Side face blowout for group of anchors in tension RAM Connection
Hi!
I am having some issues with the calculations for side-face blowoutfor a group of anchors.
I have that base plate.
A 650x650 mm pedestal, and a 470x470 base plate with 8 anchors.
(I don´t know why, but i can´t upload images right now)
This are the coordinates of the anchors.
1 -175 -175 13.18 92.96
2 -175 0 13.18 78.73
3 -175 175 13.18 64.5
4 175 -175 13.18 91.25
5 175 0 13.18 77.02
6 175 175 13.18 62.79
7 0 -175 13.18 92.1
8 0 175 13.18 63.64
As you can seeall the anchors have the same Ca1.
And all of them are tensioned.
When RAM Connection does the verification, it doesn´t compare with the total tension (the sum of the tension in each anchor) that would be 623 kN.
It compares with the sum of tensions in anchors "1", "4" and "7" (276.31 kN)
I wolud say that it is wrong.
Side-face blowout of group of anchors in tension [kN] 409.21 276.31 LC-341-78 0.68 Eq. D-17, Sec. D.4.1.1
SideFaceBlowoutApply = hef>2.5*ca1 = 450 [mm] >2.5*150 [mm] = True Sec. D.5.4.1
Abrg = F2 - Ag = 46 [mm] 2 - 707 [mm2] = 1409 [mm2]
Nsb = 160*ca1*(Abrg)1/2*l*(fc/(1 [psi] ))1/2 [psi] = 160*150 [mm] *(1409 [mm2] )1/2*1*(27.579 [N/mm2] /(1 [psi] ))1/2 [psi] = 392.84 [kN] Eq. D-17
Nsbg = (1 + s/(6*ca1))*Nsb = (1 + 350 [mm] /(6*150 [mm] ))*392.84 [kN] = 545.611 [kN] Eq. D-18
HighSeismicDesignCategory ® False
fNsbg = f*Nsbg = 0.75*545.611 [kN] = 409.208 [kN]
The ACI318 says that you must compare only with the sum of the tensions of anchors that are near the edges. But in this case i think that would be all of them.
Any ideas?
Tanks to all!