RCDC_Beam_design

1. Whenever beam is split because of node insertion, beams with smaller length are failing in shear-Tcmax (Beam 42, 36 in below figure).

How to modify these members to pass the section without failure??

 O22064-C-FB-07-DC-0001_B.std

2. Also when there is discontinuity (Beam 17, 18) "sway" condition is becomes governing.

Please find the staad, RCDC files(secure file upload) and help me how to modify my structure of beam dimensions to avoid failure??

Uploaded file names

Parents Reply
  • Dear Sir,

    As per sketch shared by you, the column present in between these beams. refer snap,

    if you design these small length beams, it might fail due to sway shear check. As this small beam is continuous beam of larger span beam, it might have attracted the more moment at right top location. Higher reinforcement with lesser span will create more shear force in the beam.

    refer above snap from IS 13920-2016 (similar approach in ACI codes). Lesser the span higher would be the shear force.


    Suggestion to pass the beam,

    1. release Major axis moment at the end short beam and design it as Non-ducrtile

    2. Increase concrete grade till is pass

    3. convert two columns in to one long column and avoid small beam