MODELLING ERROR..CHECK COLUMN DIMENSIONS AND CLEAR DISTANCE at SFA

Error at STAAD Foundation Advanced. Please help me identify the cause. Thank you.
Tagaytay Vacation House-r9_Foundation_foundation.sfa

Parents
  • Did you see this error message in the output pane:

    It is because the column positions do not look right. Supports 8 and 10096 are separated by just 200 mm while the columns at those locations are 304.8 mm in size.

    Another modification needed:

    Load cases 1 to 15 must be removed form the "Selected Load Cases" list. meaning, the footing should be solved only for the combinations. To understand why, see the answer posted at the following discussion by Kris on September 3 2021 at 11:25 PM

     Large Footing Design 



Reply
  • Did you see this error message in the output pane:

    It is because the column positions do not look right. Supports 8 and 10096 are separated by just 200 mm while the columns at those locations are 304.8 mm in size.

    Another modification needed:

    Load cases 1 to 15 must be removed form the "Selected Load Cases" list. meaning, the footing should be solved only for the combinations. To understand why, see the answer posted at the following discussion by Kris on September 3 2021 at 11:25 PM

     Large Footing Design 