Slab Designer in Staad Foundation Advanced
for the staad foundation advanced, under the Slab Designer and you click the 'Design', a table of Moments and Rebar Area Required appears. if it says 'Failed' in Area required, do I need to increase the thickness? Kindly elaborate more on this. Thanks
  • thanks for the response. but if I use the moments I can still get the bar spacing by just increasing the bar diameter. that's why I wonder why there is a need to increase the footing depth....
  • Also, I noticed that the Rebar Area Required in the next column is quite big. How is it computed?
  • When you generate a moment envelope (default 60 X 60), the program is creating a grid of points on the surface of the mat. It fetches the moments along the longitudinal and transverse directions for each of those points by scanning through the results of all the ultimate load cases that the mat has been analysed for.
    Then, at each of these envelope points, a total of 4 moments are fetched, each of which is the maximum value for that location from amongst all the ultimate load cases.
    1. for longitudinal direction, tension on top surface of the mat
    2. for longitudinal direction, tension on bottom surface of the mat
    3. for transverse direction, tension on top surface of the mat
    4. for transverse direction, tension on bottom surface of the mat
    Note that each of these moments is per unit width of the slab, 1 metre or 1 foot, depending on the design code, which is what a FE analysis of a mat gives you.
    Thus, for the purpose of flexure design, at each envelope point, the slab is treated as a beam having a unit width.
    Next, the program calculates the maximum permissible moment on the cross section based on compression failure of concrete for the thickness at that location. So, if any of these 4 moments exceeds the maximum moment capacity of the section, then, that moment cannot be designed for, and that is when you get a fail in the design status report. Envelope points that fall directly under a column or a pedestal are not designed.
    The moment capacity is based on the crushing of concrete, which if I am not mistaken is also associated with the maximum area of steel that the code permits for that thickness. So, changing the reinforcement arrangement isn't going to help. The only way to resolve it would be to increase the slab thickness. You may not need to increase it all over the slab, just find the areas of high moment and increase the thickness locally by creating regions of higher thickness in those areas.
    Regarding your question on why such large steel areas are shown in the screenshot you attached, we need your model. Also, let us know what build of the program you are checking it with.
  • thanks a lot for this explanation @Kris Sathia, just want also to know how the steel areas are calculated based from those moments? btw, how to send here my model?
Reply Children