RAM Concept Shear Reinforcement Section Design

Hi,

I'm trying to get a deeper understanding of why RAM Concept is showing my shear requirement as being larger than the same beam I have modelled in RAPT to verify. RAPT does not require any additional shear reinforcement. I have checked the shear core and that seems to be OK.

As an example, I have been looking at design section 24C-2, section 2 in the model I have uploaded via secure link and have the following questions:

1. Why is the design section minimum demand (-1427kN) significantly larger than the design strip maximum shear in this span (-533kN)? What does the design section demand mean?

2. From the cross section audit Envelope 7 of the Final Design Check for Strength design, phi Vuc = 0.75 x 2043kN = 1530kN > 1427kN. Why is shear reinforcement added when capacity > demand and what determines that they need to be closed ligs?

3. Why is there bottom reinforcement required at the column at this location rather than at mid-span if anywhere? Similar question applies to the beam in the north-eastern corner of the building.

Regards

Parents Reply Children
  • Thank you for the model.

    1) The section is subject to torsion. The higher shear force is the equivalent factored shear force (Veq*), which accounts for both the applied shear and torsion. The lower value excludes the contribution of torsion.

    2) Minimum transverse shear reinforcement is required per 8.2.1.6 because torsion exceeds 0.25*phi*Tcr. Closed ligs are detailed because the section is designed for torsion.

    3) The bottom reinforcement is added to resist the longitudinal shear-torsion tension (deltaFtd, see 8.2.7). The torsion demand is a key contributor to the shear-torsion tension requirement.