Hi everyone,
I'm using footing support (Y direction and compression only). I have notice that it only work with some load cases (gravity) by not lateral load cases. Could you please take a look at the model and tell me what is the problem. thanks:
RANA HW 2 (3) (2).std
  • Pure lateral cases cannot be run with a compression only attribute because there is no way to generate any restoring moment from a pure compression support arrangement.
    So, here are the changes needed.
    1) Remove the compression attribute from the current instance of the soil support.
    2) Convert load cases 3, 4, 5 and 6 to the Reference Load type.
    3) After load case 2, specify the soil support command again, this time include the Compression attribute
    4) Convert load cases 7 and 8 to the REFERENCE LOAD type.
    Attached is the modified file. Ignore the results of load cases 1 and 2. They would be meaningful only if they are part of a combination case like 7 or 8.
    RANA HW 2 (3) (2) - modified.std
    Answer Verified By: Khawaldah
Reply