RAM Concept - Program Shear Reinforcement (2-way slab)

I'm modeling/designing a 2-way transfer slab for a concrete podium building in RAM Concept and the program is adding one-way shear reinforcement around the columns. I was reviewing an audit of the cross section and noticed the following:

  1. ɸVc > Vu
  2. The audit reads "No stirrups required"

Why is the program adding shear reinforcement if the audit indicates they are unnecessary? Is there a setting I can check/update to avoid having the unnecessary shear stirrups added to the slab?

Thanks!

Parents Reply
  • Seth, 

    Thank you this was helpful but it's brought up a couple more questions. 

    1. Why is the slab shear being designed with the Chapter 9 BEAMS code provisions? We would assume that 8.5.1.1 (c) governs for two-way slabs. Even table 9.6.3.1 you refernced provides exceptions for beams that behave more like slabs. 

    2. The bw used for the shear sections in the 2C audit seems to be the column strip width, but the shear load appears to be higher than we would expect for just that section. Does CONCEPT redistribute the shear for the design strip or is this just a function of the finite element design? Would modelling the design strip as "Full Width" instead of "Code Slab" alleviate this distribution? In either case, the shear is averaged over the cross section, but full-width design strips would seem to be more in-step with 8.5.3.1.1. 

    Thank you

Children