Shell Interfaces in RAM Elements

Just getting the hang of Elements and was trying to model a shear wall in a steel frame and I am having trouble figuring out and applying the shell interfaces properly so the wall only attracts the in-plane lateral loads and not the vertical loads from the beams and column. I have tried a few combinations but the vertical loads are still be being transmitted to the wall and not thru the beam and columns that the shell is bordered by.

Parents
  • I have the same question. Does it have something to do with only allowing the shell to accept tensile loads? How is that done?
  • Please refer to the attached model. The frame on the left consists of a steel moment frame with a concrete wall. A Type 1 shell interface is modeled, which will allow only shear transfer across the interface so that gravity loads are resisted by the steel frame and the lateral loads are dragged into the stiffer shell. The frame on the right is the steel moment frame only, and is modeled to compare forces with the frame with the shell interface. Each frame is modeled with a vertical 2 kip/ft distributed load along the beam and a 10 K lateral load a the top of the frame.

    When viewing shears and moments in the beam and column, you will see that the forces in the frames are nearly identical (differences due to the gaps associated with the interface). The screen capture below shows the moment diagrams for each frame.

    The sum of the TX reactions at the finite element nodes at the base of the shell equals 10 k, which shows that the entire lateral load is dragged into the concrete wall.

    1.37 + 1.52 + 1.61 + 1.55 + 1.42 + 1.23 + 1.29 = 9.99 k

    Shell Interface Example.etz



    Answer Verified By: Seth Guthrie 

  • There are shell interfaces that transfer compression forces only. However, there is not a shell interface that will transfer only tension loads across the interface.



  • Hi Karl, thanks for the example model. I'm trying to do something similar, but cannot figure out how to add the interface. Once I select the shell, click add interfaces, then type I, it asks for the interface size. What are these beam and column dimensions in reference to? Also, I noticed in your example model, each corner of the left frame has (4) nodes each. Why is that?
    Thanks
Reply Children
  • Lauren, think of the interface as a gap between the frame and the shell. The interface type controls which forces are exchanged between the frame and shell across this separation. The 4 nodes correspond to the beam and column interface sizes that are entered when the interface is created. If 0.5 in is entered for both, then an intermediate node is created at a distance of 0.5 along each measured from the beam-column joint to facilitate the interface. The shell is meshed to nodes that are offset 0.5 in from the beam and column in that case and not to the intermediate finite element nodes that are added along the beam and column.



    Answer Verified By: Seth Guthrie