I am running a model in the Ram SS Concrete module and getting a few errors with the moment magnification factor exceeding 1.4. When I attempt to back-calculate the results the program is getting, I am not getting the same numbers. So my question here is two-fold:
1. Why aren't the results more transparent with its calculations of Cm, delta, beta, and Pc?
2. Why do my hand-calculated results not match the program results? Cm seems slightly off, and even if I use the program-calculated Cm to calculate delta, I don't get the same delta value. Is there a different equation being used than what ACI lists?
I see the problem with the Cm factor in this case. The program is incorrectly using the ratio of the major axis moments not the minor axis moments in the calculation of Cm associated with M1 and M2 minor. It's a reported defect already fixed for our next release (Re: Defect 813994: Cm factor and end moments calc for minor axis columns)
Answer Verified By: Brad Geyer
Thanks Seth. The Cm factor was my initial thought when I calculated the two moment ratios in my screenshot.
Regarding the 0.65Pn=Pu: That makes sense... but this all comes full circle about being more clear on the results output. I don't think you should have to read the manual to understand results output - plans examiners also need to decipher these pages without the manual. It seems "Dem/Cap" or even "demand/capacity" would be more clear than Ld/Cap because Ld is commonly used as a distance in column design. It would also be clearer if 0.65 used here was clarified as Φc, after a calculation showing that the maximum axial load is within compression-controlled strain limits.
Just my two cents
Hi Seth. Any idea when this update is happening? Quite the headache, as I am in the middle of fleshing out column sizes for an architect.