Bentley Team,
How is the effective depth for beam being calculated for a beam with two or more numbers of layers in RCDC software?
Please provide the basis and validation for the same.
I could find some formula related to effective depth in FAQ in the link below, but that is not giving correct value for the design I have.
https://communities.bentley.com/products/ram-staad/w/structural_analysis_and_design__wiki/41953/rcdc-beam
I have attached a sample file. If you refer Beam B5, top right is provided with 3 layers of rebar. In that case how is the effective depth being calculated? Based on the solution given by Abhisek M I presume that it is calculated as below:
Effective depth, d = 450 (Overall Depth) - 30 (Clear cover) - 16 (for layer 1) - 25 (spacer bar between layer 1 and layer 2) - 16/2 (upto centre of layer 2) => d = 371mm = 370mm (rounded off).
But actual provision is 3 layers of 12 dia bar as per design, as per which calculation should be as follows,
Effective depth, d = 450 (Overall Depth) - 30 (Clear cover) - 12 (for layer 1) - 13.33 (Two third of aggregate size or bar dia, whichever is higher) - 12/2 (upto centre of layer 2) => d = 388.67mm = 385mm (rounded off).
So RCDC is basically calculating lesser effective depth than required. Is that correct?
Also confirm if my assumptions are correct.
PDF
Request you to please check and confirm.
Hi Nidhi,
Could you please share the effective depth calculation of RCDC.
Beam Size 230 x 300mm
Clear Cover -20mm
Bottom R/F dia - 16mm
Stirrups dia - 8mm
As per your above calculation methodology, eff depth should be
300 - 20 - 16 - 8/2 = 300 -40mm = 260mm
But as per RCDC , eff depth is coming as 250mm
Hello Mr. Paresh,
Sharing the attached sheet for your reference and clarification.
Deff and Ast calculation.xlsx