Hi There,
I have a question about RAM Concepts usage of minimum radius parameter when it comes to post tension cable curvatures (dealing mostly with flat ducts containing 12.7mm/15.8mm strand tendons here in Aus). We have noticed that for same radius we get error in RAM Concept but we do not get that error in RAPT. For example, RAPT recommends minimum reverse curve radius of 2500mm with default being 5000mm. I have set the curve radius to match that of RAPT i.e. 2500mm but tendon radius errors is still persistent. Could you please explain why for the same radius the profile is acceptable to RAPT but not to RAM Concept. See below (note RAPT is allowing this profile on 5000mm radius):
Quick run of 1m deep beam with 9m span
Room for improvement: Sean Smith mentioned this before but could you guys make it so that we can at least see the radius of tendons on top of them like we can see other properties of tendon. The other thing is can you add a function that with click of a button gives you the lowest allowable low point based on minimum radius.