RAM Connection 13.5 Panel Zone Shear

I have some steel Intermediate Moment Frames (IMF) that I'm designing the moment connection for.  I've run a Smart DW connection in both version 13.4 and 13.5.  Version 13.4 appears to correctly calculate the panel zone shear in accordance with AISC 341-16 Section E2.6e.  Version 13.5 appears to incorrectly include the plastic moment strength of the attached beams for both IMF and SMF where it should only consider Mp for SMFs.  Has this been corrected in 13.6 or 13.7 (I didn't see it listed in the resolved issues).  

Parents Reply
  • I took a second look at the referenced work item, but there was not actually a change made. The note indicates that it's working as designed and says, "RAM Connection seismic provisions follows “Prequalified Connections for Special and Intermediate Steel Moment Frames for Seismic Applications”, where are described the design requirements for the mentioned frames (Table 2.1.). The user model, configured as a reduced beam section, follows Chapter 5 provisions. Where specifically in Step 5 is described the calculation that RAM Connection follow for both frame systems. The application is working as it was designed."  Let me know if that does not sound correct to you.  