RAM Concept - Program Shear Reinforcement (2-way slab)

I'm modeling/designing a 2-way transfer slab for a concrete podium building in RAM Concept and the program is adding one-way shear reinforcement around the columns. I was reviewing an audit of the cross section and noticed the following:

  1. ɸVc > Vu
  2. The audit reads "No stirrups required"

Why is the program adding shear reinforcement if the audit indicates they are unnecessary? Is there a setting I can check/update to avoid having the unnecessary shear stirrups added to the slab?

Thanks!

Parents Reply
  • Seth, 

    I'm working on this project with Brinn, and we did review the other design passes to verify. The "controlling criteria" pointed us to a strength provision in the code so we dug into the strength design passes and found what Brinn posted above. We also found the article you linked prior to reaching out and went through each of those potential issues (checking the effective depth, running hand calcs on the one-way-shear, etc). 

    One item we could not reconcile was the effective width of the section taken for shear. It didn't match any ACI calc, column strip width, or design strip width that we could point to to make sense of it. Even with the width presented, the PhiVc was still > Vu so we doubt that's our problem, but it may point us towards another solution. 

    Thank you again for your time. 

Children