I cant seem to find the error causing this warning: *WARNING- NO MEMBERS LOADED FOR A WIND LOAD GENERATION. I have a similar wind load in the opposite direction (Windward) but it didnt caused an error. I have this type of warning 4 times in my wind load combinations.
Please see attached file for reference.
Thanks.SUPERSTRUCTURE.STD
It can clearly be seen that some panels do not have any wind load generated in Load Cases 12 and 13. This happens because the ranges are not defined correctly. I.e., as per the screenshot below, Z Range has a maximum value entered as 7 m. This is not correct, as the outer edge of this wall is at 9.5 m. So if you change value from 7 to 9.5 the wind load should be generated fine. Similarly all other ranges needs to be reviewed and modified accordingly.
Sorry, forgot to add this photo. The concrete hollow block wall (green highlight) while the railings are in red highlight. This is same for ground floor.
Thanks.
Does this mean that you do not want to generate wind load on this members? In that case, you can avoid wind load generation on the red members by adjusting the Y range so that it would not cover the coordinates of red members.