RAM Frame Diaphragm Stiffness Clarification
I am working on a structure that has a flooring system of 3/4" concrete board spanning between cold-form metal joists at 16" O.C. The joists span up to 20' between wide-flange moment and braced frames. In an effort to simplify the modeling for this multi-story, large structure that is changing through design, I have omitted the joists and spanned the floor in the direction of the joists. My problem is that the floor system is being analyzed as semi-rigid, and the out of plane (vertical) deflections for lateral wind and seismic loads have been very large, 25" - 30". One solution is to model the joists as lateral members, but this will be very time consuming. Is it possible to make this deflection more realistic? I looked into the "Story Diaphragm" option in RAM Frame that includes out of plan stiffness for semi-rigid diaphragms with one-way decks for lateral and gravity load cases, and while this creates the result I expected, I am not sure what the program is doing since the span is still 20' and there are no gravity members joists that I would expect to be able to improve the results to 1/2" of vertical movement. A step that I have considered is using stiffness modifiers to increase the out of plan stiffness, but I am not sure that will lead to the desired outcome and how that may affect other results.
Parents Reply
  • Let me illustrate with an example.
    Double cantilever structure with loads applied along the edge. Slab is 2-way but behavior is one way due to wall supports.
    1. Using full stiffness for the slab and knife supports for the walls, delta Z at end of cantilever = 0.615"
    2. Using a modified deck with 0.25 out of plane factor:
    delta z = 2.42" (4 times as much, as expected).
    I could have used 0.25 factors in the M Stiffness Modifier section anch achieved the same thing.
    3. using the original deck, but with the out-of-plane stiffness ignored in the Ram Frame criteria:
    delta z = 300,307", ~500,000 times as much. At this point the deflections are so large that some of the assumptions for finite element analysis are not entirely valid, but it makes no significant difference to the the wall forces, reactions, etc. at least for a flat diaphragm.
    Here's my file if you want to try other tests.
    Diaphragm_deflection_check_v1703.zip