Centroid Stress Plan inaccurate compared to hand calc P/A
Gueorgui Ivanov
For context working on a 8in PT slab. In the banded direction in my interior bays I have 24 strands (26.8 kip/strand) for a trib width of 29 ft. Thus I have a stress of 230 psi (24'*26.8kip/ft / (28'*12*8")). When I look at Centroid stress plan under…
1 month ago
RAM | STAAD | ADINA
RAM | STAAD Forum
Instability in Slab Joint
Ryan Hill
Hi, I am getting 2 warnings. Both are about instability in a joint in the My direction. The joints are highlighted in red in the following image. The joints highlighted are in the middle of the slabs. I have pinned the slab edges. Why are these…
3 months ago
RAM | STAAD | ADINA
RAM | STAAD Forum
Modelling an Elevated Slab as Plates in combination with Floor Diaphragm Command
Alain Torre
Good day. I understand that for rigid diaphragm slab action, you are NOT required to model the slab as plates if you are to use the Floor Diaphragm command. But for this frame structure that I am working with, there are certain floor loads that…
9 months ago
RAM | STAAD | ADINA
RAM | STAAD Forum
One-way ribbed slab
Waleed Aboukhater
How can i design a this kind of slab on staad pro, i'm still a new user of the software so please put some detail to help me.
over 1 year ago
RAM | STAAD | ADINA
RAM | STAAD Forum
Two-Way and One-Way Slab Modeling
Eric Feuge-Miller
In RAM SS, I've previously come across a "Fatal Error" in RAM Frame. This prevents the program from opening Frame, and the cause is related to two slabs in the model. Both are One-Way slabs that are supported on one side by a continuous beam, and by a…
Answered
over 1 year ago
RAM | STAAD | ADINA
RAM | STAAD Forum
SLAB LOAD COMBINATIONS ARE NOT LOADED IN RCDC
Ignacio Rojas
Hello, I have modeled a wall that rests on a slab on four beams and when going to the RCDC I do not see the option of being able to load the slab with the load combination created in STAAD, which is, by the way: All I see in RCDC is this: Instead, as…
over 2 years ago
RAM | STAAD | ADINA
RAM | STAAD Forum
Trimming Design Strips: Ram Concept 2-Way PT Slab
Eric Feuge-Miller
Given the layout of strips, in odd configurations due to irregular structural geometries, is it in y'all's opinion reasonable to review the original strips for any code-related failures (i.e. shear or tension) and make the proper adjustments to the PT…
Answered
over 2 years ago
RAM | STAAD | ADINA
RAM | STAAD Forum
STAAD - Modeling a Slab - Why I am getting a lower moment?
Akam
Hello, I am new to STAAD and this forum, and this is my first post! I wanted to model an 8.67' X 31.5’ Slab with a 16,000 lb. load applied at the center. The slab will have fixed ends at all sides. As a “one-way slab”, the expected max moment utilizing…
over 2 years ago
RAM | STAAD | ADINA
RAM | STAAD Forum
How do I analyze the Slab Loads on this?
Sidharth Reddy
I have attached a picture of a plan where a clear head room without beams is to be provided. G+3 building with common portal frame. I am unable to assign floor loads as there is no closed boundary.
Answered
over 2 years ago
RAM | STAAD | ADINA
RAM | STAAD Forum
Dummy beam
Sulaiman Ade
Hello Everyone. I create a dummy beam with density=0 and E=0 (Figure.1) then I assign the beam (Figure.2) then Staad Error occurs( ***ERROR*** MATERIAL NAME MUST NOT CONTAIN ANY BLANK SPACE )(Figure.3), What is the solution?
Answered
over 2 years ago
RAM | STAAD | ADINA
RAM | STAAD Forum
I want to use RCC floor slab effect on the steel structure of an industrial building. Shall I use master slave command or shall I use floor diaphram command?
gaurav vijay
steel quantities especially column size get reduce while considering the rigidity of RCC floor into account. what shall be right approach to consider its effect.
over 2 years ago
RAM | STAAD | ADINA
RAM | STAAD Forum
How does STAAD determine beam deflections?
Pascual Mauricio
Hello, I am modeling a floor slab (1 ft thick) with concrete beams (all 24" wide x 36" deep). These beams will be cast monolithically with the floor slab, therefore the beams are modeled as 24" deep. My question is how does STAAD determine the following…
over 3 years ago
RAM | STAAD | ADINA
RAM | STAAD Forum
Can I design a Continuous two slabs by using RCDC STAAD?
Sulaiman Ade
Hello Sir RCDC is designed and Detailed all the slab one by one but I want to detail all Top and Bottom Reinforcement of the two-way slab once, what should I do.
Answered
over 3 years ago
RAM | STAAD | ADINA
RAM | STAAD Forum
ACI 318 SLAB CHECKS
SILVIA CONTI
Googevening, performing concrete slab verification with staad pro (ACI Code), I noticed some discrepancies between input data definition, as reported below: and output results obtanained from calculations are listed below: in particular the…
Answered
over 3 years ago
RAM | STAAD | ADINA
RAM | STAAD Forum
Warning - Instability at Joint
Pascual Mauricio
Hello, I am getting a warning at a joint that is not restrained. It is an element near a pin support. This model is for a roof slab. I am not sure how to resolve the warning. Any help would be appreciated. Thanks, Pascual 1108.GLM Childrens…
over 3 years ago
RAM | STAAD | ADINA
RAM | STAAD Forum
1 way shear effective depth calculation
Jessica Dineen
I have an existing two-way slab that I am trying to analyze. At locations of negative bending, the effective depth for one way shear calculations is much smaller than I'm calculating it to be by hand. Based on the value that the audit is showing, it…
Answered
over 3 years ago
RAM | STAAD | ADINA
RAM | STAAD Forum
Column and Wall Rigid Zone
Jiannan Wang
Hi, I am reading a post about modeling in RAM Concept. One of the questions mentioned rigid zones at columns and walls. See the snapshot below: My question is what stiffness factors one should use for these rigid zones: Thank you.
over 4 years ago
RAM | STAAD | ADINA
RAM | STAAD Forum
Results Along Line - Exporting a Moment diagram of a section.
Matt C 17
Hi I have been asked to take a cross section diagram of a slab's moment diagram and need to be able to use this within my report. How can I do this and can I add detail to the basic diagram which appears at the first instance when taking a cut of results…
over 4 years ago
RAM | STAAD | ADINA
RAM | STAAD Forum
STAAD RCDC IMPOSED LOAD
BentleyUser User1
While designing reinfoced concrete slab in RCDC it asks for the Imposed Load and Live Load to fill out; it doesnt collect the load data from STAAD model. Should include the self weight of the slab in the IMPOSED LOAD or program calculates and adds the…
over 4 years ago
RAM | STAAD | ADINA
RAM | STAAD Forum
Shear Capacity of Slab
Edward Pigozzo
Hi, In RAM concept it shows you a shear plan required for the reinforcing. I understand that these shear bars are shown over columns because of punching shear. If it is not shown over a column or a concentrated load from above, does this mean the…
Answered
over 5 years ago
RAM | STAAD | ADINA
RAM | STAAD Forum
Slab Design by plate.
Tapon Chakrabarti
I can not add plate to this area. Im not under standing this. How to add plate here for design of slab?
Answered
over 5 years ago
RAM | STAAD | ADINA
RAM | STAAD Forum
GEOMETRY PROBLEMS
GAURAV GOSWAMI
I am new in staad pro so please answer this question in very easy language....! what is differences between plates and surfaces. if i want to make slab or floor i can use both of these which one is correct for floor or slabs... and what type of…
Answered
over 5 years ago
RAM | STAAD | ADINA
RAM | STAAD Forum
RAM Structural System modeler - Gable roof warehouse slab edges and decks
WILLIAM MOORHEAD
Do I need to put separate slab edges on gable roof planes on opposite sides of a ridge, and if so, then is there a trick to getting this done? I can put in one perimeter of slab edges, with one of the four edges coinciding with the beam at the ridge,…
Answered
over 5 years ago
RAM | STAAD | ADINA
RAM | STAAD Forum
Error - No punch cutoff sections found
Liam Bryant
Hi, I'm a relatively new user and having an issue with the error message below; It is happening for all of my edge columns. I've played with the geometry, trying a flat slab, with an edge thickening and varied the punching shear "maximum search radius…
Answered
over 5 years ago
RAM | STAAD | ADINA
RAM | STAAD Forum
Pipe Rack + Vertical Vessel Slab design in Staad Pro
Jorge Ochoa León
Dear Community, I´m designing a slab foundation mat for a pipe rack and some vertical vessel, I have already designed the structure with STAAD Pro, and now I’d like to attack the model some plates “mesh” and estimate the base pressure, overturning…
over 5 years ago
RAM | STAAD | ADINA