When you place a load over a given area and then add an additional load that overlaps it, does STAAD consider the loads additive or choose one or the other?I'm thinking specifically if you define a live floor load, of say 40 psf, over an entire floor at an elevation, and then have a group defined for laundry within the confines of a smaller area (at the same elevation) with a live load of 150 psf.Will STAAD choose one over the other based on the way they are defined in the command file or is the load 190 psf?Thanks,
Sam
STAAD will consider both the loads i.e. for your example it will be 190psf.
Answer Verified By: Sam Leimer