Live load reduction parameter

Ram Concept allows users to select the code for live load reduction. I selected IBC 2018. The slab longitudinal and latitude strip trib areas were approx. 400 sq ft. each. Based on live load reduction formula, since the trib area times Kll factor was less than 450 sq ft for a two-way slab, there was no live load reduction performed. However, since I had selected IBC 2018, I was hoping Ram concept would also look at the alternate live load reduction formula where reduction for slab live load is permitted if the slab trib area is more than 150 sq ft.  I did double check that the live load that was applied, was applied under reducible live load section only. How can I make Ram Concept apply the alternate live load reduction formula? Thanks!  