15.8338 30;
    4547 17.5899 13.2225 30; 4548 17.9946 14.135 30; 4549 17.6367 16.5309 30;
    4550 17.4229 16.9834 30; 4551 17.993 13.0946 30; 4552 17.7017 13.5577 30;
    4553 17.4333 13.4072 30; 4554 17.7096 13.4324 30; 4555 17.1615 14.7273 30;
    4556 17.8012 13.2628 30; 4557 17.4823 16.1915 30; 4558 17.4604 13.1177 30;
    4559 17.486 16.7302 30; 4560 17.3902 16.4333 30; 4561 17.4499 16.6504 30;
    4562 17.2284 16.7721 30; 4563 17.3912 16.9009 30; 4564 16.8086 12.9297 30;
    4565 16.2659 14.0718 30; 4566 17.5779 13.4042 30; 4567 16.1602 16.7102 30;
    4568 16.0131 13.2045 30; 4569 17.4103 12.756 30; 4570 17.5653 16.8942 30;
    4571 17.5043 16.8147 30; 4572 17.6183 14.6242 30; 4573 16.6389 15.6407 30;
    4574 17.5815 16.7088 30; 4575 17.4117 12.8506 30; 4576 17.6682 16.3378 30;
    4577 16.5686 13.2843 30; 4578 17.6939 13.9893 30; 4579 17.2931 12.7747 30;
    4580 17.7975 16.2338 30; 4581 17.6567 12.8009 30; 4582 17.5524 12.866 30;
    4583 17.5844 16.8101 30; 4584 17.6071 14.2691 30; 4585 17.4592 12.6462 30;
    4586 17.6515 13.8494 30; 4587 16.5567 17.091 30; 4588 17.9343 17.2653 30;
    4589 17.0658 12.962 30; 4590 17.3023 12.635 30; 4591 17.1786 13.0156 30;
    4592 17.3047 16.9688 30; 4593 17.8485 17.1683 30; 4594 17.7899 14.1219 30;
    4595 17.831 15.817 30; 4596 17.8211 16.7044 30; 4597 16.9281 12.8725 30;
    4598 18.125 17.5 30.2; 4599 18.125 17.5 30.4; 4600 18.125 17.5 30.6;
    4601 18.125 17.5 30.8; 4602 18.125 17.5 31; 4603 18.125 17.5 31.2;
    4604 18.125 17.5 31.4; 4605 18.125 17.5 31.6; 4606 18.125 17.5 31.8;
    4607 18.125 17.5 32; 4608 18.125 17.5 32.2; 4609 18.125 17.5 32.4;
    4610 18.125 17.5 32.6; 4611 18.125 17.5 32.8; 4612 18.125 17.5 33;
    4613 18.125 17.3077 33.2; 4614 18.125 17.1154 33.2; 4615 18.125 16.9231 33.2;
    4616 18.125 16.7308 33.2; 4617 18.125 16.5385 33.2; 4618 18.125 16.3462 33.2;
    4619 18.125 16.1538 33.2; 4620 18.125 15.9615 33.2; 4621 18.125 15.7692 33.2;
    4622 18.125 15.5769 33.2; 4623 18.125 15.3846 33.2; 4624 18.125 15.1923 33.2;
    4625 18.125 15 33.2; 4626 18.125 14.8077 33.2; 4627 18.125 14.6154 33.2;
    4628 18.125 14.4231 33.2; 4629 18.125 14.2308 33.2; 4630 18.125 14.0385 33.2;
    4631 18.125 13.8462 33.2; 4632 18.125 13.6538 33.2; 4633 18.125 13.4615 33.2;
    4634 18.125 13.2692 33.2; 4635 18.125 13.0769 33.2; 4636 18.125 12.8846 33.2;
    4637 18.125 12.6923 33.2; 4638 18.125 12.6923 30.2; 4639 18.125 12.6923 30.4;
    4640 18.125 12.6923 30.6; 4641 18.125 12.6923 30.8; 4642 18.125 12.6923 31;
    4643 18.125 12.6923 31.2; 4644 18.125 12.6923 31.4; 4645 18.125 12.6923 31.6;
    4646 18.125 12.6923 31.8; 4647 18.125 12.6923 32; 4648 18.125 12.6923 32.2;
    4649 18.125 12.6923 32.4; 4650 18.125 12.6923 32.6; 4651 18.125 12.6923 32.8;
    4652 18.125 12.6923 33; 4653 18.125 12.8846 30.2; 4654 18.125 12.8846 30.4;
    4655 18.125 12.8846 30.6; 4656 18.125 12.8846 30.8; 4657 18.125 12.8846 31;
    4658 18.125 12.8846 31.2; 4659 18.125 12.8846 31.4; 4660 18.125 12.8846 31.6;
    4661 18.125 12.8846 31.8; 4662 18.125 12.8846 32; 4663 18.125 12.8846 32.2;
    4664 18.125 12.8846 32.4; 4665 18.125 12.8846 32.6; 4666 18.125 12.8846 32.8;
    4667 18.125 12.8846 33; 4668 18.125 13.0769 30.2; 4669 18.125 13.0769 30.4;
    4670 18.125 13.0769 30.6; 4671 18.125 13.0769 30.8; 4672 18.125 13.0769 31;
    4673 18.125 13.0769 31.2; 4674 18.125 13.0769 31.4; 4675 18.125 13.0769 31.6;
    4676 18.125 13.0769 31.8; 4677 18.125 13.0769 32; 4678 18.125 13.0769 32.2;
    4679 18.125 13.0769 32.4; 4680 18.125 13.0769 32.6; 4681 18.125 13.0769 32.8;
    4682 18.125 13.0769 33; 4683 18.125 13.2692 30.2; 4684 18.125 13.2692 30.4;
    4685 18.125 13.2692 30.6; 4686 18.125 13.2692 30.8; 4687 18.125 13.2692 31;
    4688 18.125 13.2692 31.2; 4689 18.125 13.2692 31.4; 4690 18.125 13.2692 31.6;
    4691 18.125 13.2692 31.8; 4692 18.125 13.2692 32; 4693 18.125 13.2692 32.2;
    4694 18.125 13.2692 32.4; 4695 18.125 13.2692 32.6; 4696 18.125 13.2692 32.8;
    4697 18.125 13.2692 33; 4698 18.125 13.4615 30.2; 4699 18.125 13.4615 30.4;
    4700 18.125 13.4615 30.6; 4701 18.125 13.4615 30.8; 4702 18.125 13.4615 31;
    4703 18.125 13.4615 31.2; 4704 18.125 13.4615 31.4; 4705 18.125 13.4615 31.6;
    4706 18.125 13.4615 31.8; 4707 18.125 13.4615 32; 4708 18.125 13.4615 32.2;
    4709 18.125 13.4615 32.4; 4710 18.125 13.4615 32.6; 4711 18.125 13.4615 32.8;
    4712 18.125 13.4615 33; 4713 18.125 13.6538 30.2; 4714 18.125 13.6538 30.4;
    4715 18.125 13.6538 30.6; 4716 18.125 13.6538 30.8; 4717 18.125 13.6538 31;
    4718 18.125 13.6538 31.2; 4719 18.125 13.6538 31.4; 4720 18.125 13.6538 31.6;
    4721 18.125 13.6538 31.8; 4722 18.125 13.6538 32; 4723 18.125 13.6538 32.2;
    4724 18.125 13.6538 32.4; 4725 18.125 13.6538 32.6; 4726 18.125 13.6538 32.8;
    4727 18.125 13.6538 33; 4728 18.125 13.8462 30.2; 4729 18.125 13.8462 30.4;
    4730 18.125 13.8462 30.6; 4731 18.125 13.8462 30.8; 4732 18.125 13.8462 31;
    4733 18.125 13.8462 31.2; 4734 18.125 13.8462 31.4; 4735 18.125 13.8462 31.6;
    4736 18.125 13.8462 31.8; 4737 18.125 13.8462 32; 4738 18.125 13.8462 32.2;
    4739 18.125 13.8462 32.4; 4740 18.125 13.8462 32.6; 4741 18.125 13.8462 32.8;
    4742 18.125 13.8462 33; 4743 18.125 14.0385 30.2; 4744 18.125 14.0385 30.4;
    4745 18.125 14.0385 30.6; 4746 18.125 14.0385 30.8; 4747 18.125 14.0385 31;
    4748 18.125 14.0385 31.2; 4749 18.125 14.0385 31.4; 4750 18.125 14.0385 31.6;
    4751 18.125 14.0385 31.8; 4752 18.125 14.0385 32; 4753 18.125 14.0385 32.2;
    4754 18.125 14.0385 32.4; 4755 18.125 14.0385 32.6; 4756 18.125 14.0385 32.8;
    4757 18.125 14.0385 33; 4758 18.125 14.2308 30.2; 4759 18.125 14.2308 30.4;
    4760 18.125 14.2308 30.6; 4761 18.125 14.2308 30.8; 4762 18.125 14.2308 31;
    4763 18.125 14.2308 31.2; 4764 18.125 14.2308 31.4; 4765 18.125 14.2308 31.6;
    4766 18.125 14.2308 31.8; 4767 18.125 14.2308 32; 4768 18.125 14.2308 32.2;
    4769 18.125 14.2308 32.4; 4770 18.125 14.2308 32.6; 4771 18.125 14.2308 32.8;
    4772 18.125 14.2308 33; 4773 18.125 14.4231 30.2; 4774 18.125 14.4231 30.4;
    4775 18.125 14.4231 30.6; 4776 18.125 14.4231 30.8; 4777 18.125 14.4231 31;
    4778 18.125 14.4231 31.2; 4779 18.125 14.4231 31.4; 4780 18.125 14.4231 31.6;
    4781 18.125 14.4231 31.8; 4782 18.125 14.4231 32; 4783 18.125 14.4231 32.2;
    4784 18.125 14.4231 32.4; 4785 18.125 14.4231 32.6; 4786 18.125 14.4231 32.8;
    4787 18.125 14.4231 33; 4788 18.125 14.6154 30.2; 4789 18.125 14.6154 30.4;
    4790 18.125 14.6154 30.6; 4791 18.125 14.6154 30.8; 4792 18.125 14.6154 31;
    4793 18.125 14.6154 31.2; 4794 18.125 14.6154 31.4; 4795 18.125 14.6154 31.6;
    4796 18.125 14.6154 31.8; 4797 18.125 14.6154 32; 4798 18.125 14.6154 32.2;
    4799 18.125 14.6154 32.4; 4800 18.125 14.6154 32.6; 4801 18.125 14.6154 32.8;
    4802 18.125 14.6154 33; 4803 18.125 14.8077 30.2; 4804 18.125 14.8077 30.4;
    4805 18.125 14.8077 30.6; 4806 18.125 14.8077 30.8; 4807 18.125 14.8077 31;
    4808 18.125 14.8077 31.2; 4809 18.125 14.8077 31.4; 4810 18.125 14.8077 31.6;
    4811 18.125 14.8077 31.8; 4812 18.125 14.8077 32; 4813 18.125 14.8077 32.2;
    4814 18.125 14.8077 32.4; 4815 18.125 14.8077 32.6; 4816 18.125 14.8077 32.8;
    4817 18.125 14.8077 33; 4818 18.125 15 30.2; 4819 18.125 15 30.4;
    4820 18.125 15 30.6; 4821 18.125 15 30.8; 4822 18.125 15 31;
    4823 18.125 15 31.2; 4824 18.125 15 31.4; 4825 18.125 15 31.6;
    4826 18.125 15 31.8; 4827 18.125 15 32; 4828 18.125 15 32.2;
    4829 18.125 15 32.4; 4830 18.125 15 32.6; 4831 18.125 15 32.8;
    4832 18.125 15 33; 4833 18.125 15.1923 30.2; 4834 18.125 15.1923 30.4;
    4835 18.125 15.1923 30.6; 4836 18.125 15.1923 30.8; 4837 18.125 15.1923 31;
    4838 18.125 15.1923 31.2; 4839 18.125 15.1923 31.4; 4840 18.125 15.1923 31.6;
    4841 18.125 15.1923 31.8; 4842 18.125 15.1923 32; 4843 18.125 15.1923 32.2;
    4844 18.125 15.1923 32.4; 4845 18.125 15.1923 32.6; 4846 18.125 15.1923 32.8;
    4847 18.125 15.1923 33; 4848 18.125 15.3846 30.2; 4849 18.125 15.3846 30.4;
    4850 18.125 15.3846 30.6; 4851 18.125 15.3846 30.8; 4852 18.125 15.3846 31;
    4853 18.125 15.3846 31.2; 4854 18.125 15.3846 31.4; 4855 18.125 15.3846 31.6;
    4856 18.125 15.3846 31.8; 4857 18.125 15.3846 32; 4858 18.125 15.3846 32.2;
    4859 18.125 15.3846 32.4; 4860 18.125 15.3846 32.6; 4861 18.125 15.3846 32.8;
    4862 18.125 15.3846 33; 4863 18.125 15.5769 30.2; 4864 18.125 15.5769 30.4;
    4865 18.125 15.5769 30.6; 4866 18.125 15.5769 30.8; 4867 18.125 15.5769 31;
    4868 18.125 15.5769 31.2; 4869 18.125 15.5769 31.4; 4870 18.125 15.5769 31.6;
    4871 18.125 15.5769 31.8; 4872 18.125 15.5769 32; 4873 18.125 15.5769 32.2;
    4874 18.125 15.5769 32.4; 4875 18.125 15.5769 32.6; 4876 18.125 15.5769 32.8;
    4877 18.125 15.5769 33; 4878 18.125 15.7692 30.2; 4879 18.125 15.7692 30.4;
    4880 18.125 15.7692 30.6; 4881 18.125 15.7692 30.8; 4882 18.125 15.7692 31;
    4883 18.125 15.7692 31.2; 4884 18.125 15.7692 31.4; 4885 18.125 15.7692 31.6;
    4886 18.125 15.7692 31.8; 4887 18.125 15.7692 32; 4888 18.125 15.7692 32.2;
    4889 18.125 15.7692 32.4; 4890 18.125 15.7692 32.6; 4891 18.125 15.7692 32.8;
    4892 18.125 15.7692 33; 4893 18.125 15.9615 30.2; 4894 18.125 15.9615 30.4;
    4895 18.125 15.9615 30.6; 4896 18.125 15.9615 30.8; 4897 18.125 15.9615 31;
    4898 18.125 15.9615 31.2; 4899 18.125 15.9615 31.4; 4900 18.125 15.9615 31.6;
    4901 18.125 15.9615 31.8; 4902 18.125 15.9615 32; 4903 18.125 15.9615 32.2;
    4904 18.125 15.9615 32.4; 4905 18.125 15.9615 32.6; 4906 18.125 15.9615 32.8;
    4907 18.125 15.9615 33; 4908 18.125 16.1538 30.2; 4909 18.125 16.1538 30.4;
    4910 18.125 16.1538 30.6; 4911 18.125 16.1538 30.8; 4912 18.125 16.1538 31;
    4913 18.125 16.1538 31.2; 4914 18.125 16.1538 31.4; 4915 18.125 16.1538 31.6;
    4916 18.125 16.1538 31.8; 4917 18.125 16.1538 32; 4918 18.125 16.1538 32.2;
    4919 18.125 16.1538 32.4; 4920 18.125 16.1538 32.6; 4921 18.125 16.1538 32.8;
    4922 18.125 16.1538 33; 4923 18.125 16.3462 30.2; 4924 18.125 16.3462 30.4;
    4925 18.125 16.3462 30.6; 4926 18.125 16.3462 30.8; 4927 18.125 16.3462 31;
    4928 18.125 16.3462 31.2; 4929 18.125 16.3462 31.4; 4930 18.125 16.3462 31.6;
    4931 18.125 16.3462 31.8; 4932 18.125 16.3462 32; 4933 18.125 16.3462 32.2;
    4934 18.125 16.3462 32.4; 4935 18.125 16.3462 32.6; 4936 18.125 16.3462 32.8;
    4937 18.125 16.3462 33; 4938 18.125 16.5385 30.2; 4939 18.125 16.5385 30.4;
    4940 18.125 16.5385 30.6; 4941 18.125 16.5385 30.8; 4942 18.125 16.5385 31;
    4943 18.125 16.5385 31.2; 4944 18.125 16.5385 31.4; 4945 18.125 16.5385 31.6;
    4946 18.125 16.5385 31.8; 4947 18.125 16.5385 32; 4948 18.125 16.5385 32.2;
    4949 18.125 16.5385 32.4; 4950 18.125 16.5385 32.6; 4951 18.125 16.5385 32.8;
    4952 18.125 16.5385 33; 4953 18.125 16.7308 30.2; 4954 18.125 16.7308 30.4;
    4955 18.125 16.7308 30.6; 4956 18.125 16.7308 30.8; 4957 18.125 16.7308 31;
    4958 18.125 16.7308 31.2; 4959 18.125 16.7308 31.4; 4960 18.125 16.7308 31.6;
    4961 18.125 16.7308 31.8; 4962 18.125 16.7308 32; 4963 18.125 16.7308 32.2;
    4964 18.125 16.7308 32.4; 4965 18.125 16.7308 32.6; 4966 18.125 16.7308 32.8;
    4967 18.125 16.7308 33; 4968 18.125 16.9231 30.2; 4969 18.125 16.9231 30.4;
    4970 18.125 16.9231 30.6; 4971 18.125 16.9231 30.8; 4972 18.125 16.9231 31;
    4973 18.125 16.9231 31.2; 4974 18.125 16.9231 31.4; 4975 18.125 16.9231 31.6;
    4976 18.125 16.9231 31.8; 4977 18.125 16.9231 32; 4978 18.125 16.9231 32.2;
    4979 18.125 16.9231 32.4; 4980 18.125 16.9231 32.6; 4981 18.125 16.9231 32.8;
    4982 18.125 16.9231 33; 4983 18.125 17.1154 30.2; 4984 18.125 17.1154 30.4;
    4985 18.125 17.1154 30.6; 4986 18.125 17.1154 30.8; 4987 18.125 17.1154 31;
    4988 18.125 17.1154 31.2; 4989 18.125 17.1154 31.4; 4990 18.125 17.1154 31.6;
    4991 18.125 17.1154 31.8; 4992 18.125 17.1154 32; 4993 18.125 17.1154 32.2;
    4994 18.125 17.1154 32.4; 4995 18.125 17.1154 32.6; 4996 18.125 17.1154 32.8;
    4997 18.125 17.1154 33; 4998 18.125 17.3077 30.2; 4999 18.125 17.3077 30.4;
    5000 18.125 17.3077 30.6; 5001 18.125 17.3077 30.8; 5002 18.125 17.3077 31;
    5003 18.125 17.3077 31.2; 5004 18.125 17.3077 31.4; 5005 18.125 17.3077 31.6;
    5006 18.125 17.3077 31.8; 5007 18.125 17.3077 32; 5008 18.125 17.3077 32.2;
    5009 18.125 17.3077 32.4; 5010 18.125 17.3077 32.6; 5011 18.125 17.3077 32.8;
    5012 18.125 17.3077 33; 5013 14.925 12.6923 33.2; 5014 14.925 12.8846 33.2;
    5015 14.925 13.0769 33.2; 5016 14.925 13.2692 33.2; 5017 14.925 13.4615 33.2;
    5018 14.925 13.6538 33.2; 5019 14.925 13.8462 33.2; 5020 14.925 14.0385 33.2;
    5021 14.925 14.2308 33.2; 5022 14.925 14.4231 33.2; 5023 14.925 14.6154 33.2;
    5024 14.925 14.8077 33.2; 5025 14.925 15 33.2; 5026 14.925 15.1923 33.2;
    5027 14.925 15.3846 33.2; 5028 14.925 15.5769 33.2; 5029 14.925 15.7692 33.2;
    5030 14.925 15.9615 33.2; 5031 14.925 16.1538 33.2; 5032 14.925 16.3462 33.2;
    5033 14.925 16.5385 33.2; 5034 14.925 16.7308 33.2; 5035 14.925 16.9231 33.2;
    5036 14.925 17.1154 33.2; 5037 14.925 17.3077 33.2; 5038 15.125 17.5 33.2;
    5039 15.325 17.5 33.2; 5040 15.525 17.5 33.2; 5041 15.725 17.5 33.2;
    5042 15.925 17.5 33.2; 5043 16.125 17.5 33.2; 5044 16.325 17.5 33.2;
    5045 16.525 17.5 33.2; 5046 16.725 17.5 33.2; 5047 16.925 17.5 33.2;
    5048 17.125 17.5 33.2; 5049 17.325 17.5 33.2; 5050 17.525 17.5 33.2;
    5051 17.725 17.5 33.2; 5052 17.925 17.5 33.2; 5053 15.125 12.6923 33.2;
    5054 15.325 12.6923 33.2; 5055 15.525 12.6923 33.2; 5056 15.725 12.6923 33.2;
    5057 15.925 12.6923 33.2; 5058 16.125 12.6923 33.2; 5059 16.325 12.6923 33.2;
    5060 16.525 12.6923 33.2; 5061 16.725 12.6923 33.2; 5062 16.925 12.6923 33.2;
    5063 17.125 12.6923 33.2; 5064 17.325 12.6923 33.2; 5065 17.525 12.6923 33.2;
    5066 17.725 12.6923 33.2; 5067 17.925 12.6923 33.2; 5068 15.125 12.8846 33.2;
    5069 15.325 12.8846 33.2; 5070 15.525 12.8846 33.2; 5071 15.725 12.8846 33.2;
    5072 15.925 12.8846 33.2; 5073 16.125 12.8846 33.2; 5074 16.325 12.8846 33.2;
    5075 16.525 12.8846 33.2; 5076 16.725 12.8846 33.2; 5077 16.925 12.8846 33.2;
    5078 17.125 12.8846 33.2; 5079 17.325 12.8846 33.2; 5080 17.525 12.8846 33.2;
    5081 17.725 12.8846 33.2; 5082 17.925 12.8846 33.2; 5083 15.125 13.0769 33.2;
    5084 15.325 13.0769 33.2; 5085 15.525 13.0769 33.2; 5086 15.725 13.0769 33.2;
    5087 15.925 13.0769 33.2; 5088 16.125 13.0769 33.2; 5089 16.325 13.0769 33.2;
    5090 16.525 13.0769 33.2; 5091 16.725 13.0769 33.2; 5092 16.925 13.0769 33.2;
    5093 17.125 13.0769 33.2; 5094 17.325 13.0769 33.2; 5095 17.525 13.0769 33.2;
    5096 17.725 13.0769 33.2; 5097 17.925 13.0769 33.2; 5098 15.125 13.2692 33.2;
    5099 15.325 13.2692 33.2; 5100 15.525 13.2692 33.2; 5101 15.725 13.2692 33.2;
    5102 15.925 13.2692 33.2; 5103 16.125 13.2692 33.2; 5104 16.325 13.2692 33.2;
    5105 16.525 13.2692 33.2; 5106 16.725 13.2692 33.2; 5107 16.925 13.2692 33.2;
    5108 17.125 13.2692 33.2; 5109 17.325 13.2692 33.2; 5110 17.525 13.2692 33.2;
    5111 17.725 13.2692 33.2; 5112 17.925 13.2692 33.2; 5113 15.125 13.4615 33.2;
    5114 15.325 13.4615 33.2; 5115 15.525 13.4615 33.2; 5116 15.725 13.4615 33.2;
    5117 15.925 13.4615 33.2; 5118 16.125 13.4615 33.2; 5119 16.325 13.4615 33.2;
    5120 16.525 13.4615 33.2; 5121 16.725 13.4615 33.2; 5122 16.925 13.4615 33.2;
    5123 17.125 13.4615 33.2; 5124 17.325 13.4615 33.2; 5125 17.525 13.4615 33.2;
    5126 17.725 13.4615 33.2; 5127 17.925 13.4615 33.2; 5128 15.125 13.6538 33.2;
    5129 15.325 13.6538 33.2; 5130 15.525 13.6538 33.2; 5131 15.725 13.6538 33.2;
    5132 15.925 13.6538 33.2; 5133 16.125 13.6538 33.2; 5134 16.325 13.6538 33.2;
    5135 16.525 13.6538 33.2; 5136 16.725 13.6538 33.2; 5137 16.925 13.6538 33.2;
    5138 17.125 13.6538 33.2; 5139 17.325 13.6538 33.2; 5140 17.525 13.6538 33.2;
    5141 17.725 13.6538 33.2; 5142 17.925 13.6538 33.2; 5143 15.125 13.8462 33.2;
    5144 15.325 13.8462 33.2; 5145 15.525 13.8462 33.2; 5146 15.725 13.8462 33.2;
    5147 15.925 13.8462 33.2; 5148 16.125 13.8462 33.2; 5149 16.325 13.8462 33.2;
    5150 16.525 13.8462 33.2; 5151 16.725 13.8462 33.2; 5152 16.925 13.8462 33.2;
    5153 17.125 13.8462 33.2; 5154 17.325 13.8462 33.2; 5155 17.525 13.8462 33.2;
    5156 17.725 13.8462 33.2; 5157 17.925 13.8462 33.2; 5158 15.125 14.0385 33.2;
    5159 15.325 14.0385 33.2; 5160 15.525 14.0385 33.2; 5161 15.725 14.0385 33.2;
    5162 15.925 14.0385 33.2; 5163 16.125 14.0385 33.2; 5164 16.325 14.0385 33.2;
    5165 16.525 14.0385 33.2; 5166 16.725 14.0385 33.2; 5167 16.925 14.0385 33.2;
    5168 17.125 14.0385 33.2; 5169 17.325 14.0385 33.2; 5170 17.525 14.0385 33.2;
    5171 17.725 14.0385 33.2; 5172 17.925 14.0385 33.2; 5173 15.125 14.2308 33.2;
    5174 15.325 14.2308 33.2; 5175 15.525 14.2308 33.2; 5176 15.725 14.2308 33.2;
    5177 15.925 14.2308 33.2; 5178 16.125 14.2308 33.2; 5179 16.325 14.2308 33.2;
    5180 16.525 14.2308 33.2; 5181 16.725 14.2308 33.2; 5182 16.925 14.2308 33.2;
    5183 17.125 14.2308 33.2; 5184 17.325 14.2308 33.2; 5185 17.525 14.2308 33.2;
    5186 17.725 14.2308 33.2; 5187 17.925 14.2308 33.2; 5188 15.125 14.4231 33.2;
    5189 15.325 14.4231 33.2; 5190 15.525 14.4231 33.2; 5191 15.725 14.4231 33.2;
    5192 15.925 14.4231 33.2; 5193 16.125 14.4231 33.2; 5194 16.325 14.4231 33.2;
    5195 16.525 14.4231 33.2; 5196 16.725 14.4231 33.2; 5197 16.925 14.4231 33.2;
    5198 17.125 14.4231 33.2; 5199 17.325 14.4231 33.2; 5200 17.525 14.4231 33.2;
    5201 17.725 14.4231 33.2; 5202 17.925 14.4231 33.2; 5203 15.125 14.6154 33.2;
    5204 15.325 14.6154 33.2; 5205 15.525 14.6154 33.2; 5206 15.725 14.6154 33.2;
    5207 15.925 14.6154 33.2; 5208 16.125 14.6154 33.2; 5209 16.325 14.6154 33.2;
    5210 16.525 14.6154 33.2; 5211 16.725 14.6154 33.2; 5212 16.925 14.6154 33.2;
    5213 17.125 14.6154 33.2; 5214 17.325 14.6154 33.2; 5215 17.525 14.6154 33.2;
    5216 17.725 14.6154 33.2; 5217 17.925 14.6154 33.2; 5218 15.125 14.8077 33.2;
    5219 15.325 14.8077 33.2; 5220 15.525 14.8077 33.2; 5221 15.725 14.8077 33.2;
    5222 15.925 14.8077 33.2; 5223 16.125 14.8077 33.2; 5224 16.325 14.8077 33.2;
    5225 16.525 14.8077 33.2; 5226 16.725 14.8077 33.2; 5227 16.925 14.8077 33.2;
    5228 17.125 14.8077 33.2; 5229 17.325 14.8077 33.2; 5230 17.525 14.8077 33.2;
    5231 17.725 14.8077 33.2; 5232 17.925 14.8077 33.2; 5233 15.125 15 33.2;
    5234 15.325 15 33.2; 5235 15.525 15 33.2; 5236 15.725 15 33.2;
    5237 15.925 15 33.2; 5238 16.125 15 33.2; 5239 16.325 15 33.2;
    5240 16.525 15 33.2; 5241 16.725 15 33.2; 5242 16.925 15 33.2;
    5243 17.125 15 33.2; 5244 17.325 15 33.2; 5245 17.525 15 33.2;
    5246 17.725 15 33.2; 5247 17.925 15 33.2; 5248 15.125 15.1923 33.2;
    5249 15.325 15.1923 33.2; 5250 15.525 15.1923 33.2; 5251 15.725 15.1923 33.2;
    5252 15.925 15.1923 33.2; 5253 16.125 15.1923 33.2; 5254 16.325 15.1923 33.2;
    5255 16.525 15.1923 33.2; 5256 16.725 15.1923 33.2; 5257 16.925 15.1923 33.2;
    5258 17.125 15.1923 33.2; 5259 17.325 15.1923 33.2; 5260 17.525 15.1923 33.2;
    5261 17.725 15.1923 33.2; 5262 17.925 15.1923 33.2; 5263 15.125 15.3846 33.2;
    5264 15.325 15.3846 33.2; 5265 15.525 15.3846 33.2; 5266 15.725 15.3846 33.2;
    5267 15.925 15.3846 33.2; 5268 16.125 15.3846 33.2; 5269 16.325 15.3846 33.2;
    5270 16.525 15.3846 33.2; 5271 16.725 15.3846 33.2; 5272 16.925 15.3846 33.2;
    5273 17.125 15.3846 33.2; 5274 17.325 15.3846 33.2; 5275 17.525 15.3846 33.2;
    5276 17.725 15.3846 33.2; 5277 17.925 15.3846 33.2; 5278 15.125 15.5769 33.2;
    5279 15.325 15.5769 33.2; 5280 15.525 15.5769 33.2; 5281 15.725 15.5769 33.2;
    5282 15.925 15.5769 33.2; 5283 16.125 15.5769 33.2; 5284 16.325 15.5769 33.2;
    5285 16.525 15.5769 33.2; 5286 16.725 15.5769 33.2; 5287 16.925 15.5769 33.2;
    5288 17.125 15.5769 33.2; 5289 17.325 15.5769 33.2; 5290 17.525 15.5769 33.2;
    5291 17.725 15.5769 33.2; 5292 17.925 15.5769 33.2; 5293 15.125 15.7692 33.2;
    5294 15.325 15.7692 33.2; 5295 15.525 15.7692 33.2; 5296 15.725 15.7692 33.2;
    5297 15.925 15.7692 33.2; 5298 16.125 15.7692 33.2; 5299 16.325 15.7692 33.2;
    5300 16.525 15.7692 33.2; 5301 16.725 15.7692 33.2; 5302 16.925 15.7692 33.2;
    5303 17.125 15.7692 33.2; 5304 17.325 15.7692 33.2; 5305 17.525 15.7692 33.2;
    5306 17.725 15.7692 33.2; 5307 17.925 15.7692 33.2; 5308 15.125 15.9615 33.2;
    5309 15.325 15.9615 33.2; 5310 15.525 15.9615 33.2; 5311 15.725 15.9615 33.2;
    5312 15.925 15.9615 33.2; 5313 16.125 15.9615 33.2; 5314 16.325 15.9615 33.2;
    5315 16.525 15.9615 33.2; 5316 16.725 15.9615 33.2; 5317 16.925 15.9615 33.2;
    5318 17.125 15.9615 33.2; 5319 17.325 15.9615 33.2; 5320 17.525 15.9615 33.2;
    5321 17.725 15.9615 33.2; 5322 17.925 15.9615 33.2; 5323 15.125 16.1538 33.2;
    5324 15.325 16.1538 33.2; 5325 15.525 16.1538 33.2; 5326 15.725 16.1538 33.2;
    5327 15.925 16.1538 33.2; 5328 16.125 16.1538 33.2; 5329 16.325 16.1538 33.2;
    5330 16.525 16.1538 33.2; 5331 16.725 16.1538 33.2; 5332 16.925 16.1538 33.2;
    5333 17.125 16.1538 33.2; 5334 17.325 16.1538 33.2; 5335 17.525 16.1538 33.2;
    5336 17.725 16.1538 33.2; 5337 17.925 16.1538 33.2; 5338 15.125 16.3462 33.2;
    5339 15.325 16.3462 33.2; 5340 15.525 16.3462 33.2; 5341 15.725 16.3462 33.2;
    5342 15.925 16.3462 33.2; 5343 16.125 16.3462 33.2; 5344 16.325 16.3462 33.2;
    5345 16.525 16.3462 33.2; 5346 16.725 16.3462 33.2; 5347 16.925 16.3462 33.2;
    5348 17.125 16.3462 33.2; 5349 17.325 16.3462 33.2; 5350 17.525 16.3462 33.2;
    5351 17.725 16.3462 33.2; 5352 17.925 16.3462 33.2; 5353 15.125 16.5385 33.2;
    5354 15.325 16.5385 33.2; 5355 15.525 16.5385 33.2; 5356 15.725 16.5385 33.2;
    5357 15.925 16.5385 33.2; 5358 16.125 16.5385 33.2; 5359 16.325 16.5385 33.2;
    5360 16.525 16.5385 33.2; 5361 16.725 16.5385 33.2; 5362 16.925 16.5385 33.2;
    5363 17.125 16.5385 33.2; 5364 17.325 16.5385 33.2; 5365 17.525 16.5385 33.2;
    5366 17.725 16.5385 33.2; 5367 17.925 16.5385 33.2; 5368 15.125 16.7308 33.2;
    5369 15.325 16.7308 33.2; 5370 15.525 16.7308 33.2; 5371 15.725 16.7308 33.2;
    5372 15.925 16.7308 33.2; 5373 16.125 16.7308 33.2; 5374 16.325 16.7308 33.2;
    5375 16.525 16.7308 33.2; 5376 16.725 16.7308 33.2; 5377 16.925 16.7308 33.2;
    5378 17.125 16.7308 33.2; 5379 17.325 16.7308 33.2; 5380 17.525 16.7308 33.2;
    5381 17.725 16.7308 33.2; 5382 17.925 16.7308 33.2; 5383 15.125 16.9231 33.2;
    5384 15.325 16.9231 33.2; 5385 15.525 16.9231 33.2; 5386 15.725 16.9231 33.2;
    5387 15.925 16.9231 33.2; 5388 16.125 16.9231 33.2; 5389 16.325 16.9231 33.2;
    5390 16.525 16.9231 33.2; 5391 16.725 16.9231 33.2; 5392 16.925 16.9231 33.2;
    5393 17.125 16.9231 33.2; 5394 17.325 16.9231 33.2; 5395 17.525 16.9231 33.2;
    5396 17.725 16.9231 33.2; 5397 17.925 16.9231 33.2; 5398 15.125 17.1154 33.2;
    5399 15.325 17.1154 33.2; 5400 15.525 17.1154 33.2; 5401 15.725 17.1154 33.2;
    5402 15.925 17.1154 33.2; 5403 16.125 17.1154 33.2; 5404 16.325 17.1154 33.2;
    5405 16.525 17.1154 33.2; 5406 16.725 17.1154 33.2; 5407 16.925 17.1154 33.2;
    5408 17.125 17.1154 33.2; 5409 17.325 17.1154 33.2; 5410 17.525 17.1154 33.2;
    5411 17.725 17.1154 33.2; 5412 17.925 17.1154 33.2; 5413 15.125 17.3077 33.2;
    5414 15.325 17.3077 33.2; 5415 15.525 17.3077 33.2; 5416 15.725 17.3077 33.2;
    5417 15.925 17.3077 33.2; 5418 16.125 17.3077 33.2; 5419 16.325 17.3077 33.2;
    5420 16.525 17.3077 33.2; 5421 16.725 17.3077 33.2; 5422 16.925 17.3077 33.2;
    5423 17.125 17.3077 33.2; 5424 17.325 17.3077 33.2; 5425 17.525 17.3077 33.2;
    5426 17.725 17.3077 33.2; 5427 17.925 17.3077 33.2;
    MEMBER INCIDENCES
    1 1 2; 2 2 3; 3 3 4; 4 4 5; 5 1 6; 6 2 7; 7 3 8; 8 4 9; 9 5 10; 10 6 7; 11 7 8;
    12 8 9; 13 9 10; 14 6 11; 15 7 12; 16 8 13; 17 9 14; 18 10 15; 19 11 12;
    20 12 13; 21 13 14; 22 14 15; 23 11 16; 24 12 17; 25 13 18; 26 14 19; 27 15 20;
    28 16 17; 29 17 18; 30 18 19; 31 19 20; 32 16 21; 33 17 22; 34 18 23; 35 19 24;
    36 20 25; 37 21 22; 38 22 23; 39 23 24; 40 24 25; 41 21 26; 42 22 27; 43 23 28;
    44 24 29; 45 25 30; 46 26 27; 47 27 28; 48 28 29; 50 26 31; 51 27 32; 52 28 33;
    54 30 35; 55 31 32; 56 32 33; 57 33 34; 58 34 35; 59 1 36; 60 2 37; 61 3 38;
    62 4 39; 63 5 40; 64 6 41; 65 7 42; 66 8 43; 67 9 44; 68 10 45; 69 11 46;
    70 12 47; 71 13 48; 72 14 49; 73 15 50; 74 16 51; 75 17 52; 76 18 53; 77 19 54;
    78 20 55; 79 21 56; 80 22 57; 81 23 58; 82 24 59; 83 25 60; 84 26 61; 85 27 62;
    86 28 63; 87 29 1016; 88 30 65; 89 31 66; 90 32 67; 91 33 68; 92 34 69;
    93 35 70; 94 36 37; 95 37 211; 96 38 212; 97 39 40; 98 36 41; 99 37 42;
    100 38 43; 101 39 330; 102 40 331; 103 41 42; 104 42 214; 105 43 215;
    106 44 216; 107 41 46; 108 42 47; 109 43 48; 110 44 49; 111 45 50; 112 46 47;
    113 47 217; 114 48 218; 115 49 219; 116 46 51; 117 47 52; 118 48 53; 119 49 54;
    120 50 55; 121 51 52; 122 52 220; 123 53 221; 124 54 222; 125 51 56; 126 52 57;
    127 53 58; 128 54 59; 129 55 60; 130 56 57; 131 57 223; 132 58 224; 133 59 225;
    134 56 61; 135 57 62; 136 58 63; 137 59 64; 138 60 65; 139 61 62; 140 62 226;
    141 63 227; 143 61 66; 144 62 67; 145 63 68; 147 65 70; 148 66 67; 149 67 229;
    150 68 230; 151 69 70; 153 37 72; 154 38 73; 155 39 74; 156 40 75; 158 42 77;
    159 43 78; 160 44 79; 161 45 80; 163 47 82; 164 48 83; 165 49 84; 166 50 85;
    168 52 87; 169 53 88; 170 54 89; 171 55 90; 173 57 92; 174 58 93; 175 59 94;
    176 60 95; 178 62 97; 179 63 98; 180 64 2283; 181 65 100; 183 67 102;
    184 68 103; 185 69 104; 186 70 105; 188 72 232; 189 73 233; 190 74 75;
    192 72 77; 193 73 78; 194 74 332; 195 75 333; 197 77 235; 198 78 236;
    199 79 237; 201 77 82; 202 78 83; 203 79 84; 204 80 85; 206 82 238; 207 83 239;
    208 84 240; 210 82 87; 211 83 88; 212 84 89; 213 85 90; 215 87 241; 216 88 242;
    217 89 243; 219 87 92; 220 88 93; 221 89 94; 222 90 95; 224 92 244; 225 93 245;
    226 94 246; 228 92 97; 229 93 98; 230 94 99; 231 95 100; 233 97 247;
    234 98 248; 237 97 102; 238 98 103; 240 100 105; 242 102 250; 243 103 251;
    244 104 105; 246 72 107; 247 73 108; 248 74 109; 249 75 110; 251 77 112;
    252 78 113; 253 79 114; 254 80 115; 256 82 117; 257 83 118; 258 84 119;
    259 85 120; 261 87 122; 262 88 123; 263 89 124; 264 90 125; 266 92 127;
    267 93 128; 268 94 129; 269 95 130; 271 97 132; 272 98 133; 273 99 3250;
    274 100 135; 276 102 137; 277 103 138; 278 104 139; 279 105 140; 281 107 253;
    282 108 254; 283 109 110; 285 107 112; 286 108 113; 287 109 334; 288 110 335;
    290 112 256; 291 113 257; 292 114 258; 294 112 117; 295 113 118; 296 114 119;
    297 115 120; 299 117 259; 300 118 260; 301 119 261; 303 117 122; 304 118 123;
    305 119 124; 306 120 125; 308 122 262; 309 123 263; 310 124 264; 312 122 127;
    313 123 128; 314 124 129; 315 125 130; 317 127 265; 318 128 266; 319 129 267;
    321 127 132; 322 128 133; 323 129 134; 324 130 135; 326 132 268; 327 133 269;
    330 132 137; 331 133 138; 333 135 140; 335 137 271; 336 138 272; 337 139 140;
    339 107 142; 340 108 143; 341 109 144; 342 110 145; 344 112 147; 345 113 148;
    346 114 149; 347 115 150; 349 117 152; 352 120 155; 354 122 157; 357 125 160;
    359 127 162; 362 130 165; 364 132 167; 367 135 170; 369 137 172; 370 138 173;
    371 139 174; 372 140 175; 374 142 274; 375 143 275; 376 144 145; 378 142 147;
    379 143 148; 380 144 336; 381 145 337; 383 147 277; 384 148 278; 385 149 279;
    387 147 152; 388 148 153; 389 149 154; 390 150 155; 392 152 280; 393 153 281;
    394 154 282; 396 152 157; 397 153 158; 398 154 159; 399 155 160; 401 157 283;
    402 158 284; 403 159 285; 405 157 162; 406 158 163; 407 159 164; 408 160 165;
    410 162 286; 411 163 287; 412 164 288; 414 162 167; 415 163 168; 416 164 169;
    417 165 170; 419 167 289; 420 168 290; 423 167 172; 424 168 173; 426 170 175;
    428 172 292; 429 173 293; 430 174 175; 524 211 38; 525 212 39; 527 214 43;
    528 215 44; 529 216 45; 530 217 48; 531 218 49; 532 219 50; 533 220 53;
    534 221 54; 535 222 55; 536 223 58; 537 224 59; 538 225 60; 539 226 63;
    540 227 64; 542 229 68; 543 230 69; 545 211 214; 546 214 217; 547 217 220;
    548 220 223; 549 223 226; 550 226 229; 551 212 215; 552 215 218; 553 218 221;
    554 221 224; 555 224 227; 556 227 230; 558 216 219; 559 219 222; 560 222 225;
    561 225 228; 563 232 73; 564 233 74; 566 235 78; 567 236 79; 568 237 80;
    569 238 83; 570 239 84; 571 240 85; 572 241 88; 573 242 89; 574 243 90;
    575 244 93; 576 245 94; 577 246 95; 578 247 98; 579 248 99; 581 250 103;
    582 251 104; 584 232 235; 585 235 238; 586 238 241; 587 241 244; 588 244 247;
    589 247 250; 590 233 236; 591 236 239; 592 239 242; 593 242 245; 594 245 248;
    595 248 251; 597 237 240; 598 240 243; 599 243 246; 600 246 249; 602 253 108;
    603 254 109; 605 256 113; 606 257 114; 607 258 115; 608 259 118; 609 260 119;
    610 261 120; 611 262 123; 612 263 124; 613 264 125; 614 265 128; 615 266 129;
    616 267 130; 617 268 133; 618 269 134; 620 271 138; 621 272 139; 623 253 256;
    624 256 259; 625 259 262; 626 262 265; 627 265 268; 628 268 271; 629 254 257;
    630 257 260; 631 260 263; 632 263 266; 633 266 269; 634 269 272; 636 258 261;
    637 261 264; 638 264 267; 639 267 270; 641 274 143; 642 275 144; 644 277 148;
    645 278 149; 646 279 150; 647 280 153; 648 281 154; 649 282 155; 650 283 158;
    651 284 159; 652 285 160; 653 286 163; 654 287 164; 655 288 165; 656 289 168;
    657 290 169; 659 292 173; 660 293 174; 662 274 277; 663 277 280; 664 280 283;
    665 283 286; 666 286 289; 667 289 292; 668 275 278; 669 278 281; 670 281 284;
    671 284 287; 672 287 290; 673 290 293; 675 279 282; 676 282 285; 677 285 288;
    678 288 291; 680 1 295; 681 2 296; 682 3 297; 683 4 298; 684 5 299; 685 6 300;
    686 7 301; 687 8 302; 688 9 303; 689 10 304; 690 11 305; 691 12 306;
    692 13 307; 693 14 308; 694 15 309; 695 16 310; 696 17 311; 697 18 312;
    698 19 313; 699 20 314; 700 21 315; 701 22 316; 702 23 317; 703 24 318;
    704 25 319; 705 26 320; 706 27 321; 707 28 322; 708 29 397; 709 30 324;
    710 31 325; 711 32 326; 712 33 327; 713 34 328; 714 35 329; 715 330 44;
    716 331 45; 717 330 331; 720 332 333; 723 334 335; 726 336 337; 727 332 79;
    728 333 80; 729 334 114; 730 335 115; 731 336 149; 732 337 150; 733 142 338;
    734 143 339; 735 144 340; 736 145 341; 737 147 342; 738 148 343; 739 149 344;
    740 150 345; 741 338 342; 742 339 343; 743 340 344; 744 341 345; 745 338 339;
    746 339 340; 747 340 341; 748 342 343; 749 343 344; 750 344 345; 751 66 346;
    752 67 347; 753 68 348; 754 69 349; 755 70 350; 756 229 351; 757 230 352;
    758 346 347; 759 347 351; 760 348 352; 761 349 350; 762 351 348; 763 352 349;
    765 102 355; 766 103 356; 767 104 357; 768 105 358; 769 250 359; 770 251 360;
    772 355 359; 773 356 360; 774 357 358; 775 359 356; 776 360 357; 778 137 363;
    779 138 364; 780 139 365; 781 140 366; 782 271 367; 783 272 368; 785 363 367;
    786 364 368; 787 365 366; 788 367 364; 789 368 365; 790 134 4217; 791 369 30;
    792 370 65; 793 371 100; 794 372 135; 795 373 170; 796 369 1056; 797 370 2313;
    798 371 3280; 799 369 413; 800 372 4255; 807 375 1430; 808 376 2707;
    809 377 3674; 810 375 619; 811 378 4637; 812 381 34; 814 382 69; 816 383 104;
    818 384 139; 820 385 174; 823 381 1836; 824 382 2963; 825 383 3930;
    826 381 820; 827 384 5013; 828 387 323; 829 388 387; 830 389 388; 831 390 389;
    832 391 390; 833 392 391; 834 393 392; 835 394 393; 836 395 394; 837 396 395;
    838 397 396; 854 413 414; 855 414 415; 856 415 416; 857 416 417; 858 417 418;
    859 418 419; 860 419 420; 861 420 421; 862 421 422; 863 422 423; 864 423 374;
    1072 619 620; 1073 620 621; 1074 621 622; 1075 622 623; 1076 623 624;
    1077 624 625; 1078 625 626; 1079 626 627; 1080 627 628; 1081 628 629;
    1082 629 380; 1275 810 386; 1276 811 810; 1277 812 811; 1278 813 812;
    1279 814 813; 1280 815 814; 1281 816 815; 1282 817 816; 1283 818 817;
    1284 819 818; 1285 820 819; 1493 1016 64; 1507 1030 370; 1508 1031 1030;
    1509 1032 1031; 1510 1033 1032; 1511 1034 1033; 1512 1035 1034; 1513 1036 1035;
    1514 1037 1036; 1515 1038 1037; 1516 1039 1038; 1517 1040 1039; 1518 1041 1040;
    1519 1042 1041; 1520 1043 1042; 1521 1044 1043; 1522 1045 1044; 1523 1046 1045;
    1524 1047 1046; 1525 1048 1047; 1526 1049 1048; 1527 1050 1049; 1528 1051 1050;
    1529 1052 1051; 1530 1053 1052; 1531 1054 1053; 1532 1055 1054; 1533 1056 1055;
    1924 1404 376; 1925 1405 1404; 1926 1406 1405; 1927 1407 1406; 1928 1408 1407;
    1929 1409 1408; 1930 1410 1409; 1931 1411 1410; 1932 1412 1411; 1933 1413 1412;
    1934 1414 1413; 1935 1415 1414; 1936 1416 1415; 1937 1417 1416; 1938 1418 1417;
    1939 1419 1418; 1940 1420 1419; 1941 1421 1420; 1942 1422 1421; 1943 1423 1422;
    1944 1424 1423; 1945 1425 1424; 1946 1426 1425; 1947 1427 1426; 1948 1428 1427;
    1949 1429 1428; 1950 1430 1429; 2399 1836 1837; 2400 1837 1838; 2401 1838 1839;
    2402 1839 1840; 2403 1840 1841; 2404 1841 1842; 2405 1842 1843; 2406 1843 1844;
    2407 1844 1845; 2408 1845 1846; 2409 1846 1847; 2410 1847 1848; 2411 1848 1849;
    2412 1849 1850; 2413 1850 1851; 2414 1851 1852; 2415 1852 1853; 2416 1853 1854;
    2417 1854 1855; 2418 1855 1856; 2419 1856 1857; 2420 1857 1858; 2421 1858 1859;
    2422 1859 1860; 2423 1860 1861; 2424 1861 1862; 2425 1862 382; 2889 2283 99;
    2903 2297 371; 2904 2298 2297; 2905 2299 2298; 2906 2300 2299; 2907 2301 2300;
    2908 2302 2301; 2909 2303 2302; 2910 2304 2303; 2911 2305 2304; 2912 2306 2305;
    2913 2307 2306; 2914 2308 2307; 2915 2309 2308; 2916 2310 2309; 2917 2311 2310;
    2918 2312 2311; 2919 2313 2312; 3333 2691 377; 3334 2692 2691; 3335 2693 2692;
    3336 2694 2693; 3337 2695 2694; 3338 2696 2695; 3339 2697 2696; 3340 2698 2697;
    3341 2699 2698; 3342 2700 2699; 3343 2701 2700; 3344 2702 2701; 3345 2703 2702;
    3346 2704 2703; 3347 2705 2704; 3348 2706 2705; 3349 2707 2706; 3638 2963 2964;
    3639 2964 2965; 3640 2965 2966; 3641 2966 2967; 3642 2967 2968; 3643 2968 2969;
    3644 2969 2970; 3645 2970 2971; 3646 2971 2972; 3647 2972 2973; 3648 2973 2974;
    3649 2974 2975; 3650 2975 2976; 3651 2976 2977; 3652 2977 2978; 3653 2978 2979;
    3654 2979 383; 3958 3250 134; 3972 3264 372; 3973 3265 3264; 3974 3266 3265;
    3975 3267 3266; 3976 3268 3267; 3977 3269 3268; 3978 3270 3269; 3979 3271 3270;
    3980 3272 3271; 3981 3273 3272; 3982 3274 3273; 3983 3275 3274; 3984 3276 3275;
    3985 3277 3276; 3986 3278 3277; 3987 3279 3278; 3988 3280 3279; 4402 3658 378;
    4403 3659 3658; 4404 3660 3659; 4405 3661 3660; 4406 3662 3661; 4407 3663 3662;
    4408 3664 3663; 4409 3665 3664; 4410 3666 3665; 4411 3667 3666; 4412 3668 3667;
    4413 3669 3668; 4414 3670 3669; 4415 3671 3670; 4416 3672 3671; 4417 3673 3672;
    4418 3674 3673; 4707 3930 3931; 4708 3931 3932; 4709 3932 3933; 4710 3933 3934;
    4711 3934 3935; 4712 3935 3936; 4713 3936 3937; 4714 3937 3938; 4715 3938 3939;
    4716 3939 3940; 4717 3940 3941; 4718 3941 3942; 4719 3942 3943; 4720 3943 3944;
    4721 3944 3945; 4722 3945 3946; 4723 3946 384; 5027 4217 169; 5041 4231 373;
    5042 4232 4231; 5043 4233 4232; 5044 4234 4233; 5045 4235 4234; 5046 4236 4235;
    5047 4237 4236; 5048 4238 4237; 5049 4239 4238; 5050 4240 4239; 5051 4241 4240;
    5052 4242 4241; 5053 4243 4242; 5054 4244 4243; 5055 4245 4244; 5056 4246 4245;
    5057 4247 4246; 5058 4248 4247; 5059 4249 4248; 5060 4250 4249; 5061 4251 4250;
    5062 4252 4251; 5063 4253 4252; 5064 4254 4253; 5065 4255 4254; 5463 4613 379;
    5464 4614 4613; 5465 4615 4614; 5466 4616 4615; 5467 4617 4616; 5468 4618 4617;
    5469 4619 4618; 5470 4620 4619; 5471 4621 4620; 5472 4622 4621; 5473 4623 4622;
    5474 4624 4623; 5475 4625 4624; 5476 4626 4625; 5477 4627 4626; 5478 4628 4627;
    5479 4629 4628; 5480 4630 4629; 5481 4631 4630; 5482 4632 4631; 5483 4633 4632;
    5484 4634 4633; 5485 4635 4634; 5486 4636 4635; 5487 4637 4636; 5904 5013 5014;
    5905 5014 5015; 5906 5015 5016; 5907 5016 5017; 5908 5017 5018; 5909 5018 5019;
    5910 5019 5020; 5911 5020 5021; 5912 5021 5022; 5913 5022 5023; 5914 5023 5024;
    5915 5024 5025; 5916 5025 5026; 5917 5026 5027; 5918 5027 5028; 5919 5028 5029;
    5920 5029 5030; 5921 5030 5031; 5922 5031 5032; 5923 5032 5033; 5924 5033 5034;
    5925 5034 5035; 5926 5035 5036; 5927 5036 5037; 5928 5037 385;
    ELEMENT INCIDENCES SHELL
    865 387 439 438 323; 866 439 440 437 438; 867 440 441 436 437;
    868 441 442 435 436; 869 442 443 434 435; 870 443 444 433 434;
    871 444 445 432 433; 872 445 446 431 432; 873 446 447 430 431;
    874 447 448 429 430; 875 448 449 428 429; 876 449 450 427 428;
    877 450 451 426 427; 878 451 452 425 426; 879 452 453 424 425;
    880 453 423 374 424; 881 388 454 439 387; 882 454 455 440 439;
    883 455 456 441 440; 884 456 457 442 441; 885 457 458 443 442;
    886 458 459 444 443; 887 459 460 445 444; 888 460 461 446 445;
    889 461 462 447 446; 890 462 463 448 447; 891 463 464 449 448;
    892 464 465 450 449; 893 465 466 451 450; 894 466 467 452 451;
    895 467 468 453 452; 896 468 422 423 453; 897 389 469 454 388;
    898 469 470 455 454; 899 470 471 456 455; 900 471 472 457 456;
    901 472 473 458 457; 902 473 474 459 458; 903 474 475 460 459;
    904 475 476 461 460; 905 476 477 462 461; 906 477 478 463 462;
    907 478 479 464 463; 908 479 480 465 464; 909 480 481 466 465;
    910 481 482 467 466; 911 482 483 468 467; 912 483 421 422 468;
    913 390 484 469 389; 914 484 485 470 469; 915 485 486 471 470;
    916 486 487 472 471; 917 487 488 473 472; 918 488 489 474 473;
    919 489 490 475 474; 920 490 491 476 475; 921 491 492 477 476;
    922 492 493 478 477; 923 493 494 479 478; 924 494 495 480 479;
    925 495 496 481 480; 926 496 497 482 481; 927 497 498 483 482;
    928 498 420 421 483; 929 391 499 484 390; 930 499 500 485 484;
    931 500 501 486 485; 932 501 502 487 486; 933 502 503 488 487;
    934 503 504 489 488; 935 504 505 490 489; 936 505 506 491 490;
    937 506 507 492 491; 938 507 508 493 492; 939 508 509 494 493;
    940 509 510 495 494; 941 510 511 496 495; 942 511 512 497 496;
    943 512 513 498 497; 944 513 419 420 498; 945 392 514 499 391;
    946 514 515 500 499; 947 515 516 501 500; 948 516 517 502 501;
    949 517 518 503 502; 950 518 519 504 503; 951 519 520 505 504;
    952 520 521 506 505; 953 521 522 507 506; 954 522 523 508 507;
    955 523 524 509 508; 956 524 525 510 509; 957 525 526 511 510;
    958 526 527 512 511; 959 527 528 513 512; 960 528 418 419 513;
    961 393 529 514 392; 962 529 530 515 514; 963 530 531 516 515;
    964 531 532 517 516; 965 532 533 518 517; 966 533 534 519 518;
    967 534 535 520 519; 968 535 536 521 520; 969 536 537 522 521;
    970 537 538 523 522; 971 538 539 524 523; 972 539 540 525 524;
    973 540 541 526 525; 974 541 542 527 526; 975 542 543 528 527;
    976 543 417 418 528; 977 394 544 529 393; 978 544 545 530 529;
    979 545 546 531 530; 980 546 547 532 531; 981 547 548 533 532;
    982 548 549 534 533; 983 549 550 535 534; 984 550 551 536 535;
    985 551 552 537 536; 986 552 553 538 537; 987 553 554 539 538;
    988 554 555 540 539; 989 555 556 541 540; 990 556 557 542 541;
    991 557 558 543 542; 992 558 416 417 543; 993 395 559 544 394;
    994 559 560 545 544; 995 560 561 546 545; 996 561 562 547 546;
    997 562 563 548 547; 998 563 564 549 548; 999 564 565 550 549;
    1000 565 566 551 550; 1001 566 567 552 551; 1002 567 568 553 552;
    1003 568 569 554 553; 1004 569 570 555 554; 1005 570 571 556 555;
    1006 571 572 557 556; 1007 572 573 558 557; 1008 573 415 416 558;
    1009 396 574 559 395; 1010 574 575 560 559; 1011 575 576 561 560;
    1012 576 577 562 561; 1013 577 578 563 562; 1014 578 579 564 563;
    1015 579 580 565 564; 1016 580 581 566 565; 1017 581 582 567 566;
    1018 582 583 568 567; 1019 583 584 569 568; 1020 584 585 570 569;
    1021 585 586 571 570; 1022 586 587 572 571; 1023 587 588 573 572;
    1024 588 414 415 573; 1025 397 589 574 396; 1026 589 590 575 574;
    1027 590 591 576 575; 1028 591 592 577 576; 1029 592 593 578 577;
    1030 593 594 579 578; 1031 594 595 580 579; 1032 595 596 581 580;
    1033 596 597 582 581; 1034 597 598 583 582; 1035 598 599 584 583;
    1036 599 600 585 584; 1037 600 601 586 585; 1038 601 602 587 586;
    1039 602 603 588 587; 1040 603 413 414 588; 1041 29 398 589 397;
    1042 398 399 590 589; 1043 399 400 591 590; 1044 400 401 592 591;
    1045 401 402 593 592; 1046 402 403 594 593; 1047 403 404 595 594;
    1048 404 405 596 595; 1049 405 406 597 596; 1050 406 407 598 597;
    1051 407 408 599 598; 1052 408 409 600 599; 1053 409 410 601 600;
    1054 410 411 602 601; 1055 411 412 603 602; 1056 412 369 413 603;
    1083 423 645 644 374; 1084 645 646 643 644; 1085 646 647 642 643;
    1086 647 648 641 642; 1087 648 649 640 641; 1088 649 650 639 640;
    1089 650 651 638 639; 1090 651 652 637 638; 1091 652 653 636 637;
    1092 653 654 635 636; 1093 654 655 634 635; 1094 655 656 633 634;
    1095 656 657 632 633; 1096 657 658 631 632; 1097 658 659 630 631;
    1098 659 629 380 630; 1099 422 660 645 423; 1100 660 661 646 645;
    1101 661 662 647 646; 1102 662 663 648 647; 1103 663 664 649 648;
    1104 664 665 650 649; 1105 665 666 651 650; 1106 666 667 652 651;
    1107 667 668 653 652; 1108 668 669 654 653; 1109 669 670 655 654;
    1110 670 671 656 655; 1111 671 672 657 656; 1112 672 673 658 657;
    1113 673 674 659 658; 1114 674 628 629 659; 1115 421 675 660 422;
    1116 675 676 661 660; 1117 676 677 662 661; 1118 677 678 663 662;
    1119 678 679 664 663; 1120 679 680 665 664; 1121 680 681 666 665;
    1122 681 682 667 666; 1123 682 683 668 667; 1124 683 684 669 668;
    1125 684 685 670 669; 1126 685 686 671 670; 1127 686 687 672 671;
    1128 687 688 673 672; 1129 688 689 674 673; 1130 689 627 628 674;
    1131 420 690 675 421; 1132 690 691 676 675; 1133 691 692 677 676;
    1134 692 693 678 677; 1135 693 694 679 678; 1136 694 695 680 679;
    1137 695 696 681 680; 1138 696 697 682 681; 1139 697 698 683 682;
    1140 698 699 684 683; 1141 699 700 685 684; 1142 700 701 686 685;
    1143 701 702 687 686; 1144 702 703 688 687; 1145 703 704 689 688;
    1146 704 626 627 689; 1147 419 705 690 420; 1148 705 706 691 690;
    1149 706 707 692 691; 1150 707 708 693 692; 1151 708 709 694 693;
    1152 709 710 695 694; 1153 710 711 696 695; 1154 711 712 697 696;
    1155 712 713 698 697; 1156 713 714 699 698; 1157 714 715 700 699;
    1158 715 716 701 700; 1159 716 717 702 701; 1160 717 718 703 702;
    1161 718 719 704 703; 1162 719 625 626 704; 1163 418 720 705 419;
    1164 720 721 706 705; 1165 721 722 707 706; 1166 722 723 708 707;
    1167 723 724 709 708; 1168 724 725 710 709; 1169 725 726 711 710;
    1170 726 727 712 711; 1171 727 728 713 712; 1172 728 729 714 713;
    1173 729 730 715 714; 1174 730 731 716 715; 1175 731 732 717 716;
    1176 732 733 718 717; 1177 733 734 719 718; 1178 734 624 625 719;
    1179 417 735 720 418; 1180 735 736 721 720; 1181 736 737 722 721;
    1182 737 738 723 722; 1183 738 739 724 723; 1184 739 740 725 724;
    1185 740 741 726 725; 1186 741 742 727 726; 1187 742 743 728 727;
    1188 743 744 729 728; 1189 744 745 730 729; 1190 745 746 731 730;
    1191 746 747 732 731; 1192 747 748 733 732; 1193 748 749 734 733;
    1194 749 623 624 734; 1195 416 750 735 417; 1196 750 751 736 735;
    1197 751 752 737 736; 1198 752 753 738 737; 1199 753 754 739 738;
    1200 754 755 740 739; 1201 755 756 741 740; 1202 756 757 742 741;
    1203 757 758 743 742; 1204 758 759 744 743; 1205 759 760 745 744;
    1206 760 761 746 745; 1207 761 762 747 746; 1208 762 763 748 747;
    1209 763 764 749 748; 1210 764 622 623 749; 1211 415 765 750 416;
    1212 765 766 751 750; 1213 766 767 752 751; 1214 767 768 753 752;
    1215 768 769 754 753; 1216 769 770 755 754; 1217 770 771 756 755;
    1218 771 772 757 756; 1219 772 773 758 757; 1220 773 774 759 758;
    1221 774 775 760 759; 1222 775 776 761 760; 1223 776 777 762 761;
    1224 777 778 763 762; 1225 778 779 764 763; 1226 779 621 622 764;
    1227 414 780 765 415; 1228 780 781 766 765; 1229 781 782 767 766;
    1230 782 783 768 767; 1231 783 784 769 768; 1232 784 785 770 769;
    1233 785 786 771 770; 1234 786 787 772 771; 1235 787 788 773 772;
    1236 788 789 774 773; 1237 789 790 775 774; 1238 790 791 776 775;
    1239 791 792 777 776; 1240 792 793 778 777; 1241 793 794 779 778;
    1242 794 620 621 779; 1243 413 795 780 414; 1244 795 796 781 780;
    1245 796 797 782 781; 1246 797 798 783 782; 1247 798 799 784 783;
    1248 799 800 785 784; 1249 800 801 786 785; 1250 801 802 787 786;
    1251 802 803 788 787; 1252 803 804 789 788; 1253 804 805 790 789;
    1254 805 806 791 790; 1255 806 807 792 791; 1256 807 808 793 792;
    1257 808 809 794 793; 1258 809 619 620 794; 1259 369 604 795 413;
    1260 604 605 796 795; 1261 605 606 797 796; 1262 606 607 798 797;
    1263 607 608 799 798; 1264 608 609 800 799; 1265 609 610 801 800;
    1266 610 611 802 801; 1267 611 612 803 802; 1268 612 613 804 803;
    1269 613 614 805 804; 1270 614 615 806 805; 1271 615 616 807 806;
    1272 616 617 808 807; 1273 617 618 809 808; 1274 618 375 619 809;
    1301 810 851 850 386; 1302 851 852 849 850; 1303 852 853 848 849;
    1304 853 854 847 848; 1305 854 855 846 847; 1306 855 856 845 846;
    1307 856 857 844 845; 1308 857 858 843 844; 1309 858 859 842 843;
    1310 859 860 841 842; 1311 860 861 840 841; 1312 861 862 839 840;
    1313 862 863 838 839; 1314 863 864 837 838; 1315 864 865 836 837;
    1316 865 629 380 836; 1317 811 866 851 810; 1318 866 867 852 851;
    1319 867 868 853 852; 1320 868 869 854 853; 1321 869 870 855 854;
    1322 870 871 856 855; 1323 871 872 857 856; 1324 872 873 858 857;
    1325 873 874 859 858; 1326 874 875 860 859; 1327 875 876 861 860;
    1328 876 877 862 861; 1329 877 878 863 862; 1330 878 879 864 863;
    1331 879 880 865 864; 1332 880 628 629 865; 1333 812 881 866 811;
    1334 881 882 867 866; 1335 882 883 868 867; 1336 883 884 869 868;
    1337 884 885 870 869; 1338 885 886 871 870; 1339 886 887 872 871;
    1340 887 888 873 872; 1341 888 889 874 873; 1342 889 890 875 874;
    1343 890 891 876 875; 1344 891 892 877 876; 1345 892 893 878 877;
    1346 893 894 879 878; 1347 894 895 880 879; 1348 895 627 628 880;
    1349 813 896 881 812; 1350 896 897 882 881; 1351 897 898 883 882;
    1352 898 899 884 883; 1353 899 900 885 884; 1354 900 901 886 885;
    1355 901 902 887 886; 1356 902 903 888 887; 1357 903 904 889 888;
    1358 904 905 890 889; 1359 905 906 891 890; 1360 906 907 892 891;
    1361 907 908 893 892; 1362 908 909 894 893; 1363 909 910 895 894;
    1364 910 626 627 895; 1365 814 911 896 813; 1366 911 912 897 896;
    1367 912 913 898 897; 1368 913 914 899 898; 1369 914 915 900 899;
    1370 915 916 901 900; 1371 916 917 902 901; 1372 917 918 903 902;
    1373 918 919 904 903; 1374 919 920 905 904; 1375 920 921 906 905;
    1376 921 922 907 906; 1377 922 923 908 907; 1378 923 924 909 908;
    1379 924 925 910 909; 1380 925 625 626 910; 1381 815 926 911 814;
    1382 926 927 912 911; 1383 927 928 913 912; 1384 928 929 914 913;
    1385 929 930 915 914; 1386 930 931 916 915; 1387 931 932 917 916;
    1388 932 933 918 917; 1389 933 934 919 918; 1390 934 935 920 919;
    1391 935 936 921 920; 1392 936 937 922 921; 1393 937 938 923 922;
    1394 938 939 924 923; 1395 939 940 925 924; 1396 940 624 625 925;
    1397 816 941 926 815; 1398 941 942 927 926; 1399 942 943 928 927;
    1400 943 944 929 928; 1401 944 945 930 929; 1402 945 946 931 930;
    1403 946 947 932 931; 1404 947 948 933 932; 1405 948 949 934 933;
    1406 949 950 935 934; 1407 950 951 936 935; 1408 951 952 937 936;
    1409 952 953 938 937; 1410 953 954 939 938; 1411 954 955 940 939;
    1412 955 623 624 940; 1413 817 956 941 816; 1414 956 957 942 941;
    1415 957 958 943 942; 1416 958 959 944 943; 1417 959 960 945 944;
    1418 960 961 946 945; 1419 961 962 947 946; 1420 962 963 948 947;
    1421 963 964 949 948; 1422 964 965 950 949; 1423 965 966 951 950;
    1424 966 967 952 951; 1425 967 968 953 952; 1426 968 969 954 953;
    1427 969 970 955 954; 1428 970 622 623 955; 1429 818 971 956 817;
    1430 971 972 957 956; 1431 972 973 958 957; 1432 973 974 959 958;
    1433 974 975 960 959; 1434 975 976 961 960; 1435 976 977 962 961;
    1436 977 978 963 962; 1437 978 979 964 963; 1438 979 980 965 964;
    1439 980 981 966 965; 1440 981 982 967 966; 1441 982 983 968 967;
    1442 983 984 969 968; 1443 984 985 970 969; 1444 985 621 622 970;
    1445 819 986 971 818; 1446 986 987 972 971; 1447 987 988 973 972;
    1448 988 989 974 973; 1449 989 990 975 974; 1450 990 991 976 975;
    1451 991 992 977 976; 1452 992 993 978 977; 1453 993 994 979 978;
    1454 994 995 980 979; 1455 995 996 981 980; 1456 996 997 982 981;
    1457 997 998 983 982; 1458 998 999 984 983; 1459 999 1000 985 984;
    1460 1000 620 621 985; 1461 820 1001 986 819; 1462 1001 1002 987 986;
    1463 1002 1003 988 987; 1464 1003 1004 989 988; 1465 1004 1005 990 989;
    1466 1005 1006 991 990; 1467 1006 1007 992 991; 1468 1007 1008 993 992;
    1469 1008 1009 994 993; 1470 1009 1010 995 994; 1471 1010 1011 996 995;
    1472 1011 1012 997 996; 1473 1012 1013 998 997; 1474 1013 1014 999 998;
    1475 1014 1015 1000 999; 1476 1015 619 620 1000; 1477 381 821 1001 820;
    1478 821 822 1002 1001; 1479 822 823 1003 1002; 1480 823 824 1004 1003;
    1481 824 825 1005 1004; 1482 825 826 1006 1005; 1483 826 827 1007 1006;
    1484 827 828 1008 1007; 1485 828 829 1009 1008; 1486 829 830 1010 1009;
    1487 830 831 1011 1010; 1488 831 832 1012 1011; 1489 832 833 1013 1012;
    1490 833 834 1014 1013; 1491 834 835 1015 1014; 1492 835 375 619 1015;
    1534 1148 1288 1140 1153; 1535 1260 1185 1167 1253; 1536 1110 1160 1175 1321;
    1537 1078 1073 1294 1369; 1538 1062 1094 1065 1285; 1539 1086 1197 1118 1061;
    1540 1175 1033 1034 1143; 1541 1181 1105 1084 1108; 1542 1288 1292 1264 1066;
    1543 1095 1055 1056 1072; 1544 1304 1221 1315 1059; 1545 1205 1099 409 408;
    1546 1102 1190 1192 1350; 1547 1089 1376 1132 1120; 1548 1026 1027 1102 1101;
    1549 1237 1171 1240 1016; 1550 1099 1177 410 409; 1551 1284 1226 1313 1256;
    1552 1157 1030 1031 1197; 1553 1251 1107 1173 1079; 1554 64 1242 1237 1016;
    1555 1315 1300 1062 1285; 1556 1123 1110 1321 1114; 1557 1185 1126 1198 1167;
    1558 1268 1253 1166 1080; 1559 1161 1193 1095 1346; 1560 1359 1297 1142 1263;
    1561 1117 1051 1052 1100; 1562 1297 1308 1125 1142; 1563 1288 1066 1260 1140;
    1564 1018 1019 1277 1069; 1565 1349 1341 1351 1281; 1566 1071 1183 1209 1364;
    1567 1233 1339 1203 1362; 1568 1198 1274 1136 1167; 1569 1350 1192 1365 1334;
    1570 1219 1355 1089 1141; 1571 1183 1106 1093 1209; 1572 1103 1035 1036 1104;
    1573 1185 1134 1363 1126; 1574 1312 1205 408 407; 1575 1115 1210 1323 1232;
    1576 1361 1269 1206 1308; 1577 1240 1348 1333 1335; 1578 1295 1325 1122 1380;
    1579 1352 1163 1177 1099; 1580 1081 1086 1061 1220; 1581 1177 1354 411 410;
    1582 1220 1061 1110 1123; 1583 1182 1053 1054 1193; 1584 1140 1260 1253 1268;
    1585 1217 1138 1377 1057; 1586 1264 1340 1137 1066; 1587 1299 1349 1281 1088;
    1588 1142 1125 1366 1298; 1589 1224 1100 1096 1269; 1590 1225 1164 1239 1292;
    1591 1076 1338 1301 1247; 1592 1212 1275 1207 1213; 1593 1144 1241 1058 1151;
    1594 1215 1133 402 401; 1595 1152 1150 1279 1168; 1596 1312 1323 1099 1205;
    1597 1335 1145 1372 1388; 1598 1229 1060 1221 1304; 1599 1319 1218 1331 1337;
    1600 1365 1322 1154 1124; 1601 1343 1320 1155 1067; 1602 1124 1154 1355 1219;
    1603 1249 1090 1172 1116; 1604 1165 1098 1313 1226; 1605 1072 1056 369 412;
    1606 1222 1367 1336 1322; 1607 1127 1374 1179 1354; 1608 1067 1155 1063 1068;
    1609 1354 1179 412 411; 1610 1248 1057 1144 1307; 1611 1215 1319 1337 1133;
    1612 1096 1250 1107 1251; 1613 1167 1136 1248 1267; 1614 1023 1024 1169 1148;
    1615 1065 1117 1100 1224; 1616 1192 1222 1322 1365; 1617 1197 1031 1032 1118;
    1618 1179 1174 1072 412; 1619 1021 1022 1149 1070; 1620 1137 1303 1134 1185;
    1621 1316 1282 1295 1154; 1622 1024 1025 1112 1169; 1623 1121 1289 1202 1090;
    1624 1073 1249 1116 1294; 1625 1087 1189 1157 1199; 1626 1285 1065 1224 1384;
    1627 1190 1236 1222 1192; 1628 1145 1078 1369 1372; 1629 1171 1071 1348 1240;
    1630 1307 1144 1151 1162; 1631 1162 1151 1278 1093; 1632 1360 1298 1076 1178;
    1633 1344 1038 1039 1305; 1634 1313 1208 1266 1330; 1635 1092 1245 1311 1255;
    1636 1236 1180 1367 1222; 1637 1025 1026 1101 1112; 1638 1068 1063 1138 1217;
    1639 1322 1336 1316 1154; 1640 1372 1369 1319 1215; 1641 1111 1113 1085 1328;
    1642 1118 1032 1033 1175; 1643 1291 1199 1086 1081; 1644 1382 1084 1204 1283;
    1645 1283 1212 1213 1238; 1646 1166 1196 1071 1171; 1647 1380 1122 1147 1074;
    1648 1372 1215 401 400; 1649 1378 1059 1384 1246; 1650 1286 1168 1227 1064;
    1651 1367 1119 1368 1336; 1652 1158 1271 1272 1121; 1653 1142 1298 1360 1332;
    1654 1101 1102 1244 1164; 1655 1234 1230 1352 1099; 1656 1385 1060 1229 1311;
    1657 1341 1079 1173 1351; 1658 1186 1200 1314 1290; 1659 228 370 1189 1201;
    1660 1116 1172 1261 1218; 1661 1335 1333 1228 1145; 1662 1169 1159 1288 1148;
    1663 1263 1142 1332 1233; 1664 1388 1372 399 398; 1665 1294 1116 1218 1319;
    1666 1180 1087 1199 1291; 1667 1104 1036 1037 1252; 1668 1264 1186 1290 1340;
    1669 1274 1286 1064 1136; 1670 1302 1380 1074 1376; 1671 1227 1270 1068 1217;
    1672 1058 1241 1075 1383; 1673 1258 1147 1143 1176; 1674 1189 370 1030 1157;
    1675 1196 1307 1106 1183; 1676 1301 1299 1088 1195; 1677 1199 1157 1197 1086;
    1678 1236 1201 1087 1180; 1679 1261 1312 407 406; 1680 1180 1291 1119 1367;
    1681 1281 1161 1346 1374; 1682 1327 1251 1079 1341; 1683 1094 1051 1117 1065;
    1684 1059 1315 1285 1384; 1685 1168 1279 1270 1227; 1686 1098 1176 1266 1208;
    1687 1289 1345 1115 1232; 1688 1252 1037 1038 1344; 1689 1287 1083 1231 1342;
    1690 1357 1214 1092 1356; 1691 1163 1127 1354 1177; 1692 1265 1131 1375 1257;
    1693 1279 1067 1068 1270; 1694 1272 1345 1289 1121; 1695 1383 1075 1083 1287;
    1696 1216 1379 1357 1091; 1697 1376 1074 1258 1165; 1698 1155 1344 1305 1063;
    1699 1073 1097 1158 1249; 1700 1256 1313 1330 1152; 1701 1326 1327 1341 1349;
    1702 1115 1359 1263 1210; 1703 1376 1165 1226 1132; 1704 1373 1104 1252 1320;
    1705 1320 1252 1344 1155; 1706 1342 1048 1049 1191; 1707 1187 1092 1255 1254;
    1708 1195 1088 1127 1163; 1709 1331 1218 405 404; 1710 1057 1377 1324 1144;
    1711 1075 1045 1046 1083; 1712 1269 1096 1251 1327; 1713 1184 1326 1349 1299;
    1714 1077 1259 1211 1271; 1715 1028 1029 1236 1190; 1716 1375 1342 1191 1243;
    1717 1271 1211 1296 1272; 1718 1016 1240 1335 1388; 1719 1016 1388 398 29;
    1720 1266 1103 1104 1373; 1721 1176 1143 1103 1266; 1722 1221 1243 1300 1315;
    1723 1254 1255 1259 1077; 1724 1321 1175 1143 1147; 1725 1214 1135 1386 1245;
    1726 1308 1206 1366 1125; 1727 1119 1291 1081 1113; 1728 1017 1018 1069 1370;
    1729 1066 1137 1185 1260; 1730 1085 1220 1123 1317; 1731 1083 1046 1047 1231;
    1732 1300 1109 1094 1062; 1733 1334 1365 1124 1219; 1734 1243 1191 1109 1300;
    1735 1370 1153 1140 1268; 1736 1090 1202 1188 1172; 1737 1156 1320 1343 1139;
    1738 1187 1254 1097 1280; 1739 1345 1318 1359 1115; 1740 1377 1170 1223 1324;
    1741 1088 1281 1374 1127; 1742 1209 1216 1091 1353; 1743 1170 1041 1042 1223;
    1744 1257 1375 1243 1060; 1745 1093 1278 1216 1209; 1746 1305 1039 1040 1387;
    1747 1131 1287 1342 1375; 1748 1249 1158 1121 1090; 1749 1244 1102 1350 1200;
    1750 1129 1347 1274 1198; 1751 1058 1383 1130 1146; 1752 1384 1224 1269 1361;
    1753 1371 1304 1059 1378; 1754 1374 1346 1174 1179; 1755 1165 1258 1176 1098;
    1756 1228 1280 1078 1145; 1757 1122 1114 1321 1147; 1758 1255 1235 1211 1259;
    1759 1246 1384 1361 1128; 1760 1218 1261 406 405; 1761 1241 1044 1045 1075;
    1762 1351 1173 1161 1281; 1763 1387 1040 1041 1170; 1764 1143 1034 1035 1103;
    1765 1330 1266 1150 1152; 1766 1348 1071 1364 1333; 1767 1311 1229 1235 1255;
    1768 1318 1128 1297 1359; 1769 1210 1362 1234 1323; 1770 1340 1290 1303 1137;
    1771 1061 1118 1160 1110; 1772 1135 1262 1306 1386; 1773 1355 1302 1376 1089;
    1774 1223 1043 1044 1241; 1775 1273 1130 1131 1265; 1776 1213 1207 1381 1286;
    1777 1154 1380 1302 1355; 1778 1027 1028 1190 1102; 1779 1082 1114 1122 1325;
    1780 1193 1054 1055 1095; 1781 1230 1194 1358 1352; 1782 1150 1156 1139 1279;
    1783 1362 1203 1230 1234; 1784 1266 1373 1156 1150; 1785 1069 1277 1153 1370;
    1786 1133 1337 403 402; 1787 1280 1097 1073 1078; 1788 1126 1363 1129 1198;
    1789 1346 1095 1072 1174; 1790 1309 1353 1356 1329; 1791 1329 1356 1092 1187;
    1792 1022 1023 1148 1149; 1793 1353 1091 1357 1356; 1794 1277 1070 1149 1153;
    1795 1106 1307 1162 1093; 1796 1357 1379 1135 1214; 1797 64 1017 1370 1242;
    1798 1119 1113 1111 1368; 1799 1139 1343 1067 1279; 1800 1159 1225 1292 1288;
    1801 1347 1213 1286 1274; 1802 1202 1289 1232 1188; 1803 1134 1108 1310 1363;
    1804 1275 1256 1152 1276; 1805 1063 1305 1387 1138; 1806 1200 1350 1334 1314;
    1807 1141 1089 1120 1105; 1808 1144 1324 1223 1241; 1809 1229 1304 1371 1235;
    1810 1368 1111 1282 1316; 1811 1204 1284 1212 1283; 1812 1296 1246 1128 1318;
    1813 1129 1238 1213 1347; 1814 1298 1366 1338 1076; 1815 1019 1020 1070 1277;
    1816 1206 1327 1326 1366; 1817 1303 1181 1108 1134; 1818 1231 1047 1048 1342;
    1819 1132 1226 1284 1204; 1820 1290 1314 1181 1303; 1821 1338 1184 1299 1301;
    1822 1164 1244 1186 1239; 1823 1169 1112 1225 1159; 1824 1282 1293 1325 1295;
    1825 1276 1152 1168 1381; 1826 1366 1326 1184 1338; 1827 1207 1275 1276 1381;
    1828 1267 1248 1307 1196; 1829 1113 1081 1220 1085; 1830 1364 1209 1353 1309;
    1831 1292 1239 1186 1264; 1832 1235 1371 1378 1211; 1833 1211 1378 1246 1296;
    1834 1188 1232 1323 1312; 1835 1363 1310 1238 1129; 1836 1337 1331 404 403;
    1837 1278 1146 1379 1216; 1838 1233 1332 1360 1339; 1839 1084 1120 1132 1204;
    1840 1080 1166 1171 1237; 1841 1097 1077 1271 1158; 1842 1317 1123 1114 1082;
    1843 1250 1182 1193 1107; 1844 1293 1317 1082 1325; 1845 1151 1058 1146 1278;
    1846 1064 1227 1217 1057; 1847 1112 1101 1164 1225; 1848 1310 1382 1283 1238;
    1849 1111 1328 1293 1282; 1850 1136 1064 1057 1248; 1851 1306 1257 1060 1385;
    1852 1178 1076 1247 1194; 1853 1358 1195 1163 1352; 1854 1146 1130 1273 1379;
    1855 1379 1273 1262 1135; 1856 1272 1296 1318 1345; 1857 1100 1052 1053 1182;
    1858 1172 1188 1312 1261; 1859 1108 1084 1382 1310; 1860 1370 1268 1080 1242;
    1861 1138 1387 1170 1377; 1862 1130 1383 1287 1131; 1863 1107 1193 1161 1173;
    1864 1181 1219 1141 1105; 1865 1329 1187 1280 1228; 1866 1191 1049 1050 1109;
    1867 1029 228 1201 1236; 1868 1314 1334 1219 1181; 1869 1328 1085 1317 1293;
    1870 1212 1284 1256 1275; 1871 1096 1100 1182 1250; 1872 1339 1360 1178 1203;
    1873 1128 1361 1308 1297; 1874 1253 1267 1196 1166; 1875 1109 1050 1051 1094;
    1876 1245 1386 1385 1311; 1877 1364 1309 1329 1333; 1878 1247 1301 1195 1358;
    1879 1203 1178 1194 1230; 1880 1210 1263 1233 1362; 1881 1262 1265 1257 1306;
    1882 1323 1234 1099; 1883 1253 1167 1267; 1884 1313 1098 1208;
    1885 1336 1368 1316; 1886 1223 1042 1043; 1887 1369 1294 1319;
    1888 1160 1118 1175; 1889 1074 1147 1258; 1890 1201 1189 1087;
    1891 1206 1269 1327; 1892 1060 1243 1221; 1893 399 1372 400;
    1894 1097 1254 1077; 1895 1149 1148 1153; 1896 1154 1295 1380;
    1897 1194 1247 1358; 1898 1273 1265 1262; 1899 1020 1021 1070;
    1900 1244 1200 1186; 1901 1333 1329 1228; 1902 1286 1381 1168;
    1903 1214 1245 1092; 1904 1105 1120 1084; 1905 1386 1306 1385;
    1906 1242 1080 1237; 1907 1156 1373 1320; 1908 1071 1196 1183;
    1951 1056 1431 604 369; 1952 1431 1432 605 604; 1953 1432 1433 606 605;
    1954 1433 1434 607 606; 1955 1434 1435 608 607; 1956 1435 1436 609 608;
    1957 1436 1437 610 609; 1958 1437 1438 611 610; 1959 1438 1439 612 611;
    1960 1439 1440 613 612; 1961 1440 1441 614 613; 1962 1441 1442 615 614;
    1963 1442 1443 616 615; 1964 1443 1444 617 616; 1965 1444 1445 618 617;
    1966 1445 1430 375 618; 1967 1055 1446 1431 1056; 1968 1446 1447 1432 1431;
    1969 1447 1448 1433 1432; 1970 1448 1449 1434 1433; 1971 1449 1450 1435 1434;
    1972 1450 1451 1436 1435; 1973 1451 1452 1437 1436; 1974 1452 1453 1438 1437;
    1975 1453 1454 1439 1438; 1976 1454 1455 1440 1439; 1977 1455 1456 1441 1440;
    1978 1456 1457 1442 1441; 1979 1457 1458 1443 1442; 1980 1458 1459 1444 1443;
    1981 1459 1460 1445 1444; 1982 1460 1429 1430 1445; 1983 1054 1461 1446 1055;
    1984 1461 1462 1447 1446; 1985 1462 1463 1448 1447; 1986 1463 1464 1449 1448;
    1987 1464 1465 1450 1449; 1988 1465 1466 1451 1450; 1989 1466 1467 1452 1451;
    1990 1467 1468 1453 1452; 1991 1468 1469 1454 1453; 1992 1469 1470 1455 1454;
    1993 1470 1471 1456 1455; 1994 1471 1472 1457 1456; 1995 1472 1473 1458 1457;
    1996 1473 1474 1459 1458; 1997 1474 1475 1460 1459; 1998 1475 1428 1429 1460;
    1999 1053 1476 1461 1054; 2000 1476 1477 1462 1461; 2001 1477 1478 1463 1462;
    2002 1478 1479 1464 1463; 2003 1479 1480 1465 1464; 2004 1480 1481 1466 1465;
    2005 1481 1482 1467 1466; 2006 1482 1483 1468 1467; 2007 1483 1484 1469 1468;
    2008 1484 1485 1470 1469; 2009 1485 1486 1471 1470; 2010 1486 1487 1472 1471;
    2011 1487 1488 1473 1472; 2012 1488 1489 1474 1473; 2013 1489 1490 1475 1474;
    2014 1490 1427 1428 1475; 2015 1052 1491 1476 1053; 2016 1491 1492 1477 1476;
    2017 1492 1493 1478 1477; 2018 1493 1494 1479 1478; 2019 1494 1495 1480 1479;
    2020 1495 1496 1481 1480; 2021 1496 1497 1482 1481; 2022 1497 1498 1483 1482;
    2023 1498 1499 1484 1483; 2024 1499 1500 1485 1484; 2025 1500 1501 1486 1485;
    2026 1501 1502 1487 1486; 2027 1502 1503 1488 1487; 2028 1503 1504 1489 1488;
    2029 1504 1505 1490 1489; 2030 1505 1426 1427 1490; 2031 1051 1506 1491 1052;
    2032 1506 1507 1492 1491; 2033 1507 1508 1493 1492; 2034 1508 1509 1494 1493;
    2035 1509 1510 1495 1494; 2036 1510 1511 1496 1495; 2037 1511 1512 1497 1496;
    2038 1512 1513 1498 1497; 2039 1513 1514 1499 1498; 2040 1514 1515 1500 1499;
    2041 1515 1516 1501 1500; 2042 1516 1517 1502 1501; 2043 1517 1518 1503 1502;
    2044 1518 1519 1504 1503; 2045 1519 1520 1505 1504; 2046 1520 1425 1426 1505;
    2047 1050 1521 1506 1051; 2048 1521 1522 1507 1506; 2049 1522 1523 1508 1507;
    2050 1523 1524 1509 1508; 2051 1524 1525 1510 1509; 2052 1525 1526 1511 1510;
    2053 1526 1527 1512 1511; 2054 1527 1528 1513 1512; 2055 1528 1529 1514 1513;
    2056 1529 1530 1515 1514; 2057 1530 1531 1516 1515; 2058 1531 1532 1517 1516;
    2059 1532 1533 1518 1517; 2060 1533 1534 1519 1518; 2061 1534 1535 1520 1519;
    2062 1535 1424 1425 1520; 2063 1049 1536 1521 1050; 2064 1536 1537 1522 1521;
    2065 1537 1538 1523 1522; 2066 1538 1539 1524 1523; 2067 1539 1540 1525 1524;
    2068 1540 1541 1526 1525; 2069 1541 1542 1527 1526; 2070 1542 1543 1528 1527;
    2071 1543 1544 1529 1528; 2072 1544 1545 1530 1529; 2073 1545 1546 1531 1530;
    2074 1546 1547 1532 1531; 2075 1547 1548 1533 1532; 2076 1548 1549 1534 1533;
    2077 1549 1550 1535 1534; 2078 1550 1423 1424 1535; 2079 1048 1551 1536 1049;
    2080 1551 1552 1537 1536; 2081 1552 1553 1538 1537; 2082 1553 1554 1539 1538;
    2083 1554 1555 1540 1539; 2084 1555 1556 1541 1540; 2085 1556 1557 1542 1541;
    2086 1557 1558 1543 1542; 2087 1558 1559 1544 1543; 2088 1559 1560 1545 1544;
    2089 1560 1561 1546 1545; 2090 1561 1562 1547 1546; 2091 1562 1563 1548 1547;
    2092 1563 1564 1549 1548; 2093 1564 1565 1550 1549; 2094 1565 1422 1423 1550;
    2095 1047 1566 1551 1048; 2096 1566 1567 1552 1551; 2097 1567 1568 1553 1552;
    2098 1568 1569 1554 1553; 2099 1569 1570 1555 1554; 2100 1570 1571 1556 1555;
    2101 1571 1572 1557 1556; 2102 1572 1573 1558 1557; 2103 1573 1574 1559 1558;
    2104 1574 1575 1560 1559; 2105 1575 1576 1561 1560; 2106 1576 1577 1562 1561;
    2107 1577 1578 1563 1562; 2108 1578 1579 1564 1563; 2109 1579 1580 1565 1564;
    2110 1580 1421 1422 1565; 2111 1046 1581 1566 1047; 2112 1581 1582 1567 1566;
    2113 1582 1583 1568 1567; 2114 1583 1584 1569 1568; 2115 1584 1585 1570 1569;
    2116 1585 1586 1571 1570; 2117 1586 1587 1572 1571; 2118 1587 1588 1573 1572;
    2119 1588 1589 1574 1573; 2120 1589 1590 1575 1574; 2121 1590 1591 1576 1575;
    2122 1591 1592 1577 1576; 2123 1592 1593 1578 1577; 2124 1593 1594 1579 1578;
    2125 1594 1595 1580 1579; 2126 1595 1420 1421 1580; 2127 1045 1596 1581 1046;
    2128 1596 1597 1582 1581; 2129 1597 1598 1583 1582; 2130 1598 1599 1584 1583;
    2131 1599 1600 1585 1584; 2132 1600 1601 1586 1585; 2133 1601 1602 1587 1586;
    2134 1602 1603 1588 1587; 2135 1603 1604 1589 1588; 2136 1604 1605 1590 1589;
    2137 1605 1606 1591 1590; 2138 1606 1607 1592 1591; 2139 1607 1608 1593 1592;
    2140 1608 1609 1594 1593; 2141 1609 1610 1595 1594; 2142 1610 1419 1420 1595;
    2143 1044 1611 1596 1045; 2144 1611 1612 1597 1596; 2145 1612 1613 1598 1597;
    2146 1613 1614 1599 1598; 2147 1614 1615 1600 1599; 2148 1615 1616 1601 1600;
    2149 1616 1617 1602 1601; 2150 1617 1618 1603 1602; 2151 1618 1619 1604 1603;
    2152 1619 1620 1605 1604; 2153 1620 1621 1606 1605; 2154 1621 1622 1607 1606;
    2155 1622 1623 1608 1607; 2156 1623 1624 1609 1608; 2157 1624 1625 1610 1609;
    2158 1625 1418 1419 1610; 2159 1043 1626 1611 1044; 2160 1626 1627 1612 1611;
    2161 1627 1628 1613 1612; 2162 1628 1629 1614 1613; 2163 1629 1630 1615 1614;
    2164 1630 1631 1616 1615; 2165 1631 1632 1617 1616; 2166 1632 1633 1618 1617;
    2167 1633 1634 1619 1618; 2168 1634 1635 1620 1619; 2169 1635 1636 1621 1620;
    2170 1636 1637 1622 1621; 2171 1637 1638 1623 1622; 2172 1638 1639 1624 1623;
    2173 1639 1640 1625 1624; 2174 1640 1417 1418 1625; 2175 1042 1641 1626 1043;
    2176 1641 1642 1627 1626; 2177 1642 1643 1628 1627; 2178 1643 1644 1629 1628;
    2179 1644 1645 1630 1629; 2180 1645 1646 1631 1630; 2181 1646 1647 1632 1631;
    2182 1647 1648 1633 1632; 2183 1648 1649 1634 1633; 2184 1649 1650 1635 1634;
    2185 1650 1651 1636 1635; 2186 1651 1652 1637 1636; 2187 1652 1653 1638 1637;
    2188 1653 1654 1639 1638; 2189 1654 1655 1640 1639; 2190 1655 1416 1417 1640;
    2191 1041 1656 1641 1042; 2192 1656 1657 1642 1641; 2193 1657 1658 1643 1642;
    2194 1658 1659 1644 1643; 2195 1659 1660 1645 1644; 2196 1660 1661 1646 1645;
    2197 1661 1662 1647 1646; 2198 1662 1663 1648 1647; 2199 1663 1664 1649 1648;
    2200 1664 1665 1650 1649; 2201 1665 1666 1651 1650; 2202 1666 1667 1652 1651;
    2203 1667 1668 1653 1652; 2204 1668 1669 1654 1653; 2205 1669 1670 1655 1654;
    2206 1670 1415 1416 1655; 2207 1040 1671 1656 1041; 2208 1671 1672 1657 1656;
    2209 1672 1673 1658 1657; 2210 1673 1674 1659 1658; 2211 1674 1675 1660 1659;
    2212 1675 1676 1661 1660; 2213 1676 1677 1662 1661; 2214 1677 1678 1663 1662;
    2215 1678 1679 1664 1663; 2216 1679 1680 1665 1664; 2217 1680 1681 1666 1665;
    2218 1681 1682 1667 1666; 2219 1682 1683 1668 1667; 2220 1683 1684 1669 1668;
    2221 1684 1685 1670 1669; 2222 1685 1414 1415 1670; 2223 1039 1686 1671 1040;
    2224 1686 1687 1672 1671; 2225 1687 1688 1673 1672; 2226 1688 1689 1674 1673;
    2227 1689 1690 1675 1674; 2228 1690 1691 1676 1675; 2229 1691 1692 1677 1676;
    2230 1692 1693 1678 1677; 2231 1693 1694 1679 1678; 2232 1694 1695 1680 1679;
    2233 1695 1696 1681 1680; 2234 1696 1697 1682 1681; 2235 1697 1698 1683 1682;
    2236 1698 1699 1684 1683; 2237 1699 1700 1685 1684; 2238 1700 1413 1414 1685;
    2239 1038 1701 1686 1039; 2240 1701 1702 1687 1686; 2241 1702 1703 1688 1687;
    2242 1703 1704 1689 1688; 2243 1704 1705 1690 1689; 2244 1705 1706 1691 1690;
    2245 1706 1707 1692 1691; 2246 1707 1708 1693 1692; 2247 1708 1709 1694 1693;
    2248 1709 1710 1695 1694; 2249 1710 1711 1696 1695; 2250 1711 1712 1697 1696;
    2251 1712 1713 1698 1697; 2252 1713 1714 1699 1698; 2253 1714 1715 1700 1699;
    2254 1715 1412 1413 1700; 2255 1037 1716 1701 1038; 2256 1716 1717 1702 1701;
    2257 1717 1718 1703 1702; 2258 1718 1719 1704 1703; 2259 1719 1720 1705 1704;
    2260 1720 1721 1706 1705; 2261 1721 1722 1707 1706; 2262 1722 1723 1708 1707;
    2263 1723 1724 1709 1708; 2264 1724 1725 1710 1709; 2265 1725 1726 1711 1710;
    2266 1726 1727 1712 1711; 2267 1727 1728 1713 1712; 2268 1728 1729 1714 1713;
    2269 1729 1730 1715 1714; 2270 1730 1411 1412 1715; 2271 1036 1731 1716 1037;
    2272 1731 1732 1717 1716; 2273 1732 1733 1718 1717; 2274 1733 1734 1719 1718;
    2275 1734 1735 1720 1719; 2276 1735 1736 1721 1720; 2277 1736 1737 1722 1721;
    2278 1737 1738 1723 1722; 2279 1738 1739 1724 1723; 2280 1739 1740 1725 1724;
    2281 1740 1741 1726 1725; 2282 1741 1742 1727 1726; 2283 1742 1743 1728 1727;
    2284 1743 1744 1729 1728; 2285 1744 1745 1730 1729; 2286 1745 1410 1411 1730;
    2287 1035 1746 1731 1036; 2288 1746 1747 1732 1731; 2289 1747 1748 1733 1732;
    2290 1748 1749 1734 1733; 2291 1749 1750 1735 1734; 2292 1750 1751 1736 1735;
    2293 1751 1752 1737 1736; 2294 1752 1753 1738 1737; 2295 1753 1754 1739 1738;
    2296 1754 1755 1740 1739; 2297 1755 1756 1741 1740; 2298 1756 1757 1742 1741;
    2299 1757 1758 1743 1742; 2300 1758 1759 1744 1743; 2301 1759 1760 1745 1744;
    2302 1760 1409 1410 1745; 2303 1034 1761 1746 1035; 2304 1761 1762 1747 1746;
    2305 1762 1763 1748 1747; 2306 1763 1764 1749 1748; 2307 1764 1765 1750 1749;
    2308 1765 1766 1751 1750; 2309 1766 1767 1752 1751; 2310 1767 1768 1753 1752;
    2311 1768 1769 1754 1753; 2312 1769 1770 1755 1754; 2313 1770 1771 1756 1755;
    2314 1771 1772 1757 1756; 2315 1772 1773 1758 1757; 2316 1773 1774 1759 1758;
    2317 1774 1775 1760 1759; 2318 1775 1408 1409 1760; 2319 1033 1776 1761 1034;
    2320 1776 1777 1762 1761; 2321 1777 1778 1763 1762; 2322 1778 1779 1764 1763;
    2323 1779 1780 1765 1764; 2324 1780 1781 1766 1765; 2325 1781 1782 1767 1766;
    2326 1782 1783 1768 1767; 2327 1783 1784 1769 1768; 2328 1784 1785 1770 1769;
    2329 1785 1786 1771 1770; 2330 1786 1787 1772 1771; 2331 1787 1788 1773 1772;
    2332 1788 1789 1774 1773; 2333 1789 1790 1775 1774; 2334 1790 1407 1408 1775;
    2335 1032 1791 1776 1033; 2336 1791 1792 1777 1776; 2337 1792 1793 1778 1777;
    2338 1793 1794 1779 1778; 2339 1794 1795 1780 1779; 2340 1795 1796 1781 1780;
    2341 1796 1797 1782 1781; 2342 1797 1798 1783 1782; 2343 1798 1799 1784 1783;
    2344 1799 1800 1785 1784; 2345 1800 1801 1786 1785; 2346 1801 1802 1787 1786;
    2347 1802 1803 1788 1787; 2348 1803 1804 1789 1788; 2349 1804 1805 1790 1789;
    2350 1805 1406 1407 1790; 2351 1031 1806 1791 1032; 2352 1806 1807 1792 1791;
    2353 1807 1808 1793 1792; 2354 1808 1809 1794 1793; 2355 1809 1810 1795 1794;
    2356 1810 1811 1796 1795; 2357 1811 1812 1797 1796; 2358 1812 1813 1798 1797;
    2359 1813 1814 1799 1798; 2360 1814 1815 1800 1799; 2361 1815 1816 1801 1800;
    2362 1816 1817 1802 1801; 2363 1817 1818 1803 1802; 2364 1818 1819 1804 1803;
    2365 1819 1820 1805 1804; 2366 1820 1405 1406 1805; 2367 1030 1821 1806 1031;
    2368 1821 1822 1807 1806; 2369 1822 1823 1808 1807; 2370 1823 1824 1809 1808;
    2371 1824 1825 1810 1809; 2372 1825 1826 1811 1810; 2373 1826 1827 1812 1811;
    2374 1827 1828 1813 1812; 2375 1828 1829 1814 1813; 2376 1829 1830 1815 1814;
    2377 1830 1831 1816 1815; 2378 1831 1832 1817 1816; 2379 1832 1833 1818 1817;
    2380 1833 1834 1819 1818; 2381 1834 1835 1820 1819; 2382 1835 1404 1405 1820;
    2383 370 1389 1821 1030; 2384 1389 1390 1822 1821; 2385 1390 1391 1823 1822;
    2386 1391 1392 1824 1823; 2387 1392 1393 1825 1824; 2388 1393 1394 1826 1825;
    2389 1394 1395 1827 1826; 2390 1395 1396 1828 1827; 2391 1396 1397 1829 1828;
    2392 1397 1398 1830 1829; 2393 1398 1399 1831 1830; 2394 1399 1400 1832 1831;
    2395 1400 1401 1833 1832; 2396 1401 1402 1834 1833; 2397 1402 1403 1835 1834;
    2398 1403 376 1404 1835; 2441 1836 1878 821 381; 2442 1878 1879 822 821;
    2443 1879 1880 823 822; 2444 1880 1881 824 823; 2445 1881 1882 825 824;
    2446 1882 1883 826 825; 2447 1883 1884 827 826; 2448 1884 1885 828 827;
    2449 1885 1886 829 828; 2450 1886 1887 830 829; 2451 1887 1888 831 830;
    2452 1888 1889 832 831; 2453 1889 1890 833 832; 2454 1890 1891 834 833;
    2455 1891 1892 835 834; 2456 1892 1430 375 835; 2457 1837 1893 1878 1836;
    2458 1893 1894 1879 1878; 2459 1894 1895 1880 1879; 2460 1895 1896 1881 1880;
    2461 1896 1897 1882 1881; 2462 1897 1898 1883 1882; 2463 1898 1899 1884 1883;
    2464 1899 1900 1885 1884; 2465 1900 1901 1886 1885; 2466 1901 1902 1887 1886;
    2467 1902 1903 1888 1887; 2468 1903 1904 1889 1888; 2469 1904 1905 1890 1889;
    2470 1905 1906 1891 1890; 2471 1906 1907 1892 1891; 2472 1907 1429 1430 1892;
    2473 1838 1908 1893 1837; 2474 1908 1909 1894 1893; 2475 1909 1910 1895 1894;
    2476 1910 1911 1896 1895; 2477 1911 1912 1897 1896; 2478 1912 1913 1898 1897;
    2479 1913 1914 1899 1898; 2480 1914 1915 1900 1899; 2481 1915 1916 1901 1900;
    2482 1916 1917 1902 1901; 2483 1917 1918 1903 1902; 2484 1918 1919 1904 1903;
    2485 1919 1920 1905 1904; 2486 1920 1921 1906 1905; 2487 1921 1922 1907 1906;
    2488 1922 1428 1429 1907; 2489 1839 1923 1908 1838; 2490 1923 1924 1909 1908;
    2491 1924 1925 1910 1909; 2492 1925 1926 1911 1910; 2493 1926 1927 1912 1911;
    2494 1927 1928 1913 1912; 2495 1928 1929 1914 1913; 2496 1929 1930 1915 1914;
    2497 1930 1931 1916 1915; 2498 1931 1932 1917 1916; 2499 1932 1933 1918 1917;
    2500 1933 1934 1919 1918; 2501 1934 1935 1920 1919; 2502 1935 1936 1921 1920;
    2503 1936 1937 1922 1921; 2504 1937 1427 1428 1922; 2505 1840 1938 1923 1839;
    2506 1938 1939 1924 1923; 2507 1939 1940 1925 1924; 2508 1940 1941 1926 1925;
    2509 1941 1942 1927 1926; 2510 1942 1943 1928 1927; 2511 1943 1944 1929 1928;
    2512 1944 1945 1930 1929; 2513 1945 1946 1931 1930; 2514 1946 1947 1932 1931;
    2515 1947 1948 1933 1932; 2516 1948 1949 1934 1933; 2517 1949 1950 1935 1934;
    2518 1950 1951 1936 1935; 2519 1951 1952 1937 1936; 2520 1952 1426 1427 1937;
    2521 1841 1953 1938 1840; 2522 1953 1954 1939 1938; 2523 1954 1955 1940 1939;
    2524 1955 1956 1941 1940; 2525 1956 1957 1942 1941; 2526 1957 1958 1943 1942;
    2527 1958 1959 1944 1943; 2528 1959 1960 1945 1944; 2529 1960 1961 1946 1945;
    2530 1961 1962 1947 1946; 2531 1962 1963 1948 1947; 2532 1963 1964 1949 1948;
    2533 1964 1965 1950 1949; 2534 1965 1966 1951 1950; 2535 1966 1967 1952 1951;
    2536 1967 1425 1426 1952; 2537 1842 1968 1953 1841; 2538 1968 1969 1954 1953;
    2539 1969 1970 1955 1954; 2540 1970 1971 1956 1955; 2541 1971 1972 1957 1956;
    2542 1972 1973 1958 1957; 2543 1973 1974 1959 1958; 2544 1974 1975 1960 1959;
    2545 1975 1976 1961 1960; 2546 1976 1977 1962 1961; 2547 1977 1978 1963 1962;
    2548 1978 1979 1964 1963; 2549 1979 1980 1965 1964; 2550 1980 1981 1966 1965;
    2551 1981 1982 1967 1966; 2552 1982 1424 1425 1967; 2553 1843 1983 1968 1842;
    2554 1983 1984 1969 1968; 2555 1984 1985 1970 1969; 2556 1985 1986 1971 1970;
    2557 1986 1987 1972 1971; 2558 1987 1988 1973 1972; 2559 1988 1989 1974 1973;
    2560 1989 1990 1975 1974; 2561 1990 1991 1976 1975; 2562 1991 1992 1977 1976;
    2563 1992 1993 1978 1977; 2564 1993 1994 1979 1978; 2565 1994 1995 1980 1979;
    2566 1995 1996 1981 1980; 2567 1996 1997 1982 1981; 2568 1997 1423 1424 1982;
    2569 1844 1998 1983 1843; 2570 1998 1999 1984 1983; 2571 1999 2000 1985 1984;
    2572 2000 2001 1986 1985; 2573 2001 2002 1987 1986; 2574 2002 2003 1988 1987;
    2575 2003 2004 1989 1988; 2576 2004 2005 1990 1989; 2577 2005 2006 1991 1990;
    2578 2006 2007 1992 1991; 2579 2007 2008 1993 1992; 2580 2008 2009 1994 1993;
    2581 2009 2010 1995 1994; 2582 2010 2011 1996 1995; 2583 2011 2012 1997 1996;
    2584 2012 1422 1423 1997; 2585 1845 2013 1998 1844; 2586 2013 2014 1999 1998;
    2587 2014 2015 2000 1999; 2588 2015 2016 2001 2000; 2589 2016 2017 2002 2001;
    2590 2017 2018 2003 2002; 2591 2018 2019 2004 2003; 2592 2019 2020 2005 2004;
    2593 2020 2021 2006 2005; 2594 2021 2022 2007 2006; 2595 2022 2023 2008 2007;
    2596 2023 2024 2009 2008; 2597 2024 2025 2010 2009; 2598 2025 2026 2011 2010;
    2599 2026 2027 2012 2011; 2600 2027 1421 1422 2012; 2601 1846 2028 2013 1845;
    2602 2028 2029 2014 2013; 2603 2029 2030 2015 2014; 2604 2030 2031 2016 2015;
    2605 2031 2032 2017 2016; 2606 2032 2033 2018 2017; 2607 2033 2034 2019 2018;
    2608 2034 2035 2020 2019; 2609 2035 2036 2021 2020; 2610 2036 2037 2022 2021;
    2611 2037 2038 2023 2022; 2612 2038 2039 2024 2023; 2613 2039 2040 2025 2024;
    2614 2040 2041 2026 2025; 2615 2041 2042 2027 2026; 2616 2042 1420 1421 2027;
    2617 1847 2043 2028 1846; 2618 2043 2044 2029 2028; 2619 2044 2045 2030 2029;
    2620 2045 2046 2031 2030; 2621 2046 2047 2032 2031; 2622 2047 2048 2033 2032;
    2623 2048 2049 2034 2033; 2624 2049 2050 2035 2034; 2625 2050 2051 2036 2035;
    2626 2051 2052 2037 2036; 2627 2052 2053 2038 2037; 2628 2053 2054 2039 2038;
    2629 2054 2055 2040 2039; 2630 2055 2056 2041 2040; 2631 2056 2057 2042 2041;
    2632 2057 1419 1420 2042; 2633 1848 2058 2043 1847; 2634 2058 2059 2044 2043;
    2635 2059 2060 2045 2044; 2636 2060 2061 2046 2045; 2637 2061 2062 2047 2046;
    2638 2062 2063 2048 2047; 2639 2063 2064 2049 2048; 2640 2064 2065 2050 2049;
    2641 2065 2066 2051 2050; 2642 2066 2067 2052 2051; 2643 2067 2068 2053 2052;
    2644 2068 2069 2054 2053; 2645 2069 2070 2055 2054; 2646 2070 2071 2056 2055;
    2647 2071 2072 2057 2056; 2648 2072 1418 1419 2057; 2649 1849 2073 2058 1848;
    2650 2073 2074 2059 2058; 2651 2074 2075 2060 2059; 2652 2075 2076 2061 2060;
    2653 2076 2077 2062 2061; 2654 2077 2078 2063 2062; 2655 2078 2079 2064 2063;
    2656 2079 2080 2065 2064; 2657 2080 2081 2066 2065; 2658 2081 2082 2067 2066;
    2659 2082 2083 2068 2067; 2660 2083 2084 2069 2068; 2661 2084 2085 2070 2069;
    2662 2085 2086 2071 2070; 2663 2086 2087 2072 2071; 2664 2087 1417 1418 2072;
    2665 1850 2088 2073 1849; 2666 2088 2089 2074 2073; 2667 2089 2090 2075 2074;
    2668 2090 2091 2076 2075; 2669 2091 2092 2077 2076; 2670 2092 2093 2078 2077;
    2671 2093 2094 2079 2078; 2672 2094 2095 2080 2079; 2673 2095 2096 2081 2080;
    2674 2096 2097 2082 2081; 2675 2097 2098 2083 2082; 2676 2098 2099 2084 2083;
    2677 2099 2100 2085 2084; 2678 2100 2101 2086 2085; 2679 2101 2102 2087 2086;
    2680 2102 1416 1417 2087; 2681 1851 2103 2088 1850; 2682 2103 2104 2089 2088;
    2683 2104 2105 2090 2089; 2684 2105 2106 2091 2090; 2685 2106 2107 2092 2091;
    2686 2107 2108 2093 2092; 2687 2108 2109 2094 2093; 2688 2109 2110 2095 2094;
    2689 2110 2111 2096 2095; 2690 2111 2112 2097 2096; 2691 2112 2113 2098 2097;
    2692 2113 2114 2099 2098; 2693 2114 2115 2100 2099; 2694 2115 2116 2101 2100;
    2695 2116 2117 2102 2101; 2696 2117 1415 1416 2102; 2697 1852 2118 2103 1851;
    2698 2118 2119 2104 2103; 2699 2119 2120 2105 2104; 2700 2120 2121 2106 2105;
    2701 2121 2122 2107 2106; 2702 2122 2123 2108 2107; 2703 2123 2124 2109 2108;
    2704 2124 2125 2110 2109; 2705 2125 2126 2111 2110; 2706 2126 2127 2112 2111;
    2707 2127 2128 2113 2112; 2708 2128 2129 2114 2113; 2709 2129 2130 2115 2114;
    2710 2130 2131 2116 2115; 2711 2131 2132 2117 2116; 2712 2132 1414 1415 2117;
    2713 1853 2133 2118 1852; 2714 2133 2134 2119 2118; 2715 2134 2135 2120 2119;
    2716 2135 2136 2121 2120; 2717 2136 2137 2122 2121; 2718 2137 2138 2123 2122;
    2719 2138 2139 2124 2123; 2720 2139 2140 2125 2124; 2721 2140 2141 2126 2125;
    2722 2141 2142 2127 2126; 2723 2142 2143 2128 2127; 2724 2143 2144 2129 2128;
    2725 2144 2145 2130 2129; 2726 2145 2146 2131 2130; 2727 2146 2147 2132 2131;
    2728 2147 1413 1414 2132; 2729 1854 2148 2133 1853; 2730 2148 2149 2134 2133;
    2731 2149 2150 2135 2134; 2732 2150 2151 2136 2135; 2733 2151 2152 2137 2136;
    2734 2152 2153 2138 2137; 2735 2153 2154 2139 2138; 2736 2154 2155 2140 2139;
    2737 2155 2156 2141 2140; 2738 2156 2157 2142 2141; 2739 2157 2158 2143 2142;
    2740 2158 2159 2144 2143; 2741 2159 2160 2145 2144; 2742 2160 2161 2146 2145;
    2743 2161 2162 2147 2146; 2744 2162 1412 1413 2147; 2745 1855 2163 2148 1854;
    2746 2163 2164 2149 2148; 2747 2164 2165 2150 2149; 2748 2165 2166 2151 2150;
    2749 2166 2167 2152 2151; 2750 2167 2168 2153 2152; 2751 2168 2169 2154 2153;
    2752 2169 2170 2155 2154; 2753 2170 2171 2156 2155; 2754 2171 2172 2157 2156;
    2755 2172 2173 2158 2157; 2756 2173 2174 2159 2158; 2757 2174 2175 2160 2159;
    2758 2175 2176 2161 2160; 2759 2176 2177 2162 2161; 2760 2177 1411 1412 2162;
    2761 1856 2178 2163 1855; 2762 2178 2179 2164 2163; 2763 2179 2180 2165 2164;
    2764 2180 2181 2166 2165; 2765 2181 2182 2167 2166; 2766 2182 2183 2168 2167;
    2767 2183 2184 2169 2168; 2768 2184 2185 2170 2169; 2769 2185 2186 2171 2170;
    2770 2186 2187 2172 2171; 2771 2187 2188 2173 2172; 2772 2188 2189 2174 2173;
    2773 2189 2190 2175 2174; 2774 2190 2191 2176 2175; 2775 2191 2192 2177 2176;
    2776 2192 1410 1411 2177; 2777 1857 2193 2178 1856; 2778 2193 2194 2179 2178;
    2779 2194 2195 2180 2179; 2780 2195 2196 2181 2180; 2781 2196 2197 2182 2181;
    2782 2197 2198 2183 2182; 2783 2198 2199 2184 2183; 2784 2199 2200 2185 2184;
    2785 2200 2201 2186 2185; 2786 2201 2202 2187 2186; 2787 2202 2203 2188 2187;
    2788 2203 2204 2189 2188; 2789 2204 2205 2190 2189; 2790 2205 2206 2191 2190;
    2791 2206 2207 2192 2191; 2792 2207 1409 1410 2192; 2793 1858 2208 2193 1857;
    2794 2208 2209 2194 2193; 2795 2209 2210 2195 2194; 2796 2210 2211 2196 2195;
    2797 2211 2212 2197 2196; 2798 2212 2213 2198 2197; 2799 2213 2214 2199 2198;
    2800 2214 2215 2200 2199; 2801 2215 2216 2201 2200; 2802 2216 2217 2202 2201;
    2803 2217 2218 2203 2202; 2804 2218 2219 2204 2203; 2805 2219 2220 2205 2204;
    2806 2220 2221 2206 2205; 2807 2221 2222 2207 2206; 2808 2222 1408 1409 2207;
    2809 1859 2223 2208 1858; 2810 2223 2224 2209 2208; 2811 2224 2225 2210 2209;
    2812 2225 2226 2211 2210; 2813 2226 2227 2212 2211; 2814 2227 2228 2213 2212;
    2815 2228 2229 2214 2213; 2816 2229 2230 2215 2214; 2817 2230 2231 2216 2215;
    2818 2231 2232 2217 2216; 2819 2232 2233 2218 2217; 2820 2233 2234 2219 2218;
    2821 2234 2235 2220 2219; 2822 2235 2236 2221 2220; 2823 2236 2237 2222 2221;
    2824 2237 1407 1408 2222; 2825 1860 2238 2223 1859; 2826 2238 2239 2224 2223;
    2827 2239 2240 2225 2224; 2828 2240 2241 2226 2225; 2829 2241 2242 2227 2226;
    2830 2242 2243 2228 2227; 2831 2243 2244 2229 2228; 2832 2244 2245 2230 2229;
    2833 2245 2246 2231 2230; 2834 2246 2247 2232 2231; 2835 2247 2248 2233 2232;
    2836 2248 2249 2234 2233; 2837 2249 2250 2235 2234; 2838 2250 2251 2236 2235;
    2839 2251 2252 2237 2236; 2840 2252 1406 1407 2237; 2841 1861 2253 2238 1860;
    2842 2253 2254 2239 2238; 2843 2254 2255 2240 2239; 2844 2255 2256 2241 2240;
    2845 2256 2257 2242 2241; 2846 2257 2258 2243 2242; 2847 2258 2259 2244 2243;
    2848 2259 2260 2245 2244; 2849 2260 2261 2246 2245; 2850 2261 2262 2247 2246;
    2851 2262 2263 2248 2247; 2852 2263 2264 2249 2248; 2853 2264 2265 2250 2249;
    2854 2265 2266 2251 2250; 2855 2266 2267 2252 2251; 2856 2267 1405 1406 2252;
    2857 1862 2268 2253 1861; 2858 2268 2269 2254 2253; 2859 2269 2270 2255 2254;
    2860 2270 2271 2256 2255; 2861 2271 2272 2257 2256; 2862 2272 2273 2258 2257;
    2863 2273 2274 2259 2258; 2864 2274 2275 2260 2259; 2865 2275 2276 2261 2260;
    2866 2276 2277 2262 2261; 2867 2277 2278 2263 2262; 2868 2278 2279 2264 2263;
    2869 2279 2280 2265 2264; 2870 2280 2281 2266 2265; 2871 2281 2282 2267 2266;
    2872 2282 1404 1405 2267; 2873 382 1863 2268 1862; 2874 1863 1864 2269 2268;
    2875 1864 1865 2270 2269; 2876 1865 1866 2271 2270; 2877 1866 1867 2272 2271;
    2878 1867 1868 2273 2272; 2879 1868 1869 2274 2273; 2880 1869 1870 2275 2274;
    2881 1870 1871 2276 2275; 2882 1871 1872 2277 2276; 2883 1872 1873 2278 2277;
    2884 1873 1874 2279 2278; 2885 1874 1875 2280 2279; 2886 1875 1876 2281 2280;
    2887 1876 1877 2282 2281; 2888 1877 376 1404 2282; 2920 99 2451 2323 2283;
    2921 2506 2319 2467 2422; 2922 2587 2577 2648 2423; 2923 2606 2663 2433 2652;
    2924 2404 2351 2654 2372; 2925 2496 2335 2590 2594; 2926 2515 2589 2453 2499;
    2927 2612 2609 2486 2413; 2928 2383 2415 2384 2673; 2929 2608 2569 2460 2563;
    2930 2641 2665 2383 2374; 2931 2580 2379 2490 2564; 2932 2323 2491 2430 2332;
    2933 2349 2483 2443 2362; 2934 2621 2359 1026 1025; 2935 2541 2374 2383 2673;
    2936 2375 2629 2450 2324; 2937 2563 2460 2639 2598; 2938 2503 2547 2353 2666;
    2939 2347 2310 2311 2348; 2940 2579 2612 2413 2510; 2941 2406 2650 2581 2585;
    2942 2349 2362 1029 1028; 2943 2362 2443 228 1029; 2944 2392 2495 2452 2595;
    2945 2480 2642 2497 2379; 2946 2539 2563 2598 2335; 2947 2284 2285 2355 2341;
    2948 2459 2541 2673 2315; 2949 2329 2494 2358 2611; 2950 2556 2419 2494 2329;
    2951 2344 2316 2660 2669; 2952 2488 2299 2300 2570; 2953 2360 2558 2416 2474;
    2954 2555 2463 2547 2503; 2955 2381 2390 2356 2426; 2956 2360 2635 2584 2558;
    2957 2415 2377 2659 2384; 2958 2489 2440 2627 2389; 2959 2352 2309 2310 2347;
    2960 2616 2438 2511 2524; 2961 2419 2306 2307 2494; 2962 2636 2466 2634 2328;
    2963 2335 2598 2455 2590; 2964 2326 2320 2664 2667; 2965 2367 2436 2370 2495;
    2966 2427 2503 2666 2662; 2967 2369 2498 2407 2592; 2968 2324 2450 1020 1019;
    2969 2353 2349 1028 1027; 2970 2337 2633 2485 2653; 2971 2401 2652 2477 2469;
    2972 2574 2616 2524 2327; 2973 2460 2348 2428 2639; 2974 2325 2368 2351 2404;
    2975 2416 2558 2615 2636; 2976 2411 2404 2372 2390; 2977 2634 2549 2526 2588;
    2978 2314 2462 2658 2321; 2979 2565 2538 2315 2670; 2980 2476 2508 2635 2360;
    2981 2479 2525 2379 2580; 2982 2332 2430 2629 2375; 2983 2502 2313 370 228;
    2984 2407 2498 2515 2499; 2985 2408 2298 2299 2488; 2986 2505 2418 2405 2520;
    2987 2439 2623 2337 2605; 2988 2430 2473 2628 2629; 2989 2588 2526 2458 2591;
    2990 2364 2670 2369 2387; 2991 2519 2321 2322 2620; 2992 2358 2308 2309 2352;
    2993 2292 2293 2346 2518; 2994 2643 2571 2395 2500; 2995 2447 2506 2422 2638;
    2996 2417 2423 2548 2466; 2997 2431 2469 2373 2354; 2998 2293 2294 2350 2346;
    2999 2375 2324 1019 1018; 3000 2441 2651 2461 2330; 3001 2520 2480 2379 2525;
    3002 2479 2580 2623 2439; 3003 2628 2643 2450 2629; 3004 2320 2441 2330 2457;
    3005 2290 2291 2514 2394; 3006 2633 2564 2487 2586; 3007 2291 2292 2518 2514;
    3008 2518 2644 2431 2661; 3009 2342 2376 2554 2483; 3010 2424 2535 2516 2640;
    3011 2403 2604 2359 2621; 3012 2283 2323 2332 64; 3013 2604 2666 2353 2359;
    3014 2391 2481 2533 2602; 3015 2463 2504 2349 2547; 3016 2453 2668 2512 2675;
    3017 2336 2579 2510 2674; 3018 2644 2401 2469 2431; 3019 2572 2521 2420 2560;
    3020 2518 2346 2606 2644; 3021 2517 2409 2604 2403; 3022 2623 2564 2633 2337;
    3023 2492 2520 2525 2529; 3024 2426 2356 2647 2399; 3025 2356 2574 2327 2647;
    3026 2653 2485 2447 2338; 3027 2654 2331 2438 2616; 3028 2331 2573 2391 2624;
    3029 2550 2384 2659 2603; 3030 2433 2663 2436 2367; 3031 2499 2453 2675 2396;
    3032 2468 2586 2562 2319; 3033 2520 2405 2642 2480; 3034 2373 2595 2454 2381;
    3035 2606 2442 2672 2663; 3036 2596 2399 2493 2459; 3037 2617 2505 2520 2492;
    3038 2428 2312 2313 2502; 3039 2413 2486 2408 2462; 3040 2530 371 2297 2484;
    3041 2622 2599 2435 2376; 3042 2584 2534 2318 2558; 3043 2660 2544 2388 2656;
    3044 2540 2588 2591 2398; 3045 2289 2290 2394 2576; 3046 2530 2484 2478 2651;
    3047 2446 2612 2579 2542; 3048 2543 2446 2542 2613; 3049 2390 2372 2574 2356;
    3050 2632 2336 2674 2425; 3051 2626 2570 2458 2526; 3052 2534 2425 2587 2582;
    3053 2562 2539 2335 2496; 3054 2466 2548 2549 2634; 3055 2607 2302 2303 2402;
    3056 2516 2521 2572 2568; 3057 2442 2522 2527 2672; 3058 2440 2631 2465 2627;
    3059 2359 2353 1027 1026; 3060 2453 2357 2429 2668; 3061 2507 2540 2398 2630;
    3062 2595 2452 2411 2454; 3063 2584 2632 2425 2534; 3064 2398 2591 2397 2630;
    3065 99 2284 2341 2451; 3066 2379 2497 2619 2490; 3067 2581 2414 2537 2585;
    3068 2614 2543 2613 2578; 3069 2450 2500 1021 1020; 3070 2432 2625 2569 2608;
    3071 2389 2627 2476 2610; 3072 2536 2434 2532 2583; 3073 2288 2289 2576 2385;
    3074 2350 2326 2522 2442; 3075 2491 2387 2473 2430; 3076 2394 2514 2646 2576;
    3077 2470 2617 2492 2575; 3078 2388 2653 2338 2448; 3079 2658 2488 2570 2626;
    3080 2436 2386 2657 2370; 3081 2570 2300 2301 2458; 3082 2339 2314 2321 2519;
    3083 2368 2365 2540 2507; 3084 2318 2534 2582 2417; 3085 2332 2375 1018 1017;
    3086 2517 2403 2621 2567; 3087 2435 2528 2551 2545; 3088 2354 2373 2381 2363;
    3089 2454 2411 2390 2381; 3090 2500 2395 1023 1022; 3091 2433 2367 2495 2392;
    3092 2535 2607 2521 2516; 3093 2593 2397 2475 2481; 3094 2537 2536 2583 2405;
    3095 2385 2576 2371 2355; 3096 2545 2553 228 2443; 3097 2458 2301 2302 2607;
    3098 2376 2435 2545 2554; 3099 2512 2668 2662 2409; 3100 2474 2416 2636 2436;
    3101 2639 2428 2502 2551; 3102 2436 2636 2328 2386; 3103 2320 2457 2437 2664;
    3104 2538 2596 2459 2315; 3105 2672 2527 2610 2474; 3106 2501 2639 2551 2528;
    3107 2533 2482 2650 2406; 3108 2667 2412 2557 2522; 3109 2504 2342 2483 2349;
    3110 2478 2484 2340 2609; 3111 2319 2562 2496 2467; 3112 2469 2477 2595 2373;
    3113 2423 2648 2620 2456; 3114 2445 2509 2565 2317; 3115 2533 2406 2410 2602;
    3116 2668 2429 2427 2662; 3117 2372 2654 2616 2574; 3118 2471 2371 2559 2509;
    3119 2426 2399 2596 2538; 3120 2345 2305 2434 2536; 3121 2590 2455 2601 2599;
    3122 2414 2345 2536 2537; 3123 2321 2658 2626 2322; 3124 2671 2329 2611 2464;
    3125 2627 2465 2508 2476; 3126 2432 2608 2539 2562; 3127 2527 2531 2389 2610;
    3128 2583 2532 2671 2642; 3129 2395 2567 1024 1023; 3130 2642 2671 2464 2497;
    3131 2546 2439 2605 2316; 3132 2670 2550 2603 2393; 3133 2484 2297 2298 2340;
    3134 2420 2304 2305 2345; 3135 2343 2555 2503 2427; 3136 2610 2476 2360 2474;
    3137 2524 2511 2523 2566; 3138 2545 2551 2502 2553; 3139 2532 2556 2329 2671;
    3140 2341 2445 2361 2451; 3141 2475 2482 2533 2481; 3142 2485 2468 2506 2447;
    3143 2552 2630 2573 2331; 3144 2370 2657 2368 2325; 3145 2571 2396 2567 2395;
    3146 2652 2433 2392 2477; 3147 2620 2322 2626 2456; 3148 2340 2298 2408 2486;
    3149 2399 2647 2382 2493; 3150 2422 2467 2597 2513; 3151 2286 2287 2385 2355;
    3152 2633 2586 2468 2485; 3153 2656 2388 2448 2343; 3154 2348 2311 2312 2428;
    3155 2568 2572 2560 2400; 3156 2655 2649 2446 2543; 3157 2591 2535 2424 2397;
    3158 2582 2587 2423 2417; 3159 2509 2559 2538 2565; 3160 2591 2458 2607 2535;
    3161 2667 2664 2437 2412; 3162 2674 2339 2648 2577; 3163 2558 2318 2417 2615;
    3164 2549 2456 2626 2526; 3165 2365 2561 2588 2540; 3166 2554 2545 2443 2483;
    3167 2467 2496 2594 2597; 3168 2514 2518 2661 2646; 3169 2351 2552 2331 2654;
    3170 2397 2424 2482 2475; 3171 2564 2490 2449 2487; 3172 2437 2457 2440 2333;
    3173 2425 2674 2577 2587; 3174 2573 2593 2481 2391; 3175 2645 2479 2439 2546;
    3176 2674 2510 2314 2339; 3177 2396 2675 2517 2567; 3178 2617 2410 2418 2505;
    3179 2605 2337 2653 2544; 3180 2355 2371 2471 2341; 3181 2640 2516 2568 2400;
    3182 2603 2546 2316 2344; 3183 2663 2672 2474 2436; 3184 2644 2606 2652 2401;
    3185 2510 2413 2462 2314; 3186 2487 2449 2625 2432; 3187 2567 2621 1025 1024;
    3188 2607 2402 2420 2521; 3189 2482 2424 2640 2650; 3190 2638 2422 2513 2366;
    3191 2669 2660 2656 2334; 3192 2378 2542 2336 2632; 3193 2338 2447 2638 2463;
    3194 2315 2673 2550 2670; 3195 2646 2661 2472 2444; 3196 2522 2557 2531 2527;
    3197 2657 2386 2365 2368; 3198 2651 2478 2609 2649; 3199 2380 2613 2542 2378;
    3200 2661 2354 2363 2472; 3201 2383 2665 2377 2415; 3202 2675 2512 2409 2517;
    3203 2438 2331 2624 2600; 3204 2423 2456 2549 2548; 3205 2328 2634 2588 2561;
    3206 2586 2487 2432 2562; 3207 2630 2397 2593 2573; 3208 2296 249 2441 2320;
    3209 2327 2524 2665 2641; 3210 2409 2662 2666 2604; 3211 2371 2444 2637 2559;
    3212 2444 2472 2363 2637; 3213 2366 2618 2342 2504; 3214 2566 2523 2529 2377;
    3215 2597 2594 2622 2618; 3216 2465 2578 2380 2508; 3217 2402 2303 2304 2420;
    3218 2410 2406 2585 2418; 3219 2576 2646 2444 2371; 3220 2497 2464 2611 2619;
    3221 2473 2592 2643 2628; 3222 2648 2339 2519 2620; 3223 2441 249 2530 2651;
    3224 2624 2391 2602 2470; 3225 2524 2566 2377 2665; 3226 2334 2656 2343 2357;
    3227 2457 2330 2461 2440; 3228 2393 2603 2344 2498; 3229 2440 2461 2614 2631;
    3230 2495 2370 2325 2452; 3231 2351 2507 2630 2552; 3232 2569 2347 2348 2460;
    3233 2637 2363 2381 2426; 3234 2619 2358 2352 2490; 3235 2498 2344 2589 2515;
    3236 2341 2471 2509 2445; 3237 2346 2350 2442 2606; 3238 2463 2638 2366 2504;
    3239 2387 2369 2592 2473; 3240 2451 2361 2491 2323; 3241 2560 2420 2345 2414;
    3242 2594 2590 2599 2622; 3243 2445 2317 2364 2361; 3244 2455 2598 2639 2501;
    3245 2452 2325 2404 2411; 3246 2461 2651 2649 2655; 3247 2631 2614 2578 2465;
    3248 2470 2602 2410 2617; 3249 2386 2328 2561 2365; 3250 2295 2296 2320 2326;
    3251 2649 2609 2612 2446; 3252 2294 2295 2326 2350; 3253 2448 2338 2555 2343;
    3254 2455 2501 2528 2601; 3255 2434 2305 2306 2419; 3256 2640 2400 2581 2650;
    3257 2357 2343 2427 2429; 3258 2513 2597 2618 2366; 3259 2344 2669 2334 2589;
    3260 2559 2637 2426 2538; 3261 2421 2489 2389 2531; 3262 2490 2352 2347 2449;
    3263 2317 2565 2670 2364; 3264 2592 2407 2571 2643; 3265 2407 2499 2396 2571;
    3266 2647 2327 2641 2382; 3267 2494 2307 2308 2358; 3268 2508 2380 2378 2635;
    3269 2618 2622 2376 2342; 3270 2400 2560 2414 2581; 3271 2377 2529 2525 2479;
    3272 2599 2601 2528 2435; 3273 2461 2655 2543 2614; 3274 2532 2434 2419 2556;
    3275 2462 2408 2488 2658; 3276 2361 2364 2387 2491; 3277 2316 2605 2544 2660;
    3278 2412 2437 2333 2421; 3279 2418 2585 2537 2405; 3280 2382 2641 2374 2541;
    3281 2600 2624 2470 2575; 3282 2589 2334 2357 2453; 3283 2615 2417 2466 2636;
    3284 2449 2347 2569 2625; 3285 2377 2479 2645 2659; 3286 2635 2378 2632 2584;
    3287 2523 2575 2492 2529; 3288 2670 2393 2498 2369; 3289 2659 2645 2546 2603;
    3290 2511 2600 2575 2523; 3291 2421 2333 2440 2489; 3292 2493 2382 2541 2459;
    3293 2557 2412 2421 2531; 3294 64 2332 1017; 3295 2578 2613 2380;
    3296 2609 2340 2486; 3297 2368 2507 2351; 3298 2539 2608 2563;
    3299 2477 2392 2595; 3300 2468 2319 2506; 3301 2555 2338 2463;
    3302 2553 2502 228; 3303 2287 2288 2385; 3304 2673 2384 2550;
    3305 2661 2431 2354; 3306 2623 2580 2564; 3307 2450 2643 2500;
    3308 2326 2667 2522; 3309 2542 2579 2336; 3310 2438 2600 2511;
    3311 2619 2611 2358; 3312 2544 2653 2388; 3313 2405 2583 2642;
    3314 2547 2349 2353; 3315 2285 2286 2355; 3316 249 371 2530;
    3317 1021 2500 1022; 3350 2313 2708 1389 370; 3351 2708 2709 1390 1389;
    3352 2709 2710 1391 1390; 3353 2710 2711 1392 1391; 3354 2711 2712 1393 1392;
    3355 2712 2713 1394 1393; 3356 2713 2714 1395 1394; 3357 2714 2715 1396 1395;
    3358 2715 2716 1397 1396; 3359 2716 2717 1398 1397; 3360 2717 2718 1399 1398;
    3361 2718 2719 1400 1399; 3362 2719 2720 1401 1400; 3363 2720 2721 1402 1401;
    3364 2721 2722 1403 1402; 3365 2722 2707 376 1403; 3366 2312 2723 2708 2313;
    3367 2723 2724 2709 2708; 3368 2724 2725 2710 2709; 3369 2725 2726 2711 2710;
    3370 2726 2727 2712 2711; 3371 2727 2728 2713 2712; 3372 2728 2729 2714 2713;
    3373 2729 2730 2715 2714; 3374 2730 2731 2716 2715; 3375 2731 2732 2717 2716;
    3376 2732 2733 2718 2717; 3377 2733 2734 2719 2718; 3378 2734 2735 2720 2719;
    3379 2735 2736 2721 2720; 3380 2736 2737 2722 2721; 3381 2737 2706 2707 2722;
    3382 2311 2738 2723 2312; 3383 2738 2739 2724 2723; 3384 2739 2740 2725 2724;
    3385 2740 2741 2726 2725; 3386 2741 2742 2727 2726; 3387 2742 2743 2728 2727;
    3388 2743 2744 2729 2728; 3389 2744 2745 2730 2729; 3390 2745 2746 2731 2730;
    3391 2746 2747 2732 2731; 3392 2747 2748 2733 2732; 3393 2748 2749 2734 2733;
    3394 2749 2750 2735 2734; 3395 2750 2751 2736 2735; 3396 2751 2752 2737 2736;
    3397 2752 2705 2706 2737; 3398 2310 2753 2738 2311; 3399 2753 2754 2739 2738;
    3400 2754 2755 2740 2739; 3401 2755 2756 2741 2740; 3402 2756 2757 2742 2741;
    3403 2757 2758 2743 2742; 3404 2758 2759 2744 2743; 3405 2759 2760 2745 2744;
    3406 2760 2761 2746 2745; 3407 2761 2762 2747 2746; 3408 2762 2763 2748 2747;
    3409 2763 2764 2749 2748; 3410 2764 2765 2750 2749; 3411 2765 2766 2751 2750;
    3412 2766 2767 2752 2751; 3413 2767 2704 2705 2752; 3414 2309 2768 2753 2310;
    3415 2768 2769 2754 2753; 3416 2769 2770 2755 2754; 3417 2770 2771 2756 2755;
    3418 2771 2772 2757 2756; 3419 2772 2773 2758 2757; 3420 2773 2774 2759 2758;
    3421 2774 2775 2760 2759; 3422 2775 2776 2761 2760; 3423 2776 2777 2762 2761;
    3424 2777 2778 2763 2762; 3425 2778 2779 2764 2763; 3426 2779 2780 2765 2764;
    3427 2780 2781 2766 2765; 3428 2781 2782 2767 2766; 3429 2782 2703 2704 2767;
    3430 2308 2783 2768 2309; 3431 2783 2784 2769 2768; 3432 2784 2785 2770 2769;
    3433 2785 2786 2771 2770; 3434 2786 2787 2772 2771; 3435 2787 2788 2773 2772;
    3436 2788 2789 2774 2773; 3437 2789 2790 2775 2774; 3438 2790 2791 2776 2775;
    3439 2791 2792 2777 2776; 3440 2792 2793 2778 2777; 3441 2793 2794 2779 2778;
    3442 2794 2795 2780 2779; 3443 2795 2796 2781 2780; 3444 2796 2797 2782 2781;
    3445 2797 2702 2703 2782; 3446 2307 2798 2783 2308; 3447 2798 2799 2784 2783;
    3448 2799 2800 2785 2784; 3449 2800 2801 2786 2785; 3450 2801 2802 2787 2786;
    3451 2802 2803 2788 2787; 3452 2803 2804 2789 2788; 3453 2804 2805 2790 2789;
    3454 2805 2806 2791 2790; 3455 2806 2807 2792 2791; 3456 2807 2808 2793 2792;
    3457 2808 2809 2794 2793; 3458 2809 2810 2795 2794; 3459 2810 2811 2796 2795;
    3460 2811 2812 2797 2796; 3461 2812 2701 2702 2797; 3462 2306 2813 2798 2307;
    3463 2813 2814 2799 2798; 3464 2814 2815 2800 2799; 3465 2815 2816 2801 2800;
    3466 2816 2817 2802 2801; 3467 2817 2818 2803 2802; 3468 2818 2819 2804 2803;
    3469 2819 2820 2805 2804; 3470 2820 2821 2806 2805; 3471 2821 2822 2807 2806;
    3472 2822 2823 2808 2807; 3473 2823 2824 2809 2808; 3474 2824 2825 2810 2809;
    3475 2825 2826 2811 2810; 3476 2826 2827 2812 2811; 3477 2827 2700 2701 2812;
    3478 2305 2828 2813 2306; 3479 2828 2829 2814 2813; 3480 2829 2830 2815 2814;
    3481 2830 2831 2816 2815; 3482 2831 2832 2817 2816; 3483 2832 2833 2818 2817;
    3484 2833 2834 2819 2818; 3485 2834 2835 2820 2819; 3486 2835 2836 2821 2820;
    3487 2836 2837 2822 2821; 3488 2837 2838 2823 2822; 3489 2838 2839 2824 2823;
    3490 2839 2840 2825 2824; 3491 2840 2841 2826 2825; 3492 2841 2842 2827 2826;
    3493 2842 2699 2700 2827; 3494 2304 2843 2828 2305; 3495 2843 2844 2829 2828;
    3496 2844 2845 2830 2829; 3497 2845 2846 2831 2830; 3498 2846 2847 2832 2831;
    3499 2847 2848 2833 2832; 3500 2848 2849 2834 2833; 3501 2849 2850 2835 2834;
    3502 2850 2851 2836 2835; 3503 2851 2852 2837 2836; 3504 2852 2853 2838 2837;
    3505 2853 2854 2839 2838; 3506 2854 2855 2840 2839; 3507 2855 2856 2841 2840;
    3508 2856 2857 2842 2841; 3509 2857 2698 2699 2842; 3510 2303 2858 2843 2304;
    3511 2858 2859 2844 2843; 3512 2859 2860 2845 2844; 3513 2860 2861 2846 2845;
    3514 2861 2862 2847 2846; 3515 2862 2863 2848 2847; 3516 2863 2864 2849 2848;
    3517 2864 2865 2850 2849; 3518 2865 2866 2851 2850; 3519 2866 2867 2852 2851;
    3520 2867 2868 2853 2852; 3521 2868 2869 2854 2853; 3522 2869 2870 2855 2854;
    3523 2870 2871 2856 2855; 3524 2871 2872 2857 2856; 3525 2872 2697 2698 2857;
    3526 2302 2873 2858 2303; 3527 2873 2874 2859 2858; 3528 2874 2875 2860 2859;
    3529 2875 2876 2861 2860; 3530 2876 2877 2862 2861; 3531 2877 2878 2863 2862;
    3532 2878 2879 2864 2863; 3533 2879 2880 2865 2864; 3534 2880 2881 2866 2865;
    3535 2881 2882 2867 2866; 3536 2882 2883 2868 2867; 3537 2883 2884 2869 2868;
    3538 2884 2885 2870 2869; 3539 2885 2886 2871 2870; 3540 2886 2887 2872 2871;
    3541 2887 2696 2697 2872; 3542 2301 2888 2873 2302; 3543 2888 2889 2874 2873;
    3544 2889 2890 2875 2874; 3545 2890 2891 2876 2875; 3546 2891 2892 2877 2876;
    3547 2892 2893 2878 2877; 3548 2893 2894 2879 2878; 3549 2894 2895 2880 2879;
    3550 2895 2896 2881 2880; 3551 2896 2897 2882 2881; 3552 2897 2898 2883 2882;
    3553 2898 2899 2884 2883; 3554 2899 2900 2885 2884; 3555 2900 2901 2886 2885;
    3556 2901 2902 2887 2886; 3557 2902 2695 2696 2887; 3558 2300 2903 2888 2301;
    3559 2903 2904 2889 2888; 3560 2904 2905 2890 2889; 3561 2905 2906 2891 2890;
    3562 2906 2907 2892 2891; 3563 2907 2908 2893 2892; 3564 2908 2909 2894 2893;
    3565 2909 2910 2895 2894; 3566 2910 2911 2896 2895; 3567 2911 2912 2897 2896;
    3568 2912 2913 2898 2897; 3569 2913 2914 2899 2898; 3570 2914 2915 2900 2899;
    3571 2915 2916 2901 2900; 3572 2916 2917 2902 2901; 3573 2917 2694 2695 2902;
    3574 2299 2918 2903 2300; 3575 2918 2919 2904 2903; 3576 2919 2920 2905 2904;
    3577 2920 2921 2906 2905; 3578 2921 2922 2907 2906; 3579 2922 2923 2908 2907;
    3580 2923 2924 2909 2908; 3581 2924 2925 2910 2909; 3582 2925 2926 2911 2910;
    3583 2926 2927 2912 2911; 3584 2927 2928 2913 2912; 3585 2928 2929 2914 2913;
    3586 2929 2930 2915 2914; 3587 2930 2931 2916 2915; 3588 2931 2932 2917 2916;
    3589 2932 2693 2694 2917; 3590 2298 2933 2918 2299; 3591 2933 2934 2919 2918;
    3592 2934 2935 2920 2919; 3593 2935 2936 2921 2920; 3594 2936 2937 2922 2921;
    3595 2937 2938 2923 2922; 3596 2938 2939 2924 2923; 3597 2939 2940 2925 2924;
    3598 2940 2941 2926 2925; 3599 2941 2942 2927 2926; 3600 2942 2943 2928 2927;
    3601 2943 2944 2929 2928; 3602 2944 2945 2930 2929; 3603 2945 2946 2931 2930;
    3604 2946 2947 2932 2931; 3605 2947 2692 2693 2932; 3606 2297 2948 2933 2298;
    3607 2948 2949 2934 2933; 3608 2949 2950 2935 2934; 3609 2950 2951 2936 2935;
    3610 2951 2952 2937 2936; 3611 2952 2953 2938 2937; 3612 2953 2954 2939 2938;
    3613 2954 2955 2940 2939; 3614 2955 2956 2941 2940; 3615 2956 2957 2942 2941;
    3616 2957 2958 2943 2942; 3617 2958 2959 2944 2943; 3618 2959 2960 2945 2944;
    3619 2960 2961 2946 2945; 3620 2961 2962 2947 2946; 3621 2962 2691 2692 2947;
    3622 371 2676 2948 2297; 3623 2676 2677 2949 2948; 3624 2677 2678 2950 2949;
    3625 2678 2679 2951 2950; 3626 2679 2680 2952 2951; 3627 2680 2681 2953 2952;
    3628 2681 2682 2954 2953; 3629 2682 2683 2955 2954; 3630 2683 2684 2956 2955;
    3631 2684 2685 2957 2956; 3632 2685 2686 2958 2957; 3633 2686 2687 2959 2958;
    3634 2687 2688 2960 2959; 3635 2688 2689 2961 2960; 3636 2689 2690 2962 2961;
    3637 2690 377 2691 2962; 3670 2963 2995 1863 382; 3671 2995 2996 1864 1863;
    3672 2996 2997 1865 1864; 3673 2997 2998 1866 1865; 3674 2998 2999 1867 1866;
    3675 2999 3000 1868 1867; 3676 3000 3001 1869 1868; 3677 3001 3002 1870 1869;
    3678 3002 3003 1871 1870; 3679 3003 3004 1872 1871; 3680 3004 3005 1873 1872;
    3681 3005 3006 1874 1873; 3682 3006 3007 1875 1874; 3683 3007 3008 1876 1875;
    3684 3008 3009 1877 1876; 3685 3009 2707 376 1877; 3686 2964 3010 2995 2963;
    3687 3010 3011 2996 2995; 3688 3011 3012 2997 2996; 3689 3012 3013 2998 2997;
    3690 3013 3014 2999 2998; 3691 3014 3015 3000 2999; 3692 3015 3016 3001 3000;
    3693 3016 3017 3002 3001; 3694 3017 3018 3003 3002; 3695 3018 3019 3004 3003;
    3696 3019 3020 3005 3004; 3697 3020 3021 3006 3005; 3698 3021 3022 3007 3006;
    3699 3022 3023 3008 3007; 3700 3023 3024 3009 3008; 3701 3024 2706 2707 3009;
    3702 2965 3025 3010 2964; 3703 3025 3026 3011 3010; 3704 3026 3027 3012 3011;
    3705 3027 3028 3013 3012; 3706 3028 3029 3014 3013; 3707 3029 3030 3015 3014;
    3708 3030 3031 3016 3015; 3709 3031 3032 3017 3016; 3710 3032 3033 3018 3017;
    3711 3033 3034 3019 3018; 3712 3034 3035 3020 3019; 3713 3035 3036 3021 3020;
    3714 3036 3037 3022 3021; 3715 3037 3038 3023 3022; 3716 3038 3039 3024 3023;
    3717 3039 2705 2706 3024; 3718 2966 3040 3025 2965; 3719 3040 3041 3026 3025;
    3720 3041 3042 3027 3026; 3721 3042 3043 3028 3027; 3722 3043 3044 3029 3028;
    3723 3044 3045 3030 3029; 3724 3045 3046 3031 3030; 3725 3046 3047 3032 3031;
    3726 3047 3048 3033 3032; 3727 3048 3049 3034 3033; 3728 3049 3050 3035 3034;
    3729 3050 3051 3036 3035; 3730 3051 3052 3037 3036; 3731 3052 3053 3038 3037;
    3732 3053 3054 3039 3038; 3733 3054 2704 2705 3039; 3734 2967 3055 3040 2966;
    3735 3055 3056 3041 3040; 3736 3056 3057 3042 3041; 3737 3057 3058 3043 3042;
    3738 3058 3059 3044 3043; 3739 3059 3060 3045 3044; 3740 3060 3061 3046 3045;
    3741 3061 3062 3047 3046; 3742 3062 3063 3048 3047; 3743 3063 3064 3049 3048;
    3744 3064 3065 3050 3049; 3745 3065 3066 3051 3050; 3746 3066 3067 3052 3051;
    3747 3067 3068 3053 3052; 3748 3068 3069 3054 3053; 3749 3069 2703 2704 3054;
    3750 2968 3070 3055 2967; 3751 3070 3071 3056 3055; 3752 3071 3072 3057 3056;
    3753 3072 3073 3058 3057; 3754 3073 3074 3059 3058; 3755 3074 3075 3060 3059;
    3756 3075 3076 3061 3060; 3757 3076 3077 3062 3061; 3758 3077 3078 3063 3062;
    3759 3078 3079 3064 3063; 3760 3079 3080 3065 3064; 3761 3080 3081 3066 3065;
    3762 3081 3082 3067 3066; 3763 3082 3083 3068 3067; 3764 3083 3084 3069 3068;
    3765 3084 2702 2703 3069; 3766 2969 3085 3070 2968; 3767 3085 3086 3071 3070;
    3768 3086 3087 3072 3071; 3769 3087 3088 3073 3072; 3770 3088 3089 3074 3073;
    3771 3089 3090 3075 3074; 3772 3090 3091 3076 3075; 3773 3091 3092 3077 3076;
    3774 3092 3093 3078 3077; 3775 3093 3094 3079 3078; 3776 3094 3095 3080 3079;
    3777 3095 3096 3081 3080; 3778 3096 3097 3082 3081; 3779 3097 3098 3083 3082;
    3780 3098 3099 3084 3083; 3781 3099 2701 2702 3084; 3782 2970 3100 3085 2969;
    3783 3100 3101 3086 3085; 3784 3101 3102 3087 3086; 3785 3102 3103 3088 3087;
    3786 3103 3104 3089 3088; 3787 3104 3105 3090 3089; 3788 3105 3106 3091 3090;
    3789 3106 3107 3092 3091; 3790 3107 3108 3093 3092; 3791 3108 3109 3094 3093;
    3792 3109 3110 3095 3094; 3793 3110 3111 3096 3095; 3794 3111 3112 3097 3096;
    3795 3112 3113 3098 3097; 3796 3113 3114 3099 3098; 3797 3114 2700 2701 3099;
    3798 2971 3115 3100 2970; 3799 3115 3116 3101 3100; 3800 3116 3117 3102 3101;
    3801 3117 3118 3103 3102; 3802 3118 3119 3104 3103; 3803 3119 3120 3105 3104;
    3804 3120 3121 3106 3105; 3805 3121 3122 3107 3106; 3806 3122 3123 3108 3107;
    3807 3123 3124 3109 3108; 3808 3124 3125 3110 3109; 3809 3125 3126 3111 3110;
    3810 3126 3127 3112 3111; 3811 3127 3128 3113 3112; 3812 3128 3129 3114 3113;
    3813 3129 2699 2700 3114; 3814 2972 3130 3115 2971; 3815 3130 3131 3116 3115;
    3816 3131 3132 3117 3116; 3817 3132 3133 3118 3117; 3818 3133 3134 3119 3118;
    3819 3134 3135 3120 3119; 3820 3135 3136 3121 3120; 3821 3136 3137 3122 3121;
    3822 3137 3138 3123 3122; 3823 3138 3139 3124 3123; 3824 3139 3140 3125 3124;
    3825 3140 3141 3126 3125; 3826 3141 3142 3127 3126; 3827 3142 3143 3128 3127;
    3828 3143 3144 3129 3128; 3829 3144 2698 2699 3129; 3830 2973 3145 3130 2972;
    3831 3145 3146 3131 3130; 3832 3146 3147 3132 3131; 3833 3147 3148 3133 3132;
    3834 3148 3149 3134 3133; 3835 3149 3150 3135 3134; 3836 3150 3151 3136 3135;
    3837 3151 3152 3137 3136; 3838 3152 3153 3138 3137; 3839 3153 3154 3139 3138;
    3840 3154 3155 3140 3139; 3841 3155 3156 3141 3140; 3842 3156 3157 3142 3141;
    3843 3157 3158 3143 3142; 3844 3158 3159 3144 3143; 3845 3159 2697 2698 3144;
    3846 2974 3160 3145 2973; 3847 3160 3161 3146 3145; 3848 3161 3162 3147 3146;
    3849 3162 3163 3148 3147; 3850 3163 3164 3149 3148; 3851 3164 3165 3150 3149;
    3852 3165 3166 3151 3150; 3853 3166 3167 3152 3151; 3854 3167 3168 3153 3152;
    3855 3168 3169 3154 3153; 3856 3169 3170 3155 3154; 3857 3170 3171 3156 3155;
    3858 3171 3172 3157 3156; 3859 3172 3173 3158 3157; 3860 3173 3174 3159 3158;
    3861 3174 2696 2697 3159; 3862 2975 3175 3160 2974; 3863 3175 3176 3161 3160;
    3864 3176 3177 3162 3161; 3865 3177 3178 3163 3162; 3866 3178 3179 3164 3163;
    3867 3179 3180 3165 3164; 3868 3180 3181 3166 3165; 3869 3181 3182 3167 3166;
    3870 3182 3183 3168 3167; 3871 3183 3184 3169 3168; 3872 3184 3185 3170 3169;
    3873 3185 3186 3171 3170; 3874 3186 3187 3172 3171; 3875 3187 3188 3173 3172;
    3876 3188 3189 3174 3173; 3877 3189 2695 2696 3174; 3878 2976 3190 3175 2975;
    3879 3190 3191 3176 3175; 3880 3191 3192 3177 3176; 3881 3192 3193 3178 3177;
    3882 3193 3194 3179 3178; 3883 3194 3195 3180 3179; 3884 3195 3196 3181 3180;
    3885 3196 3197 3182 3181; 3886 3197 3198 3183 3182; 3887 3198 3199 3184 3183;
    3888 3199 3200 3185 3184; 3889 3200 3201 3186 3185; 3890 3201 3202 3187 3186;
    3891 3202 3203 3188 3187; 3892 3203 3204 3189 3188; 3893 3204 2694 2695 3189;
    3894 2977 3205 3190 2976; 3895 3205 3206 3191 3190; 3896 3206 3207 3192 3191;
    3897 3207 3208 3193 3192; 3898 3208 3209 3194 3193; 3899 3209 3210 3195 3194;
    3900 3210 3211 3196 3195; 3901 3211 3212 3197 3196; 3902 3212 3213 3198 3197;
    3903 3213 3214 3199 3198; 3904 3214 3215 3200 3199; 3905 3215 3216 3201 3200;
    3906 3216 3217 3202 3201; 3907 3217 3218 3203 3202; 3908 3218 3219 3204 3203;
    3909 3219 2693 2694 3204; 3910 2978 3220 3205 2977; 3911 3220 3221 3206 3205;
    3912 3221 3222 3207 3206; 3913 3222 3223 3208 3207; 3914 3223 3224 3209 3208;
    3915 3224 3225 3210 3209; 3916 3225 3226 3211 3210; 3917 3226 3227 3212 3211;
    3918 3227 3228 3213 3212; 3919 3228 3229 3214 3213; 3920 3229 3230 3215 3214;
    3921 3230 3231 3216 3215; 3922 3231 3232 3217 3216; 3923 3232 3233 3218 3217;
    3924 3233 3234 3219 3218; 3925 3234 2692 2693 3219; 3926 2979 3235 3220 2978;
    3927 3235 3236 3221 3220; 3928 3236 3237 3222 3221; 3929 3237 3238 3223 3222;
    3930 3238 3239 3224 3223; 3931 3239 3240 3225 3224; 3932 3240 3241 3226 3225;
    3933 3241 3242 3227 3226; 3934 3242 3243 3228 3227; 3935 3243 3244 3229 3228;
    3936 3244 3245 3230 3229; 3937 3245 3246 3231 3230; 3938 3246 3247 3232 3231;
    3939 3247 3248 3233 3232; 3940 3248 3249 3234 3233; 3941 3249 2691 2692 3234;
    3942 383 2980 3235 2979; 3943 2980 2981 3236 3235; 3944 2981 2982 3237 3236;
    3945 2982 2983 3238 3237; 3946 2983 2984 3239 3238; 3947 2984 2985 3240 3239;
    3948 2985 2986 3241 3240; 3949 2986 2987 3242 3241; 3950 2987 2988 3243 3242;
    3951 2988 2989 3244 3243; 3952 2989 2990 3245 3244; 3953 2990 2991 3246 3245;
    3954 2991 2992 3247 3246; 3955 2992 2993 3248 3247; 3956 2993 2994 3249 3248;
    3957 2994 377 2691 3249; 3989 134 3418 3290 3250; 3990 3473 3286 3434 3389;
    3991 3554 3544 3615 3390; 3992 3573 3630 3400 3619; 3993 3371 3318 3621 3339;
    3994 3463 3302 3557 3561; 3995 3482 3556 3420 3466; 3996 3579 3576 3453 3380;
    3997 3350 3382 3351 3640; 3998 3575 3536 3427 3530; 3999 3608 3632 3350 3341;
    4000 3547 3346 3457 3531; 4001 3290 3458 3397 3299; 4002 3316 3450 3410 3329;
    4003 3588 3326 2293 2292; 4004 3508 3341 3350 3640; 4005 3342 3596 3417 3291;
    4006 3530 3427 3606 3565; 4007 3470 3514 3320 3633; 4008 3314 3277 3278 3315;
    4009 3546 3579 3380 3477; 4010 3373 3617 3548 3552; 4011 3316 3329 2296 2295;
    4012 3329 3410 249 2296; 4013 3359 3462 3419 3562; 4014 3447 3609 3464 3346;
    4015 3506 3530 3565 3302; 4016 3251 3252 3322 3308; 4017 3426 3508 3640 3282;
    4018 3296 3461 3325 3578; 4019 3523 3386 3461 3296; 4020 3311 3283 3627 3636;
    4021 3455 3266 3267 3537; 4022 3327 3525 3383 3441; 4023 3522 3430 3514 3470;
    4024 3348 3357 3323 3393; 4025 3327 3602 3551 3525; 4026 3382 3344 3626 3351;
    4027 3456 3407 3594 3356; 4028 3319 3276 3277 3314; 4029 3583 3405 3478 3491;
    4030 3386 3273 3274 3461; 4031 3603 3433 3601 3295; 4032 3302 3565 3422 3557;
    4033 3293 3287 3631 3634; 4034 3334 3403 3337 3462; 4035 3394 3470 3633 3629;
    4036 3336 3465 3374 3559; 4037 3291 3417 2287 2286; 4038 3320 3316 2295 2294;
    4039 3304 3600 3452 3620; 4040 3368 3619 3444 3436; 4041 3541 3583 3491 3294;
    4042 3427 3315 3395 3606; 4043 3292 3335 3318 3371; 4044 3383 3525 3582 3603;
    4045 3378 3371 3339 3357; 4046 3601 3516 3493 3555; 4047 3281 3429 3625 3288;
    4048 3532 3505 3282 3637; 4049 3443 3475 3602 3327; 4050 3446 3492 3346 3547;
    4051 3299 3397 3596 3342; 4052 3469 3280 371 249; 4053 3374 3465 3482 3466;
    4054 3375 3265 3266 3455; 4055 3472 3385 3372 3487; 4056 3406 3590 3304 3572;
    4057 3397 3440 3595 3596; 4058 3555 3493 3425 3558; 4059 3331 3637 3336 3354;
    4060 3486 3288 3289 3587; 4061 3325 3275 3276 3319; 4062 3259 3260 3313 3485;
    4063 3610 3538 3362 3467; 4064 3414 3473 3389 3605; 4065 3384 3390 3515 3433;
    4066 3398 3436 3340 3321; 4067 3260 3261 3317 3313; 4068 3342 3291 2286 2285;
    4069 3408 3618 3428 3297; 4070 3487 3447 3346 3492; 4071 3446 3547 3590 3406;
    4072 3595 3610 3417 3596; 4073 3287 3408 3297 3424; 4074 3257 3258 3481 3361;
    4075 3600 3531 3454 3553; 4076 3258 3259 3485 3481; 4077 3485 3611 3398 3628;
    4078 3309 3343 3521 3450; 4079 3391 3502 3483 3607; 4080 3370 3571 3326 3588;
    4081 3250 3290 3299 99; 4082 3571 3633 3320 3326; 4083 3358 3448 3500 3569;
    4084 3430 3471 3316 3514; 4085 3420 3635 3479 3642; 4086 3303 3546 3477 3641;
    4087 3611 3368 3436 3398; 4088 3539 3488 3387 3527; 4089 3485 3313 3573 3611;
    4090 3484 3376 3571 3370; 4091 3590 3531 3600 3304; 4092 3459 3487 3492 3496;
    4093 3393 3323 3614 3366; 4094 3323 3541 3294 3614; 4095 3620 3452 3414 3305;
    4096 3621 3298 3405 3583; 4097 3298 3540 3358 3591; 4098 3517 3351 3626 3570;
    4099 3400 3630 3403 3334; 4100 3466 3420 3642 3363; 4101 3435 3553 3529 3286;
    4102 3487 3372 3609 3447; 4103 3340 3562 3421 3348; 4104 3573 3409 3639 3630;
    4105 3563 3366 3460 3426; 4106 3584 3472 3487 3459; 4107 3395 3279 3280 3469;
    4108 3380 3453 3375 3429; 4109 3497 372 3264 3451; 4110 3589 3566 3402 3343;
    4111 3551 3501 3285 3525; 4112 3627 3511 3355 3623; 4113 3507 3555 3558 3365;
    4114 3256 3257 3361 3543; 4115 3497 3451 3445 3618; 4116 3413 3579 3546 3509;
    4117 3510 3413 3509 3580; 4118 3357 3339 3541 3323; 4119 3599 3303 3641 3392;
    4120 3593 3537 3425 3493; 4121 3501 3392 3554 3549; 4122 3529 3506 3302 3463;
    4123 3433 3515 3516 3601; 4124 3574 3269 3270 3369; 4125 3483 3488 3539 3535;
    4126 3409 3489 3494 3639; 4127 3407 3598 3432 3594; 4128 3326 3320 2294 2293;
    4129 3420 3324 3396 3635; 4130 3474 3507 3365 3597; 4131 3562 3419 3378 3421;
    4132 3551 3599 3392 3501; 4133 3365 3558 3364 3597; 4134 134 3251 3308 3418;
    4135 3346 3464 3586 3457; 4136 3548 3381 3504 3552; 4137 3581 3510 3580 3545;
    4138 3417 3467 2288 2287; 4139 3399 3592 3536 3575; 4140 3356 3594 3443 3577;
    4141 3503 3401 3499 3550; 4142 3255 3256 3543 3352; 4143 3317 3293 3489 3409;
    4144 3458 3354 3440 3397; 4145 3361 3481 3613 3543; 4146 3437 3584 3459 3542;
    4147 3355 3620 3305 3415; 4148 3625 3455 3537 3593; 4149 3403 3353 3624 3337;
    4150 3537 3267 3268 3425; 4151 3306 3281 3288 3486; 4152 3335 3332 3507 3474;
    4153 3285 3501 3549 3384; 4154 3299 3342 2285 2284; 4155 3484 3370 3588 3534;
    4156 3402 3495 3518 3512; 4157 3321 3340 3348 3330; 4158 3421 3378 3357 3348;
    4159 3467 3362 2290 2289; 4160 3400 3334 3462 3359; 4161 3502 3574 3488 3483;
    4162 3560 3364 3442 3448; 4163 3504 3503 3550 3372; 4164 3352 3543 3338 3322;
    4165 3512 3520 249 3410; 4166 3425 3268 3269 3574; 4167 3343 3402 3512 3521;
    4168 3479 3635 3629 3376; 4169 3441 3383 3603 3403; 4170 3606 3395 3469 3518;
    4171 3403 3603 3295 3353; 4172 3287 3424 3404 3631; 4173 3505 3563 3426 3282;
    4174 3639 3494 3577 3441; 4175 3468 3606 3518 3495; 4176 3500 3449 3617 3373;
    4177 3634 3379 3524 3489; 4178 3471 3309 3450 3316; 4179 3445 3451 3307 3576;
    4180 3286 3529 3463 3434; 4181 3436 3444 3562 3340; 4182 3390 3615 3587 3423;
    4183 3412 3476 3532 3284; 4184 3500 3373 3377 3569; 4185 3635 3396 3394 3629;
    4186 3339 3621 3583 3541; 4187 3438 3338 3526 3476; 4188 3393 3366 3563 3505;
    4189 3312 3272 3401 3503; 4190 3557 3422 3568 3566; 4191 3381 3312 3503 3504;
    4192 3288 3625 3593 3289; 4193 3638 3296 3578 3431; 4194 3594 3432 3475 3443;
    4195 3399 3575 3506 3529; 4196 3494 3498 3356 3577; 4197 3550 3499 3638 3609;
    4198 3362 3534 2291 2290; 4199 3609 3638 3431 3464; 4200 3513 3406 3572 3283;
    4201 3637 3517 3570 3360; 4202 3451 3264 3265 3307; 4203 3387 3271 3272 3312;
    4204 3310 3522 3470 3394; 4205 3577 3443 3327 3441; 4206 3491 3478 3490 3533;
    4207 3512 3518 3469 3520; 4208 3499 3523 3296 3638; 4209 3308 3412 3328 3418;
    4210 3442 3449 3500 3448; 4211 3452 3435 3473 3414; 4212 3519 3597 3540 3298;
    4213 3337 3624 3335 3292; 4214 3538 3363 3534 3362; 4215 3619 3400 3359 3444;
    4216 3587 3289 3593 3423; 4217 3307 3265 3375 3453; 4218 3366 3614 3349 3460;
    4219 3389 3434 3564 3480; 4220 3253 3254 3352 3322; 4221 3600 3553 3435 3452;
    4222 3623 3355 3415 3310; 4223 3315 3278 3279 3395; 4224 3535 3539 3527 3367;
    4225 3622 3616 3413 3510; 4226 3558 3502 3391 3364; 4227 3549 3554 3390 3384;
    4228 3476 3526 3505 3532; 4229 3558 3425 3574 3502; 4230 3634 3631 3404 3379;
    4231 3641 3306 3615 3544; 4232 3525 3285 3384 3582; 4233 3516 3423 3593 3493;
    4234 3332 3528 3555 3507; 4235 3521 3512 3410 3450; 4236 3434 3463 3561 3564;
    4237 3481 3485 3628 3613; 4238 3318 3519 3298 3621; 4239 3364 3391 3449 3442;
    4240 3531 3457 3416 3454; 4241 3404 3424 3407 3300; 4242 3392 3641 3544 3554;
    4243 3540 3560 3448 3358; 4244 3612 3446 3406 3513; 4245 3641 3477 3281 3306;
    4246 3363 3642 3484 3534; 4247 3584 3377 3385 3472; 4248 3572 3304 3620 3511;
    4249 3322 3338 3438 3308; 4250 3607 3483 3535 3367; 4251 3570 3513 3283 3311;
    4252 3630 3639 3441 3403; 4253 3611 3573 3619 3368; 4254 3477 3380 3429 3281;
    4255 3454 3416 3592 3399; 4256 3534 3588 2292 2291; 4257 3574 3369 3387 3488;
    4258 3449 3391 3607 3617; 4259 3605 3389 3480 3333; 4260 3636 3627 3623 3301;
    4261 3345 3509 3303 3599; 4262 3305 3414 3605 3430; 4263 3282 3640 3517 3637;
    4264 3613 3628 3439 3411; 4265 3489 3524 3498 3494; 4266 3624 3353 3332 3335;
    4267 3618 3445 3576 3616; 4268 3347 3580 3509 3345; 4269 3628 3321 3330 3439;
    4270 3350 3632 3344 3382; 4271 3642 3479 3376 3484; 4272 3405 3298 3591 3567;
    4273 3390 3423 3516 3515; 4274 3295 3601 3555 3528; 4275 3553 3454 3399 3529;
    4276 3597 3364 3560 3540; 4277 3263 270 3408 3287; 4278 3294 3491 3632 3608;
    4279 3376 3629 3633 3571; 4280 3338 3411 3604 3526; 4281 3411 3439 3330 3604;
    4282 3333 3585 3309 3471; 4283 3533 3490 3496 3344; 4284 3564 3561 3589 3585;
    4285 3432 3545 3347 3475; 4286 3369 3270 3271 3387; 4287 3377 3373 3552 3385;
    4288 3543 3613 3411 3338; 4289 3464 3431 3578 3586; 4290 3440 3559 3610 3595;
    4291 3615 3306 3486 3587; 4292 3408 270 3497 3618; 4293 3591 3358 3569 3437;
    4294 3491 3533 3344 3632; 4295 3301 3623 3310 3324; 4296 3424 3297 3428 3407;
    4297 3360 3570 3311 3465; 4298 3407 3428 3581 3598; 4299 3462 3337 3292 3419;
    4300 3318 3474 3597 3519; 4301 3536 3314 3315 3427; 4302 3604 3330 3348 3393;
    4303 3586 3325 3319 3457; 4304 3465 3311 3556 3482; 4305 3308 3438 3476 3412;
    4306 3313 3317 3409 3573; 4307 3430 3605 3333 3471; 4308 3354 3336 3559 3440;
    4309 3418 3328 3458 3290; 4310 3527 3387 3312 3381; 4311 3561 3557 3566 3589;
    4312 3412 3284 3331 3328; 4313 3422 3565 3606 3468; 4314 3419 3292 3371 3378;
    4315 3428 3618 3616 3622; 4316 3598 3581 3545 3432; 4317 3437 3569 3377 3584;
    4318 3353 3295 3528 3332; 4319 3262 3263 3287 3293; 4320 3616 3576 3579 3413;
    4321 3261 3262 3293 3317; 4322 3415 3305 3522 3310; 4323 3422 3468 3495 3568;
    4324 3401 3272 3273 3386; 4325 3607 3367 3548 3617; 4326 3324 3310 3394 3396;
    4327 3480 3564 3585 3333; 4328 3311 3636 3301 3556; 4329 3526 3604 3393 3505;
    4330 3388 3456 3356 3498; 4331 3457 3319 3314 3416; 4332 3284 3532 3637 3331;
    4333 3559 3374 3538 3610; 4334 3374 3466 3363 3538; 4335 3614 3294 3608 3349;
    4336 3461 3274 3275 3325; 4337 3475 3347 3345 3602; 4338 3585 3589 3343 3309;
    4339 3367 3527 3381 3548; 4340 3344 3496 3492 3446; 4341 3566 3568 3495 3402;
    4342 3428 3622 3510 3581; 4343 3499 3401 3386 3523; 4344 3429 3375 3455 3625;
    4345 3328 3331 3354 3458; 4346 3283 3572 3511 3627; 4347 3379 3404 3300 3388;
    4348 3385 3552 3504 3372; 4349 3349 3608 3341 3508; 4350 3567 3591 3437 3542;
    4351 3556 3301 3324 3420; 4352 3582 3384 3433 3603; 4353 3416 3314 3536 3592;
    4354 3344 3446 3612 3626; 4355 3602 3345 3599 3551; 4356 3490 3542 3459 3496;
    4357 3637 3360 3465 3336; 4358 3626 3612 3513 3570; 4359 3478 3567 3542 3490;
    4360 3388 3300 3407 3456; 4361 3460 3349 3508 3426; 4362 3524 3379 3388 3498;
    4363 99 3299 2284; 4364 3545 3580 3347; 4365 3576 3307 3453;
    4366 3335 3474 3318; 4367 3506 3575 3530; 4368 3444 3359 3562;
    4369 3435 3286 3473; 4370 3522 3305 3430; 4371 3520 3469 249;
    4372 3254 3255 3352; 4373 3640 3351 3517; 4374 3628 3398 3321;
    4375 3590 3547 3531; 4376 3417 3610 3467; 4377 3293 3634 3489;
    4378 3509 3546 3303; 4379 3405 3567 3478; 4380 3586 3578 3325;
    4381 3511 3620 3355; 4382 3372 3550 3609; 4383 3514 3316 3320;
    4384 3252 3253 3322; 4385 270 372 3497; 4386 2288 3467 2289;
    4419 3280 3675 2676 371; 4420 3675 3676 2677 2676; 4421 3676 3677 2678 2677;
    4422 3677 3678 2679 2678; 4423 3678 3679 2680 2679; 4424 3679 3680 2681 2680;
    4425 3680 3681 2682 2681; 4426 3681 3682 2683 2682; 4427 3682 3683 2684 2683;
    4428 3683 3684 2685 2684; 4429 3684 3685 2686 2685; 4430 3685 3686 2687 2686;
    4431 3686 3687 2688 2687; 4432 3687 3688 2689 2688; 4433 3688 3689 2690 2689;
    4434 3689 3674 377 2690; 4435 3279 3690 3675 3280; 4436 3690 3691 3676 3675;
    4437 3691 3692 3677 3676; 4438 3692 3693 3678 3677; 4439 3693 3694 3679 3678;
    4440 3694 3695 3680 3679; 4441 3695 3696 3681 3680; 4442 3696 3697 3682 3681;
    4443 3697 3698 3683 3682; 4444 3698 3699 3684 3683; 4445 3699 3700 3685 3684;
    4446 3700 3701 3686 3685; 4447 3701 3702 3687 3686; 4448 3702 3703 3688 3687;
    4449 3703 3704 3689 3688; 4450 3704 3673 3674 3689; 4451 3278 3705 3690 3279;
    4452 3705 3706 3691 3690; 4453 3706 3707 3692 3691; 4454 3707 3708 3693 3692;
    4455 3708 3709 3694 3693; 4456 3709 3710 3695 3694; 4457 3710 3711 3696 3695;
    4458 3711 3712 3697 3696; 4459 3712 3713 3698 3697; 4460 3713 3714 3699 3698;
    4461 3714 3715 3700 3699; 4462 3715 3716 3701 3700; 4463 3716 3717 3702 3701;
    4464 3717 3718 3703 3702; 4465 3718 3719 3704 3703; 4466 3719 3672 3673 3704;
    4467 3277 3720 3705 3278; 4468 3720 3721 3706 3705; 4469 3721 3722 3707 3706;
    4470 3722 3723 3708 3707; 4471 3723 3724 3709 3708; 4472 3724 3725 3710 3709;
    4473 3725 3726 3711 3710; 4474 3726 3727 3712 3711; 4475 3727 3728 3713 3712;
    4476 3728 3729 3714 3713; 4477 3729 3730 3715 3714; 4478 3730 3731 3716 3715;
    4479 3731 3732 3717 3716; 4480 3732 3733 3718 3717; 4481 3733 3734 3719 3718;
    4482 3734 3671 3672 3719; 4483 3276 3735 3720 3277; 4484 3735 3736 3721 3720;
    4485 3736 3737 3722 3721; 4486 3737 3738 3723 3722; 4487 3738 3739 3724 3723;
    4488 3739 3740 3725 3724; 4489 3740 3741 3726 3725; 4490 3741 3742 3727 3726;
    4491 3742 3743 3728 3727; 4492 3743 3744 3729 3728; 4493 3744 3745 3730 3729;
    4494 3745 3746 3731 3730; 4495 3746 3747 3732 3731; 4496 3747 3748 3733 3732;
    4497 3748 3749 3734 3733; 4498 3749 3670 3671 3734; 4499 3275 3750 3735 3276;
    4500 3750 3751 3736 3735; 4501 3751 3752 3737 3736; 4502 3752 3753 3738 3737;
    4503 3753 3754 3739 3738; 4504 3754 3755 3740 3739; 4505 3755 3756 3741 3740;
    4506 3756 3757 3742 3741; 4507 3757 3758 3743 3742; 4508 3758 3759 3744 3743;
    4509 3759 3760 3745 3744; 4510 3760 3761 3746 3745; 4511 3761 3762 3747 3746;
    4512 3762 3763 3748 3747; 4513 3763 3764 3749 3748; 4514 3764 3669 3670 3749;
    4515 3274 3765 3750 3275; 4516 3765 3766 3751 3750; 4517 3766 3767 3752 3751;
    4518 3767 3768 3753 3752; 4519 3768 3769 3754 3753; 4520 3769 3770 3755 3754;
    4521 3770 3771 3756 3755; 4522 3771 3772 3757 3756; 4523 3772 3773 3758 3757;
    4524 3773 3774 3759 3758; 4525 3774 3775 3760 3759; 4526 3775 3776 3761 3760;
    4527 3776 3777 3762 3761; 4528 3777 3778 3763 3762; 4529 3778 3779 3764 3763;
    4530 3779 3668 3669 3764; 4531 3273 3780 3765 3274; 4532 3780 3781 3766 3765;
    4533 3781 3782 3767 3766; 4534 3782 3783 3768 3767; 4535 3783 3784 3769 3768;
    4536 3784 3785 3770 3769; 4537 3785 3786 3771 3770; 4538 3786 3787 3772 3771;
    4539 3787 3788 3773 3772; 4540 3788 3789 3774 3773; 4541 3789 3790 3775 3774;
    4542 3790 3791 3776 3775; 4543 3791 3792 3777 3776; 4544 3792 3793 3778 3777;
    4545 3793 3794 3779 3778; 4546 3794 3667 3668 3779; 4547 3272 3795 3780 3273;
    4548 3795 3796 3781 3780; 4549 3796 3797 3782 3781; 4550 3797 3798 3783 3782;
    4551 3798 3799 3784 3783; 4552 3799 3800 3785 3784; 4553 3800 3801 3786 3785;
    4554 3801 3802 3787 3786; 4555 3802 3803 3788 3787; 4556 3803 3804 3789 3788;
    4557 3804 3805 3790 3789; 4558 3805 3806 3791 3790; 4559 3806 3807 3792 3791;
    4560 3807 3808 3793 3792; 4561 3808 3809 3794 3793; 4562 3809 3666 3667 3794;
    4563 3271 3810 3795 3272; 4564 3810 3811 3796 3795; 4565 3811 3812 3797 3796;
    4566 3812 3813 3798 3797; 4567 3813 3814 3799 3798; 4568 3814 3815 3800 3799;
    4569 3815 3816 3801 3800; 4570 3816 3817 3802 3801; 4571 3817 3818 3803 3802;
    4572 3818 3819 3804 3803; 4573 3819 3820 3805 3804; 4574 3820 3821 3806 3805;
    4575 3821 3822 3807 3806; 4576 3822 3823 3808 3807; 4577 3823 3824 3809 3808;
    4578 3824 3665 3666 3809; 4579 3270 3825 3810 3271; 4580 3825 3826 3811 3810;
    4581 3826 3827 3812 3811; 4582 3827 3828 3813 3812; 4583 3828 3829 3814 3813;
    4584 3829 3830 3815 3814; 4585 3830 3831 3816 3815; 4586 3831 3832 3817 3816;
    4587 3832 3833 3818 3817; 4588 3833 3834 3819 3818; 4589 3834 3835 3820 3819;
    4590 3835 3836 3821 3820; 4591 3836 3837 3822 3821; 4592 3837 3838 3823 3822;
    4593 3838 3839 3824 3823; 4594 3839 3664 3665 3824; 4595 3269 3840 3825 3270;
    4596 3840 3841 3826 3825; 4597 3841 3842 3827 3826; 4598 3842 3843 3828 3827;
    4599 3843 3844 3829 3828; 4600 3844 3845 3830 3829; 4601 3845 3846 3831 3830;
    4602 3846 3847 3832 3831; 4603 3847 3848 3833 3832; 4604 3848 3849 3834 3833;
    4605 3849 3850 3835 3834; 4606 3850 3851 3836 3835; 4607 3851 3852 3837 3836;
    4608 3852 3853 3838 3837; 4609 3853 3854 3839 3838; 4610 3854 3663 3664 3839;
    4611 3268 3855 3840 3269; 4612 3855 3856 3841 3840; 4613 3856 3857 3842 3841;
    4614 3857 3858 3843 3842; 4615 3858 3859 3844 3843; 4616 3859 3860 3845 3844;
    4617 3860 3861 3846 3845; 4618 3861 3862 3847 3846; 4619 3862 3863 3848 3847;
    4620 3863 3864 3849 3848; 4621 3864 3865 3850 3849; 4622 3865 3866 3851 3850;
    4623 3866 3867 3852 3851; 4624 3867 3868 3853 3852; 4625 3868 3869 3854 3853;
    4626 3869 3662 3663 3854; 4627 3267 3870 3855 3268; 4628 3870 3871 3856 3855;
    4629 3871 3872 3857 3856; 4630 3872 3873 3858 3857; 4631 3873 3874 3859 3858;
    4632 3874 3875 3860 3859; 4633 3875 3876 3861 3860; 4634 3876 3877 3862 3861;
    4635 3877 3878 3863 3862; 4636 3878 3879 3864 3863; 4637 3879 3880 3865 3864;
    4638 3880 3881 3866 3865; 4639 3881 3882 3867 3866; 4640 3882 3883 3868 3867;
    4641 3883 3884 3869 3868; 4642 3884 3661 3662 3869; 4643 3266 3885 3870 3267;
    4644 3885 3886 3871 3870; 4645 3886 3887 3872 3871; 4646 3887 3888 3873 3872;
    4647 3888 3889 3874 3873; 4648 3889 3890 3875 3874; 4649 3890 3891 3876 3875;
    4650 3891 3892 3877 3876; 4651 3892 3893 3878 3877; 4652 3893 3894 3879 3878;
    4653 3894 3895 3880 3879; 4654 3895 3896 3881 3880; 4655 3896 3897 3882 3881;
    4656 3897 3898 3883 3882; 4657 3898 3899 3884 3883; 4658 3899 3660 3661 3884;
    4659 3265 3900 3885 3266; 4660 3900 3901 3886 3885; 4661 3901 3902 3887 3886;
    4662 3902 3903 3888 3887; 4663 3903 3904 3889 3888; 4664 3904 3905 3890 3889;
    4665 3905 3906 3891 3890; 4666 3906 3907 3892 3891; 4667 3907 3908 3893 3892;
    4668 3908 3909 3894 3893; 4669 3909 3910 3895 3894; 4670 3910 3911 3896 3895;
    4671 3911 3912 3897 3896; 4672 3912 3913 3898 3897; 4673 3913 3914 3899 3898;
    4674 3914 3659 3660 3899; 4675 3264 3915 3900 3265; 4676 3915 3916 3901 3900;
    4677 3916 3917 3902 3901; 4678 3917 3918 3903 3902; 4679 3918 3919 3904 3903;
    4680 3919 3920 3905 3904; 4681 3920 3921 3906 3905; 4682 3921 3922 3907 3906;
    4683 3922 3923 3908 3907; 4684 3923 3924 3909 3908; 4685 3924 3925 3910 3909;
    4686 3925 3926 3911 3910; 4687 3926 3927 3912 3911; 4688 3927 3928 3913 3912;
    4689 3928 3929 3914 3913; 4690 3929 3658 3659 3914; 4691 372 3643 3915 3264;
    4692 3643 3644 3916 3915; 4693 3644 3645 3917 3916; 4694 3645 3646 3918 3917;
    4695 3646 3647 3919 3918; 4696 3647 3648 3920 3919; 4697 3648 3649 3921 3920;
    4698 3649 3650 3922 3921; 4699 3650 3651 3923 3922; 4700 3651 3652 3924 3923;
    4701 3652 3653 3925 3924; 4702 3653 3654 3926 3925; 4703 3654 3655 3927 3926;
    4704 3655 3656 3928 3927; 4705 3656 3657 3929 3928; 4706 3657 378 3658 3929;
    4739 3930 3962 2980 383; 4740 3962 3963 2981 2980; 4741 3963 3964 2982 2981;
    4742 3964 3965 2983 2982; 4743 3965 3966 2984 2983; 4744 3966 3967 2985 2984;
    4745 3967 3968 2986 2985; 4746 3968 3969 2987 2986; 4747 3969 3970 2988 2987;
    4748 3970 3971 2989 2988; 4749 3971 3972 2990 2989; 4750 3972 3973 2991 2990;
    4751 3973 3974 2992 2991; 4752 3974 3975 2993 2992; 4753 3975 3976 2994 2993;
    4754 3976 3674 377 2994; 4755 3931 3977 3962 3930; 4756 3977 3978 3963 3962;
    4757 3978 3979 3964 3963; 4758 3979 3980 3965 3964; 4759 3980 3981 3966 3965;
    4760 3981 3982 3967 3966; 4761 3982 3983 3968 3967; 4762 3983 3984 3969 3968;
    4763 3984 3985 3970 3969; 4764 3985 3986 3971 3970; 4765 3986 3987 3972 3971;
    4766 3987 3988 3973 3972; 4767 3988 3989 3974 3973; 4768 3989 3990 3975 3974;
    4769 3990 3991 3976 3975; 4770 3991 3673 3674 3976; 4771 3932 3992 3977 3931;
    4772 3992 3993 3978 3977; 4773 3993 3994 3979 3978; 4774 3994 3995 3980 3979;
    4775 3995 3996 3981 3980; 4776 3996 3997 3982 3981; 4777 3997 3998 3983 3982;
    4778 3998 3999 3984 3983; 4779 3999 4000 3985 3984; 4780 4000 4001 3986 3985;
    4781 4001 4002 3987 3986; 4782 4002 4003 3988 3987; 4783 4003 4004 3989 3988;
    4784 4004 4005 3990 3989; 4785 4005 4006 3991 3990; 4786 4006 3672 3673 3991;
    4787 3933 4007 3992 3932; 4788 4007 4008 3993 3992; 4789 4008 4009 3994 3993;
    4790 4009 4010 3995 3994; 4791 4010 4011 3996 3995; 4792 4011 4012 3997 3996;
    4793 4012 4013 3998 3997; 4794 4013 4014 3999 3998; 4795 4014 4015 4000 3999;
    4796 4015 4016 4001 4000; 4797 4016 4017 4002 4001; 4798 4017 4018 4003 4002;
    4799 4018 4019 4004 4003; 4800 4019 4020 4005 4004; 4801 4020 4021 4006 4005;
    4802 4021 3671 3672 4006; 4803 3934 4022 4007 3933; 4804 4022 4023 4008 4007;
    4805 4023 4024 4009 4008; 4806 4024 4025 4010 4009; 4807 4025 4026 4011 4010;
    4808 4026 4027 4012 4011; 4809 4027 4028 4013 4012; 4810 4028 4029 4014 4013;
    4811 4029 4030 4015 4014; 4812 4030 4031 4016 4015; 4813 4031 4032 4017 4016;
    4814 4032 4033 4018 4017; 4815 4033 4034 4019 4018; 4816 4034 4035 4020 4019;
    4817 4035 4036 4021 4020; 4818 4036 3670 3671 4021; 4819 3935 4037 4022 3934;
    4820 4037 4038 4023 4022; 4821 4038 4039 4024 4023; 4822 4039 4040 4025 4024;
    4823 4040 4041 4026 4025; 4824 4041 4042 4027 4026; 4825 4042 4043 4028 4027;
    4826 4043 4044 4029 4028; 4827 4044 4045 4030 4029; 4828 4045 4046 4031 4030;
    4829 4046 4047 4032 4031; 4830 4047 4048 4033 4032; 4831 4048 4049 4034 4033;
    4832 4049 4050 4035 4034; 4833 4050 4051 4036 4035; 4834 4051 3669 3670 4036;
    4835 3936 4052 4037 3935; 4836 4052 4053 4038 4037; 4837 4053 4054 4039 4038;
    4838 4054 4055 4040 4039; 4839 4055 4056 4041 4040; 4840 4056 4057 4042 4041;
    4841 4057 4058 4043 4042; 4842 4058 4059 4044 4043; 4843 4059 4060 4045 4044;
    4844 4060 4061 4046 4045; 4845 4061 4062 4047 4046; 4846 4062 4063 4048 4047;
    4847 4063 4064 4049 4048; 4848 4064 4065 4050 4049; 4849 4065 4066 4051 4050;
    4850 4066 3668 3669 4051; 4851 3937 4067 4052 3936; 4852 4067 4068 4053 4052;
    4853 4068 4069 4054 4053; 4854 4069 4070 4055 4054; 4855 4070 4071 4056 4055;
    4856 4071 4072 4057 4056; 4857 4072 4073 4058 4057; 4858 4073 4074 4059 4058;
    4859 4074 4075 4060 4059; 4860 4075 4076 4061 4060; 4861 4076 4077 4062 4061;
    4862 4077 4078 4063 4062; 4863 4078 4079 4064 4063; 4864 4079 4080 4065 4064;
    4865 4080 4081 4066 4065; 4866 4081 3667 3668 4066; 4867 3938 4082 4067 3937;
    4868 4082 4083 4068 4067; 4869 4083 4084 4069 4068; 4870 4084 4085 4070 4069;
    4871 4085 4086 4071 4070; 4872 4086 4087 4072 4071; 4873 4087 4088 4073 4072;
    4874 4088 4089 4074 4073; 4875 4089 4090 4075 4074; 4876 4090 4091 4076 4075;
    4877 4091 4092 4077 4076; 4878 4092 4093 4078 4077; 4879 4093 4094 4079 4078;
    4880 4094 4095 4080 4079; 4881 4095 4096 4081 4080; 4882 4096 3666 3667 4081;
    4883 3939 4097 4082 3938; 4884 4097 4098 4083 4082; 4885 4098 4099 4084 4083;
    4886 4099 4100 4085 4084; 4887 4100 4101 4086 4085; 4888 4101 4102 4087 4086;
    4889 4102 4103 4088 4087; 4890 4103 4104 4089 4088; 4891 4104 4105 4090 4089;
    4892 4105 4106 4091 4090; 4893 4106 4107 4092 4091; 4894 4107 4108 4093 4092;
    4895 4108 4109 4094 4093; 4896 4109 4110 4095 4094; 4897 4110 4111 4096 4095;
    4898 4111 3665 3666 4096; 4899 3940 4112 4097 3939; 4900 4112 4113 4098 4097;
    4901 4113 4114 4099 4098; 4902 4114 4115 4100 4099; 4903 4115 4116 4101 4100;
    4904 4116 4117 4102 4101; 4905 4117 4118 4103 4102; 4906 4118 4119 4104 4103;
    4907 4119 4120 4105 4104; 4908 4120 4121 4106 4105; 4909 4121 4122 4107 4106;
    4910 4122 4123 4108 4107; 4911 4123 4124 4109 4108; 4912 4124 4125 4110 4109;
    4913 4125 4126 4111 4110; 4914 4126 3664 3665 4111; 4915 3941 4127 4112 3940;
    4916 4127 4128 4113 4112; 4917 4128 4129 4114 4113; 4918 4129 4130 4115 4114;
    4919 4130 4131 4116 4115; 4920 4131 4132 4117 4116; 4921 4132 4133 4118 4117;
    4922 4133 4134 4119 4118; 4923 4134 4135 4120 4119; 4924 4135 4136 4121 4120;
    4925 4136 4137 4122 4121; 4926 4137 4138 4123 4122; 4927 4138 4139 4124 4123;
    4928 4139 4140 4125 4124; 4929 4140 4141 4126 4125; 4930 4141 3663 3664 4126;
    4931 3942 4142 4127 3941; 4932 4142 4143 4128 4127; 4933 4143 4144 4129 4128;
    4934 4144 4145 4130 4129; 4935 4145 4146 4131 4130; 4936 4146 4147 4132 4131;
    4937 4147 4148 4133 4132; 4938 4148 4149 4134 4133; 4939 4149 4150 4135 4134;
    4940 4150 4151 4136 4135; 4941 4151 4152 4137 4136; 4942 4152 4153 4138 4137;
    4943 4153 4154 4139 4138; 4944 4154 4155 4140 4139; 4945 4155 4156 4141 4140;
    4946 4156 3662 3663 4141; 4947 3943 4157 4142 3942; 4948 4157 4158 4143 4142;
    4949 4158 4159 4144 4143; 4950 4159 4160 4145 4144; 4951 4160 4161 4146 4145;
    4952 4161 4162 4147 4146; 4953 4162 4163 4148 4147; 4954 4163 4164 4149 4148;
    4955 4164 4165 4150 4149; 4956 4165 4166 4151 4150; 4957 4166 4167 4152 4151;
    4958 4167 4168 4153 4152; 4959 4168 4169 4154 4153; 4960 4169 4170 4155 4154;
    4961 4170 4171 4156 4155; 4962 4171 3661 3662 4156; 4963 3944 4172 4157 3943;
    4964 4172 4173 4158 4157; 4965 4173 4174 4159 4158; 4966 4174 4175 4160 4159;
    4967 4175 4176 4161 4160; 4968 4176 4177 4162 4161; 4969 4177 4178 4163 4162;
    4970 4178 4179 4164 4163; 4971 4179 4180 4165 4164; 4972 4180 4181 4166 4165;
    4973 4181 4182 4167 4166; 4974 4182 4183 4168 4167; 4975 4183 4184 4169 4168;
    4976 4184 4185 4170 4169; 4977 4185 4186 4171 4170; 4978 4186 3660 3661 4171;
    4979 3945 4187 4172 3944; 4980 4187 4188 4173 4172; 4981 4188 4189 4174 4173;
    4982 4189 4190 4175 4174; 4983 4190 4191 4176 4175; 4984 4191 4192 4177 4176;
    4985 4192 4193 4178 4177; 4986 4193 4194 4179 4178; 4987 4194 4195 4180 4179;
    4988 4195 4196 4181 4180; 4989 4196 4197 4182 4181; 4990 4197 4198 4183 4182;
    4991 4198 4199 4184 4183; 4992 4199 4200 4185 4184; 4993 4200 4201 4186 4185;
    4994 4201 3659 3660 4186; 4995 3946 4202 4187 3945; 4996 4202 4203 4188 4187;
    4997 4203 4204 4189 4188; 4998 4204 4205 4190 4189; 4999 4205 4206 4191 4190;
    5000 4206 4207 4192 4191; 5001 4207 4208 4193 4192; 5002 4208 4209 4194 4193;
    5003 4209 4210 4195 4194; 5004 4210 4211 4196 4195; 5005 4211 4212 4197 4196;
    5006 4212 4213 4198 4197; 5007 4213 4214 4199 4198; 5008 4214 4215 4200 4199;
    5009 4215 4216 4201 4200; 5010 4216 3658 3659 4201; 5011 384 3947 4202 3946;
    5012 3947 3948 4203 4202; 5013 3948 3949 4204 4203; 5014 3949 3950 4205 4204;
    5015 3950 3951 4206 4205; 5016 3951 3952 4207 4206; 5017 3952 3953 4208 4207;
    5018 3953 3954 4209 4208; 5019 3954 3955 4210 4209; 5020 3955 3956 4211 4210;
    5021 3956 3957 4212 4211; 5022 3957 3958 4213 4212; 5023 3958 3959 4214 4213;
    5024 3959 3960 4215 4214; 5025 3960 3961 4216 4215; 5026 3961 378 3658 4216;
    5066 4555 4345 4485 4362; 5067 4516 4391 4426 4267; 5068 4349 4384 4476 4394;
    5069 4471 4469 4302 4339; 5070 4294 4251 4252 4278; 5071 4555 4474 4572 4345;
    5072 134 4279 4399 3251; 5073 4355 4365 4274 4393; 5074 4433 4442 4421 4284;
    5075 4547 4357 4353 4438; 5076 4375 4278 4252 4295; 5077 4345 4572 4527 4504;
    5078 4456 4250 4251 4294; 5079 4554 4441 4424 4529; 5080 4524 4548 4248 4437;
    5081 4458 4472 4517 4492; 5082 4304 4322 4321 4310; 5083 4494 4465 4462 4546;
    5084 4293 4590 3263 3262; 5085 4438 4353 4306 4384; 5086 4267 4426 4553 4445;
    5087 4420 4506 4413 4587; 5088 4358 4366 4551 4368; 5089 4407 4369 4262 4446;
    5090 4531 4458 4492 4487; 5091 4295 4252 4253 4551; 5092 4460 4570 4583 4571;
    5093 4430 4582 4417 4436; 5094 4533 4300 4411 4560; 5095 4393 4416 4425 4388;
    5096 4411 4576 4256 4557; 5097 4256 4518 4595 4465; 5098 4346 4359 4535 4466;
    5099 4493 4337 4343 4459; 5100 4219 4220 4265 4261; 5101 4311 4249 4250 4456;
    5102 4383 4234 4235 4303; 5103 4341 4400 4463 4389; 5104 4374 4236 4237 4305;
    5105 4497 4451 4344 4488; 5106 4441 4294 4278 4424; 5107 4347 4577 4419 4364;
    5108 4452 4346 4466 4301; 5109 4434 4409 4335 4558; 5110 4324 4285 4502 4337;
    5111 4229 4230 4314 4299; 5112 4273 4545 4591 4589; 5113 4329 4486 4523 4280;
    5114 4491 4452 4301 4477; 5115 4594 4423 4534 4578; 5116 4448 4543 4582 4430;
    5117 4264 4327 3255 3254; 5118 4292 4291 4496 4474; 5119 4493 4459 4398 4530;
    5120 4386 4491 4477 4457; 5121 4529 4424 4556 4357; 5122 4332 4526 4594 4578;
    5123 4450 4323 4464 4291; 5124 4589 4591 4283 4461; 5125 4597 4308 4440 4521;
    5126 4221 4222 4271 4263; 5127 4479 4433 4284 4351; 5128 4345 4504 4584 4485;
    5129 4230 291 4270 4314; 5130 291 373 4290 4270; 5131 4429 4540 4452 4491;
    5132 4330 4595 4542 4490; 5133 4530 4398 4597 4564; 5134 4217 4503 4279 134;
    5135 4356 4495 4379 4390; 5136 4305 4237 4238 4373; 5137 4226 4227 4420 4320;
    5138 4429 4406 4319 4540; 5139 4587 4413 4495 4297; 5140 4592 4563 4453 4272;
    5141 4540 4319 4346 4452; 5142 4509 4244 4245 4354; 5143 4222 4223 4363 4271;
    5144 4324 4337 4493 4470; 5145 4384 4306 4458 4531; 5146 4506 4268 4289 4413;
    5147 4320 4420 4587 4378; 5148 4549 4372 4276 4576; 5149 4453 4563 4449 4519;
    5150 4466 4535 4258 4510; 5151 4220 4221 4263 4265; 5152 4568 4364 4479 4422;
    5153 4523 4447 4538 4498; 5154 4412 4350 4567 4515; 5155 4303 4235 4236 4374;
    5156 4301 4466 4510 4260; 5157 4315 4468 4532 4400; 5158 4426 4287 4566 4553;
    5159 4228 4229 4299 4506; 5160 4581 4418 4369 4407; 5161 4325 4338 4318 4402;
    5162 4342 4281 4543 4448; 5163 4510 4258 4475 4444; 5164 4351 4284 3258 3257;
    5165 4318 4508 4516 4395; 5166 4343 4467 4273 4459; 5167 4437 4248 4249 4311;
    5168 4539 4311 4456 4536; 5169 4298 4434 4558 4431; 5170 4584 4526 4332 4513;
    5171 4257 4553 4298 4431; 5172 4279 4500 4327 4399; 5173 4476 4384 4531 4336;
    5174 4372 4512 4520 4276; 5175 4505 4326 4511 4515; 5176 4596 4302 4383 4512;
    5177 4333 4393 4388 4321; 5178 4534 4381 4311 4539; 5179 4263 4271 4415 4334;
    5180 4399 4327 4264 4266; 5181 4499 4267 4445 4376; 5182 4498 4538 4292 4277;
    5183 4576 4580 4518 4256; 5184 4265 4263 4334 4328; 5185 4566 4554 4529 4544;
    5186 4357 4556 4358 4353; 5187 4287 4552 4554 4566; 5188 4271 4363 4489 4415;
    5189 4562 4365 4355 4481; 5190 4545 4431 4541 4591; 5191 4501 4254 4255 4262;
    5192 4328 4334 4415 4410; 5193 4261 4265 4328 4329; 5194 4522 4530 4564 4480;
    5195 4300 4549 4576 4411; 5196 4473 4356 4390 4414; 5197 4338 4513 4508 4318;
    5198 4597 4589 4461 4308; 5199 4344 4242 4243 4275; 5200 4565 4340 4331 4454;
    5201 4423 4524 4381 4534; 5202 4328 4410 4486 4329; 5203 4364 4419 4433 4479;
    5204 4313 4507 4478 4326; 5205 4313 4473 4414 4507; 5206 4563 4460 4571 4449;
    5207 4268 4309 4397 4289; 5208 4409 4438 4384 4349; 5209 4538 4573 4385 4292;
    5210 4336 4531 4487 4537; 5211 4413 4269 4296 4495; 5212 4546 4462 4323 4450;
    5213 4310 4315 4400 4341; 5214 4442 4522 4480 4421; 5215 4484 4565 4454 4514;
    5216 4512 4383 4303 4520; 5217 4390 4379 4304 4317; 5218 4316 4429 4491 4386;
    5219 4488 4344 4275 4496; 5220 4445 4553 4257 4396; 5221 4402 4318 4395 4285;
    5222 4541 4342 4448 4435; 5223 4424 4278 4375 4556; 5224 4467 4396 4545 4273;
    5225 4291 4464 4488 4496; 5226 4595 4239 4240 4542; 5227 4459 4273 4589 4398;
    5228 4385 4450 4291 4292; 5229 4281 4476 4336 4404; 5230 4465 4595 4330 4462;
    5231 4376 4445 4396 4467; 5232 4306 4368 4472 4458; 5233 4514 4347 4364 4568;
    5234 4285 4395 4499 4502; 5235 4558 4335 4394 4342; 5236 4361 4501 4262 4369;
    5237 4557 4256 4465 4494; 5238 4270 4290 4588 4406; 5239 4421 4521 3260 3259;
    5240 4436 4432 4585 4569; 5241 4275 4243 4244 4509; 5242 4434 4547 4438 4409;
    5243 4435 4448 4430 4575; 5244 4556 4375 4366 4358; 5245 4564 4597 4521 4480;
    5246 4298 4544 4547 4434; 5247 4227 4228 4506 4420; 5248 4284 4421 3259 3258;
    5249 4359 4593 4528 4535; 5250 4317 4341 4389 4483; 5251 4422 4351 3257 3256;
    5252 4508 4586 4391 4516; 5253 4288 4546 4450 4385; 5254 4277 4555 4362 4380;
    5255 4387 4374 4305 4580; 5256 4474 4496 4354 4572; 5257 4496 4275 4509 4354;
    5258 4551 4253 4254 4501; 5259 4323 4497 4488 4464; 5260 4352 4361 4369 4418;
    5261 4500 4568 4422 4327; 5262 4373 4238 4239 4595; 5263 4570 4510 4444 4583;
    5264 4591 4541 4435 4283; 5265 4586 4539 4536 4391; 5266 4410 4415 4412 4486;
    5267 4331 4402 4285 4324; 5268 4503 4484 4500 4279; 5269 4580 4305 4373 4518;
    5270 4414 4390 4317 4483; 5271 4370 4260 4510 4570; 5272 4447 4371 4573 4538;
    5273 4519 4559 4561 4427; 5274 4330 4490 4497 4323; 5275 4553 4566 4544 4298;
    5276 4578 4534 4539 4586; 5277 4490 4542 4451 4497; 5278 4368 4551 4501 4472;
    5279 4286 4288 4385 4573; 5280 4444 4475 4596 4408; 5281 4367 4411 4557 4532;
    5282 4577 4530 4522 4419; 5283 4419 4522 4442 4433; 5284 4475 4339 4302 4596;
    5285 4391 4536 4456 4552; 5286 4485 4584 4513 4338; 5287 4521 4440 3261 3260;
    5288 4297 4495 4356 4473; 5289 4426 4391 4552 4287; 5290 4468 4425 4367 4532;
    5291 4502 4499 4376 4337; 5292 4454 4331 4324 4470; 5293 4314 4316 4386 4309;
    5294 4528 4439 4469 4471; 5295 4224 4225 4378 4363; 5296 4525 4313 4326 4505;
    5297 4415 4489 4350 4412; 5298 4432 4407 270 4585; 5299 4454 4470 4577 4347;
    5300 4258 4471 4339 4475; 5301 4524 4437 4311 4381; 5302 4470 4493 4530 4577;
    5303 4503 4405 4565 4484; 5304 4283 4435 4579 4461; 5305 4487 4492 4352 4377;
    5306 4397 4457 4307 4550; 5307 4308 4461 4293 4440; 5308 4363 4378 4587 4489;
    5309 4337 4376 4467 4343; 5310 4389 4463 4312 4282; 5311 4354 4245 4246 4428;
    5312 4396 4257 4431 4545; 5313 4262 4255 372 4446; 5314 4484 4514 4568 4500;
    5315 4504 4527 4526 4584; 5316 4319 4593 4359 4346; 5317 4526 4259 4360 4594;
    5318 4561 4482 4533 4455; 5319 4455 4533 4560 4416; 5320 4379 4348 4322 4304;
    5321 4486 4412 4515 4523; 5322 4380 4362 4325 4340; 5323 4371 4282 4286 4573;
    5324 4400 4532 4392 4463; 5325 4562 4453 4519 4365; 5326 4321 4388 4315 4310;
    5327 4583 4444 4408 4574; 5328 4388 4425 4468 4315; 5329 4407 4446 372 270;
    5330 4535 4528 4471 4258; 5331 4394 4476 4281 4342; 5332 4463 4392 4494 4546;
    5333 4590 4585 270 3263; 5334 4489 4587 4297 4350; 5335 4408 4596 4372 4549;
    5336 4277 4292 4474 4555; 5337 4457 4260 4370 4307; 5338 4395 4516 4267 4499;
    5339 4266 4264 3253 3252; 5340 4290 373 4231 4588; 5341 4340 4325 4402 4331;
    5342 4588 4231 4232 4439; 5343 4481 4355 4393 4333; 5344 4593 4588 4439 4528;
    5345 4431 4558 4342 4541; 5346 4281 4404 4403 4543; 5347 4544 4529 4357 4547;
    5348 4498 4277 4380 4405; 5349 4299 4314 4309 4268; 5350 4582 4403 4401 4417;
    5351 4507 4414 4483 4478; 5352 4296 4269 4562 4481; 5353 4375 4295 4551 4366;
    5354 4525 4297 4473 4313; 5355 4417 4401 4581 4432; 5356 4572 4354 4428 4527;
    5357 4296 4481 4322 4348; 5358 4397 4550 4563 4592; 5359 4350 4297 4525 4567;
    5360 4478 4483 4371 4447; 5361 4451 4241 4242 4344; 5362 4495 4296 4348 4379;
    5363 3251 4399 4266 3252; 5364 4428 4246 4247 4443; 5365 4427 4561 4455 4274;
    5366 4217 4498 4405 4503; 5367 4440 4293 3262 3261; 5368 169 4218 4329 4280;
    5369 4322 4481 4333 4321; 5370 4483 4389 4282 4371; 5371 4405 4380 4340 4565;
    5372 4552 4456 4441 4554; 5373 4362 4485 4338 4325; 5374 4550 4307 4460 4563;
    5375 4567 4525 4505 4515; 5376 4309 4386 4457 4397; 5377 4259 4443 4548 4360;
    5378 4393 4274 4455 4416; 5379 4559 4574 4482 4561; 5380 4532 4557 4494 4392;
    5381 4511 4326 4478 4447; 5382 4439 4232 4233 4469; 5383 4404 4336 4537 4403;
    5384 4517 4472 4501 4361; 5385 4515 4511 4447 4523; 5386 4327 4422 3256 3255;
    5387 4276 4520 4374 4387; 5388 4353 4358 4368 4306; 5389 4492 4517 4361 4352;
    5390 4574 4408 4549 4482; 5391 4449 4571 4559 4519; 5392 4579 4569 4585 4590;
    5393 4365 4519 4427 4274; 5394 4482 4549 4300 4533; 5395 4425 4416 4560 4367;
    5396 4218 4219 4261 4329; 5397 4269 4272 4453 4562; 5398 4360 4548 4524 4423;
    5399 4435 4575 4569 4579; 5400 4469 4233 4234 4302; 5401 4335 4409 4349 4394;
    5402 4270 4406 4429 4316; 5403 4527 4428 4259 4526; 5404 4537 4487 4377 4382;
    5405 4307 4370 4570 4460; 5406 4403 4537 4382 4401; 5407 4542 4240 4241 4451;
    5408 4225 4226 4320 4378; 5409 4282 4312 4288 4286; 5410 4276 4387 4580 4576;
    5411 4571 4583 4574 4559; 5412 4575 4430 4436 4569; 5413 4443 4247 4248 4548;
    5414 4312 4463 4546 4288; 5415 4304 4310 4341 4317; 5416 4280 4523 4498 4217;
    5417 4332 4578 4586 4508; 5418 4289 4592 4272 4269; 5419 4382 4377 4352 4418;
    5420 4477 4301 4260 4457; 5421 4406 4588 4593 4319; 5422 4401 4382 4418 4581;
    5423 4461 4579 4590 4293; 5424 4518 4373 4595; 5425 4436 4417 4432;
    5426 4456 4294 4441; 5427 3253 4264 3254; 5428 4314 4270 4316;
    5429 4543 4403 4582; 5430 4398 4589 4597; 5431 4513 4332 4508;
    5432 4506 4299 4268; 5433 4432 4581 4407; 5434 4480 4521 4421;
    5435 4462 4330 4323; 5436 4367 4560 4411; 5437 4514 4454 4347;
    5438 4413 4289 4269; 5439 4594 4360 4423; 5440 4428 4443 4259;
    5441 4289 4397 4592; 5442 4422 4479 4351; 5443 169 4280 4217;
    5444 4372 4596 4512; 5445 4520 4303 4374; 5446 4223 4224 4363;
    5447 4302 4234 4383; 5488 4255 4638 3643 372; 5489 4638 4639 3644 3643;
    5490 4639 4640 3645 3644; 5491 4640 4641 3646 3645; 5492 4641 4642 3647 3646;
    5493 4642 4643 3648 3647; 5494 4643 4644 3649 3648; 5495 4644 4645 3650 3649;
    5496 4645 4646 3651 3650; 5497 4646 4647 3652 3651; 5498 4647 4648 3653 3652;
    5499 4648 4649 3654 3653; 5500 4649 4650 3655 3654; 5501 4650 4651 3656 3655;
    5502 4651 4652 3657 3656; 5503 4652 4637 378 3657; 5504 4254 4653 4638 4255;
    5505 4653 4654 4639 4638; 5506 4654 4655 4640 4639; 5507 4655 4656 4641 4640;
    5508 4656 4657 4642 4641; 5509 4657 4658 4643 4642; 5510 4658 4659 4644 4643;
    5511 4659 4660 4645 4644; 5512 4660 4661 4646 4645; 5513 4661 4662 4647 4646;
    5514 4662 4663 4648 4647; 5515 4663 4664 4649 4648; 5516 4664 4665 4650 4649;
    5517 4665 4666 4651 4650; 5518 4666 4667 4652 4651; 5519 4667 4636 4637 4652;
    5520 4253 4668 4653 4254; 5521 4668 4669 4654 4653; 5522 4669 4670 4655 4654;
    5523 4670 4671 4656 4655; 5524 4671 4672 4657 4656; 5525 4672 4673 4658 4657;
    5526 4673 4674 4659 4658; 5527 4674 4675 4660 4659; 5528 4675 4676 4661 4660;
    5529 4676 4677 4662 4661; 5530 4677 4678 4663 4662; 5531 4678 4679 4664 4663;
    5532 4679 4680 4665 4664; 5533 4680 4681 4666 4665; 5534 4681 4682 4667 4666;
    5535 4682 4635 4636 4667; 5536 4252 4683 4668 4253; 5537 4683 4684 4669 4668;
    5538 4684 4685 4670 4669; 5539 4685 4686 4671 4670; 5540 4686 4687 4672 4671;
    5541 4687 4688 4673 4672; 5542 4688 4689 4674 4673; 5543 4689 4690 4675 4674;
    5544 4690 4691 4676 4675; 5545 4691 4692 4677 4676; 5546 4692 4693 4678 4677;
    5547 4693 4694 4679 4678; 5548 4694 4695 4680 4679; 5549 4695 4696 4681 4680;
    5550 4696 4697 4682 4681; 5551 4697 4634 4635 4682; 5552 4251 4698 4683 4252;
    5553 4698 4699 4684 4683; 5554 4699 4700 4685 4684; 5555 4700 4701 4686 4685;
    5556 4701 4702 4687 4686; 5557 4702 4703 4688 4687; 5558 4703 4704 4689 4688;
    5559 4704 4705 4690 4689; 5560 4705 4706 4691 4690; 5561 4706 4707 4692 4691;
    5562 4707 4708 4693 4692; 5563 4708 4709 4694 4693; 5564 4709 4710 4695 4694;
    5565 4710 4711 4696 4695; 5566 4711 4712 4697 4696; 5567 4712 4633 4634 4697;
    5568 4250 4713 4698 4251; 5569 4713 4714 4699 4698; 5570 4714 4715 4700 4699;
    5571 4715 4716 4701 4700; 5572 4716 4717 4702 4701; 5573 4717 4718 4703 4702;
    5574 4718 4719 4704 4703; 5575 4719 4720 4705 4704; 5576 4720 4721 4706 4705;
    5577 4721 4722 4707 4706; 5578 4722 4723 4708 4707; 5579 4723 4724 4709 4708;
    5580 4724 4725 4710 4709; 5581 4725 4726 4711 4710; 5582 4726 4727 4712 4711;
    5583 4727 4632 4633 4712; 5584 4249 4728 4713 4250; 5585 4728 4729 4714 4713;
    5586 4729 4730 4715 4714; 5587 4730 4731 4716 4715; 5588 4731 4732 4717 4716;
    5589 4732 4733 4718 4717; 5590 4733 4734 4719 4718; 5591 4734 4735 4720 4719;
    5592 4735 4736 4721 4720; 5593 4736 4737 4722 4721; 5594 4737 4738 4723 4722;
    5595 4738 4739 4724 4723; 5596 4739 4740 4725 4724; 5597 4740 4741 4726 4725;
    5598 4741 4742 4727 4726; 5599 4742 4631 4632 4727; 5600 4248 4743 4728 4249;
    5601 4743 4744 4729 4728; 5602 4744 4745 4730 4729; 5603 4745 4746 4731 4730;
    5604 4746 4747 4732 4731; 5605 4747 4748 4733 4732; 5606 4748 4749 4734 4733;
    5607 4749 4750 4735 4734; 5608 4750 4751 4736 4735; 5609 4751 4752 4737 4736;
    5610 4752 4753 4738 4737; 5611 4753 4754 4739 4738; 5612 4754 4755 4740 4739;
    5613 4755 4756 4741 4740; 5614 4756 4757 4742 4741; 5615 4757 4630 4631 4742;
    5616 4247 4758 4743 4248; 5617 4758 4759 4744 4743; 5618 4759 4760 4745 4744;
    5619 4760 4761 4746 4745; 5620 4761 4762 4747 4746; 5621 4762 4763 4748 4747;
    5622 4763 4764 4749 4748; 5623 4764 4765 4750 4749; 5624 4765 4766 4751 4750;
    5625 4766 4767 4752 4751; 5626 4767 4768 4753 4752; 5627 4768 4769 4754 4753;
    5628 4769 4770 4755 4754; 5629 4770 4771 4756 4755; 5630 4771 4772 4757 4756;
    5631 4772 4629 4630 4757; 5632 4246 4773 4758 4247; 5633 4773 4774 4759 4758;
    5634 4774 4775 4760 4759; 5635 4775 4776 4761 4760; 5636 4776 4777 4762 4761;
    5637 4777 4778 4763 4762; 5638 4778 4779 4764 4763; 5639 4779 4780 4765 4764;
    5640 4780 4781 4766 4765; 5641 4781 4782 4767 4766; 5642 4782 4783 4768 4767;
    5643 4783 4784 4769 4768; 5644 4784 4785 4770 4769; 5645 4785 4786 4771 4770;
    5646 4786 4787 4772 4771; 5647 4787 4628 4629 4772; 5648 4245 4788 4773 4246;
    5649 4788 4789 4774 4773; 5650 4789 4790 4775 4774; 5651 4790 4791 4776 4775;
    5652 4791 4792 4777 4776; 5653 4792 4793 4778 4777; 5654 4793 4794 4779 4778;
    5655 4794 4795 4780 4779; 5656 4795 4796 4781 4780; 5657 4796 4797 4782 4781;
    5658 4797 4798 4783 4782; 5659 4798 4799 4784 4783; 5660 4799 4800 4785 4784;
    5661 4800 4801 4786 4785; 5662 4801 4802 4787 4786; 5663 4802 4627 4628 4787;
    5664 4244 4803 4788 4245; 5665 4803 4804 4789 4788; 5666 4804 4805 4790 4789;
    5667 4805 4806 4791 4790; 5668 4806 4807 4792 4791; 5669 4807 4808 4793 4792;
    5670 4808 4809 4794 4793; 5671 4809 4810 4795 4794; 5672 4810 4811 4796 4795;
    5673 4811 4812 4797 4796; 5674 4812 4813 4798 4797; 5675 4813 4814 4799 4798;
    5676 4814 4815 4800 4799; 5677 4815 4816 4801 4800; 5678 4816 4817 4802 4801;
    5679 4817 4626 4627 4802; 5680 4243 4818 4803 4244; 5681 4818 4819 4804 4803;
    5682 4819 4820 4805 4804; 5683 4820 4821 4806 4805; 5684 4821 4822 4807 4806;
    5685 4822 4823 4808 4807; 5686 4823 4824 4809 4808; 5687 4824 4825 4810 4809;
    5688 4825 4826 4811 4810; 5689 4826 4827 4812 4811; 5690 4827 4828 4813 4812;
    5691 4828 4829 4814 4813; 5692 4829 4830 4815 4814; 5693 4830 4831 4816 4815;
    5694 4831 4832 4817 4816; 5695 4832 4625 4626 4817; 5696 4242 4833 4818 4243;
    5697 4833 4834 4819 4818; 5698 4834 4835 4820 4819; 5699 4835 4836 4821 4820;
    5700 4836 4837 4822 4821; 5701 4837 4838 4823 4822; 5702 4838 4839 4824 4823;
    5703 4839 4840 4825 4824; 5704 4840 4841 4826 4825; 5705 4841 4842 4827 4826;
    5706 4842 4843 4828 4827; 5707 4843 4844 4829 4828; 5708 4844 4845 4830 4829;
    5709 4845 4846 4831 4830; 5710 4846 4847 4832 4831; 5711 4847 4624 4625 4832;
    5712 4241 4848 4833 4242; 5713 4848 4849 4834 4833; 5714 4849 4850 4835 4834;
    5715 4850 4851 4836 4835; 5716 4851 4852 4837 4836; 5717 4852 4853 4838 4837;
    5718 4853 4854 4839 4838; 5719 4854 4855 4840 4839; 5720 4855 4856 4841 4840;
    5721 4856 4857 4842 4841; 5722 4857 4858 4843 4842; 5723 4858 4859 4844 4843;
    5724 4859 4860 4845 4844; 5725 4860 4861 4846 4845; 5726 4861 4862 4847 4846;
    5727 4862 4623 4624 4847; 5728 4240 4863 4848 4241; 5729 4863 4864 4849 4848;
    5730 4864 4865 4850 4849; 5731 4865 4866 4851 4850; 5732 4866 4867 4852 4851;
    5733 4867 4868 4853 4852; 5734 4868 4869 4854 4853; 5735 4869 4870 4855 4854;
    5736 4870 4871 4856 4855; 5737 4871 4872 4857 4856; 5738 4872 4873 4858 4857;
    5739 4873 4874 4859 4858; 5740 4874 4875 4860 4859; 5741 4875 4876 4861 4860;
    5742 4876 4877 4862 4861; 5743 4877 4622 4623 4862; 5744 4239 4878 4863 4240;
    5745 4878 4879 4864 4863; 5746 4879 4880 4865 4864; 5747 4880 4881 4866 4865;
    5748 4881 4882 4867 4866; 5749 4882 4883 4868 4867; 5750 4883 4884 4869 4868;
    5751 4884 4885 4870 4869; 5752 4885 4886 4871 4870; 5753 4886 4887 4872 4871;
    5754 4887 4888 4873 4872; 5755 4888 4889 4874 4873; 5756 4889 4890 4875 4874;
    5757 4890 4891 4876 4875; 5758 4891 4892 4877 4876; 5759 4892 4621 4622 4877;
    5760 4238 4893 4878 4239; 5761 4893 4894 4879 4878; 5762 4894 4895 4880 4879;
    5763 4895 4896 4881 4880; 5764 4896 4897 4882 4881; 5765 4897 4898 4883 4882;
    5766 4898 4899 4884 4883; 5767 4899 4900 4885 4884; 5768 4900 4901 4886 4885;
    5769 4901 4902 4887 4886; 5770 4902 4903 4888 4887; 5771 4903 4904 4889 4888;
    5772 4904 4905 4890 4889; 5773 4905 4906 4891 4890; 5774 4906 4907 4892 4891;
    5775 4907 4620 4621 4892; 5776 4237 4908 4893 4238; 5777 4908 4909 4894 4893;
    5778 4909 4910 4895 4894; 5779 4910 4911 4896 4895; 5780 4911 4912 4897 4896;
    5781 4912 4913 4898 4897; 5782 4913 4914 4899 4898; 5783 4914 4915 4900 4899;
    5784 4915 4916 4901 4900; 5785 4916 4917 4902 4901; 5786 4917 4918 4903 4902;
    5787 4918 4919 4904 4903; 5788 4919 4920 4905 4904; 5789 4920 4921 4906 4905;
    5790 4921 4922 4907 4906; 5791 4922 4619 4620 4907; 5792 4236 4923 4908 4237;
    5793 4923 4924 4909 4908; 5794 4924 4925 4910 4909; 5795 4925 4926 4911 4910;
    5796 4926 4927 4912 4911; 5797 4927 4928 4913 4912; 5798 4928 4929 4914 4913;
    5799 4929 4930 4915 4914; 5800 4930 4931 4916 4915; 5801 4931 4932 4917 4916;
    5802 4932 4933 4918 4917; 5803 4933 4934 4919 4918; 5804 4934 4935 4920 4919;
    5805 4935 4936 4921 4920; 5806 4936 4937 4922 4921; 5807 4937 4618 4619 4922;
    5808 4235 4938 4923 4236; 5809 4938 4939 4924 4923; 5810 4939 4940 4925 4924;
    5811 4940 4941 4926 4925; 5812 4941 4942 4927 4926; 5813 4942 4943 4928 4927;
    5814 4943 4944 4929 4928; 5815 4944 4945 4930 4929; 5816 4945 4946 4931 4930;
    5817 4946 4947 4932 4931; 5818 4947 4948 4933 4932; 5819 4948 4949 4934 4933;
    5820 4949 4950 4935 4934; 5821 4950 4951 4936 4935; 5822 4951 4952 4937 4936;
    5823 4952 4617 4618 4937; 5824 4234 4953 4938 4235; 5825 4953 4954 4939 4938;
    5826 4954 4955 4940 4939; 5827 4955 4956 4941 4940; 5828 4956 4957 4942 4941;
    5829 4957 4958 4943 4942; 5830 4958 4959 4944 4943; 5831 4959 4960 4945 4944;
    5832 4960 4961 4946 4945; 5833 4961 4962 4947 4946; 5834 4962 4963 4948 4947;
    5835 4963 4964 4949 4948; 5836 4964 4965 4950 4949; 5837 4965 4966 4951 4950;
    5838 4966 4967 4952 4951; 5839 4967 4616 4617 4952; 5840 4233 4968 4953 4234;
    5841 4968 4969 4954 4953; 5842 4969 4970 4955 4954; 5843 4970 4971 4956 4955;
    5844 4971 4972 4957 4956; 5845 4972 4973 4958 4957; 5846 4973 4974 4959 4958;
    5847 4974 4975 4960 4959; 5848 4975 4976 4961 4960; 5849 4976 4977 4962 4961;
    5850 4977 4978 4963 4962; 5851 4978 4979 4964 4963; 5852 4979 4980 4965 4964;
    5853 4980 4981 4966 4965; 5854 4981 4982 4967 4966; 5855 4982 4615 4616 4967;
    5856 4232 4983 4968 4233; 5857 4983 4984 4969 4968; 5858 4984 4985 4970 4969;
    5859 4985 4986 4971 4970; 5860 4986 4987 4972 4971; 5861 4987 4988 4973 4972;
    5862 4988 4989 4974 4973; 5863 4989 4990 4975 4974; 5864 4990 4991 4976 4975;
    5865 4991 4992 4977 4976; 5866 4992 4993 4978 4977; 5867 4993 4994 4979 4978;
    5868 4994 4995 4980 4979; 5869 4995 4996 4981 4980; 5870 4996 4997 4982 4981;
    5871 4997 4614 4615 4982; 5872 4231 4998 4983 4232; 5873 4998 4999 4984 4983;
    5874 4999 5000 4985 4984; 5875 5000 5001 4986 4985; 5876 5001 5002 4987 4986;
    5877 5002 5003 4988 4987; 5878 5003 5004 4989 4988; 5879 5004 5005 4990 4989;
    5880 5005 5006 4991 4990; 5881 5006 5007 4992 4991; 5882 5007 5008 4993 4992;
    5883 5008 5009 4994 4993; 5884 5009 5010 4995 4994; 5885 5010 5011 4996 4995;
    5886 5011 5012 4997 4996; 5887 5012 4613 4614 4997; 5888 373 4598 4998 4231;
    5889 4598 4599 4999 4998; 5890 4599 4600 5000 4999; 5891 4600 4601 5001 5000;
    5892 4601 4602 5002 5001; 5893 4602 4603 5003 5002; 5894 4603 4604 5004 5003;
    5895 4604 4605 5005 5004; 5896 4605 4606 5006 5005; 5897 4606 4607 5007 5006;
    5898 4607 4608 5008 5007; 5899 4608 4609 5009 5008; 5900 4609 4610 5010 5009;
    5901 4610 4611 5011 5010; 5902 4611 4612 5012 5011; 5903 4612 379 4613 5012;
    5944 5013 5053 3947 384; 5945 5053 5054 3948 3947; 5946 5054 5055 3949 3948;
    5947 5055 5056 3950 3949; 5948 5056 5057 3951 3950; 5949 5057 5058 3952 3951;
    5950 5058 5059 3953 3952; 5951 5059 5060 3954 3953; 5952 5060 5061 3955 3954;
    5953 5061 5062 3956 3955; 5954 5062 5063 3957 3956; 5955 5063 5064 3958 3957;
    5956 5064 5065 3959 3958; 5957 5065 5066 3960 3959; 5958 5066 5067 3961 3960;
    5959 5067 4637 378 3961; 5960 5014 5068 5053 5013; 5961 5068 5069 5054 5053;
    5962 5069 5070 5055 5054; 5963 5070 5071 5056 5055; 5964 5071 5072 5057 5056;
    5965 5072 5073 5058 5057; 5966 5073 5074 5059 5058; 5967 5074 5075 5060 5059;
    5968 5075 5076 5061 5060; 5969 5076 5077 5062 5061; 5970 5077 5078 5063 5062;
    5971 5078 5079 5064 5063; 5972 5079 5080 5065 5064; 5973 5080 5081 5066 5065;
    5974 5081 5082 5067 5066; 5975 5082 4636 4637 5067; 5976 5015 5083 5068 5014;
    5977 5083 5084 5069 5068; 5978 5084 5085 5070 5069; 5979 5085 5086 5071 5070;
    5980 5086 5087 5072 5071; 5981 5087 5088 5073 5072; 5982 5088 5089 5074 5073;
    5983 5089 5090 5075 5074; 5984 5090 5091 5076 5075; 5985 5091 5092 5077 5076;
    5986 5092 5093 5078 5077; 5987 5093 5094 5079 5078; 5988 5094 5095 5080 5079;
    5989 5095 5096 5081 5080; 5990 5096 5097 5082 5081; 5991 5097 4635 4636 5082;
    5992 5016 5098 5083 5015; 5993 5098 5099 5084 5083; 5994 5099 5100 5085 5084;
    5995 5100 5101 5086 5085; 5996 5101 5102 5087 5086; 5997 5102 5103 5088 5087;
    5998 5103 5104 5089 5088; 5999 5104 5105 5090 5089; 6000 5105 5106 5091 5090;
    6001 5106 5107 5092 5091; 6002 5107 5108 5093 5092; 6003 5108 5109 5094 5093;
    6004 5109 5110 5095 5094; 6005 5110 5111 5096 5095; 6006 5111 5112 5097 5096;
    6007 5112 4634 4635 5097; 6008 5017 5113 5098 5016; 6009 5113 5114 5099 5098;
    6010 5114 5115 5100 5099; 6011 5115 5116 5101 5100; 6012 5116 5117 5102 5101;
    6013 5117 5118 5103 5102; 6014 5118 5119 5104 5103; 6015 5119 5120 5105 5104;
    6016 5120 5121 5106 5105; 6017 5121 5122 5107 5106; 6018 5122 5123 5108 5107;
    6019 5123 5124 5109 5108; 6020 5124 5125 5110 5109; 6021 5125 5126 5111 5110;
    6022 5126 5127 5112 5111; 6023 5127 4633 4634 5112; 6024 5018 5128 5113 5017;
    6025 5128 5129 5114 5113; 6026 5129 5130 5115 5114; 6027 5130 5131 5116 5115;
    6028 5131 5132 5117 5116; 6029 5132 5133 5118 5117; 6030 5133 5134 5119 5118;
    6031 5134 5135 5120 5119; 6032 5135 5136 5121 5120; 6033 5136 5137 5122 5121;
    6034 5137 5138 5123 5122; 6035 5138 5139 5124 5123; 6036 5139 5140 5125 5124;
    6037 5140 5141 5126 5125; 6038 5141 5142 5127 5126; 6039 5142 4632 4633 5127;
    6040 5019 5143 5128 5018; 6041 5143 5144 5129 5128; 6042 5144 5145 5130 5129;
    6043 5145 5146 5131 5130; 6044 5146 5147 5132 5131; 6045 5147 5148 5133 5132;
    6046 5148 5149 5134 5133; 6047 5149 5150 5135 5134; 6048 5150 5151 5136 5135;
    6049 5151 5152 5137 5136; 6050 5152 5153 5138 5137; 6051 5153 5154 5139 5138;
    6052 5154 5155 5140 5139; 6053 5155 5156 5141 5140; 6054 5156 5157 5142 5141;
    6055 5157 4631 4632 5142; 6056 5020 5158 5143 5019; 6057 5158 5159 5144 5143;
    6058 5159 5160 5145 5144; 6059 5160 5161 5146 5145; 6060 5161 5162 5147 5146;
    6061 5162 5163 5148 5147; 6062 5163 5164 5149 5148; 6063 5164 5165 5150 5149;
    6064 5165 5166 5151 5150; 6065 5166 5167 5152 5151; 6066 5167 5168 5153 5152;
    6067 5168 5169 5154 5153; 6068 5169 5170 5155 5154; 6069 5170 5171 5156 5155;
    6070 5171 5172 5157 5156; 6071 5172 4630 4631 5157; 6072 5021 5173 5158 5020;
    6073 5173 5174 5159 5158; 6074 5174 5175 5160 5159; 6075 5175 5176 5161 5160;
    6076 5176 5177 5162 5161; 6077 5177 5178 5163 5162; 6078 5178 5179 5164 5163;
    6079 5179 5180 5165 5164; 6080 5180 5181 5166 5165; 6081 5181 5182 5167 5166;
    6082 5182 5183 5168 5167; 6083 5183 5184 5169 5168; 6084 5184 5185 5170 5169;
    6085 5185 5186 5171 5170; 6086 5186 5187 5172 5171; 6087 5187 4629 4630 5172;
    6088 5022 5188 5173 5021; 6089 5188 5189 5174 5173; 6090 5189 5190 5175 5174;
    6091 5190 5191 5176 5175; 6092 5191 5192 5177 5176; 6093 5192 5193 5178 5177;
    6094 5193 5194 5179 5178; 6095 5194 5195 5180 5179; 6096 5195 5196 5181 5180;
    6097 5196 5197 5182 5181; 6098 5197 5198 5183 5182; 6099 5198 5199 5184 5183;
    6100 5199 5200 5185 5184; 6101 5200 5201 5186 5185; 6102 5201 5202 5187 5186;
    6103 5202 4628 4629 5187; 6104 5023 5203 5188 5022; 6105 5203 5204 5189 5188;
    6106 5204 5205 5190 5189; 6107 5205 5206 5191 5190; 6108 5206 5207 5192 5191;
    6109 5207 5208 5193 5192; 6110 5208 5209 5194 5193; 6111 5209 5210 5195 5194;
    6112 5210 5211 5196 5195; 6113 5211 5212 5197 5196; 6114 5212 5213 5198 5197;
    6115 5213 5214 5199 5198; 6116 5214 5215 5200 5199; 6117 5215 5216 5201 5200;
    6118 5216 5217 5202 5201; 6119 5217 4627 4628 5202; 6120 5024 5218 5203 5023;
    6121 5218 5219 5204 5203; 6122 5219 5220 5205 5204; 6123 5220 5221 5206 5205;
    6124 5221 5222 5207 5206; 6125 5222 5223 5208 5207; 6126 5223 5224 5209 5208;
    6127 5224 5225 5210 5209; 6128 5225 5226 5211 5210; 6129 5226 5227 5212 5211;
    6130 5227 5228 5213 5212; 6131 5228 5229 5214 5213; 6132 5229 5230 5215 5214;
    6133 5230 5231 5216 5215; 6134 5231 5232 5217 5216; 6135 5232 4626 4627 5217;
    6136 5025 5233 5218 5024; 6137 5233 5234 5219 5218; 6138 5234 5235 5220 5219;
    6139 5235 5236 5221 5220; 6140 5236 5237 5222 5221; 6141 5237 5238 5223 5222;
    6142 5238 5239 5224 5223; 6143 5239 5240 5225 5224; 6144 5240 5241 5226 5225;
    6145 5241 5242 5227 5226; 6146 5242 5243 5228 5227; 6147 5243 5244 5229 5228;
    6148 5244 5245 5230 5229; 6149 5245 5246 5231 5230; 6150 5246 5247 5232 5231;
    6151 5247 4625 4626 5232; 6152 5026 5248 5233 5025; 6153 5248 5249 5234 5233;
    6154 5249 5250 5235 5234; 6155 5250 5251 5236 5235; 6156 5251 5252 5237 5236;
    6157 5252 5253 5238 5237; 6158 5253 5254 5239 5238; 6159 5254 5255 5240 5239;
    6160 5255 5256 5241 5240; 6161 5256 5257 5242 5241; 6162 5257 5258 5243 5242;
    6163 5258 5259 5244 5243; 6164 5259 5260 5245 5244; 6165 5260 5261 5246 5245;
    6166 5261 5262 5247 5246; 6167 5262 4624 4625 5247; 6168 5027 5263 5248 5026;
    6169 5263 5264 5249 5248; 6170 5264 5265 5250 5249; 6171 5265 5266 5251 5250;
    6172 5266 5267 5252 5251; 6173 5267 5268 5253 5252; 6174 5268 5269 5254 5253;
    6175 5269 5270 5255 5254; 6176 5270 5271 5256 5255; 6177 5271 5272 5257 5256;
    6178 5272 5273 5258 5257; 6179 5273 5274 5259 5258; 6180 5274 5275 5260 5259;
    6181 5275 5276 5261 5260; 6182 5276 5277 5262 5261; 6183 5277 4623 4624 5262;
    6184 5028 5278 5263 5027; 6185 5278 5279 5264 5263; 6186 5279 5280 5265 5264;
    6187 5280 5281 5266 5265; 6188 5281 5282 5267 5266; 6189 5282 5283 5268 5267;
    6190 5283 5284 5269 5268; 6191 5284 5285 5270 5269; 6192 5285 5286 5271 5270;
    6193 5286 5287 5272 5271; 6194 5287 5288 5273 5272; 6195 5288 5289 5274 5273;
    6196 5289 5290 5275 5274; 6197 5290 5291 5276 5275; 6198 5291 5292 5277 5276;
    6199 5292 4622 4623 5277; 6200 5029 5293 5278 5028; 6201 5293 5294 5279 5278;
    6202 5294 5295 5280 5279; 6203 5295 5296 5281 5280; 6204 5296 5297 5282 5281;
    6205 5297 5298 5283 5282; 6206 5298 5299 5284 5283; 6207 5299 5300 5285 5284;
    6208 5300 5301 5286 5285; 6209 5301 5302 5287 5286; 6210 5302 5303 5288 5287;
    6211 5303 5304 5289 5288; 6212 5304 5305 5290 5289; 6213 5305 5306 5291 5290;
    6214 5306 5307 5292 5291; 6215 5307 4621 4622 5292; 6216 5030 5308 5293 5029;
    6217 5308 5309 5294 5293; 6218 5309 5310 5295 5294; 6219 5310 5311 5296 5295;
    6220 5311 5312 5297 5296; 6221 5312 5313 5298 5297; 6222 5313 5314 5299 5298;
    6223 5314 5315 5300 5299; 6224 5315 5316 5301 5300; 6225 5316 5317 5302 5301;
    6226 5317 5318 5303 5302; 6227 5318 5319 5304 5303; 6228 5319 5320 5305 5304;
    6229 5320 5321 5306 5305; 6230 5321 5322 5307 5306; 6231 5322 4620 4621 5307;
    6232 5031 5323 5308 5030; 6233 5323 5324 5309 5308; 6234 5324 5325 5310 5309;
    6235 5325 5326 5311 5310; 6236 5326 5327 5312 5311; 6237 5327 5328 5313 5312;
    6238 5328 5329 5314 5313; 6239 5329 5330 5315 5314; 6240 5330 5331 5316 5315;
    6241 5331 5332 5317 5316; 6242 5332 5333 5318 5317; 6243 5333 5334 5319 5318;
    6244 5334 5335 5320 5319; 6245 5335 5336 5321 5320; 6246 5336 5337 5322 5321;
    6247 5337 4619 4620 5322; 6248 5032 5338 5323 5031; 6249 5338 5339 5324 5323;
    6250 5339 5340 5325 5324; 6251 5340 5341 5326 5325; 6252 5341 5342 5327 5326;
    6253 5342 5343 5328 5327; 6254 5343 5344 5329 5328; 6255 5344 5345 5330 5329;
    6256 5345 5346 5331 5330; 6257 5346 5347 5332 5331; 6258 5347 5348 5333 5332;
    6259 5348 5349 5334 5333; 6260 5349 5350 5335 5334; 6261 5350 5351 5336 5335;
    6262 5351 5352 5337 5336; 6263 5352 4618 4619 5337; 6264 5033 5353 5338 5032;
    6265 5353 5354 5339 5338; 6266 5354 5355 5340 5339; 6267 5355 5356 5341 5340;
    6268 5356 5357 5342 5341; 6269 5357 5358 5343 5342; 6270 5358 5359 5344 5343;
    6271 5359 5360 5345 5344; 6272 5360 5361 5346 5345; 6273 5361 5362 5347 5346;
    6274 5362 5363 5348 5347; 6275 5363 5364 5349 5348; 6276 5364 5365 5350 5349;
    6277 5365 5366 5351 5350; 6278 5366 5367 5352 5351; 6279 5367 4617 4618 5352;
    6280 5034 5368 5353 5033; 6281 5368 5369 5354 5353; 6282 5369 5370 5355 5354;
    6283 5370 5371 5356 5355; 6284 5371 5372 5357 5356; 6285 5372 5373 5358 5357;
    6286 5373 5374 5359 5358; 6287 5374 5375 5360 5359; 6288 5375 5376 5361 5360;
    6289 5376 5377 5362 5361; 6290 5377 5378 5363 5362; 6291 5378 5379 5364 5363;
    6292 5379 5380 5365 5364; 6293 5380 5381 5366 5365; 6294 5381 5382 5367 5366;
    6295 5382 4616 4617 5367; 6296 5035 5383 5368 5034; 6297 5383 5384 5369 5368;
    6298 5384 5385 5370 5369; 6299 5385 5386 5371 5370; 6300 5386 5387 5372 5371;
    6301 5387 5388 5373 5372; 6302 5388 5389 5374 5373; 6303 5389 5390 5375 5374;
    6304 5390 5391 5376 5375; 6305 5391 5392 5377 5376; 6306 5392 5393 5378 5377;
    6307 5393 5394 5379 5378; 6308 5394 5395 5380 5379; 6309 5395 5396 5381 5380;
    6310 5396 5397 5382 5381; 6311 5397 4615 4616 5382; 6312 5036 5398 5383 5035;
    6313 5398 5399 5384 5383; 6314 5399 5400 5385 5384; 6315 5400 5401 5386 5385;
    6316 5401 5402 5387 5386; 6317 5402 5403 5388 5387; 6318 5403 5404 5389 5388;
    6319 5404 5405 5390 5389; 6320 5405 5406 5391 5390; 6321 5406 5407 5392 5391;
    6322 5407 5408 5393 5392; 6323 5408 5409 5394 5393; 6324 5409 5410 5395 5394;
    6325 5410 5411 5396 5395; 6326 5411 5412 5397 5396; 6327 5412 4614 4615 5397;
    6328 5037 5413 5398 5036; 6329 5413 5414 5399 5398; 6330 5414 5415 5400 5399;
    6331 5415 5416 5401 5400; 6332 5416 5417 5402 5401; 6333 5417 5418 5403 5402;
    6334 5418 5419 5404 5403; 6335 5419 5420 5405 5404; 6336 5420 5421 5406 5405;
    6337 5421 5422 5407 5406; 6338 5422 5423 5408 5407; 6339 5423 5424 5409 5408;
    6340 5424 5425 5410 5409; 6341 5425 5426 5411 5410; 6342 5426 5427 5412 5411;
    6343 5427 4613 4614 5412; 6344 385 5038 5413 5037; 6345 5038 5039 5414 5413;
    6346 5039 5040 5415 5414; 6347 5040 5041 5416 5415; 6348 5041 5042 5417 5416;
    6349 5042 5043 5418 5417; 6350 5043 5044 5419 5418; 6351 5044 5045 5420 5419;
    6352 5045 5046 5421 5420; 6353 5046 5047 5422 5421; 6354 5047 5048 5423 5422;
    6355 5048 5049 5424 5423; 6356 5049 5050 5425 5424; 6357 5050 5051 5426 5425;
    6358 5051 5052 5427 5426; 6359 5052 379 4613 5427;
    <! STAAD PRO GENERATED DATA DO NOT MODIFY !!!
    PARAMETRIC MODEL SWALL 15
    TYPE WALL
    MESH PARAM 0.2 4 1 1
    MESH ORG 1 2 3
    BOUNDARY 4
    384 0 0 385 0 0 379 0 0 378 0 0
    GENERATED NODES 5013 TO 5427
    GENERATED PLATES PLATE 5944 TO 6359
    END
    !> END GENERATED DATA BLOCK
    PARAMETRIC MODEL SWALL 14
    TYPE WALL
    MESH ORG 1 2 3
    BOUNDARY 4
    372 0 0 373 0 0 379 0 0 378 0 0
    GENERATED NODES 4598 TO 5012
    GENERATED PLATES PLATE 5488 TO 5903
    END
    PARAMETRIC MODEL SWALL 13
    TYPE WALL
    MESH ORG 1 3 4
    BOUNDARY 6
    134 0 0 169 0 0 291 0 0 373 0 0 372 0 0 270 0 0
    GENERATED NODES 4217 TO 4597
    GENERATED PLATES PLATE 5066 TO 5447
    END
    PARAMETRIC MODEL SWALL 12
    TYPE WALL
    MESH ORG 1 2 3
    BOUNDARY 4
    383 0 0 384 0 0 378 0 0 377 0 0
    GENERATED NODES 3930 TO 4216
    GENERATED PLATES PLATE 4739 TO 5026
    END
    PARAMETRIC MODEL SWALL 11
    TYPE WALL
    MESH ORG 1 2 3
    BOUNDARY 4
    371 0 0 372 0 0 378 0 0 377 0 0
    GENERATED NODES 3643 TO 3929
    GENERATED PLATES PLATE 4419 TO 4706
    END
    PARAMETRIC MODEL SWALL 10
    TYPE WALL
    MESH ORG 1 3 4
    BOUNDARY 6
    99 0 0 134 0 0 270 0 0 372 0 0 371 0 0 249 0 0
    GENERATED NODES 3250 TO 3642
    GENERATED PLATES PLATE 3989 TO 4386
    END
    PARAMETRIC MODEL SWALL 9
    TYPE WALL
    MESH ORG 1 2 3
    BOUNDARY 4
    382 0 0 383 0 0 377 0 0 376 0 0
    GENERATED NODES 2963 TO 3249
    GENERATED PLATES PLATE 3670 TO 3957
    END
    PARAMETRIC MODEL SWALL 8
    TYPE WALL
    MESH ORG 1 2 3
    BOUNDARY 4
    370 0 0 371 0 0 377 0 0 376 0 0
    GENERATED NODES 2676 TO 2962
    GENERATED PLATES PLATE 3350 TO 3637
    END
    PARAMETRIC MODEL SWALL 7
    TYPE WALL
    MESH ORG 1 3 4
    BOUNDARY 6
    64 0 0 99 0 0 249 0 0 371 0 0 370 0 0 228 0 0
    GENERATED NODES 2283 TO 2675
    GENERATED PLATES PLATE 2920 TO 3317
    END
    PARAMETRIC MODEL SWALL 6
    TYPE WALL
    MESH ORG 1 2 3
    BOUNDARY 4
    381 0 0 382 0 0 376 0 0 375 0 0
    GENERATED NODES 1836 TO 2282
    GENERATED PLATES PLATE 2441 TO 2888
    END
    PARAMETRIC MODEL SWALL 5
    TYPE WALL
    MESH ORG 1 2 3
    BOUNDARY 4
    369 0 0 370 0 0 376 0 0 375 0 0
    GENERATED NODES 1389 TO 1835
    GENERATED PLATES PLATE 1951 TO 2398
    END
    PARAMETRIC MODEL SWALL 4
    TYPE WALL
    MESH ORG 1 3 4
    BOUNDARY 5
    29 0 0 64 0 0 228 0 0 370 0 0 369 0 0
    GENERATED NODES 1016 TO 1388
    GENERATED PLATES PLATE 1534 TO 1908
    END
    PARAMETRIC MODEL SWALL 3
    TYPE WALL
    MESH ORG 1 2 3
    BOUNDARY 4
    386 0 0 381 0 0 375 0 0 380 0 0
    GENERATED NODES 810 TO 1015
    GENERATED PLATES PLATE 1301 TO 1492
    END
    PARAMETRIC MODEL SWALL 2
    TYPE WALL
    MESH ORG 1 2 3
    BOUNDARY 4
    374 0 0 369 0 0 375 0 0 380 0 0
    GENERATED NODES 604 TO 809
    GENERATED PLATES PLATE 1083 TO 1274
    END
    TYPE WALL
    MESH ORG 1 2 3
    BOUNDARY 4
    323 0 0 29 0 0 369 0 0 374 0 0
    GENERATED NODES 387 TO 603
    GENERATED PLATES PLATE 865 TO 1056
    END
    START GROUP DEFINITION
    FLOOR
    _2FLR_DL 95 96 99 TO 101 104 TO 106 108 TO 111 113 TO 115 117 TO 120 -
    122 TO 124 126 TO 129 131 TO 133 135 TO 138 140 141 144 145 149 150 524 525 -
    527 TO 540 542 543 545 TO 556 558 TO 561 715 792 814
    _2FLR_DL_2WAY 94 98 99 103 106 TO 108 112 116 117 121 125 126 130 134 135 -
    139 143 144 148 529 715 TO 717
    _3FLR_DL 188 189 192 TO 194 197 TO 199 201 TO 204 206 TO 208 210 TO 213 215 -
    216 TO 217 219 TO 222 224 TO 226 228 TO 231 233 234 237 238 242 243 563 564 -
    566 TO 579 581 582 584 TO 595 597 TO 600 720 727 728 793 816
    _4FLR_DL 281 282 285 TO 287 290 TO 292 294 TO 297 299 TO 301 303 TO 306 308 -
    309 TO 310 312 TO 315 317 TO 319 321 TO 324 326 327 330 331 335 336 602 603 -
    605 TO 618 620 621 623 TO 634 636 TO 639 723 729 730 794 818
    _5FLR_DL 374 375 378 TO 380 383 TO 385 641 642 644 TO 646 662 668 726 731 732
    _2FLR_LL_OFFICE 96 100 101 104 TO 106 108 TO 111 113 TO 115 119 120 124 128 -
    129 131 TO 133 135 TO 138 140 141 144 145 149 150 525 527 TO 532 535 TO 540 -
    542 543 546 549 TO 552 555 556 558 TO 561 715 792 814
    _2FLR_LL_ASSMBLY 122 123 126 TO 128 131 132 533 534 536 537 548 554
    _2FLR_LL_STORAGE 95 99 100 104 113 114 117 TO 119 122 123 524 527 530 531 -
    533 534 545 547 553
    _2FLR_LL_OFFICE2 94 98 99 103 106 TO 108 112 116 117 121 125 126 130 134 135 -
    _3FLR_LL_QUARTER 188 189 192 TO 194 197 198 201 TO 203 206 TO 208 210 TO 213 -
    215 TO 217 219 TO 222 224 TO 226 228 TO 230 233 234 237 238 242 243 563 564 -
    566 567 569 TO 579 581 582 584 TO 595 598 599 727 816
    _3FLR_LL_GYM 199 203 204 208 568 571 597
    _3FR_LL_STORAGE 226 230 231 577 600 793
    _3FLR_LL_GYM2 199 568 720 727 728
    _4FLR_LL_ASSMBLY 281 282 285 TO 287 290 TO 292 294 TO 297 299 TO 301 -
    303 TO 306 308 TO 310 312 TO 315 317 TO 319 321 TO 324 326 327 330 331 335 -
    336 602 603 605 TO 618 620 621 623 TO 634 636 TO 639 723 729 730 794 818
    _5TH_LL_STORAGE 375 379 380 384 641 642 644 645 662 668 731
    _2FLR_BALCONY 148 TO 150 542 543 751 TO 754 756 TO 760 762 763
    _3FLR_BALCONY 242 243 581 582 765 TO 767 769 770 772 773 775 776
    _4FLR_BALCONY 335 TO 337 620 621 778 TO 783 785 TO 789
    JOINT
    END GROUP DEFINITION
    ELEMENT PROPERTY
    865 TO 1056 1083 TO 1274 1301 TO 1492 1534 TO 1908 1951 TO 2398 2441 TO 2888 -
    2920 TO 3317 3350 TO 3637 3670 TO 3957 3989 TO 4386 4419 TO 4706 -
    4739 TO 5026 5066 TO 5447 5488 TO 5903 5944 TO 6359 THICKNESS 0.25
    DEFINE MATERIAL START
    ISOTROPIC CONCRETE
    E 2.17185e+07
    POISSON 0.17
    DENSITY 23.5616
    ALPHA 1e-05
    DAMP 0.05
    TYPE CONCRETE
    STRENGTH FCU 27579
    END DEFINE MATERIAL
    MEMBER PROPERTY AMERICAN
    153 TO 156 158 TO 161 163 TO 166 168 TO 171 173 TO 176 178 TO 181 183 TO 186 -
    246 TO 249 251 TO 254 256 TO 259 261 TO 264 266 TO 269 271 TO 274 -
    276 TO 279 797 798 808 809 824 825 2889 2903 TO 2919 3333 TO 3349 -
    3638 TO 3654 3958 3972 TO 3988 4402 TO 4418 4707 TO 4722 -
    4723 PRIS YD 0.45 ZD 0.45
    188 TO 190 192 TO 195 197 TO 199 201 TO 204 206 TO 208 210 TO 213 215 TO 217 -
    219 TO 222 224 TO 226 228 TO 231 233 234 237 238 240 281 TO 283 285 TO 288 -
    290 TO 292 294 TO 297 299 TO 301 303 TO 306 308 TO 310 312 TO 315 -
    317 TO 319 321 TO 324 326 327 330 331 333 374 TO 376 378 TO 381 383 TO 385 -
    387 TO 390 392 TO 394 396 TO 399 401 TO 403 405 TO 408 410 TO 412 -
    414 TO 417 419 420 423 424 426 428 TO 430 563 564 566 TO 579 602 603 605 -
    606 TO 618 641 642 644 TO 657 659 660 727 TO 732 793 TO 795 816 818 -
    820 PRIS YD 0.4 ZD 0.3
    1 TO 48 50 TO 52 54 TO 58 94 TO 141 143 TO 145 147 TO 151 242 TO 244 -
    335 TO 337 524 525 527 TO 540 542 543 545 TO 556 558 TO 561 581 582 -
    584 TO 595 597 TO 600 620 621 623 TO 634 636 TO 639 662 TO 673 675 TO 678 -
    715 TO 717 720 723 726 741 TO 763 765 TO 770 772 TO 776 778 TO 783 -
    785 TO 789 791 792 812 814 PRIS YD 0.3 ZD 0.25
    339 TO 342 344 TO 347 349 352 354 357 359 362 364 367 369 TO 372 733 TO 740 -
    790 800 811 827 5027 5041 TO 5065 5463 TO 5487 5904 TO 5927 -
    5928 PRIS YD 0.3 ZD 0.3
    59 TO 93 680 TO 714 796 799 807 810 823 826 828 TO 838 854 TO 864 -
    1072 TO 1082 1275 TO 1285 1493 1507 TO 1533 1924 TO 1950 2399 TO 2424 -
    2425 PRIS YD 0.5 ZD 0.5
    CONSTANTS
    MATERIAL CONCRETE ALL
    MEMBER RELEASE
    545 TO 556 558 TO 561 584 TO 595 597 TO 600 623 TO 634 636 TO 639 662 TO 673 -
    675 TO 678 START MY MZ
    675 TO 678 END MY MZ
    SUPPORTS
    295 TO 329 374 380 386 424 TO 438 630 TO 644 836 TO 850 FIXED
    MEMBER CRACKED
    59 TO 93 153 TO 156 158 TO 161 163 TO 166 168 TO 171 173 TO 176 178 TO 181 -
    183 TO 186 246 TO 249 251 TO 254 256 TO 259 261 TO 264 266 TO 269 -
    271 TO 274 276 TO 279 339 TO 342 344 TO 347 349 352 354 357 359 362 364 367 -
    369 TO 372 680 TO 714 733 TO 740 REDUCTION RIY 0.7 RIZ 0.7
    1 TO 48 50 TO 52 54 TO 58 94 TO 141 143 TO 145 147 TO 151 188 TO 190 -
    219 TO 222 224 TO 226 228 TO 231 233 234 237 238 240 242 TO 244 281 TO 283 -
    285 TO 288 290 TO 292 294 TO 297 299 TO 301 303 TO 306 308 TO 310 -
    312 TO 315 317 TO 319 321 TO 324 326 327 330 331 333 335 TO 337 374 TO 376 -
    378 TO 381 383 TO 385 387 TO 390 392 TO 394 396 TO 399 401 TO 403 -
    405 TO 408 410 TO 412 414 TO 417 419 420 423 424 426 428 TO 430 524 525 527 -
    528 TO 540 542 543 545 TO 556 558 TO 561 563 564 566 TO 579 581 582 -
    584 TO 595 597 TO 600 602 603 605 TO 618 620 621 623 TO 634 636 TO 639 641 -
    642 644 TO 657 659 660 662 TO 673 675 TO 678 715 TO 717 720 723 726 TO 732 -
    741 TO 763 765 TO 770 772 TO 776 778 TO 783 785 TO 788 -
    789 REDUCTION RIY 0.35 RIZ 0.35
    DEFINE REFERENCE LOADS
    LOAD R1 LOADTYPE Dead TITLE DL1
    ONEWAY LOAD
    _2FLR_DL ONE -2.5 GY
    _3FLR_DL ONE -2.5 GY
    _4FLR_DL ONE -2.5 GY
    _5FLR_DL ONE -2.5 GY
    FLOOR LOAD
    _2FLR_DL_2WAY FLOAD -2.5 GY
    SELFWEIGHT Y -1
    ONEWAY LOAD
    _2FLR_BALCONY ONE -2.5 GY
    _3FLR_BALCONY ONE -2.5 GY
    _4FLR_BALCONY ONE -2.5 GY
    LOAD R2 LOADTYPE Dead TITLE DL2
    ONEWAY LOAD
    _2FLR_DL ONE -3.32 GY
    _3FLR_DL ONE -3.32 GY
    _4FLR_DL ONE -3.32 GY
    _5FLR_DL ONE -3.32 GY
    FLOOR LOAD
    _2FLR_DL_2WAY FLOAD -3.32 GY
    END DEFINE REFERENCE LOADS
    FLOOR DIAPHRAGM
    DIA 1 TYPE RIG HEI 5.5
    DIA 2 TYPE RIG HEI 9
    DIA 3 TYPE RIG HEI 12.5
    CHECK SOFT STORY ASCE7
    DEFINE UBC LOAD
    ZONE 0.4 I 1.5 RWX 8.55 RWZ 8.5 STYP 4 CT 0.0731 NA 1.2 NV 1.6
    DEFINE WIND LOAD
    TYPE 1 W1
    ASCE-7-2010:PARAMS 85.000 MPH 0 1 1 0 0.000 FT 0.000 FT 0.000 FT 1 2 20.500 -
    M 20.150 M 35.600 M 2.000 0.010 0 0 0 0 0 0.882 1.000 1.000 0.850 0 0 0 0 -
    0.831 0.800 -0.180
    INT 0.407075 0.407075 0.427257 0.444583 0.459866 0.473603 0.486123 0.497658 -
    0.508373 0.518398 0.52783 0.536746 0.545209 0.553272 0.560977 HEIG 0 4.572 -
    5.79723 7.02246 8.24769 9.47292 10.6981 11.9234 13.1486 14.3738 15.5991 -
    16.8243 18.0495 19.2748 20.5
    EXP 1 JOINT 1 TO 70 72 TO 75 77 TO 80 82 TO 85 87 TO 90 92 TO 95 97 TO 100 -
    102 TO 105 107 TO 110 112 TO 115 117 TO 120 122 TO 125 127 TO 130 -
    132 TO 135 137 TO 140 142 TO 145 147 TO 150 152 TO 155 157 TO 160 -
    162 TO 165 167 TO 170 172 TO 175 211 212 214 TO 230 232 233 235 TO 251 253 -
    254 256 TO 272 274 275 277 TO 293 295 TO 345 374 380 386
    LOAD 1 LOADTYPE Seismic TITLE EX
    UBC LOAD X 1 DEC 1 ACC 0.05
    PERFORM ANALYSIS PRINT LOAD DATA
    CHANGE
    LOAD 2 LOADTYPE Seismic TITLE EZ
    UBC LOAD Z 1 DEC 1 ACC 0.05
    CHANGE
    LOAD 3 LOADTYPE Dead TITLE DL1
    REFERENCE LOAD
    R1 1.0
    LOAD 4 LOADTYPE Dead TITLE DL2
    REFERENCE LOAD
    R2 1.0
    LOAD 5 LOADTYPE Live TITLE LL1
    ONEWAY LOAD
    _2FLR_LL_OFFICE ONE -2.4 GY
    FLOOR LOAD
    _2FLR_LL_OFFICE2 FLOAD -2.4 GY
    ONEWAY LOAD
    _3FLR_LL_QUARTER ONE -1.9 GY
    _2FLR_BALCONY ONE -2.9 GY
    _3FLR_BALCONY ONE -2.9 GY
    _4FLR_BALCONY ONE -2.9 GY
    LOAD 6 LOADTYPE Live TITLE LL2
    ONEWAY LOAD
    _2FLR_LL_ASSMBLY ONE -4.8 GY
    _2FLR_LL_STORAGE ONE -6 GY
    _3FLR_LL_GYM ONE -6 GY
    _3FR_LL_STORAGE ONE -6 GY
    FLOOR LOAD
    _3FLR_LL_GYM2 FLOAD -6 GY
    ONEWAY LOAD
    _4FLR_LL_ASSMBLY ONE -4.8 GY
    _5TH_LL_STORAGE ONE -6 GY
    LOAD 7 LOADTYPE Roof Live TITLE LLR
    JOINT LOAD
    152 155 157 160 162 165 167 170 172 TO 175 338 TO 345 FY -30
    LOAD 8 LOADTYPE Wind TITLE WZ1
    WIND LOAD Z 1 TYPE 1
    LOAD 9 LOADTYPE Wind TITLE WZ2
    WIND LOAD Z -1 TYPE 1
    LOAD 10 LOADTYPE Wind TITLE WX1
    WIND LOAD X 1 TYPE 1
    LOAD 11 LOADTYPE Wind TITLE WX2
    WIND LOAD X -1 TYPE 1
    **DESIGN LOAD COMBINATIONS - LRFD
    LOAD COMB 101 1.4DL
    1 0.0 2 0.0 3 1.4 4 1.4 5 0.0 6 0.0 7 0.0 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 102 1.2DL + 1.6LL + 0.5LLR
    1 0.0 2 0.0 3 1.2 4 1.2 5 1.6 6 1.6 7 0.5 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 103 1.2DL + 1.6LLR + F1LL
    1 0.0 2 0.0 3 1.2 4 1.2 5 0.5 6 1.0 7 1.6 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 104 (1.2 + 0.5CAI)DL + F1LL + 1.0EX + 0.3EZ
    1 1.0 2 0.3 3 1.42 4 1.42 5 0.5 6 1.0 7 0.5 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 105 (1.2 + 0.5CAI)DL + F1LL + 1.0EX - 0.3EZ
    1 1.0 2 -0.3 3 1.42 4 1.42 5 0.5 6 1.0 7 0.5 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 106 (1.2 + 0.5CAI)DL + F1LL - 1.0EX + 0.3EZ
    1 -1.0 2 0.3 3 1.42 4 1.42 5 0.5 6 1.0 7 0.5 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 107 (1.2 + 0.5CAI)DL + F1LL - 1.0EX - 0.3EZ
    1 -1.0 2 -0.3 3 1.42 4 1.42 5 0.5 6 1.0 7 0.5 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 108 (1.2 + 0.5CAI)DL + F1LL + 1.0EZ + 0.3EX
    1 0.3 2 1.0 3 1.42 4 1.42 5 0.5 6 1.0 7 0.5 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 109 (1.2 + 0.5CAI)DL + F1LL + 1.0EZ - 0.3EX
    1 -0.3 2 1.0 3 1.42 4 1.42 5 0.5 6 1.0 7 0.5 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 110 (1.2 + 0.5CAI)DL + F1LL - 1.0EZ + 0.3EX
    1 0.3 2 -1.0 3 1.42 4 1.42 5 0.5 6 1.0 7 0.5 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 111 (1.2 + 0.5CAI)DL + F1LL - 1.0EZ - 0.3EX
    1 -0.3 2 -1.0 3 1.42 4 1.42 5 0.5 6 1.0 7 0.5 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 112 (0.9 + 0.5CAI)DL + 1.0EX + 0.3EZ
    1 1.0 2 0.3 3 1.12 4 1.12 5 0.0 6 0.0 7 0.0 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 113 (0.9 + 0.5CAI)DL + 1.0EX - 0.3EZ
    1 1.0 2 -0.3 3 1.12 4 1.12 5 0.0 6 0.0 7 0.0 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 114 (0.9 + 0.5CAI)DL - 1.0EX + 0.3EZ
    1 -1.0 2 0.3 3 1.12 4 1.12 5 0.0 6 0.0 7 0.0 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 115 (0.9 + 0.5CAI)DL - 1.0EX - 0.3EZ
    1 -1.0 2 -0.3 3 1.12 4 1.12 5 0.0 6 0.0 7 0.0 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 116 (0.9 + 0.5CAI)DL + 1.0EZ + 0.3EX
    1 0.3 2 1.0 3 1.12 4 1.12 5 0.0 6 0.0 7 0.0 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 117 (0.9 + 0.5CAI)DL + 1.0EZ - 0.3EX
    1 -0.3 2 1.0 3 1.12 4 1.12 5 0.0 6 0.0 7 0.0 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 118 (0.9 + 0.5CAI)DL - 1.0EZ + 0.3EX
    1 0.3 2 -1.0 3 1.12 4 1.12 5 0.0 6 0.0 7 0.0 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 119 (0.9 + 0.5CAI)DL - 1.0EZ - 0.3EX
    1 -0.3 2 -1.0 3 1.12 4 1.12 5 0.0 6 0.0 7 0.0 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 120 1.2DL + F1LL + 0.5LLR + 1.0WZ1
    1 0.0 2 0.0 3 1.2 4 1.2 5 0.5 6 1.0 7 0.5 8 1.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 121 1.2DL + F1LL + 0.5LLR + 1.0WZ2
    1 0.0 2 0.0 3 1.2 4 1.2 5 0.5 6 1.0 7 0.5 8 0.0 9 1.0 10 0.0 11 0.0
    LOAD COMB 122 1.2DL + F1LL + 0.5LLR + 1.0WX1
    1 0.0 2 0.0 3 1.2 4 1.2 5 0.5 6 1.0 7 0.5 8 0.0 9 0.0 10 1.0 11 0.0
    LOAD COMB 123 1.2DL + F1LL + 0.5LLR + 1.0WX2
    1 0.0 2 0.0 3 1.2 4 1.2 5 0.5 6 1.0 7 0.5 8 0.0 9 0.0 10 0.0 11 1.0
    LOAD COMB 124 0.9DL + 1.0WZ1
    1 0.0 2 0.0 3 0.9 4 0.9 5 0.0 6 0.0 7 0.0 8 1.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 125 0.9DL + 1.0WZ2
    1 0.0 2 0.0 3 0.9 4 0.9 5 0.0 6 0.0 7 0.0 8 0.0 9 1.0 10 0.0 11 0.0
    LOAD COMB 126 0.9DL + 1.0WX1
    1 0.0 2 0.0 3 0.9 4 0.9 5 0.0 6 0.0 7 0.0 8 0.0 9 0.0 10 1.0 11 0.0
    LOAD COMB 127 0.9DL + 1.0WX2
    1 0.0 2 0.0 3 0.9 4 0.9 5 0.0 6 0.0 7 0.0 8 0.0 9 0.0 10 0.0 11 1.0
    LOAD COMB 128 (0.9 - 0.5CAI)DL + 1.0EX + 0.3EZ
    1 1.0 2 0.3 3 0.68 4 0.68 5 0.0 6 0.0 7 0.0 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 129 (0.9 - 0.5CAI)DL + 1.0EX - 0.3EZ
    1 1.0 2 -0.3 3 0.68 4 0.68 5 0.0 6 0.0 7 0.0 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 130 (0.9 - 0.5CAI)DL - 1.0EX + 0.3EZ
    1 -1.0 2 0.3 3 0.68 4 0.68 5 0.0 6 0.0 7 0.0 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 131 (0.9 - 0.5CAI)DL - 1.0EX - 0.3EZ
    1 -1.0 2 -0.3 3 0.68 4 0.68 5 0.0 6 0.0 7 0.0 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 132 (0.9 - 0.5CAI)DL + 1.0EZ + 0.3EX
    1 0.3 2 1.0 3 0.68 4 0.68 5 0.0 6 0.0 7 0.0 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 133 (0.9 - 0.5CAI)DL + 1.0EZ - 0.3EX
    1 -0.3 2 1.0 3 0.68 4 0.68 5 0.0 6 0.0 7 0.0 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 134 (0.9 - 0.5CAI)DL - 1.0EZ + 0.3EX
    1 0.3 2 -1.0 3 0.68 4 0.68 5 0.0 6 0.0 7 0.0 8 0.0 9 0.0 10 0.0 11 0.0
    LOAD COMB 135 (0.9 - 0.5CAI)DL - 1.0EZ - 0.3EX
    1 -0.3 2 -1.0 3 0.68 4 0.68 5 0.0 6 0.0 7 0.0 8 0.0 9 0.0 10 0.0 11 0.0
    PERFORM ANALYSIS
    PRINT STORY DRIFT 0.003361
    FINISH
    The support reactions became very unrealistic.