Ram Concept PT Slab Gross Bottom Stress

Hello,

My RAM Concept Model is showing a failure at slab midspans in the Design Status: Status Plan. However, when I audit the cross section the Final Check for ACI 318-14 Service Designer Section Analysis says No Failures. 

For example, the attached screenshot shows the Audit of 24C-2, section 6 stating No Failures, but the Gross Bottom Stress max demand is 347.3psi while the max capacity is 158.5psi.

Where did the 158.5psi max capacity come from? The RAM failure in the Status Plan references ACI Sections 8.3.4.1/24.5.2.1. Per Table 24.5.2.1, our two-way PT slab should be analyzed as Class U with ft </= 6*SQRT(f'c). Our f'c = 6280psi, so the max capacity should be 475psi. We are analyzing an existing PT slab that was constructed in 2018. I've also uploaded the RAM Concept Model through the Secure File Upload for reference.

Thanks