Hi
in my model the subgrade reaction is calculated like follows,
** SBC 30T/M3 = 300 kN/m3** ALLOWABLE DEFLECTION IS 15mm*** SUBGRADE MODULUS = 20000 kN/m2
and the plate mesh i have created is 0.5mx0.5m. so in this case do i need to change the subgrade value to this 20000/(0.5*0.5) = 80000kN/m2 for internal plates
and for end plates 20000(0.5*0.25) = 160000
and for corner plates 320000 kN/m2 ????
can you clear this doubt? thanks in advance.
When you assign PLATE MAT support to plate elements in a model, the program automatically determines the tributary area for each plate element’s corner nodes. Then, that area is multiplied by the subgrade modulus to calculate the linear spring stiffness to be assigned at that node.
IS THIS THE SAME FOR ELASTIC MAT ASWELL?
OR ELASTIC MAT IS ASSIGNED TO NODES, SO DO WE NEED TO CAHGNE THE SUBGRADE AS PER LOCATION ?
For ELASTIC MAT it works the same way as well. You just provide one value of subgrade modulus. The program will internally figure out the influence area for each node and multiply that by the subgrade modulus to generate the spring stiffness at that node. If you have modeled your mat using a mesh of plates, you should use PLATE MAT as opposed to ELASETIC MAT
Thanks for the Quick help.
I have tried the same model with Plate mat and Elastic mat. and i noticed differences in Both base pressure and maximum forces.
if the both works same way, why the difference is coming. am i doing in correct way, or did i missed any?
Please check, i have added both the design files and a picture shows this difference.
Thanks your time. FOUNDATION Elastic.txtFOUNDATION Plate.txt
You should be using PLATE MAT option is the structure is used from plates. More details can be found here: Mat Foundation: Elastic and Plate Mat - RAM | STAAD Files - RAM | STAAD - Bentley Communities