RCDC - Beam Design with ACI 318M-14 - Crack Width Calculation

Dear Bentley team,

I encountered an issue regarding crack width calculation in RCDC with ACI 318M-14 code, described as follows:

Refer to the outputs attached below. The considered beam is B5 and Zone is Top right.

When beam is designed with permissible crack width set as 0.25mm, then actual crack width with 1 layer of bar with 3 no. of 13 dia bars is coming out to be 0.1539mm which is within the limit.

Now for the same design if I restrict the permissible crack width to 0.2mm, then also it should satisfy the design (as 0.1539mm < 0.2mm). But when I reduce the limit to 0.2mm, RCDC is increasing the rebar to 2 no. of layers with 3 no. of 13 dia bars in first layer and 2 no. of 13 dia bars in second layer. 

Changing only the permissible crack width limit should not ideally affect the actual crackwidth calculation. But it is somehow dependent on that and leads to increase in rebar. Please help in rectifying the issue.

Please find attached RCDC file, and two output sheets with maximum crack width set as 0.25mm and 0.2mm for your reference

PDFPDFFMO_P01_01(02.12.2021)-NV-2-Beam-1-0 m.rcdx.7z

  • Hi Abhijeet,

    Correct me if my understanding is wrong.

    What I understood is irrespective of whatever number of bars user has entered in the above form, RCDC always take only 2 numbers of bars (due to internal error) for all the designs for crackwidth check.

    But if that is the case then please clear following things:

    1) For both the outputs, 3 bars are given as the input in the above form.

    For output with crack width limit 0.25mm and 3no. of 13 dia bars, the actual crackwidth value calculated is correct with respect to 3no. of 13 dia bar provision. 

    For output with crack width limit 0.20mm and 5no. of 13 dia bars (3 in 1st layer and 2 in 2nd layer), the actual crackwidth value calculated is correct with respect to 5no. of 13 dia bar provision. 

    Point is whatever actual crack width calculation shown in output is correct as per our manual calculations also for both the calculations. If it is calculating based on 2 no. of rebars in the bottom layer then crackwidth value should correspond to 2 no. of rebars. Shouldn't it?

  • Hi

    it is not always 2 rebars used. The Number of rebars used are depend on the width of the beam. More the width higher number of rebars assumed.

    As rightly said by you, in both the cases crack-width is satisfied with provided reinforcement. In any case the final Crackwidth is checked against the final reinforcement provided in the beam which includes the number of rebars and diameters. So, if beam is passed it will always show the pass in crack-width.

    As a software we have a internal logic check whether beam is passed for higher diameter with available rebar numbers. this is just to check that if any case if beam fails for higher diameter with maximum reinforcement (total Ast) it should be reported as failed. This is just performed to avoid multiple iterations in the design as software.

    after performing this, we always check the Crackwidth for the final reinforcement arrangement . if it fails we increase the Ast or diameter to satisfy the Crackwidth check. So  user will never get the incorrect design.

    The issue here , it is not optimizing the reinforcement for available rebars from user. Higher the numbers lesser would be the crack-width. This is caused the issue as final detailing is done with rebars (lesser c/c spacing)

    Hope this clarifies your doubt.