When the temperature load apply model seems abnormal. What is the reason
2703.std
To attached the summary table with temperature load (Image1),without temperature load (Image2).
Image 1
Image 2
Temperature load can lead to high support reactions and that is expected. What support reactions due to temperature load would you expect?
Thanks for your reply.
Does temperature load applied is correct or not?
If applied load is correct, then why more reaction for temperature load combination.
without temp load, reaction is around 30kN,
when temp load is applied, then reaction shot up to 107kN.
does temperature load alone increase this much reaction to support is my doubt?
please guide me on this issue.../
00.std
When the temperature load apply model seems abnormal. What is the reason.
I don't see any issues in the temperature load application. Yes, the temperature load can lead to quite high support reactions due to deformations induced between the fixed supported.
Ok thanks for your reply.I have revised temperature load calculation as below image.pl review and give your comments
The calculation of temperature loads is explained here:
communities.bentley.com/.../temperature-loading
or here:
communities.bentley.com/.../temperature-load-on-plate-element
As yous see, to calculate the load due to temperature you must know what the temperature at the stress-free condition is. So what is that temperature at your case?
ok thanks, i have used above links to calculated temperature load.
temperature at the stress-free condition for me is 28.15 degree C.../
OK, so in that case you need to provide your calculated f1 values in your model instead of 33 degrees which is currently used.
yes correct, now i changed model with temperature load with two cases as T1 and T2.
as soon in below image, pl review
Yes, this looks reasonable.