Can Soft Storey Check result be Ignored
I am designing an existing building being retrofitted for vertical brace, I added the concrete pedestal in the  model just to see the maximum node displacement result.  Due to this, STAAD output now show an extreme soft storey for pedestal location.  Reading questions related to soft storey check, the advice is usually to upsize column or add bracing/shear wall however I cannot do that in this situation.  Please advise if I can ignore the extreme soft storey result at Elev.3.20M in my STAAD Output or remove the concrete pedestal from my analysis altogether instead.
STAAD SPACE
START JOB INFORMATION
ENGINEER DATE 09-Aug-22
END JOB INFORMATION
INPUT WIDTH 79
UNIT METER KN
JOINT COORDINATES
1 0 3.2 0; 2 9.35 3.2 0; 3 18.35 3.2 0; 4 27.7 3.2 0; 5 0 3.2 5.7;
6 9.35 3.2 5.7; 7 18.35 3.2 5.7; 8 27.7 3.2 5.7; 9 0 3.2 11.7;
10 9.35 3.2 11.7; 11 18.35 3.2 11.7; 12 27.7 3.2 11.7; 13 0 3.2 17.7;
14 9.35 3.2 17.7; 15 18.35 3.2 17.7; 16 27.7 3.2 17.7; 17 0 3.2 23.7;
18 9.35 3.2 23.7; 19 18.35 3.2 23.7; 20 27.7 3.2 23.7; 21 0 3.2 29.45;
22 9.35 3.2 29.45; 23 18.35 3.2 29.45; 24 27.7 3.2 29.45; 25 0 3.2 40.35;
26 9.35 3.2 40.35; 27 18.35 3.2 40.35; 28 27.7 3.2 40.35; 1000 0 6.55 0;
1001 9.35 6.55 0; 1002 18.35 6.55 0; 1003 27.7 6.55 0; 1004 0 6.55 5.7;
1005 27.7 6.55 5.7; 1006 0 6.55 11.7; 1009 27.7 6.55 11.7; 1010 0 6.55 17.7;
1011 27.7 6.55 17.7; 1012 0 6.55 23.7; 1015 27.7 6.55 23.7; 1016 0 6.55 29.45;
1017 27.7 6.55 29.45; 1018 0 6.55 40.35; 1019 9.35 6.55 40.35;
1020 18.35 6.55 40.35; 1021 27.7 6.55 40.35; 1022 25.4144 6.55 0;
1023 25.4144 6.55 11.7; 1024 25.4144 6.55 23.7; 1025 0 6.55 34.9;
1026 0 6.55 14.7; 1027 0 6.55 20.7; 1028 0 6.55 26.575; 1029 27.7 6.55 14.7;
1030 27.7 6.55 20.7; 1031 27.7 6.55 26.575; 1032 27.7 6.55 34.9;
1033 25.4144 6.55 29.45; 1034 4.675 6.55 40.35; 1035 13.85 6.55 40.35;
1036 23.025 6.55 40.35; 1045 25.4144 6.55 5.7; 1046 25.4144 6.55 17.7;
2000 0 10.785 0; 2001 9.35 10.785 0; 2002 18.35 10.785 0; 2003 27.7 10.785 0;
2004 0 10.785 5.7; 2005 9.35 10.785 5.7; 2006 18.35 10.785 5.7;
2007 27.7 10.785 5.7; 2008 0 10.785 11.7; 2009 9.35 10.785 11.7;
2010 18.35 10.785 11.7; 2011 27.7 10.785 11.7; 2012 0 10.785 17.7;
2013 9.35 10.785 17.7; 2014 18.35 10.785 17.7; 2015 27.7 10.785 17.7;
2016 0 10.785 23.7; 2017 9.35 10.785 23.7; 2018 18.35 10.785 23.7;
2019 27.7 10.785 23.7; 2020 0 10.785 29.45; 2021 9.35 10.785 29.45;
2022 18.35 10.785 29.45; 2023 27.7 10.785 29.45; 2024 0 10.785 14.7;
2025 0 10.785 20.7; 2026 0 10.785 26.575; 2027 27.7 10.785 26.575;
2028 4.675 10.785 23.7; 2029 13.85 10.785 23.7; 2030 4.675 10.785 11.7;
2031 13.85 10.785 11.7; 2032 13.85 10.785 0; 2037 18.35 10.785 2.85;
2038 18.35 10.785 8.7; 2039 27.7 10.785 2.85; 2040 27.7 10.785 8.7;
2041 9.35 10.785 2.85; 2046 9.35 10.785 8.7; 2047 9.35 10.785 14.7;
2048 18.35 10.785 14.7; 2049 27.7 10.785 14.7; 2054 9.35 10.785 19.7;
2055 9.35 10.785 21.7; 2060 18.35 10.785 20.7; 2061 27.7 10.785 20.7;
2062 9.35 10.785 20.7; 2065 18.35 10.785 26.575; 2066 9.35 10.785 26.575;
2067 23.025 10.785 0; 2068 13.85 10.785 5.7; 2069 23.025 10.785 5.7;
2070 23.025 10.785 2.85; 2071 13.85 10.785 2.85; 2072 4.675 10.785 0;
2075 4.675 10.785 5.7; 2078 23.025 10.785 11.7; 2079 23.025 10.785 8.7;
2080 13.85 10.785 8.7; 2081 4.675 10.785 17.7; 2082 13.85 10.785 17.7;
2083 23.025 10.785 17.7; 2084 13.85 10.785 14.7; 2085 23.025 10.785 14.7;
2088 13.85 10.785 29.45; 2089 23.025 10.785 29.45; 2090 23.025 10.785 23.7;
2091 13.85 10.785 20.7; 2092 23.025 10.785 20.7; 2093 13.85 10.785 26.575;
2094 23.025 10.785 26.575; 2095 4.675 10.785 29.45; 2100 5.679 10.785 0;
2103 5.679 10.785 5.7; 2104 4.675 10.785 7.261; 2105 5.679 10.785 7.261;
2106 9.35 10.785 7.261; 2107 9.35 10.785 4.249; 2108 5.679 10.785 4.249;
2109 4.675 10.785 4.249; 2110 0 10.785 4.249; 2111 0 10.785 11.5266;
2112 4.675 10.785 11.5266; 2113 13.2615 10.785 0; 2114 13.2615 10.785 5.7;
2115 13.2615 10.785 2.85; 2116 18.35 10.785 7.261; 2117 13.2615 10.785 7.261;
2118 13.2615 10.785 4.249; 2119 14.992 10.785 5.7; 2120 14.992 10.785 2.85;
2121 18.35 10.785 6.741; 2122 14.992 10.785 6.741; 2123 14.2655 10.785 0;
2124 14.2655 10.785 5.7; 2125 14.2655 10.785 2.85; 2126 14.2655 10.785 7.261;
2127 14.992 10.785 7.261; 2128 9.35 10.785 11.5266; 2129 12.119 10.785 11.7;
2130 12.119 10.785 14.7; 2131 13.123 10.785 11.7; 2132 13.123 10.785 14.7;
2133 14.127 10.785 11.7; 2134 14.127 10.785 14.7; 2135 15.131 10.785 11.7;
2136 15.131 10.785 14.7; 2137 12.119 10.785 12.7; 2138 13.123 10.785 12.7;
2139 14.127 10.785 12.7; 2140 15.131 10.785 12.7; 2141 12.119 10.785 13.7;
2142 13.123 10.785 13.7; 2143 14.127 10.785 13.7; 2144 15.131 10.785 13.7;
2145 14.4039 10.785 20.7; 2146 17.6577 10.785 20.7; 2147 14.4039 10.785 26.575;
2148 17.6577 10.785 26.575; 2149 17.6577 10.785 23.7; 2150 14.4039 10.785 23.7;
2151 14.4039 10.785 21.3936; 2152 17.6577 10.785 21.3936;
2153 14.4039 10.785 25.1202; 2154 17.6577 10.785 25.1202;
2155 26.107 10.785 23.7; 2156 26.107 10.785 26.575; 2157 27.111 10.785 23.7;
2158 27.111 10.785 26.575; 2159 26.107 10.785 24.046;
2160 27.111 10.785 24.046; 2161 26.107 10.785 25.951;
2162 27.111 10.785 25.951; 2163 19.32 10.785 11.7; 2164 19.32 10.785 17.7;
2165 19.32 10.785 14.7; 2166 22.575 10.785 11.7; 2167 22.575 10.785 17.7;
2168 22.575 10.785 14.7; 2169 19.32 10.785 15.493; 2170 22.575 10.785 15.493;
3000 0 12.95 29.45; 3001 9.35 12.95 29.45; 3002 18.35 12.95 29.45;
3003 27.7 12.95 29.45; 3004 0 12.95 40.35; 3005 9.35 12.95 40.35;
3006 18.35 12.95 40.35; 3007 27.7 12.95 40.35; 3008 0 12.95 34.9;
3009 27.7 12.95 34.9; 3010 4.675 12.95 40.35; 3011 13.85 12.95 40.35;
3012 23.025 12.95 40.35; 3014 9.35 12.95 34.9; 3015 18.35 12.95 34.9;
3016 0.00863946 12.95 29.455; 3017 9.35855 12.95 34.9052;
3018 9.35855 12.95 29.4552; 3019 18.3586 12.95 34.905;
3020 0.00863946 12.95 34.895; 3021 0.00863947 12.95 40.345;
3022 9.35855 12.95 34.8948; 3023 9.35855 12.95 40.3448;
3024 18.3586 12.95 34.895; 3025 18.3586 12.95 40.345;
3026 0.00863947 12.95 34.905; 3027 18.3586 12.95 29.455;
3028 4.675 12.95 37.625; 3029 4.675 12.95 32.175; 3030 13.85 12.95 37.625;
3031 13.85 12.95 32.175; 3032 23.025 12.95 37.625; 3033 23.025 12.95 32.175;
3038 0 10.785 2.85; 3039 4.675 10.785 2.85; 3040 5.679 10.785 2.85;
3041 0 10.785 8.7; 3042 4.675 10.785 8.7; 3043 4.675 10.785 14.7;
3044 4.675 10.785 26.575; 3045 4.675 10.785 20.7; 3046 13.85 10.785 7.261;
3047 4.675 6.55 0; 3048 13.85 6.55 0; 3049 23.025 6.55 0; 3050 27.7 6.55 8.7;
3051 0 0 0; 3052 9.35 0 0; 3053 18.35 0 0; 3054 27.7 0 0; 3055 0 0 5.7;
3056 9.35 0 5.7; 3057 18.35 0 5.7; 3058 27.7 0 5.7; 3059 0 0 11.7;
3060 9.35 0 11.7; 3061 18.35 0 11.7; 3062 27.7 0 11.7; 3063 0 0 17.7;
3064 9.35 0 17.7; 3065 18.35 0 17.7; 3066 27.7 0 17.7; 3067 0 0 23.7;
3068 9.35 0 23.7; 3069 18.35 0 23.7; 3070 27.7 0 23.7; 3071 0 0 29.45;
3072 9.35 0 29.45; 3073 18.35 0 29.45; 3074 27.7 0 29.45; 3075 0 0 40.35;
3076 9.35 0 40.35; 3077 18.35 0 40.35; 3078 27.7 0 40.35;
MEMBER INCIDENCES
100 1 1000; 101 2 1001; 102 3 1002; 103 4 1003; 104 5 1004; 105 9 1006;
106 13 1010; 107 17 1012; 108 21 1016; 109 25 1018; 110 6 2005; 111 10 2009;
112 14 2013; 113 18 2017; 114 26 1019; 115 7 2006; 116 11 2010; 117 15 2014;
118 19 2018; 119 27 1020; 120 8 1005; 121 12 1009; 122 16 1011; 123 20 1015;
124 24 1017; 125 28 1021; 126 9 1026; 127 13 1027; 128 17 1028; 129 21 1025;
130 25 1025; 131 21 1028; 132 17 1027; 133 13 1026; 134 12 1029; 135 16 1030;
136 20 1031; 137 24 1032; 138 28 1032; 139 24 1031; 140 20 1030; 141 16 1029;
142 25 1034; 143 26 1035; 144 27 1036; 145 28 1036; 146 27 1035; 147 26 1034;
164 22 2021; 165 23 2022; 200 1000 2000; 201 1001 2001; 202 1002 2002;
203 1003 2003; 204 1004 2004; 205 1005 2007; 206 1006 2008; 209 1009 2011;
210 1010 2012; 211 1011 2015; 212 1012 2016; 215 1015 2019; 216 1016 2020;
217 1017 2023; 218 1006 2024; 219 1010 2025; 220 1012 2026; 221 1016 2026;
222 1012 2025; 223 1010 2024; 224 1015 2027; 225 1017 2027; 300 2020 3000;
301 2021 3001; 302 2022 3002; 303 2023 3003; 304 1018 3004; 305 1019 3005;
306 1020 3006; 307 1021 3007; 308 1016 3008; 309 1018 3008; 310 1017 3009;
311 1021 3009; 312 1018 3010; 313 1019 3011; 314 1020 3012; 315 1021 3012;
316 1020 3011; 317 1019 3010; 1000 1000 3047; 1001 1001 3048; 1002 1002 3049;
1003 1000 1004; 1004 1003 1005; 1005 1004 1006; 1006 1005 3050; 1007 1006 1026;
1008 1009 1029; 1009 1010 1027; 1010 1011 1030; 1011 1012 1028; 1012 1015 1031;
1013 1016 1025; 1014 1017 1032; 1015 1018 1034; 1016 1019 1035; 1017 1020 1036;
1024 1022 1003; 1025 1023 1009; 1026 1024 1015; 1027 1022 1045; 1028 1023 1046;
1029 1024 1033; 1030 1025 1018; 1031 1026 1010; 1032 1027 1012; 1033 1028 1016;
1034 1029 1011; 1035 1030 1015; 1036 1031 1017; 1037 1032 1021; 1038 1033 1017;
1039 1034 1019; 1040 1035 1020; 1041 1036 1021; 1050 1045 1023; 1051 1046 1024;
1052 1045 1005; 1053 1046 1011; 2000 2000 2072; 2001 2001 2113; 2002 2002 2067;
2003 2000 3038; 2004 2004 3041; 2005 2008 2024; 2006 2012 2025; 2007 2016 2026;
2008 2001 2041; 2009 2005 2106; 2010 2009 2047; 2011 2013 2054; 2012 2017 2066;
2013 2002 2037; 2014 2006 2121; 2015 2010 2048; 2016 2014 2060; 2017 2018 2065;
2018 2003 2039; 2019 2007 2040; 2020 2011 2049; 2021 2015 2061; 2022 2019 2027;
2023 2020 2095; 2024 2021 2088; 2025 2022 2089; 2028 2026 2020; 2029 2027 2023;
2030 2016 2028; 2031 2017 2029; 2032 2018 2090; 2033 2028 2017; 2034 2029 2150;
2035 2008 2030; 2036 2009 2129; 2037 2010 2163; 2038 2030 2009; 2039 2031 2133;
2040 2032 2123; 2044 2107 2041; 2047 2004 2075; 2048 2005 2114; 2049 2006 2069;
2050 2012 2081; 2051 2013 2082; 2052 2014 2164; 2053 2037 2006; 2054 2038 2010;
2055 2039 2007; 2056 2040 2011; 2057 2037 2070; 2058 2038 2079; 2060 2041 2115;
2063 2046 2106; 2064 2128 2046; 2068 2046 2080; 2069 2047 2013; 2070 2048 2014;
2071 2049 2015; 2072 2047 2130; 2073 2048 2165; 2080 2054 2062; 2081 2055 2017;
2083 2021 2066; 2088 2060 2018; 2089 2061 2019; 2090 2062 2055; 2091 2062 2091;
2092 2060 2092; 2097 2065 2022; 2099 2066 2093; 2100 2065 2094; 2101 2067 2003;
2102 2068 2124; 2103 2069 2007; 2104 2070 2039; 2105 2071 2125; 2106 2032 2071;
2107 2071 2068; 2108 2067 2070; 2109 2070 2069; 2110 2072 2100; 2113 2075 2103;
2114 2072 3039; 2118 2104 3042; 2119 2078 2011; 2120 2079 2040; 2121 2080 2038;
2122 2080 2031; 2123 2079 2078; 2124 2081 2013; 2125 2082 2014; 2126 2083 2015;
2127 2084 2134; 2128 2085 2049; 2131 2030 3043; 2133 2084 2082; 2134 2085 2083;
2135 2088 2022; 2136 2089 2023; 2137 2090 2155; 2138 2091 2145; 2139 2092 2061;
2140 2093 2147; 2141 2094 2156; 2142 2091 2029; 2143 2092 2090; 2144 2093 2088;
2145 2094 2089; 2146 2095 2021; 2152 2028 3044; 2154 2100 2001; 2156 2100 3040;
2159 2103 2005; 2161 2075 2104; 2162 2103 2105; 2163 2104 2105; 2164 2105 2106;
2166 2107 2005; 2167 2108 2103; 2168 2108 2107; 2169 2109 2075; 2170 2110 2004;
2171 2110 2109; 2173 2111 2008; 2174 2111 2112; 2176 2113 2032; 2177 2114 2068;
2178 2115 2071; 2179 2113 2115; 2180 2115 2118; 2181 2116 2038; 2182 2106 2117;
2183 2117 3046; 2184 2114 2117; 2185 2118 2114; 2186 2107 2118; 2187 2119 2006;
2188 2120 2037; 2189 2120 2119; 2190 2121 2116; 2191 2119 2122; 2192 2122 2121;
2193 2123 2002; 2194 2124 2119; 2195 2125 2120; 2196 2126 2127; 2197 2123 2125;
2198 2125 2124; 2199 2124 2126; 2200 2127 2116; 2201 2122 2127; 2203 2128 2009;
2204 2112 2128; 2205 2026 3044; 2206 2129 2131; 2207 2130 2132; 2208 2129 2137;
2209 2131 2031; 2210 2132 2084; 2211 2131 2138; 2212 2133 2135; 2213 2134 2136;
2214 2135 2010; 2215 2136 2048; 2216 2133 2139; 2217 2135 2140; 2218 2137 2141;
2219 2138 2142; 2220 2139 2143; 2221 2140 2144; 2222 2141 2130; 2223 2142 2132;
2224 2143 2134; 2225 2144 2136; 2226 2137 2138; 2227 2141 2142; 2228 2139 2140;
2229 2143 2144; 2230 2145 2146; 2231 2146 2060; 2232 2147 2148; 2233 2145 2151;
2234 2148 2065; 2235 2146 2152; 2236 2149 2018; 2237 2150 2149; 2238 2150 2153;
2239 2149 2154; 2240 2151 2150; 2241 2152 2149; 2242 2151 2152; 2243 2153 2147;
2244 2154 2148; 2245 2153 2154; 2246 2155 2157; 2247 2156 2158; 2248 2157 2019;
2249 2158 2027; 2250 2155 2159; 2251 2157 2160; 2252 2159 2161; 2253 2160 2162;
2254 2161 2156; 2255 2162 2158; 2256 2159 2160; 2257 2161 2162; 2258 2163 2166;
2259 2164 2167; 2260 2165 2168; 2261 2166 2078; 2262 2167 2083; 2263 2168 2085;
2264 2163 2165; 2265 2165 2169; 2266 2166 2168; 2267 2168 2170; 2268 2169 2164;
2269 2170 2167; 2270 2169 2170; 3000 3000 3001; 3001 3001 3002; 3002 3002 3003;
3003 3000 3008; 3004 3003 3009; 3005 3001 3014; 3006 3002 3015; 3007 3004 3010;
3008 3005 3011; 3009 3006 3012; 3010 3008 3004; 3011 3009 3007; 3012 3010 3005;
3013 3011 3006; 3014 3012 3007; 3017 3014 3005; 3018 3015 3006; 3019 3000 3016;
3020 3014 3017; 3021 3001 3018; 3022 3015 3019; 3023 3008 3020; 3024 3004 3021;
3025 3014 3022; 3026 3005 3023; 3027 3015 3024; 3028 3006 3025; 3029 3008 3026;
3030 3002 3027; 3031 3016 3029; 3032 3017 3030; 3033 3018 3031; 3034 3019 3032;
3035 3020 3029; 3036 3021 3028; 3037 3022 3031; 3038 3023 3030; 3039 3024 3033;
3040 3025 3032; 3042 3027 3033; 3043 3028 3014; 3044 3029 3014; 3045 3030 3006;
3046 3031 3015; 3047 3032 3007; 3048 3029 3001; 3049 3031 3002; 3050 3030 3015;
3051 3033 3003; 3052 3032 3009; 3053 3033 3009; 3054 3020 3028; 3055 3028 3005;
3072 3038 2110; 3073 3038 3039; 3074 3039 2109; 3075 3040 2108; 3076 3040 2041;
3077 3039 3040; 3078 3041 2111; 3079 3041 3042; 3080 3042 2112; 3081 3042 2046;
3082 2024 2012; 3083 2024 3043; 3084 3043 2081; 3085 3043 2047; 3086 3044 2095;
3087 3044 2066; 3088 2025 3045; 3089 2081 3045; 3090 2025 2016; 3091 3045 2062;
3092 3045 2028; 3093 2068 3046; 3094 2031 2084; 3095 2082 2091; 3096 2029 2093;
3097 2069 2079; 3098 2078 2085; 3099 2083 2092; 3100 2090 2094; 3101 3046 2126;
3102 3046 2080; 3103 3047 1001; 3104 3048 1002; 3105 1 3047; 3106 2 3047;
3107 2 3048; 3108 3 3048; 3109 2112 2030; 3110 1000 2072; 3111 1001 2072;
3112 1001 2032; 3113 1002 2032; 3114 1011 2061; 3115 1015 2061; 3116 1009 2049;
3117 1011 2049; 3118 1002 2067; 3119 1003 2067; 3120 3049 1022; 3121 3 3049;
3122 4 3049; 3123 3050 1009; 3124 8 3050; 3125 12 3050; 3126 1005 2040;
3127 1009 2040; 3128 3051 1; 3129 3055 5; 3130 3059 9; 3131 3063 13;
3132 3067 17; 3133 3071 21; 3134 3075 25; 3135 3076 26; 3136 3077 27;
3137 3078 28; 3138 3074 24; 3139 3070 20; 3140 3066 16; 3141 3062 12;
3142 3058 8; 3143 3054 4; 3144 3053 3; 3145 3052 2; 3146 3072 22; 3147 3073 23;
3148 3069 19; 3149 3068 18; 3150 3064 14; 3151 3060 10; 3152 3065 15;
3153 3056 6; 3154 3057 7; 3155 3061 11; 3156 3051 3052; 3157 3052 3053;
3158 3053 3054; 3159 3055 3056; 3160 3056 3057; 3161 3057 3058; 3162 3059 3060;
3163 3060 3061; 3164 3061 3062; 3165 3063 3064; 3166 3064 3065; 3167 3065 3066;
3168 3067 3068; 3169 3068 3069; 3170 3069 3070; 3171 3071 3072; 3172 3072 3073;
3173 3073 3074; 3174 3075 3076; 3175 3076 3077; 3176 3077 3078; 3177 3051 3055;
3178 3055 3059; 3179 3059 3063; 3180 3063 3067; 3181 3067 3071; 3182 3071 3075;
3183 3052 3056; 3184 3056 3060; 3185 3060 3064; 3186 3064 3068; 3187 3068 3072;
3188 3072 3076; 3189 3053 3057; 3190 3057 3061; 3191 3061 3065; 3192 3065 3069;
3193 3069 3073; 3194 3073 3077; 3195 3054 3058; 3196 3058 3062; 3197 3062 3066;
3198 3066 3070; 3199 3070 3074; 3200 3074 3078;
START GROUP DEFINITION
FLOOR
_VIEW_DECK 1004 1006 1008 1010 1012 1024 TO 1029 1034 TO 1036 1038 -
1050 TO 1053 3123
_ROOF_DECK_165 2000 2003 TO 2012 2023 2028 2030 2033 2035 2038 2044 2047 2050 -
2063 2064 2069 2080 2081 2083 2090 2110 2113 2114 2118 2124 2131 2146 2152 -
2154 2159 2161 2166 2169 2170 2173 2203 2205 3072 TO 3074 3076 TO 3092 3109
_ROOF_DECK_125 2001 2002 2008 TO 2022 2024 2025 2029 2031 2032 2034 2036 2037 -
2039 2040 2044 2048 2049 2051 TO 2058 2060 2063 2064 2068 TO 2073 2080 2081 -
2083 2088 TO 2092 2097 2099 TO 2109 2119 TO 2123 2125 TO 2128 2133 TO 2145 -
2166 2176 TO 2178 2181 2187 2188 2190 2193 TO 2195 2203 2206 2207 2209 2210 -
2212 TO 2215 2230 TO 2232 2234 2236 2237 2246 TO 2249 2258 TO 2263 -
3093 TO 3100 3102
_SCANICO_VESSEL 2004 2118 2161 2169 TO 2171 2174 3078 3080
_OP_WT 2162 2164 2167 2168 2182 2184 TO 2186
_ROLLO_BRINE 2040 2110 2114 2156 2161 TO 2163 2167 2169 2176 2179 2180 2183 -
2184 TO 2185 2197 TO 2199 3074 3075 3101
_TUNNEL_5 2024 2025 2029 2083 2099 2100 2135 2136 2140 2141 2232 2234 2247 2249
_TUNNEL_6 2023 2028 2083 2146 2205 3087
_CARRIER_AIR 2014 2053 2188 2189 2191 2192 2238 TO 2242 2245 2258 -
2264 TO 2267 2270
_AHU 2014 2053 2188 2189 2191 2192 2238 TO 2242 2245 2258 2264 TO 2267 2270
_AIR_RECEIVER 2218 TO 2221 2226 TO 2229
_MCC 2252 2253 2256 2257
_CABLE_TRAY 2000 TO 2025 2028 TO 2040 2044 2047 TO 2058 2060 2063 2064 2068 -
2069 TO 2073 2080 2081 2083 2088 TO 2092 2097 2099 TO 2110 2113 2114 2118 -
2119 TO 2128 2131 2133 TO 2146 2152 2154 2159 2161 2166 2169 2170 2173 2176 -
2177 TO 2178 2181 2187 2188 2190 2193 TO 2195 2203 2205 TO 2207 2209 2210 -
3072 TO 3074 3076 TO 3100 3102 3109
_CATWALK 2000 TO 2025 2028 TO 2040 2044 2047 TO 2058 2060 2063 2064 -
2068 TO 2073 2080 2081 2083 2088 TO 2092 2097 2099 TO 2110 2113 2114 2118 -
_ROOF_TUNNEL 3000 TO 3014 3017 3018
MEMBER
_TRUSS 126 TO 147 218 TO 225 308 TO 317
END GROUP DEFINITION
SUPPORTS
3051 TO 3078 FIXED
MEMBER TRUSS
126 TO 147 218 TO 225 308 TO 317 3105 TO 3108 3110 TO 3119 3121 3122 3124 -
3125 TO 3127
DEFINE MATERIAL START
ISOTROPIC STEEL
E 2.05e+08
POISSON 0.3
DENSITY 76.8195
ALPHA 1.2e-05
DAMP 0.03
TYPE STEEL
STRENGTH FY 253200 FU 407800 RY 1.5 RT 1.2
ISOTROPIC DUMMY
E 2.05e+08
POISSON 0.3
ALPHA 1.2e-05
DAMP 0.03
G 7.88462e+07
TYPE STEEL
ISOTROPIC CONCRETE
E 2.17185e+07
POISSON 0.17
DENSITY 23.5616
ALPHA 1e-05
DAMP 0.05
TYPE CONCRETE
STRENGTH FCU 27579
END DEFINE MATERIAL
START USER TABLE
TABLE 1 W10X33RF.UPT
TABLE 2 W14X61RF.UPT
TABLE 3 W8X24RF.UPT
TABLE 4 W21X62RF.UPT
TABLE 5 W21X93RF.UPT
END
MEMBER PROPERTY AMERICAN
100 101 104 TO 108 164 200 201 204 206 210 212 216 300 301 TABLE ST W14X109
102 103 115 TO 118 120 TO 124 165 202 203 205 209 211 215 217 302 -
303 TABLE ST W12X72
110 TO 113 TABLE ST W14X145
109 125 304 307 TABLE ST W12X50
114 119 305 306 TABLE ST W12X53
1000 1001 1013 TO 1017 1030 1037 1039 TO 1041 3000 TO 3002 3007 TO 3009 3012 -
3013 TO 3014 3103 3104 TABLE ST W14X61
1002 1024 3120 TABLE ST W21X62
1038 TABLE ST W8X24
1004 1006 1008 1010 1034 1035 3123 TABLE ST W14X48
1012 1027 TO 1029 1036 1050 1051 TABLE ST W12X30
2013 TO 2017 2053 2054 2070 2088 2097 2181 2190 TABLE ST W21X101
3003 3004 3010 3011 TABLE ST W18X50
3005 3006 3017 3018 TABLE ST W18X55
3125 TO 3127 TABLE ST HSST7X7X0.5
2156 2162 TO 2164 2167 2168 2171 2174 2179 2180 2182 TO 2186 2189 2191 2192 -
2196 TO 2201 2204 2208 2211 2216 TO 2229 2233 2235 2238 TO 2245 2250 TO 2257 -
2264 TO 2270 3075 3101 TABLE ST W8X67
3019 TO 3040 3042 TO 3055 TABLE ST PIPE OD 0.016 ID 0
1025 1026 1052 1053 UPTABLE 3 W8X24RF
1003 1005 1007 1009 1011 1031 TO 1033 TABLE ST W10X33
2000 TO 2002 2023 2040 2101 2110 2146 2154 2176 2193 TABLE ST W27X94
2057 2058 2060 2068 2099 2100 2104 2105 2120 2121 2140 2141 2178 2188 2195 -
2205 2232 2234 2247 2249 3073 3076 3077 3079 3081 3087 3088 -
3091 TABLE ST W27X178
2008 TO 2012 2044 2047 TO 2049 2063 2064 2069 2080 2081 2083 2090 2102 2103 -
2113 2159 2166 2177 2187 2194 2203 TABLE ST W27X129
2035 2038 TABLE ST W27X146
2024 2025 2031 2032 2034 2036 2037 2039 2051 2052 2114 2118 2119 2125 2126 -
2131 2135 TO 2137 2161 2169 2206 2209 2212 2214 2236 2237 2246 2248 2258 -
2259 2261 2262 3074 3080 3084 3089 3092 3109 TABLE ST W21X57
3083 3085 TABLE ST W27X194
2018 TO 2022 2029 2055 2056 2071 TO 2073 2089 2091 2092 2127 2128 2138 2139 -
2152 2207 2210 2213 2215 2230 2231 2260 2263 3086 TABLE ST W21X68
2030 2033 2050 2124 TABLE ST W27X161
2003 TO 2007 2028 2170 2173 3072 3078 3082 3090 TABLE ST W27X102
2106 TO 2109 2122 2123 2133 2134 2142 TO 2145 3093 TO 3100 3102 TABLE ST W10X19
3134 TO 3137 PRIS YD 0.5 ZD 0.5
3138 TO 3144 3147 3148 3152 3154 3155 PRIS YD 0.55 ZD 0.55
3128 TO 3133 3145 3146 PRIS YD 0.6 ZD 0.6
3149 TO 3151 3153 PRIS YD 0.65 ZD 0.65
3156 TO 3200 PRIS YD 0.9 ZD 0.55
CONSTANTS
BETA 90 MEMB 100 TO 125 164 165 200 TO 206 209 TO 212 215 TO 217 300 TO 307
MATERIAL STEEL MEMB 100 TO 147 164 165 200 TO 206 209 TO 212 215 TO 225 300 -
301 TO 317 1000 TO 1017 1024 TO 1041 1050 TO 1053 2000 TO 2025 2028 TO 2040 -
2044 2047 TO 2058 2060 2063 2064 2068 TO 2073 2080 2081 2083 2088 TO 2092 -
2097 2099 TO 2110 2113 2114 2118 TO 2128 2131 2133 TO 2146 2152 2154 2159 -
2161 2166 2169 2170 2173 2176 TO 2178 2181 2187 2188 2190 2193 TO 2195 2203 -
2205 TO 2207 2209 2210 2212 TO 2215 2230 TO 2232 2234 2236 2237 2246 TO 2249 -
2258 TO 2263 3000 TO 3014 3017 3018 3072 TO 3074 3076 TO 3100 3102 TO 3127
MATERIAL DUMMY MEMB 2156 2162 TO 2164 2167 2168 2171 2174 2179 2180 -
2182 TO 2186 2189 2191 2192 2196 TO 2201 2204 2208 2211 2216 TO 2229 2233 -
2235 2238 TO 2245 2250 TO 2257 2264 TO 2270 3019 TO 3040 3042 TO 3055 3075 -
3101
MATERIAL CONCRETE MEMB 3128 TO 3200
MEMBER RELEASE
1000 TO 1002 1006 TO 1017 2000 TO 2002 2005 TO 2007 2019 TO 2022 2057 2058 -
2060 2068 2072 2073 2091 2092 2099 2100 2106 TO 2109 2114 2122 2123 2131 -
2133 2134 2142 TO 2145 2152 2161 2205 3003 3004 3007 TO 3009 3073 3074 3079 -
3080 3083 3084 3086 3088 3089 3092 TO 3100 START MPY 0.99 MPZ 0.99
1024 1030 TO 1037 1039 TO 1041 2028 2029 2056 2071 2089 2101 2104 -
2106 TO 2109 2114 2118 2120 TO 2123 2128 2131 2133 2134 2139 2142 TO 2145 -
2152 2154 2169 2188 2193 2215 2231 2234 2249 3010 TO 3014 3076 3081 3082 -
3084 TO 3087 3089 TO 3092 3094 TO 3100 3102 TO 3104 3109 -
3123 END MPY 0.99 MPZ 0.99
DEFINE REFERENCE LOADS
LOAD R1 LOADTYPE Dead  TITLE DL1
SELFWEIGHT Y -1
LOAD R2 LOADTYPE Dead  TITLE DL2
ONEWAY LOAD
_VIEW_DECK ONE -4.81 GY
_ROOF_DECK_165 ONE -7.473 GY
_ROOF_DECK_125 ONE -7.164 GY
FLOOR LOAD
_SCANICO_VESSEL FLOAD -1.605 GY
_OP_WT FLOAD -2.098 GY
_ROLLO_BRINE FLOAD -16.143 GY
_TUNNEL_5 FLOAD -2.587 GY
_TUNNEL_6 FLOAD -4.062 GY
_CARRIER_AIR FLOAD -0.629 GY
_AHU FLOAD -1.258 GY
_AIR_RECEIVER FLOAD -4.884 GY
_MCC FLOAD -2.564 GY
ONEWAY LOAD
_CABLE_TRAY ONE -0.018 GY
MEMBER LOAD
1000 TO 1012 1024 1031 TO 1036 3103 3104 3120 3123 UNI GY -15.82
2023 TO 2025 2135 2136 2146 UNI GY -8.1
2000 TO 2007 2018 TO 2022 2028 2029 2040 2055 2056 2071 2089 2101 2110 2154 -
2170 2173 2176 2193 3072 3078 3082 3090 UNI GY -3.77
1013 TO 1017 1030 1037 1039 TO 1041 UNI GY -24.76
3003 3010 UNI GY -4.524
3004 3011 UNI GY -2.4505
3000 3001 3007 3008 3012 3013 UNI GY -7.62
3002 3009 3014 UNI GY -2.45
JOINT LOAD
3000 3004 FY -8.71
3001 3005 FY -22.23
3002 3006 FY -5.87
3002 3006 FY -8.66
3003 3007 FY -10
3008 FY -15.74
3009 FY -18.65
MEMBER LOAD
3005 CON GY -41.71 5.44
3006 CON GY -11.1 5.44
3006 CON GY -16.4 5.44
FLOOR LOAD
_CATWALK FLOAD -0.725 GY
END DEFINE REFERENCE LOADS
FLOOR DIAPHRAGM
DIA 1 TYPE RIG HEI 3.2
DIA 2 TYPE RIG HEI 6.55
DIA 3 TYPE RIG HEI 10.785
DEFINE UBC LOAD
ZONE 0.4 I 1 RWX 6 RWZ 6 STYP 4 CT 0.0853 NA 1.5 NV 2
REFERENCE LOAD Y
R1 1.0 R2 1.0
LOAD 1 LOADTYPE Seismic  TITLE EQX
UBC LOAD X 1 DEC 1 ACC 0.05
PERFORM ANALYSIS PRINT LOAD DATA
CHANGE
LOAD 2 LOADTYPE Seismic  TITLE EQZ
UBC LOAD Z 1 DEC 1 ACC 0.05
CHANGE
LOAD 3 LOADTYPE Dead  TITLE DL1
REFERENCE LOAD
R1 1.0
LOAD 4 LOADTYPE Dead  TITLE DL2
REFERENCE LOAD
R2 1.0
LOAD 5 LOADTYPE Live  TITLE LL1
ONEWAY LOAD
_VIEW_DECK ONE -1.9 GY
_CABLE_TRAY ONE -1.9 GY
_CATWALK FLOAD -0.475 GY
FLOOR LOAD
_ROOF_TUNNEL FLOAD -0.96 GY
LOAD 6 LOADTYPE Roof Live  TITLE LLR
JOINT LOAD
3000 3004 FY -8.146
3001 3005 FY -18.909
3002 3006 FY -5.241
3002 3006 FY -7.573
3003 3007 FY -9.801
3008 FY -16.26
3009 FY -19.6
MEMBER LOAD
3005 CON GY -37.89 5.44
3006 CON GY -10.45 5.44
3006 CON GY -15.15 5.44
*TABLE 1 - LRFD DESIGN LOAD COMBINATION - FOR STEEL ELEMENTS (BEAMS, COLUMNS,
* BRACINGS) AND STEEL JOINT CONNECTIONS
LOAD COMB 101 1.4DL
3 1.4 4 1.4
LOAD COMB 102 1.2DL + 1.6LL + 0.5LLR
3 1.2 4 1.0 5 1.6 6 0.5
LOAD COMB 103 1.2DL + 1.6LLR + F1LL
3 1.2 4 1.2 5 0.5 6 1.6
* X DIRECTION SEISMIC LOAD COMBO (DIRECT + ORTHOGONAL)
LOAD COMB 104 1.42(DL1 + DL2) + 0.5LL1 + 0.5LLR + 1.0EX + 0.3EZ
3 1.42 4 1.42 5 0.5 6 0.5 1 1.0 2 0.3
LOAD COMB 105 1.42(DL1 + DL2) + 0.5LL1 + 0.5LLR + 1.0EX - 0.3EZ
3 1.42 4 1.42 5 0.5 6 0.5 1 1.0 2 -0.3
LOAD COMB 106 1.42(DL1 + DL2) + 0.5LL1 + 0.5LLR - 1.0EX + 0.3EZ
3 1.42 4 1.42 5 0.5 6 0.5 1 -1.0 2 0.3
LOAD COMB 107 1.42(DL1 + DL2) + 0.5LL1 + 0.5LLR - 1.0EX - 0.3EZ
3 1.42 4 1.42 5 0.5 6 0.5 1 -1.0 2 -0.3
* Z DIRECTION SEISMIC LOAD COMBO (DIRECT + ORTHOGONAL)
LOAD COMB 108 1.42(DL1 + DL2) + 0.5LL1 + 0.5LLR + 1.0EZ + 0.3EX
3 1.42 4 1.42 5 0.5 6 0.5 1 0.3 2 1.0
LOAD COMB 109 1.42(DL1 + DL2) + 0.5LL1 + 0.5LLR + 1.0EZ - 0.3EX
3 1.42 4 1.42 5 0.5 6 0.5 1 -0.3 2 1.0
LOAD COMB 110 1.42(DL1 + DL2) + 0.5LL1 + 0.5LLR - 1.0EZ + 0.3EX
3 1.42 4 1.42 5 0.5 6 0.5 1 0.3 2 -1.0
LOAD COMB 111 1.42(DL1 + DL2) + 0.5LL1 + 0.5LLR - 1.0EZ - 0.3EX
3 1.42 4 1.42 5 0.5 6 0.5 1 -0.3 2 -1.0
LOAD COMB 112 0.68(DL1 + DL2) + 1.0EX + 0.3EZ
3 0.68 4 0.68 1 1.0 2 0.3
LOAD COMB 113 0.68(DL1 + DL2) + 1.0EX - 0.3EZ
3 0.68 4 0.68 1 1.0 2 -0.3
LOAD COMB 114 0.68(DL1 + DL2) - 1.0EX + 0.3EZ
3 0.68 4 0.68 1 -1.0 2 0.3
LOAD COMB 115 0.68(DL1 + DL2) - 1.0EX - 0.3EZ
3 0.68 4 0.68 1 -1.0 2 -0.3
LOAD COMB 116 0.68(DL1 + DL2) + 1.0EZ + 0.3EX
3 0.68 4 0.68 2 1.0 1 0.3
LOAD COMB 117 0.68(DL1 + DL2) + 1.0EZ - 0.3EX
3 0.68 4 0.68 2 1.0 1 -0.3
LOAD COMB 118 0.68(DL1 + DL2) - 1.0EZ + 0.3EX
3 0.68 4 0.68 2 -1.0 1 0.3
LOAD COMB 119 0.68(DL1 + DL2) - 1.0EZ - 0.3EX
3 0.68 4 0.68 2 -1.0 1 -0.3
* SEISMIC DRIFT CHECK LOAD COMBINATION
LOAD COMB 201 1.2(DL1 + DL2) + 0.5LL1 + 0.5LLR + 1.0EX + 0.3EZ
3 1.2 4 1.2 5 0.5 6 0.5 1 1.0 2 0.3
LOAD COMB 202 1.2(DL1 + DL2) + 0.5LL1 + 0.5LLR + 1.0EX + 0.3EZ
3 1.2 4 1.2 5 0.5 6 0.5 1 1.0 2 -0.3
LOAD COMB 203 1.2(DL1 + DL2) + 0.5LL1 + 0.5LLR - 1.0EX + 0.3EZ
3 1.2 4 1.2 5 0.5 6 0.5 1 -1.0 2 0.3
LOAD COMB 204 1.2(DL1 + DL2) + 0.5LL1 + 0.5LLR - 1.0EX + 0.3EZ
3 1.2 4 1.2 5 0.5 6 0.5 1 -1.0 2 -0.3
LOAD COMB 205 1.2(DL1 + DL2) + 0.5LL1 + 0.5LLR + 1.0EZ + 0.3EX
3 1.2 4 1.2 5 0.5 6 0.5 2 1.0 1 0.3
LOAD COMB 206 1.2(DL1 + DL2) + 0.5LL1 + 0.5LLR + 1.0EZ - 0.3EX
3 1.2 4 1.2 5 0.5 6 0.5 2 1.0 1 -0.3
LOAD COMB 207 1.2(DL1 + DL2) + 0.5LL1 + 0.5LLR - 1.0EZ + 0.3EX
3 1.2 4 1.2 5 0.5 6 0.5 2 -1.0 1 0.3
LOAD COMB 208 1.2(DL1 + DL2) + 0.5LL1 + 0.5LLR - 1.0EZ - 0.3EX
3 1.2 4 1.2 5 0.5 6 0.5 2 -1.0 1 -0.3
LOAD COMB 209 0.9(DL1 + DL2) + 1.0EX + 0.3Z
3 0.9 4 0.9 1 1.0 2 0.3
LOAD COMB 210 0.9(DL1 + DL2) + 1.0EX - 0.3Z
3 0.9 4 0.9 1 1.0 2 -0.3
LOAD COMB 211 0.9(DL1 + DL2) - 1.0EX + 0.3Z
3 0.9 4 0.9 1 -1.0 2 0.3
LOAD COMB 212 0.9(DL1 + DL2) - 1.0EX - 0.3Z
3 0.9 4 0.9 1 -1.0 2 -0.3
LOAD COMB 213 0.9(DL1 + DL2) + 1.0EZ + 0.3EX
3 0.9 4 0.9 2 1.0 1 0.3
LOAD COMB 214 0.9(DL1 + DL2) + 1.0EZ - 0.3EX
3 0.9 4 0.9 2 -1.0 1 -0.3
LOAD COMB 215 0.9(DL1 + DL2) - 1.0EZ + 0.3EX
LOAD COMB 216 0.9(DL1 + DL2) - 1.0EZ - 0.3EX
* LRFD DESIGN LOAD COMBINATION - REINFORCED CONCRETE (BEAMS, COLUMNS AND WALLS)
LOAD COMB 301 1.4DL
3 1.4 4 1.4
LOAD COMB 302 1.2DL + 1.6LL
3 1.2 4 1.2 5 1.6
LOAD COMB 303 1.2DL + F1LL
3 1.2 4 1.2 5 0.5
LOAD COMB 304 1.42(DL1 + DL2) + 0.5LL1 + 1.0EX + 0.3EZ
3 1.42 4 1.42 5 0.5 1 1.0 2 0.3
LOAD COMB 305 1.42(DL1 + DL2) + 0.5LL1 + 1.0EX - 0.3EZ
3 1.42 4 1.42 5 0.5 1 1.0 2 -0.3
LOAD COMB 306 1.42(DL1 + DL2) + 0.5LL1 - 1.0EX + 0.3EZ
3 1.42 4 1.42 5 0.5 1 -1.0 2 0.3
LOAD COMB 307 1.42(DL1 + DL2) + 0.5LL1 - 1.0EX - 0.3EZ
3 1.42 4 1.42 5 0.5 1 -1.0 2 -0.3
LOAD COMB 308 1.42(DL1 + DL2) + 0.5LL1 + 1.0EZ + 0.3EX
3 1.42 4 1.42 5 0.5 1 0.3 2 1.0
LOAD COMB 309 1.42(DL1 + DL2) + 0.5LL1 + 1.0EZ - 0.3EX
3 1.42 4 1.42 5 0.5 1 -0.3 2 1.0
LOAD COMB 310 1.42(DL1 + DL2) + 0.5LL1 - 1.0EZ + 0.3EX
3 1.42 4 1.42 5 0.5 1 0.3 2 -1.0
LOAD COMB 311 1.42(DL1 + DL2) + 0.5LL1 - 1.0EZ - 0.3EX
3 1.42 4 1.42 5 0.5 1 -0.3 2 -1.0
LOAD COMB 312 1.12(DL1 + DL2) + 1.0EX + 0.3EZ
3 1.12 4 1.12 1 1.0 2 0.3
LOAD COMB 313 1.12(DL1 + DL2) + 1.0EX - 0.3EZ
3 1.12 4 1.12 1 1.0 2 -0.3
LOAD COMB 314 1.12(DL1 + DL2) - 1.0EX + 0.3EZ
3 1.12 4 1.12 1 -1.0 2 0.3
LOAD COMB 315 1.12(DL1 + DL2) - 1.0EX - 0.3EZ
3 1.12 4 1.12 1 -1.0 2 -0.3
LOAD COMB 316 1.12(DL1 + DL2) + 1.0EZ + 0.3EX
3 1.12 4 1.12 1 0.3 2 1.0
LOAD COMB 317 1.12(DL1 + DL2) + 1.0EZ - 0.3EX
LOAD COMB 318 1.12(DL1 + DL2) - 1.0EZ + 0.3EX
3 1.12 4 1.12 1 0.3 2 -1.0
LOAD COMB 319 1.12(DL1 + DL2) - 1.0EZ - 0.3EX
3 1.12 4 1.12 1 -0.3 2 -1.0
LOAD COMB 320 0.68(DL1 + DL2) + 1.0EX + 0.3EZ
LOAD COMB 321 0.68(DL1 + DL2) + 1.0EX - 0.3EZ
LOAD COMB 322 0.68(DL1 + DL2) - 1.0EX + 0.3EZ
LOAD COMB 323 0.68(DL1 + DL2) - 1.0EX - 0.3EZ
LOAD COMB 324 0.68(DL1 + DL2) + 1.0EZ + 0.3EX
LOAD COMB 325 0.68(DL1 + DL2) + 1.0EZ - 0.3EX
LOAD COMB 326 0.68(DL1 + DL2) - 1.0EZ + 0.3EX
LOAD COMB 327 0.68(DL1 + DL2) - 1.0EZ - 0.3EX
* SERVICE LOAD COMBINATION - FOR FOOTING DESIGN
LOAD COMB 401 1.0(DL1 + DL2) + 1.0(LL1 + LLR)
3 1.0 4 1.0 5 1.0 6 1.0
LOAD COMB 402 1.0(DL1 + DL2) + 0.75(LL1 + LLR) + 0.535EX
3 1.0 4 1.0 5 0.75 6 0.75 1 0.535
LOAD COMB 403 1.0(DL1 + DL2) + 0.75(LL1 + LLR) - 0.535EX
3 1.0 4 1.0 5 0.75 6 0.75 1 -0.535
LOAD COMB 404 1.0(DL1 + DL2) + 0.75(LL1 + LLR) + 0.535EZ
3 1.0 4 1.0 5 0.75 6 0.75 2 0.535
LOAD COMB 405 1.0(DL1 + DL2) + 0.75(LL1 + LLR) - 0.535EZ
3 1.0 4 1.0 5 0.75 6 0.75 2 -0.535
LOAD COMB 406 0.6(DL1 + DL2) + 0.7EX
3 1.0 4 1.0 1 0.7
LOAD COMB 407 0.6(DL1 + DL2) - 0.7EX
3 1.0 4 1.0 1 -0.7
LOAD COMB 408 0.6(DL1 + DL2) + 0.7EZ
3 1.0 4 1.0 2 0.7
LOAD COMB 409 0.6(DL1 + DL2) - 0.7EZ
3 1.0 4 1.0 2 -0.7
LOAD COMB 410 1.0(DL1 + DL2) + 1.0(LL1 + LLR) + 0.71EX
3 1.0 4 1.0 5 1.0 6 1.0 1 0.71
LOAD COMB 411 1.0(DL1 + DL2) + 1.0(LL1 + LLR) - 0.71EX
3 1.0 4 1.0 5 1.0 6 1.0 1 -0.71
LOAD COMB 412 1.0(DL1 + DL2) + 1.0(LL1 + LLR) + 0.71EZ
3 1.0 4 1.0 5 1.0 6 1.0 2 0.71
LOAD COMB 413 1.0(DL1 + DL2) + 1.0(LL1 + LLR) - 0.71EZ
3 1.0 4 1.0 5 1.0 6 1.0 2 -0.71
* ULTIMATE LOAD COMBINATION - FOR FOOTING DESIGN
LOAD COMB 501 1.4(DL1 + DL2)
3 1.4 4 1.4
LOAD COMB 502 1.2(DL1 + DL2) + 1.6(LL1) + 0.5LLR
3 1.2 4 1.2 5 1.6 6 0.5
LOAD COMB 503 1.2(DL1 + DL2) + 1.6LLR + 0.5LL1
3 1.2 4 1.2 6 1.6 5 0.5
LOAD COMB 504 1.2(DL1 + DL2) + 0.5LL1 + 0.5LLR + 1.0EX
LOAD COMB 505 1.2(DL1 + DL2) + 0.5LL1 + 0.5LLR - 1.0EX
LOAD COMB 506 1.2(DL1 + DL2) + 0.5LL1 + 0.5LLR + 1.0EZ
LOAD COMB 507 1.2(DL1 + DL2) + 0.5LL1 + 0.5LLR - 1.0EZ
LOAD COMB 508 0.9(DL1 + DL2) + 1.0EX
3 0.9 4 0.9 1 1.0
LOAD COMB 509 0.9(DL1 + DL2) - 1.0EX
3 0.9 4 0.9 1 -1.0
LOAD COMB 510 0.9(DL1 + DL2) + 1.0EZ
3 0.9 4 0.9 2 1.0
LOAD COMB 511 0.9(DL1 + DL2) - 1.0EZ
3 0.9 4 0.9 2 -1.0
* ALL LOAD COMBINATIONS END HERE
PERFORM ANALYSIS
CHANGE
PERFORM ANALYSIS
DEFINE ENVELOPE
101 TO 119 ENVELOPE 1000 TYPE STRENGTH
201 TO 216 ENVELOPE 2000 TYPE SERVICEABILITY
301 TO 327 ENVELOPE 3000 TYPE STRENGTH
401 TO 413 ENVELOPE 4000 TYPE SERVICEABILITY
501 TO 511 ENVELOPE 5000 TYPE STRENGTH
END DEFINE ENVELOPE
LOAD LIST 101 TO 119 301 TO 327
PRINT STORY DRIFT 0.005950
PRINT DIA CR
CHECK SOFT STORY ASCE7
*STEEL DESIGN
CHANGE
PARAMETER 1
CODE AISC UNIFIED 2010
METHOD LRFD
FYLD 248000 MEMB 100 TO 147 164 165 200 TO 206 209 TO 212 215 TO 225 -
300 TO 317 1000 TO 1017 1024 TO 1041 1050 TO 1053 2000 TO 2025 2028 TO 2040 -
2097 2099 TO 2110 2113 2114 2118 TO 2128 2131 2133 TO 2146 2152 2154 2156 -
2159 2161 TO 2164 2166 TO 2171 2173 2174 2176 TO 2201 2203 TO 2270 -
3000 TO 3014 3017 TO 3040 3042 TO 3055 3072 TO 3127
LZ 9.35 MEMB 1000 1002 1015 1017 1024 1039 1041 2000 2002 2023 2025 2030 2032 -
2033 2035 2037 2038 2047 2049 2050 2052 2057 2058 2073 2092 2100 2101 2103 -
2104 2110 2113 2119 2120 2124 2126 2128 2136 2137 2139 2141 2146 2154 2159 -
2231 2246 TO 2249 2258 TO 2263 3007 3009 3012 3014 3103 3120
LZ 10.9 MEMB 1013 1014 1030 1037
LZ 5.45 MEMB 3003 TO 3006 3010 3011 3017 3018
LZ 5.75 MEMB 1011 1012 1033 1036 2007 2012 2017 2022 2028 2029 2083 2097
LZ 6 MEMB 1006 TO 1010 1031 1032 1034 1035 2004 2005 2009 2011 2014 TO 2016 -
2019 TO 2021 2054 2056 2063 2064 2070 2071 2080 2081 2088 TO 2090 2173 2181 -
2190 2203 3078 3082 3123
LZ 9 MEMB 1016 1040 2001 2024 2031 2034 2036 2039 2040 2048 2051 2060 2068 -
2072 2091 2099 2102 2105 2121 2125 2127 2135 2138 2140 2176 TO 2178 2187 -
2188 2193 TO 2195 2206 2207 2209 2210 2212 TO 2215 2230 TO 2232 2234 2236 -
2237 3008 3013
LZ 5.7 MEMB 2003 2008 2013 2018 2044 2053 2055 2166 2170 3072
LZ 2.798 MEMB 2169 2180 2185 3074
LY 9 MEMB 2024 2031 2034 2036 2039 2048 2051 2060 2068 2072 2091 2099 2102 -
2105 2121 2125 2127 2135 2138 2140 2177 2178 2182 2183 2187 2188 -
2194 TO 2196 2200 2206 2207 2209 2210 2212 TO 2215 2230 TO 2232 2234 2236 -
2237 3101
LY 9.35 MEMB 2023 2025 2030 2032 2033 2035 2037 2038 2047 2049 2050 2052 2057 -
2058 2073 2092 2100 2103 2104 2113 2119 2120 2124 2126 2128 2136 2137 2139 -
2141 2146 2159 2174 2204 2205 2246 TO 2249 2258 TO 2263 3087
LY 4.675 MEMB 1024 3120
LY 5.75 MEMB 2012 2017 2083 2097
LY 6 MEMB 2004 2009 TO 2011 2014 TO 2016 2054 2063 2064 2069 2070 2080 2081 -
2088 2090 2181 2190 2203 3078
LY 5.7 MEMB 2003 2008 2013 2018 2044 2053 2055 2166 2170 3072
LY 2.798 MEMB 2169 2180 2185 3074
LY 5.45 MEMB 3003 TO 3006 3010 3011 3017 3018
LY 7.585 MEMB 101 102 201 202
LZ 7.585 MEMB 104 TO 108 120 TO 124 204 TO 206 209 TO 212 215 TO 217
CHECK CODE MEMB 100 TO 147 164 165 200 TO 206 209 TO 212 215 TO 225 -
STEEL MEMBER TAKE OFF LIST 100 TO 147 164 165 200 TO 206 209 TO 212 -
215 TO 225 300 TO 317 1000 TO 1017 1024 TO 1041 1050 TO 1053 2000 TO 2025 -
2028 TO 2040 2044 2047 TO 2058 2060 2063 2064 2068 TO 2073 2080 2081 2083 -
2088 TO 2092 2097 2099 TO 2110 2113 2114 2118 TO 2128 2131 2133 TO 2146 2152 -
2154 2156 2159 2161 TO 2164 2166 TO 2171 2173 2174 2176 TO 2201 2203 TO 2270 -
*CONCRETE DESIGN
LOAD LIST ENV 3000
START CONCRETE DESIGN
CODE ACI
DESIGN COLUMN 3128 TO 3155
DESIGN BEAM 3156 TO 3200
TRACK 1 MEMB 3128 TO 3200
FYSEC 276000 MEMB 3128 TO 3200
FYMAIN 415000 MEMB 3128 TO 3200
FC 20700 MEMB 3128 TO 3200
END CONCRETE DESIGN
FINISH
Parents Reply Children