Kindly help me to know how SFA is calculating the dimension of footing.
Input Data
1. SBC - 120 KN/m2
2. Net Bearing capacity Input Selected.
3. Load Case Table
4. Multiplier Factor - 2
Question - How staad is calculating min area required is 1.58 m2 ? Please explain calculation to be followed here ?
5. How Final area of footing is coming 2.25 m2 ?
As per my calculation, area should be = Total Load /SBC
Total Load - 213.80+33.75+73.96 = 321.51
Therefore, Area = 321.51 / 120 = 2.67m2
6. How pressure value are being calculated in STAAD. I am not able to find the calculation done here in verification manual ?
Your calculation in step 5 is not correct. You are dividing a force which is in the gross frame of reference by an allowable soil pressure which is in the net frame of reference. You need to use the gross bearing capacity in the denominator. (net bearing capacity needs to be converted to the gross bearing capacity as explained in an earlier discussion).
Also, you need to add the pressure contribution from the 2 moments at the base of the footing. The Canadian example 6 in the verification manual shows you how to calculate the pressures due to a vertical force plus two moments. If you attach your SFA file, we can show you how the values in your step 6 are obtained.
PFA, SFA analysis. Please check for footing no 103. Also in the attached model for footing no 103, tota load is 557.69 KN ( 383.07 +54.15 + 120.47) and GBC is 330 KN /m2. Area is coming 557.69 /330 = 1.68 m2.However staad reports 3.61 m2. Please elaborate this also.
Assembly Hall Project 4 with meshing and FL and LC_foundation.sfa
Results as per the latest version - SFA Build 9.6.1.74
Total vertical load = 383.069 + 54.15 + 120.473 = 557.692 kN
MZ at base of footing = (-1.0 * -1.389 * 0.6) + 0.254 = 1.0874 kN-m
MX at base of footing = (-10.523 * 0.6) -4.297 = -10.6108 kN-m
Plan area of footing = 1.9m * 1.9m = 3.61 sq.mSection Modulus = (1/6) * 1.9 * (1.9*1.9) = 1.143 m3
Maximum "Gross" corner pressure = (557.692/3.61) + (1.0874/1.143) + (10.6108/1.143) = 164.7185 kN/m2
Minimum "Gross" corner pressure = (557.692/3.61) - (1.0874/1.143) - (10.6108/1.143) = 144.2522 kN/m2 which is greater than zero, hence no uplift
Gross Bearing capacity = Net bearing capacity + Gamma*H = 120 + (18.0 kN/m3 * 2.5m) = 165 kN/m2
164.7185 < 165 --- Hence safe..
For reporting purposes:
Maximum Net Bearing pressure = 164.7185 - 45 = 119.7185 kN/m2Minimum Net Bearing pressure = 144.2522 - 45 = 99.2522 kN/m2
Kris Sathia said:MZ at base of footing = (-1.0 * -1.389 * 0.6) + 0.254 = 1.0874 kN-m MX at base of footing = (-10.523 * 0.6) -4.297 = -10.6108 kN-m
I have 2 questions here,
1. While calculating MZ and MX, How and from where do you get the value shown above to arrive Final Mz and Mx value ? Also why we multiply by factor 1 and add 0.254 to calculate MZ value and -10.523 and (-4.297) to calculate Mx value ? As, Final moment for which the foundation should be designed in both the direction should be ( Total Overturning Moment - Total Restoring Moment )
2. As shown in attached screenshot below, GBC is ( 2*(120 +18*2.5)) = 330 KN /M2 and we calculate 165 KN /m2 . Please explain the use of 330 KN /m2 ?
In the current version,
Reactions from the superstructure columns are assumed to act at the top of the footing. The lateral forces FX and FZ produce a moment at the bottom of the footing.
MZ due to FX = -1.0 * FX * DMX due to FZ = +1.0 * FZ * D
Total Moment for each direction = moment due to the lateral force + moment from the reactions at the base of the column.
D is the thickness of the footing = 0.6 m
The multiplier 2 is used to obtain the allowable bearing pressure for utimate load cases. That is why the term is called Multiplier on Soil Bearing Capacity for Ultimate Load cases.
allowable bearing capacity for ultimate load cases = Multiplier on Soil Bearing Capacity for Ultimate Load cases * Base value of Soil bearing capacity
Allowable Gross bearing capacity for service load cases = 120 + 45 = 165Allowable Gross bearing capacity for Ultimate load cases = 2*120 + 45 = 285
Load case 3 is declared as a Primary type, which means it serves as a Service case and an Ultimate case. The check being done here is for the service case, hence we use 165 and not 285.