• RAM v13.9 Max shear plate length

    Hello, I would like to confirm on how RAM calculates the max length of shear plate. In my manual calculation Max shear plate length Lmax=d-dct-dcb Beam used in the image below was W10X33 (d=9.75) Lmax = 9.75 - 2.0 - 1.75 = 6.0 However, RAM gives 5.73…
  • Bolted Beam Splice Connection

    Below is an image of a bolted beam splice connection that I'm working on. RAM Connection considers the eccentricity of the bolt group to be 3.125in and the coefficient for eccentrically loaded bolt groups to be 8. I believe that the eccentricity…
  • BG splice connection warning

    I got this warning while designing beam splice connection (apex): - The connection does not comply with the section depth limits (AISC Design Guide 16 - Table 4-7) My question is that can I ignore this warning given that my connections have no other…
  • RAM Connection Design For Only Load Combinations